I agree as long as you have a long history with the battery/BMS. Since all of this is so new or constantly changing I would add a class T as it has a minor chance of being a failure item.

When I was testing this for Schneider, even they added the T fuse for insurance as no-one had tested the internal T fuse and contactor. Cheap insurance.

Dave Angelini Offgrid Solar
"we go where powerlines don't"
   [2]https://offgridsolar1.com/ [3]  [2]
e-mail  [email protected]
text 209 813 0060

On 2025-07-14 10:12 pm, William Miller via RE-wrenches wrote:

Friends:

When I design a lead-acid battery system I decide if I need over-current protection right at the battery or not. My logic is: if the leads are short, don't go through a wall and are well protected, I can rely on OCPD in the BOS cabinets. If any of these criteria is a no I put appropriately rated class T fuses right at the battery.

I'm thinking that since BMS devices have over-current protection baked-in, fusing at the battery would not be necessary for BMS equipped batteries in any case. Do you agree with that premise?

William Miller
Miller Solar.com
805-438-5600
www.millersolar.com [1]
_______________________________________________
List sponsored by Redwood Alliance

Pay optional member dues here: http://re-wrenches.org

List Address: [email protected]

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

There are two list archives for searching. When one doesn't work, try the other:
https://www.mail-archive.com/[email protected]/
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
http://www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
http://www.members.re-wrenches.org


Links:
------
[1] http://www.millersolar.com
[2] http://members.sti.net/offgridsolar/
[3] https://offgridsolar1.com/
_______________________________________________
List sponsored by Redwood Alliance

Pay optional member dues here: http://re-wrenches.org

List Address: [email protected]

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

There are two list archives for searching. When one doesn't work, try the other:
https://www.mail-archive.com/[email protected]/
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
http://www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
http://www.members.re-wrenches.org

Reply via email to