I always use breakers more because they are easy to reset and visible if 
tripped.  And if a class T  fuse blows, you don’t actually know it and then you 
have the situation of having to go out to replace a $100 fuse or have the 
customer replace a fuse with live ends which I stopped doing a long time ago. 

I wonder if midnite power is going to build a combiner box with breakers.  I’m 
sure the breakers used in their batteries are way less expensive than the big 
250’s we have used.  I’d sure like to see one.  

A question on the Class T fuses.  Is it UL ok to mount the fuses not in a fuse 
holder?  Like to a buss bar?

jay

> On Jul 16, 2025, at 5:23 AM, Jason Szumlanski via RE-wrenches 
> <[email protected]> wrote:
> 
> I like the Midnite 1000/2000A battery combiners for this purpose. The 250A DC 
> breakers are not cheap, but they add a level of convenience and protection 
> that I think it worthwhile.
> 
> 
> Jason Szumlanski
> Principal Solar Designer | Florida Solar Design Group
> NABCEP Certified Solar Professional (PVIP)
> Florida State Certified Solar Contractor CVC56956
> Florida Certified Electrical Contractor EC13013208
> 
> 
> On Tue, Jul 15, 2025 at 1:36 PM William Miller via RE-wrenches 
> <[email protected] 
> <mailto:[email protected]>> wrote:
>> Kirk:
>> 
>> First of all, I apologize for the typo in the subject line. I fixed it. I 
>> take my writing seriously but sometimes my devices fight me with 
>> autocorrect. 
>> 
>> You make good point regarding a scenario with a battery combiner. Relying on 
>> multiple BMSs for OCP would be a bad choice. 
>> 
>> Fortunately some cabinets come with breakers and those should be sufficient. 
>> 
>> William Miller
>> Miller Solar.com
>> 805-438-5600
>> www.millersolar.com <http://www.millersolar.com/>
>> 
>> 
>> On Tue, Jul 15, 2025 at 9:50 AM Kirk Herander <[email protected]> wrote:
>>> Hello William-
>>> 
>>> I agree with your approach.
>>> 
>>> I never historically have OCPD'ed lead acids at both ends of the battery 
>>> cable run, but do now, esp. with high kwh LFP, where a DC combiner is in 
>>> use.
>>> 
>>> For instance, I had to design a 2000 ADC bus @ a nominal 55 vdc, for a 500 
>>> kwh Blue Ion LFP bank. To create enough space for cables and fuses, I 
>>> started with -2- 2000A Midnite combiners, using one for positive and one 
>>> for negative.
>>> 
>>> Class T fuses are bolted directly to the DC bus (properly sized copper from 
>>> copper.org <http://copper.org/> charts), and the BI BMS breaker protects at 
>>> each respective battery cabinet.
>>> 
>>> Same thing on the  DC to inverter cables, class T's bolted to the bus, to 
>>> its respective outback Radian, where the standard 175A breaker resides.
>>> 
>>> I would never again do a building power system of any type or size without 
>>> both ends of a power cable (point of use & point of origin) being 
>>> protected, A best practice IMO.
>>> 
>>> 
>>> 
>>> On Tue, Jul 15, 2025 at 1:13 AM William Miller via RE-wrenches 
>>> <[email protected] 
>>> <mailto:[email protected]>> wrote:
>>>> Friends:
>>>> 
>>>> When I design a lead-acid battery system I decide if I need over-current 
>>>> protection right at the battery or not.  My logic is:  if the leads are 
>>>> short, don’t go through a wall and are well protected,  I can rely on OCPD 
>>>> in the BOS cabinets. If any of these criteria is a no I put appropriately 
>>>> rated class T fuses right at the battery. 
>>>> 
>>>> I’m thinking that since BMS devices have over-current protection baked-in, 
>>>> fusing at the battery would not be necessary for BMS equipped batteries in 
>>>> any case. Do you agree with that premise?
>>>> 
>>>> 
>>>> William Miller
>>>> Miller Solar.com
>>>> 805-438-5600
>>>> www.millersolar.com <http://www.millersolar.com/>
>>>> _______________________________________________
>>>> List sponsored by Redwood Alliance
>>>> 
>>>> Pay optional member dues here: http://re-wrenches.org 
>>>> <http://re-wrenches.org/>
>>>> 
>>>> List Address: [email protected] 
>>>> <mailto:[email protected]>
>>>> 
>>>> Change listserver email address & settings:
>>>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>>>> 
>>>> There are two list archives for searching. When one doesn't work, try the 
>>>> other:
>>>> https://www.mail-archive.com/[email protected]/
>>>> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>>>> 
>>>> List rules & etiquette:
>>>> http://www.re-wrenches.org/etiquette.htm
>>>> 
>>>> Check out or update participant bios:
>>>> http://www.members.re-wrenches.org <http://www.members.re-wrenches.org/>
>>>> 
>>> 
>>> 
>>> 
>>> --
>>> 
>>> 
>>>  <>
>>> Kirk Herander /  <>[email protected] <mailto:[email protected]>
>>> Owner|Principal, VT Solar, LLC
>>> Celebrating our 34st Anniversary 1991-2025!!
>>> dba Vermont Solar Engineering
>>> 802.559.1225
>> _______________________________________________
>> List sponsored by Redwood Alliance
>> 
>> Pay optional member dues here: http://re-wrenches.org 
>> <http://re-wrenches.org/>
>> 
>> List Address: [email protected] 
>> <mailto:[email protected]>
>> 
>> Change listserver email address & settings:
>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>> 
>> There are two list archives for searching. When one doesn't work, try the 
>> other:
>> https://www.mail-archive.com/[email protected]/
>> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>> 
>> List rules & etiquette:
>> http://www.re-wrenches.org/etiquette.htm
>> 
>> Check out or update participant bios:
>> http://www.members.re-wrenches.org <http://www.members.re-wrenches.org/>
>> 
> _______________________________________________
> List sponsored by Redwood Alliance
> 
> Pay optional member dues here: http://re-wrenches.org
> 
> List Address: [email protected]
> 
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
> 
> There are two list archives for searching. When one doesn't work, try the 
> other:
> https://www.mail-archive.com/[email protected]/
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
> 
> List rules & etiquette:
> http://www.re-wrenches.org/etiquette.htm
> 
> Check out or update participant bios:
> http://www.members.re-wrenches.org
> 

_______________________________________________
List sponsored by Redwood Alliance

Pay optional member dues here: http://re-wrenches.org

List Address: [email protected]

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

There are two list archives for searching. When one doesn't work, try the other:
https://www.mail-archive.com/[email protected]/
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
http://www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
http://www.members.re-wrenches.org

Reply via email to