Id recommend taking the generator start duties away from the sunny Island
if you don't have a BMS that can communicate.

Id recommend using a Victron Ekrano (or whichever gx device) coupled with a
smart shunt to measure current flow and calculate state of charge. This can
calculate soc nicely and start your generator. It can also be accessed
remotely.

As far as I know, there is no setting that can allow the soc on the Sunny
Island to be accurate with lithium.

Good luck




Mac Lewis

*"Yo solo sé que no sé nada." -Sócrates*

On Fri, Sep 11, 2026, 4:38 PM Jerry Shafer <[email protected]> wrote:

> Wrenches,
> I've done a few SI to Li set ups, One must do is to eliminate the BTS with
> resistor to get 75⁰F
> Funtimes
>
> On Fri, Sep 11, 2026, 10:15 AM Lou Russo <[email protected]>
> wrote:
>
>> What brand of batteries are you using?
>>
>> There is no way to get an accurate SOC on an SI paired with lithium
>> batteries without closed-loop comms nor is there a means to adjust voltage
>> setpoints for generator start.
>>
>> Every decision the SI makes is based on SOC.
>>
>> As far as I can tell, when selecting the battery type
>> when commissioning the SI, it loads pre-determined setting (none of which
>> are documented) that SMA has decided on and they can not be changed. So if
>> you select FLA or VRLA and use lithium it will never work quite right.
>>
>> The only lithium batteries I have every used with a SI is Discover Energy
>> lithium batteries and their Lynk 2. So my experience is limited in this
>> regard but the combo works well for me.
>> Lead-acid batteries also work great.
>>
>> The SI is a unique beast. Programming it is very different from other
>> inverters from that time period.
>>
>> Lou Russo
>> Owner
>> [email protected]
>> Office - 808 345 6762
>> Direct Line - 808 731 1907
>> Spree Solar Systems LLC
>> CT-34322
>>
>>
>>
>> On Fri, Sep 11, 2026 at 4:04 AM Jim Gowdy <[email protected]>
>> wrote:
>>
>>> Good Morning,
>>>      I've integrated some lithium battery cells to a single Sunny Island
>>> inverter (model SI4548-US-10) and I'm having an issue with the Sunny
>>> Island's SOC.  My batteries will be at pretty much full charge and the
>>> inverter will show something like 50% SOC and it's causing me problems of
>>> starting the generator prematurely and one time it shut the system down.  I
>>> am still looking through the manual, but I was wondering if there is a way
>>> to calibrate the state of charge or use battery voltage for my setpoints.
>>> I'm timid to call their tech support because these batteries are not on
>>> their approved list.  Any input would be appreciated.
>>>
>>> --
>>> Jim with Gowdy Electric
>>> Cambria, Ca 93428
>>> business  805 927 2630 <(805)%20927-2630>
>>> cell  805 975 5279 <(805)%20975-5279>
>>> _______________________________________________
>>> List sponsored by Redwood Alliance
>>>
>>> Pay optional member dues here: http://re-wrenches.org
>>>
>>> List Address: [email protected]
>>>
>>> Change listserver email address & settings:
>>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>>>
>>> There are two list archives for searching. When one doesn't work, try
>>> the other:
>>> https://www.mail-archive.com/[email protected]/
>>> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>>>
>>> List rules & etiquette:
>>> http://www.re-wrenches.org/etiquette.htm
>>>
>>> Check out or update participant bios:
>>> http://www.members.re-wrenches.org
>>>
>> _______________________________________________
>> List sponsored by Redwood Alliance
>>
>> Pay optional member dues here: http://re-wrenches.org
>>
>> List Address: [email protected]
>>
>> Change listserver email address & settings:
>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>>
>> There are two list archives for searching. When one doesn't work, try the
>> other:
>> https://www.mail-archive.com/[email protected]/
>> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>>
>> List rules & etiquette:
>> http://www.re-wrenches.org/etiquette.htm
>>
>> Check out or update participant bios:
>> http://www.members.re-wrenches.org
>>
> _______________________________________________
> List sponsored by Redwood Alliance
>
> Pay optional member dues here: http://re-wrenches.org
>
> List Address: [email protected]
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> There are two list archives for searching. When one doesn't work, try the
> other:
> https://www.mail-archive.com/[email protected]/
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>
> List rules & etiquette:
> http://www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> http://www.members.re-wrenches.org
>
_______________________________________________
List sponsored by Redwood Alliance

Pay optional member dues here: http://re-wrenches.org

List Address: [email protected]

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

There are two list archives for searching. When one doesn't work, try the other:
https://www.mail-archive.com/[email protected]/
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
http://www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
http://www.members.re-wrenches.org

Reply via email to