RE: [EXTERNAL] Re: C-Clamp Hangers

2020-08-26 Thread Prahl, Craig/GVL via Sprinklerforum
What do the specs say you're supposed to use in place of c-clamps?

Craig Prahl | Jacobs | Group Lead/SME - Fire Protection | 864.676.5252 | 
craig.pr...@jacobs.com | www.jacobs.com
1041 East Butler Road   Greenville, South Carolina  29606

> -Original Message-
> From: Sprinklerforum 
> On Behalf Of Jerry Van Kolken via Sprinklerforum
> Sent: Wednesday, August 26, 2020 12:52 PM
> To: sprinklerforum@lists.firesprinkler.org
> Cc: jvankol...@mfpc.us
> Subject: C-Clamp Hangers
>
> Does anyone know the reasoning Why you would not be allowed to use
> C-Clamps for your hanger attachments?
>
>
>
> I've had a couple of specs have this requirement pass by my desk recently.
>
>
>
> Jerry Van Kolken
>
> Millennium Fire Protection Corp.
>
> 2950 San Luis Rey Rd.
>
> Oceanside, CA 92058
>
> (760) 722-2722 FX 722-2730
>
>
>



NOTICE - This communication may contain confidential and privileged information 
that is for the sole use of the intended recipient. Any viewing, copying or 
distribution of, or reliance on this message by unintended recipients is 
strictly prohibited. If you have received this message in error, please notify 
us immediately by replying to the message and deleting it from your computer.
___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org


Re: C-Clamp Hangers

2020-08-26 Thread John Denhardt via Sprinklerforum
I think Ryan is onto the issue.  If it is in the specification, request
clarification from the engineer.  A large percentage of time, the engineer
is not clear enough when the specification is written.

Thanks,
John

John August Denhardt, PE
*Vice President, Engineering and Technical Services*

*American Fire Sprinkler Association*
m: p: 301-343-1457
214-349-5965 ext 121
w: firesprinkler.org
<https://www.facebook.com/firesprinkler.org/>
<https://twitter.com/afsa/status/1039528345367732224>
<https://www.linkedin.com/company/american-fire-sprinkler-association-afsa-/>
   <https://www.instagram.com/firesprinklerorg/>

*Our members are at the heart of everything we do.*

*AFSA Summer Sale!*

For a limited time only, AFSA is offering members up to 50% off its
on-demand recorded webinars! Featuring the most sought-after thought
leaders, AFSA On-Demand offers a superior learning experience with ability
to earn CEU and CPD credits anytime, anywhere. Visit
http://www.firesprinkler.org/ondemand to learn more.


On Wed, Aug 26, 2020 at 2:30 PM Jerry Van Kolken via Sprinklerforum <
sprinklerforum@lists.firesprinkler.org> wrote:

> Ryan,
> That was my thinking. We always us the restraining straps  on our hanger
> assemblies.
>
> Mike,
> The products I'm using are listed. This is a requirement from the client
> side.
>
>
>
> Jerry Van Kolken
> Millennium Fire Protection Corp.
> 2950 San Luis Rey Rd.
> Oceanside, CA 92058
> (760) 722-2722 FX 722-2730
>
> -Original Message-
> From: Sprinklerforum  On
> Behalf Of Hinson, Ryan via Sprinklerforum
> Sent: Wednesday, August 26, 2020 11:11 AM
> To: sprinklerforum@lists.firesprinkler.org
> Cc: Hinson, Ryan 
> Subject: RE: C-Clamp Hangers
>
> Hanger attachments are being confused with bracing attachments.
> -   NFPA 13 (2019) Section 18.5.11.10 explicitly DOES NOT allow
> C-clamps
> used for seismic bracing structural attachments with or without
> restraining straps unless specifically listed for such use.
> -   Section 18.7.1 allows their use for hangers in seismically active
> areas when a restraining strap is included.
> -   Chapter 17 explicitly DOES allow listed use of c-clamps for hangers
> alone.
>
> See commentary for further discussion and pictures depicting their allowed
> hanger usage.
>
> Hope this helps,
>
> Ryan L. Hinson, PE*, SET**  \  Burns & McDonnell Senior Fire Protection
> Engineer O 952-656-3662 \  M 763-688-4045 \  F 952-229-2923
> rhin...@burnsmcd.com  \  burnsmcd.com
> 8201 Norman Center Drive, Suite 500  \  Minneapolis-St. Paul, MN 55437
> *Registered in: LA, MD, MN, PA, TX, & UT **NICET IV - Water-Based Systems
> Layout
>
>
>
> -Original Message-
> From: Sprinklerforum  On
> Behalf Of Jerry Van Kolken via Sprinklerforum
> Sent: Wednesday, August 26, 2020 12:52 PM
> To: sprinklerforum@lists.firesprinkler.org
> Cc: jvankol...@mfpc.us
> Subject: C-Clamp Hangers
>
> Does anyone know the reasoning Why you would not be allowed to use C-Clamps
> for your hanger attachments?
>
>
>
> I've had a couple of specs have this requirement pass by my desk recently.
>
>
>
> Jerry Van Kolken
>
> Millennium Fire Protection Corp.
>
> 2950 San Luis Rey Rd.
>
> Oceanside, CA 92058
>
> (760) 722-2722 FX 722-2730
>
>
>
> ___
> Sprinklerforum mailing list
> Sprinklerforum@lists.firesprinkler.org
>
> https://nam05.safelinks.protection.outlook.com/?url=http%3A%2F%2Flists.fires
> prinkler.org%2Flistinfo.cgi%2Fsprinklerforum-firesprinkler.org
> data=02%7
> C01%7Crhinson%40burnsmcd.com
> %7C1d14008726f74fa34d4308d849e89359%7Cbfbb9a2b6d
>
> 994e78b3c795005d555c8b%7C0%7C0%7C637340610543326549sdata=%2Bt0YUDv8iKf9
> xPab8hEUmLbdCBOX%2FIZ5VDKB7jaeLls%3Dreserved=0
> ___
> Sprinklerforum mailing list
> Sprinklerforum@lists.firesprinkler.org
>
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
>
> ___
> Sprinklerforum mailing list
> Sprinklerforum@lists.firesprinkler.org
>
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
>
___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org


RE: C-Clamp Hangers

2020-08-26 Thread Jerry Van Kolken via Sprinklerforum
Ryan,
That was my thinking. We always us the restraining straps  on our hanger
assemblies.

Mike, 
The products I'm using are listed. This is a requirement from the client
side.



Jerry Van Kolken
Millennium Fire Protection Corp.
2950 San Luis Rey Rd.
Oceanside, CA 92058
(760) 722-2722 FX 722-2730

-Original Message-
From: Sprinklerforum  On
Behalf Of Hinson, Ryan via Sprinklerforum
Sent: Wednesday, August 26, 2020 11:11 AM
To: sprinklerforum@lists.firesprinkler.org
Cc: Hinson, Ryan 
Subject: RE: C-Clamp Hangers

Hanger attachments are being confused with bracing attachments.  
-   NFPA 13 (2019) Section 18.5.11.10 explicitly DOES NOT allow C-clamps
used for seismic bracing structural attachments with or without
restraining straps unless specifically listed for such use. 
-   Section 18.7.1 allows their use for hangers in seismically active
areas when a restraining strap is included.  
-   Chapter 17 explicitly DOES allow listed use of c-clamps for hangers
alone.  

See commentary for further discussion and pictures depicting their allowed
hanger usage.

Hope this helps,

Ryan L. Hinson, PE*, SET**  \  Burns & McDonnell Senior Fire Protection
Engineer O 952-656-3662 \  M 763-688-4045 \  F 952-229-2923
rhin...@burnsmcd.com  \  burnsmcd.com
8201 Norman Center Drive, Suite 500  \  Minneapolis-St. Paul, MN 55437
*Registered in: LA, MD, MN, PA, TX, & UT **NICET IV - Water-Based Systems
Layout



-Original Message-
From: Sprinklerforum  On
Behalf Of Jerry Van Kolken via Sprinklerforum
Sent: Wednesday, August 26, 2020 12:52 PM
To: sprinklerforum@lists.firesprinkler.org
Cc: jvankol...@mfpc.us
Subject: C-Clamp Hangers

Does anyone know the reasoning Why you would not be allowed to use C-Clamps
for your hanger attachments? 

 

I've had a couple of specs have this requirement pass by my desk recently. 

 

Jerry Van Kolken

Millennium Fire Protection Corp.

2950 San Luis Rey Rd.

Oceanside, CA 92058

(760) 722-2722 FX 722-2730

 

___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
https://nam05.safelinks.protection.outlook.com/?url=http%3A%2F%2Flists.fires
prinkler.org%2Flistinfo.cgi%2Fsprinklerforum-firesprinkler.orgdata=02%7
C01%7Crhinson%40burnsmcd.com%7C1d14008726f74fa34d4308d849e89359%7Cbfbb9a2b6d
994e78b3c795005d555c8b%7C0%7C0%7C637340610543326549sdata=%2Bt0YUDv8iKf9
xPab8hEUmLbdCBOX%2FIZ5VDKB7jaeLls%3Dreserved=0
___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org


Re: C-Clamp Hangers

2020-08-26 Thread John Denhardt via Sprinklerforum
Possibly an outdated specification.

I have not heard of any issues with properly installed listed C-clamps.

Thanks,
John

John August Denhardt, PE
*Vice President, Engineering and Technical Services*

*American Fire Sprinkler Association*
m: p: 301-343-1457
214-349-5965 ext 121
w: firesprinkler.org



   

*Our members are at the heart of everything we do.*

*AFSA Summer Sale!*

For a limited time only, AFSA is offering members up to 50% off its
on-demand recorded webinars! Featuring the most sought-after thought
leaders, AFSA On-Demand offers a superior learning experience with ability
to earn CEU and CPD credits anytime, anywhere. Visit
http://www.firesprinkler.org/ondemand to learn more.


On Wed, Aug 26, 2020 at 1:50 PM Jerry Van Kolken via Sprinklerforum <
sprinklerforum@lists.firesprinkler.org> wrote:

> Does anyone know the reasoning Why you would not be allowed to use C-Clamps
> for your hanger attachments?
>
>
>
> I've had a couple of specs have this requirement pass by my desk recently.
>
>
>
> Jerry Van Kolken
>
> Millennium Fire Protection Corp.
>
> 2950 San Luis Rey Rd.
>
> Oceanside, CA 92058
>
> (760) 722-2722 FX 722-2730
>
>
>
> ___
> Sprinklerforum mailing list
> Sprinklerforum@lists.firesprinkler.org
>
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
>
___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org


RE: C-Clamp Hangers

2020-08-26 Thread Hinson, Ryan via Sprinklerforum
Hanger attachments are being confused with bracing attachments.  
-   NFPA 13 (2019) Section 18.5.11.10 explicitly DOES NOT allow C-clamps 
used for seismic bracing structural attachments with orwithout restraining 
straps unless specifically listed for such use. 
-   Section 18.7.1 allows their use for hangers in seismically active areas 
when a restraining strap is included.  
-   Chapter 17 explicitly DOES allow listed use of c-clamps for hangers 
alone.  

See commentary for further discussion and pictures depicting their allowed 
hanger usage.

Hope this helps,

Ryan L. Hinson, PE*, SET**  \  Burns & McDonnell
Senior Fire Protection Engineer
O 952-656-3662 \  M 763-688-4045 \  F 952-229-2923
rhin...@burnsmcd.com  \  burnsmcd.com
8201 Norman Center Drive, Suite 500  \  Minneapolis-St. Paul, MN 55437
*Registered in: LA, MD, MN, PA, TX, & UT
**NICET IV - Water-Based Systems Layout



-Original Message-
From: Sprinklerforum  On Behalf 
Of Jerry Van Kolken via Sprinklerforum
Sent: Wednesday, August 26, 2020 12:52 PM
To: sprinklerforum@lists.firesprinkler.org
Cc: jvankol...@mfpc.us
Subject: C-Clamp Hangers

Does anyone know the reasoning Why you would not be allowed to use C-Clamps for 
your hanger attachments? 

 

I've had a couple of specs have this requirement pass by my desk recently. 

 

Jerry Van Kolken

Millennium Fire Protection Corp.

2950 San Luis Rey Rd.

Oceanside, CA 92058

(760) 722-2722 FX 722-2730

 

___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
https://nam05.safelinks.protection.outlook.com/?url=http%3A%2F%2Flists.firesprinkler.org%2Flistinfo.cgi%2Fsprinklerforum-firesprinkler.orgdata=02%7C01%7Crhinson%40burnsmcd.com%7C1d14008726f74fa34d4308d849e89359%7Cbfbb9a2b6d994e78b3c795005d555c8b%7C0%7C0%7C637340610543326549sdata=%2Bt0YUDv8iKf9xPab8hEUmLbdCBOX%2FIZ5VDKB7jaeLls%3Dreserved=0
___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org


Re: C-Clamp Hangers

2020-08-26 Thread Mike Hairfield via Sprinklerforum
They have to be FM approved and/or UL listed.

What type of C-Clamps are planning on using?

Mike


From: Sprinklerforum  on behalf 
of Jerry Van Kolken via Sprinklerforum 
Sent: Wednesday, August 26, 2020 1:52 PM
To: sprinklerforum@lists.firesprinkler.org 

Cc: jvankol...@mfpc.us 
Subject: C-Clamp Hangers

Does anyone know the reasoning Why you would not be allowed to use C-Clamps
for your hanger attachments?



I've had a couple of specs have this requirement pass by my desk recently.



Jerry Van Kolken

Millennium Fire Protection Corp.

2950 San Luis Rey Rd.

Oceanside, CA 92058

(760) 722-2722 FX 722-2730



___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org