The design relies on a relay relaxing upon *loss* of grid voltage. This is
fail-safe.

Furthermore, Enphase can be configured to send an email if production is
lost so if the system fails as it should, in the no-production state,
someone gets notified.


William Miller
Miller Solar.com
805-438-5600
www.millersolar.com


On Tue, Jan 27, 2026 at 9:17 AM Jason Szumlanski via RE-wrenches <
[email protected]> wrote:

> I don't like to install anything that isn't failsafe for this purpose, so
> if it relies on a NC relay opening upon receiving generator voltage, I
> usually won't consider it because the relay can fail. And if the
> relay fails, there is no indication of that (other than the adverse effects
> that might happen).
>
> That's just my opinion, but I can understand fringe scenarios where there
> just isn't a way to get the solar connected on the line side. As long as
> the customer signs off on the risks, I would do it, but cautiously.
>
>
> Jason Szumlanski
> Principal Solar Designer | Florida Solar Design Group
> NABCEP Certified Solar Professional (PVIP)
> Florida State Certified Solar Contractor CVC56956
> Florida Certified Electrical Contractor EC13013208
>
>
> On Mon, Jan 26, 2026 at 4:41 PM Howard Scot Arey via RE-wrenches <
> [email protected]> wrote:
>
>> Interesting. Somebody else recommended a web-based version of what you
>> did. You were ahead of the times. I might pursue this with the web
>> option...not the radios. Same concept - different technology.
>>
>> Thank you.
>>
>> *Howard "Scot" Arey*
>> *Owner, Solar CenTex*
>>
>> NABCEP PV Installation Professional
>> TECL 29755
>> 254-300-1228
>>
>> ------------------------------
>> *From:* William Miller <[email protected]>
>> *Sent:* Monday, January 26, 2026 3:28:04 PM
>> *To:* RE-wrenches <[email protected]>
>> *Cc:* [email protected] <[email protected]>
>> *Subject:* RE: [RE-wrenches] Will IQ8 microinverters backfeed a
>> generator during grid interruptions
>>
>> Friends:
>>
>>
>>
>> I had the same problem:  Enphase arrays on an outbuilding which was
>> connected to the generator side of a transfer switch.  I had no independent
>> power path from the grid to the outbuilding so the Enphase had to be
>> connected to the load side of the transfer switch.  When the large
>> generator was powering the facility and the sun was out the generator acted
>> wonky (unstable voltage).
>>
>>
>>
>> My solution was to buy a transceiver set (National Control Devices
>> MlrXR2x).  I powered one radio from the grid side of the transfer switch
>> and the other radio controlled a contactor on the remote Enphase feeders.
>> When the grid goes down the contactor opens.
>>
>>
>>
>> The radios were inside of two buildings and the reception was
>> borderline.  I augmented the included 900 mHz rubber duckies by replacing
>> them with panel antennas from Pasternak.  So far the system is operating as
>> intended.
>>
>>
>>
>> If anyone wants details let me know.
>>
>>
>>
>> William
>>
>>
>>
>> William Miller
>>
>> Miller Solar
>>
>> www.millersolar.com
>>
>> CA License C-10 77398
>>
>>
>>
>> *From:* RE-wrenches [mailto:[email protected]] *On
>> Behalf Of *scot.arey--- via RE-wrenches
>> *Sent:* Wednesday, January 21, 2026 12:45 PM
>> *To:* RE-wrenches
>> *Cc:* [email protected]
>> *Subject:* Re: [RE-wrenches] Will IQ8 microinverters backfeed a
>> generator during grid interruptions
>>
>>
>>
>> Thanks but I'm just trying to grid-tie a small Enphase array without ESS
>> where the point of interconnection is on the customer side of the
>> generator/ATS.
>>
>> Trying to use existing wires in place to simplify and lower costs...but
>> the generator is my constraint because I need the PoI to be on line side of
>> the ATS.
>>
>>
>>
>> *Howard "Scot" Arey*
>>
>> *Owner, Solar CenTex*
>>
>> 254-300-1228
>>
>>
>> ------------------------------
>>
>> *From:* RE-wrenches <[email protected]> on
>> behalf of Jason Szumlanski via RE-wrenches <
>> [email protected]>
>> *Sent:* Wednesday, January 21, 2026 2:33 PM
>> *To:* RE-wrenches <[email protected]>
>> *Cc:* Jason Szumlanski <[email protected]>
>> *Subject:* Re: [RE-wrenches] Will IQ8 microinverters backfeed a
>> generator during grid interruptions
>>
>>
>>
>> I should have also noted that Enphase DOES allow use of a generator with
>> its System Controller 3G, and supposedly the inverter, battery, and
>> generator sources can all power loads simultaneously, so I could be wrong
>> about how the IQ8s work. That said, Enphase has strict pairing
>> specifications and an approved generator list. They seem confident in their
>> ability to limit backfeed to the generator in this scenario.
>>
>>
>>
>> Jason Szumlanski
>>
>> Principal Solar Designer | Florida Solar Design Group
>> NABCEP Certified Solar Professional (PVIP)
>> Florida State Certified Solar Contractor CVC56956
>>
>> Florida Certified Electrical Contractor EC13013208
>>
>>
>>
>>
>>
>> On Wed, Jan 21, 2026 at 3:16 PM William Bryce via RE-wrenches <
>> [email protected]> wrote:
>>
>> If the AC coupled exported energy is more than the generator produced
>> energy, it can destroy the generator controller.
>>
>> That is why most AIO inverters have a relay on the dedicated AC coupling
>> input. It will open the relay if the inverter sees generator power.
>>
>>
>>
>> The MNP AIO will allow both inputs, but will open the relay if the AC
>> coupled power increases to 20% of the Generator input (firmware dependent).
>>
>>
>>
>>
>>
>> On Wed, Jan 21, 2026 at 2:27 PM Jason Szumlanski via RE-wrenches <
>> [email protected]> wrote:
>>
>> Enphase IQ8 microinverters will absolutely leak some power back to the
>> grid when set to a no-export grid profile. How much, and if that is
>> detrimental to the generator is another question. I suspect if the
>> generator is large enough relative to the PV array, the impact will be nil,
>> but I would not take the risk.
>>
>>
>>
>> I don't think the fast switching really does the trick in terms of not
>> exporting. That function relies on the consumption CTs connected to the
>> Gateway, which in turn communicates with the microinverters. Aside from the
>> CTs not being totally accurate, I don't see how that communication loop
>> could be fast enough.
>>
>>
>>
>> Jason Szumlanski
>>
>> Principal Solar Designer | Florida Solar Design Group
>> NABCEP Certified Solar Professional (PVIP)
>> Florida State Certified Solar Contractor CVC56956
>>
>> Florida Certified Electrical Contractor EC13013208
>>
>>
>>
>>
>>
>> On Wed, Jan 21, 2026 at 12:09 PM scot.arey--- via RE-wrenches <
>> [email protected]> wrote:
>>
>> Good day,
>>
>>
>>
>> I many years ago watched the fast-switching capabilities of the IQ-8
>> microinverters to produce only what demanded of the MI, and wondered if it
>> might have application in a grid-tied system that is served by a
>> whole-house generator.
>>
>>
>>
>> We have the opportunity to install grid-tied-only array of 24 IQ8 but all
>> the MIs will be on the customer side of an auto-transfer switch and
>> generator. We want to leverage using existing building wiring to carry the
>> solar and all solar sizing meets the 120% rules.
>>
>>
>>
>> But I know that grid-tied solar on the customer load-side of the transfer
>> switch means no place for full solar power production to flow to when the
>> grid is not available...but  then I thought back to that fast switching
>> capability: is there a way to ensure the IQ8 don't backfeed a generator
>> when it is operating for a grid anomaly?
>>
>> I suspect the answer is "are you nuts???" but that video of capability
>> got me thinking, "why not?" and if not, how is it - what tells the MI to
>> cease production? - when it is within a full and proper ISC/ESS system
>> design?
>>
>>
>>
>> *Howard "Scot" Arey*
>>
>> *Owner, Solar CenTex*
>>
>>
>>
>> NABCEP PV Installation Professional
>>
>> TECL 29755
>>
>> 254-300-1228
>>
>> [image: cid:[email protected]]
>>
>>
>>
>> _______________________________________________
>> List sponsored by Redwood Alliance
>>
>> Pay optional member dues here: http://re-wrenches.org
>>
>> List Address: [email protected]
>>
>> Change listserver email address & settings:
>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>>
>> There are two list archives for searching. When one doesn't work, try the
>> other:
>> https://www.mail-archive.com/[email protected]/
>> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>>
>> List rules & etiquette:
>> http://www.re-wrenches.org/etiquette.htm
>>
>> Check out or update participant bios:
>> http://www.members.re-wrenches.org
>>
>> _______________________________________________
>> List sponsored by Redwood Alliance
>>
>> Pay optional member dues here: http://re-wrenches.org
>>
>> List Address: [email protected]
>>
>> Change listserver email address & settings:
>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>>
>> There are two list archives for searching. When one doesn't work, try the
>> other:
>> https://www.mail-archive.com/[email protected]/
>> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>>
>> List rules & etiquette:
>> http://www.re-wrenches.org/etiquette.htm
>>
>> Check out or update participant bios:
>> http://www.members.re-wrenches.org
>>
>> _______________________________________________
>> List sponsored by Redwood Alliance
>>
>> Pay optional member dues here: http://re-wrenches.org
>>
>> List Address: [email protected]
>>
>> Change listserver email address & settings:
>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>>
>> There are two list archives for searching. When one doesn't work, try the
>> other:
>> https://www.mail-archive.com/[email protected]/
>> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>>
>> List rules & etiquette:
>> http://www.re-wrenches.org/etiquette.htm
>>
>> Check out or update participant bios:
>> http://www.members.re-wrenches.org
>>
>>
>> _______________________________________________
>> List sponsored by Redwood Alliance
>>
>> Pay optional member dues here: http://re-wrenches.org
>>
>> List Address: [email protected]
>>
>> Change listserver email address & settings:
>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>>
>> There are two list archives for searching. When one doesn't work, try the
>> other:
>> https://www.mail-archive.com/[email protected]/
>> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>>
>> List rules & etiquette:
>> http://www.re-wrenches.org/etiquette.htm
>>
>> Check out or update participant bios:
>> http://www.members.re-wrenches.org
>>
>> _______________________________________________
> List sponsored by Redwood Alliance
>
> Pay optional member dues here: http://re-wrenches.org
>
> List Address: [email protected]
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> There are two list archives for searching. When one doesn't work, try the
> other:
> https://www.mail-archive.com/[email protected]/
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>
> List rules & etiquette:
> http://www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> http://www.members.re-wrenches.org
>
>
_______________________________________________
List sponsored by Redwood Alliance

Pay optional member dues here: http://re-wrenches.org

List Address: [email protected]

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

There are two list archives for searching. When one doesn't work, try the other:
https://www.mail-archive.com/[email protected]/
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
http://www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
http://www.members.re-wrenches.org

Reply via email to