Hi John, Do you know what firmware version was causing your initial over-voltage situation? Kevin From: RE-wrenches On Behalf Of John Blittersdorf via RE-wrenches Sent: Friday, February 9, 2024 8:09 PM To: RE-wrenches Cc: John Blittersdorf Subject: Re: [RE-wrenches] Lithium batteries Ray

Re: [RE-wrenches] Lithium batteries

2024-02-09 Thread John Blittersdorf via RE-wrenches
Ray, With this batch of posts about lithium batteriem and several mentions of XW inverters and overcharging, I just have to chime in with my experience with one I installed and one installed by someone else. Both were charging 48V L16 wet cell batteries. In both cases with charge settings doubl

Re: [RE-wrenches] Lithium batteries

2024-02-08 Thread Ray Walters via RE-wrenches
Hi Richard; Off list, what was your outcome from Simpliphi?  Did they make any deal with you?  What did you put in as replacements? Thanks, Ray Walters Remote Solar On 2/8/2024 7:35 AM, Richard Nicol via RE-wrenches wrote: Hi Ray We had a complete failure of 6 Simpliphi batteries with the s

Re: [RE-wrenches] Lithium batteries

2024-02-08 Thread Ray Walters via RE-wrenches
The auxiliary charger was only used after Simpliphi recommended it.  This was also a requirement before they would even issue an RMA: charge each battery individually for 2 hours with a separate DC power supply or battery charger.  That's 8 hours total on site by the way, and another problem I

Re: [RE-wrenches] Lithium batteries

2024-02-08 Thread Darryl Thayer via RE-wrenches
About 4 years ago I wrote about my failure of Simplify in service 3 years. after much delay, I took each unit to shop and charged each one on bench power supply, all returned to full function and are still working today off grid system. I agree with the comments they are tricky, MorningStar knows

Re: [RE-wrenches] Lithium batteries

2024-02-08 Thread Chris Schaefer via RE-wrenches
Ray, Oddly enough we're getting ready to replace our 22 year old 48v bank of Rolls Surrette batteries at our offgrid Design and Training Center in Western NY with a set of Lithium batteries.The reason for the jump to Lithium is because of the numerous request by clients for them over the past 5 ye

Re: [RE-wrenches] Lithium batteries

2024-02-08 Thread Richard Nicol via RE-wrenches
Hi Ray We had a complete failure of 6 Simpliphi batteries with the same symptoms you found. Another installer had replaced the inverter with an XW and appeared to leave the charger programing on factory defaults along with temp compensation so when the generator was called for it would rise to abso

Re: [RE-wrenches] Lithium batteries

2024-02-08 Thread Michael Morningstar via RE-wrenches
I've been having the same thoughts about Li and off-grid systems. It used to be that I would install a system and then hear back from the clients a decade later when it was time for new batteries. Now, almost every other week I'm dealing with Li related issues (that I feel obligated to pay for). Sa

Re: [RE-wrenches] Lithium batteries

2024-02-08 Thread Jay via RE-wrenches
Hi RayI’m going more and more with same oem for systems with lithium. Specifically so I don’t have an issue with finger pointing between OEMS. But that sure sucks. JayOn Feb 7, 2024, at 10:17 PM, Ray Walters via RE-wrenches wrote: We just had a complete failure of a set of four

Re: [RE-wrenches] Lithium batteries

2024-02-08 Thread Jason Szumlanski via RE-wrenches
For what it's worth, B&S has a stellar reputation around here for dealer warranty support on their generators. I know that doesn't always translate when companies acquire others (a case in point is the disastrous ADT/SunPro mess). How battery manufacturers will handle LiPO warranty claims is still

Re: [RE-wrenches] Lithium batteries

2024-02-07 Thread Ray Walters via RE-wrenches
We just had a complete failure of a set of four Simpliphi 3.8 KWh batteries, 48 v.  It has completely changed my thoughts on Li+ for off grid.  This set lasted 5 years, which is about equal to bottom of the barrel Golf Cart batteries.  The RMA/ Warranty process has not been smooth.  It took alm

[RE-wrenches] Lithium batteries

2024-02-07 Thread jay via RE-wrenches
One of the things that I’m just now learning is about BMS failure/warranty/fix/replacement. Some can be field installed some need to go back to the OEM. I guess its something else we need to check on. Jay > On Feb 7, 2024, at 9:06 AM, Bradley Bassett via RE-wrenches > wrote: > > Read

Re: [RE-wrenches] Lithium batteries

2019-05-07 Thread Howie Michaelson
Jerry, have you used an XW with the Blue Ion? If so, is there a reason to use a Conext Battery Monitor with the system? In this system, which is grid-tied, there will also be a backup generator (he likes redundancy). What settings would trigger the AGS if there was no Battery Monitor in the syste

Re: [RE-wrenches] Lithium batteries

2019-05-07 Thread Dave Angelini Offgrid Solar
The owner of Blue Ion runs XW's or at least I saw pix of him in front of one. They have their own monitor program but it is not compatible with Outback or Schneider comms. That lets them out for my use. Just finished the circuit validation testing of XW pro here. It really was just to make su

Re: [RE-wrenches] Lithium batteries

2019-05-07 Thread Sindelar Solar
Howie, I have now installed three Blue Ion systems (2 x 16 kwh and one 48kwh) and am very pleased with them. It's a complete package with clear instructions, all parts labeled, good technical support, and presents very well to the client when installed. BMS info is accessed online through the

Re: [RE-wrenches] Lithium batteries

2019-05-07 Thread Howie Michaelson
Jerry, thanks for this recommendation. I've been looking at the Blue Ion, but for some reason they off my top tier choices. Have you integrated them with XW battery backup systems? How is the BMS info access? The one thing that I really like about the AES batteries is their integration with the Con

Re: [RE-wrenches] Lithium batteries

2019-05-04 Thread Howie Michaelson
Thanks Jason. Great videos! Any thoughts on why AES is so much more than some others that seem pretty solid as well? Howie On Fri, May 3, 2019 at 5:30 PM Jason Andrade < ja...@westcoastsustainables.com> wrote: > > Howie, > I’ve used a few different brands and am currently using the Discover AES

Re: [RE-wrenches] Lithium Batteries - Li-ion battery warning

2019-05-03 Thread Starlight Solar Power Systems
Hello Howie, You should be aware that Discover Li-ion battery does not have adequate protection to prevent damage if charged below freezing. The data sheet (see attachment) shows that you can charge the battery down to -4°F and adds a text warning not to charge below 32°F. "Care should be tak

Re: [RE-wrenches] Lithium batteries

2019-05-03 Thread MiJo Nels
SL# 868816 www.SustainableEnergyGroup.com<http://www.SustainableEnergyGroup.com> 530-273-4422 (Office) 530-217-8385 (Cell)      From: RE-wrenches on behalf of Jerry Shafer Sent: Friday, May 3, 2019 2:32:37 PM To: RE-wrenches Subject: Re: [RE-w

Re: [RE-wrenches] Lithium batteries

2019-05-03 Thread Jerry Shafer
Just my 2 cents, look at Blue ion from Blue Planet Energy, l have installed new and also switched over from other batteries, been very happy with performance On Fri, May 3, 2019, 2:30 PM Jason Andrade wrote: > > Howie, > I’ve used a few different brands and am currently using the Discover AES, >

[RE-wrenches] Lithium batteries

2019-05-03 Thread Jason Andrade
Howie, I’ve used a few different brands and am currently using the Discover AES, I have a quad stack of the coupled to an dual stack of XW inverters and they are working great, As for another post comment that these companies are looking to be bought out, Discover is long time battery manufact

Re: [RE-wrenches] Lithium Batteries

2019-05-03 Thread Howie Michaelson
Chris, Thanks for the reminder. I've stayed out of the Lithium option until now, largely because of just that, but now that I'm delving in, that is a good reminder. I swore off bleeding edge products years ago, but I guess I'm running the risk of bleeding again... Howie On Fri, May 3, 2019 at 4:4

Re: [RE-wrenches] Lithium Batteries

2019-05-03 Thread Howie Michaelson
Thanks Dave. Do you need an add-on to get the interface from the AES to the Conext gateway? Have you used Iron Edison's lithium offering? Is there a comprehensible reason for the significant price differential between the 2? Do you know where the IronEdison are manufactured? Howie On Fri, May 3,

Re: [RE-wrenches] Lithium Batteries

2019-05-03 Thread Chris Mason
I'd be very cautious about getting too cosy with any of these battery companies, it seems their only aim is to get bought. Sonnen was acquired by Shell Oil, Pika by Generac. I'm a generac dealer so I am exploring what their intentions are. I doubt Shell will be gung-ho to continue to support solar

Re: [RE-wrenches] Lithium Batteries

2019-05-03 Thread penobscotsolar
Hi Howie, Have you looked at Fortress Power batteries? We're about to install some and they look like a very decent battery. Google will get you the basic info to start. Daryl Penobscot Solar Design > Hi Folks, > About to spec my first Lithium battery backup job. The client is not a > hea

[RE-wrenches] Lithium Batteries

2019-05-03 Thread Howie Michaelson
Hi Folks, About to spec my first Lithium battery backup job. The client is not a heavy user, but wants things done right more than being totally cost effective. We put in 14kW of net metered solar using SolarEdge and now he wants the backup component. This was significantly oversized for his use,

Re: [RE-wrenches] lithium batteries

2017-10-12 Thread Glenn Burt
The sonnen eco series of products were available before the PW2, and are available today through distributors. They also take AC in and out, with batteries and inverter internal in a sleek enclosure. They are programmable for exporting restrictions. -Glenn -Original Message- From: RE-wr

Re: [RE-wrenches] Lithium batteries for Polaris Ranger EV

2015-05-27 Thread frenergy
bject: [RE-wrenches] Lithium batteries for Polaris Ranger EV Jay, I saw your post on RE-Wrenches, asking about a source for lithium batteries for the Polaris Ranger EV utility vehicle. I’m friends with a Polaris Ranger EV owner who recently converted his to lithium. His contact in

[RE-wrenches] Lithium batteries for Polaris Ranger EV

2015-05-27 Thread Randy Brooks
t; 509-784-1747 Jack can provide you details. I helped range test the lithium version. Very nice. take care, Randy Brooks Brooks Solar, Inc. Chelan, WA 509-682-9646 ra...@brookssolar.com <mailto:ra...@brookssolar.com> From: jay peltz mailto:jay.pe...@gmail.com>> Subject: Re: [RE

Re: [RE-wrenches] Lithium batteries for Polaris

2015-05-26 Thread jay peltz
Hi All, I've got a call about lithium batteries for the battery powered polaris EV ranger. I've looked but can't find any. Anybody know of a supplier for this? Sorry in advance if this is supposed to go to marketing. jay peltz power ___ List sponsore

Re: [RE-wrenches] Lithium batteries

2013-02-20 Thread Ray Walters
I'd try a set with a few adventurous customers, but the price needs to be really good for Beta testing. Once you get a couple of years of proof of concept, and work out the charging details, etc. then your friend could set the price higher. Its all about amp hours and cycle life. If he can p

Re: [RE-wrenches] lithium batteries

2013-01-26 Thread Kevin Pegg
40.4 to 50.4 VDC. Kevin -Original Message- From: re-wrenches-boun...@lists.re-wrenches.org [mailto:re-wrenches-boun...@lists.re-wrenches.org]On Behalf Of jay peltz Sent: January 24, 2013 7:41 PM To: RE-wrenches Subject: [RE-wrenches] lithium batteries HI All, Is there a rough voltage

Re: [RE-wrenches] lithium batteries

2013-01-25 Thread John Berdner
-boun...@lists.re-wrenches.org] On Behalf Of jay peltz Sent: Thursday, January 24, 2013 7:41 PM To: RE-wrenches Subject: [RE-wrenches] lithium batteries HI All, Is there a rough voltage range ( high/low nominal) for the lithium family of batteries? I'm curious if our current range of inverter

[RE-wrenches] lithium batteries

2013-01-24 Thread jay peltz
HI All, Is there a rough voltage range ( high/low nominal) for the lithium family of batteries? I'm curious if our current range of inverters can work with these batteries, at least on the load side, probably not on the charging side. thanks, jay peltz power _

Re: [RE-wrenches] Lithium Batteries

2012-07-17 Thread James Surrette
Hi Jeremy, How large a bank is your client looking for? We have worked with Corvus Energy on some projects but the numbers have never worked, yet, for off-grid. Regards, Jamie >>> "Jeremy Rodriguez- All Solar Inc." 7/17/2012 12:01 >>> AM >>> I have a request for Lithium batteries (io

[RE-wrenches] Lithium Batteries

2012-07-16 Thread Jeremy Rodriguez- All Solar Inc.
I have a request for Lithium batteries (ion?). Not sure how to respond. The application is an off grid, part time mountain home Any thoughts? Thank you Jeremy Ridriguez All Solar Colorado Sent via BlackBerry. Sorry for typos and shorthand! ___ List spon

Re: [RE-wrenches] Lithium batteries.....

2008-08-25 Thread R . Walters
I agree with Mick there about using lead acid, that's just a few pounds for a bit of trouble. On the other hand if you're going to play with Li on solar, you might as well start small in case something cooks. Keep us posted, I was wondering when one of us would try Li+. Ray In term

Re: [RE-wrenches] Lithium batteries.....

2008-08-24 Thread Darryl Thayer
. Darryl --- On Sun, 8/24/08, John Veix <[EMAIL PROTECTED]> wrote: > From: John Veix <[EMAIL PROTECTED]> > Subject: [RE-wrenches] Lithium batteries. > To: re-wrenches@lists.re-wrenches.org > Date: Sunday, August 24, 2008, 3:45 PM > Hi there, > > I have a customer wi

Re: [RE-wrenches] Lithium batteries.....

2008-08-24 Thread mick abraham
John Veix wrote: "I have a customer with a hot air balloon (who) doesn't want to use F.L.A. deep cycle battery due to weight factors, but wants to use Li instead - and also wants to use PV to charge it." Mick says: If one recalls the YouTube videos of flaming notebook computers, that underscor

Re: [RE-wrenches] Lithium batteries.....

2008-08-24 Thread Michael Welch
Hi John. Sounds like a good application for Li. Energy densities max out around 95 WH per pound. Lead acid is up to 20 WH per pound. Li batteries are about 3.3 volts per cell, so the pack your client is looking at may be 4 or 5 cells in series. It is probably important to buy a commercial pack, b

[RE-wrenches] Lithium batteries.....

2008-08-24 Thread John Veix
Hi there, I have a customer with a hot air balloon doesn't want to use F.L.A. deep cycle battery due to weight factors, but wants to use Li instead - and also wants to use PV to charge it. I have never looked into this, but he seems to think the Li battery charges at 16.8v. The battery will