25 A Isc is good. Thanks for pointing that out. I will consider using the 12KW. I noticed that it accepts a lower voltage for the PV input, but 2 strings can go on each MPPT.

On 2026-07-14 11:23, Jay via RE-wrenches wrote:

Hi drake

Unless you have high elevation or edge of cloud, you should be good to
go.
Max short circuit is 25 amps fyi.

I've always recommended the 12kw. Only slightly more expensive but
gives lots better out of balance load rating than the 6kw.

Jay

On Jul 14, 2026, at 9:02 AM, Drake Chamberlin via RE-wrenches
<[email protected]> wrote:

I am looking for a module to use with an EG4 6000 XP inverter. The
module I am looking at has an Isc of 14.47 A. Multiplied by 1.56,
that comes out to 22.6 A. The max current allowed on the PV input is
17 A?

A distributor thought it would be fine to use this combination. Do
you think it would be safe?

Thank you,

Drake