I know this has been discussed before-
   
  If you go the route of a 12 battery system tied to the power supply- what is 
the best way to handle the 9.6v on a Micor repeater?
   
  Tom
  W9SRV

Lee <[EMAIL PROTECTED]> wrote:
  Don and all,

I work as a computer IT technician and have used older computer UPS 
supplies for a number of different applications. It's easy to hook 
up a couple of standard lead-acid batteries from Wal-Mart to these 
and gain extra run-time capacity than the original batteries 
provided. 

But a couple of things I've noticed. The charging voltage the UPS 
provides to the batteries is a bit higher than I like and usually 
slow-cooks the batteries giving a life expectency of about 3 years. 
Also, even when lightly loaded, the run-time of a typical UPS is not 
very impressive. 

I used one of these set-ups at my repeater site but found it didn't 
work as well as I hoped. I reasoned that if I ran the repeater and 
controllers on just batteries I didn't like what happened to 
the controllers as the battery voltage faded into the sunset - I 
wanted everything, especially the controllers to completly power off 
at a certain voltage - so I tried a UPS. Well, at the first power 
outage the controller and repeater ran a couple of hours and shut 
down as planned but when the AC returned it never came back up. A 
trip to the site found that the UPS was squaking its alarm. Hitting 
the power-up button brought everything up for a few seconds but 
everything shut back down when the UPS tried to do a self-test. I 
guessed that the batteries had not recharged enough to pass the self 
test. I bypassed the UPS to get everything back on the air. 

I've since gone back to having the 12v batteries connected directly 
to my repeater power supply but I've built a simple little 
comparator circuit that monitors the battery voltage and if it falls 
below 11.5 volts it removes the power to the controllers - 
effectively shutting down the repeater. I've also put relays into 
the repeaters power amplifiers that drop the PA from full power to 
about 1 watt output. These relays engage when the AC goes out and 
greatly reduce the current draw from the batteries when the AC is 
off. This works much cleaner than using a UPS and the repeater has 
run off of batteries for DAYS instead of HOURS with this 
configuration. YMMV

Lee

--- In [email protected], Mike Morris WA6ILQ 
wrote:
>
> At 09:37 AM 05/23/07, you wrote:
> >Hello all,
> >
> >I'm in the process of rebuilding one of my repeaters and I'm 
looking 
> >to place a UPS in line for backup.
> >
> >I'm looking for information on make and models - what's good and 
> >what to stay away from. The VA range is 1300 to 1500, and I'm 
> >willing to spend no more than $200.00.
> >
> >Thoughts and comments appreciated.
> >
> >TIA,
> >
> >Don, KD9PT
> 
> For a cheap UPS talk to any of your friend in the IT world. There
> are enough uninformed "technicians" (and it use that term 
generously)
> in the IT universe that have no idea as to which end of a 
screwdriver is
> the handle...
> When a UPS dies (at about the 3 years point) they just throw it 
away
> and buy a new one. In fact I just recently "re-batteried" a 
several APC
> "Back-UPS PRO 1000" units for a client.
> 
> Three comments of warning about APC:
> 1) They pass all the AC line junk through the unit (via relay 
contacts)
> until there is a brownout (i.e. low AC voltage) or an outage (no 
AC voltage).
> Then the inverter fires up, and the relay switches over. You WILL 
have an
> outage as long as one to two tenths of a second. I've seen 
desktops and
> servers reboot under those conditions (usually mans that the 
computer
> power supply has dying caps, which is a whole 'nother problem).
> 2) APC runs the batteries hard. Plan on replacing them every 3 
years.
> 3) They over-rate their units. Rarely does any APC give you over
> 25-30 minutes of run-time. They are designed to provide graceful
> shutdown time, not to ride out an outage of any length. Graceful
> shutdown means that the server power cord is plugged into the UPS,
> and a serial port is plugged into the DB9 jack in the back of the
> UPS (via a special cable they sell, one that has a transistorized
> circuit buried in one of the molded rubber shells). When the power
> fails the UPS sends a signal to the server over the serial port
> announcing power fail (they simply change the CD signal from
> active to inactive).
> In a properly designed network the server messages all the users
> and gives them 5 minutes to save the current work and log out.
> Then the server shuts down before the battery runs out (or in
> large data centers the generator starts up).
> 
> The biggest problem with using an IT UPS in a solid state
> repeater environment is efficiency. You are running
> AC to 12 or 24 or 48V DC and then back to AC into the
> repeater power supply which makes 12vDC.
> 
> The better way is to simply use the batteries directly on
> the repeater - just use a Absorbed Glass Mat battery
> (also known as an AGM battery) and float it across the
> repeater power buss. The efficiency goes up, if you are
> paying the AC power bill your wallet is happier, and you
> get zero switchover time.
> 
> A compromise design that I've seen has the repeater
> power supply and the backup battery diode OR'd to
> the repeater itself with 75amp stud-mount diodes
> (from a dead fire truck alternator), with an IOTA brand
> charger on the backup battery (which was a bank of
> glass-cased Exide telephone central office style
> batteries - 5 gallons of electrolyte per cell)
> 
> So my recommendation, if you have a solid state repeater,
> is an AGM battery with a IOTA power supply / charger.
> Don't save money on the charger - a good one will last,
> a cheap one won't and may take your battery bank with it.
> A good IOTA power supply / charger is NOT a waste of
> money and a cheap one is false economy.
> 
> Mike WA6ILQ
>







Yahoo! Groups Links