Hi drake

Unless you have high elevation or edge of cloud, you should be good to go. 
Max short circuit is 25 amps fyi. 

I’ve always recommended the 12kw. Only slightly more expensive but gives lots 
better out of balance load rating than the 6kw. 

Jay

> On Jul 14, 2026, at 9:02 AM, Drake Chamberlin via RE-wrenches 
> <[email protected]> wrote:
> 
> 
> 
> I am looking for a module to use with an EG4 6000 XP inverter. The module I 
> am looking at has an Isc of 14.47 A. Multiplied by 1.56, that comes out to 
> 22.6 A. The max current allowed on the PV input is 17 A?
>  
> A distributor thought it would be fine to use this combination. Do you think 
> it would be safe?
>  
> Thank you,
>  
> Drake 
>  
> Drake Chamberlin
> 
> Athens Electric LLC
> 
> Ohio Electrical Contractor’s License 44810
> 
> NABCEP Certified PV Installation Professional
> 
>  
> --
>  
> _______________________________________________
> List sponsored by Redwood Alliance
> 
> Pay optional member dues here: http://re-wrenches.org
> 
> List Address: [email protected]
> 
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
> 
> There are two list archives for searching. When one doesn't work, try the 
> other:
> https://www.mail-archive.com/[email protected]/
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
> 
> List rules & etiquette:
> http://www.re-wrenches.org/etiquette.htm
> 
> Check out or update participant bios:
> http://www.members.re-wrenches.org
> 
_______________________________________________
List sponsored by Redwood Alliance

Pay optional member dues here: http://re-wrenches.org

List Address: [email protected]

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

There are two list archives for searching. When one doesn't work, try the other:
https://www.mail-archive.com/[email protected]/
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
http://www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
http://www.members.re-wrenches.org

Reply via email to