Re: Room grounding

1998-10-13 Thread Tim Haynes G-Net 701 3239 / 3455
Hmmm, forgive me if I am wrong but I wonder if the following will
help?
unknown wrote..
#Chaps,
#
#The grounding of a shield room has always been a tricky subject. In the
US we
#have the NEC code that basically want's everything connected, which
#contradicts some EMC requirements. The Shield room hence needs some
tricks:
Same here in the UK with IEE regs.
#
#1) One of the functions of the outer skin is to terminate impinging
fields.
#Current is generated on the shield surface that will flow across joints
and
#seams ( and hence leak into the chamber ) unless it's routed
somewhere
#Earth.
However, if the seams are good, then there will be no leaks. Of course
if you earth the screened room, then some RF will flow across a joint to
get to the earthing point but a _good_ Faraday cage does not need to be
earthed in order to provide screening.

#
#2) While buildings usually have a good earth, they typically have a
noisy
#earth. The last thing we need is building noise on our room, so an
earth
#dedicated to the chamber is provided.
To provide electrical safety, the screened room must be connected to the
_earth_ or _ground_ of the electrical supply. This is particularly
important when the room is supplied with a filtered single phase supply
via filters with high leakage current. (The filter on live and neutral
will bring the screened room to half line potential without the earth!)
Of course, any RF _noise_ from the building or environment will get into
the room via any penetration - so make sure the seams are tight and that
you do not take an earth bolt _through_ the screened room wall. If the
room is good, there will be no leakage of the external environment to
the inside.

#
#3) To stop building noise from using the shield room earth, all
metallic
#connections are cut, and plastic used instead. This is where the NEC
folks can
#get upset. Their concern is that the two grounds could lift with
respect to
#each other I've never seen that happen, and I've gone looking for
it. So
#that I can sleep at night, I ensure that an operator can't touch metal
#referenced to the different grounds at any one time.
Hmmm... possibly, but is depends on what the _metallic connection_ was
providing.
If the connection is just a fortuitous connection - or a room support,
then it should be made of insulating material.
If you need a, say, water or compressed air supply in the screened room,
then there are two ways of bringing it in. First (and my preference) is
to BOND the pipe to the outside of the screened room. I mean weld,
braise, solder or clamp (in that order) around 360 deg. of the periphery
and then do the same on the inside! Second is to use a section of
plastic pipe through the room wall. However - since the plastic does not
stop RF and there is a hole, the room will leak RF at this point. The
degree of leakage will depend on the size of hole, the thickness of the
metal wall(s) and the frequency.

I NEVER have different grounds in the area. I have the electrical ground
(earth) ONLY. This is connected to the outside of the room at the point
where the filters are mounted. I pick up the ground (earth) again on the
inside. This point inside and outside the room is often called the
common reference point (C.R.P.).

#
#4) Power supplied to the room has to be directly connected. To stop
building
#noise from entering the room through this wiring, the noise is removed
to the
#case of a filter. I've located my filters very close to the room single
point
#room earth connection, so the noise can get there easily without
crossing one
#of my room seams or joints.
If the filters are not connected directly to the room, then the _clean_
wires will need to be protected from the environment by screening or in
conduit.
Don't forget, that many filters have a high leakage current and so
should be fed directly from the main supply to the building or floor -
that is - don't supply sockets off the same feed. The other supplies for
the lab outside the screened room _must_ be on the same phase as a room
supplied with a single phase supply..

#
#5) Any equipment I use with the room is referenced to the room ground.
Power
#for this equipment is filtered at the same point the room power is.
Most
#instrumentation used in EMC is quiet so they don't supply much
noise.
It is not a good idea to use the _clean_ room supply to power external
equipment, 1/ because the external equipment can generate noise on the
_clean_ supply line and 2/ the equipment can act as an antenna - feeding
the external environment onto the power lines.
At DC / 50 / 60Hz the arrangement I have given will provide a common
ground. If however, the room filters have very high leakage or the room
supply is very long, then you might need to provide an isolation
transformer and bring the protective earth from the room C.R.P.
#
#I don't believe there is guess work involved with room grounding. The
above is
#based on conversations with many room installers. I suggest that if you

Re: Shield Room Grounding

1998-10-12 Thread ed . price
Bob:

Barry is trying to say that a dummy power load is only resistive at the power 
frequency, and may not truly represent the EUT at all of the other frequencies 
within the test range. He's right. 

Bob suggests a powerline filter be added to my El Cheapo lightbulb load bank to 
more closely approximate an EUT. He's right, too. My bank of lightbulbs is 
versatile, but it IS spread out over a few square feet. There are stray lead 
inductances and capacitances, and the lamp filaments are also inductors. At a 
low frequency starting point of 10KHz (or 30Hz for me), this is negligible. But 
yes, as we go up to 10MHz or 30MHz, these undefined and uncontrolled variables 
will start causing some weird effects.

A better load bank could be constructed of non-inductive bulk silicon carbide 
resistors, but these are expensive ($150 each) and not as versatile. (OTOH, I 
have NEVER had one burn out during a test!)

Practically, I assume that the load is mostly resistive, having had the 
experience of using ordinary light bulbs on the end of a coax cable for loading 
amateur transmitters in the HF and VHF regions. Lamp filaments do a good job of 
converting RF to heat and light, so I trust that they retain a considerable 
resistive component of the impedance at any of these frequencies!

But, I don't think we need to know what the impedance curve of my loadbank is, 
because there is no standard to compare it against.

What we are groping toward here is that there seems to be a need to define a 
standard dummy power load. This load would have an impedance similar to the 
typical EUT. Placing this dummy load into the test setup would then allow test 
conductors to verify the quality of the supplied power and the sensitivity of 
the measurement equipment.

So, if there is a need to have a defined dummy load impedance, then we'll have 
to start with a survey of typical EUT's to find the value and variation of the 
impedance. Maybe we'll need several categories of dummy loads (appliance, 
computer, entertainment)?

But, as far as I'm concerned, I still have a few cases of light bulbs to use up 
first!  ;-)

Ed



  From: Robert Macy m...@california.com
  Subject: Re: Shield Room Grounding
  Date: Fri, 9 Oct 1998 16:27:11 -0700 (PDT) 
  To: b...@namg.us.anritsu.com, Bailin Ma@unspecified-domain
  Cc: emc-p...@ieee.org


 
 Lightbulbs make great AC loads, but use a line filter in series with them
 and you'll probably duplicate most EUT's since they'll be using filters.
 
   - Robert -
 
 
 On Fri, 9 Oct 1998 b...@namg.us.anritsu.com wrote:
 
  Hi Ed,
  
  I appreciate your kindness to share your experience with us about 
  constructing equivalent load: I constructed a load bank consisting of 16 
  surface mount light bulb sockets, all wired in parallel. I just screw in an 
  array of 25/60/75/100 Watt rated lamps until I get the necessary current. 
  Sure, there's some unknown slight lead inductance and capacitance. But all 
  I want to do is draw a few amps DC
  
  I have two questions: (1)What is the impedance of your bulb array at 30 
  MHz?   i.e.,  Zb=? @30 MHz.  (2)What is the impedance of EUT at 30 MHz?
  i.e.,  Ze=? @30 MHz

(DETAILS SNIPPED)
 
  Suggestion: We might need to check the equivalence of Zb and Ze @30 MHz by 
  using an Impedance Analyzer, e. g., HP4191A(?).
  
  
  Thank you.
  Please correct me.
  Best Regards,
  Barry Ma
 

--
Ed Price
ed.pr...@cubic.com
Electromagnetic Compatibility Lab
Cubic Defense Systems
San Diego, CA.  USA
619-505-2780
List-Post: emc-pstc@listserv.ieee.org
Date: 10/12/1998
Time: 10:47:22
--



-
This message is coming from the emc-pstc discussion list.
To cancel your subscription, send mail to majord...@ieee.org
with the single line: unsubscribe emc-pstc (without the
quotes).  For help, send mail to ed.pr...@cubic.com,
j...@gwmail.monarch.com, ri...@sdd.hp.com, or
roger.volgst...@compaq.com (the list administrators).


Re: Shield Room Grounding

1998-10-09 Thread ed . price



  From: Scott Roleson sc...@hpsdde.sdd.hp.com
  Subject: Re: Shield Room Grounding
  Date: Thu, 8 Oct 1998 14:17:56 -0700 
  To: emc-p...@ieee.org
  Cc: sc...@hpsdde.sdd.hp.com


 
 Barry Ma forwarded to me a message from Peter Hays that said:
  
  Can someone tell me what is the best method to find out and ensure 
  that a screen room is adequately grounded?

(SNIP)
 
 There is some debate on this single-point ground approach.  I know
 some people who think it doesn't matter, so long as the room doesn't
 have any gaps so that ALL potentially interfering currents stay on 
 the outside surface of the room.  This may be true, but in practice
 it's not always possible to have a room without any holes or gaps.
 
   -- Scott Roleson
 

Scott:

Grounding for safety is a must, since a shielded enclosure will almost always 
have a set of low-pass powerline filters which bring the 60Hz power into the 
equipment within the room. These filters usually have a few large (15uF or so) 
capacitors from line to filter case to bypass RF currents. Since the capacitors 
also have a modest Xc at 60 Hz, there will also be a 60 Hz current component to 
the filter case. If the room isn't grounded, a hazardous voltage potential can 
exist on the room wall. A person standing on the concrete floor of the parent 
structure can get a very serious shock just by reaching out to open the door 
handle or to connect a coax cable to a port. So, for almost every situation, we 
have to ground the room to protect the people around it.

But grounding for RF shielding effectiveness isn't needed. A copper spherical 
Faraday cage floating in mid air (what a sight!) would make an fine RF shield. 
The shielding would be limited primarily by the gaps, intentional seams and 
accidental cracks and gaps. But... it's not very useful. Let's land that baby 
and now think of it as a shielded room.

To be of any use, this room has to be big, say 10 feet tall. And maybe 30 feet 
wide. Now, let's get very simplistic. To an RF wave, propagating along happily 
in air, your room looks like a little old antenna. I mean, it's conductive, and 
it has a height above ground. An effective height. Right, it looks like a 
stubby, broadband vertical monopole above a ground plane. And that RF wave 
gives that antenna a present; it induces some RF current into the conductive 
structure.

Now, that RF current would like to flow, along the outer surface of the 
conductor (skin depth effect), somewhere. By providing a single, well defined 
ground path, you prevent that current from flowing along paths which would 
create problems. What problems? Well, imagine the current flowing to ground 
through the outer jacket of a coax cable connected to a grounded spectrum 
analyzer. The noise currents would sum with the valid RF currents on the 
analyzer coax.

Now, with all that said, let me tell you a story. At both General Dynamics and 
Cubic in San Diego, I needed a large shielded room (for the EUT) and a smaller 
shielded room or antechamber (for the program support equipment. (Support 
equipment is notorious for being built just barely able to work, with a rat's 
nest construction and no thought to EMC.)

At GD, I had a solid, welded main room and a modular, 8' cube antechamber. At 
Cubic, I have a modular main room and a modular, screen antechamber. Both 
locations used the same technique to join the large and small rooms; a 
penetration port was located in each facing wall, and a steel tunnel was 
fabricated to bolt onto each room's penetration port bolt pattern. In effect, 
the shielded volume turned into a dumbbell shape, with the tunnel at the 
waist of the dumbbell. Then, a penetration port cover plate, equipped with 
multiple signal line filters, is bolted across the tunnel throat at one end. 
(This isolates the two test chambers from each other.)

Each shielded room has it's own set of powerline filters (400Hz three phase, 
60Hz three phase and two DC lines). The modular panel (on each room) that 
carries the filter sets has it's own ground well. The two powerline filter sets 
were over fifty feet apart in both examples.

I can't remember when anybody would have recommended a design like this. I know 
I wouldn't. But the GD example grew from merging existing facilities, and it 
worked. It worked good enough that we NEVER had a trace of any ambient signals 
in the many emission tests that were performed there over about 15 years (using 
Eaton receivers and HP spectrum analyzers, often with active antennas). It was 
good enough to do TEMPEST testing at the facility. It worked good enough that I 
decided to deliberately emulate the design here at Cubic. And it's working 
again, good enough that my fancy HP-8571A Receiver (a re-worked 8566B), even 
operating with external pre-amps in some bands, doesn't see any ambient 
distractions.

So what's the lesson in all of this? Well, I was scrupulous about seam quality 
and using very good powerline

RE: Room grounding

1998-10-09 Thread Robert F. Martin ITS/QS-Box
'Single point ground' in this situation is used for the same purpose 
as we would in electronics design. When using a shielded room for 
making low frequency measurements (particularly MIL-STD), multiple 
ground connections can make significant power frequency and harmonic 
noise. Generally this is not so much of a problem for commercial 
operations because emission measurements are not as restrictive 
(either in frequency or in limit). Because,as Jon says, the conduit, 
etc. is not always reliable (particularly at the higher frequencies 
which filters are designed to shunt) an effort is made to provide 
ground through an independent means. I have used enclosures where 
great care has been taken (multiple 12' ground rods in close 
proximity, with Cu Sulfate 'salting') to provide a very 'robust' 
ground. This is then connected to both the enclosure and the building 
ground.

In some cases, you have to convince the electrician and/or the 
inspector that your room provides at least as good a ground as the 
conduit in order to be able to take advantage of the isolation 
provided by the PVC. It goes against their grain to connect a metal 
box without using metal conduit.

Bob Martin
Sr. Technical Manager
Intertek Testing Services
(978)263-2662
fax(978)263-7086
r...@itsqs.com

The opinions expressed are my own and not necessarily those of my 
employer.


-Original Message-
From:   Jon D. Curtis [SMTP:j...@curtis-straus.com]
Sent:   Thursday, October 08, 1998 11:52 AM
To: lfresea...@aol.com
Cc: mhopk...@keytek.com; emc-p...@ieee.org
Subject:Re: Room grounding

As I understand it, Lingren connects the shielded rooms they build 
back to the
main building ground point by a separate ground wire.  The conduit is
disconnected by use of a plastic sleave.  I assume they do this 
because the AC
filters incorporated in the shielded room include LARGE capacitors to 
the
shielded room walls.  Effectively the leakage through these capacitors 
turns the
ENTIRE room surface into an AC electrode with respect to building 
ground.  This
leakage current is potentially leathal unless returned back to the 
source where
the neutrals of the building are tied to ground at the circuit panel.

Not grounding the room (if it incorporates standard room filters) 
should not be
considered acceptable.  If there is an regular outlet on an adjacent 
building
wall, then a lethal hazard will exist between a metal test instrument 
pluged into
that outlet and the room surface.  I would hazard a bet that most 
room
installations are not well enough controlled to insure that building 
ground and a
separate room ground are NEVER allowed to meet.  Consider that no 
sparks will fly
if it happens, but hearts may stop.  People automatically consider 
dead metal as
ground.

I would also caution against those in this thread who rely on conduit. 
 Conduit
breaks, is removed, etc.  For high leakage threats only a dedicated 
ground wire
of suitable gage to carry the total fault current of the supply should 
be
employed.

This is not about a single fault problem.  You have a hazardous 
condition with NO
fault because of filter leakage if you do not ground the room to the 
building
ground at the circuit panel.

Watch out for LISNs Also.  The design of all lisns incorporate LARGE 
capacitors
to ground for filtering.  Without a ground connection on the LISN 
case, high
leakage threats exist.  Most use LISNs bonded to the ground plane 
which addresses
this threat as long as the ground plane is connected to the building 
ground.

The debate on reduction of noise and effects on EMC results should 
continue, BUT
personel safety comes FIRST and should not be compromised.

lfresea...@aol.com wrote:

 Mike,

 sorry you disagree.

 Inside the room, all equipment is referenced to the room itself, 
there is no
 new safety risk introduced by the room being grounded differently.

 Outside the room, again, all equipment is referenced tightly to the 
room, so
 the operator does not see any differential.

 Should lightning strike the building, then true, the building earth 
potential
 may lift, but the operator is protected because he is referenced to 
the room
 which will not move much because the energy has been dissipated by 
the
 building earthing system.

 I state again this is for performance reasons, and is accepted 
practice. In a
 true Faraday shielded room, earthing the room is not even 
neccessary. Mind
 you, since these don't exist off the shelf, I'll stick to grounding 
using my
 original guidlines. NEC inspectors, when the rationale is explained 
to them
 have little problem. However, I have come across situations were the 
two
 unique earths were tied by a very heavy inductor

 Best regards,

 Derek N. Walton

 -
 This message is coming from the emc-pstc discussion list.
 To cancel your subscription, send mail to majord...@ieee.org
 with the single line: unsubscribe emc-pstc (without the
 quotes).  For help, send mail to ed.pr

Re: Shield Room Grounding

1998-10-09 Thread bma
Hi Ed,

I appreciate your kindness to share your experience with us about 
constructing equivalent load: I constructed a load bank consisting of 16 
surface mount light bulb sockets, all wired in parallel. I just screw in an 
array of 25/60/75/100 Watt rated lamps until I get the necessary current. 
Sure, there's some unknown slight lead inductance and capacitance. But all 
I want to do is draw a few amps DC

I have two questions: (1)What is the impedance of your bulb array at 30 
MHz?   i.e.,  Zb=? @30 MHz.  (2)What is the impedance of EUT at 30 MHz?
i.e.,  Ze=? @30 MHz

If we are not sure Zb=Ze @30 MHz, I am afraid, it's hard to say the 
spectrum analyzer would receive the same RF emission at 30 MHz from noise 
sources other than EUT, although the bulb array draws the same current at 
60 Hz as EUT does.  In other words, Zb=Ze @60 Hz is one thing, and  Zb=Ze 
@30 MHz would be another.

Let's see an example, assuming
Ze=Re+jXe, where Xe=Omega*Le, and Omega=2*Pi*F.
Re=20 Ohm, Xe=0.1 Ohm @60 Hz,   Ze=20+j*0.1=20 Ohm
Be=20 Ohm, Xe=5 Ohm @30 MHz,Ze=j*5 Ohm

Conclusion: As far as the equivalent load is concerned, we can only pay 
attention to the equivalence of resistance part of Zb and Ze @60 Hz.  At 30 
MHz, however, we should pay more attention to the equivalence of reactance 
part of Ze and Zb instead.

Suggestion: We might need to check the equivalence of Zb and Ze @30 MHz by 
using an Impedance Analyzer, e. g., HP4191A(?).


Thank you.
Please correct me.
Best Regards,
Barry Ma



-
This message is coming from the emc-pstc discussion list.
To cancel your subscription, send mail to majord...@ieee.org
with the single line: unsubscribe emc-pstc (without the
quotes).  For help, send mail to ed.pr...@cubic.com,
j...@gwmail.monarch.com, ri...@sdd.hp.com, or
roger.volgst...@compaq.com (the list administrators).


RE: Shield Room Grounding

1998-10-09 Thread Kevin Harris
Hi Barry et al,

I'm I missing something here? Is this exercise worth the trouble? If one
doesn't have a clear margin to any commercial limit line with any kind
of resistive dummy load attached to your LISN shouldn't you examine the
your system setup? Accurate determination of your measurement system
noise floor with a known impedance through the frequency range is really
only of academic use in this case, isn't it? This should have no bearing
on pass/fail of an EUT as the measurement system noise floor and the
limit line should be well separated for conducted emissions in a
shielded room.


Regards,


Kevin Harris



 -Original Message-
 From: b...@namg.us.anritsu.com [SMTP:b...@namg.us.anritsu.com]
 Sent: Friday, October 09, 1998 1:33 PM
 To:   emc-p...@ieee.org
 Subject:  Re: Shield Room Grounding
 
 Hi Ed,
 
 I appreciate your kindness to share your experience with us about 
 constructing equivalent load: I constructed a load bank consisting of
 16 
 surface mount light bulb sockets, all wired in parallel. I just screw
 in an 
 array of 25/60/75/100 Watt rated lamps until I get the necessary
 current. 
 Sure, there's some unknown slight lead inductance and capacitance. But
 all 
 I want to do is draw a few amps DC
 
 I have two questions: (1)What is the impedance of your bulb array at
 30 
 MHz?   i.e.,  Zb=? @30 MHz.  (2)What is the impedance of EUT at 30
 MHz?
 i.e.,  Ze=? @30 MHz
 
 If we are not sure Zb=Ze @30 MHz, I am afraid, it's hard to say the 
 spectrum analyzer would receive the same RF emission at 30 MHz from
 noise 
 sources other than EUT, although the bulb array draws the same current
 at 
 60 Hz as EUT does.  In other words, Zb=Ze @60 Hz is one thing, and
 Zb=Ze 
 @30 MHz would be another.
 
 Let's see an example, assuming
   Ze=Re+jXe, where Xe=Omega*Le, and Omega=2*Pi*F.
   Re=20 Ohm, Xe=0.1 Ohm @60 Hz,   Ze=20+j*0.1=20 Ohm
   Be=20 Ohm, Xe=5 Ohm @30 MHz,Ze=j*5 Ohm
 
 Conclusion: As far as the equivalent load is concerned, we can only
 pay 
 attention to the equivalence of resistance part of Zb and Ze @60 Hz.
 At 30 
 MHz, however, we should pay more attention to the equivalence of
 reactance 
 part of Ze and Zb instead.
 
 Suggestion: We might need to check the equivalence of Zb and Ze @30
 MHz by 
 using an Impedance Analyzer, e. g., HP4191A(?).
 
 
 Thank you.
 Please correct me.
 Best Regards,
 Barry Ma
 
 

-
This message is coming from the emc-pstc discussion list.
To cancel your subscription, send mail to majord...@ieee.org
with the single line: unsubscribe emc-pstc (without the
quotes).  For help, send mail to ed.pr...@cubic.com,
j...@gwmail.monarch.com, ri...@sdd.hp.com, or
roger.volgst...@compaq.com (the list administrators).


RE: Room grounding

1998-10-07 Thread Mike Hopkins
I absolutely disagree about having a separate ground for the shielded room.
Any ac fault inside the room can potentially cause a personnel hazard, as
will any lightning strike to the vicinity. A separate ground for the
shielded room is acceptable ONLY if it is bonded to building ground. The
risk may be minimal, but why take any at all.

Mike Hopkins
mhopk...@keytek.com

 -Original Message-
 From: lfresea...@aol.com [SMTP:lfresea...@aol.com]
 Sent: Tuesday, October 06, 1998 3:36 PM
 To:   emc-p...@majordomo.ieee.org
 Subject:  Room grounding
 
 Chaps,
 
 The grounding of a shield room has always been a tricky subject. In the US
 we
 have the NEC code that basically want's everything connected, which
 contradicts some EMC requirements. The Shield room hence needs some
 tricks:
 
 1) One of the functions of the outer skin is to terminate impinging
 fields.
 Current is generated on the shield surface that will flow across joints
 and
 seams ( and hence leak into the chamber ) unless it's routed somewhere
 Earth.
 
 2) While buildings usually have a good earth, they typically have a noisy
 earth. The last thing we need is building noise on our room, so an earth
 dedicated to the chamber is provided.
 
 3) To stop building noise from using the shield room earth, all metallic
 connections are cut, and plastic used instead. This is where the NEC folks
 can
 get upset. Their concern is that the two grounds could lift with respect
 to
 each other I've never seen that happen, and I've gone looking for it.
 So
 that I can sleep at night, I ensure that an operator can't touch metal
 referenced to the different grounds at any one time.
 
 4) Power supplied to the room has to be directly connected. To stop
 building
 noise from entering the room through this wiring, the noise is removed to
 the
 case of a filter. I've located my filters very close to the room single
 point
 room earth connection, so the noise can get there easily without crossing
 one
 of my room seams or joints.
 
 5) Any equipment I use with the room is referenced to the room ground.
 Power
 for this equipment is filtered at the same point the room power is. Most
 instrumentation used in EMC is quiet so they don't supply much noise.
 
 I don't believe there is guess work involved with room grounding. The
 above is
 based on conversations with many room installers. I suggest that if you
 have
 specific questions, contact the folks that made yours.
 
 -
 This message is coming from the emc-pstc discussion list.
 To cancel your subscription, send mail to majord...@ieee.org
 with the single line: unsubscribe emc-pstc (without the
 quotes).  For help, send mail to ed.pr...@cubic.com,
 j...@gwmail.monarch.com, ri...@sdd.hp.com, or
 roger.volgst...@compaq.com (the list administrators).

-
This message is coming from the emc-pstc discussion list.
To cancel your subscription, send mail to majord...@ieee.org
with the single line: unsubscribe emc-pstc (without the
quotes).  For help, send mail to ed.pr...@cubic.com,
j...@gwmail.monarch.com, ri...@sdd.hp.com, or
roger.volgst...@compaq.com (the list administrators).


Re: Room grounding

1998-10-07 Thread Lfresearch
Mike,

sorry you disagree.

Inside the room, all equipment is referenced to the room itself, there is no
new safety risk introduced by the room being grounded differently.

Outside the room, again, all equipment is referenced tightly to the room, so
the operator does not see any differential.

Should lightning strike the building, then true, the building earth potential
may lift, but the operator is protected because he is referenced to the room
which will not move much because the energy has been dissipated by the
building earthing system.

I state again this is for performance reasons, and is accepted practice. In a
true Faraday shielded room, earthing the room is not even neccessary. Mind
you, since these don't exist off the shelf, I'll stick to grounding using my
original guidlines. NEC inspectors, when the rationale is explained to them
have little problem. However, I have come across situations were the two
unique earths were tied by a very heavy inductor

Best regards,

Derek N. Walton

-
This message is coming from the emc-pstc discussion list.
To cancel your subscription, send mail to majord...@ieee.org
with the single line: unsubscribe emc-pstc (without the
quotes).  For help, send mail to ed.pr...@cubic.com,
j...@gwmail.monarch.com, ri...@sdd.hp.com, or
roger.volgst...@compaq.com (the list administrators).


Room grounding

1998-10-06 Thread Lfresearch
Chaps,

The grounding of a shield room has always been a tricky subject. In the US we
have the NEC code that basically want's everything connected, which
contradicts some EMC requirements. The Shield room hence needs some tricks:

1) One of the functions of the outer skin is to terminate impinging fields.
Current is generated on the shield surface that will flow across joints and
seams ( and hence leak into the chamber ) unless it's routed somewhere
Earth.

2) While buildings usually have a good earth, they typically have a noisy
earth. The last thing we need is building noise on our room, so an earth
dedicated to the chamber is provided.

3) To stop building noise from using the shield room earth, all metallic
connections are cut, and plastic used instead. This is where the NEC folks can
get upset. Their concern is that the two grounds could lift with respect to
each other I've never seen that happen, and I've gone looking for it. So
that I can sleep at night, I ensure that an operator can't touch metal
referenced to the different grounds at any one time.

4) Power supplied to the room has to be directly connected. To stop building
noise from entering the room through this wiring, the noise is removed to the
case of a filter. I've located my filters very close to the room single point
room earth connection, so the noise can get there easily without crossing one
of my room seams or joints.

5) Any equipment I use with the room is referenced to the room ground. Power
for this equipment is filtered at the same point the room power is. Most
instrumentation used in EMC is quiet so they don't supply much noise.

I don't believe there is guess work involved with room grounding. The above is
based on conversations with many room installers. I suggest that if you have
specific questions, contact the folks that made yours.

-
This message is coming from the emc-pstc discussion list.
To cancel your subscription, send mail to majord...@ieee.org
with the single line: unsubscribe emc-pstc (without the
quotes).  For help, send mail to ed.pr...@cubic.com,
j...@gwmail.monarch.com, ri...@sdd.hp.com, or
roger.volgst...@compaq.com (the list administrators).