Yes, that’s the way to do it. I suppose there is still the chance, however,
that the grid could still be present, but the transfer switch is still in
off-grid mode (like if the main breaker is turned off for some reason).
That could still result in AC coupled solar backfeeding a generator if
close attention is not paid to the relay coil source relative to all
disconnects in a system.


Jason Szumlanski
Principal Solar Designer | Florida Solar Design Group
NABCEP Certified Solar Professional (PVIP)
Florida State Certified Solar Contractor CVC56956
Florida Certified Electrical Contractor EC13013208


On Tue, Jan 27, 2026 at 1:07 PM William Miller <[email protected]>
wrote:

> The design relies on a relay relaxing upon *loss* of grid voltage. This
> is fail-safe.
>
> Furthermore, Enphase can be configured to send an email if production is
> lost so if the system fails as it should, in the no-production state,
> someone gets notified.
>
>
>
> William Miller
> Miller Solar.com
> 805-438-5600
> www.millersolar.com
>
>
> On Tue, Jan 27, 2026 at 9:17 AM Jason Szumlanski via RE-wrenches <
> [email protected]> wrote:
>
>> I don't like to install anything that isn't failsafe for this purpose, so
>> if it relies on a NC relay opening upon receiving generator voltage, I
>> usually won't consider it because the relay can fail. And if the
>> relay fails, there is no indication of that (other than the adverse effects
>> that might happen).
>>
>> That's just my opinion, but I can understand fringe scenarios where there
>> just isn't a way to get the solar connected on the line side. As long as
>> the customer signs off on the risks, I would do it, but cautiously.
>>
>>
>> Jason Szumlanski
>> Principal Solar Designer | Florida Solar Design Group
>> NABCEP Certified Solar Professional (PVIP)
>> Florida State Certified Solar Contractor CVC56956
>> Florida Certified Electrical Contractor EC13013208
>>
>>
>> On Mon, Jan 26, 2026 at 4:41 PM Howard Scot Arey via RE-wrenches <
>> [email protected]> wrote:
>>
>>> Interesting. Somebody else recommended a web-based version of what you
>>> did. You were ahead of the times. I might pursue this with the web
>>> option...not the radios. Same concept - different technology.
>>>
>>> Thank you.
>>>
>>> *Howard "Scot" Arey*
>>> *Owner, Solar CenTex*
>>>
>>> NABCEP PV Installation Professional
>>> TECL 29755
>>> 254-300-1228
>>>
>>> ------------------------------
>>> *From:* William Miller <[email protected]>
>>> *Sent:* Monday, January 26, 2026 3:28:04 PM
>>> *To:* RE-wrenches <[email protected]>
>>> *Cc:* [email protected] <[email protected]>
>>> *Subject:* RE: [RE-wrenches] Will IQ8 microinverters backfeed a
>>> generator during grid interruptions
>>>
>>> Friends:
>>>
>>>
>>>
>>> I had the same problem:  Enphase arrays on an outbuilding which was
>>> connected to the generator side of a transfer switch.  I had no independent
>>> power path from the grid to the outbuilding so the Enphase had to be
>>> connected to the load side of the transfer switch.  When the large
>>> generator was powering the facility and the sun was out the generator acted
>>> wonky (unstable voltage).
>>>
>>>
>>>
>>> My solution was to buy a transceiver set (National Control Devices
>>> MlrXR2x).  I powered one radio from the grid side of the transfer switch
>>> and the other radio controlled a contactor on the remote Enphase feeders.
>>> When the grid goes down the contactor opens.
>>>
>>>
>>>
>>> The radios were inside of two buildings and the reception was
>>> borderline.  I augmented the included 900 mHz rubber duckies by replacing
>>> them with panel antennas from Pasternak.  So far the system is operating as
>>> intended.
>>>
>>>
>>>
>>> If anyone wants details let me know.
>>>
>>>
>>>
>>> William
>>>
>>>
>>>
>>> William Miller
>>>
>>> Miller Solar
>>>
>>> www.millersolar.com
>>>
>>> CA License C-10 77398
>>>
>>>
>>>
>>> *From:* RE-wrenches [mailto:[email protected]] *On
>>> Behalf Of *scot.arey--- via RE-wrenches
>>> *Sent:* Wednesday, January 21, 2026 12:45 PM
>>> *To:* RE-wrenches
>>> *Cc:* [email protected]
>>> *Subject:* Re: [RE-wrenches] Will IQ8 microinverters backfeed a
>>> generator during grid interruptions
>>>
>>>
>>>
>>> Thanks but I'm just trying to grid-tie a small Enphase array without ESS
>>> where the point of interconnection is on the customer side of the
>>> generator/ATS.
>>>
>>> Trying to use existing wires in place to simplify and lower costs...but
>>> the generator is my constraint because I need the PoI to be on line side of
>>> the ATS.
>>>
>>>
>>>
>>> *Howard "Scot" Arey*
>>>
>>> *Owner, Solar CenTex*
>>>
>>> 254-300-1228
>>>
>>>
>>> ------------------------------
>>>
>>> *From:* RE-wrenches <[email protected]> on
>>> behalf of Jason Szumlanski via RE-wrenches <
>>> [email protected]>
>>> *Sent:* Wednesday, January 21, 2026 2:33 PM
>>> *To:* RE-wrenches <[email protected]>
>>> *Cc:* Jason Szumlanski <[email protected]>
>>> *Subject:* Re: [RE-wrenches] Will IQ8 microinverters backfeed a
>>> generator during grid interruptions
>>>
>>>
>>>
>>> I should have also noted that Enphase DOES allow use of a generator with
>>> its System Controller 3G, and supposedly the inverter, battery, and
>>> generator sources can all power loads simultaneously, so I could be wrong
>>> about how the IQ8s work. That said, Enphase has strict pairing
>>> specifications and an approved generator list. They seem confident in their
>>> ability to limit backfeed to the generator in this scenario.
>>>
>>>
>>>
>>> Jason Szumlanski
>>>
>>> Principal Solar Designer | Florida Solar Design Group
>>> NABCEP Certified Solar Professional (PVIP)
>>> Florida State Certified Solar Contractor CVC56956
>>>
>>> Florida Certified Electrical Contractor EC13013208
>>>
>>>
>>>
>>>
>>>
>>> On Wed, Jan 21, 2026 at 3:16 PM William Bryce via RE-wrenches <
>>> [email protected]> wrote:
>>>
>>> If the AC coupled exported energy is more than the generator produced
>>> energy, it can destroy the generator controller.
>>>
>>> That is why most AIO inverters have a relay on the dedicated AC coupling
>>> input. It will open the relay if the inverter sees generator power.
>>>
>>>
>>>
>>> The MNP AIO will allow both inputs, but will open the relay if the AC
>>> coupled power increases to 20% of the Generator input (firmware dependent).
>>>
>>>
>>>
>>>
>>>
>>> On Wed, Jan 21, 2026 at 2:27 PM Jason Szumlanski via RE-wrenches <
>>> [email protected]> wrote:
>>>
>>> Enphase IQ8 microinverters will absolutely leak some power back to the
>>> grid when set to a no-export grid profile. How much, and if that is
>>> detrimental to the generator is another question. I suspect if the
>>> generator is large enough relative to the PV array, the impact will be nil,
>>> but I would not take the risk.
>>>
>>>
>>>
>>> I don't think the fast switching really does the trick in terms of not
>>> exporting. That function relies on the consumption CTs connected to the
>>> Gateway, which in turn communicates with the microinverters. Aside from the
>>> CTs not being totally accurate, I don't see how that communication loop
>>> could be fast enough.
>>>
>>>
>>>
>>> Jason Szumlanski
>>>
>>> Principal Solar Designer | Florida Solar Design Group
>>> NABCEP Certified Solar Professional (PVIP)
>>> Florida State Certified Solar Contractor CVC56956
>>>
>>> Florida Certified Electrical Contractor EC13013208
>>>
>>>
>>>
>>>
>>>
>>> On Wed, Jan 21, 2026 at 12:09 PM scot.arey--- via RE-wrenches <
>>> [email protected]> wrote:
>>>
>>> Good day,
>>>
>>>
>>>
>>> I many years ago watched the fast-switching capabilities of the IQ-8
>>> microinverters to produce only what demanded of the MI, and wondered if it
>>> might have application in a grid-tied system that is served by a
>>> whole-house generator.
>>>
>>>
>>>
>>> We have the opportunity to install grid-tied-only array of 24 IQ8 but
>>> all the MIs will be on the customer side of an auto-transfer switch and
>>> generator. We want to leverage using existing building wiring to carry the
>>> solar and all solar sizing meets the 120% rules.
>>>
>>>
>>>
>>> But I know that grid-tied solar on the customer load-side of the
>>> transfer switch means no place for full solar power production to flow to
>>> when the grid is not available...but  then I thought back to that fast
>>> switching capability: is there a way to ensure the IQ8 don't backfeed a
>>> generator when it is operating for a grid anomaly?
>>>
>>> I suspect the answer is "are you nuts???" but that video of capability
>>> got me thinking, "why not?" and if not, how is it - what tells the MI to
>>> cease production? - when it is within a full and proper ISC/ESS system
>>> design?
>>>
>>>
>>>
>>> *Howard "Scot" Arey*
>>>
>>> *Owner, Solar CenTex*
>>>
>>>
>>>
>>> NABCEP PV Installation Professional
>>>
>>> TECL 29755
>>>
>>> 254-300-1228
>>>
>>> [image: cid:[email protected]]
>>>
>>>
>>>
>>> _______________________________________________
>>> List sponsored by Redwood Alliance
>>>
>>> Pay optional member dues here: http://re-wrenches.org
>>>
>>> List Address: [email protected]
>>>
>>> Change listserver email address & settings:
>>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>>>
>>> There are two list archives for searching. When one doesn't work, try
>>> the other:
>>> https://www.mail-archive.com/[email protected]/
>>> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>>>
>>> List rules & etiquette:
>>> http://www.re-wrenches.org/etiquette.htm
>>>
>>> Check out or update participant bios:
>>> http://www.members.re-wrenches.org
>>>
>>> _______________________________________________
>>> List sponsored by Redwood Alliance
>>>
>>> Pay optional member dues here: http://re-wrenches.org
>>>
>>> List Address: [email protected]
>>>
>>> Change listserver email address & settings:
>>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>>>
>>> There are two list archives for searching. When one doesn't work, try
>>> the other:
>>> https://www.mail-archive.com/[email protected]/
>>> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>>>
>>> List rules & etiquette:
>>> http://www.re-wrenches.org/etiquette.htm
>>>
>>> Check out or update participant bios:
>>> http://www.members.re-wrenches.org
>>>
>>> _______________________________________________
>>> List sponsored by Redwood Alliance
>>>
>>> Pay optional member dues here: http://re-wrenches.org
>>>
>>> List Address: [email protected]
>>>
>>> Change listserver email address & settings:
>>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>>>
>>> There are two list archives for searching. When one doesn't work, try
>>> the other:
>>> https://www.mail-archive.com/[email protected]/
>>> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>>>
>>> List rules & etiquette:
>>> http://www.re-wrenches.org/etiquette.htm
>>>
>>> Check out or update participant bios:
>>> http://www.members.re-wrenches.org
>>>
>>>
>>> _______________________________________________
>>> List sponsored by Redwood Alliance
>>>
>>> Pay optional member dues here: http://re-wrenches.org
>>>
>>> List Address: [email protected]
>>>
>>> Change listserver email address & settings:
>>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>>>
>>> There are two list archives for searching. When one doesn't work, try
>>> the other:
>>> https://www.mail-archive.com/[email protected]/
>>> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>>>
>>> List rules & etiquette:
>>> http://www.re-wrenches.org/etiquette.htm
>>>
>>> Check out or update participant bios:
>>> http://www.members.re-wrenches.org
>>>
>>> _______________________________________________
>> List sponsored by Redwood Alliance
>>
>> Pay optional member dues here: http://re-wrenches.org
>>
>> List Address: [email protected]
>>
>> Change listserver email address & settings:
>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>>
>> There are two list archives for searching. When one doesn't work, try the
>> other:
>> https://www.mail-archive.com/[email protected]/
>> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>>
>> List rules & etiquette:
>> http://www.re-wrenches.org/etiquette.htm
>>
>> Check out or update participant bios:
>> http://www.members.re-wrenches.org
>>
>>
_______________________________________________
List sponsored by Redwood Alliance

Pay optional member dues here: http://re-wrenches.org

List Address: [email protected]

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

There are two list archives for searching. When one doesn't work, try the other:
https://www.mail-archive.com/[email protected]/
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
http://www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
http://www.members.re-wrenches.org

Reply via email to