One comment with regard to Rolls AGM’s. I, like yourself, have sold very few 
AGM’s over the years, preferring lead acid. But I supplied a set of Rolls AGM’s 
to a client who self installed and didn’t recognize the need for a minimum 85a 
charge. His inverter/pv combination was unable to supply that and the batteries 
sulphated within months to an unrecoverable state. $20k down the drain. Most 
other AGM’s get by with around 50a charge.

Ron

> On Jan 12, 2025, at 12:55 PM, Jay via RE-wrenches 
> <[email protected]> wrote:
> 
> You guys are making my point. 
> Melting the cases is not a fire. And every melted agm case is due to 
> incorrect charging mechanisms. 
> 
> But there have been some cases on this site of catastrophic lithium failures. 
> 
> I am starting to see people asking about fires and lithium. 
> 
> These batteries are in the house. Not my design and not an easy fix to move 
> them. 
> 
> Thanks again
> 
> Jay 
> 
> 
> 
>> On Jan 12, 2025, at 10:52 AM, Tyrone Houck via RE-wrenches 
>> <[email protected]> wrote:
>> 
>> 
>> I had the exact same thing happen(even down to the crowbar) with the only 
>> set of full river 400 6's I've ever installed. I personally lean away from 
>> agm though we've had pretty good luck with the Outback and Northstar PLR 
>> platform over the year..
>> 
>> 
>>    
>> 
>> On Sun, Jan 12, 2025, 9:39 AM Ray Walters via RE-wrenches 
>> <[email protected] 
>> <mailto:[email protected]>> wrote:
>>> The only thermal runaway event I've ever seen, was with AGM in an over 
>>> insulated battery box.  Got so hot that the cases fused to each other, and 
>>> we had to pry the batteries apart with a crow bar.  She wants ZERO risk of 
>>> fire?  She needs to live in a concrete bunker with no electricity at all.  
>>> Every electrical connection, every outlet, every appliance has a risk of 
>>> fire.  Period.
>>> 
>>> Ray Walters
>>> Remote Solar
>>> 
>>> On 1/12/2025 9:39 AM, Tyrone Houck via RE-wrenches wrote:
>>>> I hate to be the one to say it but LFP has arguably less fire risk than 
>>>> agm. A short circuit in an agm could be disastrous and AGM is not 
>>>> necessarily any safer or less prone to thermal runaway events than modern 
>>>> LFP. I'd recommend a cobalt free LFP like homegrid, simpliphi, or midnite 
>>>> if it were me..
>>>> 
>>>> 
>>>>    
>>>> 
>>>> On Sat, Jan 11, 2025, 3:38 PM jay via RE-wrenches 
>>>> <[email protected] 
>>>> <mailto:[email protected]>> wrote:
>>>>> I was going to try and steer her towards lithium but she wants zero, 
>>>>> absolutely zero chance of fire, so no lithium.
>>>>> 
>>>>> great batteries though
>>>>> 
>>>>> jay
>>>>> 
>>>>> 
>>>>> 
>>>>>> On Jan 11, 2025, at 4:35 PM, MD Electric & Solar via RE-wrenches 
>>>>>> <[email protected] 
>>>>>> <mailto:[email protected]>> wrote:
>>>>>> 
>>>>>> 30KWH of LFP from discover energy, fits in one enclosure, around 
>>>>>> $14000.00
>>>>>> Enclosure is indoor/outdoor rated.
>>>>>> 
>>>>>> https://discoverenergysys.com/products/lithium-batteries/aes-rackmount
>>>>>> https://discoverenergysys.com/products/accessories/slimline-enclosure
>>>>>> 
>>>>>> On Sat, Jan 11, 2025 at 3:31 PM jay via RE-wrenches 
>>>>>> <[email protected] 
>>>>>> <mailto:[email protected]>> wrote:
>>>>>>> HI Willam 
>>>>>>> 
>>>>>>> Thanks for the input.
>>>>>>> I didn’t know that trojan was sold, and from what you say, yeah scratch 
>>>>>>> them off.  
>>>>>>> 
>>>>>>> It’s currently at 30kwh.  And thats probably a good size.  
>>>>>>> As always, cost and time is a factor.  
>>>>>>> 
>>>>>>> I’ll check the others out.
>>>>>>> 
>>>>>>> jay
>>>>>>> 
>>>>>>> 
>>>>>>> 
>>>>>>> 
>>>>>>> 
>>>>>>> > On Jan 11, 2025, at 4:17 PM, William Miller <[email protected] 
>>>>>>> > <mailto:[email protected]>> wrote:
>>>>>>> > 
>>>>>>> > Jay:
>>>>>>> > 
>>>>>>> > What AH or Kwh level are you looking for?
>>>>>>> > 
>>>>>>> > Trojan was acquired by another company a few years ago and quality 
>>>>>>> > had gone
>>>>>>> > downhill.
>>>>>>> > 
>>>>>>> > Rolls is very sensitive to high temperatures.  They will deny a 
>>>>>>> > warranty
>>>>>>> > claim if all of your parameters are not exactly right.
>>>>>>> > 
>>>>>>> > For larger AH systems:
>>>>>>> > 
>>>>>>> > I like the Full River DC-400-2.  You might be able to do a one string
>>>>>>> > installation.
>>>>>>> > 
>>>>>>> > Unigy II is a great system.  Very robust.  Hard to deliver but I can 
>>>>>>> > offer
>>>>>>> > tips.  Lots of AH size options.
>>>>>>> > 
>>>>>>> > William
>>>>>>> > 
>>>>>>> > Miller Solar
>>>>>>> > 17395 Oak Road, Atascadero, CA 93422
>>>>>>> > 805-438-5600
>>>>>>> > www.millersolar.com <http://www.millersolar.com/>
>>>>>>> > CA Lic. 773985
>>>>>>> > 
>>>>>>> > 
>>>>>>> > 
>>>>>>> > -----Original Message-----
>>>>>>> > From: RE-wrenches [mailto:[email protected] 
>>>>>>> > <mailto:[email protected]>] On
>>>>>>> > Behalf Of jay via RE-wrenches
>>>>>>> > Sent: Saturday, January 11, 2025 2:48 PM
>>>>>>> > To: RE-wrenches
>>>>>>> > Cc: jay
>>>>>>> > Subject: [RE-wrenches] AGM battery recommendations
>>>>>>> > 
>>>>>>> > Hi All
>>>>>>> > 
>>>>>>> > I have a customer what is set on AGM.
>>>>>>> > 
>>>>>>> > It been so long since I’ve bought any, wondering if there are any
>>>>>>> > recommendations?
>>>>>>> > 
>>>>>>> > The ones I’m looking at:
>>>>>>> > 
>>>>>>> > Rolls  S6-460AGM-RE
>>>>>>> > 
>>>>>>> > Full river DC-400-6
>>>>>>> > 
>>>>>>> > Trojan SAES 06 375 6V
>>>>>>> > 
>>>>>>> > sun Xtender  brand.
>>>>>>> > 
>>>>>>> > What’s interesting is the trojan has about 3000 cycles vs the others 
>>>>>>> > at
>>>>>>> > around 1250 cycles to 50%.
>>>>>>> > Im wondering if that is a marketing idea or if its real.
>>>>>>> > 
>>>>>>> > thanks in advance
>>>>>>> > 
>>>>>>> > jay
>>>>>>> > _______________________________________________
>>>>>>> > List sponsored by Redwood Alliance
>>>>>>> > 
>>>>>>> > Pay optional member dues here: http://re-wrenches.org 
>>>>>>> > <http://re-wrenches.org/>
>>>>>>> > 
>>>>>>> > List Address: [email protected] 
>>>>>>> > <mailto:[email protected]>
>>>>>>> > 
>>>>>>> > Change listserver email address & settings:
>>>>>>> > http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>>>>>>> > 
>>>>>>> > There are two list archives for searching. When one doesn't work, try 
>>>>>>> > the
>>>>>>> > other:
>>>>>>> > https://www.mail-archive.com/[email protected]/
>>>>>>> > http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>>>>>>> > 
>>>>>>> > List rules & etiquette:
>>>>>>> > http://www.re-wrenches.org/etiquette.htm
>>>>>>> > 
>>>>>>> > Check out or update participant bios:
>>>>>>> > http://www.members.re-wrenches.org 
>>>>>>> > <http://www.members.re-wrenches.org/>
>>>>>>> 
>>>>>>> _______________________________________________
>>>>>>> List sponsored by Redwood Alliance
>>>>>>> 
>>>>>>> Pay optional member dues here: http://re-wrenches.org 
>>>>>>> <http://re-wrenches.org/>
>>>>>>> 
>>>>>>> List Address: [email protected] 
>>>>>>> <mailto:[email protected]>
>>>>>>> 
>>>>>>> Change listserver email address & settings:
>>>>>>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>>>>>>> 
>>>>>>> There are two list archives for searching. When one doesn't work, try 
>>>>>>> the other:
>>>>>>> https://www.mail-archive.com/[email protected]/
>>>>>>> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>>>>>>> 
>>>>>>> List rules & etiquette:
>>>>>>> http://www.re-wrenches.org/etiquette.htm
>>>>>>> 
>>>>>>> Check out or update participant bios:
>>>>>>> http://www.members.re-wrenches.org <http://www.members.re-wrenches.org/>
>>>>>>> 
>>>>>> 
>>>>>> 
>>>>>> 
>>>>>> -- 
>>>>>> Michael D Nelson
>>>>>> MD Electric & Solar Inc.
>>>>>> Office: 707-412-3181
>>>>>> Cell: 707-684-0064
>>>>>> www.mdelectricsolar.com <http://www.mdelectricsolar.com/>
>>>>>> www.facebook.com/mdelectricandsolar 
>>>>>> <http://www.facebook.com/mdelectricandsolar>
>>>>>> 
>>>>>> 
>>>>>> _______________________________________________
>>>>>> List sponsored by Redwood Alliance
>>>>>> 
>>>>>> Pay optional member dues here: http://re-wrenches.org 
>>>>>> <http://re-wrenches.org/>
>>>>>> 
>>>>>> List Address: [email protected] 
>>>>>> <mailto:[email protected]>
>>>>>> 
>>>>>> Change listserver email address & settings:
>>>>>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>>>>>> 
>>>>>> There are two list archives for searching. When one doesn't work, try 
>>>>>> the other:
>>>>>> https://www.mail-archive.com/[email protected]/
>>>>>> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>>>>>> 
>>>>>> List rules & etiquette:
>>>>>> http://www.re-wrenches.org/etiquette.htm
>>>>>> 
>>>>>> Check out or update participant bios:
>>>>>> http://www.members.re-wrenches.org <http://www.members.re-wrenches.org/>
>>>>>> 
>>>>> 
>>>>> _______________________________________________
>>>>> List sponsored by Redwood Alliance
>>>>> 
>>>>> Pay optional member dues here: http://re-wrenches.org 
>>>>> <http://re-wrenches.org/>
>>>>> 
>>>>> List Address: [email protected] 
>>>>> <mailto:[email protected]>
>>>>> 
>>>>> Change listserver email address & settings:
>>>>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>>>>> 
>>>>> There are two list archives for searching. When one doesn't work, try the 
>>>>> other:
>>>>> https://www.mail-archive.com/[email protected]/
>>>>> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>>>>> 
>>>>> List rules & etiquette:
>>>>> http://www.re-wrenches.org/etiquette.htm
>>>>> 
>>>>> Check out or update participant bios:
>>>>> http://www.members.re-wrenches.org <http://www.members.re-wrenches.org/>
>>>>> 
>>>> 
>>>> 
>>>> _______________________________________________
>>>> List sponsored by Redwood Alliance
>>>> 
>>>> Pay optional member dues here: http://re-wrenches.org 
>>>> <http://re-wrenches.org/>
>>>> 
>>>> List Address: [email protected] 
>>>> <mailto:[email protected]>
>>>> 
>>>> Change listserver email address & settings:
>>>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>>>> 
>>>> There are two list archives for searching. When one doesn't work, try the 
>>>> other:
>>>> https://www.mail-archive.com/[email protected]/
>>>> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>>>> 
>>>> List rules & etiquette:
>>>> http://www.re-wrenches.org/etiquette.htm
>>>> 
>>>> Check out or update participant bios:
>>>> http://www.members.re-wrenches.org <http://www.members.re-wrenches.org/>
>>>> 
>>> _______________________________________________
>>> List sponsored by Redwood Alliance
>>> 
>>> Pay optional member dues here: http://re-wrenches.org 
>>> <http://re-wrenches.org/>
>>> 
>>> List Address: [email protected] 
>>> <mailto:[email protected]>
>>> 
>>> Change listserver email address & settings:
>>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>>> 
>>> There are two list archives for searching. When one doesn't work, try the 
>>> other:
>>> https://www.mail-archive.com/[email protected]/
>>> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>>> 
>>> List rules & etiquette:
>>> http://www.re-wrenches.org/etiquette.htm
>>> 
>>> Check out or update participant bios:
>>> http://www.members.re-wrenches.org <http://www.members.re-wrenches.org/>
>>> 
>> _______________________________________________
>> List sponsored by Redwood Alliance
>> 
>> Pay optional member dues here: http://re-wrenches.org
>> 
>> List Address: [email protected]
>> 
>> Change listserver email address & settings:
>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>> 
>> There are two list archives for searching. When one doesn't work, try the 
>> other:
>> https://www.mail-archive.com/[email protected]/
>> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>> 
>> List rules & etiquette:
>> http://www.re-wrenches.org/etiquette.htm
>> 
>> Check out or update participant bios:
>> http://www.members.re-wrenches.org
>> 
> _______________________________________________
> List sponsored by Redwood Alliance
> 
> Pay optional member dues here: http://re-wrenches.org
> 
> List Address: [email protected]
> 
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
> 
> There are two list archives for searching. When one doesn't work, try the 
> other:
> https://www.mail-archive.com/[email protected]/
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
> 
> List rules & etiquette:
> http://www.re-wrenches.org/etiquette.htm
> 
> Check out or update participant bios:
> http://www.members.re-wrenches.org
> 

_______________________________________________
List sponsored by Redwood Alliance

Pay optional member dues here: http://re-wrenches.org

List Address: [email protected]

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

There are two list archives for searching. When one doesn't work, try the other:
https://www.mail-archive.com/[email protected]/
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
http://www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
http://www.members.re-wrenches.org

Reply via email to