Hello Drake, 
Absorption is the phase where voltage remains constant. Until the Absorb 
voltage value is achieved, you will be bulk charging. You can only force Float 
or Bulk. 

Larry Crutcher
Starlight Power Systems






On Dec 12, 2025, at 8:58 AM, Drake Chamberlin via RE-wrenches 
<[email protected]> wrote:

Hi Jay,

The system feeds the grid through an SMA H-FUS inverter. The Outbacks are off 
grid inverters, but are AC coupled to the batteries to provide power when the 
grid is down. 

The inverters monitor the batteries and go into REFLOAT when the batteries hit 
25 volts. I would like the inverters to go strait into the ABSORB cycle instead 
of going to REFLOAT.
 
The grid tie came after the the Outbacks were already in as a backup system. 
 
Thank you,
 
Drake
 
Drake Chamberlin

Athens Electric LLC

Ohio Electrical Contractor’s License 44810

NABCEP Certified PV Installation Professional

 

---
 


On 2025-12-11 10:54, Jay via RE-wrenches wrote:
> 
> Hi drake. 
> 
> You’re talking about the inverters charging the battereis, meaning
> this is a grid connected system?
> 
> Do you have a mate3/s or 1?
> 
> Jay
> 
>> On Dec 11, 2025, at 7:39 AM, Drake Chamberlin via RE-wrenches 
>> <[email protected] 
>> <mailto:[email protected]>> wrote:
>> 
>> 
>> Hello Wrenches,
>> 
>> We have a rental property with two, stacked VFX 3524 inverters. In the 
>> winter the batteries don't get an adequate solar charge. I would like to 
>> have the batteries get a bulk charge when the voltage drops to 24 volts, but 
>> it keeps hitting refloat.
>> 
>> How do I disable refloat? Can I just set the refloat time to zero?
>> 
>> Thank you,
>> 
>> Drake
>> 
>> --
>> 
>> _______________________________________________
>> List sponsored by Redwood Alliance
>> 
>> Pay optional member dues here: http://re-wrenches.org 
>> <http://re-wrenches.org/>
>> 
>> List Address: [email protected] 
>> <mailto:[email protected]>
>> 
>> Change listserver email address & settings:
>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>> 
>> There are two list archives for searching. When one doesn't work, try the 
>> other:
>> https://www.mail-archive.com/[email protected]/
>> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>> 
>> List rules & etiquette:
>> http://www.re-wrenches.org/etiquette.htm
>> 
>> Check out or update participant bios:
>> http://www.members.re-wrenches.org <http://www.members.re-wrenches.org/>
>> 
> _______________________________________________
> List sponsored by Redwood Alliance
> 
> Pay optional member dues here: http://re-wrenches.org 
> <http://re-wrenches.org/>
> 
> List Address: [email protected] 
> <mailto:[email protected]>
> 
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
> 
> There are two list archives for searching. When one doesn't work, try the 
> other:
> https://www.mail-archive.com/[email protected]/
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
> 
> List rules & etiquette:
> http://www.re-wrenches.org/etiquette.htm
> 
> Check out or update participant bios:
> http://www.members.re-wrenches.org 
> <http://www.members.re-wrenches.org/>_______________________________________________
List sponsored by Redwood Alliance

Pay optional member dues here: http://re-wrenches.org

List Address: [email protected]

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

There are two list archives for searching. When one doesn't work, try the other:
https://www.mail-archive.com/[email protected]/
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
http://www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
http://www.members.re-wrenches.org


_______________________________________________
List sponsored by Redwood Alliance

Pay optional member dues here: http://re-wrenches.org

List Address: [email protected]

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

There are two list archives for searching. When one doesn't work, try the other:
https://www.mail-archive.com/[email protected]/
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
http://www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
http://www.members.re-wrenches.org

Reply via email to