As Tyrone says, times may have changed, but I've always approached supply-side 
connections based on the type of supply I'm connecting to. In Vermont, we see 
two types of connections. One with four wires between the meter and the main 
service disconnect (L1, L2, N, G). In this configuration, we do not make a 
neutral/ground bond at the PV system disconnect because one was made at the 
meter.

The other is three wires between the meter and main service disconnect (L1, L2, 
N). In this configuration, we do make a neutral/ground bond at the PV system 
disconnect.

Also, if I recall correctly, the PV system is not considered a second service 
under the NEC. But smarter people than I may have more up-to-date information.

Thanks,
Will
________________________________
From: RE-wrenches <[email protected]> on behalf of 
Tyrone Houck via RE-wrenches <[email protected]>
Sent: Thursday, October 23, 2025 11:01 AM
To: RE-wrenches <[email protected]>
Cc: Tyrone Houck <[email protected]>
Subject: [EXTERNAL] Re: [RE-wrenches] N-G bond for supply side connection 
Midnite Power


CAUTION: This email originated from outside of the organization. Do not click 
links or open attachments unless you recognize the sender and know the content 
is safe.



My interpretation, and the way it was explained to me by both Ryan Mayfield and 
Kyle Bolger(several years ago at this point, popular opinion may have changed 
since). Is that it is not a seperate service.
 It is however required to have a ground-neutral bond( though in my opinion 
pointless and redundant as there is a bond in the enclosure where the tap is 
made). If it gives you any issue, ensure as close to equal potential to the 
grounding electrode as possible(and make sure your neutral is appropriately 
sized). I personally don't see the point but it is an NEC requirement




On Thu, Oct 23, 2025, 6:08 AM Dave Tedeyan via RE-wrenches 
<[email protected]<mailto:[email protected]>> 
wrote:
Hi All,

For years I have understood that when doing a supply side connection, you are 
supposed to bond the neutral to ground in the solar service disconnect. I have 
a Midnite AIO system with two inverters (set up as a supply side connection) 
that recently was getting a CA-DC link Overvoltage error. When talking to 
Midnite, their first response was to make sure that there was only one N-G bond 
in the whole system. When I mentioned that the solar is a separate service and 
thus there is a N-G bond in both the main panel and the inverter distribution 
panel, they said to remove it from the inverter distribution panel. I want to 
make the system work right, but I also am hesitant to do something against how 
I have understood the NEC to be for a long time. I am curious if you all have 
thoughts on this or run into a similar situation.

Cheers,
Dave

--

[Logo]<https://urldefense.com/v3/__https://www.sungineersolar.com/__;!!KPww_GFiJXw!cfCkA7tAgtw29oHcZgoFLPG0fYrtoep5hMrKhWU7oKhftyB0eQP_x5leI3wGe5PYBW9joTZSqb8HdY4mSW7c6u6pM7l27rFH$>
Dave Tedeyan, P.E.
Owner | Sungineer Solar
p: he | him | his
a: 1653 Slaterville 
Rd.<https://urldefense.com/v3/__https://www.google.com/maps/search/1653*Slaterville*Rd.**D7C**AIthaca,*NY*14850?entry=gmail&source=g__;KysrwqArJcKgKys!!KPww_GFiJXw!cfCkA7tAgtw29oHcZgoFLPG0fYrtoep5hMrKhWU7oKhftyB0eQP_x5leI3wGe5PYBW9joTZSqb8HdY4mSW7c6u6pM4tZUfh6$>
 
<https://urldefense.com/v3/__https://www.google.com/maps/search/1653*Slaterville*Rd.**D7C**AIthaca,*NY*14850?entry=gmail&source=g__;KysrwqArJcKgKys!!KPww_GFiJXw!cfCkA7tAgtw29oHcZgoFLPG0fYrtoep5hMrKhWU7oKhftyB0eQP_x5leI3wGe5PYBW9joTZSqb8HdY4mSW7c6u6pM4tZUfh6$>
 | Ithaca, NY 
14850<https://urldefense.com/v3/__https://www.google.com/maps/search/1653*Slaterville*Rd.**D7C**AIthaca,*NY*14850?entry=gmail&source=g__;KysrwqArJcKgKys!!KPww_GFiJXw!cfCkA7tAgtw29oHcZgoFLPG0fYrtoep5hMrKhWU7oKhftyB0eQP_x5leI3wGe5PYBW9joTZSqb8HdY4mSW7c6u6pM4tZUfh6$>
w: 
www.sungineersolar.com<https://urldefense.com/v3/__http://www.sungineersolar.com/__;!!KPww_GFiJXw!cfCkA7tAgtw29oHcZgoFLPG0fYrtoep5hMrKhWU7oKhftyB0eQP_x5leI3wGe5PYBW9joTZSqb8HdY4mSW7c6u6pMwaujZYw$>
c: (607) 270-0370
_______________________________________________
List sponsored by Redwood Alliance

Pay optional member dues here: 
http://re-wrenches.org<https://urldefense.com/v3/__http://re-wrenches.org__;!!KPww_GFiJXw!cfCkA7tAgtw29oHcZgoFLPG0fYrtoep5hMrKhWU7oKhftyB0eQP_x5leI3wGe5PYBW9joTZSqb8HdY4mSW7c6u6pM44nwc7n$>

List Address: 
[email protected]<mailto:[email protected]>

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org<https://urldefense.com/v3/__http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org__;!!KPww_GFiJXw!cfCkA7tAgtw29oHcZgoFLPG0fYrtoep5hMrKhWU7oKhftyB0eQP_x5leI3wGe5PYBW9joTZSqb8HdY4mSW7c6u6pM_TSO_MP$>

There are two list archives for searching. When one doesn't work, try the other:
https://www.mail-archive.com/[email protected]/<https://urldefense.com/v3/__https://www.mail-archive.com/[email protected]/__;!!KPww_GFiJXw!cfCkA7tAgtw29oHcZgoFLPG0fYrtoep5hMrKhWU7oKhftyB0eQP_x5leI3wGe5PYBW9joTZSqb8HdY4mSW7c6u6pM214HEdk$>
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org<https://urldefense.com/v3/__http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org__;!!KPww_GFiJXw!cfCkA7tAgtw29oHcZgoFLPG0fYrtoep5hMrKhWU7oKhftyB0eQP_x5leI3wGe5PYBW9joTZSqb8HdY4mSW7c6u6pM9SAWGzk$>

List rules & etiquette:
http://www.re-wrenches.org/etiquette.htm<https://urldefense.com/v3/__http://www.re-wrenches.org/etiquette.htm__;!!KPww_GFiJXw!cfCkA7tAgtw29oHcZgoFLPG0fYrtoep5hMrKhWU7oKhftyB0eQP_x5leI3wGe5PYBW9joTZSqb8HdY4mSW7c6u6pMxgahljj$>

Check out or update participant bios:
http://www.members.re-wrenches.org<https://urldefense.com/v3/__http://www.members.re-wrenches.org__;!!KPww_GFiJXw!cfCkA7tAgtw29oHcZgoFLPG0fYrtoep5hMrKhWU7oKhftyB0eQP_x5leI3wGe5PYBW9joTZSqb8HdY4mSW7c6u6pMz1fDKvi$>

________________________________

Please be advised that this email may contain confidential information. If you 
are not the intended recipient, please notify us by email by replying to the 
sender and delete this message.
_______________________________________________
List sponsored by Redwood Alliance

Pay optional member dues here: http://re-wrenches.org

List Address: [email protected]

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

There are two list archives for searching. When one doesn't work, try the other:
https://www.mail-archive.com/[email protected]/
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
http://www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
http://www.members.re-wrenches.org

Reply via email to