For years I have understood that when doing a supply side connection, you
are supposed to bond the neutral to ground in the solar service disconnect.
I have a Midnite AIO system with two inverters (set up as a supply side
connection) that recently was getting a CA-DC link Overvoltage error. When
talking to Midnite, their first response was to make sure that there was
only one N-G bond in the whole system. When I mentioned that the solar is a
separate service and thus there is a N-G bond in both the main panel and
the inverter distribution panel, they said to remove it from the inverter
distribution panel. I want to make the system work right, but I also am
hesitant to do something against how I have understood the NEC to be for a
long time. I am curious if you all have thoughts on this or run into a
similar situation.

Cheers,
Dave

-- 

[image: Logo] <https://www.sungineersolar.com/>
Dave Tedeyan, P.E.
Owner | Sungineer Solar
p: he | him | his
a: 1653 Slaterville Rd. | Ithaca, NY 14850
w: www.sungineersolar.com <http://www.sungineersolar.com/>
c: (607) 270-0370
_______________________________________________
List sponsored by Redwood Alliance

Pay optional member dues here: http://re-wrenches.org

List Address: [email protected]

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

There are two list archives for searching. When one doesn't work, try the other:
https://www.mail-archive.com/[email protected]/
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
http://www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
http://www.members.re-wrenches.org

Reply via email to