HI Chris,

They are all 12v fans and universal between 12,24,48v units

jay

> On Jan 9, 2026, at 4:35 PM, Chris Schaefer via RE-wrenches 
> <[email protected]> wrote:
> 
> While on the subject of VFX inverters in regards to the fan and internal temp 
> sensors, I've got a client with a circa 2010 VFX3624 that appears to have a 
> failed fan. I don't normally deal with 24 volt inverters. I've got many dead 
> VFX3648 units hanging out. My question is can I cannibalize a fan out of a 48 
> volt unit and put it in a 24 volt unit? Next, let's say the fan is ok and 
> based on the readings above I should look into replacing the xfmr temp 
> sensor. Again, can I take one out of a 48v inverter and use it on a 24v unit? 
> Which board might be suspect as well that the xfmr temp sensor feeds its 
> information too?
> 
> Thanks,
> Christopher
> 
> On Thu, Jan 8, 2026 at 9:23 PM Jerry Shafer via RE-wrenches 
> <[email protected] 
> <mailto:[email protected]>> wrote:
>> Wrenches, Jay,
>> Transformer temp sensors in the FX Fails, fans fail causing fet boards to 
>> overheat, dirty filters cause high temps on all the intervals. When outback 
>> was still running the parts department you always got temp senders with 
>> fans, boards and a relocation procedure, yes you must put the sensor in a 
>> new location.
>> FunTimes
>> 
>> On Thu, Jan 8, 2026, 3:26 PM Jay via RE-wrenches 
>> <[email protected] 
>> <mailto:[email protected]>> wrote:
>>> I’ve replaced dozens of internal temp sensors over the years. 
>>> 
>>> I learned to also replace the fan at the same time. 
>>> 
>>> Or vice versa. 
>>> 
>>> Jay
>>> 
>>>> On Jan 8, 2026, at 4:01 PM, Luke Christy via RE-wrenches 
>>>> <[email protected] 
>>>> <mailto:[email protected]>> wrote:
>>>> 
>>>> Drake,
>>>> I agree with Ray,
>>>> The message you’re seeing does not refer to the RTS that has been absent 
>>>> for years- it’s an issue with an internal sensor. 
>>>> I have seen intermittent warnings relating to internal sensors on VFX 
>>>> units that have self-resolved with a reboot, but if the warning is 
>>>> persistent then you’ll likely need to open the unit up and replace the 
>>>> sensor. 
>>>> 
>>>> Luke Christy
>>>> Renewable energy consultant
>>>> 
>>>> NABCEP Certified PV Installation Professional™: 
>>>> 
>>>> Solar Gain Services, LLC
>>>> PO Box 531
>>>> Monte Vista, CO 81144
>>>> 719.588.3044
>>>> [email protected] <mailto:[email protected]>
>>>> 
>>>>> On Jan 8, 2026, at 3:00 PM, Drake Chamberlin via RE-wrenches 
>>>>> <[email protected] 
>>>>> <mailto:[email protected]>> wrote:
>>>>> 
>>>>> A couple of years back, a client changed from lead acid batteries to 
>>>>> LiFeBlue, lithium batteries. At that time the temperature sensor was 
>>>>> removed. 
>>>>>  
>>>>> The other day, a warning light started blinking. The warning turned out 
>>>>> to be a bad temperature sensor. It is strange that this message showed up 
>>>>> now, as the sensor has been gone for years.
>>>>>  
>>>>> Is there any way to turn off the warning light?
>>>>>  
>>>>> Thank you,
>>>>>  
>>>>> Drake
>>>>>  
>>>>> Drake Chamberlin
>>>>> 
>>>>> Athens Electric LLC
>>>>> 
>>>>> Ohio Electrical Contractor’s License 44810
>>>>> 
>>>>> NABCEP Certified PV Installation Professional
>>>>> 
>>>>> 
>>>>> 
>>>>> --
>>>>>  
>>>>> _______________________________________________
>>>>> List sponsored by Redwood Alliance
>>>>> 
>>>>> Pay optional member dues here: http://re-wrenches.org 
>>>>> <http://re-wrenches.org/>
>>>>> 
>>>>> List Address: [email protected] 
>>>>> <mailto:[email protected]>
>>>>> 
>>>>> Change listserver email address & settings:
>>>>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>>>>> 
>>>>> There are two list archives for searching. When one doesn't work, try the 
>>>>> other:
>>>>> https://www.mail-archive.com/[email protected]/
>>>>> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>>>>> 
>>>>> List rules & etiquette:
>>>>> http://www.re-wrenches.org/etiquette.htm
>>>>> 
>>>>> Check out or update participant bios:
>>>>> http://www.members.re-wrenches.org <http://www.members.re-wrenches.org/>
>>>>> 
>>>> 
>>>> _______________________________________________
>>>> List sponsored by Redwood Alliance
>>>> 
>>>> Pay optional member dues here: http://re-wrenches.org 
>>>> <http://re-wrenches.org/>
>>>> 
>>>> List Address: [email protected] 
>>>> <mailto:[email protected]>
>>>> 
>>>> Change listserver email address & settings:
>>>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>>>> 
>>>> There are two list archives for searching. When one doesn't work, try the 
>>>> other:
>>>> https://www.mail-archive.com/[email protected]/
>>>> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>>>> 
>>>> List rules & etiquette:
>>>> http://www.re-wrenches.org/etiquette.htm
>>>> 
>>>> Check out or update participant bios:
>>>> http://www.members.re-wrenches.org <http://www.members.re-wrenches.org/>
>>>> 
>>> _______________________________________________
>>> List sponsored by Redwood Alliance
>>> 
>>> Pay optional member dues here: http://re-wrenches.org 
>>> <http://re-wrenches.org/>
>>> 
>>> List Address: [email protected] 
>>> <mailto:[email protected]>
>>> 
>>> Change listserver email address & settings:
>>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>>> 
>>> There are two list archives for searching. When one doesn't work, try the 
>>> other:
>>> https://www.mail-archive.com/[email protected]/
>>> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>>> 
>>> List rules & etiquette:
>>> http://www.re-wrenches.org/etiquette.htm
>>> 
>>> Check out or update participant bios:
>>> http://www.members.re-wrenches.org <http://www.members.re-wrenches.org/>
>>> 
>> _______________________________________________
>> List sponsored by Redwood Alliance
>> 
>> Pay optional member dues here: http://re-wrenches.org 
>> <http://re-wrenches.org/>
>> 
>> List Address: [email protected] 
>> <mailto:[email protected]>
>> 
>> Change listserver email address & settings:
>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>> 
>> There are two list archives for searching. When one doesn't work, try the 
>> other:
>> https://www.mail-archive.com/[email protected]/
>> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>> 
>> List rules & etiquette:
>> http://www.re-wrenches.org/etiquette.htm
>> 
>> Check out or update participant bios:
>> http://www.members.re-wrenches.org <http://www.members.re-wrenches.org/>
>> 
> 
> 
> 
> --
> Chris Schaefer’s
> 
> Tel 585-229-2083 or Cell 585-748-1870 
> 5115 S Hill Road ~ Canandaigua New York 14424
> www.solarandwindfx.com <http://www.solarandwindfx.com/> ~ E-mail: 
> [email protected] <mailto:[email protected]>
> 
> Thomas Jefferson, the author of our great Constitution, once said, 
> "democracy" will cease to exist when you take away from those who are willing 
> to work and give to those who would not."
> 
> _______________________________________________
> List sponsored by Redwood Alliance
> 
> Pay optional member dues here: http://re-wrenches.org
> 
> List Address: [email protected]
> 
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
> 
> There are two list archives for searching. When one doesn't work, try the 
> other:
> https://www.mail-archive.com/[email protected]/
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
> 
> List rules & etiquette:
> http://www.re-wrenches.org/etiquette.htm
> 
> Check out or update participant bios:
> http://www.members.re-wrenches.org
> 

_______________________________________________
List sponsored by Redwood Alliance

Pay optional member dues here: http://re-wrenches.org

List Address: [email protected]

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

There are two list archives for searching. When one doesn't work, try the other:
https://www.mail-archive.com/[email protected]/
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
http://www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
http://www.members.re-wrenches.org

Reply via email to