Wrenches,
I've done a few SI to Li set ups, One must do is to eliminate the BTS with
resistor to get 75⁰F
Funtimes

On Fri, Sep 11, 2026, 10:15 AM Lou Russo <[email protected]> wrote:

> What brand of batteries are you using?
>
> There is no way to get an accurate SOC on an SI paired with lithium
> batteries without closed-loop comms nor is there a means to adjust voltage
> setpoints for generator start.
>
> Every decision the SI makes is based on SOC.
>
> As far as I can tell, when selecting the battery type
> when commissioning the SI, it loads pre-determined setting (none of which
> are documented) that SMA has decided on and they can not be changed. So if
> you select FLA or VRLA and use lithium it will never work quite right.
>
> The only lithium batteries I have every used with a SI is Discover Energy
> lithium batteries and their Lynk 2. So my experience is limited in this
> regard but the combo works well for me.
> Lead-acid batteries also work great.
>
> The SI is a unique beast. Programming it is very different from other
> inverters from that time period.
>
> Lou Russo
> Owner
> [email protected]
> Office - 808 345 6762
> Direct Line - 808 731 1907
> Spree Solar Systems LLC
> CT-34322
>
>
>
> On Fri, Sep 11, 2026 at 4:04 AM Jim Gowdy <[email protected]>
> wrote:
>
>> Good Morning,
>>      I've integrated some lithium battery cells to a single Sunny Island
>> inverter (model SI4548-US-10) and I'm having an issue with the Sunny
>> Island's SOC.  My batteries will be at pretty much full charge and the
>> inverter will show something like 50% SOC and it's causing me problems of
>> starting the generator prematurely and one time it shut the system down.  I
>> am still looking through the manual, but I was wondering if there is a way
>> to calibrate the state of charge or use battery voltage for my setpoints.
>> I'm timid to call their tech support because these batteries are not on
>> their approved list.  Any input would be appreciated.
>>
>> --
>> Jim with Gowdy Electric
>> Cambria, Ca 93428
>> business  805 927 2630 <(805)%20927-2630>
>> cell  805 975 5279 <(805)%20975-5279>
>> _______________________________________________
>> List sponsored by Redwood Alliance
>>
>> Pay optional member dues here: http://re-wrenches.org
>>
>> List Address: [email protected]
>>
>> Change listserver email address & settings:
>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>>
>> There are two list archives for searching. When one doesn't work, try the
>> other:
>> https://www.mail-archive.com/[email protected]/
>> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>>
>> List rules & etiquette:
>> http://www.re-wrenches.org/etiquette.htm
>>
>> Check out or update participant bios:
>> http://www.members.re-wrenches.org
>>
> _______________________________________________
> List sponsored by Redwood Alliance
>
> Pay optional member dues here: http://re-wrenches.org
>
> List Address: [email protected]
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> There are two list archives for searching. When one doesn't work, try the
> other:
> https://www.mail-archive.com/[email protected]/
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>
> List rules & etiquette:
> http://www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> http://www.members.re-wrenches.org
>
_______________________________________________
List sponsored by Redwood Alliance

Pay optional member dues here: http://re-wrenches.org

List Address: [email protected]

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

There are two list archives for searching. When one doesn't work, try the other:
https://www.mail-archive.com/[email protected]/
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
http://www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
http://www.members.re-wrenches.org

Reply via email to