HI William 

This is for both on and off grid correct?
jay

> On Oct 29, 2025, at 10:34 AM, William Bryce via RE-wrenches 
> <[email protected]> wrote:
> 
> Hi Dave
> 
> The AC wires need to be the same size and try to have the same length. This 
> is important because the inverter when stacked "shares" the power so you want 
> to try to prevent any imbalance in voltage and resistance issues, or circle 
> issues. 
> 
> In older stacked systems you have a master and a slave and when the power 
> demand increases then the slave would take the excess. On AIO's the power is 
> shared equally all the time (this is a good thing as you don't get the 
> flicker as the slave picks up). It is important that the install takes into 
> account the  different way the power is used and delivered. Have a clean 
> install, with the correct sized conductors as specified by the manufacturer, 
> and try to keep the wire run short and equal when connecting the inverter AC 
> runs  together.
> 
> On Wed, Oct 29, 2025 at 9:41 AM Dave Tedeyan via RE-wrenches 
> <[email protected] 
> <mailto:[email protected]>> wrote:
>> William this is really good information, thanks for sharing the technical 
>> perspective.
>> 
>> I have two sites with two of these inverters and both of them are exhibiting 
>> very similar behavior. On Friday, I was out at the other one to wrap up a 
>> few things. While I was out there I verified some of the things that Midnite 
>> tech support suggested like making sure that the AC wires to each inverter's 
>> grid in and cables are the same length and also from the battery bus bar to 
>> each inverter are the same length. This was actually a bit surprising to me, 
>> considering with lead acid it is more important to have the battery cables 
>> from the bus bar to the batteries be the exact same length and the cables to 
>> the inverters did not matter as much. 
>> 
>> Based on what we were talking about last week, I removed the N-G bond in the 
>> disconnect for the solar, but I have not yet gone looking for other N-G 
>> connections in the way that Jason suggested. I have not gotten a CA-DC link 
>> overvoltage error, but I have still seen some of the symptoms. It is not as 
>> bad as the other site, but what I notice on the monitoring is that in the 
>> late afternoon/early evening one inverter shows an unreasonable amount of 
>> solar (with power going into the grid and into the battery), while the other 
>> inverter shows low solar (with a ton of power coming out of the battery 
>> going to the load and the grid), and the battery SOC drops very quickly down 
>> to the discharge end SOC (on grid) setting of 85%. 
>> Jason and William, do you know whether any faulty wiring with N-G connected 
>> in loads on the non-backed up side will affect the system the same way? Or 
>> is it mostly just important to check for any neutrals connected to ground on 
>> the backed up loads side?
>> 
>> Jason, as to why a supply side connection - I was under the impression that 
>> a Power Control System just effectively limits the amount of power that can 
>> be sold to the grid. But on a standard 200A service, that limits you to 
>> about 7.7kw of sell back. I would not want to limit the system that much for 
>> a roughly 20kw system, even if more than the 7.7kw can go to powering loads 
>> and battery charging. In the Midnite monitoring, it is pretty easy to limit 
>> the grid sell back with the "maximum feed in grid power" in the Power 
>> Control settings.
>> 
>> Cheers,
>> Dave
>> 
>> On Sun, Oct 26, 2025 at 8:51 AM William Bryce via RE-wrenches 
>> <[email protected] 
>> <mailto:[email protected]>> wrote:
>>> All
>>> 
>>> Most modern all-in-one (AIO) inverters are designed around a non-isolated 
>>> high-voltage DC bus. This design is what allows manufacturers to advertise 
>>> higher output numbers — for example, “15–18 kW” — while the inverter may 
>>> only deliver 12 kW during nighttime operation when PV isn’t contributing 
>>> (it is also cheaper to build). Without the shared non-isolated DC link, 
>>> these power-boosted daytime ratings wouldn’t be possible.
>>> 
>>> A DC-bus overvoltage fault almost always points to one of two issues:
>>> 
>>> Improper system design
>>> 
>>> Wiring and installation mistakes
>>> 
>>> Off-Grid Example
>>> 
>>> A common DIY mistake is pairing a large solar array (because glass is 
>>> cheap) with a relatively small battery (not as cheap).
>>> When the battery is full and a large load suddenly turns off, the excess 
>>> energy has nowhere to go. The inverter throttles back, but the stored 
>>> energy can still push the DC-bus voltage up rapidly. If the inverter didn’t 
>>> protect itself, the capacitors would be at risk — so it shuts down with an 
>>> overvoltage error. This is also common when using a large retrofitted AC 
>>> coupled array.
>>> 
>>> Grid-Tie Example
>>> 
>>> In grid-connected systems, DC-bus overvoltage is typically caused by wiring 
>>> mistakes, some common examples are:
>>> 
>>> Multiple neutral-to-ground bonds
>>> 
>>> Reversed hot/neutral at outlets
>>> 
>>> A single inverter is usually more forgiving. However, stacked inverters 
>>> must share phase, neutral, and grounding relationships precisely. Any 
>>> mis-wiring can create circulating currents. That circulating energy is not 
>>> accounted for in the inverter’s internal power calculations, so the DC-bus 
>>> voltage rises unexpectedly — and the inverter shuts down for protection.
>>> 
>>> A DC Link Overvoltage error is usually not an inverter defect — it’s a 
>>> system design or system wiring problem 99% of the time. Ensuring proper 
>>> neutral/ground bonding, correct polarity, adequate battery capacity, and 
>>> proper commissioning is critical to reliable AIO operation. 
>>> 
>>> This behavior is not unique to the MN AIO — all AIO inverters using a 
>>> non-isolated DC-bus topology share the same fundamental protection 
>>> limitations.
>>> 
>>> Inverters are getting more complex to deal with the new rules and utility 
>>> requirements, this causes reliability issues as we move (or pushed) to full 
>>> integration with the grid.  Because you know we all want the utility to 
>>> have full control over our systems!
>>> 
>>> 
>>> On Sat, Oct 25, 2025 at 9:51 AM Jay via RE-wrenches 
>>> <[email protected] 
>>> <mailto:[email protected]>> wrote:
>>>> I had an issue with a EG4 inverter and tech support was an insistent that 
>>>> there was multiple ground neutral bonds in the system. Fully off grid 
>>>> system with no generator. 
>>>> It wasn’t the issue but it seems like these inverters are sensitive to it. 
>>>> 
>>>> Is the inverter internally bonded, not that I’m aware of or what I’ve 
>>>> measured. 
>>>> And so I can’t figure out what it’s measuring between N/G to have a 
>>>> potential issue. 
>>>> 
>>>> Maybe someone can explain?
>>>> 
>>>> Jay
>>>> 
>>>> 
>>>> 
>>>>> On Oct 24, 2025, at 6:49 PM, Dave Tedeyan via RE-wrenches 
>>>>> <[email protected] 
>>>>> <mailto:[email protected]>> wrote:
>>>>> 
>>>>> 
>>>>> Thanks all for your thoughts here. It seems that the general consensus so 
>>>>> far is that the N-G should be bonded in the solar main disconnecting 
>>>>> means when doing a supply side connection (even if it is not technically 
>>>>> a separate service). When talking with Midnite Power, we made it very 
>>>>> clear that we were talking about a N-G bond in the inverter combiner / 
>>>>> solar main disconnect, and not the backed up loads panel. And being that 
>>>>> NY is still on 2017 code (only going to 2020 next year), with the 
>>>>> ambiguity in the code I am probably okay to undo the N-G connection in 
>>>>> the main solar disconnect.
>>>>> 
>>>>> In this case specifically, we are backing up only a small subset of loads 
>>>>> in the house. The reason for the two inverters is because there is about 
>>>>> 24kw of solar. There is also a manual transfer switch to normally be able 
>>>>> to power the loads off the inverters, but to be able to switch to 
>>>>> powering the loads off the main panel in case of service needed on the 
>>>>> inverters. The neutrals in this system are all connected together, and I 
>>>>> am not sure if that could cause issues. It is probably difficult to 
>>>>> explain all the details in words, so I am copying part of the three line 
>>>>> diagram here. The second picture is the conductor and conduit schedule.
>>>>> 
>>>>> Tom, I get it that the error sounds like it is on the DC side based on 
>>>>> the words, but when I talked to Midnite about it they were pretty clear 
>>>>> about it being due to multiple N-G bonds and they did not mention that it 
>>>>> could have anything to do with the DC side.
>>>>> 
>>>>> Jason, that is a good idea as well to check the loads that got moved over 
>>>>> to see if there are any other inadvertent N-G bonds on the premises. This 
>>>>> also similar to what Midnite suggested, which was to lift the N-G bond in 
>>>>> the main panel and then see if they are still bonded somewhere else. It 
>>>>> seems like it can be a slow process to track that down with power cut to 
>>>>> the house, but that might be what I have to try if removing the N-G bond 
>>>>> in the solar main disconnect does not help.
>>>>> 
>>>>> So, my main questions to anyone who has an opinion here are two fold:
>>>>> 1. Do you bond the N-G in general in the main solar disconnect for a 
>>>>> supply side connection?
>>>>> 2. Specifically with the Midnite AIO inverters, has anyone else had 
>>>>> issues with this "CA-DC link Overvoltage error" due to having a second 
>>>>> N-G bond in the house? (one in the main service panel, and one in the 
>>>>> solar main disconnect if it is a supply side connection). Or have you 
>>>>> seen this error and found that it was caused by something else?
>>>>> 
>>>>> Cheers,
>>>>> Dave
>>>>> 
>>>>> 
>>>>> 
>>>>> On Thu, Oct 23, 2025 at 5:25 PM Jason Szumlanski via RE-wrenches 
>>>>> <[email protected] 
>>>>> <mailto:[email protected]>> wrote:
>>>>>> I agree. It is not a separate service. It is a "tap" of the existing 
>>>>>> service (I use that term loosely here). The additional service 
>>>>>> disconnect for the supply side interconnection should have L1, L2, and N 
>>>>>> connected ahead of the premises main disconnect with no EGC. There 
>>>>>> should be a N-G bonding jumper in the PV service disconnect. Then there 
>>>>>> should be no N-G bonds downstream of both the premises main disconnect 
>>>>>> and the PV service disconnect.
>>>>>> 
>>>>>> Basically, it's the same as two main disconnects running from a meter 
>>>>>> enclosure. Each of the service disconnects has a N-G bond required.
>>>>>> 
>>>>>> Some AHJs (the crazy ones) require an EGC between the enclosure where 
>>>>>> the supply side connection is made and the PV service disconnect. This 
>>>>>> creates a parallel fault path, and should not be allowed, in my humble 
>>>>>> opinion.
>>>>>> 
>>>>>> Now it sounds like you might be doing a partial home backup. The issue 
>>>>>> there is that sometimes the loads or enclosures you moved over the 
>>>>>> backup load panel have inadvertent N-G bonds. Sometimes it's as simple 
>>>>>> as someone who got creative and used a ground as a neutral in a switch 
>>>>>> box. I say simple, but that can be hard to track down.
>>>>>> 
>>>>>> When Midnite said to remove it from the inverter distribution panel, 
>>>>>> they were probably talking about the protected loads panel.
>>>>>> 
>>>>>> I think more information is needed.
>>>>>> 
>>>>>> 
>>>>>> 
>>>>>> Jason Szumlanski
>>>>>> Principal Solar Designer | Florida Solar Design Group
>>>>>> NABCEP Certified Solar Professional (PVIP)
>>>>>> Florida State Certified Solar Contractor CVC56956
>>>>>> Florida Certified Electrical Contractor EC13013208
>>>>>> 
>>>>>> 
>>>>>> On Thu, Oct 23, 2025 at 11:03 AM Tyrone Houck via RE-wrenches 
>>>>>> <[email protected] 
>>>>>> <mailto:[email protected]>> wrote:
>>>>>>> My interpretation, and the way it was explained to me by both Ryan 
>>>>>>> Mayfield and Kyle Bolger(several years ago at this point, popular 
>>>>>>> opinion may have changed since). Is that it is not a seperate service.
>>>>>>>  It is however required to have a ground-neutral bond( though in my 
>>>>>>> opinion pointless and redundant as there is a bond in the enclosure 
>>>>>>> where the tap is made). If it gives you any issue, ensure as close to 
>>>>>>> equal potential to the grounding electrode as possible(and make sure 
>>>>>>> your neutral is appropriately sized). I personally don't see the point 
>>>>>>> but it is an NEC requirement 
>>>>>>> 
>>>>>>> 
>>>>>>>    
>>>>>>> 
>>>>>>> On Thu, Oct 23, 2025, 6:08 AM Dave Tedeyan via RE-wrenches 
>>>>>>> <[email protected] 
>>>>>>> <mailto:[email protected]>> wrote:
>>>>>>>> Hi All, 
>>>>>>>> 
>>>>>>>> For years I have understood that when doing a supply side connection, 
>>>>>>>> you are supposed to bond the neutral to ground in the solar service 
>>>>>>>> disconnect. I have a Midnite AIO system with two inverters (set up as 
>>>>>>>> a supply side connection) that recently was getting a CA-DC link 
>>>>>>>> Overvoltage error. When talking to Midnite, their first response was 
>>>>>>>> to make sure that there was only one N-G bond in the whole system. 
>>>>>>>> When I mentioned that the solar is a separate service and thus there 
>>>>>>>> is a N-G bond in both the main panel and the inverter distribution 
>>>>>>>> panel, they said to remove it from the inverter distribution panel. I 
>>>>>>>> want to make the system work right, but I also am hesitant to do 
>>>>>>>> something against how I have understood the NEC to be for a long time. 
>>>>>>>> I am curious if you all have thoughts on this or run into a similar 
>>>>>>>> situation.
>>>>>>>> 
>>>>>>>> Cheers, 
>>>>>>>> Dave
>>>>>>>> 
>>>>>>>> --
>>>>>>>> 
>>>>>>>>  <https://www.sungineersolar.com/>     
>>>>>>>> Dave Tedeyan, P.E.
>>>>>>>> Owner | Sungineer Solar
>>>>>>>> p: he | him | his
>>>>>>>> a: 1653 Slaterville Rd. 
>>>>>>>> <https://www.google.com/maps/search/1653+Slaterville+Rd.+%C2%A0+%7C%C2%A0Ithaca,+NY+14850?entry=gmail&source=g>
>>>>>>>>   
>>>>>>>> <https://www.google.com/maps/search/1653+Slaterville+Rd.+%C2%A0+%7C%C2%A0Ithaca,+NY+14850?entry=gmail&source=g>|
>>>>>>>>  Ithaca, NY 14850 
>>>>>>>> <https://www.google.com/maps/search/1653+Slaterville+Rd.+%C2%A0+%7C%C2%A0Ithaca,+NY+14850?entry=gmail&source=g>
>>>>>>>> w: www.sungineersolar.com <http://www.sungineersolar.com/>
>>>>>>>> c: (607) 270-0370
>>>>>>>> _______________________________________________
>>>>>>>> List sponsored by Redwood Alliance
>>>>>>>> 
>>>>>>>> Pay optional member dues here: http://re-wrenches.org 
>>>>>>>> <http://re-wrenches.org/>
>>>>>>>> 
>>>>>>>> List Address: [email protected] 
>>>>>>>> <mailto:[email protected]>
>>>>>>>> 
>>>>>>>> Change listserver email address & settings:
>>>>>>>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>>>>>>>> 
>>>>>>>> There are two list archives for searching. When one doesn't work, try 
>>>>>>>> the other:
>>>>>>>> https://www.mail-archive.com/[email protected]/
>>>>>>>> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>>>>>>>> 
>>>>>>>> List rules & etiquette:
>>>>>>>> http://www.re-wrenches.org/etiquette.htm
>>>>>>>> 
>>>>>>>> Check out or update participant bios:
>>>>>>>> http://www.members.re-wrenches.org 
>>>>>>>> <http://www.members.re-wrenches.org/>
>>>>>>>> 
>>>>>>> _______________________________________________
>>>>>>> List sponsored by Redwood Alliance
>>>>>>> 
>>>>>>> Pay optional member dues here: http://re-wrenches.org 
>>>>>>> <http://re-wrenches.org/>
>>>>>>> 
>>>>>>> List Address: [email protected] 
>>>>>>> <mailto:[email protected]>
>>>>>>> 
>>>>>>> Change listserver email address & settings:
>>>>>>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>>>>>>> 
>>>>>>> There are two list archives for searching. When one doesn't work, try 
>>>>>>> the other:
>>>>>>> https://www.mail-archive.com/[email protected]/
>>>>>>> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>>>>>>> 
>>>>>>> List rules & etiquette:
>>>>>>> http://www.re-wrenches.org/etiquette.htm
>>>>>>> 
>>>>>>> Check out or update participant bios:
>>>>>>> http://www.members.re-wrenches.org <http://www.members.re-wrenches.org/>
>>>>>>> 
>>>>>> _______________________________________________
>>>>>> List sponsored by Redwood Alliance
>>>>>> 
>>>>>> Pay optional member dues here: http://re-wrenches.org 
>>>>>> <http://re-wrenches.org/>
>>>>>> 
>>>>>> List Address: [email protected] 
>>>>>> <mailto:[email protected]>
>>>>>> 
>>>>>> Change listserver email address & settings:
>>>>>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>>>>>> 
>>>>>> There are two list archives for searching. When one doesn't work, try 
>>>>>> the other:
>>>>>> https://www.mail-archive.com/[email protected]/
>>>>>> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>>>>>> 
>>>>>> List rules & etiquette:
>>>>>> http://www.re-wrenches.org/etiquette.htm
>>>>>> 
>>>>>> Check out or update participant bios:
>>>>>> http://www.members.re-wrenches.org <http://www.members.re-wrenches.org/>
>>>>>> 
>>>>> 
>>>>> <PV3.0 as built.jpg>
>>>>> <PV3.1 as built.jpg>
>>>>> _______________________________________________
>>>>> List sponsored by Redwood Alliance
>>>>> 
>>>>> Pay optional member dues here: http://re-wrenches.org 
>>>>> <http://re-wrenches.org/>
>>>>> 
>>>>> List Address: [email protected] 
>>>>> <mailto:[email protected]>
>>>>> 
>>>>> Change listserver email address & settings:
>>>>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>>>>> 
>>>>> There are two list archives for searching. When one doesn't work, try the 
>>>>> other:
>>>>> https://www.mail-archive.com/[email protected]/
>>>>> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>>>>> 
>>>>> List rules & etiquette:
>>>>> http://www.re-wrenches.org/etiquette.htm
>>>>> 
>>>>> Check out or update participant bios:
>>>>> http://www.members.re-wrenches.org <http://www.members.re-wrenches.org/>
>>>>> 
>>>> _______________________________________________
>>>> List sponsored by Redwood Alliance
>>>> 
>>>> Pay optional member dues here: http://re-wrenches.org 
>>>> <http://re-wrenches.org/>
>>>> 
>>>> List Address: [email protected] 
>>>> <mailto:[email protected]>
>>>> 
>>>> Change listserver email address & settings:
>>>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>>>> 
>>>> There are two list archives for searching. When one doesn't work, try the 
>>>> other:
>>>> https://www.mail-archive.com/[email protected]/
>>>> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>>>> 
>>>> List rules & etiquette:
>>>> http://www.re-wrenches.org/etiquette.htm
>>>> 
>>>> Check out or update participant bios:
>>>> http://www.members.re-wrenches.org <http://www.members.re-wrenches.org/>
>>>> 
>>> _______________________________________________
>>> List sponsored by Redwood Alliance
>>> 
>>> Pay optional member dues here: http://re-wrenches.org 
>>> <http://re-wrenches.org/>
>>> 
>>> List Address: [email protected] 
>>> <mailto:[email protected]>
>>> 
>>> Change listserver email address & settings:
>>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>>> 
>>> There are two list archives for searching. When one doesn't work, try the 
>>> other:
>>> https://www.mail-archive.com/[email protected]/
>>> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>>> 
>>> List rules & etiquette:
>>> http://www.re-wrenches.org/etiquette.htm
>>> 
>>> Check out or update participant bios:
>>> http://www.members.re-wrenches.org <http://www.members.re-wrenches.org/>
>>> 
>> _______________________________________________
>> List sponsored by Redwood Alliance
>> 
>> Pay optional member dues here: http://re-wrenches.org 
>> <http://re-wrenches.org/>
>> 
>> List Address: [email protected] 
>> <mailto:[email protected]>
>> 
>> Change listserver email address & settings:
>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>> 
>> There are two list archives for searching. When one doesn't work, try the 
>> other:
>> https://www.mail-archive.com/[email protected]/
>> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>> 
>> List rules & etiquette:
>> http://www.re-wrenches.org/etiquette.htm
>> 
>> Check out or update participant bios:
>> http://www.members.re-wrenches.org <http://www.members.re-wrenches.org/>
>> 
> _______________________________________________
> List sponsored by Redwood Alliance
> 
> Pay optional member dues here: http://re-wrenches.org
> 
> List Address: [email protected]
> 
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
> 
> There are two list archives for searching. When one doesn't work, try the 
> other:
> https://www.mail-archive.com/[email protected]/
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
> 
> List rules & etiquette:
> http://www.re-wrenches.org/etiquette.htm
> 
> Check out or update participant bios:
> http://www.members.re-wrenches.org
> 

_______________________________________________
List sponsored by Redwood Alliance

Pay optional member dues here: http://re-wrenches.org

List Address: [email protected]

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

There are two list archives for searching. When one doesn't work, try the other:
https://www.mail-archive.com/[email protected]/
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
http://www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
http://www.members.re-wrenches.org

Reply via email to