Re: [RE-wrenches] SMA 1800u not generating power

2015-07-25 Thread frenergy
Is another possible solution.use the prior version of the SB (non-TL)?, of 
course if the VDC of the strings works out.  You wouldn't need to worry about 
any of the wiring, or trying to convince a clueless AHJ one inverter in safer 
than another.  I've used exclusively TL's in all my installs lately, I assume 
the non-TL SB's are still available.

Bill

Feather River Solar Electric
  - Original Message - 
  From: billbroo...@sbcglobal.net 
  To: 'RE-wrenches' 
  Sent: Friday, July 24, 2015 4:07 PM
  Subject: Re: [RE-wrenches] SMA 1800u not generating power


  Glenn,

   

  While the installation may not claim exact compliance with the current NEC 
(debatable), you can easily show that the TL inverter is much safer than the 
older 1800U. The TL has arc-fault detection and much better ground-fault 
detection. Conduit is not the answer since it breaks several other code 
requirements like the module manufacturer’s instructions (110.3(B)).

   

  Bill Brooks.

   
___
List sponsored by Redwood Alliance

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org



[RE-wrenches] SMA 1800u not generating power

2015-07-24 Thread Jason Szumlanski
I am looking at a 1800u from 2004 that has a green light and in mpp mode,
but Pac is zero. Grid and DC voltage are good.  No other indication of
problems. I saw Pac tick up to 2W a couple of times,  but that's it. It's
just not delivering AC power.

Any thoughts?

Sadly, it doesn't make much financial sense for the owner to replace it
with a current model, as the replacement cost would take almost 10 years to
recover with the small BIPV array connected to it. I'm hoping for a field
repair option.

Jason Szumlanski
___
List sponsored by Redwood Alliance

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] SMA 1800u not generating power

2015-07-24 Thread Jason Szumlanski
Someone contacted me off list and said this company does out of warranty
SMA repairs:

http://www.shop.solarcowboyzoutlet.com/Inverter-Repair-Service-Inverter-Repair-Service.htm

Looks like there is a risk in how big the repair is, but apparently they
are willing to talk about the diagnostics before you send it in, and fix
minor problems for a flat rate.

One bad part about these small systems is that labor to repair or replace
failed units can easily turn into a cost equivalent to years of energy
production, not to mention the hardware cost itself... I've only sold a few
tiny systems over the years, and never really considered this. It makes
much more financial sense for an owner to replace a failed 5kW inverter
when the labor is basically the same as a 2kW.

Jason Szumlanski


On Fri, Jul 24, 2015 at 10:04 AM, Sky Sims s...@ecologicalsystems.biz
wrote:

 This is a known issue. I've come across a bunch of their inverters that
 have had this problem. In addition to seeing this issue on their 1800's
 I've seen it happen on their 2500's as well. Shows a solid green light but
 isn't putting out power.
 The first time I came across this issue they had a refurbishment program,
 where they would rebuild the inverter and send it back with a one year
 warranty for under $400. The refurbishment program was a great program that
 I hope they bring back someday.
 The last few times I contacted SMA about one of these defective inverters,
 they said the product was not under warranty and they no longer supported
 it. Only option they gave was to buy a new unit.

 Sky Sims
 Ecological Systems


 On Jul 24, 2015, at 5:49 AM, Jason Szumlanski 
 ja...@floridasolardesigngroup.com wrote:

 I am looking at a 1800u from 2004 that has a green light and in mpp mode,
 but Pac is zero. Grid and DC voltage are good.  No other indication of
 problems. I saw Pac tick up to 2W a couple of times,  but that's it. It's
 just not delivering AC power.

 Any thoughts?

 Sadly, it doesn't make much financial sense for the owner to replace it
 with a current model, as the replacement cost would take almost 10 years to
 recover with the small BIPV array connected to it. I'm hoping for a field
 repair option.

 Jason Szumlanski

 ___
 List sponsored by Redwood Alliance

 List Address: RE-wrenches@lists.re-wrenches.org

 Change listserver email address  settings:
 http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

 List-Archive:
 http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html

 List rules  etiquette:
 www.re-wrenches.org/etiquette.htm

 Check out or update participant bios:
 www.members.re-wrenches.org


 ___
 List sponsored by Redwood Alliance

 List Address: RE-wrenches@lists.re-wrenches.org

 Change listserver email address  settings:
 http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

 List-Archive:
 http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html

 List rules  etiquette:
 www.re-wrenches.org/etiquette.htm

 Check out or update participant bios:
 www.members.re-wrenches.org



___
List sponsored by Redwood Alliance

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] SMA 1800u not generating power

2015-07-24 Thread Glenn Burt
All the way back to the module jboxes? Sounds pricey.
That is assuming the module jboxes accept conduit.

Indeed it I not only the home runs that need to be concerned with the PV 
rating, but the module conductors as well, as there is no distinction made in 
the code between them.

Sincerely,
Glenn Burt
Sent from my 'smart' phone so please excuse grammar and typos.

-Original Message-
From: William Miller will...@millersolar.com
Sent: ‎7/‎24/‎2015 16:59
To: RE-wrenches re-wrenches@lists.re-wrenches.org
Subject: Re: [RE-wrenches] SMA 1800u not generating power

Put it in conduit. 



 On Jul 24, 2015, at 8:14 PM, Glenn Burt glenn.b...@glbcc.com wrote:
 
 How do you get around the code requirement for the use of PV wire with a TL 
 inverter on the existing array?
 
 Sincerely,
 Glenn Burt
 Sent from my 'smart' phone so please excuse grammar and typos.
 From: jerrysgarage01
 Sent: ‎7/‎24/‎2015 12:57
 To: RE-wrenches
 Subject: Re: [RE-wrenches] SMA 1800u not generating power
 
 SMA used to to do repairs but last I heard they no longer have replacement 
 parts. I have used the new SMA TL-22 because of the low voltage dc input. If 
 you added some additional modules to the B input it might qualify for the 
 tax credit (I did say might)
 Good luck
 Jerry
 
 
 Sent via the Samsung Galaxy S™ III, an ATT 4G LTE smartphone
 
 
  Original message 
 From: Jason Szumlanski
 Date:07/24/2015 4:25 AM (GMT-10:00)
 To: RE-wrenches
 Subject: Re: [RE-wrenches] SMA 1800u not generating power
 
 Someone contacted me off list and said this company does out of warranty SMA 
 repairs:
 
 http://www.shop.solarcowboyzoutlet.com/Inverter-Repair-Service-Inverter-Repair-Service.htm
 
 Looks like there is a risk in how big the repair is, but apparently they are 
 willing to talk about the diagnostics before you send it in, and fix minor 
 problems for a flat rate.
 
 One bad part about these small systems is that labor to repair or replace 
 failed units can easily turn into a cost equivalent to years of energy 
 production, not to mention the hardware cost itself... I've only sold a few 
 tiny systems over the years, and never really considered this. It makes 
 much more financial sense for an owner to replace a failed 5kW inverter when 
 the labor is basically the same as a 2kW.
 
 Jason Szumlanski
 
 
 On Fri, Jul 24, 2015 at 10:04 AM, Sky Sims s...@ecologicalsystems.biz 
 wrote:
 This is a known issue. I've come across a bunch of their inverters that have 
 had this problem. In addition to seeing this issue on their 1800's I've seen 
 it happen on their 2500's as well. Shows a solid green light but isn't 
 putting out power. 
 The first time I came across this issue they had a refurbishment program, 
 where they would rebuild the inverter and send it back with a one year 
 warranty for under $400. The refurbishment program was a great program that 
 I hope they bring back someday.
 The last few times I contacted SMA about one of these defective inverters, 
 they said the product was not under warranty and they no longer supported 
 it. Only option they gave was to buy a new unit. 
 
 Sky Sims
 Ecological Systems
 
 
 On Jul 24, 2015, at 5:49 AM, Jason Szumlanski 
 ja...@floridasolardesigngroup.com wrote:
 
 I am looking at a 1800u from 2004 that has a green light and in mpp mode,  
 but Pac is zero. Grid and DC voltage are good.  No other indication of 
 problems. I saw Pac tick up to 2W a couple of times,  but that's it. It's 
 just not delivering AC power.
 
 Any thoughts?
 
 Sadly, it doesn't make much financial sense for the owner to replace it 
 with a current model, as the replacement cost would take almost 10 years to 
 recover with the small BIPV array connected to it. I'm hoping for a field 
 repair option.
 
 Jason Szumlanski
 
 ___
 List sponsored by Redwood Alliance
 
 List Address: RE-wrenches@lists.re-wrenches.org
 
 Change listserver email address  settings:
 http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
 
 List-Archive: 
 http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
 
 List rules  etiquette:
 www.re-wrenches.org/etiquette.htm
 
 Check out or update participant bios:
 www.members.re-wrenches.org
 
 ___
 List sponsored by Redwood Alliance
 
 List Address: RE-wrenches@lists.re-wrenches.org
 
 Change listserver email address  settings:
 http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
 
 List-Archive: 
 http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
 
 List rules  etiquette:
 www.re-wrenches.org/etiquette.htm
 
 Check out or update participant bios:
 www.members.re-wrenches.org
 
 ___
 List sponsored by Redwood Alliance
 
 List Address: RE-wrenches@lists.re-wrenches.org
 
 Change listserver email address  settings:
 http://lists.re-wrenches.org/options.cgi/re

Re: [RE-wrenches] SMA 1800u not generating power

2015-07-24 Thread Jerry Shafer
From what I was told from SMA the board level components are no longer
available from there lower level manufactures.
Jerry
On Jul 24, 2015 9:30 AM, August Goers aug...@luminalt.com wrote:

 Hi Glenn and All –



 Most of these old systems have module cables made out of USE-2. So, just
 changing out the array USE-2 home runs won’t technically cut it.



 Something should be written into the code to allow old systems to use TL
 inverters for upgrades, especially since TL inverters are safer than their
 transformer based (isolated) counterparts.



 For now I guess we either make a decision to source transformer based
 inverters for replacements or install TL inverters despite the code
 violation.



 It is definitely a bummer that SMA isn’t doing the refurbished program
 anymore with their old units.



 Best,



 August



 *From:* RE-wrenches [mailto:re-wrenches-boun...@lists.re-wrenches.org] *On
 Behalf Of *Glenn Burt
 *Sent:* Friday, July 24, 2015 11:14 AM
 *To:* RE-wrenches
 *Subject:* Re: [RE-wrenches] SMA 1800u not generating power



 How do you get around the code requirement for the use of PV wire with a
 TL inverter on the existing array?

 Sincerely,
 Glenn Burt
 Sent from my 'smart' phone so please excuse grammar and typos.
 --

 *From: *jerrysgarage01 jerrysgarag...@gmail.com
 *Sent: *‎7/‎24/‎2015 12:57
 *To: *RE-wrenches re-wrenches@lists.re-wrenches.org
 *Subject: *Re: [RE-wrenches] SMA 1800u not generating power

 SMA used to to do repairs but last I heard they no longer have replacement
 parts. I have used the new SMA TL-22 because of the low voltage dc input.
 If you added some additional modules to the B input it might qualify for
 the tax credit (I did say might)

 Good luck

 Jerry





 Sent via the Samsung Galaxy S™ III, an ATT 4G LTE smartphone



  Original message 

 From: Jason Szumlanski

 Date:07/24/2015 4:25 AM (GMT-10:00)

 To: RE-wrenches

 Subject: Re: [RE-wrenches] SMA 1800u not generating power



 Someone contacted me off list and said this company does out of warranty
 SMA repairs:




 http://www.shop.solarcowboyzoutlet.com/Inverter-Repair-Service-Inverter-Repair-Service.htm



 Looks like there is a risk in how big the repair is, but apparently they
 are willing to talk about the diagnostics before you send it in, and fix
 minor problems for a flat rate.



 One bad part about these small systems is that labor to repair or replace
 failed units can easily turn into a cost equivalent to years of energy
 production, not to mention the hardware cost itself... I've only sold a few
 tiny systems over the years, and never really considered this. It makes
 much more financial sense for an owner to replace a failed 5kW inverter
 when the labor is basically the same as a 2kW.



 Jason Szumlanski





 On Fri, Jul 24, 2015 at 10:04 AM, Sky Sims s...@ecologicalsystems.biz
 wrote:

 This is a known issue. I've come across a bunch of their inverters that
 have had this problem. In addition to seeing this issue on their 1800's
 I've seen it happen on their 2500's as well. Shows a solid green light but
 isn't putting out power.

 The first time I came across this issue they had a refurbishment program,
 where they would rebuild the inverter and send it back with a one year
 warranty for under $400. The refurbishment program was a great program that
 I hope they bring back someday.

 The last few times I contacted SMA about one of these defective inverters,
 they said the product was not under warranty and they no longer supported
 it. Only option they gave was to buy a new unit.

 Sky Sims

 Ecological Systems


 On Jul 24, 2015, at 5:49 AM, Jason Szumlanski 
 ja...@floridasolardesigngroup.com wrote:

 I am looking at a 1800u from 2004 that has a green light and in mpp mode,
 but Pac is zero. Grid and DC voltage are good.  No other indication of
 problems. I saw Pac tick up to 2W a couple of times,  but that's it. It's
 just not delivering AC power.

 Any thoughts?

 Sadly, it doesn't make much financial sense for the owner to replace it
 with a current model, as the replacement cost would take almost 10 years to
 recover with the small BIPV array connected to it. I'm hoping for a field
 repair option.

 Jason Szumlanski

 ___
 List sponsored by Redwood Alliance

 List Address: RE-wrenches@lists.re-wrenches.org

 Change listserver email address  settings:
 http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

 List-Archive:
 http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html

 List rules  etiquette:
 www.re-wrenches.org/etiquette.htm

 Check out or update participant bios:
 www.members.re-wrenches.org


 ___
 List sponsored by Redwood Alliance

 List Address: RE-wrenches@lists.re-wrenches.org

 Change listserver email address  settings:
 http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

Re: [RE-wrenches] SMA 1800u not generating power

2015-07-24 Thread William Miller
Put it in conduit. 



 On Jul 24, 2015, at 8:14 PM, Glenn Burt glenn.b...@glbcc.com wrote:
 
 How do you get around the code requirement for the use of PV wire with a TL 
 inverter on the existing array?
 
 Sincerely,
 Glenn Burt
 Sent from my 'smart' phone so please excuse grammar and typos.
 From: jerrysgarage01
 Sent: ‎7/‎24/‎2015 12:57
 To: RE-wrenches
 Subject: Re: [RE-wrenches] SMA 1800u not generating power
 
 SMA used to to do repairs but last I heard they no longer have replacement 
 parts. I have used the new SMA TL-22 because of the low voltage dc input. If 
 you added some additional modules to the B input it might qualify for the 
 tax credit (I did say might)
 Good luck
 Jerry
 
 
 Sent via the Samsung Galaxy S™ III, an ATT 4G LTE smartphone
 
 
  Original message 
 From: Jason Szumlanski
 Date:07/24/2015 4:25 AM (GMT-10:00)
 To: RE-wrenches
 Subject: Re: [RE-wrenches] SMA 1800u not generating power
 
 Someone contacted me off list and said this company does out of warranty SMA 
 repairs:
 
 http://www.shop.solarcowboyzoutlet.com/Inverter-Repair-Service-Inverter-Repair-Service.htm
 
 Looks like there is a risk in how big the repair is, but apparently they are 
 willing to talk about the diagnostics before you send it in, and fix minor 
 problems for a flat rate.
 
 One bad part about these small systems is that labor to repair or replace 
 failed units can easily turn into a cost equivalent to years of energy 
 production, not to mention the hardware cost itself... I've only sold a few 
 tiny systems over the years, and never really considered this. It makes 
 much more financial sense for an owner to replace a failed 5kW inverter when 
 the labor is basically the same as a 2kW.
 
 Jason Szumlanski
 
 
 On Fri, Jul 24, 2015 at 10:04 AM, Sky Sims s...@ecologicalsystems.biz 
 wrote:
 This is a known issue. I've come across a bunch of their inverters that have 
 had this problem. In addition to seeing this issue on their 1800's I've seen 
 it happen on their 2500's as well. Shows a solid green light but isn't 
 putting out power. 
 The first time I came across this issue they had a refurbishment program, 
 where they would rebuild the inverter and send it back with a one year 
 warranty for under $400. The refurbishment program was a great program that 
 I hope they bring back someday.
 The last few times I contacted SMA about one of these defective inverters, 
 they said the product was not under warranty and they no longer supported 
 it. Only option they gave was to buy a new unit. 
 
 Sky Sims
 Ecological Systems
 
 
 On Jul 24, 2015, at 5:49 AM, Jason Szumlanski 
 ja...@floridasolardesigngroup.com wrote:
 
 I am looking at a 1800u from 2004 that has a green light and in mpp mode,  
 but Pac is zero. Grid and DC voltage are good.  No other indication of 
 problems. I saw Pac tick up to 2W a couple of times,  but that's it. It's 
 just not delivering AC power.
 
 Any thoughts?
 
 Sadly, it doesn't make much financial sense for the owner to replace it 
 with a current model, as the replacement cost would take almost 10 years to 
 recover with the small BIPV array connected to it. I'm hoping for a field 
 repair option.
 
 Jason Szumlanski
 
 ___
 List sponsored by Redwood Alliance
 
 List Address: RE-wrenches@lists.re-wrenches.org
 
 Change listserver email address  settings:
 http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
 
 List-Archive: 
 http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
 
 List rules  etiquette:
 www.re-wrenches.org/etiquette.htm
 
 Check out or update participant bios:
 www.members.re-wrenches.org
 
 ___
 List sponsored by Redwood Alliance
 
 List Address: RE-wrenches@lists.re-wrenches.org
 
 Change listserver email address  settings:
 http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
 
 List-Archive: 
 http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
 
 List rules  etiquette:
 www.re-wrenches.org/etiquette.htm
 
 Check out or update participant bios:
 www.members.re-wrenches.org
 
 ___
 List sponsored by Redwood Alliance
 
 List Address: RE-wrenches@lists.re-wrenches.org
 
 Change listserver email address  settings:
 http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
 
 List-Archive: 
 http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
 
 List rules  etiquette:
 www.re-wrenches.org/etiquette.htm
 
 Check out or update participant bios:
 www.members.re-wrenches.org
 
___
List sponsored by Redwood Alliance

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org

Re: [RE-wrenches] SMA 1800u not generating power

2015-07-24 Thread Glenn Burt
How do you get around the code requirement for the use of PV wire with a TL 
inverter on the existing array?

Sincerely,
Glenn Burt
Sent from my 'smart' phone so please excuse grammar and typos.

-Original Message-
From: jerrysgarage01 jerrysgarag...@gmail.com
Sent: ‎7/‎24/‎2015 12:57
To: RE-wrenches re-wrenches@lists.re-wrenches.org
Subject: Re: [RE-wrenches] SMA 1800u not generating power

SMA used to to do repairs but last I heard they no longer have replacement 
parts. I have used the new SMA TL-22 because of the low voltage dc input. If 
you added some additional modules to the B input it might qualify for the tax 
credit (I did say might)
Good luck
Jerry


Sent via the Samsung Galaxy S™ III, an ATT 4G LTE smartphone

div Original message /divdivFrom: Jason Szumlanski 
ja...@floridasolardesigngroup.com /divdivDate:07/24/2015  4:25 AM  
(GMT-10:00) /divdivTo: RE-wrenches re-wrenches@lists.re-wrenches.org 
/divdivSubject: Re: [RE-wrenches] SMA 1800u not generating power /divdiv
/divSomeone contacted me off list and said this company does out of warranty 
SMA repairs:

http://www.shop.solarcowboyzoutlet.com/Inverter-Repair-Service-Inverter-Repair-Service.htm

Looks like there is a risk in how big the repair is, but apparently they are 
willing to talk about the diagnostics before you send it in, and fix minor 
problems for a flat rate.

One bad part about these small systems is that labor to repair or replace 
failed units can easily turn into a cost equivalent to years of energy 
production, not to mention the hardware cost itself... I've only sold a few 
tiny systems over the years, and never really considered this. It makes much 
more financial sense for an owner to replace a failed 5kW inverter when the 
labor is basically the same as a 2kW.

Jason Szumlanski


On Fri, Jul 24, 2015 at 10:04 AM, Sky Sims s...@ecologicalsystems.biz wrote:
This is a known issue. I've come across a bunch of their inverters that have 
had this problem. In addition to seeing this issue on their 1800's I've seen it 
happen on their 2500's as well. Shows a solid green light but isn't putting out 
power. 
The first time I came across this issue they had a refurbishment program, where 
they would rebuild the inverter and send it back with a one year warranty for 
under $400. The refurbishment program was a great program that I hope they 
bring back someday.
The last few times I contacted SMA about one of these defective inverters, they 
said the product was not under warranty and they no longer supported it. Only 
option they gave was to buy a new unit. 

Sky Sims
Ecological Systems


On Jul 24, 2015, at 5:49 AM, Jason Szumlanski 
ja...@floridasolardesigngroup.com wrote:

I am looking at a 1800u from 2004 that has a green light and in mpp mode,  but 
Pac is zero. Grid and DC voltage are good.  No other indication of problems. I 
saw Pac tick up to 2W a couple of times,  but that's it. It's just not 
delivering AC power.

Any thoughts?

Sadly, it doesn't make much financial sense for the owner to replace it with a 
current model, as the replacement cost would take almost 10 years to recover 
with the small BIPV array connected to it. I'm hoping for a field repair option.

Jason Szumlanski

___
List sponsored by Redwood Alliance

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org


___
List sponsored by Redwood Alliance

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org



___
List sponsored by Redwood Alliance

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] SMA 1800u not generating power

2015-07-24 Thread jerrysgarage01
SMA used to to do repairs but last I heard they no longer have replacement 
parts. I have used the new SMA TL-22 because of the low voltage dc input. If 
you added some additional modules to the B input it might qualify for the tax 
credit (I did say might)
Good luck
Jerry


Sent via the Samsung Galaxy S™ III, an ATT 4G LTE smartphone

div Original message /divdivFrom: Jason Szumlanski 
ja...@floridasolardesigngroup.com /divdivDate:07/24/2015  4:25 AM  
(GMT-10:00) /divdivTo: RE-wrenches re-wrenches@lists.re-wrenches.org 
/divdivSubject: Re: [RE-wrenches] SMA 1800u not generating power /divdiv
/divSomeone contacted me off list and said this company does out of warranty 
SMA repairs:

http://www.shop.solarcowboyzoutlet.com/Inverter-Repair-Service-Inverter-Repair-Service.htm

Looks like there is a risk in how big the repair is, but apparently they are 
willing to talk about the diagnostics before you send it in, and fix minor 
problems for a flat rate.

One bad part about these small systems is that labor to repair or replace 
failed units can easily turn into a cost equivalent to years of energy 
production, not to mention the hardware cost itself... I've only sold a few 
tiny systems over the years, and never really considered this. It makes much 
more financial sense for an owner to replace a failed 5kW inverter when the 
labor is basically the same as a 2kW.

Jason Szumlanski


On Fri, Jul 24, 2015 at 10:04 AM, Sky Sims s...@ecologicalsystems.biz wrote:
This is a known issue. I've come across a bunch of their inverters that have 
had this problem. In addition to seeing this issue on their 1800's I've seen it 
happen on their 2500's as well. Shows a solid green light but isn't putting out 
power. 
The first time I came across this issue they had a refurbishment program, where 
they would rebuild the inverter and send it back with a one year warranty for 
under $400. The refurbishment program was a great program that I hope they 
bring back someday.
The last few times I contacted SMA about one of these defective inverters, they 
said the product was not under warranty and they no longer supported it. Only 
option they gave was to buy a new unit. 

Sky Sims
Ecological Systems


On Jul 24, 2015, at 5:49 AM, Jason Szumlanski 
ja...@floridasolardesigngroup.com wrote:

I am looking at a 1800u from 2004 that has a green light and in mpp mode,  but 
Pac is zero. Grid and DC voltage are good.  No other indication of problems. I 
saw Pac tick up to 2W a couple of times,  but that's it. It's just not 
delivering AC power.

Any thoughts?

Sadly, it doesn't make much financial sense for the owner to replace it with a 
current model, as the replacement cost would take almost 10 years to recover 
with the small BIPV array connected to it. I'm hoping for a field repair option.

Jason Szumlanski

___
List sponsored by Redwood Alliance

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org


___
List sponsored by Redwood Alliance

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org



___
List sponsored by Redwood Alliance

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] SMA 1800u not generating power

2015-07-24 Thread Jerry Shafer
There you go, I just assumed it was
Jerry
On Jul 24, 2015 10:59 AM, William Miller will...@millersolar.com wrote:

 Put it in conduit.



 On Jul 24, 2015, at 8:14 PM, Glenn Burt glenn.b...@glbcc.com wrote:

 How do you get around the code requirement for the use of PV wire with a
 TL inverter on the existing array?

 Sincerely,
 Glenn Burt
 Sent from my 'smart' phone so please excuse grammar and typos.
 --
 From: jerrysgarage01 jerrysgarag...@gmail.com
 Sent: ‎7/‎24/‎2015 12:57
 To: RE-wrenches re-wrenches@lists.re-wrenches.org
 Subject: Re: [RE-wrenches] SMA 1800u not generating power

 SMA used to to do repairs but last I heard they no longer have replacement
 parts. I have used the new SMA TL-22 because of the low voltage dc input.
 If you added some additional modules to the B input it might qualify for
 the tax credit (I did say might)
 Good luck
 Jerry


 Sent via the Samsung Galaxy S™ III, an ATT 4G LTE smartphone


  Original message 
 From: Jason Szumlanski
 Date:07/24/2015 4:25 AM (GMT-10:00)
 To: RE-wrenches
 Subject: Re: [RE-wrenches] SMA 1800u not generating power

 Someone contacted me off list and said this company does out of warranty
 SMA repairs:


 http://www.shop.solarcowboyzoutlet.com/Inverter-Repair-Service-Inverter-Repair-Service.htm

 Looks like there is a risk in how big the repair is, but apparently they
 are willing to talk about the diagnostics before you send it in, and fix
 minor problems for a flat rate.

 One bad part about these small systems is that labor to repair or replace
 failed units can easily turn into a cost equivalent to years of energy
 production, not to mention the hardware cost itself... I've only sold a few
 tiny systems over the years, and never really considered this. It makes
 much more financial sense for an owner to replace a failed 5kW inverter
 when the labor is basically the same as a 2kW.

 Jason Szumlanski


 On Fri, Jul 24, 2015 at 10:04 AM, Sky Sims s...@ecologicalsystems.biz
 wrote:

 This is a known issue. I've come across a bunch of their inverters that
 have had this problem. In addition to seeing this issue on their 1800's
 I've seen it happen on their 2500's as well. Shows a solid green light but
 isn't putting out power.
 The first time I came across this issue they had a refurbishment program,
 where they would rebuild the inverter and send it back with a one year
 warranty for under $400. The refurbishment program was a great program that
 I hope they bring back someday.
 The last few times I contacted SMA about one of these defective
 inverters, they said the product was not under warranty and they no longer
 supported it. Only option they gave was to buy a new unit.

 Sky Sims
 Ecological Systems


 On Jul 24, 2015, at 5:49 AM, Jason Szumlanski 
 ja...@floridasolardesigngroup.com wrote:

 I am looking at a 1800u from 2004 that has a green light and in mpp
 mode,  but Pac is zero. Grid and DC voltage are good.  No other indication
 of problems. I saw Pac tick up to 2W a couple of times,  but that's it.
 It's just not delivering AC power.

 Any thoughts?

 Sadly, it doesn't make much financial sense for the owner to replace it
 with a current model, as the replacement cost would take almost 10 years to
 recover with the small BIPV array connected to it. I'm hoping for a field
 repair option.

 Jason Szumlanski

 ___
 List sponsored by Redwood Alliance

 List Address: RE-wrenches@lists.re-wrenches.org

 Change listserver email address  settings:
 http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

 List-Archive:
 http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html

 List rules  etiquette:
 www.re-wrenches.org/etiquette.htm

 Check out or update participant bios:
 www.members.re-wrenches.org


 ___
 List sponsored by Redwood Alliance

 List Address: RE-wrenches@lists.re-wrenches.org

 Change listserver email address  settings:
 http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

 List-Archive:
 http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html

 List rules  etiquette:
 www.re-wrenches.org/etiquette.htm

 Check out or update participant bios:
 www.members.re-wrenches.org



 ___
 List sponsored by Redwood Alliance

 List Address: RE-wrenches@lists.re-wrenches.org

 Change listserver email address  settings:
 http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

 List-Archive:
 http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html

 List rules  etiquette:
 www.re-wrenches.org/etiquette.htm

 Check out or update participant bios:
 www.members.re-wrenches.org


 ___
 List sponsored by Redwood Alliance

 List Address: RE-wrenches@lists.re-wrenches.org

 Change listserver email address  settings:
 http

Re: [RE-wrenches] SMA 1800u not generating power

2015-07-24 Thread billbrooks7
Glenn,



While the installation may not claim exact compliance with the current NEC 
(debatable), you can easily show that the TL inverter is much safer than the 
older 1800U. The TL has arc-fault detection and much better ground-fault 
detection. Conduit is not the answer since it breaks several other code 
requirements like the module manufacturer’s instructions (110.3(B)).



Bill Brooks.





From: RE-wrenches [mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf 
Of Glenn Burt
Sent: Friday, July 24, 2015 2:14 PM
To: RE-wrenches
Subject: Re: [RE-wrenches] SMA 1800u not generating power



All the way back to the module jboxes? Sounds pricey.
That is assuming the module jboxes accept conduit.

Indeed it I not only the home runs that need to be concerned with the PV 
rating, but the module conductors as well, as there is no distinction made in 
the code between them.

Sincerely,
Glenn Burt
Sent from my 'smart' phone so please excuse grammar and typos.

  _

From: William Miller mailto:will...@millersolar.com
Sent: ‎7/‎24/‎2015 16:59
To: RE-wrenches mailto:re-wrenches@lists.re-wrenches.org
Subject: Re: [RE-wrenches] SMA 1800u not generating power

Put it in conduit.




On Jul 24, 2015, at 8:14 PM, Glenn Burt glenn.b...@glbcc.com 
mailto:glenn.b...@glbcc.com  wrote:

How do you get around the code requirement for the use of PV wire with a TL 
inverter on the existing array?

Sincerely,
Glenn Burt
Sent from my 'smart' phone so please excuse grammar and typos.

  _

From: jerrysgarage01 mailto:jerrysgarag...@gmail.com
Sent: ‎7/‎24/‎2015 12:57
To: RE-wrenches mailto:re-wrenches@lists.re-wrenches.org
Subject: Re: [RE-wrenches] SMA 1800u not generating power

SMA used to to do repairs but last I heard they no longer have replacement 
parts. I have used the new SMA TL-22 because of the low voltage dc input. If 
you added some additional modules to the B input it might qualify for the tax 
credit (I did say might)

Good luck

Jerry





Sent via the Samsung Galaxy S™ III, an ATT 4G LTE smartphone



 Original message 

From: Jason Szumlanski

Date:07/24/2015 4:25 AM (GMT-10:00)

To: RE-wrenches

Subject: Re: [RE-wrenches] SMA 1800u not generating power



Someone contacted me off list and said this company does out of warranty SMA 
repairs:



http://www.shop.solarcowboyzoutlet.com/Inverter-Repair-Service-Inverter-Repair-Service.htm



Looks like there is a risk in how big the repair is, but apparently they are 
willing to talk about the diagnostics before you send it in, and fix minor 
problems for a flat rate.



One bad part about these small systems is that labor to repair or replace 
failed units can easily turn into a cost equivalent to years of energy 
production, not to mention the hardware cost itself... I've only sold a few 
tiny systems over the years, and never really considered this. It makes much 
more financial sense for an owner to replace a failed 5kW inverter when the 
labor is basically the same as a 2kW.



Jason Szumlanski





On Fri, Jul 24, 2015 at 10:04 AM, Sky Sims s...@ecologicalsystems.biz 
mailto:s...@ecologicalsystems.biz  wrote:

This is a known issue. I've come across a bunch of their inverters that have 
had this problem. In addition to seeing this issue on their 1800's I've seen it 
happen on their 2500's as well. Shows a solid green light but isn't putting out 
power.

The first time I came across this issue they had a refurbishment program, where 
they would rebuild the inverter and send it back with a one year warranty for 
under $400. The refurbishment program was a great program that I hope they 
bring back someday.

The last few times I contacted SMA about one of these defective inverters, they 
said the product was not under warranty and they no longer supported it. Only 
option they gave was to buy a new unit.

Sky Sims

Ecological Systems


On Jul 24, 2015, at 5:49 AM, Jason Szumlanski 
ja...@floridasolardesigngroup.com mailto:ja...@floridasolardesigngroup.com  
wrote:

I am looking at a 1800u from 2004 that has a green light and in mpp mode,  but 
Pac is zero. Grid and DC voltage are good.  No other indication of problems. I 
saw Pac tick up to 2W a couple of times,  but that's it. It's just not 
delivering AC power.

Any thoughts?

Sadly, it doesn't make much financial sense for the owner to replace it with a 
current model, as the replacement cost would take almost 10 years to recover 
with the small BIPV array connected to it. I'm hoping for a field repair option.

Jason Szumlanski

___
List sponsored by Redwood Alliance

List Address: RE-wrenches@lists.re-wrenches.org 
mailto:RE-wrenches@lists.re-wrenches.org

Change listserver email address  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html

List rules  etiquette:
www.re-wrenches.org/etiquette.htm http://www.re

Re: [RE-wrenches] SMA 1800u not generating power

2015-07-24 Thread Sky Sims
This is a known issue. I've come across a bunch of their inverters that have 
had this problem. In addition to seeing this issue on their 1800's I've seen it 
happen on their 2500's as well. Shows a solid green light but isn't putting out 
power. 
The first time I came across this issue they had a refurbishment program, where 
they would rebuild the inverter and send it back with a one year warranty for 
under $400. The refurbishment program was a great program that I hope they 
bring back someday.
The last few times I contacted SMA about one of these defective inverters, they 
said the product was not under warranty and they no longer supported it. Only 
option they gave was to buy a new unit. 

Sky Sims
Ecological Systems


 On Jul 24, 2015, at 5:49 AM, Jason Szumlanski 
 ja...@floridasolardesigngroup.com wrote:
 
 I am looking at a 1800u from 2004 that has a green light and in mpp mode,  
 but Pac is zero. Grid and DC voltage are good.  No other indication of 
 problems. I saw Pac tick up to 2W a couple of times,  but that's it. It's 
 just not delivering AC power.
 
 Any thoughts?
 
 Sadly, it doesn't make much financial sense for the owner to replace it with 
 a current model, as the replacement cost would take almost 10 years to 
 recover with the small BIPV array connected to it. I'm hoping for a field 
 repair option.
 
 Jason Szumlanski
 
 ___
 List sponsored by Redwood Alliance
 
 List Address: RE-wrenches@lists.re-wrenches.org
 
 Change listserver email address  settings:
 http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
 
 List-Archive: 
 http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
 
 List rules  etiquette:
 www.re-wrenches.org/etiquette.htm
 
 Check out or update participant bios:
 www.members.re-wrenches.org
 
___
List sponsored by Redwood Alliance

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] SMA 1800u not generating power

2015-07-24 Thread jerrysgarage01
Replacing the wire would be in most cases a simple solution
Jerry


Sent via the Samsung Galaxy S™ III, an ATT 4G LTE smartphone

div Original message /divdivFrom: Glenn Burt 
glenn.b...@glbcc.com /divdivDate:07/24/2015  8:14 AM  (GMT-10:00) 
/divdivTo: RE-wrenches re-wrenches@lists.re-wrenches.org 
/divdivSubject: Re: [RE-wrenches] SMA 1800u not generating power /divdiv
/divHow do you get around the code requirement for the use of PV wire with a 
TL inverter on the existing array?

Sincerely,
Glenn Burt
Sent from my 'smart' phone so please excuse grammar and typos.
From: jerrysgarage01
Sent: ‎7/‎24/‎2015 12:57
To: RE-wrenches
Subject: Re: [RE-wrenches] SMA 1800u not generating power

SMA used to to do repairs but last I heard they no longer have replacement 
parts. I have used the new SMA TL-22 because of the low voltage dc input. If 
you added some additional modules to the B input it might qualify for the tax 
credit (I did say might)
Good luck
Jerry


Sent via the Samsung Galaxy S™ III, an ATT 4G LTE smartphone


 Original message 
From: Jason Szumlanski
Date:07/24/2015 4:25 AM (GMT-10:00)
To: RE-wrenches
Subject: Re: [RE-wrenches] SMA 1800u not generating power

Someone contacted me off list and said this company does out of warranty SMA 
repairs:

http://www.shop.solarcowboyzoutlet.com/Inverter-Repair-Service-Inverter-Repair-Service.htm

Looks like there is a risk in how big the repair is, but apparently they are 
willing to talk about the diagnostics before you send it in, and fix minor 
problems for a flat rate.

One bad part about these small systems is that labor to repair or replace 
failed units can easily turn into a cost equivalent to years of energy 
production, not to mention the hardware cost itself... I've only sold a few 
tiny systems over the years, and never really considered this. It makes much 
more financial sense for an owner to replace a failed 5kW inverter when the 
labor is basically the same as a 2kW.

Jason Szumlanski


On Fri, Jul 24, 2015 at 10:04 AM, Sky Sims s...@ecologicalsystems.biz wrote:
This is a known issue. I've come across a bunch of their inverters that have 
had this problem. In addition to seeing this issue on their 1800's I've seen it 
happen on their 2500's as well. Shows a solid green light but isn't putting out 
power. 
The first time I came across this issue they had a refurbishment program, where 
they would rebuild the inverter and send it back with a one year warranty for 
under $400. The refurbishment program was a great program that I hope they 
bring back someday.
The last few times I contacted SMA about one of these defective inverters, they 
said the product was not under warranty and they no longer supported it. Only 
option they gave was to buy a new unit. 

Sky Sims
Ecological Systems


On Jul 24, 2015, at 5:49 AM, Jason Szumlanski 
ja...@floridasolardesigngroup.com wrote:

I am looking at a 1800u from 2004 that has a green light and in mpp mode,  but 
Pac is zero. Grid and DC voltage are good.  No other indication of problems. I 
saw Pac tick up to 2W a couple of times,  but that's it. It's just not 
delivering AC power.

Any thoughts?

Sadly, it doesn't make much financial sense for the owner to replace it with a 
current model, as the replacement cost would take almost 10 years to recover 
with the small BIPV array connected to it. I'm hoping for a field repair option.

Jason Szumlanski

___
List sponsored by Redwood Alliance

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org


___
List sponsored by Redwood Alliance

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org



___
List sponsored by Redwood Alliance

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] SMA 1800u not generating power

2015-07-24 Thread August Goers
Hi Glenn and All –



Most of these old systems have module cables made out of USE-2. So, just
changing out the array USE-2 home runs won’t technically cut it.



Something should be written into the code to allow old systems to use TL
inverters for upgrades, especially since TL inverters are safer than their
transformer based (isolated) counterparts.



For now I guess we either make a decision to source transformer based
inverters for replacements or install TL inverters despite the code
violation.



It is definitely a bummer that SMA isn’t doing the refurbished program
anymore with their old units.



Best,



August



*From:* RE-wrenches [mailto:re-wrenches-boun...@lists.re-wrenches.org] *On
Behalf Of *Glenn Burt
*Sent:* Friday, July 24, 2015 11:14 AM
*To:* RE-wrenches
*Subject:* Re: [RE-wrenches] SMA 1800u not generating power



How do you get around the code requirement for the use of PV wire with a TL
inverter on the existing array?

Sincerely,
Glenn Burt
Sent from my 'smart' phone so please excuse grammar and typos.
--

*From: *jerrysgarage01 jerrysgarag...@gmail.com
*Sent: *‎7/‎24/‎2015 12:57
*To: *RE-wrenches re-wrenches@lists.re-wrenches.org
*Subject: *Re: [RE-wrenches] SMA 1800u not generating power

SMA used to to do repairs but last I heard they no longer have replacement
parts. I have used the new SMA TL-22 because of the low voltage dc input.
If you added some additional modules to the B input it might qualify for
the tax credit (I did say might)

Good luck

Jerry





Sent via the Samsung Galaxy S™ III, an ATT 4G LTE smartphone



 Original message 

From: Jason Szumlanski

Date:07/24/2015 4:25 AM (GMT-10:00)

To: RE-wrenches

Subject: Re: [RE-wrenches] SMA 1800u not generating power



Someone contacted me off list and said this company does out of warranty
SMA repairs:



http://www.shop.solarcowboyzoutlet.com/Inverter-Repair-Service-Inverter-Repair-Service.htm



Looks like there is a risk in how big the repair is, but apparently they
are willing to talk about the diagnostics before you send it in, and fix
minor problems for a flat rate.



One bad part about these small systems is that labor to repair or replace
failed units can easily turn into a cost equivalent to years of energy
production, not to mention the hardware cost itself... I've only sold a few
tiny systems over the years, and never really considered this. It makes
much more financial sense for an owner to replace a failed 5kW inverter
when the labor is basically the same as a 2kW.



Jason Szumlanski





On Fri, Jul 24, 2015 at 10:04 AM, Sky Sims s...@ecologicalsystems.biz
wrote:

This is a known issue. I've come across a bunch of their inverters that
have had this problem. In addition to seeing this issue on their 1800's
I've seen it happen on their 2500's as well. Shows a solid green light but
isn't putting out power.

The first time I came across this issue they had a refurbishment program,
where they would rebuild the inverter and send it back with a one year
warranty for under $400. The refurbishment program was a great program that
I hope they bring back someday.

The last few times I contacted SMA about one of these defective inverters,
they said the product was not under warranty and they no longer supported
it. Only option they gave was to buy a new unit.

Sky Sims

Ecological Systems


On Jul 24, 2015, at 5:49 AM, Jason Szumlanski 
ja...@floridasolardesigngroup.com wrote:

I am looking at a 1800u from 2004 that has a green light and in mpp mode,
but Pac is zero. Grid and DC voltage are good.  No other indication of
problems. I saw Pac tick up to 2W a couple of times,  but that's it. It's
just not delivering AC power.

Any thoughts?

Sadly, it doesn't make much financial sense for the owner to replace it
with a current model, as the replacement cost would take almost 10 years to
recover with the small BIPV array connected to it. I'm hoping for a field
repair option.

Jason Szumlanski

___
List sponsored by Redwood Alliance

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive:
http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org


___
List sponsored by Redwood Alliance

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive:
http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org
___
List sponsored by Redwood

Re: [RE-wrenches] SMA 1800u not generating power

2015-07-24 Thread Glenn Burt
Bill,

 

Thanks for chiming in and going on the record with a good position!

 

-Glenn Burt

 

From: RE-wrenches [mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf 
Of billbroo...@sbcglobal.net
Sent: Friday, July 24, 2015 7:07 PM
To: 'RE-wrenches'
Subject: Re: [RE-wrenches] SMA 1800u not generating power

 

Glenn,

 

While the installation may not claim exact compliance with the current NEC 
(debatable), you can easily show that the TL inverter is much safer than the 
older 1800U. The TL has arc-fault detection and much better ground-fault 
detection. Conduit is not the answer since it breaks several other code 
requirements like the module manufacturer’s instructions (110.3(B)).

 

Bill Brooks.

 

 

From: RE-wrenches [mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf 
Of Glenn Burt
Sent: Friday, July 24, 2015 2:14 PM
To: RE-wrenches
Subject: Re: [RE-wrenches] SMA 1800u not generating power

 

All the way back to the module jboxes? Sounds pricey.
That is assuming the module jboxes accept conduit.

Indeed it I not only the home runs that need to be concerned with the PV 
rating, but the module conductors as well, as there is no distinction made in 
the code between them.

Sincerely,
Glenn Burt
Sent from my 'smart' phone so please excuse grammar and typos.

  _  

From: William Miller mailto:will...@millersolar.com 
Sent: ‎7/‎24/‎2015 16:59
To: RE-wrenches mailto:re-wrenches@lists.re-wrenches.org 
Subject: Re: [RE-wrenches] SMA 1800u not generating power

Put it in conduit. 


On Jul 24, 2015, at 8:14 PM, Glenn Burt glenn.b...@glbcc.com wrote:

How do you get around the code requirement for the use of PV wire with a TL 
inverter on the existing array?

Sincerely,
Glenn Burt
Sent from my 'smart' phone so please excuse grammar and typos.

  _  

From: jerrysgarage01 mailto:jerrysgarag...@gmail.com 
Sent: ‎7/‎24/‎2015 12:57
To: RE-wrenches mailto:re-wrenches@lists.re-wrenches.org 
Subject: Re: [RE-wrenches] SMA 1800u not generating power

SMA used to to do repairs but last I heard they no longer have replacement 
parts. I have used the new SMA TL-22 because of the low voltage dc input. If 
you added some additional modules to the B input it might qualify for the tax 
credit (I did say might)

Good luck

Jerry

 

 

Sent via the Samsung Galaxy S™ III, an ATT 4G LTE smartphone

 

 Original message 

From: Jason Szumlanski 

Date:07/24/2015 4:25 AM (GMT-10:00) 

To: RE-wrenches 

Subject: Re: [RE-wrenches] SMA 1800u not generating power 

 

Someone contacted me off list and said this company does out of warranty SMA 
repairs:

 

http://www.shop.solarcowboyzoutlet.com/Inverter-Repair-Service-Inverter-Repair-Service.htm

 

Looks like there is a risk in how big the repair is, but apparently they are 
willing to talk about the diagnostics before you send it in, and fix minor 
problems for a flat rate.

 

One bad part about these small systems is that labor to repair or replace 
failed units can easily turn into a cost equivalent to years of energy 
production, not to mention the hardware cost itself... I've only sold a few 
tiny systems over the years, and never really considered this. It makes much 
more financial sense for an owner to replace a failed 5kW inverter when the 
labor is basically the same as a 2kW.

 

Jason Szumlanski

 

 

On Fri, Jul 24, 2015 at 10:04 AM, Sky Sims s...@ecologicalsystems.biz wrote:

This is a known issue. I've come across a bunch of their inverters that have 
had this problem. In addition to seeing this issue on their 1800's I've seen it 
happen on their 2500's as well. Shows a solid green light but isn't putting out 
power. 

The first time I came across this issue they had a refurbishment program, where 
they would rebuild the inverter and send it back with a one year warranty for 
under $400. The refurbishment program was a great program that I hope they 
bring back someday.

The last few times I contacted SMA about one of these defective inverters, they 
said the product was not under warranty and they no longer supported it. Only 
option they gave was to buy a new unit. 

Sky Sims

Ecological Systems


On Jul 24, 2015, at 5:49 AM, Jason Szumlanski 
ja...@floridasolardesigngroup.com wrote:

I am looking at a 1800u from 2004 that has a green light and in mpp mode,  but 
Pac is zero. Grid and DC voltage are good.  No other indication of problems. I 
saw Pac tick up to 2W a couple of times,  but that's it. It's just not 
delivering AC power. 

Any thoughts? 

Sadly, it doesn't make much financial sense for the owner to replace it with a 
current model, as the replacement cost would take almost 10 years to recover 
with the small BIPV array connected to it. I'm hoping for a field repair 
option. 

Jason Szumlanski 

___
List sponsored by Redwood Alliance

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address  settings:
http://lists.re-wrenches.org