[PSES] optoisolators

2012-02-24 Thread Goedderz, Jim
Group,

 

I would like to get some input on how 60950-1 people and others deal
with  60950-1  2.10.5.4 Semiconductor devices: optoisolators

 

We are dealing with the issue of option a) vs option b) to show
compliance.

 

The end goal is to identify that the component satisfies the following, 

 

a) - passes the TYPE TESTS and inspection criteria of 2.10.11; and

- passes ROUTINE TESTS for electric strength during manufacturing, using
the

appropriate value of the test voltage in 5.2.2; or

 

b) for an optocoupler only, complies with the requirements of IEC
60747-5-51), where

the test voltages as specified in 5.2.6 (of IEC 60747-5-5):

- the voltage V ini,a for TYPE TESTING and

- the voltage V ini,b for ROUTINE TESTING,

shall be the appropriate value of the test voltage in 5.2.2 of this
standard.

 

We do a routine electric strength test, and the parts are certified to
standards older than IEC 60747-5-5.

 

Experience on what option is being used in industry may give me some
additional direction.

 

Appreciate your input, as always.

 

 

James Goedderz

Sr. Principal Engineer-Product Safety

Sensormatic Electronics, LLC

561.912.6378

 

Please note that any views or opinions presented in this email are
solely those of the author and do not necessarily represent those of the
company. This email and any attachments are confidential and intended
solely for the use of the individual or entity to whom they are
addressed. If you have received this email in error please notify the
sender immediately and delete any copies in your possession.

 


-

This message is from the IEEE Product Safety Engineering Society emc-pstc 
discussion list. To post a message to the list, send your e-mail to 
emc-p...@ieee.org

All emc-pstc postings are archived and searchable on the web at:
http://www.ieee-pses.org/emc-pstc.html

Attachments are not permitted but the IEEE PSES Online Communities site at 
http://product-compliance.oc.ieee.org/ can be used for graphics (in well-used 
formats), large files, etc.

Website:  http://www.ieee-pses.org/
Instructions:  http://listserv.ieee.org/request/user-guide.html
List rules: http://www.ieee-pses.org/listrules.html

For help, send mail to the list administrators:
Scott Douglas emcp...@radiusnorth.net
Mike Cantwell mcantw...@ieee.org

For policy questions, send mail to:
Jim Bacher:  j.bac...@ieee.org
David Heald: dhe...@gmail.com


[PSES] IR illumination

2012-02-16 Thread Goedderz, Jim
Forum,

 

We have a low voltage camera (class 3) that appears to NOT legally
require a NRTL certification for National Electric Code acceptance.

 

The product is powered by a LPS and should therefore be out of the
jurisdiction of the LVD also.

 

However, the camera also houses an IR light bank (presumably risk class
1) and marked with:

NOTICE

IR emitted from this product

Use appropriate shielding or eye protection

 

I am concerned about there being some LEGAL requirement limiting or
requiring marking for brightness. (i.e it needs certification.)

 

I'd like to know, that even with the IR LEDs, the camera can be put on
the market with a CE marking, without further investigation. (i.e., it
does not required certification.)

 

As always, any assistance is appreciated.

 

James Goedderz

Sr. Principal Engineer-Product Safety

Sensormatic Electronics, LLC

561.912.6378

 

Please note that any views or opinions presented in this email are
solely those of the author and do not necessarily represent those of the
company. This email and any attachments are confidential and intended
solely for the use of the individual or entity to whom they are
addressed. If you have received this email in error please notify the
sender immediately and delete any copies in your possession.

 


-

This message is from the IEEE Product Safety Engineering Society emc-pstc 
discussion list. To post a message to the list, send your e-mail to 
emc-p...@ieee.org

All emc-pstc postings are archived and searchable on the web at:
http://www.ieee-pses.org/emc-pstc.html

Attachments are not permitted but the IEEE PSES Online Communities site at 
http://product-compliance.oc.ieee.org/ can be used for graphics (in well-used 
formats), large files, etc.

Website:  http://www.ieee-pses.org/
Instructions:  http://listserv.ieee.org/request/user-guide.html
List rules: http://www.ieee-pses.org/listrules.html

For help, send mail to the list administrators:
Scott Douglas emcp...@radiusnorth.net
Mike Cantwell mcantw...@ieee.org

For policy questions, send mail to:
Jim Bacher:  j.bac...@ieee.org
David Heald: dhe...@gmail.com


RE: South Africa CB

2008-07-14 Thread Goedderz, Jim
You all know what it’s like trying to get something done in the final
minutes Friday. You forget to add critical data such as the standard is
60950-1.

Thank you again.

James Goedderz

Product Safety Engineer

Tyco/Sensormatic

561.912.6378

_
From: Goedderz, Jim
Sent: Friday, July 11, 2008 4:33 PM
To: 'emc-p...@ieee.org'
Subject: South Africa CB

Group,

Can anyone inform me if there are “National Deviations” to the CB scheme
for South Africa?

Our customer is asking for a CB report, and I see that SA is a CB member, but
I don’t have any list of national deviations.  

Thank you for your support.

James Goedderz

Product Safety Engineer

Tyco/Sensormatic

561.912.6378

-  This
message is from the IEEE Product Safety Engineering Society emc-pstc
discussion list. Website: http://www.ieee-pses.org/ 

To post a message to the list, send your e-mail to emc-p...@ieee.org 

Instructions: http://listserv.ieee.org/request/user-guide.html 

List rules: http://www.ieee-pses.org/listrules.html 

For help, send mail to the list administrators: 

Scott Douglas emcp...@ptcnh.net Mike Cantwell mcantw...@ieee.org 

For policy questions, send mail to: 

Jim Bacher: j.bac...@ieee.org David Heald: emc-p...@daveheald.com 

All emc-pstc postings are archived and searchable on the web at: 

http://www.ieeecommunities.org/emc-pstc 



South Africa CB

2008-07-11 Thread Goedderz, Jim
Group,

Can anyone inform me if there are “National Deviations” to the CB scheme
for South Africa?

Our customer is asking for a CB report, and I see that SA is a CB member, but
I don’t have any list of national deviations.  

Thank you for your support.

James Goedderz

Product Safety Engineer

Tyco/Sensormatic

561.912.6378

-  This
message is from the IEEE Product Safety Engineering Society emc-pstc
discussion list. Website: http://www.ieee-pses.org/ 

To post a message to the list, send your e-mail to emc-p...@ieee.org 

Instructions: http://listserv.ieee.org/request/user-guide.html 

List rules: http://www.ieee-pses.org/listrules.html 

For help, send mail to the list administrators: 

Scott Douglas emcp...@ptcnh.net Mike Cantwell mcantw...@ieee.org 

For policy questions, send mail to: 

Jim Bacher: j.bac...@ieee.org David Heald: emc-p...@daveheald.com 

All emc-pstc postings are archived and searchable on the web at: 

http://www.ieeecommunities.org/emc-pstc 



Australia power grid

2008-06-04 Thread Goedderz, Jim
Group,

We have some indirect evidence, and some damaged product, that appears to be
related to over voltage on the power grid in Australia.

The nominal is 240V 50Hz, but we are hearing accounts of voltages as high as
285V.

Has anyone else had to deal with damaged product, or can confirm that sections
of “down under” may occasionally be running well beyond normal tolerance?

Thank you.

James Goedderz

Product Safety Engineer

Tyco/Sensormatic

561.912.6378

-  This
message is from the IEEE Product Safety Engineering Society emc-pstc
discussion list. Website: http://www.ieee-pses.org/ 

To post a message to the list, send your e-mail to emc-p...@ieee.org 

Instructions: http://listserv.ieee.org/request/user-guide.html 

List rules: http://www.ieee-pses.org/listrules.html 

For help, send mail to the list administrators: 

Scott Douglas emcp...@ptcnh.net Mike Cantwell mcantw...@ieee.org 

For policy questions, send mail to: 

Jim Bacher: j.bac...@ieee.org David Heald: emc-p...@daveheald.com 

All emc-pstc postings are archived and searchable on the web at: 

http://www.ieeecommunities.org/emc-pstc 



Sound measurement

1999-04-08 Thread GOEDDERZ, JIM
Hello group,

I have been able to find limits for noise exposure, but not measurement
methods. Can anyone give the measurement methods, or a reference to a
method. Specifically, I'm looking for something like the distance from the
microphone, to the noise source.

Thank you

James Goedderz
Sensormatic

-
This message is coming from the emc-pstc discussion list.
To cancel your subscription, send mail to majord...@ieee.org
with the single line: unsubscribe emc-pstc (without the
quotes).  For help, send mail to ed.pr...@cubic.com,
j...@gwmail.monarch.com, ri...@sdd.hp.com, or
roger.volgst...@compaq.com (the list administrators).


RE: HALT/HASS Testing

1998-07-20 Thread GOEDDERZ, JIM
Dwight,

Our engineering group regularly sends products out for HALT testing. We
design ITE, although not computers. Some of the system problems that they
uncover are broken solder joints (mass of component), poor connections
(circuit boards), and other mechanical problem (fasteners).
The main idea is to increase the thermal stress on the product, with
vibration, until failure occurs. The test temperature starts at your maximum
operating temperature.
The products generally undergo about 3 days of testing. The cost is related
to how long it takes to verify functionality. We need about 15 minutes. It
will cost you about $8k for 3 days of test. You will need to either send an
engineer, or include a lot of replacement parts. Figure about two months to
schedule.

James Goedderz
Sensormatic Electronics
goedd...@sensormatic.com
Views expressed by the author do not necessarily represent those of
Sensormatic.


 --
 From: Dwight Hunnicutt[SMTP:dwight.hunnic...@vina-tech.com]
 Reply To: Dwight Hunnicutt
 Sent: Monday, July 20, 1998 12:01 PM
 To:   EMC PSTC; TREG Newsgroup; NEBS Newsgroup
 Subject:  HALT/HASS Testing
 
 In a related area of compliance world, have any of you had experience
 subjecting your prototypes to HALT testing, then your production units
 to HASS testing (such as by QualMark)??  I'm wondering if this sort of
 accelerated life testing is something out there for the satellite and
 space shuttle designers, rather than for ITE and Telecom equipment
 manufacturers.
 
 For those that did do some of this, did you break the bank and use 6
 months of your life for this testing, or was it relatively quick and
 painless (yeah, right)?
 
 We're considering shaking and baking our telecom unit using these types
 of tests as a design verification tool, but one doesn't hear much about
 it on the newswire...
 
 Dwight
 
 p.s. HALT - Highly Accelerated Life Testing
  HASS - Highly Accelerated Stress Screening
 
 -- 
 
 DWIGHT HUNNICUTT
 Sr. Compliance Engineer
 
 
 *  dwi...@vina-tech.com  *
 *  (510) 413-1349 direct   *
 *  (510) 492-0808 fax  *
 *  VINA Technologies,Inc.  *
 *  42709 Lawrence Place*
 *  Fremont, CA  94538  *
 
 


RE: Blatant Suggestion

1998-07-13 Thread GOEDDERZ, JIM
Just to offer another idea.

These recorders work great in the car. Taking a note on paper can be quite a
hazard while your driving along. I've used one for about a year now, and
it's helped me remember lots of ideas, and tasks to jog down later.

James Goedderz
Sensormatic Electronics
goedd...@sensormatic.com
Views expressed by the author do not necessarily represent those of
Sensormatic.



 --
 From: Grant, Tania (Tania)[SMTP:tania.gr...@octel.com]
 Reply To: Grant, Tania (Tania)
 Sent: Monday, July 13, 1998 2:35 PM
 To:   emc-p...@majordomo.ieee.org; 'ed.pr...@cubic.com'
 Subject:  RE: Blatant Suggestion
 
 Thank you, Ed!
 
 I am using Voice-It in my photography to record my camera settings,
 filters used, if any, aperture, etc., but it never dawned on me that I
 could/should use it at work!
 
 Thanks for the suggestion.
 
   Tania Grant
 
  --
  From:   ed.pr...@cubic.com[SMTP:ed.pr...@cubic.com]
  Reply To:   ed.pr...@cubic.com
  Sent:   Friday, July 10, 1998 6:02 PM
  To: emc-p...@majordomo.ieee.org
  Subject:Blatant Suggestion
  
  A very short note to my friends in emc-pstc:
  
  This is not an advertisement.
  This is a product review.
  For people who have to keep track of lots of stuff.
  I'm going to suggest that you buy something.
  
  Did you ever walk into a room and wonder why you went there? I reached
  that stage when I was thirty. So, you resolved to make notes, or even
  carry a notebook. Maybe get a micro tape recorder.
  
  Did it work? Not for me. I kept leaving the tape recorder someplace,
  and I never seemed to be able to get pencil, paper, and ideas at the
  same place and time.
  
  I think I found a great solution. I just discovered a thing called
  Voice It, Model VT-90. It's a 1/4 thick, credit card sized digital
  note recorder. No moving parts. Fits your pocket easily. Very light.
  Simple controls. You get 90 seconds of recording time (more with
  fancier models). I bought mine at Office Depot for $30.
  
  I've been using mine for about a week now, and I can say that the
  price  performance  convenience make this an excellent gadget. I
  just wanted everyone who I've crossed emails with in the past couple
  of years to know about this organizational aid.
  
  Ed
   
  --
  Ed Price
  ed.pr...@cubic.com
  Electromagnetic Compatibility Lab
  Cubic Defense Systems
  San Diego, CA.  USA
  619-505-2780
  Date: 07/10/98
  Time: 17:02:37
  --
  
  
 


RE: Flame Retardants in Europe

1998-07-01 Thread GOEDDERZ, JIM
Darrell, 

I had this information on record. Maybe it will assist your efforts.
**
On July 6th, 1994, the German Government formally revised the Chemical
Prohibition Regulation to include various congeners of brominated dioxins
and furans.  This legislative action, referred to as the German Dioxin
Ordinance, restricts  he allowable concentration (parts per billion level)
of brominated dioxins and furans in products sold in Germany.  Brominated
compounds thought to generate these dioxins and furans may be used as flame
retardants in plastic resins and components   using plastic resins. The law
will prohibit marketing in Germany any substance, preparation or product
containing more than  the specified limits for the brominated dioxins and
furans listed in the ordinance. Products and parts that weigh less than 50
grams are exempt from the limit requirements for some compounds.

James Goedderz
Sensormatic Electronics
goedd...@sensormatic.com
Views expressed by the author do not necessarily represent those of
Sensormatic.




 --
 From: Darrell Locke (MSMail)[SMTP:dlo...@advanced-input.com]
 Reply To: Darrell Locke (MSMail)
 Sent: Tuesday, June 30, 1998 5:40 PM
 To:   'emc-p...@majordomo.ieee.org'
 Subject:  Flame Retardants in Europe
 
 Dear Members,
 
 We recently had an issue with a plastic bezel and the flammability
 requirements for the part.  We were told by our molder that the material
 we wished to use contained polybrominated diphenyl ether (PBDE) as a
 flame retardant  additive to achieve the required flammability, and that
 these additives have been banned in Europe.  I have been trying to
 identify which law, regulation, or standard states this but all I have
 found so far is mostly heresay.  Can anyone give me any more definitive
 information on the prohibition of these flame retardants in Europe.
 
 Thanks as always
 
 Darrell Locke
 Advanced Input Devices
 


Cordage

1998-04-16 Thread GOEDDERZ, JIM
Hello group,

I have a vendor that wants to sell us line cords for use in Europe. There
are several agency marks on the cordage, but no HAR.  The plugs have
several agency approvals.

Does anyone know the legal requirement for marking the cordage.

I have seen references to HD-21 and HD-22, but do not have a copy.
Apparently these indicate that either the approval agency, or the HAR is
to appear on the cordage.

Thank you for your responses.

James Goedderz
Sensormatic


optocoupler

1998-02-19 Thread GOEDDERZ, JIM

 Does anyone have knowledge of VDE 0884, 'optocouplers', and why it is
 more difficult to get approval to than UL1577 Optical Isolators?
 
 Particularly, the Dielectric withstand voltage required, and something
 about charge transfer between the emitter and detector.
 
 Thank you
 
 James Goedderz
 goedd...@sensormatic.com
 
 


RE: Who

1998-01-30 Thread GOEDDERZ, JIM
I recently confirmed that the correct addressing is:

To: majord...@majordomo.ieee.org

Message: who emc-pstc

James Goedderz
Sensormatic
 --
 From: ben_perrea...@ub.com[SMTP:ben_perrea...@ub.com]
 Reply To: ben_perrea...@ub.com
 Sent: Friday, January 30, 1998 8:59 AM
 To:   chasgra...@aol.com
 Cc:   emc-p...@majordomo.ieee.org
 Subject:  Re: Who
 
 
 
 To all the people trying the who I'm pretty sure you have to address
 the
 message to the address
 
 majord...@world.std.com
 
 not emc-p...@majordomo.ieee.org or t...@majordomo.ieee.org
 
 Ben Perreault
 EMC Engineer
 Newbridge Networks
 
 =
 
 
 
 
 
 chasgra...@aol.com on 01/30/98 08:37:37 AM
 
 Please respond to chasgra...@aol.com
 
 
 
 To:   emc-p...@majordomo.ieee.org
 cc:(bcc: Ben Perreault/UB Networks)
 Subject:  Who
 
 
 
 
 who emc-pstc
 
 
 
 
 
 
 


Signal Words

1997-09-02 Thread GOEDDERZ, JIM
In an effort to be as compliant as possible, the following concern has
been raised 
by one of our technical writers.
I know I have seen information on this in the past, but need a
refresher.
Does anyone have details on when a warning or caution should, and should
not be used?
Some sources indicate that a warning is related to personal injury, and
caution to product damage.

Secondly, is there official requirements for letter height, bolding,
spacings of 
additional text from the Warning keyword. Some UL standards indicate
2.8mm 
minimum for the precautionary word, and other words to be 1.6mm high,
and 
contrasting to the background. (UL1409)
 
Thank you in advance for any assistance.

James Goedderz
goedd...@sensormatic.com





HTML 1.1

1997-06-27 Thread GOEDDERZ, JIM

 HTML-Internet References

This is to let you know that I have just completed an amended version of
the 
HTML for all (relevant?) Internet references mentioned on this
newsgroup.

Hope you find it useful:  suggestions for additions or corrections are
welcomed.

Netscape:
FILE, OPEN FILE..., locate the PSNet.htm file in your directory and
choose it;  or

OPTIONS, GENERAL PREFERENCES, APPEARANCE
Choose  START WITH, Home page or FILE LOCATION (depends on version), and
enter  FILE:///...location...\PSNet.HTM in the field. (...location...
indicates what drive and directories you saved the PSNet.HTM file to.)
When you start, the file will open for you.
***
Internet Explorer:
FILE.OPEN.ADDRESS  ...location...\PSNet.HTM   or

VIEW.OPTIONS.NAVIGATION.ADDRESS
ENTER  file:...location...\PSNet.HTM
or start the PSNet.HTM page, and then VIEW.OPTIONS.NAVIGATION, press
Use Current.
When you start, the file will open for you.
***
 
James Goedderz - goedd...@sensormatic.com

=
As always, the content of this message can not be blamed on my employer.

=



PSNET.HTM
Description: Binary data


Bromine

1997-06-10 Thread GOEDDERZ, JIM
Safety People:

A few years back, I remember there being some controversy, or dictates,
about the use of  plastics containing bromine (to improve flammability
rating).

I am unable to find any of the reference material on this, and would
like to know if anyone has information concerning laws, prohibitions,
permissions of use, or whatever, especially as regards the use in
Europe.

Thank you for your assistance.

*
Jim Goedderz *
goedd...@sensormatic.com  *
 *
*


Netscape

1997-04-03 Thread GOEDDERZ, JIM

Fellow Internet users. I have taken all the Web references that I have
received over the past months on this newsgroup, and compiled them into
a file that you can load into your browser. My apologies to any site
that was missed. All sites were checked for functionality. Enjoy.

For Netscape 1  2

Choose FILE, OPEN FILE..., locate the PSNet.htm file in your directory
and choose it. Click OK.

or

Start Netscape, Choose OPTIONS, GENERAL PREFERENCES, APPEARANCE
Choose Start up; START WITH, Home page or FILE LOCATION (depends on
version), and enter  FILE:///C:\...location...\PSNet.html  in the field.
(...location... indicates what drive and directories you saved the
PSNet.htm file to.) Press OK. Exit Netscape.

When you start Netscape, the file will open for you.

The location window should read something similar to
FILE:///C:\NETRUN\NETSCAPE\HTTP\PSNet.HTM

A similar system will probably work with other browsers.

James Goedderz
Sensormatic
goedd...@sensormatic.com for comments

 


PSNET.HTM
Description: Binary data


Corona

1997-03-11 Thread GOEDDERZ, JIM

Question:

Does anyone have information on a Commercial corona detector?

As an alternate, how about info on : corona sensors, ozone sensors,
ozone detection equipment (low level)?

How about reliable homebrew methods?

Thank you in advance for your assistance.

James Goedderz
Sensormatic
goedd...@sensormatic.com