Re: [RE-wrenches] Trojan L-16s

2013-07-23 Thread Tom Duffy
Jay

Sorry I should have explained that too... Absorb starts off at around 50% of 
the available amps and tapers down to around 20% So I divided 20 by 50 = .40 
there's a 5% loss factor hence .42

Tom Duffy
Senior Solar Design Engineer

Toll Free 888-895-8179
t...@thesolar.biz
Customer Service and Accounting 888-895-6810 
Grid tie sales 888-895-7847 
Off Grid sales 888-895-4058 
Other Product Sales 888-895-9612 
Central America Sales (Panama) 507-6-126-1253 
Shipping and Receiving 888-895-6497 
Tech Support 888-895-8179
SKYPE:  thesolarbiz

-Original Message-
From: re-wrenches-boun...@lists.re-wrenches.org 
[mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf Of Jay Peltz
Sent: Monday, July 22, 2013 1:27 PM
To: RE-wrenches
Subject: Re: [RE-wrenches] Trojan L-16s

Hi Tom

Where did you get the .42 from?

Jay
Peltz power 

Sent from my iPhone

On Jul 22, 2013, at 11:04 AM, Tom Duffy t...@thesolar.biz wrote:

 Drake
 
 Keep the absorb rate recommended for the CC. The trimetric strays over 
 time and will become accurate again when you overcharge (equalize)
 
 The math:
 Amp hours of battery @ 20 hour rate divided by max charge available in 
 amps, from whatever you using to charge (solar or inverter/charger) 
 Times .42 = absorb time in hours
 
 i.e. your system 980 watts,  980 divided by 28.8 (average volts) = 34 
 amps max charge
 370 AH divided by 34 = 10.88 X .42 = 4.57 round up to 4.6 hours absorb 
 time for the CC Your inverter VFX3524 max charge 85 amps... 370 
 divided by 85 = 4.35 X .42 = 1.82 absorb time for the inverter/charger 
 when running generator
 
 Tom Duffy
 Senior Solar Design Engineer
 
 Toll Free 888-895-8179
 t...@thesolar.biz
 Customer Service and Accounting 888-895-6810 Grid tie sales 
 888-895-7847 Off Grid sales 888-895-4058 Other Product Sales 
 888-895-9612 Central America Sales (Panama) 507-6-126-1253 Shipping 
 and Receiving 888-895-6497 Tech Support 888-895-8179
 SKYPE:  thesolarbiz
 
 -Original Message-
 From: re-wrenches-boun...@lists.re-wrenches.org 
 [mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf Of Drake
 Sent: Monday, July 22, 2013 10:04 AM
 To: RE-wrenches
 Subject: Re: [RE-wrenches] Trojan L-16s
 
 Hi Larry,
 
 I will bump up the absorb voltage to 29.6 V. How long do you think the bank 
 should stay in absorb at that rate?  The bank now seems healthy, with the bad 
 battery replaced.  It does accept charge, without going high prematurely.  
 The max charge rate from the array is around C/10. The system can also be 
 fast charged from a Honda 6500 inverter generator through the Outback 3524 
 VFX.
 
 We have a Trimetric meter on the system. The discrepancy between the percent 
 charge and the voltage is what demonstrated that we had a problem.
 
 Thanks,
 
 Drake
 
 
 
 At 09:30 PM 7/19/2013, you wrote:
 Hi Drake,
 
 It always concerns me when I hear that a battery bank reaches absorb 
 setting very quickly. It typically means one of two things: very few 
 AH were removed from the bank; the battery bank has sulfated cells 
 due to chronic undercharging. Far too often I find the latter to be true.
 
 Healthy batteries will accept current and hold the charge voltage 
 down with a fairly linear, slow climb to absorption voltage. Sulfated 
 batteries do not accept current well which allows voltage to climb 
 rapidly as the battery presents little load on the charging system. 
 I'm not sure how this plays into your original post about a bad cell 
 but it seemed worth mentioning.
 
 My opinion is to aggressively charge, by using higher voltage, large 
 flooded batteries. This is especially true when the PV system is 
 moderate or undersized. 29.6 volts is what Trojan recommends. You can 
 go as high as 32 volts on the L-16's but make sure the temperature 
 compensation is installed properly and working. You will use more water.
 
 One last comment, I highly recommend that ALL off grid systems have a 
 battery capacity monitor installed. It's kind of like flying an 
 airplane without a fuel gauge...it might not end in disaster.
 
 Larry Crutcher
 Starlight Solar Power Systems
 
 
 
 On Jul 18, 2013, at 1:11 PM, Drake
 drake.chamber...@redwoodalliance.org wrote:
 
 Tom,
 
 The batteries usually reach absorb voltage shortly after the sun hits 
 the array. The reason the bank wasn't working correctly is that one 
 cell was dead in one of the batteries.
 
 I could increase the absorb time to 4.6 hours and the voltage to 
 29.6, especially since the bank has a new battery. That is longer and 
 higher than I'd previously heard recommended.
 What would be the effect on water
 consumption?  How did you calculate the absorb time?
 
 Thanks,
 
 
 Drake
 
 ___
 List sponsored by Home Power magazine
 
 List Address: RE-wrenches@lists.re-wrenches.org
 
 Change email address  settings:
 http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
 
 List-Archive: 
 

Re: [RE-wrenches] RE-wrenches Digest, Vol 6, Issue 276

2013-07-23 Thread Bill Loesch


Hi Corey,

3M makes VHB (Very High Bond) glue used extensively in the automotive 
industry to attach trim to body panels without fasteners. If the surface 
is irregular you might want to use a double sided VHB tape with a thin 
layer of foam between the two glue surfaces. I would suggest contacting 
3M customer service/tech support to make sure all the requirements of 
your application are met by the multitude of 3M product offerings.


Good luck,

Bill Loesch
Solar 1 - Saint Louis Solar

On 22-Jul-13 11:46 AM, Corey Shalanski wrote:
Our local inspector is allowing sticker-type labels, so we have begun 
printing our own with a laser printer. We found weatherproof sheets 
available in a variety of size configurations: 
http://www.onlinelabels.com/material_polyester_laser_labels.htm


After about six months of testing they seem to be adhering alright to 
most surfaces, but we can't seem to get anything - including trophy 
plaques - to stick to SMA inverter cabinets (or any surface with a 
grainy texture) without using some sort of super glue. I'd be 
interested to hear from anyone who's found a successful method or 
product for this application.


--
Corey Shalanski
Joule Energy
New Orleans, LA


On Wed, Jul 17, 2013 at 2:50 PM, Bob Ellison reelli...@gmail.com 
mailto:reelli...@gmail.com wrote:



If you're using a P touch there are labels with adhesives
available that are non-removable and stick on real well
The regular labels will unpeel at some point
The nonremovable ones don't unpeel their labels and hold their
colors very well especially inside a box

Opening a box and finding five labels laying on the bottom isn't
pleasant!



___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Change email address  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



No virus found in this message.
Checked by AVG - www.avg.com http://www.avg.com
Version: 2013.0.3349 / Virus Database: 3204/6511 - Release Date: 07/22/13






-
No virus found in this message.
Checked by AVG - www.avg.com
Version: 2013.0.3349 / Virus Database: 3204/6513 - Release Date: 07/23/13___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Change email address  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



[RE-wrenches] Request for efficient hydronics links

2013-07-23 Thread Allan Sindelar

  
  
Wrenches, 
Can anyone provide links to online articles or resources on reducing
the electrical consumption of a hydronic boiler-based residential
heating system, in order to make it more electrically efficient for
an off grid home? Articles or links about efficient circulator
pumps, zone valves, low-idle controls, plumbing designs, etc. would
be quite useful. I would like to provide such links or articles to a
customer and her designer/builder and hydronic subcontractor.

Thank you,
Allan
-- 
  
  
  
  
  
  
  
  
Allan Sindelar
  al...@positiveenergysolar.com
  NABCEP Certified PV
Installation Professional 
NABCEP Certified Technical Sales Professional
New Mexico EE98J Journeyman Electrician
Founder and Chief Technology Officer
Positive Energy, Inc., a Certified B CorporationTM
3209 Richards Lane
Santa Fe, New Mexico 87507
505 424-1112 office 780-2738 cell
www.positiveenergysolar.com

  

  

___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Change email address  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] Tri-Star MPPT

2013-07-23 Thread Brian Teitelbaum
William,

What does the PV array consist of? What size and type, and how many, modules?

Which TriStar? 45 or 60A?

What controller did she have before the upgrade?

The high charging voltage might be a sign of sulfation. Depending on her load 
profile, that 8A charge rate might have caused chronic undercharging. In a 5 
peak sun-hour location, that's only 40Ah/day of charging capacity.

Brian Teitelbaum
AEE Solar

From: re-wrenches-boun...@lists.re-wrenches.org 
[mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf Of William Miller
Sent: Tuesday, July 23, 2013 1:13 PM
To: RE-wrenches
Subject: [RE-wrenches] Tri-Star MPPT

Friends:

I have a customer with a new Tristar MPPT controller.  The customer has some 
older L-16 batteries mixed with new and she thinks the controller has damaged 
her batteries.  I am trying to convince her that the batteries were already 
damaged and mixing old with new is a bad idea.

I removed the worst batteries from the array, leaving one string of older 
batteries with reasonable SG readings.  The CC still acts strangely:  When 
programmed to charge the L-16 batteries, the battery voltage shoots up to 30.2 
volts and the batteries boil a lot.  The green light on the controller blinks 
at variable rates, at one moment fast, the next slow, the next solid.

I believe the client started with bad batteries, 6 are 4 years old, 2 are 1 
year old.  She is convinced that the CC damaged her batteries.  She replaced 
panels and CC recently, installing the Tristar.  I believe the old PV system 
charged at such a slow rate (8 amps) that the battery deficiency was not 
apparent.  The higher charging rate has emphasized the problem.

Any one have any thing to add to my theory?

Thanks in advance.

William Miller



[cid:image002.jpg@01CE87A8.28D5F890]
17395 Oak Rd. Atascadero, CA 93422
www.millersolar.comhttp://www.millersolar.com/
805-438-5600 voice*
*Note: above number replaces cell number

inline: image002.jpg___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Change email address  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] Tri-Star MPPT

2013-07-23 Thread William
Brian:

I don't have the PV details handy but I will provide them. 

Question:  will a sulfated cell exhibit a SG of 1.26?  I thought a sulfated 
cell locked the acid onto the plates, minimizing the SG readings below that of 
a healthy cell. 1.26 is a relatively high reading. 

William

On Jul 23, 2013, at 1:28 PM, Brian Teitelbaum bteitelb...@aeesolar.com wrote:

 William,
  
 What does the PV array consist of? What size and type, and how many, modules?
  
 Which TriStar? 45 or 60A?
  
 What controller did she have before the upgrade?
  
 The high charging voltage might be a sign of sulfation. Depending on her load 
 profile, that 8A charge rate might have caused chronic undercharging. In a 5 
 peak sun-hour location, that’s only 40Ah/day of charging capacity.
  
 Brian Teitelbaum
 AEE Solar
  
 From: re-wrenches-boun...@lists.re-wrenches.org 
 [mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf Of William Miller
 Sent: Tuesday, July 23, 2013 1:13 PM
 To: RE-wrenches
 Subject: [RE-wrenches] Tri-Star MPPT
  
 Friends:
  
 I have a customer with a new Tristar MPPT controller.  The customer has some 
 older L-16 batteries mixed with new and she thinks the controller has damaged 
 her batteries.  I am trying to convince her that the batteries were already 
 damaged and mixing old with new is a bad idea.
  
 I removed the worst batteries from the array, leaving one string of older 
 batteries with reasonable SG readings.  The CC still acts strangely:  When 
 programmed to charge the L-16 batteries, the battery voltage shoots up to 
 30.2 volts and the batteries boil a lot.  The green light on the controller 
 blinks at variable rates, at one moment fast, the next slow, the next solid.
  
 I believe the client started with bad batteries, 6 are 4 years old, 2 are 1 
 year old.  She is convinced that the CC damaged her batteries.  She replaced 
 panels and CC recently, installing the Tristar.  I believe the old PV system 
 charged at such a slow rate (8 amps) that the battery deficiency was not 
 apparent.  The higher charging rate has emphasized the problem.
  
 Any one have any thing to add to my theory?
  
 Thanks in advance.
  
 William Miller
  
  
  
 image002.jpg
 17395 Oak Rd. Atascadero, CA 93422
 www.millersolar.com
 805-438-5600 voice*
 *Note: above number replaces cell number
  
 ___
 List sponsored by Home Power magazine
 
 List Address: RE-wrenches@lists.re-wrenches.org
 
 Change email address  settings:
 http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
 
 List-Archive: 
 http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
 
 List rules  etiquette:
 www.re-wrenches.org/etiquette.htm
 
 Check out participant bios:
 www.members.re-wrenches.org
 
___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Change email address  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] SMA Secure Power Supply

2013-07-23 Thread Jesse Dahl
I know the MREA in WI has one installed on site, but not sure who installed it. 

Do they have a representative on the list?

Jesse  

Sent from my iPhone

On Jul 22, 2013, at 6:18 PM, wire...@gmail.com wrote:

 If we have another long outage here in CT and we seem to have one every year 
 now, I don't want to have to explain to my customers why I didn't use this 
 inverter. 
 Sent from my Verizon Wireless BlackBerry
 
 -Original Message-
 From: Gary Willett g...@icarussolarservices.com
 Sender: re-wrenches-boun...@lists.re-wrenches.orgDate: Mon, 22 Jul 2013 
 17:33:26 
 To: re-wrenches@lists.re-wrenches.org
 Reply-To: RE-wrenches re-wrenches@lists.re-wrenches.org
 Subject: Re: [RE-wrenches] SMA Secure Power Supply
 
 ___
 List sponsored by Home Power magazine
 
 List Address: RE-wrenches@lists.re-wrenches.org
 
 Change email address  settings:
 http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
 
 List-Archive: 
 http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
 
 List rules  etiquette:
 www.re-wrenches.org/etiquette.htm
 
 Check out participant bios:
 www.members.re-wrenches.org
 
 
 
 ___
 List sponsored by Home Power magazine
 
 List Address: RE-wrenches@lists.re-wrenches.org
 
 Change email address  settings:
 http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
 
 List-Archive: 
 http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
 
 List rules  etiquette:
 www.re-wrenches.org/etiquette.htm
 
 Check out participant bios:
 www.members.re-wrenches.org
 
___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Change email address  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] Tri-Star MPPT

2013-07-23 Thread Ray Walters
Did you look for dead cells?   I've seen many L 16 sets  (including my 
own) only last 4-1/2 years, so that set was already almost done.  If she 
started mixing new batteries in before, she knew she already had a 
problem.  Did this system change from 12 v to 24 v?  The rule of thumb 
for eons  (or at least the long history of lead acid batteries) is that 
a mixed set of new and old batteries will only last as long as the 
oldest battery.   The new batteries will be chronically undercharged, 
while the old ones will be chronically over charged.
My guess is the higher charging rate available  caused some already 
heavily sulfated cells to go ahead and short out.
It's like giving a gasping man some oxygen, and then he goes into 
cardiac arrest.  You did what you could, but those batteries were on 
their way out already.


R.Ray Walters
CTO, Solarray, Inc
Nabcep Certified PV Installer,
Licensed Master Electrician
Solar Design Engineer
303 505-8760

On 7/23/2013 3:36 PM, William wrote:

Brian:

I don't have the PV details handy but I will provide them.

Question:  will a sulfated cell exhibit a SG of 1.26?  I thought a 
sulfated cell locked the acid onto the plates, minimizing the SG 
readings below that of a healthy cell. 1.26 is a relatively high reading.


William

On Jul 23, 2013, at 1:28 PM, Brian Teitelbaum 
bteitelb...@aeesolar.com mailto:bteitelb...@aeesolar.com wrote:



William,

What does the PV array consist of? What size and type, and how many, 
modules?


Which TriStar? 45 or 60A?

What controller did she have before the upgrade?

The high charging voltage might be a sign of sulfation. Depending on 
her load profile, that 8A charge rate might have caused chronic 
undercharging. In a 5 peak sun-hour location, that's only 40Ah/day of 
charging capacity.


Brian Teitelbaum

AEE Solar

*From:*re-wrenches-boun...@lists.re-wrenches.org 
mailto:re-wrenches-boun...@lists.re-wrenches.org 
[mailto:re-wrenches-boun...@lists.re-wrenches.org] *On Behalf Of 
*William Miller

*Sent:* Tuesday, July 23, 2013 1:13 PM
*To:* RE-wrenches
*Subject:* [RE-wrenches] Tri-Star MPPT

Friends:

I have a customer with a new Tristar MPPT controller. The customer 
has some older L-16 batteries mixed with new and she thinks the 
controller has damaged her batteries.  I am trying to convince her 
that the batteries were already damaged and mixing old with new is a 
bad idea.


I removed the worst batteries from the array, leaving one string of 
older batteries with reasonable SG readings.  The CC still acts 
strangely:  When programmed to charge the L-16 batteries, the battery 
voltage shoots up to 30.2 volts and the batteries boil a lot.  The 
green light on the controller blinks at variable rates, at one moment 
fast, the next slow, the next solid.


I believe the client started with bad batteries, 6 are 4 years old, 2 
are 1 year old.  She is convinced that the CC damaged her batteries.  
She replaced panels and CC recently, installing the Tristar.  I 
believe the old PV system charged at such a slow rate (8 amps) that 
the battery deficiency was not apparent.  The higher charging rate 
has emphasized the problem.


Any one have any thing to add to my theory?

Thanks in advance.

William Miller

image002.jpg

17395 Oak Rd. Atascadero, CA 93422

www.millersolar.com http://www.millersolar.com/

805-438-5600 voice*

*Note: above number replaces cell number

___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org 
mailto:RE-wrenches@lists.re-wrenches.org


Change email address  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org


List rules  etiquette:
www.re-wrenches.org/etiquette.htm 
http://www.re-wrenches.org/etiquette.htm


Check out participant bios:
www.members.re-wrenches.org http://www.members.re-wrenches.org




___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Change email address  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Change email address  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] Trojan L-16s

2013-07-23 Thread Allan Sindelar

  
  
Tom,
  Except that absorb starts off at 100% of the available amps, not
  50%. Absorb starts as soon as bulk reaches the bulk voltage
  setpoint. It starts out at the same current as was available in
  bulk, then ramps back incrementally as the batteries continue to
  approach full, allowing only as much of the available current to
  flow to the batteries as is necessary to maintain the voltage
  setpoint plus loads.
  
  On the finishing end, absorb doesn't have much to do with
  available amps. Rather, it either completes a timed cycle, with no
  particular control of the available amps except as regulated as
  above, or it switches to float when the amps necessary to maintain
  the bulk (a.k.a. absorption) voltage drops below a threshold,
  typically 2% of bank capacity.
  
  And finally, the midpoint between 20 and 50 is 35, not 40.
  
  Given that these principles form the basis of your definitive .42
  figure, this number sounds pretty arbitrary. Is there anything
  more you can say by way of explanation?
  Thanks, Allan
  
  








  Allan Sindelar
al...@positiveenergysolar.com
NABCEP Certified PV
  Installation Professional 
  NABCEP Certified Technical Sales Professional
  New Mexico EE98J Journeyman Electrician
  Founder and Chief Technology Officer
  Positive Energy, Inc., a Certified B CorporationTM
  3209 Richards Lane
  Santa Fe, New Mexico 87507
  505 424-1112 office 780-2738 cell
  www.positiveenergysolar.com
  

  
  On 7/23/2013 7:57 AM, Tom Duffy wrote:


  Jay

Sorry I should have explained that too... Absorb starts off at around 50% of the available amps and tapers down to around 20% So I divided 20 by 50 = .40 there's a 5% loss factor hence .42

Tom Duffy
Senior Solar Design Engineer

Toll Free 888-895-8179
t...@thesolar.biz
Customer Service and Accounting 888-895-6810 
Grid tie sales 888-895-7847 
Off Grid sales 888-895-4058 
Other Product Sales 888-895-9612 
Central America Sales (Panama) 507-6-126-1253 
Shipping and Receiving 888-895-6497 
Tech Support 888-895-8179
SKYPE:  thesolarbiz

-Original Message-
From: re-wrenches-boun...@lists.re-wrenches.org [mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf Of Jay Peltz
Sent: Monday, July 22, 2013 1:27 PM
To: RE-wrenches
Subject: Re: [RE-wrenches] Trojan L-16s

Hi Tom

Where did you get the .42 from?

Jay
Peltz power 

Sent from my iPhone

On Jul 22, 2013, at 11:04 AM, Tom Duffy t...@thesolar.biz wrote:


  
Drake

Keep the absorb rate recommended for the CC. The trimetric strays over 
time and will become accurate again when you overcharge (equalize)

The math:
Amp hours of battery @ 20 hour rate divided by max charge available in 
amps, from whatever you using to charge (solar or inverter/charger) 
Times .42 = absorb time in hours

i.e. your system 980 watts,  980 divided by 28.8 (average volts) = 34 
amps max charge
370 AH divided by 34 = 10.88 X .42 = 4.57 round up to 4.6 hours absorb 
time for the CC Your inverter VFX3524 max charge 85 amps... 370 
divided by 85 = 4.35 X .42 = 1.82 absorb time for the inverter/charger 
when running generator

Tom Duffy
Senior Solar Design Engineer

Toll Free 888-895-8179
t...@thesolar.biz
Customer Service and Accounting 888-895-6810 Grid tie sales 
888-895-7847 Off Grid sales 888-895-4058 Other Product Sales 
888-895-9612 Central America Sales (Panama) 507-6-126-1253 Shipping 
and Receiving 888-895-6497 Tech Support 888-895-8179
SKYPE:  thesolarbiz

-Original Message-
From: re-wrenches-boun...@lists.re-wrenches.org 
[mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf Of Drake
Sent: Monday, July 22, 2013 10:04 AM
To: RE-wrenches
Subject: Re: [RE-wrenches] Trojan L-16s

Hi Larry,

I will bump up the absorb voltage to 29.6 V. How long do you think the bank should stay in absorb at that rate?  The bank now seems healthy, with the bad battery replaced.  It does accept charge, without going high prematurely.  The max charge rate from the array is around C/10. The system can also be fast charged from a Honda 6500 inverter generator through the Outback 3524 VFX.

We have a Trimetric meter on the system. The discrepancy between the percent charge and the voltage is what demonstrated that we had a problem.

Thanks,

Drake



At 09:30 PM 7/19/2013, you wrote:


  Hi Drake,

It always concerns me when I hear that a battery bank reaches absorb 
setting very quickly. It typically means one of two things: very few 
AH were removed from the bank; the battery bank has sulfated cells 
due to chronic undercharging. Far too often I find the latter to be true.

Healthy batteries will accept current and hold the charge 

[RE-wrenches] Tri Star MPPT

2013-07-23 Thread Hilton Dier III
What you have there is a set of completely hammered batteries. It sounds 
like an off-grid system with parallel strings of batteries of different 
ages being chronically undercharged., which is the renewable energy 
equivalent of a car full of teenagers with guns and whiskey. Something 
bad inevitably happens.


I'd recommend that you get an automotive style battery load tester and 
clamp that on to each one in turn. Measure the voltage with your 
multimeter, because those load testers have iffy analog meters. I'll bet 
one will collapse under load.


Does this customer also have a generator? Sometimes with undersized PV 
arrays and a generator you get a gorge and starve charging pattern. 
The customer lets the batteries get totally flailed and then grudgingly 
goes out and starts the generator. The batteries get blasted with high 
amperage for a while, shedding positive plate material, and then get 
starved again. Perfect storm.


Tell her that she needs a new set of matched batteries. If she balks, 
politely tell her you can't help her, and let someone with less 
judgement deal with it.


Good luck,

Hilton

--
Hilton Dier III
Renewable Energy Design
Partner, Solar Gain LLC
453 East Hill Rd.
Middlesex, VT 05602

___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Change email address  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] Tri-Star MPPT

2013-07-23 Thread Ray Walters
The sulfated cell would show an artificially high SQ reading, if she 
tried to add acid to it: another bogus trick people try, when their 
batteries are going out.  You might ask.   Customers often have to try 
every other trick in the book before admitting they need to pay for new 
batteries.   (adding acid, or EDHT additive, using magicpulsing 
technology, replacing just a couple of batteries, super over charging 
equalizing, buying a used set from their neighbors, trying to use 2 
separate sets (use one for a couple of days, charge the other in town..)


R.Ray Walters
CTO, Solarray, Inc
Nabcep Certified PV Installer,
Licensed Master Electrician
Solar Design Engineer
303 505-8760

On 7/23/2013 3:36 PM, William wrote:

Brian:

Question:  will a sulfated cell exhibit a SG of 1.26?  I thought a 
sulfated cell locked the acid onto the plates, minimizing the SG 
readings below that of a healthy cell. 1.26 is a relatively high reading.


William



___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Change email address  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] Tri-Star MPPT

2013-07-23 Thread jay peltz
Hi Eric,

While agree with most all your assessments, 
Can you please elaborate on the sulfation causes the voltage not to climb?

This is quite counter to what I have seen and what the battery people say?

Thanks

Jay

Peltz power

Sent from my iPad

On Jul 23, 2013, at 2:48 PM, eric.bent...@schneider-electric.com wrote:

 
 Hi William, 
 
  If the SG was 1.26, of course the battery voltage would increase 
 quickly to 30V (which is high for warm weather, BTW). 
  It has been my experience that sulfation causes the voltage NOT to climb. 
 Especially when you have a very large bank, and a 
  relatively small amount of solar. 
  Sometimes it is necessary to reduce the bank size into smaller sets to 
 equalize them and recover their performance. 
 This method of reducing bank size is also effective to compare performance 
 and weed out a potentially bad battery. 
  Systems that have a lot of capacity, with a relatively small amount of 
 charge current usually creates problems, because 
  the load demand exceeds solar production. 
  This results in batteries that operate with partial SOC, which is when 
 sulfation is most prevalent. With (8) L16s, you have approx 
  800Ahrs of capacity (24V bank). It would take significantly more than 8A of 
 charge current to properly care for a bank that size. 
 
 Rgds,
 _
  
 
 Eric Bentsen  |   Schneider Electric   |  Solar Business  |   UNITED STATES  
 |   Technical Support Representative 
 Phone: +(650) 351-8237 ext. 001#  |   
 Email: eric.bent...@schneider-electric.com  |   Site: 
 www.schneider-electric.com/solar  |   Address: 250 South Vasco Rd., 
 Livermore, CA 94551 
 
 
___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Change email address  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] SMA Secure Power Supply

2013-07-23 Thread Orion Thornton
Hi Carl and All,

This spring we had the opportunity to install a 5000-TLUS inverter for a
client, as a pre-release version.  The inverter was commissioned on April
1st and has produced about 2.7 MWhs thus far.  As mentioned, the secure
power supply (SPS) requires a dedicated outlet with a switch to control its
operation.   For this installation we installed the SPS in the mechanical
room, which is about 50 ft from where the inverter is located.  We chose the
mechanical room because it is centrally located within the floor plan of the
home, making it easily accessible to plug in emergency type loads, i.e. cell
phone chargers, laptops, lamps, etc.. It is also very close to the fridge,
which we plugged in with a short extension cord and tested its operation in
the stand-alone mode (which is what the inverter display when the grid is
down and the SPS in activated).  The inverter had no problem powering the
fridge.  The inverter display showed about 900 watts bypassed from the solar
array to the SPS when the fridge cycled onI must say it was a very cool
feeling seeing this happen.

As far as the inverter itself goes, I only have a few minor complaints.
Like the old SMA 1800U and 2500U, the conduit knockouts on the bottom of the
inverter are at a slight angle, which means you must put a slight bend in
your conduit.  This is obviously a bit annoying and I can only guess it has
something to do with the plug and play nature of non-U.S. installation
techniques.  The TLUS inverters are also lacking Bluetooth communication,
unlike their HFUS counterparts. I think this is a nice feature of the HFUS
inverters and wish it was integrated into the TL's.  

With no real difference in cost compared to traditional grid-direct
inverters, I see no reason not to specify the TL, especially for someone who
has a desire for limited power supply during a grid outage.   They can
always add a Sunny Island later on, if a more robust backup system is
needed.  

I hope this helps.

Orion Thornton
Onsite Energy 
NABCEP Certified Solar PV Installer

-Original Message-
From: re-wrenches-boun...@lists.re-wrenches.org
[mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf Of Jesse Dahl
Sent: Tuesday, July 23, 2013 4:11 PM
To: wire...@gmail.com; RE-wrenches
Subject: Re: [RE-wrenches] SMA Secure Power Supply

I know the MREA in WI has one installed on site, but not sure who installed
it. 

Do they have a representative on the list?

Jesse  

Sent from my iPhone

On Jul 22, 2013, at 6:18 PM, wire...@gmail.com wrote:

 If we have another long outage here in CT and we seem to have one every
year now, I don't want to have to explain to my customers why I didn't use
this inverter. 
 Sent from my Verizon Wireless BlackBerry
 
 -Original Message-
 From: Gary Willett g...@icarussolarservices.com
 Sender: re-wrenches-boun...@lists.re-wrenches.orgDate: Mon, 22 Jul 2013
17:33:26 
 To: re-wrenches@lists.re-wrenches.org
 Reply-To: RE-wrenches re-wrenches@lists.re-wrenches.org
 Subject: Re: [RE-wrenches] SMA Secure Power Supply
 
 ___
 List sponsored by Home Power magazine
 
 List Address: RE-wrenches@lists.re-wrenches.org
 
 Change email address  settings:
 http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
 
 List-Archive:
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
 
 List rules  etiquette:
 www.re-wrenches.org/etiquette.htm
 
 Check out participant bios:
 www.members.re-wrenches.org
 
 
 
 ___
 List sponsored by Home Power magazine
 
 List Address: RE-wrenches@lists.re-wrenches.org
 
 Change email address  settings:
 http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
 
 List-Archive:
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
 
 List rules  etiquette:
 www.re-wrenches.org/etiquette.htm
 
 Check out participant bios:
 www.members.re-wrenches.org
 
___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Change email address  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive:
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org


___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Change email address  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org