RE: Class 1 AC/DC adapter

2003-11-05 Thread ChengWee Lai

Hello Guys,

Apologies for getting into many IF's. Yes, our discussion is based on
assumption and description provided. There are many unknown for us on his
unit.

I believe the fundamental of the safety concept, which have been discussed
should be look in depth by Raymond.

Maybe it is time for Raymond to give us some input over the different area
we discussed.

Best Regards,
Chengwee






From: Peter L. Tarver [mailto:peter.tar...@sanmina-sci.com]
Sent: Wednesday, November 05, 2003 7:40 AM
To: emc-p...@ieee.org
Cc: raymond...@omnisourceasia.com.hk; c...@netscreen.com; 'Rich Nute'
Subject: RE: Class 1 AC/DC adapter



Let's look at these what ifs.

 From: ChengWee Lai
 Sent: Tuesday, November 04, 2003 4:38 PM

 Raymond might be able to convince Safety agency
 to accept PE continuity test
 with 1500Vac Hipot at the production line.
 However in the Scenerio with end
 customer, it could mean business or no business.

 Question regarding:

 Whether customer can accept his adaptor with only
 1500Vac hipot tested where
 other power supplies can withstand 3000Vac?

The only clear answer is some form of redesign is necessary.
Simple solutions work best.  For any reasoned advice, there
are too many unknowns about the physical construction of the
power supply.  See the below for more on this.

 Would that affect his customer Safety testing,
 because his customer unit
 with his power supply only meet 1500Vac hipot
 after heating test?

Only Raymond and his customers can answer this.

 Or what if Safety agency require his customer
 unit to do grounding test to
 accessible metal part?

OK, but why?  The discussions have centered around an SELV
output, making the end product Class III.  There would have
to be some specific about the final application to justify
this.  We have no information to base such an assumption on.

 Regards,
 Chengwee

As with many discussions on the list, practical issue
discussions often get side tracked by the hypothetical and
theoretical.

More to the point, Raymond hasn't given us specifics on the
physical orientation of parts in the power supply to any
great degree.  Proprietary information aside, we know:

K1) the insulation between earthed parts and mains
connected parts is somewhat better than Basic, but not
Reinforced

K2) the EST potential where breakdown occurs (though I've
discarded the e-mail with the identified potential)

K3) the breakdown is suspected (or possibly confirmed) to
occur to the earthed board that is used as an EMC shield and
which also electrically connects to an SELV output


What we don't know (or I've lost track of):

DK1) if the power supply is a linear or switched mode type
(we can assume it's a SMPS, since EMC shielding was
mentioned, but it would be nice to have confirmation)

DK2) what mains connected part(s) are involved in the
dielectric breaking down (transformer winding terminations,
leads or bodies of filtering, surge suppression or other
components and how they are mounted)

DK3) what area or specific portion of the earthed parts are
involved in breaking down (at solder connection points for
lead wires, the copper on the shielding board)

DK4) if the supply uses an appliance inlet, has a
nondetachable power supply cord or if it a direct plug-in
type and how the mains circuit is brought to the power
conversion element(s) of the primary circuit


With some of this additional information, a more practical
solution may be possible, rather than talking around the
specifics.

A WAG or two:

One issue that hasn't come up is whether or not the copper
on the shielding board is facing the mains/primary circuitry
or not.  Based on the application and the general
discussion, this board appears to be separate and
independent of the mains/primary circuit board.  If this is
true, it seems logical that the board is single-sided.  If
the board is single-sided and the copper is facing the
mains/primary circuit, has anyone considered flipping the
board over and relying on the base laminate to provide
Supplementary insulation to a clearance?

If the first WAG is unusable, why not add a 0.4mm thick
insulating sheet between the earthed board and the portion
of the primary circuit involved in breaking down?  This will
effect margins and pricing, but sometimes one must bite the
bullet to get into the market or meet a customer's time
constraint.


Regards,

Peter L. Tarver, PE
ptar...@ieee.org


This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

Visit our web site at:  http://www.ewh.ieee.org/soc/emcs/pstc/

To cancel your subscription, send mail to:
 majord...@ieee.org
with the single line:
 unsubscribe emc-pstc

For help, send mail to the list administrators:
 Ron Pickard:  emc-p...@hypercom.com
 Dave Heald:   emc_p...@symbol.com

For policy questions, send mail to:
 Richard Nute:   ri...@ieee.org
 Jim Bacher: 

Re: LVD voltage limits

2003-11-05 Thread Arthur Michael

Hi John,

The following article was published in the last issue of Int'l Product
Safety News.  Enjoy!

Regards, Art Michael

Int'l Product Safety News
A.E. Michael, Editor
P.O. Box 1561 INT
Middletown CT 06457-8061 U.S.A.

Phone  :  (860) 344-1651
Fax:  (860) 346-9066
Email  :  i...@safetylink.com
Website:  http://www.safetylink.com
ISSN   :  1040-7529


_EC2000  Beyond_

Major Changes Proposed for the Low Voltage Directive

by Arthur E. Michael, Editor, Int'l Product Safety News*

The working document LVD Update.4 details proposals which have been in
development since 2001 for updating of the Low Voltage Directive 73/23/EEC
(LVD). There are significant changes proposed and we draw your attention
to the following:

Re Voltage Range: ... for use with a supply or output voltage not
exceeding 1000 Volt for alternating current and 1500 Volt for direct
current . The minimum voltages, previously designated as 50V AC  75V
DC are noticeably absent in the proposal. Therefore, the lower end of the
range is proposed to be 0V AC or DC.

Re Components: The directive shall not apply to the following equipment:
Basic components intended to be incorporated into electrical equipment
whose compliance with the essential requirements of this Directive cannot
be assessed independently.

The original LVD called for equipment to be safe - and then is fairly
quiet on what safe  entails. The proposed directive, in Annex I (titled,
Essential health and safety requirements)  provides a long list of
required 'protections'. Under the topic of Electric Shock and other
electrical hazards it lists: Leakage Current, Energy Supply, ESD, Arcs and
these must all take into account electrical, mechanical, chemical and
physical stresses.

Additional hazards that the user must be protected from include Fire
Hazards, Mechanical Hazards, Other Hazards (including explosions caused by
the product itself or by substances produced, emitted or used by the
equipment);  this section lists an additional 12 subdivisions of hazards.

Annex I also calls for protection again hazards arising from incorrect
functioning, hazards arising from electric, magnetic and electromagnetic
fields, other ionizing and non-ionizing radiation. Ergonomic compliance is
also a requirement of this proposal.

The proposal provides a detailed listing of Information Requirements
which covers elements such as identification of the equipment by means
such as type, batch, serial number or similar. It also requires
instructions, identification of the manufacturer, and the name of the
responsible person in the EC if the manufacturer is not established in the
EC. The proposal calls for instructions for safe installation,
maintenance, cleaning, operation, storage and warnings where potential
risks are not evident.

There is much more of interest in this proposal that we cannot address due
to space considerations. The latest iteration of the full report, titled,
LVD Update.4 is now available on the Europa site, we located a copy at:

europa.eu.int/comm/enterprise/electr_equipment/lv/direct/lvdupdate4.pdf

And, a report commissioned by the UK's Dept. of Trade and Industry,
titled, Limited Regulatory Impact Assessment on the revised limits for
the Low Voltage Directive, dated APR 2002, can be found at:
www.com-met2005.org.uk/events_lit/newsletters/DTI_LVD_Report.pdf

Reprinted with permission of Int'l Product Safety News, Vol 16, No, 5
Sept/Oct 2003. Copyright 2003 Arthur E. Michael

For further information, see: www.safetylink.com/ipsninfo.html

REF: IPSN1608.A   3.4K char's

 -

On Wed, 5 Nov 2003, Tyra, John wrote:

 Hello Everyone,

 I have read on this list and have been told by TUV that the lower limits for
 the voltages of products which fall under the Low Voltage Directive may be
 eliminated so that low voltage products would now fall under that directive.

 On the Europa website I read an LVD Working Document, dated 7/13/01, that
 there were two proposals:

 1. Delete the lower limit and introduce risk assessment similar to the
 Machinery Directive
 2. Leave the limits as is but add an annex to include certain low voltage
 products, lighting system, household appliances, TV/Radio etc

 I found a Working Guide for the LVD dated 3/7/02 which  showed that there
 are countries which favor one or the other proposal while the UK favored no
 change..

 Does anyone have any new information or can point me in the direction which
 would give me a more recent an update of this proposal? I am very interested
 in where this proposal is heading..

 Thanks in advance for your help..

 Regards,


 John Tyra
 Product Safety and Regulatory Compliance Manager

 Bose Corporation
 The Mountain, MS-450
 Framingham, MA 01701-9168
 Phone: 508-766-1502
 Fax: 508-766-1145
 john_t...@bose.com






This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

Visit our 

Re: LVD voltage limits

2003-11-05 Thread Joe P Martin





John,

The following link has the LVD Update #4.  This update followed a June 2003
Working Party Meeting.


http://www.europa.eu.int/comm/enterprise/electr_equipment/lv/direct/review.htm

Best Regards

Joe Martin
Applied Biosystems
marti...@appliedbiosystems.com



  
   
  Tyra, John
   
  john_t...@bose.com  To:  
emc-p...@ieee.org   
  Sent by:  cc:   
   
  owner-emc-pstc@majordoSubject:  LVD voltage
limits  
  mo.ieee.org 
   
  
   
  
   
  11/05/2003 01:34 PM 
   
  Please respond to   
   
  Tyra, John
   
  
   
  
   




Hello Everyone,


I have read on this list and have been told by TUV that the lower limits
for the voltages of products which fall under the Low Voltage Directive may
be eliminated so that low voltage products would now fall under that
directive.


On the Europa website I read an LVD Working Document, dated 7/13/01, that
there were two proposals:

1. Delete the lower limit and introduce risk assessment similar to the
Machinery Directive
2. Leave the limits as is but add an annex to include certain low voltage
products, lighting system, household appliances, TV/Radio etc


I found a Working Guide for the LVD dated 3/7/02 which  showed that there
are countries which favor one or the other proposal while the UK favored no
change..


Does anyone have any new information or can point me in the direction which
would give me a more recent an update of this proposal? I am very
interested in where this proposal is heading..


Thanks in advance for your help..


Regards,





John Tyra
Product Safety and Regulatory Compliance Manager


Bose Corporation
The Mountain, MS-450
Framingham, MA 01701-9168
Phone: 508-766-1502
Fax: 508-766-1145
john_t...@bose.com








This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

Visit our web site at:  http://www.ewh.ieee.org/soc/emcs/pstc/

To cancel your subscription, send mail to:
 majord...@ieee.org
with the single line:
 unsubscribe emc-pstc

For help, send mail to the list administrators:
 Ron Pickard:  emc-p...@hypercom.com
 Dave Heald:   emc_p...@symbol.com

For policy questions, send mail to:
 Richard Nute:   ri...@ieee.org
 Jim Bacher: j.bac...@ieee.org

Archive is being moved, we will announce when it is back on-line.
All emc-pstc postings are archived and searchable on the web at:
http://www.ieeecommunities.org/emc-pstc



Ciena Job Opening, CM Analyst- San Jose CA.

2003-11-05 Thread Collins, Jeffrey

Group,

Not directly an EMC or Safety position but in this position you will work with
all of engineering including Compliance.

Please forward all emails to me directly. No phone calls please.

Regards,


Jeffrey Collins 
Sr. HW Engineering Manager 
Corporate Compliance  Homologation
CIENA  Corporation
5965 Silver Creek Valley Rd. 
San Jose, CA. 95138
(408) 571-3002, Fax (408) 965-2705
jcoll...@ciena.com
http://www.ciena.com






 Position Description
 __
 
 DATE: 10-21-03
 
 TITLE: Change Analyst 
 
 LOCATION:San Jose building 3
 
 REPORTS TO (use title): HW Manager  
 
 POSITION SUMMARY 
 * Process ECOs, DCOs, Deviations etc. in Agile.  Administer Change Control
processes in accordance with Ciena released polices.  Responsible for
interacting with multiple departments in order to lead, support, administer
and complete Change Orders.  Support the administration of Agile and Oracle
databases.  Review and check details of change orders and bills of materials
for accuracy.
 * 
 * ESSENTIAL DUTIES AND RESPONSIBILITIES
 * Administer all aspects of Agile including the processing and routing of
ECOs, DCOs, Deviations etc.
 * Help to assign part numbers
 * Create and analyze changes as required
 * Interact and train Engineers to create changes in Agile as necessary
 
 SKILLS
 * PC Literate
 * Ability to operate Word, Adobe Acrobat, Excel
 * Agile CM and iCM
 * Oracle ERP
 * Experience interacting with Contract Manufacturer
 * Documentation Control Experience
 
 DESIRED CHARACTERISTICS
 * Independent
 * Dependable
 * Team Player
 * Self motivated and proactive
 * Attention to detail
 *  
 * EDUCATION and/or RELEVANT EXPERIENCE
 * 5+ years of related Documentation experience required.  Experience with
Agile is required.  Experience working for an OEM with established systems is
needed. Strong written and verbal communication skills required.  Ability to
multitask in a fast paced environment.  This position requires an energetic
person who can maintain a positive attitude during constant procedure and task
changes.  Strong attention to detail is mandatory. 
 * 
 
 


This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

Visit our web site at:  http://www.ewh.ieee.org/soc/emcs/pstc/

To cancel your subscription, send mail to:
 majord...@ieee.org
with the single line:
 unsubscribe emc-pstc

For help, send mail to the list administrators:
 Ron Pickard:  emc-p...@hypercom.com
 Dave Heald:   emc_p...@symbol.com

For policy questions, send mail to:
 Richard Nute:   ri...@ieee.org
 Jim Bacher: j.bac...@ieee.org

Archive is being moved, we will announce when it is back on-line.
All emc-pstc postings are archived and searchable on the web at:
http://www.ieeecommunities.org/emc-pstc



Product Safety job posting message

2003-11-05 Thread Georgerian, Richard
Greetings All,
 
For those of you interested in a Product Safety position, please see below. I
am just posting this as a courtesy and on behalf for the company. Please
contact the company for details, not me.
 
Thanks.
 
Richard
=
Richard Georgerian
Compliance Engineer 
Carrier Access Corporation
5395 Pearl Parkway
Boulder, CO 80301
USA
Tele: 303-218-5748 Fax: 303-218-5503  mailto:rgeorger...@carrieraccess.com
mailto:rgeorger...@carrieraccess.com
 
 ==
Subject: EE Ad - 102803
 
Location: Boulder/Fort Collins, Colorado, USA -Electrical Design Engineer
  
Status:   Full Time, Employee
Shift: First Shift (Day)
 
Established Boulder, Colorado manufacturing company has an immediate opening
for a hands-on Electrical Engineer with 3 to 5 years experience. Primary
responsibility is the design and manufacturing of TVSS products and grounding
systems.  Duties include coordinating with regulatory agencies (UL),
management of TVSS product line and manufacturing documentation.
 
The position requires a degree in Electrical Engineering (BSEE) and a working
knowledge of AutoCAD.  Working experience with MAS-90 or other inventory
control systems a plus.
 
Excellent salary and benefit package including 401K, EEOC.  No relocation
provided.
 
Contact:
Joseph A. Lanzoni
Vice President of Operations
Lightning Eliminators  Consultants, Inc.
Ph: 303-447-2828 x104
Fx: 303-447-8122
E: jlanz...@lightningeliminators.com
 
=
 



LVD voltage limits

2003-11-05 Thread Tyra, John
Hello Everyone, 

I have read on this list and have been told by TUV that the lower limits for
the voltages of products which fall under the Low Voltage Directive may be
eliminated so that low voltage products would now fall under that directive.

On the Europa website I read an LVD Working Document, dated 7/13/01, that
there were two proposals: 
  
1. Delete the lower limit and introduce risk assessment similar to the
Machinery Directive 
2. Leave the limits as is but add an annex to include certain low voltage
products, lighting system, household appliances, TV/Radio etc

I found a Working Guide for the LVD dated 3/7/02 which  showed that there are
countries which favor one or the other proposal while the UK favored no
change..

Does anyone have any new information or can point me in the direction which
would give me a more recent an update of this proposal? I am very interested
in where this proposal is heading..

Thanks in advance for your help.. 

Regards, 


John Tyra 
Product Safety and Regulatory Compliance Manager 

Bose Corporation 
The Mountain, MS-450 
Framingham, MA 01701-9168 
Phone: 508-766-1502 
Fax: 508-766-1145 
john_t...@bose.com 




RE: IEC 61010-1:2001 section 6.7.3.2 Clearance Calculation

2003-11-05 Thread POWELL, DOUG
John  Dave,
 
Thank you for your replies.  I was hoping someone else had independently found
these issues with the document.  My only other choices were, I am somehow
going senile or worse, insane.
 
I am concerned becuase this lack of attention to detail on the part of the
committee, brings the rest of the document into question.  I have a fair
background in high voltage technology and in addition have carefully checked
into IEC 60664 for help.  Suffice it to say, there are other things in the IEC
61010-1 that bother me when it comes to safety spacings requirements.
 
Is there anyone in this discussion group who was part of the committee and can
answer some of these concerns?
 
Regards,
 
 
-doug


Douglas E. Powell 
Corporate Compliance Dept.
Advanced Energy Industries, Inc. 
Fort Collins, CO 80525 USA 


From: John Allen [mailto:john.al...@era.co.uk]
Sent: Wednesday, November 05, 2003 2:46 AM
To: 'drcuthb...@micron.com'; POWELL, DOUG
Cc: emc-p...@ieee.org
Subject: RE: IEC 61010-1:2001 section 6.7.3.2 Clearance Calculation


Doug, Dave
 
This is not the first time the formulae and examples in 6.7 have been called
into question.
 
One of my customers raised a query about a year ago, and I forwarded the query
to the Chairman of the IEC TC for 61010, as well as the (BSI) Secretary
thereof, as attached - I received an acknowlegement from Mr Chapman but I
never received an answer!
 
There might well be misprints in this case as I found quite a few elsewhere on
an earlier occasion, as per a previous message to Mr Chapman, also attached!
 
Therefore I think you need to view the text of this edition of 61010-1 with
the proverbial pinch of salt :- if it doesnt look right then it probably
isn't!!
 
Regards
John Allen, 
Technical Consultant
EMC and Safety Engineering
ERA Technology Ltd.
Cleeve Road
Leatherhead 
Surrey KT22 7SA
UK
Tel: +44-1372-367025 (Direct)
+44-1372-367000 (Switchboard)
Fax: +44-1372-367102

 
 


From: drcuthb...@micron.com [mailto:drcuthb...@micron.com]
Sent: 04 November 2003 16:46
To: doug.pow...@aei.com; emc-p...@ieee.org
Subject: RE: IEC 61010-1:2001 section 6.7.3.2 Clearance Calculation


Doug,
 
I find it confusing. Good thing there are examples.
 
example b) gives the correct answer. 
 
example a) does not look correct.
 
Reasoning:
 
1) F is solved incorrectly. It should be 0.297
2) The remainder looks correct. I get 20.5 mm (without interpolation)
 
With interpolation I get 18.4 mm.
 
 Dave Cuthbert
 Micron Technology
 
 
 

From: owner-emc-p...@majordomo.ieee.org
[mailto:owner-emc-p...@majordomo.ieee.org]On Behalf Of POWELL, DOUG
Sent: Monday, November 03, 2003 2:48 PM
To: EMC-PSTC (E-mail)
Subject: IEC 61010-1:2001 section 6.7.3.2 Clearance Calculation


 
Has anyone tried to work through the two examples given in this section?  In
trying to understand how to use the CLEARANCE = D1 + F(D2-D1) equation, I was
hoping to check my work with the examples that were given.  Either I'm missing
something or these examples have some really fundamental errors.
 
In my application, I am attempting to calculate the basic clearance for a
working voltage of 1500 VDC with transients that peak to 1800V and ride on the
VDC. The final peak voltage is 300 Volts higher than the steady-state 1500VDC,
which apparently meets the 6.7.3.1 b) 2) criteria.
 
 
 
Please help!
 
-doug
 
 
 

end



Douglas E. Powell 
Corporate Compliance Dept.
Advanced Energy Industries, Inc. 
Fort Collins, CO 80525 USA 

 
___
This message, including any attachments, may contain information
that is confidential and proprietary information of Advanced 
Energy Industries, Inc.  The dissemination, distribution, use 
or copying of this message or any of its attachments is 
strictly prohibited without the express written consent of 
Advanced Energy Industries, Inc.

_
This e-mail has been scanned for viruses by MCI's Internet Managed Scanning
Services - powered by MessageLabs. For further information visit
http://www.mci.com




*
Copyright ERA Technology Ltd. 2003. (www.era.co.uk). All rights reserved. 
The information supplied in this Commercial Communication should be treated
in confidence.
No liability whatsoever is accepted for any loss or damage 
suffered as a result of accessing this message or any attachments.

_
This e-mail has been scanned for viruses by MCI's Internet Managed Scanning
Services - powered by MessageLabs. For further information visit
http://www.mci.com




RE: Casino gaming machine

2003-11-05 Thread Sosnoski, Michael
Doug,
IEC 60035-2-82 is the current prevalent safety standard for gaming machines.
Testing and meeting the EN version will suffice for Europe, but meeting the
IEC with all group differences, and country deviations is quickest and easies
way to go.  On that note—Please remember that not all countries have adopted
–2-82 yet (US for one) and still requires you meet UL 22, but some countries
have made it mandatory by Jan.1 2004.
Gaming like many products has been waiting for a single harmonized standard
that will be accepted by all, but until it is, you have to meet the
requirements of the country you are selling to.
Does your product have spinning reels or a video display?  The only country I
am aware of that ever-required IEC 60065 was Sweden, and that was with a video
display.  Most other countries accepted IEC 60950.
Contact me personally if you wish.
 
Mike Sosnoski
Senior Manager--PSER
WMS Gaming
3401 N. California Ave., Chicago,IL. 60073
gl...@wmsgaming.com
 

From: Doug Massey [mailto:dmas...@acstestlab.com]
Sent: Wednesday, November 05, 2003 11:30 AM
To: emc-p...@majordomo.ieee.org
Subject: Casino gaming machine
 
Hello group;
 
Recently a client has requested a product safety evaluation for CE Marking of
their casino game – a fairly typical electronic slot machine. The machine
does not issue tokens to a winner, but rather prints a redeemable coupon.
 
Similar products by the client have been evaluated by a Notified Body lab in
the Community; the standard used was EN 60065, Audio / Video.
 
My initial research – checking the harmonized standards available – seems
to indicate that this may not be the appropriate standard. I find that the
following:
 
EN 60335-1:2002
Household and similar electrical appliances - Safety --
Part 1: General requirements
 
Along with
 
EN 60335-2-82:2000
Safety of household and similar electrical appliances --
Part 2-82: Particular requirements for service machines and amusement machines
 
Would appear to be more appropriate than EN 60065.
 
I do not have a copy of the 60335-2-82 standard – if anyone has experience
with this type product, or has a copy of the standard, I would be very
appreciative of opinions as to the appropriate standard, or would love to have
a peek at the scope of 60335-2-82 before purchasing it. I’m wondering if the
-2-82 standard only applies to machines that redeem coins or tokens.
 
I have requested justification / reasoning from the Notified Body, but am
trying to move forward while waiting for their reply. As always, any
assistance is appreciated, and opinions welcomed. 
 
Doug Massey
Product Safety Engineer
Advanced Compliance Solutions
Ph. (770) 831-8048
FAX (770) 831-8598
Visit our web home at http://www.acstestlab.com http://www.acstestlab.com/ 
 



Re: Class 1 AC/DC adapter

2003-11-05 Thread Rich Nute




Hello Chengwee:


   Whether customer can accept his adaptor with only 1500Vac hipot tested
where
   other power supplies can withstand 3000Vac?

This is an interesting question as it implies 
that the higher the withstand voltage the better
the unit.  The statement may even imply that a
double-insulation scheme provides a better
safeguard against electric shock than does a PE
scheme.

In fact, the two schemes provide equal protection
against electric shock.  There is no *inherent*
advantage of one over the other.

The 1500-volt withstand value is derived from 
the normally-occuring mains-to-earth overvoltages 
plus margin.  In other words, the 1500-volt test
represents an acceptable insulation that will not
fail when subjected to mains-to-earth overvoltage.

The 3000-volt withstand value is derived from 
testing two 1500-volt insulations in series.  The
3000-volt test tells us that the two insulations,
as a system, are acceptable, assuming that the 
voltage divides equally across each insulation.  
(The two insulations will never see overvoltages 
as high as 1500 volts.)

There is no inherent advantage to a unit that
passes a 3000-volt withstand test versus a unit
that passes a 1500-volt withstand test.  The only
thing that the 3000-volt withstand test tells us
is that the double-insulation system is intact.

If I recall correctly, Raymond Li said that the
unit in question passes 3000 volts primary-to-
secondary, fails 3000 volts primary-to-earth, 
but passes 1500-volts primary-to-earth.

This tells us that both the basic insulation and
the double insulation are acceptable.

   Would that affect his customer Safety testing, because his customer unit
   with his power supply only meet 1500Vac hipot after heating test? 

If the customer wants double-insulation throughout
the unit, then the adapter is unacceptable.

If the customer wants a unit that is certified to
a safety standard, then the adapter is acceptable.

   Or what if Safety agency require his customer unit to do grounding test to
   accessible metal part?

Based on Raymond Li's description and on my own
experience, I believe there should be no problem
passing the production-line grounding test at 
25-amperes.

*

Despite the preceding comments, such an adapter 
should easily pass double-insulation requirements
between primary and ground, and between primary 
and secondary.  In my experience, adapters designed
to IEC 60950 can easily achieve more than 4500 V 
rms withstand.  And, they can easily achieve 25
amperes dc-to-PE.

So, I am a bit disturbed that the unit does not
pass 3000 V rms to earth.  This says to me that 
there is a clearance within the unit that does not
meet the IEC 60950 requirements.  I would further
guess that the clearance is likely to be an 
operator-dependent clearance that is determined
during the assembly of the unit.  (The IEC 60950
clearance dimensions are quite conservative, and
should not break down below about 5000 V rms.)


Best regards,
Rich






This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

Visit our web site at:  http://www.ewh.ieee.org/soc/emcs/pstc/

To cancel your subscription, send mail to:
 majord...@ieee.org
with the single line:
 unsubscribe emc-pstc

For help, send mail to the list administrators:
 Ron Pickard:  emc-p...@hypercom.com
 Dave Heald:   emc_p...@symbol.com

For policy questions, send mail to:
 Richard Nute:   ri...@ieee.org
 Jim Bacher: j.bac...@ieee.org

Archive is being moved, we will announce when it is back on-line.
All emc-pstc postings are archived and searchable on the web at:
http://www.ieeecommunities.org/emc-pstc



Casino gaming machine

2003-11-05 Thread Doug Massey
Hello group;

 

Recently a client has requested a product safety evaluation for CE Marking of
their casino game – a fairly typical electronic slot machine. The machine
does not issue tokens to a winner, but rather prints a redeemable coupon.

 

Similar products by the client have been evaluated by a Notified Body lab in
the Community; the standard used was EN 60065, Audio / Video.

 

My initial research – checking the harmonized standards available – seems
to indicate that this may not be the appropriate standard. I find that the
following:

 

EN 60335-1:2002

Household and similar electrical appliances - Safety --

Part 1: General requirements

 

Along with

 

EN 60335-2-82:2000

Safety of household and similar electrical appliances --

Part 2-82: Particular requirements for service machines and amusement machines

 

Would appear to be more appropriate than EN 60065.

 

I do not have a copy of the 60335-2-82 standard – if anyone has experience
with this type product, or has a copy of the standard, I would be very
appreciative of opinions as to the appropriate standard, or would love to have
a peek at the scope of 60335-2-82 before purchasing it. I’m wondering if the
-2-82 standard only applies to machines that redeem coins or tokens.

 

I have requested justification / reasoning from the Notified Body, but am
trying to move forward while waiting for their reply. As always, any
assistance is appreciated, and opinions welcomed. 

 

Doug Massey

Product Safety Engineer

Advanced Compliance Solutions

Ph. (770) 831-8048

FAX (770) 831-8598

Visit our web home at http://www.acstestlab.com http://www.acstestlab.com/ 

 




Re: Class 1 AC/DC adapter

2003-11-05 Thread Rich Nute




Hi Peter:


I have and continue to advocate (in IEC TC 108)
that such classes should apply to CIRCUITS, not
to products.
   
   If this is endemic in IEC (as your statement implies), it
   may require a elephantine effort.  Good luck.

Yes.  And thank you.

The IEC Class I and Class II is an attempt to 
categorize products according to the supplemental 
safeguard, i.e., earthing or supplemental 
insulation, respectively, against electric shock.

The IEC Committee that developed the class
definitions is an electrical installation 
committee, not a product committee.  I would guess
that they had electrical installations, not 
products, in mind when they developed the 
definitions.  Its fairly easy to encase an outlet
box in metal or plastic and thereby get *pure*
Class I or Class II products.

With the advent of TC 108, supplemental safeguards
will be treated as independent supplemental
safeguards without reference to the IEC classes.  
I believe this will demonstrate that the IEC class
designations actually confuse product design and
evaluation rather than help.  (This string is an
example of how we get tied up with the issue of
IEC Class versus actual construction!)


Best regards,
Rich





This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

Visit our web site at:  http://www.ewh.ieee.org/soc/emcs/pstc/

To cancel your subscription, send mail to:
 majord...@ieee.org
with the single line:
 unsubscribe emc-pstc

For help, send mail to the list administrators:
 Ron Pickard:  emc-p...@hypercom.com
 Dave Heald:   emc_p...@symbol.com

For policy questions, send mail to:
 Richard Nute:   ri...@ieee.org
 Jim Bacher: j.bac...@ieee.org

Archive is being moved, we will announce when it is back on-line.
All emc-pstc postings are archived and searchable on the web at:
http://www.ieeecommunities.org/emc-pstc



digital tv -vs- medical telemetry

2003-11-05 Thread Peter L. Tarver


This is an old issue for some (from a 20MAR1998 FDA
advisory), but an interesting spectrum allocation issue for
your edification


http://www.fda.gov/cdrh/dtvalert.html



Regards,

Peter L. Tarver, PE
ptar...@ieee.org



This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

Visit our web site at:  http://www.ewh.ieee.org/soc/emcs/pstc/

To cancel your subscription, send mail to:
 majord...@ieee.org
with the single line:
 unsubscribe emc-pstc

For help, send mail to the list administrators:
 Ron Pickard:  emc-p...@hypercom.com
 Dave Heald:   emc_p...@symbol.com

For policy questions, send mail to:
 Richard Nute:   ri...@ieee.org
 Jim Bacher: j.bac...@ieee.org

Archive is being moved, we will announce when it is back on-line.
All emc-pstc postings are archived and searchable on the web at:
http://www.ieeecommunities.org/emc-pstc



RE: Class 1 AC/DC adapter

2003-11-05 Thread Peter L. Tarver


Let's look at these what ifs.

 From: ChengWee Lai
 Sent: Tuesday, November 04, 2003 4:38 PM

 Raymond might be able to convince Safety agency
 to accept PE continuity test
 with 1500Vac Hipot at the production line.
 However in the Scenerio with end
 customer, it could mean business or no business.

 Question regarding:

 Whether customer can accept his adaptor with only
 1500Vac hipot tested where
 other power supplies can withstand 3000Vac?

The only clear answer is some form of redesign is necessary.
Simple solutions work best.  For any reasoned advice, there
are too many unknowns about the physical construction of the
power supply.  See the below for more on this.

 Would that affect his customer Safety testing,
 because his customer unit
 with his power supply only meet 1500Vac hipot
 after heating test?

Only Raymond and his customers can answer this.

 Or what if Safety agency require his customer
 unit to do grounding test to
 accessible metal part?

OK, but why?  The discussions have centered around an SELV
output, making the end product Class III.  There would have
to be some specific about the final application to justify
this.  We have no information to base such an assumption on.

 Regards,
 Chengwee

As with many discussions on the list, practical issue
discussions often get side tracked by the hypothetical and
theoretical.

More to the point, Raymond hasn't given us specifics on the
physical orientation of parts in the power supply to any
great degree.  Proprietary information aside, we know:

K1) the insulation between earthed parts and mains
connected parts is somewhat better than Basic, but not
Reinforced

K2) the EST potential where breakdown occurs (though I've
discarded the e-mail with the identified potential)

K3) the breakdown is suspected (or possibly confirmed) to
occur to the earthed board that is used as an EMC shield and
which also electrically connects to an SELV output


What we don't know (or I've lost track of):

DK1) if the power supply is a linear or switched mode type
(we can assume it's a SMPS, since EMC shielding was
mentioned, but it would be nice to have confirmation)

DK2) what mains connected part(s) are involved in the
dielectric breaking down (transformer winding terminations,
leads or bodies of filtering, surge suppression or other
components and how they are mounted)

DK3) what area or specific portion of the earthed parts are
involved in breaking down (at solder connection points for
lead wires, the copper on the shielding board)

DK4) if the supply uses an appliance inlet, has a
nondetachable power supply cord or if it a direct plug-in
type and how the mains circuit is brought to the power
conversion element(s) of the primary circuit


With some of this additional information, a more practical
solution may be possible, rather than talking around the
specifics.

A WAG or two:

One issue that hasn't come up is whether or not the copper
on the shielding board is facing the mains/primary circuitry
or not.  Based on the application and the general
discussion, this board appears to be separate and
independent of the mains/primary circuit board.  If this is
true, it seems logical that the board is single-sided.  If
the board is single-sided and the copper is facing the
mains/primary circuit, has anyone considered flipping the
board over and relying on the base laminate to provide
Supplementary insulation to a clearance?

If the first WAG is unusable, why not add a 0.4mm thick
insulating sheet between the earthed board and the portion
of the primary circuit involved in breaking down?  This will
effect margins and pricing, but sometimes one must bite the
bullet to get into the market or meet a customer's time
constraint.


Regards,

Peter L. Tarver, PE
ptar...@ieee.org



This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

Visit our web site at:  http://www.ewh.ieee.org/soc/emcs/pstc/

To cancel your subscription, send mail to:
 majord...@ieee.org
with the single line:
 unsubscribe emc-pstc

For help, send mail to the list administrators:
 Ron Pickard:  emc-p...@hypercom.com
 Dave Heald:   emc_p...@symbol.com

For policy questions, send mail to:
 Richard Nute:   ri...@ieee.org
 Jim Bacher: j.bac...@ieee.org

Archive is being moved, we will announce when it is back on-line.
All emc-pstc postings are archived and searchable on the web at:
http://www.ieeecommunities.org/emc-pstc



RE: IEC 61010-1:2001 section 6.7.3.2 Clearance Calculation

2003-11-05 Thread John Allen
This is a multi-part message in MIME format.
Doug, Dave
 
This is not the first time the formulae and examples in 6.7 have been called
into question.
 
One of my customers raised a query about a year ago, and I forwarded the query
to the Chairman of the IEC TC for 61010, as well as the (BSI) Secretary
thereof, as attached - I received an acknowlegement from Mr Chapman but I
never received an answer!
 
There might well be misprints in this case as I found quite a few elsewhere on
an earlier occasion, as per a previous message to Mr Chapman, also attached!
 
Therefore I think you need to view the text of this edition of 61010-1 with
the proverbial pinch of salt :- if it doesnt look right then it probably
isn't!!
 
Regards
John Allen, 
Technical Consultant
EMC and Safety Engineering
ERA Technology Ltd.
Cleeve Road
Leatherhead 
Surrey KT22 7SA
UK
Tel: +44-1372-367025 (Direct)
+44-1372-367000 (Switchboard)
Fax: +44-1372-367102

 
 


From: drcuthb...@micron.com [mailto:drcuthb...@micron.com]
Sent: 04 November 2003 16:46
To: doug.pow...@aei.com; emc-p...@ieee.org
Subject: RE: IEC 61010-1:2001 section 6.7.3.2 Clearance Calculation


Doug,
 
I find it confusing. Good thing there are examples.
 
example b) gives the correct answer. 
 
example a) does not look correct.
 
Reasoning:
 
1) F is solved incorrectly. It should be 0.297
2) The remainder looks correct. I get 20.5 mm (without interpolation)
 
With interpolation I get 18.4 mm.
 
 Dave Cuthbert
 Micron Technology
 
 
 

From: owner-emc-p...@majordomo.ieee.org
[mailto:owner-emc-p...@majordomo.ieee.org]On Behalf Of POWELL, DOUG
Sent: Monday, November 03, 2003 2:48 PM
To: EMC-PSTC (E-mail)
Subject: IEC 61010-1:2001 section 6.7.3.2 Clearance Calculation


 
Has anyone tried to work through the two examples given in this section?  In
trying to understand how to use the CLEARANCE = D1 + F(D2-D1) equation, I was
hoping to check my work with the examples that were given.  Either I'm missing
something or these examples have some really fundamental errors.
 
In my application, I am attempting to calculate the basic clearance for a
working voltage of 1500 VDC with transients that peak to 1800V and ride on the
VDC. The final peak voltage is 300 Volts higher than the steady-state 1500VDC,
which apparently meets the 6.7.3.1 b) 2) criteria.
 
 
 
Please help!
 
-doug
 
 
 

end



Douglas E. Powell 
Corporate Compliance Dept.
Advanced Energy Industries, Inc. 
Fort Collins, CO 80525 USA 

 
___
This message, including any attachments, may contain information
that is confidential and proprietary information of Advanced 
Energy Industries, Inc.  The dissemination, distribution, use 
or copying of this message or any of its attachments is 
strictly prohibited without the express written consent of 
Advanced Energy Industries, Inc.

_
This e-mail has been scanned for viruses by MCI's Internet Managed Scanning
Services - powered by MessageLabs. For further information visit
http://www.mci.com




*
Copyright ERA Technology Ltd. 2003. (www.era.co.uk). All rights reserved. 
The information supplied in this Commercial Communication should be treated
in confidence.
No liability whatsoever is accepted for any loss or damage 
suffered as a result of accessing this message or any attachments.

_
This e-mail has been scanned for viruses by MCI's Internet Managed Scanning
Services - powered by MessageLabs. For further information visit
http://www.mci.com


---BeginMessage---
This attachment, originally named Message Text,
was removed because it is zero length.
---End Message---
---BeginMessage---
For the attention of the following Officers of IEC TC66 

 

Chairman:  Mr. Cecil CHAPMAN

Grant Instruments (Cambridge) Ltd.

Mill Barn

Bassingbourn, SG8 5PP, UK



 



Secretary: Mr. N.A.R. BRADFIELD

British Electrotechnical Committee

Electrical Department - Floor 11-6

British Standards Institution

389 Chiswick High Road

London W4 4AL, UK



Dear Sirs

 

It has been suggested that we draw to your attention the following technical 
and/or printing errors which appear in copies of BS EN 61010-1:2001 - and thus 
presumably in EN 61010-1:2001 and IEC 61010-1:2001

 

1) Clause 6.8.4 Voltage tests  Table 9 Test voltages for BASIC INSULATION 
(Page 52).



We are reasonably sure that there is a misprint in Column 1 Clearance of 
Table 9 , as follows: The line entry between 1.0 and 2.0 is 1.4 but it 
should be 1.5 (mm).



We believe that this is obvious from Table 8 Clearance for measurement 
categories II, III and IV where 1.5 (mm) is mentioned in numerous places but 
1.4 is not mentioned at all.



Apart from anything else, 1.5mm is the category II minimum value for nominal 
line voltages of 150V=300V - which