Hello all... The first issue is that inverter/charger parasitic loads have increased exponentially in the past 20+ years. When the LBCO cuts out, the inverter may shut off, but it does not remove itself or any other DC-connected device from the battery. These devices still draw a parasitic load. In the 1990s, the Trace SW would pull about .3 to .4 amps of current from the battery when connected to it. Today, many manufacturers use cheaper transformers, and the high-frequency inverters draw a much higher current. Some of these all-in-one inverters draw 1-2 amps of current from battery banks, just connected and not even turned on.
What's important here is that the battery voltage is already very low when you trigger an LBCO shutdown (it's not a disconnect). For a 48-volt system, this is 44 to 47 volts, depending on where you set the LBCO. When a Lithium battery is this low, the voltage dropoff is much higher. With a lead battery, the voltage dropoff is much more linear, but with Lithium chemistry, this voltage dropoff is more like a cliff. This is why it's important for many of these Lithium systems to set the Battery cutouts a bit higher so people have more time to fix the situation before the BMS shuts down. Ideally, the customer should be educated not to over-discharge the bank, which would help. Many of these customers want turnkey systems that they don't want to think about but don't want to pay for it or do the work that is required to maintain it. Now, if the battery had gone into "Protect" mode and the BMS had shut down, the battery is outputting very little votlage... the inverter/charger needs voltage to run. There used to be a line of inverters in the marine and RV market that would do what we called "Dead Battery Restart". This meant there was a parallel circuit in the power supply so that when you supplied AC to the input, a secondary power supply bypassed the regular battery power supply and would power up the inverter and allow the charger to run. Most of the inverter manufacturers got rid of this circuitry because it was not cheap, took up space on the boards, and was just another circuit that could get damaged with generator/shore power surges. I don't know of an inverter today with this dead battery restarting circuit. With this, you need to be very careful. If the customer has cratered the battery voltage and drawn down the voltage so low that they have damaged the cells, jumpstarting the battery can create a charging hazard, and that could cause the cells to swell internally. If that happens, the battery will get warmer and warmer under charge, and eventually, you could have a cell rupture. This can happen quickly with Li-ion, but with LFP, it's much harder to create this problem. Usually, in LFP, cells will swell a bit, and the current interrupter on the individual cell will open up and drop that string, and you will lose capacity. Like everything else, it's a race to the bottom on cost; this affects quality and features... Everyone wants the "Bells & Whistles," but they don't want to pay for it. Steve Higgins On Sat, Feb 22, 2025 at 5:08 AM Jason Szumlanski via RE-wrenches < [email protected]> wrote: > I have been thinking a lot recently about the reasons off-grid systems can > shut down, and working on strategies to prevent these nuisances that > require manual intervention. > > Ideally, a BMS should never shut down due to low voltage/SOC because a > properly programmed inverter should reach it's cut off well before the BMS > decides it needs to protect the battery, especially where there is closed > loop communication. But let's say that happens, where the BMS does make the > DC battery output go to zero. > > It seems to me like the inverter should be able to start a generator, and > then signal to the BMS that a charging source is available. But I'm not > aware of any system that actually does this. The inverter should be able to > wake up the battery. I can see this being particularly possible where one > manufacturer is writing the code (I'm thinking Midnite AIO/Powerflo). > > Of course, the inverter would have to have power in order to do that, so > if it's nighttime and there is no PV, the inverter power would need to come > from somewhere. I have two thoughts. First, someone could manually start > the generator, waking up the inverter, but they would not have to reset the > BMS if the inverter told it to wake up. The second way would be for the > inverter to somehow close the 2-wire start circuit upon inverter shutdown, > restoring power to the inverter automatically. > > If those are not options, an external NO relay powered by the inverter > output could be added to the 2-wire start circuit, perhaps with a time > delay to return to the NO position to allow the generator to remain powered > until the inverter does it's thing and starts charging the batteries. > > Anyway, my question is whether any inverter/battery combination out there > works in a way that the inverter tells the battery there is a charging > source available to wake up the BMS and reconnect DC power. And if not, why? > > Jason Szumlanski > Florida Solar Design Group > _______________________________________________ > List sponsored by Redwood Alliance > > Pay optional member dues here: http://re-wrenches.org > > List Address: [email protected] > > Change listserver email address & settings: > http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org > > There are two list archives for searching. When one doesn't work, try the > other: > https://www.mail-archive.com/[email protected]/ > http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org > > List rules & etiquette: > http://www.re-wrenches.org/etiquette.htm > > Check out or update participant bios: > http://www.members.re-wrenches.org > >
_______________________________________________ List sponsored by Redwood Alliance Pay optional member dues here: http://re-wrenches.org List Address: [email protected] Change listserver email address & settings: http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org There are two list archives for searching. When one doesn't work, try the other: https://www.mail-archive.com/[email protected]/ http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org List rules & etiquette: http://www.re-wrenches.org/etiquette.htm Check out or update participant bios: http://www.members.re-wrenches.org