RE: SMPS Derating reqs for Altitude range of 5000-10000ft

2002-01-08 Thread Carmen.Filimon


Thank you for all your answers related to my question. I' ve got good ideas
for this area and I appreciate your time and kindness to do it.

Best wishes and Happy New Year to all of you!

Regards,
Carmen Filimon
Leitch Canada




 -Original Message-
 From: Alexandru Guidea [SMTP:gui...@cae.com]
 Sent: Tuesday, January 08, 2002 8:57 AM
 To:   'Carmen.Filimon'; 'EMC Forum'
 Subject:  RE: SMPS Derating  reqs for Altitude range of 5000-1ft
 Importance:   Low
 
 As mentioned by some colleagues in this forum, some thermal effects due to
 altitude are caused by reduced air density, which decreases the heath
 dissipation through convection.
 The percentage of heath dissipation by convection depends of the
 construction of each power supply (I don't believe most of the
 manufacturers
 are able to provide a number there). For terrestrial application, the
 convection being the dominant path, anything above 50% can be a good
 guess.
 By determining the density of the air at a given altitude versus normal
 operating level it can be determined the impact on convection, and
 ultimately the derating of the PS.
 To be noted that: forced air, or natural convection cooling processes are
 not affected the same way; PS' working in uncontrolled environments at
 high
 altitude can be affected by low ambient temperatures.
 And as a final note, sometimes the experiment is the fastest, easiest way.
 
 Alexandru Guidea
 
 CAE Inc.
 Canada
 
 (my opinion and only mine)
 
 
 -Original Message-
 From: Carmen.Filimon [mailto:carmen.fili...@leitch.com]
 Sent: Friday, January 04, 2002 11:28 AM
 To: EMC Forum
 Subject: SMPS Derating reqs for Altitude range of 5000-1ft
 
 
 
   Hi All
 
   I'm trying to find out what the specified operational altitude
 range(s) is (are) for power supplies (particularly switching mode ones).
 Do
 any of you know what that spec may be, and particularly what is the rule
 for
 derating at altitude for thermal issues. Many manufacturers don't specify
 a
 maximum altitude but instead design in enough thermal overhead to
 accommodate any reasonable terrestrial location. 
 According to GR-63-CORE the operating range without derating is 1800m
 above
 sea level.  If derating is required above 1800m
 then the manufacturer must specify any additional requirements. Is it a
 safety derating factor so that customers at 5000-1ft don't smell
 smoke?
 Do we have any recommendations for derating the operational temperature /
 power consumption of power supplies as the operational altitude increases?
 
 Any information or ideas you have would be appreciated. 
 
 Regards,
 
 Carmen Filimon
 Leitch Canada
   
  
 
 ---
 This message is from the IEEE EMC Society Product Safety
 Technical Committee emc-pstc discussion list.
 
 Visit our web site at:  http://www.ewh.ieee.org/soc/emcs/pstc/
 
 To cancel your subscription, send mail to:
  majord...@ieee.org
 with the single line:
  unsubscribe emc-pstc
 
 For help, send mail to the list administrators:
  Michael Garretson:pstc_ad...@garretson.org
  Dave Healddavehe...@mediaone.net
 
 For policy questions, send mail to:
  Richard Nute:   ri...@ieee.org
  Jim Bacher: j.bac...@ieee.org
 
 All emc-pstc postings are archived and searchable on the web at:
 No longer online until our new server is brought online and the old
 messages are imported into the new server.

---
This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

Visit our web site at:  http://www.ewh.ieee.org/soc/emcs/pstc/

To cancel your subscription, send mail to:
 majord...@ieee.org
with the single line:
 unsubscribe emc-pstc

For help, send mail to the list administrators:
 Michael Garretson:pstc_ad...@garretson.org
 Dave Healddavehe...@mediaone.net

For policy questions, send mail to:
 Richard Nute:   ri...@ieee.org
 Jim Bacher: j.bac...@ieee.org

All emc-pstc postings are archived and searchable on the web at:
No longer online until our new server is brought online and the old 
messages are imported into the new server.


Re: SMPS Derating reqs for Altitude range of 5000-10000ft

2002-01-04 Thread Rich Nute




Hi Chris, Andrew, Carmen:


With regard to safety, both effects of altitude
must be considered:

1)  effect of air pressure on the electric 
strength of air (clearance), and

2)  effect of lower density air on the 
temperature of solid insulation.

(Creepage is a surface degradation phenomenon
that is solely a function of working voltage,
and is independent of altitude.  But, creepage
can never be less than the parallel clearance,
so the creepage may also be affected for those
situations where the minimum clearance is 
greater than the allowed creepage.)


Best wishes for the New Year,
Rich





---
This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

Visit our web site at:  http://www.ewh.ieee.org/soc/emcs/pstc/

To cancel your subscription, send mail to:
 majord...@ieee.org
with the single line:
 unsubscribe emc-pstc

For help, send mail to the list administrators:
 Michael Garretson:pstc_ad...@garretson.org
 Dave Healddavehe...@mediaone.net

For policy questions, send mail to:
 Richard Nute:   ri...@ieee.org
 Jim Bacher: j.bac...@ieee.org

All emc-pstc postings are archived and searchable on the web at:
No longer online until our new server is brought online and the old 
messages are imported into the new server.


RE: SMPS Derating reqs for Altitude range of 5000-10000ft

2002-01-04 Thread Chris Maxwell

I agree that creepage and clearance distances change.

However, I'm not sure if you can answer that it is not a power issue.
If the power supply depends on air for cooling; wouldn't the less dense
air at higher altitudes be less effective at cooling the supply?  

A rough guess (admittedly thought up as I'm typing this message) would
be that the cooling effectiveness of air would vary proportionally with
air density.  A furthur stretch of that reasoning would lead me to
believe that the power ratings of forced air cooled supplies would also
vary  with air density.   It may not vary  with one to one
correspondence due to the fact that there are other cooling mechanisms
such as radiative cooling which can occur without air.

As altidude goes up, air density goes down. Wouldn't cooling
effectiveness also go down leading to a slightly lower power rating for
air cooled supplies?

Chris Maxwell | Design Engineer - Optical Division
email chris.maxw...@nettest.com | dir +1 315 266 5128 | fax +1 315 797
8024

NetTest | 6 Rhoads Drive, Utica, NY 13502 | USA
web www.nettest.com | tel +1 315 797 4449 | 




 -Original Message-
 From: Andrew Carson [SMTP:acar...@uk.xyratex.com]
 Sent: Friday, January 04, 2002 12:59 PM
 To:   Carmen.Filimon
 Cc:   EMC Forum
 Subject:  Re: SMPS Derating  reqs for Altitude range of
 5000-1ft
 
 
 Carmen
 
 If your power supply is approved to IEC60950, then normally it will be
 approved upto 2000m. Above this altitude the
 required creepage and clearance distances start to increase. It is an
 electrical insulation issue, not a thermal
 issue.
 
 Carmen.Filimon wrote:
 
  Hi All
 
  I'm trying to find out what the specified operational
 altitude
  range(s) is (are) for power supplies (particularly switching mode
 ones). Do
  any of you know what that spec may be, and particularly what is the
 rule for
  derating at altitude for thermal issues. Many manufacturers don't
 specify a
  maximum altitude but instead design in enough thermal overhead to
  accommodate any reasonable terrestrial location.
  According to GR-63-CORE the operating range without derating is
 1800m above
  sea level.  If derating is required above 1800m
  then the manufacturer must specify any additional requirements. Is
 it a
  safety derating factor so that customers at 5000-1ft don't smell
 smoke?
  Do we have any recommendations for derating the operational
 temperature /
  power consumption of power supplies as the operational altitude
 increases?
 
  Any information or ideas you have would be appreciated.
 
  Regards,
 
  Carmen Filimon
  Leitch Canada
  
  
 
  ---
  This message is from the IEEE EMC Society Product Safety
  Technical Committee emc-pstc discussion list.
 
  Visit our web site at:  http://www.ewh.ieee.org/soc/emcs/pstc/
 
  To cancel your subscription, send mail to:
   majord...@ieee.org
  with the single line:
   unsubscribe emc-pstc
 
  For help, send mail to the list administrators:
   Michael Garretson:pstc_ad...@garretson.org
   Dave Healddavehe...@mediaone.net
 
  For policy questions, send mail to:
   Richard Nute:   ri...@ieee.org
   Jim Bacher: j.bac...@ieee.org
 
  All emc-pstc postings are archived and searchable on the web at:
  No longer online until our new server is brought online and the
 old messages are imported into the new server.
 
 --
 
 Andrew Carson - Senior Compliance Engineer, Xyratex, UK
 Phone: +44 (0)23 9249 6855 Fax: +44 (0)23 9249 6014
 
 
 
 ---
 This message is from the IEEE EMC Society Product Safety
 Technical Committee emc-pstc discussion list.
 
 Visit our web site at:  http://www.ewh.ieee.org/soc/emcs/pstc/
 
 To cancel your subscription, send mail to:
  majord...@ieee.org
 with the single line:
  unsubscribe emc-pstc
 
 For help, send mail to the list administrators:
  Michael Garretson:pstc_ad...@garretson.org
  Dave Healddavehe...@mediaone.net
 
 For policy questions, send mail to:
  Richard Nute:   ri...@ieee.org
  Jim Bacher: j.bac...@ieee.org
 
 All emc-pstc postings are archived and searchable on the web at:
 No longer online until our new server is brought online and the
 old messages are imported into the new server.

---
This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

Visit our web site at:  http://www.ewh.ieee.org/soc/emcs/pstc/

To cancel your subscription, send mail to:
 majord...@ieee.org
with the single line:
 unsubscribe emc-pstc

For help, send mail to the list administrators:
 Michael Garretson:pstc_ad...@garretson.org
 Dave Healddavehe...@mediaone.net

For policy questions, send mail to:
 Richard Nute:   ri...@ieee.org
 Jim Bacher

Re: SMPS Derating reqs for Altitude range of 5000-10000ft

2002-01-04 Thread ed . rauch


Actually, it is both. The decreasing density of air results in a lower
voltage withstand and a lower rate of convection cooling.. IEC 60950 only
addresses the safety aspect of the change, not the operational aspects.



acar...@uk.xyratex.com (Andrew Carson)@majordomo.ieee.org on 01/04/2002
11:59:15 AM

Please respond to acar...@uk.xyratex.com (Andrew Carson)

Sent by:  owner-emc-p...@majordomo.ieee.org


To:   Carmen.Filimon carmen.fili...@leitch.com
cc:   EMC Forum emc-p...@ieee.org

Subject:  Re: SMPS Derating  reqs for Altitude range of 5000-1ft



Carmen

If your power supply is approved to IEC60950, then normally it will be
approved upto 2000m. Above this altitude the
required creepage and clearance distances start to increase. It is an
electrical insulation issue, not a thermal
issue.

Carmen.Filimon wrote:

 Hi All

 I'm trying to find out what the specified operational altitude
 range(s) is (are) for power supplies (particularly switching mode ones).
Do
 any of you know what that spec may be, and particularly what is the rule
for
 derating at altitude for thermal issues. Many manufacturers don't specify
a
 maximum altitude but instead design in enough thermal overhead to
 accommodate any reasonable terrestrial location.
 According to GR-63-CORE the operating range without derating is 1800m
above
 sea level.  If derating is required above 1800m
 then the manufacturer must specify any additional requirements. Is it a
 safety derating factor so that customers at 5000-1ft don't smell
smoke?
 Do we have any recommendations for derating the operational temperature /
 power consumption of power supplies as the operational altitude
increases?

 Any information or ideas you have would be appreciated.

 Regards,

 Carmen Filimon
 Leitch Canada
 
 

 ---
 This message is from the IEEE EMC Society Product Safety
 Technical Committee emc-pstc discussion list.

 Visit our web site at:  http://www.ewh.ieee.org/soc/emcs/pstc/

 To cancel your subscription, send mail to:
  majord...@ieee.org
 with the single line:
  unsubscribe emc-pstc

 For help, send mail to the list administrators:
  Michael Garretson:pstc_ad...@garretson.org
  Dave Healddavehe...@mediaone.net

 For policy questions, send mail to:
  Richard Nute:   ri...@ieee.org
  Jim Bacher: j.bac...@ieee.org

 All emc-pstc postings are archived and searchable on the web at:
 No longer online until our new server is brought online and the old
messages are imported into the new server.

--

Andrew Carson - Senior Compliance Engineer, Xyratex, UK
Phone: +44 (0)23 9249 6855 Fax: +44 (0)23 9249 6014



---
This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

Visit our web site at:  http://www.ewh.ieee.org/soc/emcs/pstc/

To cancel your subscription, send mail to:
 majord...@ieee.org
with the single line:
 unsubscribe emc-pstc

For help, send mail to the list administrators:
 Michael Garretson:pstc_ad...@garretson.org
 Dave Healddavehe...@mediaone.net

For policy questions, send mail to:
 Richard Nute:   ri...@ieee.org
 Jim Bacher: j.bac...@ieee.org

All emc-pstc postings are archived and searchable on the web at:
No longer online until our new server is brought online and the old
messages are imported into the new server.




---
This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

Visit our web site at:  http://www.ewh.ieee.org/soc/emcs/pstc/

To cancel your subscription, send mail to:
 majord...@ieee.org
with the single line:
 unsubscribe emc-pstc

For help, send mail to the list administrators:
 Michael Garretson:pstc_ad...@garretson.org
 Dave Healddavehe...@mediaone.net

For policy questions, send mail to:
 Richard Nute:   ri...@ieee.org
 Jim Bacher: j.bac...@ieee.org

All emc-pstc postings are archived and searchable on the web at:
No longer online until our new server is brought online and the old 
messages are imported into the new server.


RE: SMPS Derating reqs for Altitude range of 5000-10000ft

2002-01-04 Thread Dan Teninty

From the Paschen curve, the electrical spacings must be increased 14% at
3000 meters over those at 2000 meters. Thermal derating is a tougher call
since some smps vendors engineer in more cooling capacity than others.
Testing for your application is the only reliable way to make a good
determination if the manufacturer does not specify a derating curve.

Daniel E. Teninty, P.E.
Managing Partner
DTEC Associates LLC
Streamlining The Compliance Process
Advancing New Products To Market
http://www.dtec-associates.com
(509) 443-0215
(509) 443-0181 fax

-Original Message-
From: owner-emc-p...@majordomo.ieee.org
[mailto:owner-emc-p...@majordomo.ieee.org]On Behalf Of Carmen.Filimon
Sent: Friday, January 04, 2002 8:28 AM
To: EMC Forum
Subject: SMPS Derating reqs for Altitude range of 5000-1ft



Hi All

I'm trying to find out what the specified operational altitude
range(s) is (are) for power supplies (particularly switching mode ones). Do
any of you know what that spec may be, and particularly what is the rule for
derating at altitude for thermal issues. Many manufacturers don't specify a
maximum altitude but instead design in enough thermal overhead to
accommodate any reasonable terrestrial location.
According to GR-63-CORE the operating range without derating is 1800m above
sea level.  If derating is required above 1800m
then the manufacturer must specify any additional requirements. Is it a
safety derating factor so that customers at 5000-1ft don't smell smoke?
Do we have any recommendations for derating the operational temperature /
power consumption of power supplies as the operational altitude increases?

Any information or ideas you have would be appreciated.

Regards,

Carmen Filimon
Leitch Canada



---
This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

Visit our web site at:  http://www.ewh.ieee.org/soc/emcs/pstc/

To cancel your subscription, send mail to:
 majord...@ieee.org
with the single line:
 unsubscribe emc-pstc

For help, send mail to the list administrators:
 Michael Garretson:pstc_ad...@garretson.org
 Dave Healddavehe...@mediaone.net

For policy questions, send mail to:
 Richard Nute:   ri...@ieee.org
 Jim Bacher: j.bac...@ieee.org

All emc-pstc postings are archived and searchable on the web at:
No longer online until our new server is brought online and the old
messages are imported into the new server.


---
This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

Visit our web site at:  http://www.ewh.ieee.org/soc/emcs/pstc/

To cancel your subscription, send mail to:
 majord...@ieee.org
with the single line:
 unsubscribe emc-pstc

For help, send mail to the list administrators:
 Michael Garretson:pstc_ad...@garretson.org
 Dave Healddavehe...@mediaone.net

For policy questions, send mail to:
 Richard Nute:   ri...@ieee.org
 Jim Bacher: j.bac...@ieee.org

All emc-pstc postings are archived and searchable on the web at:
No longer online until our new server is brought online and the old 
messages are imported into the new server.


Re: SMPS Derating reqs for Altitude range of 5000-10000ft

2002-01-04 Thread Andrew Carson

Carmen

If your power supply is approved to IEC60950, then normally it will be approved 
upto 2000m. Above this altitude the
required creepage and clearance distances start to increase. It is an 
electrical insulation issue, not a thermal
issue.

Carmen.Filimon wrote:

 Hi All

 I'm trying to find out what the specified operational altitude
 range(s) is (are) for power supplies (particularly switching mode ones). Do
 any of you know what that spec may be, and particularly what is the rule for
 derating at altitude for thermal issues. Many manufacturers don't specify a
 maximum altitude but instead design in enough thermal overhead to
 accommodate any reasonable terrestrial location.
 According to GR-63-CORE the operating range without derating is 1800m above
 sea level.  If derating is required above 1800m
 then the manufacturer must specify any additional requirements. Is it a
 safety derating factor so that customers at 5000-1ft don't smell smoke?
 Do we have any recommendations for derating the operational temperature /
 power consumption of power supplies as the operational altitude increases?

 Any information or ideas you have would be appreciated.

 Regards,

 Carmen Filimon
 Leitch Canada
 
 

 ---
 This message is from the IEEE EMC Society Product Safety
 Technical Committee emc-pstc discussion list.

 Visit our web site at:  http://www.ewh.ieee.org/soc/emcs/pstc/

 To cancel your subscription, send mail to:
  majord...@ieee.org
 with the single line:
  unsubscribe emc-pstc

 For help, send mail to the list administrators:
  Michael Garretson:pstc_ad...@garretson.org
  Dave Healddavehe...@mediaone.net

 For policy questions, send mail to:
  Richard Nute:   ri...@ieee.org
  Jim Bacher: j.bac...@ieee.org

 All emc-pstc postings are archived and searchable on the web at:
 No longer online until our new server is brought online and the old 
 messages are imported into the new server.

--

Andrew Carson - Senior Compliance Engineer, Xyratex, UK
Phone: +44 (0)23 9249 6855 Fax: +44 (0)23 9249 6014



---
This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

Visit our web site at:  http://www.ewh.ieee.org/soc/emcs/pstc/

To cancel your subscription, send mail to:
 majord...@ieee.org
with the single line:
 unsubscribe emc-pstc

For help, send mail to the list administrators:
 Michael Garretson:pstc_ad...@garretson.org
 Dave Healddavehe...@mediaone.net

For policy questions, send mail to:
 Richard Nute:   ri...@ieee.org
 Jim Bacher: j.bac...@ieee.org

All emc-pstc postings are archived and searchable on the web at:
No longer online until our new server is brought online and the old 