RE: Legacy Historian Upgrade

2001-09-27 Thread Millan, Alexander

Re: foxpai.cfg and fastest_rsr

There is a brief description of "fastest_rsr" in the QF990084 and how you can change 
it. I have used this variable with FoxAPI. The deafult value is 1 (means 1/2 seconds), 
every steps means 1/2 sec, i.e., if fastest_rsr = 10, that means 5 seconds. I am not 
sure if this parameters modify the historian scan rate (neither legacy nor AIM*)


Re: Historian Upgrade

I don't remenber why, but I think that you can get some problems if you try to just 
recommit. On version 4.3 we commit the station twice: First remove the historian and 
then install again with the new size.

Regards,

Alexander Millan
Automation Enginneer
PDVSA El Palito Refnery
Phone: +58-242-3603461
Fax:  +58-242-3604766



***  PDVSA´S INTERNET E-MAIL USE  ***
This message may contain information solely  of the interest of PDVSA or
its businesses. Copying,  distribution,  disclosure  or any  use  of the
information   contained  in  this  transmission  is  permitted  only  to
authorized  parties. If you have  received this e-mail by  error, please
destroy it and notify [EMAIL PROTECTED] or the sender by reply email.

**  USO DEL CORREO ELECTRONICO DE PDVSA HACIA INTERNET  **
Esta nota puede contener informacion de interes solo  para  PDVSA o  sus
negocios. Solo esta  permitida su  copia, distribucion  o uso a personas
autorizadas. Si recibio esta  nota  por  error,  por  favor destruyala y
notifique al remitente o a [EMAIL PROTECTED]


---
This list is neither sponsored nor endorsed by the Foxboro Company. All 
postings from this list are the work of list subscribers and no warranty 
is made or implied as to the accuracy of any information disseminated 
through this medium. By subscribing to this list you agree to hold the 
list sponsor(s) blameless for any and all mishaps which might occur due to 
your application of information received from this mailing list.

To be removed from this list, send mail to 
[EMAIL PROTECTED] 
with "unsubscribe foxboro" in the Subject. Or, send any mail to
[EMAIL PROTECTED]




RE: PLC Question

2001-09-27 Thread duc . do

John Metsker experienced some unknown problems posting his message to the
list, so I'm trying to see if I can do it for him. Let's hope the server
doesn't pass all of his postings now, including this one. Anyway, here
goes

Duc


~

From: John Metsker
Sent: Wednesday, September 26, 2001 6:28 PM
To: 'Foxboro DCS Mail List'
Subject: RE: PLC Question

List,

I have been meaning to chime in on this topic, but I was "stuck" on the road
when it was first raised and I have struggling to catch up on a lot of
things ever since.

>I have nine overloaded AB30's connected to one PLC-3 that I plan on
updating
>to a ControlLogix 5550.  This is absurd.  I would like to have something
>LIKE an AB30 (with no hard drives, moving parts, configure in ICC, ...) but
with
> a much larger capacity - like a CP60 communicating over Ethernet to
> ControlLogix.

We have been using the AW51 Integrator as a dedicated "Gateway 51's" since
the product was introduced.  The advantages are that it supports Ethernet
communications to AB PLCs and it utilizes Rockwell's API software
(Interchange) so it is not an entirely Foxboro developed integration
solution.  To improve robustness, we try to operate them as dedicated
control stations by limiting other AW functionality performed by the
station. For platform consistency and remote support, we have emphasized the
AW51 Integrator and not the AW70 Int.

Connectivity to Control Logix was achieved by simply loading the latest
version of Interchange (V6.2, not be confused with I/A version) and
configuring the necessary communications daemon.  It is very helpful to have
one Foxboro AB integration device that allows communications to CL, PLC5E,
SLC505, or any legacy DH+ based PLC via a Pyramid Integrator or CL gateway.

Yes, applications using Interchange function calls must utilize "PLC 5
style" addressing when communicating to a CL processor, but this needs only
be done for the data elements that I/A is  accessing.  The full freedom of
native CL addressing can not really be enjoyed since there is no existing
I/A input/output block that supports mixed data types.

>I actually purchased AB Interchange for Solaris and was considering
>installing it
>when I realized how much maintenance and configuration is required.  One of
>our plants does us this method and is not happy with the results.

Interchange runs as a pkgadd on Solaris and it really is just a "C" shared
library that gets linked to cio_cp.csx task that runs in the AW Int. when
the top-level ECB is created.  Configuration of the communications daemon
necessary to communicate to CL is straightforward and well documented by AB.
There is no additional maintenance necessary.

There are 3 layers of ECBs to configure, but straightforward and
understandable none the less.

> 6. AW51 or AW70 through an Ethernet interface with a third party OPC
> software which addresses data in the native ControLogic naming structure.

>This is what I will probably have to end up doing.  AW51 with a third party
>OPC server.  I just wish I didn't have go this way.  It has a hard drive,
has
>to be configured a couple of places instead of one, and I will have to deal
>with finger pointing when something goes wrong.

I would be the first person to agree that the utilizing a host box as a
control station is hardly an idealized solution.  I consider the current
AW51 Integrator product to be a fairly robust one, but having lived through
it's evolution and Foxboro's ability to support network communication to AB
PLCs, I would not consider a hard drive to be the weakest link of the
implementation.  I think that point can easily be balanced by the fact that
an open operating system is available where system and network diagnostics
are available and a fully supported vendor API (Interchange) is able to run.

I would definitely look to reduce product layers/interfaces to reduce the
potential for finger pointing, but I would never implement a system that
would eliminate AB-Rockwell as solution/support provider when the goal is to
communicate to AB PLCs.

Like any other non-fault tolerant control station, it is necessary to manage
the risk that is carried by a single station.  The large capacity AW
Integrator station image has a huge equivalent block capability (15,000),
but I would not recommend utilizing it.

My immediate wish is to have the Invensys I/A marketing people recognize the
use of an AW51 Int. as a dedicated PLC gateway and offer pricing for the
functionality utilized and not be penalized for the additional, full AW
functionality that comes bundled with it that I do not use.

A little commentary on the other solutions listed.

> 1. AB Integrator 30 to AB 1770-KF2 or 1779-KFL DH+ module in single or
> redundant ControLogix configuration.

Ethernet is the way to go.

> 2. AW51 or AW70 with Ethernet interface, FoxBlocks and AB Interchange or
> RSLinx software.

I think the best way to go.  Pi

Re: AW70 & AKP

2001-09-27 Thread Stefano Persico

Sorry
AKP is for Annunciator Keyboard Panel

"Johnson, Alex (Foxboro)" wrote:

> I'll start with the simplest question. What is AKP?
>
> Regards,
>
> Alex Johnson
> 10707 Haddington
> Houston, TX 77043
> 713.722.2859 (office)
> 713.722.2700 (switchboard)
> 713.932.0222 (fax)
> [EMAIL PROTECTED] 
>
> -Original Message-
> From:   Stefano Persico [SMTP:[EMAIL PROTECTED]]
> Sent:   Wednesday, September 26, 2001 5:45 PM
> To: Foxboro DCS Mail List
> Subject:AW70 & AKP
>
> Hi all
> is anyone experienced with AKP on AW70 ???
> I've one Plant with 70s Series running 6.2 with AKP configured which
> very (very !!) often freeze - stop calling displays,receiving alarms
>  - and the only way to restore the functionality is to
> power-off/power-on.
> From CSC no trace of this problem - as i can see - so why not ask
> about
> it on Foxboro's GURU list ???
> Bye Bye
> Stefano Persico
> [EMAIL PROTECTED]
>
>
> ---
> This list is neither sponsored nor endorsed by the Foxboro Company.
> All
> postings from this list are the work of list subscribers and no
> warranty
> is made or implied as to the accuracy of any information
> disseminated
> through this medium. By subscribing to this list you agree to hold
> the
> list sponsor(s) blameless for any and all mishaps which might occur
> due to
> your application of information received from this mailing list.
>
> To be removed from this list, send mail to
> [EMAIL PROTECTED]
> with "unsubscribe foxboro" in the Subject. Or, send any mail to
> [EMAIL PROTECTED]
>
> ---
> This list is neither sponsored nor endorsed by the Foxboro Company. All
> postings from this list are the work of list subscribers and no warranty
> is made or implied as to the accuracy of any information disseminated
> through this medium. By subscribing to this list you agree to hold the
> list sponsor(s) blameless for any and all mishaps which might occur due to
> your application of information received from this mailing list.
>
> To be removed from this list, send mail to
> [EMAIL PROTECTED]
> with "unsubscribe foxboro" in the Subject. Or, send any mail to
> [EMAIL PROTECTED]


---
This list is neither sponsored nor endorsed by the Foxboro Company. All 
postings from this list are the work of list subscribers and no warranty 
is made or implied as to the accuracy of any information disseminated 
through this medium. By subscribing to this list you agree to hold the 
list sponsor(s) blameless for any and all mishaps which might occur due to 
your application of information received from this mailing list.

To be removed from this list, send mail to 
[EMAIL PROTECTED] 
with "unsubscribe foxboro" in the Subject. Or, send any mail to
[EMAIL PROTECTED]




RE: Legacy Historian Upgrade

2001-09-27 Thread Cyrus W. Taft

I am familiar with the Legacy Historian but I was recently at a plant where
they had the new AIM* Historian.  It was installed on a Sun machine.  I
really like the fact that you can change its configuration without shutting
it down. This allowed us to tighten many deadbands specifically for the
tests we were running without impacting their normal data collection. 
There is a GUI configuration program for Solaris and it is not too bad.  We
had a strange problem trying to enter new deadband number for a few points.
 For some reason it would not accept the number we wanted to enter.  So
instead we ended up entering 0.0 which worked.

The main thing I didn't like was the data extraction capabilities.  It may
be that there is a better tool, but the only one I could find was the Data
Display function.  This is much improved over the same program for the
Legacy Historian but it is still a pain to use for extracting a large
amount of data.  I ended up having to extract 63 separate files to get all
the data we needed.  It then took me about 6 hours to merge all that data
into a single Excel file.  On our Legacy system we use a program called
ProcIns_extract to extract data and it is much easier to use.  I am always
amazed that Historian developers and vendors don't include a simple program
to extract data to a text file in their base system.  Westinghouse has the
same problem as Foxboro in this area.

Cyrus Taft
Chief Engineer
EPRI I&C Center
Harriman, TN

---
This list is neither sponsored nor endorsed by the Foxboro Company. All postings from 
this list are the work of list subscribers and no warranty is made or implied as to 
the accuracy of any information disseminated through this medium. By subscribing to 
this list you agree to hold the list sponsor(s) blameless for any and all mishaps 
which might occur due to your application of information received from this mailing 
list.

To be removed from this list, send mail to [EMAIL PROTECTED]
with "unsubscribe foxboro" in the Subject. Or, send any mail to
[EMAIL PROTECTED]




RE: Legacy Historian Upgrade

2001-09-27 Thread Johnson, Alex (Foxboro)

Re: fastest_rsr

I believe that parameter of the same name is in the AIM*API file. By
default, it forces all updates to 0.5 second scans regardless of the
recording rate set in the historian. I suspect that this is most of your
load.


Re: Obtaining the Solaris Configurator

You should contact your acct rep. I don't know what is required to get it,
but I do know that it is shipping and useful.



Regards,


Alex Johnson
10707 Haddington
Houston, TX 77043
713.722.2859 (office)
713.722.2700 (switchboard)
713.932.0222 (fax)
[EMAIL PROTECTED]  


-Original Message-
From:   Lowell, Tim: [SMTP:[EMAIL PROTECTED]]
Sent:   Thursday, September 27, 2001 10:04 AM
To: 'Foxboro DCS Mail List'
Subject:RE: Legacy Historian Upgrade

Alex,

We have configured most flows to update at 10 seconds, and most
everything
else to update at 30 seconds, with change deltas of 0.1% of
engineering
units.  I wish there was a way to configure deltas as percent of
actual
observed range, like the Biles AIM product used to have.  That would
really
be nice.

I had never even heard of fastest_rsr until the Connoisseur guys
added it to
foxapi.cfg, but that of course does not affect AIM*Historian.  That
would be
/opt/aim/bin/aimapi.cfg.  Does fastest_rsr also apply there, or is
it
something different?

How does one obtain the Solaris Configurator?  Is it part of the
"you must
ante-up some more cash" version 3.1, or can I get it for my current
version
3.02?

I did refer to I/A Report Writer, which I think is the same thing as
the
Foxboro Canada report package with a different name.

Tim Lowell
Control Systems Engineer
Phillips Petroleum Company, Trainer Refinery
Phone:  610-364-8362
Fax:610-364-8211
[EMAIL PROTECTED]


-Original Message-
From:   Johnson, Alex (Foxboro) [SMTP:[EMAIL PROTECTED]]
Sent:   Thursday, September 27, 2001 10:29 AM
To: Foxboro DCS Mail List
Subject:RE: Legacy Historian Upgrade

Re: Loading


The load is proportional to the number of changes and the
update
rates. 


What is your setting for fastest_rsr in
/opt/fox/ais/bin/foxapi.cfg?
This
controls how often updates are sent from the CP to the
historian.


How do you change deltas now compare with the ones then?



Re: You must have at least one Windows NT workstation or
server on
the
network to configure it.  It cannot be configured from
Solaris
except with
the command line interface, which is great for bulk edits
but
cumbersome for
small changes.  This could be a problem for sites not
running
Windows NT.


The Solaris Configurator is available and has been for a few
months.



Re: no tools are provided for extracting real-time data into
tabular
or text
format with AIM*Historian by itself


The I/A Series Report Writer is available.



Regards,


Alex Johnson
10707 Haddington
Houston, TX 77043
713.722.2859 (office)
713.722.2700 (switchboard)
713.932.0222 (fax)
[EMAIL PROTECTED]  


-Original Message-
From:   Lowell, Tim: [SMTP:[EMAIL PROTECTED]]
Sent:   Thursday, September 27, 2001 9:07 AM
To: 'Foxboro DCS Mail List'
Subject:RE: Legacy Historian Upgrade

And now a customer perspective...

Pros of AIM*Historian:

1.  You can modify it while it is running.
2.  You can run it on the NT platform as well as
AW51,
and you
can set
up remote collectors on both NT and Unix platforms.
3.  Much better archiving and storage tools.
4.  Reasonably clean Windows NT interface (with
some
annoying
little
quirks) as well as the usual bulk command line
interface.

Cons of AIM* Historian:

1.  It can be an enormous resource hog.  Our
6000-points-or-so
AIM*Historian runs on an AW51E, 256 MB RAM, a 9.1 GB
hard
drive, and
we
notice considerable sluggishness over the AW51E we
have that
doesn't
r

RE: Legacy Historian Upgrade

2001-09-27 Thread Ries, Gerry

We have migrated our legacy historian several times using saveh50 and
loadh50.  It actually works pretty well.  

The saveh50 utility unloads the Informix data and table structure to a
series of sql scripts and files of ascii data.  There is not a lot of
interaction once the process starts.  It takes quite a bit of time (hours)
to unload the database depending on the machine and the amount of data. Be
patient while it runs.

Before running the loadh50 make sure you have allocated enough space to the
informix raw partition.  If I remember correctly the default is only 50 Meg.
There is a helpful hint HH528 on expanding the raw partition and checking
the size of your current partition.

Gerry Ries
City of San Francisco
Water Pollution Control Division
750 Phelps St 
San Francisco CA 94124
Phone: 415.648.6882 ext. 1256
Fax: 415.648.8420



-Original Message-
From: Bertollini, Paride [mailto:[EMAIL PROTECTED]]
Sent: Thursday, September 27, 2001 5:54 AM
To: Foxboro DCS Mail List (E-mail)
Subject: Legacy Historian Upgrade


Hi,
Is anyone of you already experienced with an upgrade of a Legacy historian?
Customer needs to make larger  his historian, from 500 to 1000 points
without loosing his preexisting configuration.
Do the saveh50 and loadh50 utilities allow this?

Step by step:
-saveh50
-recommit with new historian size(same name)
-loadh50
is this possible or is it enough?I've looked on Helpful hints, CARS, but
i've not found documents about this.
Thank you in advance.  

Paride Bertollini
Invensys Foxboro Italia
Customer Service Dept.
mailto:[EMAIL PROTECTED]

---
This list is neither sponsored nor endorsed by the Foxboro Company. All 
postings from this list are the work of list subscribers and no warranty 
is made or implied as to the accuracy of any information disseminated 
through this medium. By subscribing to this list you agree to hold the 
list sponsor(s) blameless for any and all mishaps which might occur due to 
your application of information received from this mailing list.

To be removed from this list, send mail to 
[EMAIL PROTECTED] 
with "unsubscribe foxboro" in the Subject. Or, send any mail to
[EMAIL PROTECTED]

---
This list is neither sponsored nor endorsed by the Foxboro Company. All 
postings from this list are the work of list subscribers and no warranty 
is made or implied as to the accuracy of any information disseminated 
through this medium. By subscribing to this list you agree to hold the 
list sponsor(s) blameless for any and all mishaps which might occur due to 
your application of information received from this mailing list.

To be removed from this list, send mail to 
[EMAIL PROTECTED] 
with "unsubscribe foxboro" in the Subject. Or, send any mail to
[EMAIL PROTECTED]




RE: Legacy Historian Upgrade

2001-09-27 Thread Lowell, Tim:

Alex,

We have configured most flows to update at 10 seconds, and most everything
else to update at 30 seconds, with change deltas of 0.1% of engineering
units.  I wish there was a way to configure deltas as percent of actual
observed range, like the Biles AIM product used to have.  That would really
be nice.

I had never even heard of fastest_rsr until the Connoisseur guys added it to
foxapi.cfg, but that of course does not affect AIM*Historian.  That would be
/opt/aim/bin/aimapi.cfg.  Does fastest_rsr also apply there, or is it
something different?

How does one obtain the Solaris Configurator?  Is it part of the "you must
ante-up some more cash" version 3.1, or can I get it for my current version
3.02?

I did refer to I/A Report Writer, which I think is the same thing as the
Foxboro Canada report package with a different name.

Tim Lowell
Control Systems Engineer
Phillips Petroleum Company, Trainer Refinery
Phone:  610-364-8362
Fax:610-364-8211
[EMAIL PROTECTED]


-Original Message-
From:   Johnson, Alex (Foxboro) [SMTP:[EMAIL PROTECTED]]
Sent:   Thursday, September 27, 2001 10:29 AM
To: Foxboro DCS Mail List
Subject:RE: Legacy Historian Upgrade

Re: Loading


The load is proportional to the number of changes and the update
rates. 


What is your setting for fastest_rsr in /opt/fox/ais/bin/foxapi.cfg?
This
controls how often updates are sent from the CP to the historian.


How do you change deltas now compare with the ones then?



Re: You must have at least one Windows NT workstation or server on
the
network to configure it.  It cannot be configured from Solaris
except with
the command line interface, which is great for bulk edits but
cumbersome for
small changes.  This could be a problem for sites not running
Windows NT.


The Solaris Configurator is available and has been for a few months.



Re: no tools are provided for extracting real-time data into tabular
or text
format with AIM*Historian by itself


The I/A Series Report Writer is available.



Regards,


Alex Johnson
10707 Haddington
Houston, TX 77043
713.722.2859 (office)
713.722.2700 (switchboard)
713.932.0222 (fax)
[EMAIL PROTECTED]  


-Original Message-
From:   Lowell, Tim: [SMTP:[EMAIL PROTECTED]]
Sent:   Thursday, September 27, 2001 9:07 AM
To: 'Foxboro DCS Mail List'
Subject:RE: Legacy Historian Upgrade

And now a customer perspective...

Pros of AIM*Historian:

1.  You can modify it while it is running.
2.  You can run it on the NT platform as well as AW51,
and you
can set
up remote collectors on both NT and Unix platforms.
3.  Much better archiving and storage tools.
4.  Reasonably clean Windows NT interface (with some
annoying
little
quirks) as well as the usual bulk command line interface.

Cons of AIM* Historian:

1.  It can be an enormous resource hog.  Our
6000-points-or-so
AIM*Historian runs on an AW51E, 256 MB RAM, a 9.1 GB hard
drive, and
we
notice considerable sluggishness over the AW51E we have that
doesn't
run
AIM*Historian.  The Legacy Historian is no slouch hogging up
resources also
of course, but I can recall a few years back at another site
running
a
similar number of points on an AW51C with a 1.2 GB drive
without
many
problems.
2.  Could be a cost issue for some companies.  And the
AIM*Suite
utilities (AIM*Datalink, et. al.) don't buy you much over
the ODBC
interface
you can already get with the Legacy Historian.  AIM*Datalink
is a
woefully
inadequate product.  The only thing we use it for here is
the DDE
interface
so that we can link AIM*Historian real-time data to our
Excel Visual
Basic
sheets.  Otherwise, no one uses it because it is cumbersome
and
requires
intimate knowledge of how the I/A system is put together,
which our
process
engineers don't have.
3.  You must have at least one Windows NT workstation or
server
on the
network to configure it.  It cannot be configured from
Solaris
except with
the command line interface, which is great for bulk edits
but
cumbersome for
small changes.  This could be a problem for sites not
running
Windows NT.
4.

RE: Legacy Historian Upgrade

2001-09-27 Thread Johnson, Alex (Foxboro)

Re: Loading


The load is proportional to the number of changes and the update rates. 


What is your setting for fastest_rsr in /opt/fox/ais/bin/foxapi.cfg? This
controls how often updates are sent from the CP to the historian.


How do you change deltas now compare with the ones then?



Re: You must have at least one Windows NT workstation or server on the
network to configure it.  It cannot be configured from Solaris except with
the command line interface, which is great for bulk edits but cumbersome for
small changes.  This could be a problem for sites not running Windows NT.


The Solaris Configurator is available and has been for a few months.



Re: no tools are provided for extracting real-time data into tabular or text
format with AIM*Historian by itself


The I/A Series Report Writer is available.



Regards,


Alex Johnson
10707 Haddington
Houston, TX 77043
713.722.2859 (office)
713.722.2700 (switchboard)
713.932.0222 (fax)
[EMAIL PROTECTED]  


-Original Message-
From:   Lowell, Tim: [SMTP:[EMAIL PROTECTED]]
Sent:   Thursday, September 27, 2001 9:07 AM
To: 'Foxboro DCS Mail List'
Subject:RE: Legacy Historian Upgrade

And now a customer perspective...

Pros of AIM*Historian:

1.  You can modify it while it is running.
2.  You can run it on the NT platform as well as AW51, and you
can set
up remote collectors on both NT and Unix platforms.
3.  Much better archiving and storage tools.
4.  Reasonably clean Windows NT interface (with some annoying
little
quirks) as well as the usual bulk command line interface.

Cons of AIM* Historian:

1.  It can be an enormous resource hog.  Our 6000-points-or-so
AIM*Historian runs on an AW51E, 256 MB RAM, a 9.1 GB hard drive, and
we
notice considerable sluggishness over the AW51E we have that doesn't
run
AIM*Historian.  The Legacy Historian is no slouch hogging up
resources also
of course, but I can recall a few years back at another site running
a
similar number of points on an AW51C with a 1.2 GB drive without
many
problems.
2.  Could be a cost issue for some companies.  And the AIM*Suite
utilities (AIM*Datalink, et. al.) don't buy you much over the ODBC
interface
you can already get with the Legacy Historian.  AIM*Datalink is a
woefully
inadequate product.  The only thing we use it for here is the DDE
interface
so that we can link AIM*Historian real-time data to our Excel Visual
Basic
sheets.  Otherwise, no one uses it because it is cumbersome and
requires
intimate knowledge of how the I/A system is put together, which our
process
engineers don't have.
3.  You must have at least one Windows NT workstation or server
on the
network to configure it.  It cannot be configured from Solaris
except with
the command line interface, which is great for bulk edits but
cumbersome for
small changes.  This could be a problem for sites not running
Windows NT.
4.  Unlike Legacy Historian, no tools are provided for
extracting
real-time data into tabular or text format with AIM*Historian by
itself.
There is an Excel add-in, which is only somewhat helpful, but you
must buy
the whole AIM*Suite to get it.  If you want any sort of
customization at
all, you must create your own tools using C or Visual Basic.  If you
happen
to know or want to learn C or VB, that's great, but if you don't
know it or
don't have time to learn, you'll have to spend more money to hire
someone
who does.  You could also buy the Foxboro Canada report package,
which also
works with the Legacy Historian.

We have AIM*Historian here, and I would never want to go back to the
Legacy
Historian, despite the myriad of problems we have had with issues
mostly
related to the remote collector we set up.  We bought the whole
AIM*Suite as
a small part of a huge project, we have NT here, and I happen to
know a
little VB, so the cons are not an issue here, but they may be for
some
sites.  The fact that you can modify it while it is running is a big
enough
pro for me to recommend it, especially to sites where historian
uptime is a
big deal, like a refinery.  

Tim Lowell
Control Systems Engineer
Phillips Petroleum Company, Trainer Refinery
Phone:  610-364-8362
Fax:610-364-8211
[EMAIL PROTECTED]


-Original Message-
From:   Johnson, Alex (Foxboro) [SMTP:[EMAIL PROTECTED]]
Sent:   Thursday, September 27, 2001 9:25 AM
To: Foxboro DCS Mail List
Subject:RE: Legacy Historian Upgrade

You should g

RE: Legacy Historian Upgrade

2001-09-27 Thread Lowell, Tim:

And now a customer perspective...

Pros of AIM*Historian:

1.  You can modify it while it is running.
2.  You can run it on the NT platform as well as AW51, and you can set
up remote collectors on both NT and Unix platforms.
3.  Much better archiving and storage tools.
4.  Reasonably clean Windows NT interface (with some annoying little
quirks) as well as the usual bulk command line interface.

Cons of AIM* Historian:

1.  It can be an enormous resource hog.  Our 6000-points-or-so
AIM*Historian runs on an AW51E, 256 MB RAM, a 9.1 GB hard drive, and we
notice considerable sluggishness over the AW51E we have that doesn't run
AIM*Historian.  The Legacy Historian is no slouch hogging up resources also
of course, but I can recall a few years back at another site running a
similar number of points on an AW51C with a 1.2 GB drive without many
problems.
2.  Could be a cost issue for some companies.  And the AIM*Suite
utilities (AIM*Datalink, et. al.) don't buy you much over the ODBC interface
you can already get with the Legacy Historian.  AIM*Datalink is a woefully
inadequate product.  The only thing we use it for here is the DDE interface
so that we can link AIM*Historian real-time data to our Excel Visual Basic
sheets.  Otherwise, no one uses it because it is cumbersome and requires
intimate knowledge of how the I/A system is put together, which our process
engineers don't have.
3.  You must have at least one Windows NT workstation or server on the
network to configure it.  It cannot be configured from Solaris except with
the command line interface, which is great for bulk edits but cumbersome for
small changes.  This could be a problem for sites not running Windows NT.
4.  Unlike Legacy Historian, no tools are provided for extracting
real-time data into tabular or text format with AIM*Historian by itself.
There is an Excel add-in, which is only somewhat helpful, but you must buy
the whole AIM*Suite to get it.  If you want any sort of customization at
all, you must create your own tools using C or Visual Basic.  If you happen
to know or want to learn C or VB, that's great, but if you don't know it or
don't have time to learn, you'll have to spend more money to hire someone
who does.  You could also buy the Foxboro Canada report package, which also
works with the Legacy Historian.

We have AIM*Historian here, and I would never want to go back to the Legacy
Historian, despite the myriad of problems we have had with issues mostly
related to the remote collector we set up.  We bought the whole AIM*Suite as
a small part of a huge project, we have NT here, and I happen to know a
little VB, so the cons are not an issue here, but they may be for some
sites.  The fact that you can modify it while it is running is a big enough
pro for me to recommend it, especially to sites where historian uptime is a
big deal, like a refinery.  

Tim Lowell
Control Systems Engineer
Phillips Petroleum Company, Trainer Refinery
Phone:  610-364-8362
Fax:610-364-8211
[EMAIL PROTECTED]


-Original Message-
From:   Johnson, Alex (Foxboro) [SMTP:[EMAIL PROTECTED]]
Sent:   Thursday, September 27, 2001 9:25 AM
To: Foxboro DCS Mail List
Subject:RE: Legacy Historian Upgrade

You should give consideration to moving to AIM*. It contains
migration
utilities that preserve the customer's data and configuration
information.


Regards,


Alex Johnson
10707 Haddington
Houston, TX 77043
713.722.2859 (office)
713.722.2700 (switchboard)
713.932.0222 (fax)
[EMAIL PROTECTED]  



---
This list is neither sponsored nor endorsed by the Foxboro Company. All 
postings from this list are the work of list subscribers and no warranty 
is made or implied as to the accuracy of any information disseminated 
through this medium. By subscribing to this list you agree to hold the 
list sponsor(s) blameless for any and all mishaps which might occur due to 
your application of information received from this mailing list.

To be removed from this list, send mail to 
[EMAIL PROTECTED] 
with "unsubscribe foxboro" in the Subject. Or, send any mail to
[EMAIL PROTECTED]




RE: Legacy Historian Upgrade

2001-09-27 Thread Johnson, Alex (Foxboro)

You should give consideration to moving to AIM*. It contains migration
utilities that preserve the customer's data and configuration information.


Regards,


Alex Johnson
10707 Haddington
Houston, TX 77043
713.722.2859 (office)
713.722.2700 (switchboard)
713.932.0222 (fax)
[EMAIL PROTECTED]  


-Original Message-
From:   Bertollini, Paride [SMTP:[EMAIL PROTECTED]]
Sent:   Thursday, September 27, 2001 7:54 AM
To: Foxboro DCS Mail List (E-mail)
Subject:Legacy Historian Upgrade

Hi,
Is anyone of you already experienced with an upgrade of a Legacy
historian?
Customer needs to make larger  his historian, from 500 to 1000
points
without loosing his preexisting configuration.
Do the saveh50 and loadh50 utilities allow this?

Step by step:
-saveh50
-recommit with new historian size(same name)
-loadh50
is this possible or is it enough?I've looked on Helpful hints, CARS,
but
i've not found documents about this.
Thank you in advance.  

Paride Bertollini
Invensys Foxboro Italia
Customer Service Dept.
mailto:[EMAIL PROTECTED]


---
This list is neither sponsored nor endorsed by the Foxboro Company.
All 
postings from this list are the work of list subscribers and no
warranty 
is made or implied as to the accuracy of any information
disseminated 
through this medium. By subscribing to this list you agree to hold
the 
list sponsor(s) blameless for any and all mishaps which might occur
due to 
your application of information received from this mailing list.

To be removed from this list, send mail to 
[EMAIL PROTECTED] 
with "unsubscribe foxboro" in the Subject. Or, send any mail to
[EMAIL PROTECTED]

---
This list is neither sponsored nor endorsed by the Foxboro Company. All 
postings from this list are the work of list subscribers and no warranty 
is made or implied as to the accuracy of any information disseminated 
through this medium. By subscribing to this list you agree to hold the 
list sponsor(s) blameless for any and all mishaps which might occur due to 
your application of information received from this mailing list.

To be removed from this list, send mail to 
[EMAIL PROTECTED] 
with "unsubscribe foxboro" in the Subject. Or, send any mail to
[EMAIL PROTECTED]




Legacy Historian Upgrade

2001-09-27 Thread Bertollini, Paride

Hi,
Is anyone of you already experienced with an upgrade of a Legacy historian?
Customer needs to make larger  his historian, from 500 to 1000 points
without loosing his preexisting configuration.
Do the saveh50 and loadh50 utilities allow this?

Step by step:
-saveh50
-recommit with new historian size(same name)
-loadh50
is this possible or is it enough?I've looked on Helpful hints, CARS, but
i've not found documents about this.
Thank you in advance.  

Paride Bertollini
Invensys Foxboro Italia
Customer Service Dept.
mailto:[EMAIL PROTECTED]

---
This list is neither sponsored nor endorsed by the Foxboro Company. All 
postings from this list are the work of list subscribers and no warranty 
is made or implied as to the accuracy of any information disseminated 
through this medium. By subscribing to this list you agree to hold the 
list sponsor(s) blameless for any and all mishaps which might occur due to 
your application of information received from this mailing list.

To be removed from this list, send mail to 
[EMAIL PROTECTED] 
with "unsubscribe foxboro" in the Subject. Or, send any mail to
[EMAIL PROTECTED]




Re: CP40 malfunction

2001-09-27 Thread shoudek

Hafedh:

I recommend having your system upgraded to version 6.1.2 (release update).
I have recently observed a similar issue at another site.
Installing 6.1.2 fixed the problem at that site.
After the upgrade verify that your CP40 style "A" processor is at EPROM ver.
1.20 (check in Sys Mgmt) and the software version (check in the SELECT page,
station block) should be V2K_01.
Keep in mind, the release update it self only takes about 10 minutes + a
reboot of the AW, however the Compliance media CD, which must be installed
prior to the release update takes about 1.5 hours on an AW51B box, and about
20 minutes max on an AW51E box.
Also, all CP's will require a  reboot.
More information (release notes) may be found on the Foxboro CSC web.
I recommend a review of the "Problems resolved in 6.1.2" section.

Regards
Steven Houdek
Foxboro Field Service
Invensys email: [EMAIL PROTECTED]
Personal broadband, subscribed to Cassandra as: [EMAIL PROTECTED]


- Original Message -
From: "Ghodhbani, Hafedh" <[EMAIL PROTECTED]>
To: "'Foxboro DCS Mail List'" <[EMAIL PROTECTED]>
Sent: Thursday, September 27, 2001 3:38 AM
Subject: RE: CP40 malfunction


> John,
> Since 1999 we have version 6.1.1.
>
> Hafedh Ghodhbani
> Control and Instrument Engineer
> British Gas Group
> Hannibal Gas Plant Tunisia
> ph 00 216 4 259 250
> Fax 00 216 4 259 449
>
> -Original Message-
> From: John Miller [mailto:[EMAIL PROTECTED]]
> Sent: 26 September 2001 12:22
> To: 'Foxboro DCS Mail List'
> Subject: RE: CP40 malfunction
>
>
> Hafedh,
> What version of I/A are you running?
> John Miller
> Hunt Refining Company
> 1855 Fairlawn Road
> Tuscaloosa, AL 35401
> voice:  205.391.3345
> fax:  205.345.8769
> [EMAIL PROTECTED]
>
> -Original Message-
> From: Ghodhbani, Hafedh [mailto:[EMAIL PROTECTED]]
> Sent: Wednesday, September 26, 2001 5:39 AM
> To: Foxboro DCS Mail List
> Subject: CP40 malfunction
>
>
> Gents,
> I notice a strange malfunction that concerns some of my CP40FT type A
> modules. It consists in the following:
>
> * frequently some single CP modules are auto-rebooted.
> *sometimes some single CP modules are stopped. I reboot them manually.
> *It happened one time that a CP40FT  both modules stopped and a  total
plant
> Shutdown occured
>
> It was reported to Foxboro, But they always asked to change the CP module!
> Recently CAR2000274 was defined. However no feedback yet.
> The type of system alarm messages I received last 4 months are the
> following:
>
> EHSS 000141 Memory Parity Error - NMI Exception  6C024868
> EHSS 000141 Memory Parity Error - NMI Exception  6C078425
> RAMDSS 03 COOP IOBUS Fail FBM I/O FAILURE.  6C073595
> FTXSS 90 Modules failed to sync up prior to mem to mem
> 6C079819
> EHSS 000141 Memory Parity Error - NMI Exception  6C024868
> FTXSS 80 Memory violation occured 6C073595
> FTXSS 80 Memory violation occured 6C078463
>
> Have someone experienced or resolved a similar malfunction?
> What is the root-cause of this?
> How can it be resolved?
> Is there a chance that another plant shutdown take place due to CP40FT
> Shutdown of  both modules?
>
> Thanks
>
> Hafedh Ghodhbani
> Control and Instrument Engineer
> British Gas Group
> Hannibal Gas Plant Tunisia
> ph 00 216 4 259 250
> Fax 00 216 4 259 449
>
>  -
> BG Energy Holdings Limited (a member of BG Group)
> Registered in England No: 3763515
> Registered Address:
> 100 Thames Valley Park Drive
> Reading
> Berkshire   RG6 1PT   UK
> Telephone: +44 (0) 118 935 3222
> Website: http://www.BG-Group.com
>
> This e-mail is intended only for the addressee named above.  As this
> e-mail may contain confidential or privileged information, please
> advise us immediately if you are not the named addressee or the person
> responsible for delivering the message to the named addressee.  The
> contents should not be disclosed to any other person nor copies taken.
>  -
>
> ---
> This list is neither sponsored nor endorsed by the Foxboro Company. All
> postings from this list are the work of list subscribers and no warranty
> is made or implied as to the accuracy of any information disseminated
> through this medium. By subscribing to this list you agree to hold the
> list sponsor(s) blameless for any and all mishaps which might occur due to
> your application of information received from this mailing list.
>
> To be removed from this list, send mail to
> [EMAIL PROTECTED]
> with "unsubscribe foxboro" in the Subject. Or, send any mail to
> [EMAIL PROTECTED]
>
> ---
> This list is neither sponsored nor endorsed by the Foxboro Company. All
> postings from this list are the work of list subscribers and no warranty
> is made or implied as to the accuracy of an

RE: CP40 malfunction

2001-09-27 Thread Ghodhbani, Hafedh

John,
Since 1999 we have version 6.1.1.

Hafedh Ghodhbani
Control and Instrument Engineer
British Gas Group
Hannibal Gas Plant Tunisia
ph  00 216 4 259 250
Fax 00 216 4 259 449

-Original Message-
From: John Miller [mailto:[EMAIL PROTECTED]]
Sent: 26 September 2001 12:22
To: 'Foxboro DCS Mail List'
Subject: RE: CP40 malfunction


Hafedh,
What version of I/A are you running?
John Miller
Hunt Refining Company
1855 Fairlawn Road
Tuscaloosa, AL 35401
voice:  205.391.3345
fax:  205.345.8769
[EMAIL PROTECTED]

-Original Message-
From: Ghodhbani, Hafedh [mailto:[EMAIL PROTECTED]]
Sent: Wednesday, September 26, 2001 5:39 AM
To: Foxboro DCS Mail List
Subject: CP40 malfunction


Gents,
I notice a strange malfunction that concerns some of my CP40FT type A
modules. It consists in the following:

* frequently some single CP modules are auto-rebooted. 
*sometimes some single CP modules are stopped. I reboot them manually.
*It happened one time that a CP40FT  both modules stopped and a  total plant
Shutdown occured 

It was reported to Foxboro, But they always asked to change the CP module!
Recently CAR2000274 was defined. However no feedback yet.
The type of system alarm messages I received last 4 months are the
following:

EHSS000141  Memory Parity Error - NMI Exception  6C024868
EHSS000141  Memory Parity Error - NMI Exception  6C078425
RAMDSS  03  COOP IOBUS Fail FBM I/O FAILURE.  6C073595
FTXSS   90 Modules failed to sync up prior to mem to mem
6C079819
EHSS000141  Memory Parity Error - NMI Exception  6C024868
FTXSS   80 Memory violation occured 6C073595
FTXSS   80 Memory violation occured 6C078463

Have someone experienced or resolved a similar malfunction?
What is the root-cause of this?
How can it be resolved?
Is there a chance that another plant shutdown take place due to CP40FT
Shutdown of  both modules?

Thanks

Hafedh Ghodhbani
Control and Instrument Engineer
British Gas Group
Hannibal Gas Plant Tunisia
ph  00 216 4 259 250
Fax 00 216 4 259 449

 -
BG Energy Holdings Limited (a member of BG Group)
Registered in England No: 3763515
Registered Address:
100 Thames Valley Park Drive
Reading
Berkshire   RG6 1PT   UK
Telephone:  +44 (0) 118 935 3222
Website:http://www.BG-Group.com

This e-mail is intended only for the addressee named above.  As this 
e-mail may contain confidential or privileged information, please 
advise us immediately if you are not the named addressee or the person 
responsible for delivering the message to the named addressee.  The 
contents should not be disclosed to any other person nor copies taken.
 -

---
This list is neither sponsored nor endorsed by the Foxboro Company. All 
postings from this list are the work of list subscribers and no warranty 
is made or implied as to the accuracy of any information disseminated 
through this medium. By subscribing to this list you agree to hold the 
list sponsor(s) blameless for any and all mishaps which might occur due to 
your application of information received from this mailing list.

To be removed from this list, send mail to 
[EMAIL PROTECTED] 
with "unsubscribe foxboro" in the Subject. Or, send any mail to
[EMAIL PROTECTED]

---
This list is neither sponsored nor endorsed by the Foxboro Company. All 
postings from this list are the work of list subscribers and no warranty 
is made or implied as to the accuracy of any information disseminated 
through this medium. By subscribing to this list you agree to hold the 
list sponsor(s) blameless for any and all mishaps which might occur due to 
your application of information received from this mailing list.

To be removed from this list, send mail to 
[EMAIL PROTECTED] 
with "unsubscribe foxboro" in the Subject. Or, send any mail to
[EMAIL PROTECTED]


_
This message has been checked for all known viruses by the 
Message Labs Virus Control Centre.

 -
BG Energy Holdings Limited (a member of BG Group)
Registered in England No: 3763515
Registered Address:
100 Thames Valley Park Drive
Reading
Berkshire   RG6 1PT   UK
Telephone:  +44 (0) 118 935 3222
Website:http://www.BG-Group.com

This e-mail is intended only for the addressee named above.  As this 
e-mail may contain confidential or privileged information, please 
advise us immediately if you are not the named addresse