RE: isolation of battery (72V max) input

1998-10-23 Thread Peter Merguerian
Dear Edward and Moshe,

The EN60950 standard allows you various options for compliance 
with insulation between the max 72 Vdc source of supply 
(considered a hazardous secondary circuit) and SELV. 

One way to comply is reinfoced insulation as Edward has stated. 
But based on the many products which we have tested in our labs, 
we find that this providing reinforced insulation is not a practical 
solution for most clients. In many cases, our clients do not have 
insulation at all. In this case, the standard allows you to 
interconnect hazardous secondary circuits and SELV if abnormals 
are done (shorting or opening of components or circuits) to 
detrmine that the SELV limits are not exceeded.

Remember that for some countries (Australia and Germany), CO's 
recognize the max 72 Vdc supply as a TNV-2 circuit. As such for 
these countries where the CO supply voltage can reach up to 72 
Vdc, you may wish to comply with the TNV-2 to SELV limits 
specified in my previous e-mail. For most other countries, the CO 
supply voltage is earthed SELV and does not exceed 60 Vdc. For 
these countries you may wish to comply with the SELV to SELV 
or operational insulation requirements.

Regards, 





Date sent:  Thu, 22 Oct 1998 14:47:40 -0400
From:   Edward Eszlari e_eszl...@compuserve.com
Subject:RE: isolation of battery (72V max) input
To: INTERNET:mvald...@netvision.net.il 
mvald...@netvision.net.il,
t...@world.std.com, emc-p...@ieee.org
Send reply to:  Edward Eszlari e_eszl...@compuserve.com

 Moshe, 
 
 The answer to your question is Reinforced insulation for the working
 voltage measured in that location.
 
 The 72V supply is considered hazardous voltage and if an SELV circuit is
 present on conductors nearby, this is the type of insulation system that is
 required. If this CO like enviroment can be considered a Restricted
 Access Area per 2.1.4.2 (EN60950), or Service Access Area per 2.1.4.1,
 lesser requirements may apply. Also consider if this SELV circuit does
 not need to be classified as SELV (no operator access), you may be able to
 get away with no insulation, but other requirements may apply depending on
 how this system is set-up.
 
 Regards,
 
 
 Edward Eszlari
 TUV Rheinland of N.A., Inc.
 Marlborough, MA
 508-460-0792 
 

 
 -
 This message is coming from the emc-pstc discussion list.
 To cancel your subscription, send mail to majord...@ieee.org
 with the single line: unsubscribe emc-pstc (without the
 quotes).  For help, send mail to ed.pr...@cubic.com,
 j...@gwmail.monarch.com, ri...@sdd.hp.com, or
 roger.volgst...@compaq.com (the list administrators).
 



-
This message is coming from the emc-pstc discussion list.
To cancel your subscription, send mail to majord...@ieee.org
with the single line: unsubscribe emc-pstc (without the
quotes).  For help, send mail to ed.pr...@cubic.com,
j...@gwmail.monarch.com, ri...@sdd.hp.com, or
roger.volgst...@compaq.com (the list administrators).


RE: isolation of battery (72V max) input

1998-10-22 Thread Edward Eszlari
Moshe, 

The answer to your question is Reinforced insulation for the working
voltage measured in that location.

The 72V supply is considered hazardous voltage and if an SELV circuit is
present on conductors nearby, this is the type of insulation system that is
required. If this CO like enviroment can be considered a Restricted
Access Area per 2.1.4.2 (EN60950), or Service Access Area per 2.1.4.1,
lesser requirements may apply. Also consider if this SELV circuit does
not need to be classified as SELV (no operator access), you may be able to
get away with no insulation, but other requirements may apply depending on
how this system is set-up.

Regards,


Edward Eszlari
TUV Rheinland of N.A., Inc.
Marlborough, MA
508-460-0792 

   

RE: isolation of battery (72V max) input

1998-10-21 Thread Kretsch, John
Moshe:
We treat the 48V input as a secondary voltage with primary voltage
rules.  Therefore, you will have to hold to the _reinforced_ distances
for creepage and clearance.

Regards,

John R. Kretsch, P.E.
Compliance Engineering Supervisor
ADC Broadband Communications
john_kret...@adc.com 


-Original Message-
From: mvald...@netvision.net.il [mailto:mvald...@netvision.net.il]
Sent: Wednesday, October 21, 1998 03:44
To: emc-p...@ieee.org; t...@world.std.com
Subject: isolation of battery (72V max) input


Hello everyone,

What are creepage/clearance requirements between battery (60V nominal
which could go to 72V) 
conductors and SELV conductors? The equipment resides in CO like
environment.

thanks in advance,
Moshe

Name: moshe valdman
E-mail: mvald...@netvision.net.il
Phone: 972-52-941200
Telefax: 972-3-5496369
List-Post: emc-pstc@listserv.ieee.org
Date: 21/10/98
Time: 0:44:10
You are most welcome to visit my homepage at:

http://www.geocities.com/CapeCanaveral/5233/



-
This message is coming from the emc-pstc discussion list.
To cancel your subscription, send mail to majord...@ieee.org
with the single line: unsubscribe emc-pstc (without the
quotes).  For help, send mail to ed.pr...@cubic.com,
j...@gwmail.monarch.com, ri...@sdd.hp.com, or
roger.volgst...@compaq.com (the list administrators).

-
This message is coming from the emc-pstc discussion list.
To cancel your subscription, send mail to majord...@ieee.org
with the single line: unsubscribe emc-pstc (without the
quotes).  For help, send mail to ed.pr...@cubic.com,
j...@gwmail.monarch.com, ri...@sdd.hp.com, or
roger.volgst...@compaq.com (the list administrators).


Re: isolation of battery (72V max) input from SELV Circuits

1998-10-21 Thread Peter Merguerian
Dear Moshe,

I assume you mean creepages and clearances between input 
circuits and SELV circuits (and not conductors). I am also 
assuming  you are familiar with the clearance and creepage Tables 
in UL1950 and/or EN 60950 which depends on the Installation 
Category and Pollution Degree.

In regards to insulation for North America, because of limitations on 
TNV circuits, a max 72 Vdc supply is considered a secondary 
hazardous circuit. If you do not have the required insulation 
between these circuits (basic or reinforced insulation depending on 
whether circuits are reliably earthed or not), the standard allows 
you to interconnect the two circuits if abnormals are done between 
components in the two circuits and you still maintain the criteria for 
SELV voltage limits. Regret I cannot reference the claues at this 
time since I am at home and not in our laboratories. 

For Europe, the max 72 Vdc supply circuit can be considered a 
TNV-2 circuit if not subject to overvoltages. In this case, between a 
TNV-2 circuit and SELV, you need to comply with the basic 
insulation requirements and also the Dielectric Sterngth or Impulse 
Test requirements (again I do not have the standard to give you 
details).

I suggest for worldwide Approvals, you consider the strictest of  the 
above specified requirements. 

Although you have not asked, do not forget that in the US, a 
means for connection to the supply is needed in accordance to the 
NEC, such as a field wiring compartment with terminal blocks or 
min 6 inch pigtail leads. A compartment (with knockouts or holes 
for field wiring) is not needed for equipment to be Recognized or 
which is intended for Restricted Access Locations (RAL). In the 
latter case, instructions are needed for routing of the field wiring so 
that they are not damaged during installation and normal use of 
your equipment.

Hope this helps.


Best Regards, 


From:   mvald...@netvision.net.il
Date sent:  Wed, 21 Oct 98 00:44:09 PDT
Subject:isolation of battery (72V max) input
To: emc-p...@ieee.org, t...@world.std.com
Send reply to:  mvald...@netvision.net.il

 Hello everyone,
 
 What are creepage/clearance requirements between battery (60V nominal which 
 could go to 72V) 
 conductors and SELV conductors? The equipment resides in CO like 
 environment.
 
 thanks in advance,
 Moshe
 
 Name: moshe valdman
 E-mail: mvald...@netvision.net.il
 Phone: 972-52-941200
 Telefax: 972-3-5496369
 Date: 21/10/98
 Time: 0:44:10
 You are most welcome to visit my homepage at:
 
 http://www.geocities.com/CapeCanaveral/5233/
 
 
 
 -
 This message is coming from the emc-pstc discussion list.
 To cancel your subscription, send mail to majord...@ieee.org
 with the single line: unsubscribe emc-pstc (without the
 quotes).  For help, send mail to ed.pr...@cubic.com,
 j...@gwmail.monarch.com, ri...@sdd.hp.com, or
 roger.volgst...@compaq.com (the list administrators).
 



-
This message is coming from the emc-pstc discussion list.
To cancel your subscription, send mail to majord...@ieee.org
with the single line: unsubscribe emc-pstc (without the
quotes).  For help, send mail to ed.pr...@cubic.com,
j...@gwmail.monarch.com, ri...@sdd.hp.com, or
roger.volgst...@compaq.com (the list administrators).


(Fwd) Re: isolation of battery (72V max) input from SELV Circu

1998-10-21 Thread Peter Merguerian

--- Forwarded Message Follows ---
From:   Self Single-user mode
To: emc-p...@ieee.org, t...@world.std.com, 
mvald...@netvision.net.il
Subject:Re: isolation of battery (72V max) input from SELV 
Circuits
Date sent:  Wed, 21 Oct 1998 23:11:48 +0200

Dear Moshe,

I assume you mean creepages and clearances between input 
circuits and SELV circuits (and not conductors). I am also 
assuming  you are familiar with the clearance and creepage Tables 
in UL1950 and/or EN 60950 which depends on the Installation 
Category and Pollution Degree.

In regards to insulation for North America, because of limitations on 
TNV circuits, a max 72 Vdc supply is considered a secondary 
hazardous circuit. If you do not have the required insulation 
between these circuits (basic or reinforced insulation depending on 
whether circuits are reliably earthed or not), the standard allows 
you to interconnect the two circuits if abnormals are done between 
components in the two circuits and you still maintain the criteria for 
SELV voltage limits. Regret I cannot reference the claues at this 
time since I am at home and not in our laboratories. 

For Europe, the max 72 Vdc supply circuit can be considered a 
TNV-2 circuit if not subject to overvoltages. In this case, between a 
TNV-2 circuit and SELV, you need to comply with the basic 
insulation requirements and also the Dielectric Sterngth or Impulse 
Test requirements (again I do not have the standard to give you 
details).

I suggest for worldwide Approvals, you consider the strictest of  the 
above specified requirements. 

Although you have not asked, do not forget that in the US, a 
means for connection to the supply is needed in accordance to the 
NEC, such as a field wiring compartment with terminal blocks or 
min 6 inch pigtail leads. A compartment (with knockouts or holes 
for field wiring) is not needed for equipment to be Recognized or 
which is intended for Restricted Access Locations (RAL). In the 
latter case, instructions are needed for routing of the field wiring so 
that they are not damaged during installation and normal use of 
your equipment.

Hope this helps.


Best Regards, 


From:   mvald...@netvision.net.il
Date sent:  Wed, 21 Oct 98 00:44:09 PDT
Subject:isolation of battery (72V max) input
To: emc-p...@ieee.org, t...@world.std.com
Send reply to:  mvald...@netvision.net.il

 Hello everyone,
 
 What are creepage/clearance requirements between battery (60V nominal which 
 could go to 72V) 
 conductors and SELV conductors? The equipment resides in CO like 
 environment.
 
 thanks in advance,
 Moshe
 
 Name: moshe valdman
 E-mail: mvald...@netvision.net.il
 Phone: 972-52-941200
 Telefax: 972-3-5496369
 Date: 21/10/98
 Time: 0:44:10
 You are most welcome to visit my homepage at:
 
 http://www.geocities.com/CapeCanaveral/5233/
 
 
 
 -
 This message is coming from the emc-pstc discussion list.
 To cancel your subscription, send mail to majord...@ieee.org
 with the single line: unsubscribe emc-pstc (without the
 quotes).  For help, send mail to ed.pr...@cubic.com,
 j...@gwmail.monarch.com, ri...@sdd.hp.com, or
 roger.volgst...@compaq.com (the list administrators).
 



-
This message is coming from the emc-pstc discussion list.
To cancel your subscription, send mail to majord...@ieee.org
with the single line: unsubscribe emc-pstc (without the
quotes).  For help, send mail to ed.pr...@cubic.com,
j...@gwmail.monarch.com, ri...@sdd.hp.com, or
roger.volgst...@compaq.com (the list administrators).