Re: Earth Potential Equalizing

1999-11-23 Thread Frank West

Good Morning Janne!

It has been my experience that units seperate from the
control cabinet that supplies power to them are
grounded to the same ground potential as the the
cabinet, assuming you are not using an IT type power
system (which is what is used in the Nordic countries
for example) where the PE is seperated from true
ground by protective impedances.  

IEC 60204-1 indicates that all parts of equipment
should have earth continuity back to the primary earth
stud/connection.  In fact, section 19 gives testing
requirements for this to be 0.1 ohms or less.

I hope this helps.  Please email me if you need
specific data.

Regards, 

Frank West
Sr. Engineer
TUV Rheinland NA

--- Janne_Engström janne.engst...@ivtg.se wrote:
 
 Hi all,
 
 We are manufacturing heating equipment for
 industrial use.
 Our equipment is one part in an in line setup of
 machines.
  We are required, by one company we deliver to, to
 provide a wire
 for equalizing the earth potential between our
 control cabinet and 
 the frame of the main machine.
 
 The heater is about 50kW at 400V. 
 
 The required wire is 35 square millimeters copper
 wire.
 
 The equiment in this case is for the European
 market.
 
 I think what they are afraid of is that current will
 flow in the shields in
 the control cables between the different parts of
 the setup, creating problems.
 
 Are there any standards that require this? Is this
 standard procedure?
 
 Best regards
 
 Janne Engstrom
 
  
 
 
 -
 This message is coming from the emc-pstc discussion
 list.
 To cancel your subscription, send mail to
 majord...@ieee.org
 with the single line: unsubscribe emc-pstc
 (without the
 quotes).  For help, send mail to ed.pr...@cubic.com,
 jim_bac...@monarch.com, ri...@sdd.hp.com, or
 roger.volgst...@compaq.com (the list
 administrators).
 
 
 

__
Do You Yahoo!?
Bid and sell for free at http://auctions.yahoo.com

-
This message is coming from the emc-pstc discussion list.
To cancel your subscription, send mail to majord...@ieee.org
with the single line: unsubscribe emc-pstc (without the
quotes).  For help, send mail to ed.pr...@cubic.com,
jim_bac...@monarch.com, ri...@sdd.hp.com, or
roger.volgst...@compaq.com (the list administrators).



Re: Earth Potential Equalizing

1999-11-22 Thread Csgilks

In the industrial equipment world, covered by standards such as UL508 and UL347,
as well as IEC 60204, it is standard practice to provide a ground conductor
that is of sufficient size that the potential of the equipment ground bus, under
foreseeable ground fault conditions, does not rise to a hazardous decisive
voltage.  In practice, this means ensuring that the resistance of the ground
path is low enough to ensure that the rise in potential is less than, say, 50
volts (although we use a figure of 24 volts for safety) before either the
upstream protection operates, or after the current level reaches short-circuit
fault levels (which is the safer course, but may not be practical in all cases
when dealing with heavy equipment).  The 35 sq.mm ground wire size that you
specify is probably not an unreasonable requirment at 500kW, but it depends on
the ground loop resistance at the lengths that you are using.
Chris Gilks

-Original Message-
From: Janne Engström janne.engst...@ivtg.se
To: emc-p...@majordomo.ieee.org emc-p...@majordomo.ieee.org
List-Post: emc-pstc@listserv.ieee.org
Date: Sunday, November 21, 1999 1:26 PM
Subject: Earth Potential Equalizing



Hi all,

We are manufacturing heating equipment for industrial use.
Our equipment is one part in an in line setup of machines.
 We are required, by one company we deliver to, to provide a wire
for equalizing the earth potential between our control cabinet and
the frame of the main machine.

The heater is about 50kW at 400V.

The required wire is 35 square millimeters copper wire.

The equiment in this case is for the European market.

I think what they are afraid of is that current will flow in the shields in
the control cables between the different parts of the setup, creating
problems.

Are there any standards that require this? Is this standard procedure?

Best regards

Janne Engstrom




-
This message is coming from the emc-pstc discussion list.
To cancel your subscription, send mail to majord...@ieee.org
with the single line: unsubscribe emc-pstc (without the
quotes).  For help, send mail to ed.pr...@cubic.com,
jim_bac...@monarch.com, ri...@sdd.hp.com, or
roger.volgst...@compaq.com (the list administrators).



Re: Earth Potential Equalizing

1999-11-22 Thread PRYOR MCGINNIS

EN 60204-1 Clause 8 covers Equipotential bonding.

-Original Message-
From: Janne Engström janne.engst...@ivtg.se
To: emc-p...@majordomo.ieee.org emc-p...@majordomo.ieee.org
List-Post: emc-pstc@listserv.ieee.org
Date: Sunday, November 21, 1999 1:26 PM
Subject: Earth Potential Equalizing



Hi all,

We are manufacturing heating equipment for industrial use.
Our equipment is one part in an in line setup of machines.
 We are required, by one company we deliver to, to provide a wire
for equalizing the earth potential between our control cabinet and
the frame of the main machine.

The heater is about 50kW at 400V.

The required wire is 35 square millimeters copper wire.

The equiment in this case is for the European market.

I think what they are afraid of is that current will flow in the shields in
the control cables between the different parts of the setup, creating
problems.

Are there any standards that require this? Is this standard procedure?

Best regards

Janne Engstrom




-
This message is coming from the emc-pstc discussion list.
To cancel your subscription, send mail to majord...@ieee.org
with the single line: unsubscribe emc-pstc (without the
quotes).  For help, send mail to ed.pr...@cubic.com,
jim_bac...@monarch.com, ri...@sdd.hp.com, or
roger.volgst...@compaq.com (the list administrators).




-
This message is coming from the emc-pstc discussion list.
To cancel your subscription, send mail to majord...@ieee.org
with the single line: unsubscribe emc-pstc (without the
quotes).  For help, send mail to ed.pr...@cubic.com,
jim_bac...@monarch.com, ri...@sdd.hp.com, or
roger.volgst...@compaq.com (the list administrators).