We're not the only ones wondering about best settings for LFPs. I've noticed over the years both Simpliphi and Fortress have changed their recommended charge settings substantially.  Fortress seems to have gone to a higher voltage and very low absorb time. Considering they're roughly the same cells inside on all of these, I find the variations in settings interesting.

Beware, some batteries like the Simpliphi will literally let the smoke out if they go over 60 v.  I was excited about the 15 cell (48 v nominal) HomeGrid batteries, since they would be closer to lead acid voltages. However, we ended up having quite a bit of firmware troubles, and the "outdoor" enclosure and heating left a lot to be desired.

 Like William, I don't consider myself quite an expert on LFP, but I've done systems with Blue Planet, LiFe Blue, Simpliphi, Fortress, Homegrid, and Midnite. Even though I had a hard time finding charge settings, the Midnite Powerflo 16 has been my favorite so far.  I just did a system with a Rosie and a pair of Powerflo s.  Every possible load on in the house, then kicked the well pump, and it didn't even blink the LED lights.

Ray Walters
Remote Solar

On 1/26/2026 9:51 AM, Maverick Brown via RE-wrenches wrote:
I have never believed any LFP battery maker that has 58.4V for charge voltage. That’s 3.65 Volts per cell in a 16S configuration. If you have any cell imbalance inside the pack, one cell could go above the upper limit of 3.65Vpc.

I have installed serval brands of LFP batteries, some great brands and some not as great.

In pretty much all cases, I used 3.45Vpc (55.2V) as the Absorb and then set other voltages as appropriate based on that. In several cases, I also enabled EQ and set it to 3.5Vpc (56) just to make sure that cell balancing has a chance. If the voltage is too low, you will see a wider battery to battery SOC spread. I have corrected that by increasing the Absorb time and/or bump up the ABS Voltage.

Many battery companies have been integration guides for their battery to Outback or Scheider. I have digested this to see what the ranges are for open charging. It would be good to get more details about:
 Cell balancing activation voltage
 Method for reading the cell voltages internal to batteries (a few companies have simple cables and easy apps for such, Pytes and Fortress)  Method for reading individual battery SOC (Pytes has a serial cable and an app; Fortress has Guardian comm box, and there are others)

It would be good for long term health and understanding for wrenches to have more information…

Here is my current working document on charging open loop. Let me know what you would do differently. Any suggestions are appreciated. I will send the XLS version to anyone who wants it.



Maverick Brown
Off-Grid Solar Commander since 2006
*Maverick Solar Enterprises, Inc.*
* • Solar Commander Remote Power*
* • SunFlow Systems Cathodic Protection
*[email protected]
512-460-9825

On Jan 25, 2026, at 3:48 PM, Jason Szumlanski via RE-wrenches <[email protected]> wrote:

The specs for this particular battery list a charging voltage up to 58.4V. I believe the BMS protection level is set at 60V, but I need to confirm with the manufacturer when they open on Monday.

I just noticed that the AIOs responded to a relatively high load and entered a re-bulk type of behavior. But the voltage stayed withing an acceptable range. I'm not clear on how the AIO handles re-bulk and also why the float voltage setpoint isn't being respected (or how absorb time is determined).


Jason Szumlanski
Principal Solar Designer | Florida Solar Design Group
NABCEP Certified Solar Professional (PVIP)
Florida State Certified Solar Contractor CVC56956
Florida Certified Electrical Contractor EC13013208

On Sun, Jan 25, 2026, 12:48 PM Zeke Yewdall via RE-wrenches <[email protected]> wrote:

    I see on the Lithionics spec sheet it says a charged voltage of
    57.6 volts   This seems very high for a 16 cell LFP battery.  I
    am used to using 55 to 56 volts, maybe 56.5 volts at most on a 16
    cell LFP.  I suspect that the 57.6 is the protection voltage of
    the BMS, not the appropriate absorb voltage setting.  I have seen
    this error a lot on lithium battery spec sheets, where they give
    the overvoltage protection level, which is not an appropriate
    absorb setting for typical solar equipment.

    Not everyone will agree with me, but the way I set up absorb
    voltages when doing open loop lithium battery systems is to NEVER
    let the BMS do anything.  if the BMS shuts off charging, that
    means that I already failed... the charge controller or inverter
    should have stopped charging before the BMS feels the need to
    protect the cells.  Same with low voltage disconnect... if the
    BMS shuts off due to low voltage, I already failed -- I should
    have shut the load off before the BMS felt the need to turn of
    discharge to protect the cells.  The BMS is like an airbag...only
    to react in cases of emergency when the rest of the system
    doesn't work properly.

    Open loop equipment (all of the traditional
    outback/magnum/schneider, etc stuff, plus any AIO's in open loop
    setup) is designed to always have a battery in the system to
    stabilize the DC bus voltage.  Without the stabilizing effect of
    the battery, voltage spikes can occur.  I find that many charge
    controllers, especially the midnite classic and victron ones, can
    actually keep the system fairly stable without batteries, but
    charging from inverters is more questionable, and especially
    charging from any DC generators can cause severe spikes if the
    battery disconnects. I have fried equipment when a lithium
    battery disconnected from a large kohler DC generator and the
    generator couldn't react fast enough to keep it from spiking to
    75 volts or more.  This is why you never want the BMS to
    disconnect... which means setting absorb at a level where the BMS
    never feels threatened.  Lithium battery manufactures giving the
    voltage at which the BMS disconnects as the "charge to" voltage
    does not help the situation.  That may work when charging it with
    a dedicated lithium battery charger, without anything else
    connected to the battery while it's charging.  But in a
    functioning solar system with charging from multiple sources and
    loads all occurring at the same time, we need to be smarter than
    the battery, IMO.

    Zeke

    _______________________________________________
    List sponsored by Redwood Alliance

    Pay optional member dues here: http://re-wrenches.org

    List Address: [email protected]

    Change listserver email address & settings:
    http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

    There are two list archives for searching. When one doesn't work,
    try the other:
    https://www.mail-archive.com/[email protected]/
    http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

    List rules & etiquette:
    http://www.re-wrenches.org/etiquette.htm

    Check out or update participant bios:
    http://www.members.re-wrenches.org

<51V110A-8D-MODULE-REV2 (1).pdf><Screenshot_20260125_155512_Chrome.jpg><Screenshot_20260125_155550_Chrome.jpg><Screenshot_20260125_155623_Chrome.jpg><Screenshot_20260125_155722_Chrome.jpg>_______________________________________________
List sponsored by Redwood Alliance

Pay optional member dues here: http://re-wrenches.org

List Address: [email protected]

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

There are two list archives for searching. When one doesn't work, try the other:
https://www.mail-archive.com/[email protected]/
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
http://www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
http://www.members.re-wrenches.org



_______________________________________________
List sponsored by Redwood Alliance

Pay optional member dues here:http://re-wrenches.org

List Address:[email protected]

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

There are two list archives for searching. When one doesn't work, try the other:
https://www.mail-archive.com/[email protected]/
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
http://www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
http://www.members.re-wrenches.org
_______________________________________________
List sponsored by Redwood Alliance

Pay optional member dues here: http://re-wrenches.org

List Address: [email protected]

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

There are two list archives for searching. When one doesn't work, try the other:
https://www.mail-archive.com/[email protected]/
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
http://www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
http://www.members.re-wrenches.org

Reply via email to