I don’t understand how 3 inverters on a single buss could be recording such 
wildly different dc voltage readings. Regardless if the inverters are 
independent or paralleled. 

I don’t have those battereis specs but would expect absorb if there is any to 
be less than 90 minutes? 
Or did the issue occur at the exact end of absorb?

What a pain. 

Jay



> On Jan 24, 2026, at 1:36 PM, Jason Szumlanski via RE-wrenches 
> <[email protected]> wrote:
> 
> 
> I have a triple stack of off-grid Midnite AIO connected to a 60 kWh 
> lithionics battery bank (51.2V LFP) in open loop. Today the site had BMS 
> shutdowns (there are two BMSs, one for each 30 kWh stack of batteries). Both 
> BMSs shut down about 90 minutes after the solar got the batteries to 100% and 
> were just meeting loads with solar.
> 
> I got some data from Solar Assistant (attached) that shows erratic voltage 
> readings from each of the three inverters. This has never happened at this 
> site before. Some of the voltage readings exceeded 60V, which I am guessing 
> caused one or both BMS to shut off and come back on, possibly quickly. 
> 
> I do see some solar charging spikes, so it looks like the inverters would 
> detect a low battery state and start charging, raising the voltage of the 
> batteries quickly, and the process repeating itself.
> 
> Any ideas on what the source of the problem might be?
> 
> Thanks,
> 
> Jason Szumlanski 
> Florida Solar Design Group
> 
> 
> 
> <Image 1149.jpg>
> <Image 1148.jpg>
> <Image 1151.jpg>
> <Image 1150.jpg>
> _______________________________________________
> List sponsored by Redwood Alliance
> 
> Pay optional member dues here: http://re-wrenches.org
> 
> List Address: [email protected]
> 
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
> 
> There are two list archives for searching. When one doesn't work, try the 
> other:
> https://www.mail-archive.com/[email protected]/
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
> 
> List rules & etiquette:
> http://www.re-wrenches.org/etiquette.htm
> 
> Check out or update participant bios:
> http://www.members.re-wrenches.org
> 
_______________________________________________
List sponsored by Redwood Alliance

Pay optional member dues here: http://re-wrenches.org

List Address: [email protected]

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

There are two list archives for searching. When one doesn't work, try the other:
https://www.mail-archive.com/[email protected]/
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
http://www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
http://www.members.re-wrenches.org

Reply via email to