I added a 130 Volt MOV across the hot and neutral
of an Astron 50 Amp power supply for a repeater
and had an interesting effect.

We lost AC power and switched over to the generator.
When the load was added to the generator, the Onan's
voltage sagged a bit and the throttle opened to
bring the speed back.  It overshot slightly and was
high enough to trip the MOV.  That short slowed the
generator down until the voltage was too low and
then the generator sped up again.  And again it fired
the MOV and slowed down until it cleared.  It kept
oscillating with huge voltage swings until I unplugged
the Astron power supply.

Sigh.


kq7dx wrote:
>  
> 
> Hello to group,
> Is putting a MOV from hot to ground, neutral to ground, on the primary 
> of the transformer of the power supply a good idea..
> I have a ICE surge suppressor on in front as well but thought I would 
> put more inside the supply for back up.
> 
> Also, are the MOVs that radio shack sell any good. Rated at 130VAC. Any 
> body used them...
> 
> Last question: when MOVs fail or take a surge do they fail in a shorted 
> condition taking out the fuse till the MOV can be replaced, or do they 
> blow or fail open leaving the supply working.
> 
> Thanks for the help..
> 73s
> 

Reply via email to