Reading that the problem started AFTER the gen set was rebuilt, seems to
point to adjusting generator voltage and frequency set points, or a
faulty voltage regulator. My guess is something went wrong with the
rebuild. Unless it was factory rebuilt, I've found local generator
service companies to be overall fair to bad. All the knowledgeable old
timers are retiring, replaced with younger folks that mostly are there
to just collect a paycheck. My experience with gen sets that start
having trouble, is they have to be replaced. I just haven't seen them
ever be reliable again, once they start needing work.
As soon as the gen set service company hears "Solar", they pin the blame
on us, and to be fair, Inverter battery charging is a tricky load.
Ray Walters
Remote Solar
On 1/3/2025 1:21 PM, Blair May via RE-wrenches wrote:
What IS the AC output prior to connecting to the Inverters? Hzs? Is
the generator an older unit w/ mechanical speed controls? 55kW gen set
should have no problem that load and the OV will usually occur during
the disconnection phase not once loaded. On a generator, the "Gain"
setting controls the sensitivity of the voltage regulator, essentially
determining how quickly the generator responds to changes in load by
adjusting the excitation current to maintain a stable output voltage;
a higher gain means a faster response to load fluctuations, while a
lower gain results in a slower response, potentially leading to larger
voltage swings under changing load conditions. TUMP
On Jan 3, 2025, at 3:01 PM, Jerry Shafer via RE-wrenches
<re-wrenches@lists.re-wrenches.org> wrote:
I work with gen set and inverter integration all the time, unless you
have an inverter beginning to fail, it has to be the gen set, when l
run load banks it for 2, 4 hr. or even longer and the voltage may
only be checked at intervals and not continues. Use a fluke or other
high quality meter set to min max and test all the integration, now
the inverter may be pushing back spikes. You should also be able to
tune in voltage at the gen set regulator, it can set volts and freq.
Fun times
On Fri, Jan 3, 2025, 6:17 AM Jim Gowdy via RE-wrenches
<re-wrenches@lists.re-wrenches.org> wrote:
Hi all,
I need some help with a generator overvoltage troubleshoot.
I'm working on an outback offgrid system that consists of 2 x
Radian GS8048a, 1 x MATE3S controller, 1 x FM 80 charge
controller, 1 x 55kw single phase propane AC cummins generator,
about 4kw of solar *not sufficient enough to keep up with the
load, and 24 x 4v Rolls batteries series/paralleled to make 48v.
The generator was rebuilt and the batteries replaced about a year
ago and since then, the generator has been faulting due to
overvoltage. I had help and first found that the MATE needed
calibrating so that was done, but the generator still was
faulting. I found changing the AC Input Charging from 30a to 20a
seemed to work. I put a power monitor on the generator output
and found that, with the AC Input Charging set at 30a, noticed
that there was a voltage spike up to 300+V at about a 70a draw.
The generator company put a load bank on and verified the
generator may not be at fault and the problem is after the
generator. Has anyone encountered a problem like this and have
suggestions? I've attached a PDF with a timeline of what I've
done for troubleshooting so far.
--
Jim with Gowdy Electric
Cambria, Ca 93428
business 805 927 2630
cell 805 975 5279
_______________________________________________
List sponsored by Redwood Alliance
Pay optional member dues here: http://re-wrenches.org
List Address: RE-wrenches@lists.re-wrenches.org
Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
There are two list archives for searching. When one doesn't work,
try the other:
https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
List rules & etiquette:
http://www.re-wrenches.org/etiquette.htm
Check out or update participant bios:
http://www.members.re-wrenches.org
_______________________________________________
List sponsored by Redwood Alliance
Pay optional member dues here: http://re-wrenches.org
List Address: RE-wrenches@lists.re-wrenches.org
Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
There are two list archives for searching. When one doesn't work, try
the other:
https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
List rules & etiquette:
http://www.re-wrenches.org/etiquette.htm
Check out or update participant bios:
http://www.members.re-wrenches.org
"We must all learn to live together as brothers,
or we all will perish as fools."
MLK
_______________________________________________
List sponsored by Redwood Alliance
Pay optional member dues here:http://re-wrenches.org
List Address:RE-wrenches@lists.re-wrenches.org
Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
There are two list archives for searching. When one doesn't work, try the other:
https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
List rules & etiquette:
http://www.re-wrenches.org/etiquette.htm
Check out or update participant bios:
http://www.members.re-wrenches.org
_______________________________________________
List sponsored by Redwood Alliance
Pay optional member dues here: http://re-wrenches.org
List Address: RE-wrenches@lists.re-wrenches.org
Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
There are two list archives for searching. When one doesn't work, try the other:
https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
List rules & etiquette:
http://www.re-wrenches.org/etiquette.htm
Check out or update participant bios:
http://www.members.re-wrenches.org