Re: 120V Ground Faults

2001-10-26 Thread Robert Macy

Michael,

The arcing was between hot and neutral.  GFCI outlets would have made no
difference.

- Robert -

   Robert A. Macy, PEm...@california.com
   408 286 3985  fx 408 297 9121
   AJM International Electronics Consultants
   619 North First St,   San Jose, CA  95112

-Original Message-
From: michael.garret...@radisys.com 
To: emc-p...@majordomo.ieee.org 
Cc: Robert Macy 
List-Post: emc-pstc@listserv.ieee.org
Date: Thursday, October 25, 2001 5:52 PM
Subject: 120V Ground Faults


>
>Robert,
>
>>From my experience,  I think you will find that arcing ground faults are
>inherently high-resistance in nature and, while dramatic, do not
>necessarily pull significant amounts of current.  Most 15 amp breakers will
>likely require several seconds/minutes to blow at 60/30 amps, which is what
>you'd get with a 2/4 ohm arc.  In reality, I wouldn't be surprised to see
>something more like a 10-20 ohm figure being used for this type of
>phenomenon, which would allow a 15 amp breaker to arc virtually
>continuously (i.e. the home arc-welder).  The fact that arcs are drawn -
>and sustained - at 120 volts is, I believe, relatively rare.
>
>Higher voltage systems (and GFCI outlets) have ground fault systems that
>rely on the detection of zero sequence (neutral leakage) currents.  My
>understanding is that the decision to require this type of protection on
>480 volt systems over 1200 amps was largely due to the increased likelihood
>they'd be able to draw and sustain an arc, as well as the damage that can
>be caused at these higher power levels (balanced with the concerns of
>cost-effectiveness of installing them more broadly).  I feel they drew the
>line in an appropriate place.
>
>In my experience, while problems, such as this, do arise, the frequency and
>relative damage caused by them is relatively small.  I think you would have
>seen a change (like the addition of GFCI about 25 years ago) if the case
>were otherwise.  You should be able to add zero sequence current sensing to
>your household panel, should you care to do so, for ~$500, but where
>out-of-the-box systems exist for 480 volt systems, this would need to be a
>custom design amploying the combination of a sensor relay and a shunt-trip
>breaker.  Of course any nuisance trips you may experience similar to your
>GFCI would take down your main You can buy a LOT of GFCI breakers for
>these dollars.  Caveat Emptor/Engineer.
>
>Regards,
>
>Michael Garretson
>Compliance Engineering Manager
>RadiSys Corporation
>+1 503 615-1227
>
>
>
>"Robert Macy"
> To: "Dan Kwok"
, 
>Sent by:  cc:
>owner-emc-pstc@majordom   Subject: Re: skinny
power cords.
>o.ieee.org
>
>
>10/25/01 02:36 PM
>Please respond to
>"Robert Macy"
>
>
>
>
>
>
>
>It definitely was not supplied by the heater company.  It was a high
>quality
>UL approved cord.  It's just that this cord carbonized and burst into flame
>as the arc was existing.  The flames did immediately extinguish when the
>arc
>was stopped by unplugging the cord which is good.
>
>But again, it was disturbing that the 15A breaker provided no protection.
>
>Anyway, it was a good lesson for this "sleeping" guy.  Now I take
>electrical
>distribution inside my home much more seriously.
>
>   - Robert -
>
>   Robert A. Macy, PEm...@california.com
>   408 286 3985  fx 408 297 9121
>   AJM International Electronics Consultants
>   619 North First St,   San Jose, CA  95112
>
>-Original Message-
>From: Dan Kwok 
>To: Robert Macy ; emc-p...@majordomo.ieee.org
>
>Date: Thursday, October 25, 2001 1:42 PM
>Subject: Re: skinny power cords.
>
>
>>
>>Hi Robert,
>>
>>Recently, I bought several similar heaters for my home. I recall reading
>in
>>the operation instructions, explicit safety warnings against using
>extension
>>cords with the heater. Was the extension cord supplied with the heater?
>>
>>
>>-
>>Dan Kwok,  P.Eng.
>>Principal Engineer
>>Electromagnetic Compatibility
>>Intetron Consulting,  Inc.
>>Ph  (604) 432-9874
>>E-mail dk...@intetron.com
>>Internet  http://www.intetron.com
>>
>>- Original Message -
>>From: "Robert Macy" 
>>To: "Roman, Dan" ; 
>>Sent: Thursday, Octobe

120V Ground Faults

2001-10-26 Thread Michael . Garretson


Robert,

>From my experience,  I think you will find that arcing ground faults are
inherently high-resistance in nature and, while dramatic, do not
necessarily pull significant amounts of current.  Most 15 amp breakers will
likely require several seconds/minutes to blow at 60/30 amps, which is what
you'd get with a 2/4 ohm arc.  In reality, I wouldn't be surprised to see
something more like a 10-20 ohm figure being used for this type of
phenomenon, which would allow a 15 amp breaker to arc virtually
continuously (i.e. the home arc-welder).  The fact that arcs are drawn -
and sustained - at 120 volts is, I believe, relatively rare.

Higher voltage systems (and GFCI outlets) have ground fault systems that
rely on the detection of zero sequence (neutral leakage) currents.  My
understanding is that the decision to require this type of protection on
480 volt systems over 1200 amps was largely due to the increased likelihood
they'd be able to draw and sustain an arc, as well as the damage that can
be caused at these higher power levels (balanced with the concerns of
cost-effectiveness of installing them more broadly).  I feel they drew the
line in an appropriate place.

In my experience, while problems, such as this, do arise, the frequency and
relative damage caused by them is relatively small.  I think you would have
seen a change (like the addition of GFCI about 25 years ago) if the case
were otherwise.  You should be able to add zero sequence current sensing to
your household panel, should you care to do so, for ~$500, but where
out-of-the-box systems exist for 480 volt systems, this would need to be a
custom design amploying the combination of a sensor relay and a shunt-trip
breaker.  Of course any nuisance trips you may experience similar to your
GFCI would take down your main You can buy a LOT of GFCI breakers for
these dollars.  Caveat Emptor/Engineer.

Regards,

Michael Garretson
Compliance Engineering Manager
RadiSys Corporation
+1 503 615-1227




"Robert Macy"   

 To: "Dan Kwok" 
, 
Sent by:  cc:   

owner-emc-pstc@majordom   Subject: Re: skinny power 
cords.  
o.ieee.org  





10/25/01 02:36 PM   

Please respond to   

"Robert Macy"   










It definitely was not supplied by the heater company.  It was a high
quality
UL approved cord.  It's just that this cord carbonized and burst into flame
as the arc was existing.  The flames did immediately extinguish when the
arc
was stopped by unplugging the cord which is good.

But again, it was disturbing that the 15A breaker provided no protection.

Anyway, it was a good lesson for this "sleeping" guy.  Now I take
electrical
distribution inside my home much more seriously.

   - Robert -

   Robert A. Macy, PEm...@california.com
   408 286 3985  fx 408 297 9121
   AJM International Electronics Consultants
   619 North First St,   San Jose, CA  95112

-Original Message-
From: Dan Kwok 
To: Robert Macy ; emc-p...@majordomo.ieee.org

List-Post: emc-pstc@listserv.ieee.org
Date: Thursday, October 25, 2001 1:42 PM
Subject: Re: skinny power cords.


>
>Hi Robert,
>
>Recently, I bought several similar heaters for my home. I recall reading
in
>the operation instructions, explicit safety warnings against using
extension
>cords with the heater. Was the extension cord supplied with the heater?
>
>
>-
>Dan Kwok,  P.Eng.
>Principal Engineer
>Electromagnetic Compatibility
>Intetron Consulting,  Inc.
>Ph  (604) 432-9874
>E-mail dk...@intetron.com
>Internet  http://www.intetron.com
>
>-