Re: Surge Testing per EN 55024/EN61000-4-5

2000-03-03 Thread rc

In the Test-Setup Section, Conditions during Testing of EN 55024 it is said:

Test should be made in the most representative mode.

To my understanding, in the present days most ITE Equipment and Peripherals
comes with a 3-prong plug, i.e. it is grounded.

So, if the EUT has external ports intended to be connected to  ITE Peripherals ,
Surge Testing should be done Line to Ground, with the secondary side of the
Equipment Grounded, or with a Grounded ITE Peripheral connected.

Dipl.-Ing. Rene Charton
Manager
EMC Services
_
TUV Rheinland Taiwan Ltd.
TAIPEI HEAD OFFICE
Spring Plaza Building
14F, No.6, Min Chuan E. Rd., Sec. 3,
Taipei 104, Taiwan, R. O. C.
Tel. (02) 2516 6040 Ext. [ 086 ]   e-mail:  r...@twn.tuv.com






Please respond to Jim Hulbert hulbe...@pb.com

To:   emc-p...@ieee.org
cc:(bcc: Rene Charton/TUV-Twn)
Subject:  Surge Testing per EN 55024/EN61000-4-5






Colleagues,

EN 55024 calls for surge pulses to be applied line-to-line and line-to-earth on
the AC mains port and line-to-ground on signal and telecommunications ports that
connect directly to outdoor cables.   However, if my EUT is encased in plastic
covers and has no direct earth ground connection (class 2 power supply), is the
line-to-line test on the AC mains the only surge test that I need to apply?   It
seems to me that performing a line-to-earth test on either the AC mains port or
on signal/telecommunications ports is not warranted since the basic standard EN
61000-4-5 does not specify placing the EUT over a reference ground plane.   With
no reference ground plane and no direct ground connection how can a test be
applied with respect to ground?

Jim Hulbert
Pitney Bowes



-
This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

To cancel your subscription, send mail to:
 majord...@ieee.org
with the single line:
 unsubscribe emc-pstc

For help, send mail to the list adminstrators:
 Jim Bacher:  jim_bac...@mail.monarch.com, or
 Michael Garretson:pstc_ad...@garretson.org
For policy questions, send mail to:
 Richard Nute:   ri...@ieee.org









---
This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

To cancel your subscription, send mail to:
 majord...@ieee.org
with the single line:
 unsubscribe emc-pstc

For help, send mail to the list administrators:
 Jim Bacher:  jim_bac...@mail.monarch.com
 Michael Garretson:pstc_ad...@garretson.org

For policy questions, send mail to:
 Richard Nute:   ri...@ieee.org



RE: Surge Testing per EN 55024/EN61000-4-5

2000-03-02 Thread Lacey,Scott

Jim,
You do in fact have a potential ground connection - at the phone line. In
the static (on-hook) state you will have -48 Vdc, referenced to earth. If
you look at your home phone service you will see a wire running to a cold
water pipe, with a tag that says something like Telephone Company Ground -
Do Not Remove. PBX systems at work will be different. I have little
knowledge of whether they ground or not. I have learned the hard way to look
for these non-obvious ground connections.

Best wishes,

Scott Lacey

-Original Message-
From:   Jim Hulbert [SMTP:hulbe...@pb.com]
Sent:   Thursday, March 02, 2000 8:52 AM
To: Lacey,Scott; emc-p...@ieee.org
Subject:RE: Surge Testing per EN 55024/EN61000-4-5




Scott,

The product I'm currently looking at uses a 2 -prong AC mains plug.
Actually
the supply is small direct plug-in type with DC leads that connect
to the
product.  The product itself is encased in plastic and the only
other connection
is through an internal modem board to a standard analog telephone
line.  The
connection to the phone line is a simple 2-wire (tip and ring)
configuration.
As I see it, surge tests with reference to earth ground are
pointless.

Others have pointed out that an ungrounded product may in the real
world
actually have a reference to ground depending on how it is installed
or what
other equipment it is connected to.   That is a good point which I
hadn't
thought about.  However, I don't think that in my particular
situation that's
that case.

Thanks to all who responded with their opinions.

Jim





Lacey,Scott sla...@foxboro.com on 03/01/2000 01:31:46 PM

Please respond to Lacey,Scott sla...@foxboro.com

To:   'Jim Hulbert' hulbe...@micro2.pb.com
cc:   'emc-p...@ieee.org' emc-p...@ieee.org (bcc: Jim
Hulbert/MSD/US/PBI)

Subject:  RE: Surge Testing per EN 55024/EN61000-4-5





Jim,
I'm not quite sure from the description what your product looks
like, but,
here are a few things to keep in mind. If you use a 3-prong ac mains
plug
you absolutely should do the line-to-ground test. If you use a
2-prong ac
mains plug you still might want to perform the test anyway,
depending on how
your product is used. For example, if your plastic housing may be
DIN rail
mounted or screwed to a wall, you may have a leakage or arc path to
earth.
Your customer may have deliberately grounded the DIN rail to satisfy
the
requirements of other vendor's equipment already mounted. Even if it
only
gets screwed to a plasterboard wall, it still may get grounded by
accident.
I have seen two such scenarios over the years. In the first instance
one
mounting screw went through the wallboard and touched the grounded
sheath of
a BX cable in an older building. In the second instance a screw
penetrated a
metal stud used to frame the wall. An outlet box was attached to
another
stud. Bingo - instant ground.

I'm sure there are many who will disagree with me, but we test
products not
only to conform to a standard, but also to ensure a more robust
product. I
want to find any vulnerability first, before the product gets to a
customer.
Customers tend to get VERY angry when their new product hiccups,
and the
nasty stuff tends to flow downhill real fast when their CEO calls
yours.

Scott Lacey

 -Original Message-
 From: Jim Hulbert [SMTP:hulbe...@pb.com]
 Sent: Wednesday, March 01, 2000 10:32 AM
 To:  emc-p...@ieee.org
 Subject:  Surge Testing per EN 55024/EN61000-4-5




 Colleagues,

 EN 55024 calls for surge pulses to be applied line-to-line and
line-to-earth on
 the AC mains port and line-to-ground on signal and
telecommunications ports that
 connect directly to outdoor cables.   However, if my EUT is
encased
in plastic
 covers and has no direct earth ground connection (class 2 power
supply), is the
 line-to-line test on the AC mains the only surge test that I
need to
apply?   It
 seems to me that performing a line-to-earth test on either the
AC
mains port or
 on signal/telecommunications ports is not warranted since the
basic
standard EN
 61000-4-5 does not specify placing the EUT over a reference
ground
plane.   With
 no reference ground plane and no direct ground connection how
can a
test be
 applied with respect to ground?

 Jim Hulbert
 Pitney Bowes



 -
 This message is from the IEEE EMC Society Product Safety

RE: Surge Testing per EN 55024/EN61000-4-5

2000-03-02 Thread Jim Hulbert



Scott,

The product I'm currently looking at uses a 2 -prong AC mains plug.  Actually
the supply is small direct plug-in type with DC leads that connect to the
product.  The product itself is encased in plastic and the only other connection
is through an internal modem board to a standard analog telephone line.  The
connection to the phone line is a simple 2-wire (tip and ring) configuration.
As I see it, surge tests with reference to earth ground are pointless.

Others have pointed out that an ungrounded product may in the real world
actually have a reference to ground depending on how it is installed or what
other equipment it is connected to.   That is a good point which I hadn't
thought about.  However, I don't think that in my particular situation that's
that case.

Thanks to all who responded with their opinions.

Jim





Lacey,Scott sla...@foxboro.com on 03/01/2000 01:31:46 PM

Please respond to Lacey,Scott sla...@foxboro.com

To:   'Jim Hulbert' hulbe...@micro2.pb.com
cc:   'emc-p...@ieee.org' emc-p...@ieee.org (bcc: Jim Hulbert/MSD/US/PBI)

Subject:  RE: Surge Testing per EN 55024/EN61000-4-5





Jim,
I'm not quite sure from the description what your product looks like, but,
here are a few things to keep in mind. If you use a 3-prong ac mains plug
you absolutely should do the line-to-ground test. If you use a 2-prong ac
mains plug you still might want to perform the test anyway, depending on how
your product is used. For example, if your plastic housing may be DIN rail
mounted or screwed to a wall, you may have a leakage or arc path to earth.
Your customer may have deliberately grounded the DIN rail to satisfy the
requirements of other vendor's equipment already mounted. Even if it only
gets screwed to a plasterboard wall, it still may get grounded by accident.
I have seen two such scenarios over the years. In the first instance one
mounting screw went through the wallboard and touched the grounded sheath of
a BX cable in an older building. In the second instance a screw penetrated a
metal stud used to frame the wall. An outlet box was attached to another
stud. Bingo - instant ground.

I'm sure there are many who will disagree with me, but we test products not
only to conform to a standard, but also to ensure a more robust product. I
want to find any vulnerability first, before the product gets to a customer.
Customers tend to get VERY angry when their new product hiccups, and the
nasty stuff tends to flow downhill real fast when their CEO calls yours.

Scott Lacey

 -Original Message-
 From: Jim Hulbert [SMTP:hulbe...@pb.com]
 Sent: Wednesday, March 01, 2000 10:32 AM
 To:  emc-p...@ieee.org
 Subject:  Surge Testing per EN 55024/EN61000-4-5




 Colleagues,

 EN 55024 calls for surge pulses to be applied line-to-line and
line-to-earth on
 the AC mains port and line-to-ground on signal and
telecommunications ports that
 connect directly to outdoor cables.   However, if my EUT is encased
in plastic
 covers and has no direct earth ground connection (class 2 power
supply), is the
 line-to-line test on the AC mains the only surge test that I need to
apply?   It
 seems to me that performing a line-to-earth test on either the AC
mains port or
 on signal/telecommunications ports is not warranted since the basic
standard EN
 61000-4-5 does not specify placing the EUT over a reference ground
plane.   With
 no reference ground plane and no direct ground connection how can a
test be
 applied with respect to ground?

 Jim Hulbert
 Pitney Bowes



 -
 This message is from the IEEE EMC Society Product Safety
 Technical Committee emc-pstc discussion list.

 To cancel your subscription, send mail to:
  majord...@ieee.org
 with the single line:
  unsubscribe emc-pstc

 For help, send mail to the list adminstrators:
  Jim Bacher:  jim_bac...@mail.monarch.com, or
  Michael Garretson:pstc_ad...@garretson.org
 For policy questions, send mail to:
  Richard Nute:   ri...@ieee.org


---
This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

To cancel your subscription, send mail to:
 majord...@ieee.org
with the single line:
 unsubscribe emc-pstc

For help, send mail to the list administrators:
 Jim Bacher:  jim_bac...@mail.monarch.com
 Michael Garretson:pstc_ad...@garretson.org

For policy questions, send mail to:
 Richard Nute:   ri...@ieee.org









---
This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

To cancel your subscription, send mail to:
 majord...@ieee.org
with the single line:
 unsubscribe emc-pstc

For help, send mail to the list administrators:
 Jim Bacher:  jim_bac

RE: Surge Testing per EN 55024/EN61000-4-5

2000-03-02 Thread Lacey,Scott

Chris,
In the case you mention, setting the CD player in its normal position on a
grounded steel plate should do. The unit may end up sitting on a steel shelf
unit along with other equipment with grounded chassis. I used such a setup
at home for years.

Scott Lacey

-Original Message-
From:   Colgan, Chris [SMTP:chris.col...@tagmclarenaudio.com]
Sent:   Thursday, March 02, 2000 4:41 AM
To: emc-p...@ieee.org
Subject:RE: Surge Testing per EN 55024/EN61000-4-5


Let's say I'm testing a Class II double insulated CD player - no
reference
to earth.  If the product were stand alone, line to earth testing
would be
pointless, at least as I see it.

It is conceivable that the CD player could be connected to a Class
I,
earthed amplifier.  Through the interconnects, the chassis of the CD
player
could become grounded (there would probably horrendous hum problems
but
that's another story).

Line to earth tests are now valid but how would I set this up in the
lab?  A
lead from the CD player chassis to the nearest socket outlet earth?
A lead
to the chassis of my Keytek surge tester?  A thin lead, a thick
lead?  I
guess the test should be representative of the real world and
repeatable.

Any suggestions?

Regards

Chris Colgan
EMC  Safety
TAG McLaren Audio Ltd

mailto:chris.col...@tagmclarenaudio.com
 


 -Original Message-
 From: Mike  Hopkins [SMTP:mhopk...@keytek.com]
 Sent: 01 March 2000 18:32
 To:   'Jim Hulbert'; emc-p...@ieee.org
 Subject:  RE: Surge Testing per EN 55024/EN61000-4-5
 
 
 As long as there is no other path to ground, a line to line test
would be
 all thats required, but keep in mind, if you have other I/O,
telecom,
 control lines, or anything else coming out of that plastic box,
you then
 have a potential path back to ground, and in fact, will likely
have REAL
 ground connections. For example, many television sets have two
wire power
 plugs, are in plastic cases, but if you have cable tv, the odds
are that
 coax cable is grounded.  Same thing applies if there is a telecom
line
 involved -- very likely one of the telecom lines is ground. ..

 
  Mike Hopkins
 mhopk...@keytek.com
 
  -Original Message-
  From:   Jim Hulbert [SMTP:hulbe...@pb.com]
  Sent:   Wednesday, March 01, 2000 10:32 AM
  To: emc-p...@ieee.org
  Subject:Surge Testing per EN 55024/EN61000-4-5
  
  
  
  
  Colleagues,
  
  EN 55024 calls for surge pulses to be applied line-to-line and
  line-to-earth on
  the AC mains port and line-to-ground on signal and
telecommunications
  ports that
  connect directly to outdoor cables.   However, if my EUT is
encased in
  plastic
  covers and has no direct earth ground connection (class 2 power
supply),
  is the
  line-to-line test on the AC mains the only surge test that I
need to
  apply?   It
  seems to me that performing a line-to-earth test on either the
AC mains
  port or
  on signal/telecommunications ports is not warranted since the
basic
  standard EN
  61000-4-5 does not specify placing the EUT over a reference
ground
 plane.
  With
  no reference ground plane and no direct ground connection how
can a test
  be
  applied with respect to ground?
  
  Jim Hulbert
  Pitney Bowes
  
  
  
  -
  This message is from the IEEE EMC Society Product Safety
  Technical Committee emc-pstc discussion list.
  
  To cancel your subscription, send mail to:
   majord...@ieee.org
  with the single line:
   unsubscribe emc-pstc
  
  For help, send mail to the list adminstrators:
   Jim Bacher:  jim_bac...@mail.monarch.com, or
   Michael Garretson:pstc_ad...@garretson.org
  For policy questions, send mail to:
   Richard Nute:   ri...@ieee.org
  
 
 ---
 This message is from the IEEE EMC Society Product Safety
 Technical Committee emc-pstc discussion list.
 
 To cancel your subscription, send mail to:
  majord...@ieee.org
 with the single line:
  unsubscribe emc-pstc
 
 For help, send mail to the list administrators:
  Jim Bacher:  jim_bac...@mail.monarch.com
  Michael Garretson

RE: Surge Testing per EN 55024/EN61000-4-5

2000-03-02 Thread John Allen

Chris

A comment, which is probably representative of many audio systems (although 
I do appreciate that your company makes fairly high end equipment!).

My Yamaha AV tuner amp (RX-V592RDS) is Class II, as is most of the rest of 
the audio system, but the user manual states that it may be necessary to 
ground the chassis for noise reduction purposes and provides a terminal on 
the back for the purpose. I assume that this can be the star point for both 
the external and the internal earthing since it states nothing to the 
contrary.

There werer certainly noticeable successive reductions in hum/noise on the 
phono input when, very recently, I earthed first the metal chassis of the 
(very old!) turntable to the star point, and then connected the star point 
to a the earth of a spare socket in the mains distribution block.

Both of the above connections would be representative of what most people 
would do - I do'nt think many would star the earths at the 
mains-distribution block first as this could actually increase hum/noise 
problems due to increasing the size of the earth loops.

Both earths were small diameter (0.5/0.75 sq mm or 20/18 AWG) and I would 
not expect anyone to use anything much larger unless specified in the 
installation instructions.

The length of the turntable wire is about 2m and it is incorporated as a 
drain wire in the twin phono lead. The length of the wire from the star 
point is only some 0.5m as that is the actual distance required.

I think these numbers will vary according to the needs to the actual user - 
OR according to what you state in the installation instructions!

Maybe you need to consider real-life situations, make some tests and then 
specify the actual installation cabling requirements or options in the 
instructions. Then YOU will have more control of the situation and the 
pass/fail criteria.

Regards

John Allen
Racal
--
From:   Colgan, Chris[SMTP:chris.col...@tagmclarenaudio.com]
Sent:   02 March 2000 09:40
To: emc-p...@ieee.org
Subject:RE: Surge Testing per EN 55024/EN61000-4-5


Let's say I'm testing a Class II double insulated CD player - no reference
to earth.  If the product were stand alone, line to earth testing would be
pointless, at least as I see it.

It is conceivable that the CD player could be connected to a Class I,
earthed amplifier.  Through the interconnects, the chassis of the CD player
could become grounded (there would probably horrendous hum problems but
that's another story).

Line to earth tests are now valid but how would I set this up in the lab? 
 A
lead from the CD player chassis to the nearest socket outlet earth?  A lead
to the chassis of my Keytek surge tester?  A thin lead, a thick lead?  I
guess the test should be representative of the real world and repeatable.

Any suggestions?

Regards

Chris Colgan
EMC  Safety
TAG McLaren Audio Ltd

mailto:chris.col...@tagmclarenaudio.com



 -Original Message-
 From: Mike  Hopkins [SMTP:mhopk...@keytek.com]
 Sent: 01 March 2000 18:32
 To:   'Jim Hulbert'; emc-p...@ieee.org
 Subject:  RE: Surge Testing per EN 55024/EN61000-4-5


 As long as there is no other path to ground, a line to line test would be
 all thats required, but keep in mind, if you have other I/O, telecom,
 control lines, or anything else coming out of that plastic box, you then
 have a potential path back to ground, and in fact, will likely have REAL
 ground connections. For example, many television sets have two wire power
 plugs, are in plastic cases, but if you have cable tv, the odds are that
 coax cable is grounded.  Same thing applies if there is a telecom line
 involved -- very likely one of the telecom lines is ground. ..

  Mike Hopkins
 mhopk...@keytek.com

  -Original Message-
  From:   Jim Hulbert [SMTP:hulbe...@pb.com]
  Sent:   Wednesday, March 01, 2000 10:32 AM
  To: emc-p...@ieee.org
  Subject:Surge Testing per EN 55024/EN61000-4-5
 
 
 
 
  Colleagues,
 
  EN 55024 calls for surge pulses to be applied line-to-line and
  line-to-earth on
  the AC mains port and line-to-ground on signal and telecommunications
  ports that
  connect directly to outdoor cables.   However, if my EUT is encased in
  plastic
  covers and has no direct earth ground connection (class 2 power 
supply),
  is the
  line-to-line test on the AC mains the only surge test that I need to
  apply?   It
  seems to me that performing a line-to-earth test on either the AC mains
  port or
  on signal/telecommunications ports is not warranted since the basic
  standard EN
  61000-4-5 does not specify placing the EUT over a reference ground
 plane.
  With
  no reference ground plane and no direct ground connection how can a 
test
  be
  applied with respect to ground?
 
  Jim Hulbert
  Pitney Bowes
 
 
 
  -
  This message is from the IEEE EMC Society Product Safety
  Technical Committee emc-pstc discussion list.
 
  To cancel your subscription, send mail to:
   majord...@ieee.org

RE: Surge Testing per EN 55024/EN61000-4-5

2000-03-01 Thread UMBDENSTOCK

Jim,

Does your product connect to any auxiliary equipment that has an earth
connection, whether directly or indirectly?

Don Umbdenstock
Sensormatic

 --
 From: Jim Hulbert[SMTP:hulbe...@pb.com]
 Reply To: Jim Hulbert
 Sent: Wednesday, March 01, 2000 10:32 AM
 To:   emc-p...@ieee.org
 Subject:  Surge Testing per EN 55024/EN61000-4-5
 
 
 
 
 Colleagues,
 
 EN 55024 calls for surge pulses to be applied line-to-line and
 line-to-earth on
 the AC mains port and line-to-ground on signal and telecommunications
 ports that
 connect directly to outdoor cables.   However, if my EUT is encased in
 plastic
 covers and has no direct earth ground connection (class 2 power supply),
 is the
 line-to-line test on the AC mains the only surge test that I need to
 apply?   It
 seems to me that performing a line-to-earth test on either the AC mains
 port or
 on signal/telecommunications ports is not warranted since the basic
 standard EN
 61000-4-5 does not specify placing the EUT over a reference ground plane.
 With
 no reference ground plane and no direct ground connection how can a test
 be
 applied with respect to ground?
 
 Jim Hulbert
 Pitney Bowes
 
 
 
 -
 This message is from the IEEE EMC Society Product Safety
 Technical Committee emc-pstc discussion list.
 
 To cancel your subscription, send mail to:
  majord...@ieee.org
 with the single line:
  unsubscribe emc-pstc
 
 For help, send mail to the list adminstrators:
  Jim Bacher:  jim_bac...@mail.monarch.com, or
  Michael Garretson:pstc_ad...@garretson.org
 For policy questions, send mail to:
  Richard Nute:   ri...@ieee.org
 
 

---
This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

To cancel your subscription, send mail to:
 majord...@ieee.org
with the single line:
 unsubscribe emc-pstc

For help, send mail to the list administrators:
 Jim Bacher:  jim_bac...@mail.monarch.com
 Michael Garretson:pstc_ad...@garretson.org

For policy questions, send mail to:
 Richard Nute:   ri...@ieee.org



RE: Surge Testing per EN 55024/EN61000-4-5

2000-03-01 Thread Lfresearch

Mike,

can't agree with you on this one. See Scotts comments in his e-mail. You test 
to prove things are as you think they are... Otherwise why test at all?

Derek Walton
Invensys

---
This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

To cancel your subscription, send mail to:
 majord...@ieee.org
with the single line:
 unsubscribe emc-pstc

For help, send mail to the list administrators:
 Jim Bacher:  jim_bac...@mail.monarch.com
 Michael Garretson:pstc_ad...@garretson.org

For policy questions, send mail to:
 Richard Nute:   ri...@ieee.org



RE: Surge Testing per EN 55024/EN61000-4-5

2000-03-01 Thread Mike Hopkins

As long as there is no other path to ground, a line to line test would be
all thats required, but keep in mind, if you have other I/O, telecom,
control lines, or anything else coming out of that plastic box, you then
have a potential path back to ground, and in fact, will likely have REAL
ground connections. For example, many television sets have two wire power
plugs, are in plastic cases, but if you have cable tv, the odds are that
coax cable is grounded.  Same thing applies if there is a telecom line
involved -- very likely one of the telecom lines is ground. ..   

 Mike Hopkins
mhopk...@keytek.com

 -Original Message-
 From: Jim Hulbert [SMTP:hulbe...@pb.com]
 Sent: Wednesday, March 01, 2000 10:32 AM
 To:   emc-p...@ieee.org
 Subject:  Surge Testing per EN 55024/EN61000-4-5
 
 
 
 
 Colleagues,
 
 EN 55024 calls for surge pulses to be applied line-to-line and
 line-to-earth on
 the AC mains port and line-to-ground on signal and telecommunications
 ports that
 connect directly to outdoor cables.   However, if my EUT is encased in
 plastic
 covers and has no direct earth ground connection (class 2 power supply),
 is the
 line-to-line test on the AC mains the only surge test that I need to
 apply?   It
 seems to me that performing a line-to-earth test on either the AC mains
 port or
 on signal/telecommunications ports is not warranted since the basic
 standard EN
 61000-4-5 does not specify placing the EUT over a reference ground plane.
 With
 no reference ground plane and no direct ground connection how can a test
 be
 applied with respect to ground?
 
 Jim Hulbert
 Pitney Bowes
 
 
 
 -
 This message is from the IEEE EMC Society Product Safety
 Technical Committee emc-pstc discussion list.
 
 To cancel your subscription, send mail to:
  majord...@ieee.org
 with the single line:
  unsubscribe emc-pstc
 
 For help, send mail to the list adminstrators:
  Jim Bacher:  jim_bac...@mail.monarch.com, or
  Michael Garretson:pstc_ad...@garretson.org
 For policy questions, send mail to:
  Richard Nute:   ri...@ieee.org
 

---
This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

To cancel your subscription, send mail to:
 majord...@ieee.org
with the single line:
 unsubscribe emc-pstc

For help, send mail to the list administrators:
 Jim Bacher:  jim_bac...@mail.monarch.com
 Michael Garretson:pstc_ad...@garretson.org

For policy questions, send mail to:
 Richard Nute:   ri...@ieee.org