Hi All, For years I have understood that when doing a supply side connection, you are supposed to bond the neutral to ground in the solar service disconnect. I have a Midnite AIO system with two inverters (set up as a supply side connection) that recently was getting a CA-DC link Overvoltage error. When talking to Midnite, their first response was to make sure that there was only one N-G bond in the whole system. When I mentioned that the solar is a separate service and thus there is a N-G bond in both the main panel and the inverter distribution panel, they said to remove it from the inverter distribution panel. I want to make the system work right, but I also am hesitant to do something against how I have understood the NEC to be for a long time. I am curious if you all have thoughts on this or run into a similar situation.
Cheers, Dave -- [image: Logo] <https://www.sungineersolar.com/> Dave Tedeyan, P.E. Owner | Sungineer Solar p: he | him | his a: 1653 Slaterville Rd. | Ithaca, NY 14850 w: www.sungineersolar.com <http://www.sungineersolar.com/> c: (607) 270-0370
_______________________________________________ List sponsored by Redwood Alliance Pay optional member dues here: http://re-wrenches.org List Address: [email protected] Change listserver email address & settings: http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org There are two list archives for searching. When one doesn't work, try the other: https://www.mail-archive.com/[email protected]/ http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org List rules & etiquette: http://www.re-wrenches.org/etiquette.htm Check out or update participant bios: http://www.members.re-wrenches.org