Which Cummins?

On Sat, Nov 9, 2024 at 4:59 AM Mac Lewis via RE-wrenches <
[email protected]> wrote:

> Hi Jim,
>
> I think the voltage regulator on the generator is the issue, but you may
> be able to fix it by trying a different AC input mode.  What is the AC
> input mode are you using on the Radians?  Are the modes the same on each
> Radian?  Since you have a range of input that you can get it to hiccup, I'd
> try playing with the AC input modes through the problematic range.  I tend
> to use support mode with the least trouble.
>
> What are the downstream loads?
>
> I could see perhaps how a downstream load that is large and inductive and
> shuts down rapidly could cause a voltage spike, but really the voltage
> regulator is in charge of that.
>
> ANother thing to check is torque/corrosion on your connections.  I like to
> use an IR camera to speed up looking for connection issues.
>
> Let us know what you find out.
>
> On Fri, Nov 8, 2024 at 9:34 PM Jim Gowdy via RE-wrenches <
> [email protected]> wrote:
>
>> Hi all,
>>      I need some help with a generator overvoltage troubleshoot.  I'm
>> working on an outback offgrid system that consists of 2 x Radian GS8048a, 1
>> x MATE3S controller, 1 x FM 80 charge controller, 1 x 55kw cummins
>> generator, about 4kw of solar *not sufficient enough to keep up with the
>> load, and 24 x 4v Rolls batteries series/paralleled to make 48v.  The
>> generator was rebuilt and the batteries replaced about a year ago and since
>> then, the generator has been faulting due to overvoltage.  I had help and
>> first found that the MATE needed calibrating so that was done, but the
>> generator still was faulting.  I found changing the AC Input Charging from
>> 30a to 20a seemed to work.  I put a power monitor on the generator output
>> and found that, with the AC Input Charging set at 30a, noticed that there
>> was a voltage spike up to 300+V at about a 70a draw.  The generator company
>> put a load bank on and verified the generator may not be at fault and the
>> problem is after the generator.  Has anyone encountered a problem like this
>> and have suggestions?
>>
>> --
>> Jim with Gowdy Electric
>> Cambria, Ca 93428
>> business  805 927 2630
>> cell  805 975 5279
>> _______________________________________________
>> List sponsored by Redwood Alliance
>>
>> Pay optional member dues here: http://re-wrenches.org
>>
>> List Address: [email protected]
>>
>> Change listserver email address & settings:
>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>>
>> There are two list archives for searching. When one doesn't work, try the
>> other:
>> https://www.mail-archive.com/[email protected]/
>> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>>
>> List rules & etiquette:
>> http://www.re-wrenches.org/etiquette.htm
>>
>> Check out or update participant bios:
>> http://www.members.re-wrenches.org
>>
>>
>
> --
>
>
>
> Mac Lewis
>
> *"Yo solo sé que no sé nada." -Sócrates*
> _______________________________________________
> List sponsored by Redwood Alliance
>
> Pay optional member dues here: http://re-wrenches.org
>
> List Address: [email protected]
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> There are two list archives for searching. When one doesn't work, try the
> other:
> https://www.mail-archive.com/[email protected]/
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>
> List rules & etiquette:
> http://www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> http://www.members.re-wrenches.org
>
>

-- 

Michael Morningstar


Morningstar Electric Inc

PO Box 1494

Mount Shasta, CA 96067

530-921-0560

CSLB 1116835

[email protected]
_______________________________________________
List sponsored by Redwood Alliance

Pay optional member dues here: http://re-wrenches.org

List Address: [email protected]

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

There are two list archives for searching. When one doesn't work, try the other:
https://www.mail-archive.com/[email protected]/
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
http://www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
http://www.members.re-wrenches.org

Reply via email to