Title: National Electrical Code 2008 Edition
Wrenches,
I need similar advice, please, especially a Code section citation.
In 2005 we installed an Outback system for a new home in town that
was designed and installed to be a grid-backup solar home. It was,
i
I'm not clear on the specific situation the inspector was speaking about -
it could have been inter-module conductors under the array or it could have
been between an array and remote junction box.
It sounds like generally speaking they should be run together. -August
*From:* re-wrenches-boun
Hi August,
The handbook has a note regarding this under 690.31(B):
. Long runs of separated conductors (with loop inductance and distributed
capacitance) and the resulting long-time constants in dc circuits may result
in improper operation of overcurrent devices. It is suggested that, where
Hi August,
I can only assume that the inspectors are talking about say running a return
leg which would have no pair back to the combiner/junction box?
jay
peltz power
On Nov 19, 2013, at 9:38 AM, August Goers wrote:
> Hi All –
>
> On a related note, I’ve become good friends with some of t
** *300.3(B) Conductors of the Same Circuit.* All conductors of the same
circuit and, where used, the grounded conductor and all equipment
grounding conductors and bonding conductors shall be contained within
the same raceway, auxiliary gutter, cable tray, cablebus assembly,
trench, cable, or c
August,
Timely question. I am working with a TenK solar array right now and the wire
management from TenK is poor. From the combiner to the inverter they have #2 CU
in free air. It looks ugly. The inverter won't allow for one raceway with both
conductors plus ground. If each could be installed
Hi All –
On a related note, I’ve become good friends with some of the inspectors in
San Francisco and they called me yesterday with a question. Is it okay to
run *individual* DC conductors through EMT for wire management purposes? We
have always run paired positive and negative conductors in con
DPW Easy Feet are a great product for metal roofs going into roof decking.
Aaron Mandelkorn
Owner / Solar Specialist
Renewable Energy Outfitters
Box 65 Salida CO. 81201
719-221-5249
970-596-3744
reoso...@gmail.com
www.reosolar.com
On Nov 19, 2013, at 6:14 AM, Mac Lewis wrote:
> H
Try Schletter. They have just what you're looking for, and if they don't
They'll make it. Plus everything comes with a PE stamp.
Good Luck!
Chad Waits
President- Net Zero Solar
(520) 270-4873
101 W. 5th St., Tucson, AZ 85705
AZ ROC# 248710(B-), 259521(K-78), 259756 (K-11)
NABCEP Certified PV I
Hello wrenches,
I have an application that I am considering finding a mounting system that
attaches to the roof deck only. Does anyone have experience with this type
of mounting solution? Does anyone have a favorite product for roof
sheathing attachment to a metal roof?
Thanks
--
Mac Lew
10 matches
Mail list logo