Re: [MBZ] OT: measuring Power Factor

2010-01-28 Thread LWB250
Nope, never even seen a kill a watt but I know what they are.

We have to provide documentation for most commercial customers on new units 
when they are installed, showing that they do indeed produce rated (nameplate) 
power.  That's done with a resistive load bank and this device.

It's also handy when we run into issues with the generator not carrying load, 
or to dispel concerns that the generator is not working to its rating.  A good 
example is with large UPS systems, which are non-linear as heck, and don't like 
generators as power supplies.

Glad to hear the generator is working OK.  It's always a good idea to test it 
under load on a regular basis, as just exercising it without doing so doesn't 
mean the transfer switch works.

I run mine every Saturday morning at 9:00 for 15 minutes, and test it under 
load once a month by pulling the breaker to the circuit that feeds the transfer 
switch.  It's a PITA because doing this knocks things like clocks off, but I 
would rather have to reset clocks than be in the dark when there is a power 
failure and the transfer switch doesn't work


Dan




--- On Mon, 1/25/10, Mitch Haley m...@voyager.net wrote:

 From: Mitch Haley m...@voyager.net
 Subject: Re: [MBZ] OT: measuring Power Factor
 To: Mercedes Discussion List mercedes@okiebenz.com
 Date: Monday, January 25, 2010, 12:21 PM
 LWB250 wrote:
  
  We have very sophisticated devices we use for testing
 and commissioning of generators (as well as for
 troubleshooting) that measure power factor among other
 values, but you're talking about several thousand dollars
 for something like this:
  
  http://www.tequipment.net/pdf/Fluke/435_datasheet.pdf
 
 Have you ever run something like that alongside a
 Kill-A-Watt and compared the readings?
 
 BTW, the transfer switch on the Generac seems to have cured
 itself. My last four simulated power failures have gone off
 without a hitch. Maybe the thing just needed exercise
 somehow? (the engine runs several minutes a week, but the
 transfer switch only trips during a power failure or
 simulation)
 
 Mitch.
 
 ___
 http://www.okiebenz.com
 For new and used parts go to www.okiebenz.com
 To search list archives http://www.okiebenz.com/archive/
 
 To Unsubscribe or change delivery options go to:
 http://okiebenz.com/mailman/listinfo/mercedes_okiebenz.com
 


  


___
http://www.okiebenz.com
For new and used parts go to www.okiebenz.com
To search list archives http://www.okiebenz.com/archive/

To Unsubscribe or change delivery options go to:
http://okiebenz.com/mailman/listinfo/mercedes_okiebenz.com


Re: [MBZ] OT: measuring Power Factor

2010-01-26 Thread Craig McCluskey
On Mon, 25 Jan 2010 08:13:22 -0800 Jim Cathey j...@windwireless.net
wrote:

 If you can get a dual-trace oscilloscope picture of both the
 voltage and amperage waveforms, superimposed, you can calculate
 the degrees of shift between the peaks and get a power factor
 that way. 

That's what I did when we lived in rural Colorado and were our own power
company. I added capacitors to the well pump to get its power factor back
to unity.


 That assumes a fairly sine-like current waveform, which is no
 guarantee.

Indeed, and that is a strong assumption. The current spikes drawn by an
older computer power supply are just about in phase with the voltage, but
because they are so non-sinusoidal, the power factor is about 0.8.


Craig

___
http://www.okiebenz.com
For new and used parts go to www.okiebenz.com
To search list archives http://www.okiebenz.com/archive/

To Unsubscribe or change delivery options go to:
http://okiebenz.com/mailman/listinfo/mercedes_okiebenz.com


Re: [MBZ] OT: measuring Power Factor

2010-01-25 Thread Dieselhead
Can you put on an ampprobe (clamp-on) to measure amps and measure 
volts with a different meter (simultaneously) and use that data to do 
the calculation?


With all these fancy digital handheld meters out there, is there a 
clamp-on meter that will give you a power factor while clamped on a 
wire?


No.  You cannot measure power factor without simultaneously
measuring both instantaneous current and voltage.  No clamp-on
measures any kind of voltage without a metallic connection.
The kill-a-watt is the only inexpensive tool I know of that
measures power factor.

-- Jim



___
http://www.okiebenz.com
For new and used parts go to www.okiebenz.com
To search list archives http://www.okiebenz.com/archive/

To Unsubscribe or change delivery options go to:
http://okiebenz.com/mailman/listinfo/mercedes_okiebenz.com



___
http://www.okiebenz.com
For new and used parts go to www.okiebenz.com
To search list archives http://www.okiebenz.com/archive/

To Unsubscribe or change delivery options go to:
http://okiebenz.com/mailman/listinfo/mercedes_okiebenz.com


Re: [MBZ] OT: measuring Power Factor

2010-01-25 Thread LWB250
Understand that power factor is a value that is constantly changing based on 
the types of loads that are present.  Power factor can lead or lag, and in the 
case of loads with motors or capacitance the value is not a constant.

In a balanced single phase circuit you could measure power factor with a 
wattmeter, ammeter and voltmeter, if you have them.  You could do this as well 
in a three phase system as long as the loads are balanced across the three 
phases.

My suggestion: Buy a kill-a-watt.

We have very sophisticated devices we use for testing and commissioning of 
generators (as well as for troubleshooting) that measure power factor among 
other values, but you're talking about several thousand dollars for something 
like this:

http://www.tequipment.net/pdf/Fluke/435_datasheet.pdf

Dan




--- On Mon, 1/25/10, Dieselhead 126die...@gmail.com wrote:

 From: Dieselhead 126die...@gmail.com
 Subject: Re: [MBZ] OT: measuring Power Factor
 To: Mercedes Discussion List mercedes@okiebenz.com
 Date: Monday, January 25, 2010, 9:55 AM
 Can you put on an ampprobe (clamp-on)
 to measure amps and measure 
 volts with a different meter (simultaneously) and use that
 data to do 
 the calculation?
 
 With all these fancy digital handheld meters out
 there, is there a 
 clamp-on meter that will give you a power factor
 while clamped on a 
 wire?
 
 No.  You cannot measure power factor without
 simultaneously
 measuring both instantaneous current and voltage. 
 No clamp-on
 measures any kind of voltage without a metallic
 connection.
 The kill-a-watt is the only inexpensive tool I know of
 that
 measures power factor.
 
 -- Jim
 
 
 
 ___
 http://www.okiebenz.com
 For new and used parts go to www.okiebenz.com
 To search list archives http://www.okiebenz.com/archive/
 
 To Unsubscribe or change delivery options go to:
 http://okiebenz.com/mailman/listinfo/mercedes_okiebenz.com
 
 
 ___
 http://www.okiebenz.com
 For new and used parts go to www.okiebenz.com
 To search list archives http://www.okiebenz.com/archive/
 
 To Unsubscribe or change delivery options go to:
 http://okiebenz.com/mailman/listinfo/mercedes_okiebenz.com
 


  


___
http://www.okiebenz.com
For new and used parts go to www.okiebenz.com
To search list archives http://www.okiebenz.com/archive/

To Unsubscribe or change delivery options go to:
http://okiebenz.com/mailman/listinfo/mercedes_okiebenz.com


Re: [MBZ] OT: measuring Power Factor

2010-01-25 Thread Dieselhead

Thanks Jim and Dan.

What I want to do is determine PF at hardwired 240 1 phase devices, 
such as central air cond. compressor/condensor units.  The 
Kill-A-Watt is great for 110v devices.  Is there any low-cost way to 
do that?


I can get amps with a clamp-on, volts with a voltmeter.  Is there any 
way to determine watts without rewiring a wattmeter inline?  If I 
have to rewire, then I could use two kill-a-watts with leads and 
clamps.


The Fluke would be nice, but the price is not justified for my needs.

Thanks again.

Understand that power factor is a value that is constantly changing 
based on the types of loads that are present.  Power factor can lead 
or lag, and in the case of loads with motors or capacitance the 
value is not a constant.


Yes, but there is an average value for a period of time.



In a balanced single phase circuit you could measure power factor 
with a wattmeter, ammeter and voltmeter, if you have them.  You 
could do this as well in a three phase system as long as the loads 
are balanced across the three phases.


My suggestion: Buy a kill-a-watt.

We have very sophisticated devices we use for testing and 
commissioning of generators (as well as for troubleshooting) that 
measure power factor among other values, but you're talking about 
several thousand dollars for something like this:


http://www.tequipment.net/pdf/Fluke/435_datasheet.pdf

Dan




--- On Mon, 1/25/10, Dieselhead 126die...@gmail.com wrote:


 From: Dieselhead 126die...@gmail.com
 Subject: Re: [MBZ] OT: measuring Power Factor
 To: Mercedes Discussion List mercedes@okiebenz.com
 Date: Monday, January 25, 2010, 9:55 AM
 Can you put on an ampprobe (clamp-on)
 to measure amps and measure
 volts with a different meter (simultaneously) and use that
 data to do
 the calculation?

 With all these fancy digital handheld meters out
 there, is there a
 clamp-on meter that will give you a power factor
 while clamped on a
 wire?
 
 No.  You cannot measure power factor without
 simultaneously
 measuring both instantaneous current and voltage. 
 No clamp-on

 measures any kind of voltage without a metallic
 connection.
 The kill-a-watt is the only inexpensive tool I know of
 that
 measures power factor.
 
 -- Jim
 
 
 
 ___
 http://www.okiebenz.com
 For new and used parts go to www.okiebenz.com
 To search list archives http://www.okiebenz.com/archive/
 
 To Unsubscribe or change delivery options go to:
 http://okiebenz.com/mailman/listinfo/mercedes_okiebenz.com


 ___
 http://www.okiebenz.com
 For new and used parts go to www.okiebenz.com
 To search list archives http://www.okiebenz.com/archive/

 To Unsubscribe or change delivery options go to:
 http://okiebenz.com/mailman/listinfo/mercedes_okiebenz.com




 



___
http://www.okiebenz.com
For new and used parts go to www.okiebenz.com
To search list archives http://www.okiebenz.com/archive/

To Unsubscribe or change delivery options go to:
http://okiebenz.com/mailman/listinfo/mercedes_okiebenz.com



___
http://www.okiebenz.com
For new and used parts go to www.okiebenz.com
To search list archives http://www.okiebenz.com/archive/

To Unsubscribe or change delivery options go to:
http://okiebenz.com/mailman/listinfo/mercedes_okiebenz.com


Re: [MBZ] OT: measuring Power Factor

2010-01-25 Thread Mitch Haley

LWB250 wrote:


We have very sophisticated devices we use for testing and commissioning of 
generators (as well as for troubleshooting) that measure power factor among 
other values, but you're talking about several thousand dollars for something 
like this:

http://www.tequipment.net/pdf/Fluke/435_datasheet.pdf


Have you ever run something like that alongside a Kill-A-Watt and compared the 
readings?


BTW, the transfer switch on the Generac seems to have cured itself. My last four 
simulated power failures have gone off without a hitch. Maybe the thing just 
needed exercise somehow? (the engine runs several minutes a week, but the 
transfer switch only trips during a power failure or simulation)


Mitch.

___
http://www.okiebenz.com
For new and used parts go to www.okiebenz.com
To search list archives http://www.okiebenz.com/archive/

To Unsubscribe or change delivery options go to:
http://okiebenz.com/mailman/listinfo/mercedes_okiebenz.com


Re: [MBZ] OT: measuring Power Factor

2010-01-25 Thread Craig McCluskey
On Mon, 25 Jan 2010 11:02:19 -0600 Dieselhead 126die...@gmail.com wrote:

 I can get amps with a clamp-on, volts with a voltmeter.  Is there any 
 way to determine watts without rewiring a wattmeter inline? 

Shut off other loads, record your house's kilowatt-hour meter's reading,
run your load for awhile, record the meter's reading again, subtract the
two and divide by the time.


 If I have to rewire, then I could use two kill-a-watts with leads and 
 clamps.

That will probably work.


Craig

___
http://www.okiebenz.com
For new and used parts go to www.okiebenz.com
To search list archives http://www.okiebenz.com/archive/

To Unsubscribe or change delivery options go to:
http://okiebenz.com/mailman/listinfo/mercedes_okiebenz.com


Re: [MBZ] OT: measuring Power Factor

2010-01-25 Thread Jim Cathey
Can you put on an ampprobe (clamp-on) to measure amps and measure 
volts with a different meter (simultaneously) and use that data to do 
the calculation?


No.  That gives you volt-amps, which is watts only if you assume
a 1.0 power factor.  You have to do the multiplication on a
cycle-by-cycle basis, using the instantaneous value of one
datum at the peak instant of the other, in order to calculate
the true wattage (and power factor).  Or average them through
the cycle, for true RMS.

It's tricky, in other words.  That's what's so slick about
the Kill-a-Watt, it's quite cheap for something that actually
does this.

If you can get a dual-trace oscilloscope picture of both the
voltage and amperage waveforms, superimposed, you can calculate
the degrees of shift between the peaks and get a power factor
that way.  That assumes a fairly sine-like current waveform,
which is no guarantee.  You multiply this power factor by the
volt-amp reading to get watts.

-- Jim



___
http://www.okiebenz.com
For new and used parts go to www.okiebenz.com
To search list archives http://www.okiebenz.com/archive/

To Unsubscribe or change delivery options go to:
http://okiebenz.com/mailman/listinfo/mercedes_okiebenz.com


Re: [MBZ] OT: measuring Power Factor

2010-01-25 Thread Jim Cathey
What I want to do is determine PF at hardwired 240 1 phase devices, 
such as central air cond. compressor/condensor units.  The Kill-A-Watt 
is great for 110v devices.  Is there any low-cost way to do that?


I designed a wattmeter circuit for the big generator, but I
haven't built it yet.  You could prototype it for me!  It might
not work, of course...

-- Jim



___
http://www.okiebenz.com
For new and used parts go to www.okiebenz.com
To search list archives http://www.okiebenz.com/archive/

To Unsubscribe or change delivery options go to:
http://okiebenz.com/mailman/listinfo/mercedes_okiebenz.com


[MBZ] OT: measuring Power Factor

2010-01-24 Thread Dieselhead

For all you EE types out there

With all these fancy digital handheld meters out there, is there a 
clamp-on meter that will give you a power factor while clamped on a 
wire?


Hopefully you don't have to buy a $5000-8000 fluke to do this.  The 
Kill-A-Watt does it on 120v for $25-50 if you have a 120 v motor you 
can plug in to it.  Thanks!


___
http://www.okiebenz.com
For new and used parts go to www.okiebenz.com
To search list archives http://www.okiebenz.com/archive/

To Unsubscribe or change delivery options go to:
http://okiebenz.com/mailman/listinfo/mercedes_okiebenz.com


[MBZ] OT: measuring Power Factor

2010-01-24 Thread Loren Faeth

For all you EE types out there

With all these fancy digital handheld meters out there, is there a 
clamp-on meter that will give you a power factor while clamped on a 
wire?


Hopefully you don't have to buy a $5000-8000 fluke to do this.  The 
Kill-A-Watt does it on 120v for $25-50 if you have a 120 v motor you 
can plug in to it.  Thanks!


___
http://www.okiebenz.com
For new and used parts go to www.okiebenz.com
To search list archives http://www.okiebenz.com/archive/

To Unsubscribe or change delivery options go to:
http://okiebenz.com/mailman/listinfo/mercedes_okiebenz.com


Re: [MBZ] OT: measuring Power Factor

2010-01-24 Thread Jim Cathey
With all these fancy digital handheld meters out there, is there a 
clamp-on meter that will give you a power factor while clamped on a 
wire?


No.  You cannot measure power factor without simultaneously
measuring both instantaneous current and voltage.  No clamp-on
measures any kind of voltage without a metallic connection.
The kill-a-watt is the only inexpensive tool I know of that
measures power factor.

-- Jim