[RE-wrenches] Fwd: AC Coupled

2012-02-18 Thread Larry Brown

 
 Wrenches,
 
 I have a client with a 4.6 kw grid tied system using a Sunny Boy 6000 
 inverter.  We have AC Coupled to that system with 2 Sunny Island 5048's and 
 8-Concorde SunXtender 3050T 6 volt batteries in series feeding an essential 
 load/critical load sub panel.  The wiring to the sub panel from the Sunny 
 Islands is #6, the max wire size that can be used in the AC 1 and AC 2, in 
 and out, of the Sunny Islands.  The 2 pole breaker at the sub panel is 70 
 amps ( 56 amps feed through current x 1.25 = 70 amps ).
 This allow the 4.6 kw solar system and the Sunny Boy 6000 to act as a micro 
 grid and charge the batteries and support the loads in the SubPanel when the 
 grid is down and still be isolated from the main service panel and the grid. 
 
 We have moved several loads from the main 200 amp service panel into the 
 essential load/critical load panel, the well pump, the refrigerator, the 
 circulator/boiler controls for the propane fired radiant heating system and 
 some lights and communication circuits.  
 
 The main 200 amp main service panel has an integrated manual transfer switch 
 that has allowed them to fire up the gas powered Honda generator and run all 
 of the loads when the grid was down before we installed any systems to their 
 home.  They would like to be able to continue to do this in an extended power 
 outage.
 
 So here is the question?  In a power outage, if they fire up the generator 
 and move the manual transfer switch in the Main Service Panel to generator, 
 the Sunny Islands will see this generator power coming from the Main Service 
 Panel and switch from Back Up Mode to Pass Through Mode.  The Sunny Boy 6000 
 will send any excess power not used by the loads to the the generator (as if 
 it was a net metering arrangement ) believing it is the grid. This would 
 probably destroy the generator or some other disasterous scenario.  
 
 So how can the generator feeding the Main Service panel be isolated from the 
 Sunny Islands and Sunny Boy feeding the SubPanel as a micro grid in a power 
 outage and still provide power to the loads that are in the Main Service 
 Panel?
 
 Thank you for the collective wisdom and knowledge that this group has 
 acquired from years in the trenches making it all happen.
 
 Larry
 
 Larry Brown
 Sun Mountain
 NABCEP Certified PV Installer
 
 

___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



[RE-wrenches] Interstate L-16 vs Trojan L-16REB

2012-02-18 Thread Doug Wells
Maverick,

But you would think after 20 years, inverter manufacturers would make some 
software similar to generator cycling to handle this cycling issue. 

I believe that the XW Inverters have this ability in sell mode.  There is 
traditional sell voltage.  And then there is a setting that puts the batteries 
through a traditional bulk cycle while still selling back any excess energy.  
The next question would be, is this better for battery longevity.  Seems like a 
hybrid of the two would be ideal.

Doug Wells
The Solar Specialists
Morrisville, VT 05661
(p) 802-223-7014
(c) 802-498-5856
www.thesolarspecialists.com

___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] Fwd: AC Coupled

2012-02-18 Thread Richard L Ratico
Larry,

Would it not be better to connect the Honda directly to the the Sunny Islands?
Use a manual transfer switch to choose between the grid and the Honda. Then, in
an extended outage, your client could charge the batteries with it and turn the
darn thing off once in awhile. Maybe you could transfer more of the loads to the
backup panel. How big is the Honda? I don't know of one bigger than 10KW. That's
too small to support a busy 200 Amp panel anyway.

Dick Ratico
Solarwind Electric


--- You wrote:
 
 Wrenches,
 
 I have a client with a 4.6 kw grid tied system using a Sunny Boy 6000
inverter.  We have AC Coupled to that system with 2 Sunny Island 5048's and
8-Concorde SunXtender 3050T 6 volt batteries in series feeding an essential
load/critical load sub panel.  The wiring to the sub panel from the Sunny
Islands is #6, the max wire size that can be used in the AC 1 and AC 2, in and
out, of the Sunny Islands.  The 2 pole breaker at the sub panel is 70 amps ( 56
amps feed through current x 1.25 = 70 amps ).
 This allow the 4.6 kw solar system and the Sunny Boy 6000 to act as a micro
grid and charge the batteries and support the loads in the SubPanel when the
grid is down and still be isolated from the main service panel and the grid. 
 
 We have moved several loads from the main 200 amp service panel into the
essential load/critical load panel, the well pump, the refrigerator, the
circulator/boiler controls for the propane fired radiant heating system and some
lights and communication circuits.  
 
 The main 200 amp main service panel has an integrated manual transfer switch
that has allowed them to fire up the gas powered Honda generator and run all of
the loads when the grid was down before we installed any systems to their home. 
They would like to be able to continue to do this in an extended power outage.
 
 So here is the question?  In a power outage, if they fire up the generator and
move the manual transfer switch in the Main Service Panel to generator, the
Sunny Islands will see this generator power coming from the Main Service Panel
and switch from Back Up Mode to Pass Through Mode.  The Sunny Boy 6000 will send
any excess power not used by the loads to the the generator (as if it was a net
metering arrangement ) believing it is the grid. This would probably destroy the
generator or some other disasterous scenario.  
 
 So how can the generator feeding the Main Service panel be isolated from the
Sunny Islands and Sunny Boy feeding the SubPanel as a micro grid in a power
outage and still provide power to the loads that are in the Main Service Panel?
 
 Thank you for the collective wisdom and knowledge that this group has acquired
from years in the trenches making it all happen.
 
 Larry
 
 Larry Brown
 Sun Mountain
 NABCEP Certified PV Installer
 
--- end of quote ---
___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] Fwd: AC Coupled

2012-02-18 Thread Kent Osterberg

Larry,

It sounds like the customer can power all loads with the generator and 
the non-critical load may even be the motivation for starting the 
generator? How about a relay that opens the SunnyBoy output or the Sunny 
Island input when the generator runs?


Kent Osterberg
Blue Mountain Solar, Inc.
www.bluemountainsolar.com
t: 541-568-4882


On 2/18/2012 6:03 AM, Larry Brown wrote:

Wrenches,

I have a client with a 4.6 kw grid tied system using a Sunny Boy 6000 inverter. 
 We have AC Coupled to that system with 2 Sunny Island 5048's and 8-Concorde 
SunXtender 3050T 6 volt batteries in series feeding an essential load/critical 
load sub panel.  The wiring to the sub panel from the Sunny Islands is #6, the 
max wire size that can be used in the AC 1 and AC 2, in and out, of the Sunny 
Islands.  The 2 pole breaker at the sub panel is 70 amps ( 56 amps feed through 
current x 1.25 = 70 amps ).
This allow the 4.6 kw solar system and the Sunny Boy 6000 to act as a micro 
grid and charge the batteries and support the loads in the SubPanel when the 
grid is down and still be isolated from the main service panel and the grid.

We have moved several loads from the main 200 amp service panel into the 
essential load/critical load panel, the well pump, the refrigerator, the 
circulator/boiler controls for the propane fired radiant heating system and 
some lights and communication circuits.

The main 200 amp main service panel has an integrated manual transfer switch 
that has allowed them to fire up the gas powered Honda generator and run all of 
the loads when the grid was down before we installed any systems to their home. 
 They would like to be able to continue to do this in an extended power outage.

So here is the question?  In a power outage, if they fire up the generator and 
move the manual transfer switch in the Main Service Panel to generator, the 
Sunny Islands will see this generator power coming from the Main Service Panel 
and switch from Back Up Mode to Pass Through Mode.  The Sunny Boy 6000 will 
send any excess power not used by the loads to the the generator (as if it was 
a net metering arrangement ) believing it is the grid. This would probably 
destroy the generator or some other disasterous scenario.

So how can the generator feeding the Main Service panel be isolated from the 
Sunny Islands and Sunny Boy feeding the SubPanel as a micro grid in a power 
outage and still provide power to the loads that are in the Main Service Panel?

Thank you for the collective wisdom and knowledge that this group has acquired 
from years in the trenches making it all happen.

Larry

Larry Brown
Sun Mountain
NABCEP Certified PV Installer



___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] AC Coupled

2012-02-18 Thread Hilton Dier III

Larry,

I have run into similar situations. The simplest thing is to wire the 
Sunny Boy 6000 into a breaker in a small dedicated box on the *grid 
side* of the transfer switch.


Grid present: feeds back normally
Grid absent: interacts with Sunny Islands
Grid absent, genset on: Sunny Boy cut off from the system

I'd assume that they wouldn't lose much, if any production from the PV, 
since they'd probably be running the genset for short runs, at night, or 
in cloudy weather.


Best,

Hilton


Wrenches,

I have a client with a 4.6 kw grid tied system using a Sunny Boy 6000 inverter. 
 We have AC Coupled to that system with 2 Sunny Island 5048's and 8-Concorde 
SunXtender 3050T 6 volt batteries in series feeding an essential load/critical 
load sub panel.  The wiring to the sub panel from the Sunny Islands is #6, the 
max wire size that can be used in the AC 1 and AC 2, in and out, of the Sunny 
Islands.  The 2 pole breaker at the sub panel is 70 amps ( 56 amps feed through 
current x 1.25 = 70 amps ).
This allow the 4.6 kw solar system and the Sunny Boy 6000 to act as a micro 
grid and charge the batteries and support the loads in the SubPanel when the 
grid is down and still be isolated from the main service panel and the grid.

We have moved several loads from the main 200 amp service panel into the 
essential load/critical load panel, the well pump, the refrigerator, the 
circulator/boiler controls for the propane fired radiant heating system and 
some lights and communication circuits.

The main 200 amp main service panel has an integrated manual transfer switch 
that has allowed them to fire up the gas powered Honda generator and run all of 
the loads when the grid was down before we installed any systems to their home. 
 They would like to be able to continue to do this in an extended power outage.

So here is the question?  In a power outage, if they fire up the generator and 
move the manual transfer switch in the Main Service Panel to generator, the 
Sunny Islands will see this generator power coming from the Main Service Panel 
and switch from Back Up Mode to Pass Through Mode.  The Sunny Boy 6000 will 
send any excess power not used by the loads to the the generator (as if it was 
a net metering arrangement ) believing it is the grid. This would probably 
destroy the generator or some other disasterous scenario.

So how can the generator feeding the Main Service panel be isolated from the 
Sunny Islands and Sunny Boy feeding the SubPanel as a micro grid in a power 
outage and still provide power to the loads that are in the Main Service Panel?

Thank you for the collective wisdom and knowledge that this group has acquired 
from years in the trenches making it all happen.

Larry



--
Hilton Dier III
Renewable Energy Design
Partner, Solar Gain LLC

___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



[RE-wrenches] cycling flooded batteries is not necessary

2012-02-18 Thread toddcory

to reiterate wrenches:
 
two battery manufacturers (surrette  trojan) have both stated there is NO NEED 
to cycle floating, flooded lead-antimony batteries. i have heard this urban 
legend for some time and it is nice to finally have it put to rest as an 
incorrect myth.
 
todd
 
 
 
 
On Saturday, February 18, 2012 7:04am, Doug Wells 
dwe...@thesolarspecialists.com said:



 Maverick,
 
 But you would think after 20 years, inverter manufacturers would make some
 software similar to generator cycling to handle this cycling issue. 
 
 I believe that the XW Inverters have this ability in sell mode.  There is
 traditional sell voltage.  And then there is a setting that puts the batteries
 through a traditional bulk cycle while still selling back any excess energy.
 The next question would be, is this better for battery longevity.  Seems like 
 a
 hybrid of the two would be ideal.
 
 Doug Wells
 The Solar Specialists
 Morrisville, VT 05661
 (p) 802-223-7014
 (c) 802-498-5856
 www.thesolarspecialists.com
 
 ___
 List sponsored by Home Power magazine
 
 List Address: RE-wrenches@lists.re-wrenches.org
 
 Options  settings:
 http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
 
 List-Archive: 
 http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
 
 List rules  etiquette:
 www.re-wrenches.org/etiquette.htm
 
 Check out participant bios:
 www.members.re-wrenches.org
 



Sent from Finest Planet WebMail.
___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] cycling flooded batteries is not necessary

2012-02-18 Thread Dan Fink
This thread has been quite riveting for me over the last few days!

Over the last couple decades in my remote mostly off-grid area here.we
have seen quite a passel (perhaps the proper group term might instead
be a thud,  deadweight or boat anchor) of different battery
types.

My personal observations (and my aching back) say:

~Cycling flooded lead acid batteries when new, either PbSb or PbCa, to
bring them up to full capacity is an urban legend and is actually
deleterious to battery life; not necessarily so with other more exotic
battery types that PV folks don't use and can't afford yet (lithium
ion etc) -- all a new flooded battery bank needs is water and a proper
initial equalization cycle;
~PbCa batteries have the amazing property of using very little water.
The ones we've used (CD) also have a very large sludge pit at the
bottom, and clear plastic sides so you can watch it build up. Woe to
the homeowner that replaces Ca with Sb and doesn't follow the NEW
maintenance guidelines for Sb (water them only every year or two with
Ca, not so with Sb)
~The difference in cycle life between 2 volt batteries and 6 volt is
huge. Just the difference in sludge pit capacity per amp-hour is big,
maybe that's part of it. On that note;
~L-16s have only one advantage over T105s IMHO, other than portability
for the 105s - you don't need as many parallel strings to get the same
capacity, and parallel strings cause all kinds of unforeseen problems
creeping up on the unwary owner;
~And, if you need a huge battery bank, 2 volt cells are the way to go.
For all of the above reasons. And if you are paying for a big bank of
2-volt cells to make 48 volts, you can probably afford a system
maintenance contract too.
~If the system is owner-maintained and not installer-maintained, avoid
AGMs gels etc at all costs. Most folks just don't understand. If we
can do all the system programming, and lock the owner's know-it-all
buddies, cousins, inlaws and outlaws out of the system, AGMs are
great. If some unauthorized know-it-all tweaks a controller setting
somewhere for their buddy over a few beers, watch out!

-- 
Dan Fink,
Executive Director;
Otherpower
Buckville Energy Consulting
Buckville Publications LLC
NABCEP / IREC accredited Continuing Education Providers
970.672.4342 (voicemail)

On Sat, Feb 18, 2012 at 2:37 PM,  toddc...@finestplanet.com wrote:
 to reiterate wrenches:

 two battery manufacturers (surrette  trojan) have both stated there is NO
 NEED to cycle floating, flooded lead-antimony batteries. i have heard this
 urban legend for some time and it is nice to finally have it put to rest as
 an incorrect myth.

 todd
___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] cycling flooded batteries is not necessary

2012-02-18 Thread Darryl Thayer
But they say that periodic  equalazation is, the is this same as one good hard 
cycle.  So it could be said that One cycle a month is all a lead antinmony 
battery needs.  and of course water replacement, and sp gr testing to be sure 
the equalization was successful and when the battery gets old and the self 
discharge gets higher you may have to cycle more like once a week.  
 
DT.  
 


 From: toddc...@finestplanet.com toddc...@finestplanet.com
To: RE-wrenches re-wrenches@lists.re-wrenches.org 
Sent: Saturday, February 18, 2012 3:37 PM
Subject: [RE-wrenches] cycling flooded batteries is not necessary
  

to reiterate wrenches: 
  
two battery manufacturers (surrette  trojan) have both stated there is NO NEED 
to cycle floating, flooded lead-antimony batteries. i have heard this urban 
legend for some time and it is nice to finally have it put to rest as an 
incorrect myth. 
  
todd 
  
  
  
  
On Saturday, February 18, 2012 7:04am, Doug Wells 
dwe...@thesolarspecialists.com said:

 
 Maverick,
 
 But you would think after 20 years, inverter manufacturers would make some
 software similar to generator cycling to handle this cycling issue. 
 
 I believe that the XW Inverters have this ability in sell mode.  There is
 traditional sell voltage.  And then there is a setting that puts the batteries
 through a traditional bulk cycle while still selling back any excess energy.
 The next question would be, is this better for battery longevity.  Seems like 
 a
 hybrid of the two would be ideal.
 
 Doug Wells
 The Solar Specialists
 Morrisville, VT 05661
 (p) 802-223-7014
 (c) 802-498-5856
 www.thesolarspecialists.com
 
 ___
 List sponsored by Home Power magazine
 
 List Address: RE-wrenches@lists.re-wrenches.org
 
 Options  settings:
 http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
 
 List-Archive: 
 http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
 
 List rules  etiquette:
 www.re-wrenches.org/etiquette.htm
 
 Check out participant bios:
 www.members.re-wrenches.org
 
 


Sent from Finest Planet WebMail.

___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] AC Coupled

2012-02-18 Thread Darryl Thayer
If it was connected such that the gen start would disable the DGI inverter and 
any manuel start would use the gen start module the syn would happen.
 
Darryl
 


 From: Hilton Dier III hiltond...@gmail.com
To: RE-wrenches@lists.re-wrenches.org 
Sent: Saturday, February 18, 2012 3:12 PM
Subject: Re: [RE-wrenches] AC Coupled
  

Larry,

I have run into similar situations. The simplest thing is to wire
  the Sunny Boy 6000 into a breaker in a small dedicated box on the
  *grid side* of the transfer switch.

Grid present: feeds back normally
Grid absent: interacts with Sunny Islands
Grid absent, genset on: Sunny Boy cut off from the system

I'd assume that they wouldn't lose much, if any production from
  the PV, since they'd probably be running the genset for short
  runs, at night, or in cloudy weather.

Best,

Hilton


 
Wrenches, I have a client with a 4.6 kw grid tied system using a Sunny Boy 6000 
inverter.  We have AC Coupled to that system with 2 Sunny Island 5048's and 
8-Concorde SunXtender 3050T 6 volt batteries in series feeding an essential 
load/critical load sub panel.  The wiring to the sub panel from the Sunny 
Islands is #6, the max wire size that can be used in the AC 1 and AC 2, in and 
out, of the Sunny Islands.  The 2 pole breaker at the sub panel is 70 amps ( 56 
amps feed through current x 1.25 = 70 amps ).
This allow the 4.6 kw solar system and the Sunny Boy 6000 to act as a micro 
grid and charge the batteries and support the loads in the SubPanel when the 
grid is down and still be isolated from the main service panel and the grid.  
We have moved several loads from the main 200 amp service panel into the 
essential load/critical load panel, the well pump, the refrigerator, the 
circulator/boiler controls for the propane fired radiant heating system and 
some lights and communication circuits.   The main 200 amp main service panel 
has an integrated manual transfer switch that has allowed them to fire up the 
gas powered Honda generator and run all of the loads when the grid was down 
before we installed any systems to their home.  They would like to be able to 
continue to do this in an extended power outage. So here is the question?  In a 
power outage, if they fire up the generator and move the manual transfer switch 
in the Main Service Panel to generator, the
 Sunny Islands will see this generator power coming from the Main Service Panel 
and switch from Back Up Mode to Pass Through Mode.  The Sunny Boy 6000 will 
send any excess power not used by the loads to the the generator (as if it was 
a net metering arrangement ) believing it is the grid. This would probably 
destroy the generator or some other disasterous scenario.   So how can the 
generator feeding the Main Service panel be isolated from the Sunny Islands and 
Sunny Boy feeding the SubPanel as a micro grid in a power outage and still 
provide power to the loads that are in the Main Service Panel? Thank you for 
the collective wisdom and knowledge that this group has acquired from years in 
the trenches making it all happen. Larry  

 
-- 
Hilton Dier III
Renewable Energy Design
Partner, Solar Gain LLC   
___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



[RE-wrenches] Net-Metering Vs. Net-Billing

2012-02-18 Thread Comet Systems
I've been invited to take part in stake holder consultation meetings with a
consultancy employed  by the Government to make recommendations on
renewable energy legislation for Anguilla. In the first of two meetings,
they announced their intention to recommend a net-billing arrangement for
grid-tied residential solar systems on the basis of offering the consumer
less-than-avoided-cost. I was vocally opposed to anything other than
net-metering at retail as I believe it cannot work and will fail and I have
written a blog entry describing the issues.
http://caribbeanrenewable.blogspot.com/

As I have another meeting with them, I would like to prepare some examples
of how this is a failed system. If anyone can offer some information I can
use, or would like to critic my post, I would like to hear from you.
As background, this is a tropical island with great sunshine, electricity
at 43c/Kwh, and no incentives for solar installation.

-- 
Chris Mason
Skype: netconcepts
___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org