RE: Seismic Bracing - Clean Agent

2011-08-09 Thread Rod DiBona
Well I think that might be the point. The bracing that is needed (although not 
stated) on clean agent is clearly very robust. The question however is are 
additional listed seismic braces required to be installed and calculated? My 
experience has been no they are not, but this has been driven by AHJ response. 
I have wondered as Bill did as to the intent of the code and standard. I will 
shoot our main manufacturer and email and share the results back to the forum.

-Original Message-
From: sprinklerforum-boun...@firesprinkler.org 
[mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of max brown
Sent: Monday, August 08, 2011 6:42 PM
To: burtell
Subject: RE: Seismic Bracing - Clean Agent


On our installations we always have additional bracing. Restraint in all 
directions similar to underground mains, high pressure discharge with 360 
degree, upward restraint, 180 degree nozzles rotational restraint. No question 
that clean agent delivered to protected area. Seen 180 nozzles rotate above 
ceiling on discharg and 360 nozzles raising up above ceiling upon discharge. 
Sprinkler System seismic restraint on Clean Agent for us is not considered 
seismic as much as necessary system component. No question about meeting 
seismic capabilitiy. 

 From: r...@rapidfireinc.com
 To: sprinklerforum@firesprinkler.org
 Date: Mon, 8 Aug 2011 12:41:01 -0600
 Subject: RE: Seismic Bracing - Clean Agent
 
 We braced the clean agent as we normally would and interpreted it to mean 
 that no additional seismic would be required. Sprinkler system in same area 
 hung as per usual but fully EQ braced. USACE project. I was curious as to why 
 but once the response came back that no additional bracing was required I 
 wasn't near as anxious to dig into it. It will be interesting to see if Bill 
 gets anything back from NFPA.
 
 -Original Message-
 From: sprinklerforum-boun...@firesprinkler.org 
 [mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of 
 craig.pr...@ch2m.com
 Sent: Monday, August 08, 2011 12:31 PM
 To: sprinklerforum@firesprinkler.org
 Subject: RE: Seismic Bracing - Clean Agent
 
 So how did you interpret that since there are no specific bracing 
 requirements or methods stated within NFPA 2001 other than to say it is to be 
 securely supported?
 
 Craig L. Prahl, CET
 Fire Protection
 CH2MHILL
 Lockwood Greene
 1500 International Drive
 Spartanburg, SC  29304-0491
 Direct - 864.599.4102
 Fax - 864.599.8439
 CH2MHILL Extension 74102
 craig.pr...@ch2m.com
 
 
 
 -Original Message-
 From: sprinklerforum-boun...@firesprinkler.org 
 [mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of Rod 
 DiBona
 Sent: Monday, August 08, 2011 2:05 PM
 To: sprinklerforum@firesprinkler.org
 Subject: RE: Seismic Bracing - Clean Agent
 
 Had a large clean agent project where we sent an RFI with the same question. 
 Their response was that the bracing requirements of NFPA 2001 were 
 sufficient. The sprinkler system had seismic and each brace even had to be 
 modeled. 
 
 -Original Message-
 From: sprinklerforum-boun...@firesprinkler.org 
 [mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of Bill 
 Brooks
 Sent: Monday, August 08, 2011 11:31 AM
 To: sprinklerforum@firesprinkler.org
 Subject: Seismic Bracing - Clean Agent
 
 Perhaps a bit off the reservation here but does anyone out there have some 
 reason for the lack of clean agent system seismic bracing requirements?
 Empty piping? Bracing already factored into piping design per ???
 
 Feel free to send me to another listserv if one exists for special hazard 
 systems.
 
 Bill Brooks
 
 William N. Brooks, P.E.
 Brooks Fire Protection Engineering Inc.
 372 Wilett Drive
 Severna Park, MD 21146-1904
 410-544-3620
 410-544-3032 FAX
 412-400-6528 Cell
 
 
 ___
 Sprinklerforum mailing list
 Sprinklerforum@firesprinkler.org
 http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
 
 For Technical Assistance, send an email to: supp...@firesprinkler.org
 
 To Unsubscribe, send an email 
 to:sprinklerforum-requ...@firesprinkler.org
 (Put the word unsubscribe in the subject field) 
 ___
 Sprinklerforum mailing list
 Sprinklerforum@firesprinkler.org
 http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
 
 For Technical Assistance, send an email to: supp...@firesprinkler.org
 
 To Unsubscribe, send an email 
 to:sprinklerforum-requ...@firesprinkler.org
 (Put the word unsubscribe in the subject field) 
 ___
 Sprinklerforum mailing list
 Sprinklerforum@firesprinkler.org
 http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
 
 For Technical Assistance, send an email to: supp...@firesprinkler.org
 
 To Unsubscribe, send an email 
 to:sprinklerforum-requ...@firesprinkler.org
 (Put the word unsubscribe in the subject field) 
 ___
 

Re: Seismic Bracing - Clean Agent

2011-08-09 Thread Ron Greenman
So the purpose of the bracing on clean agents is to keep the pipe from
moving (reacting) to the forces exerted on it by the discharge of the agent,
whereas the purpose of EQ bracing is to force the pipe to move (overcome
inertia) in relation and parallel to the movement of the building. Standard
sprinkler hanging/bracing/restraint rules are adequate for sprinkler
discharge forces. Empty clean agent piping is lighter (less inertia to
overcome) than water-filled sprinkler piping (typically more and bigger) in
an earthquake. Seems we have not only apples and oranges here but an entire
fruit salad. I'm kind of leery when it comes to buying one set of numbers
covers two completely different scenarios when so many variables are
present. Just because ASME 7 is referenced doesn't say that EQ rules are
covered.

On Tue, Aug 9, 2011 at 8:39 AM, Rod DiBona r...@rapidfireinc.com wrote:

 Well I think that might be the point. The bracing that is needed (although
 not stated) on clean agent is clearly very robust. The question however is
 are additional listed seismic braces required to be installed and
 calculated? My experience has been no they are not, but this has been driven
 by AHJ response. I have wondered as Bill did as to the intent of the code
 and standard. I will shoot our main manufacturer and email and share the
 results back to the forum.

 -Original Message-
 From: sprinklerforum-boun...@firesprinkler.org [mailto:
 sprinklerforum-boun...@firesprinkler.org] On Behalf Of max brown
 Sent: Monday, August 08, 2011 6:42 PM
 To: burtell
 Subject: RE: Seismic Bracing - Clean Agent


 On our installations we always have additional bracing. Restraint in all
 directions similar to underground mains, high pressure discharge with 360
 degree, upward restraint, 180 degree nozzles rotational restraint. No
 question that clean agent delivered to protected area. Seen 180 nozzles
 rotate above ceiling on discharg and 360 nozzles raising up above ceiling
 upon discharge. Sprinkler System seismic restraint on Clean Agent for us is
 not considered seismic as much as necessary system component. No question
 about meeting seismic capabilitiy.

  From: r...@rapidfireinc.com
  To: sprinklerforum@firesprinkler.org
  Date: Mon, 8 Aug 2011 12:41:01 -0600
  Subject: RE: Seismic Bracing - Clean Agent
 
  We braced the clean agent as we normally would and interpreted it to mean
 that no additional seismic would be required. Sprinkler system in same area
 hung as per usual but fully EQ braced. USACE project. I was curious as to
 why but once the response came back that no additional bracing was required
 I wasn't near as anxious to dig into it. It will be interesting to see if
 Bill gets anything back from NFPA.
 
  -Original Message-
  From: sprinklerforum-boun...@firesprinkler.org
  [mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of
  craig.pr...@ch2m.com
  Sent: Monday, August 08, 2011 12:31 PM
  To: sprinklerforum@firesprinkler.org
  Subject: RE: Seismic Bracing - Clean Agent
 
  So how did you interpret that since there are no specific bracing
 requirements or methods stated within NFPA 2001 other than to say it is to
 be securely supported?
 
  Craig L. Prahl, CET
  Fire Protection
  CH2MHILL
  Lockwood Greene
  1500 International Drive
  Spartanburg, SC  29304-0491
  Direct - 864.599.4102
  Fax - 864.599.8439
  CH2MHILL Extension 74102
  craig.pr...@ch2m.com
 
 
 
  -Original Message-
  From: sprinklerforum-boun...@firesprinkler.org
  [mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of Rod
  DiBona
  Sent: Monday, August 08, 2011 2:05 PM
  To: sprinklerforum@firesprinkler.org
  Subject: RE: Seismic Bracing - Clean Agent
 
  Had a large clean agent project where we sent an RFI with the same
 question. Their response was that the bracing requirements of NFPA 2001 were
 sufficient. The sprinkler system had seismic and each brace even had to be
 modeled.
 
  -Original Message-
  From: sprinklerforum-boun...@firesprinkler.org
  [mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of Bill
  Brooks
  Sent: Monday, August 08, 2011 11:31 AM
  To: sprinklerforum@firesprinkler.org
  Subject: Seismic Bracing - Clean Agent
 
  Perhaps a bit off the reservation here but does anyone out there have
 some reason for the lack of clean agent system seismic bracing requirements?
  Empty piping? Bracing already factored into piping design per ???
 
  Feel free to send me to another listserv if one exists for special hazard
 systems.
 
  Bill Brooks
 
  William N. Brooks, P.E.
  Brooks Fire Protection Engineering Inc.
  372 Wilett Drive
  Severna Park, MD 21146-1904
  410-544-3620
  410-544-3032 FAX
  412-400-6528 Cell
 
 
  ___
  Sprinklerforum mailing list
  Sprinklerforum@firesprinkler.org
  http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
 
  For Technical Assistance, send an email to: supp...@firesprinkler.org
 
  To 

Water storage

2011-08-09 Thread A.P.Silva
The duration of water supply for a hydraulically calculated ord. hazard
sprinkler system is 60 to 90 minutes. So if the sprinkler demand is 250 gpm
the required water storage is 15,000 gallons using the lower duration. There
used to be a requirement (which I don't see now) that the water supply
should be 150% of the pump rating. Is that still required? The rated
capacity of the pump in this case is 250 gpm. 

Also, is 60 minute duration enough for fire department hose streams? So,
water storage for hose streams is another 15,000 gallons?

Tony  

___
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: supp...@firesprinkler.org

To Unsubscribe, send an email to:sprinklerforum-requ...@firesprinkler.org
(Put the word unsubscribe in the subject field)


RE: Water storage

2011-08-09 Thread Craig.Prahl
Assuming Ord. II at .20/gpm sf over 1500 sf would be 300 gpm flow rate minimum. 
 Now remember that sprinkler system flows will always exceed the base design 
criteria because the .20gpm/sf is the hyd. remote sprinkler and those upstream 
will put out more. So typically you will see a 10-15% overage in actual system 
flow.  To be conservative for a wet system if you take that 300 gpm and than 
increase that by 15% you'd get 345 gpm.  Just say 350 for simplicity.  Then add 
the 250 gpm for hose stream allowance and you've got 600 gpm total system 
demand.  For total capacity at 60  minutes (IF THE SPRINKLER SYSTEM WATERFLOW, 
TAMPER SWITCHES AND SUPERVISORY DEVICES ARE ELECTRICALLY SUPERVISED) 600 GPM X 
60 MINUTES = 36000 gallons.  If you have to use the higher value you'd be 
looking at 54000 gallons.   

Fire department hydrant hose streams fall under the category of Fire Flow 
within the Fire Code.  This is a whole other topic of discussion that can get 
rather muddied and is very often totally overlooked by the EOR or others 
designing underground fire service piping systems.   If the local Fire Service 
requires a site or building to provide Fire Flow the flow rates and durations 
can be considerably higher.   One recent project I had was requiring over a 
million gallons of storage for fire flow based on unprotected building size and 
construction types.  IFC Appendix B was applied as the approved method.   I 
have encountered few fire protection system designers and engineers who 
understand or even implement the fire flow section of the Code.

Craig L. Prahl, CET   
Fire Protection 
CH2MHILL
Lockwood Greene
1500 International Drive
Spartanburg, SC  29304-0491
Direct - 864.599.4102
Fax - 864.599.8439
CH2MHILL Extension  74102
craig.pr...@ch2m.com


-Original Message-
From: sprinklerforum-boun...@firesprinkler.org 
[mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of A.P.Silva
Sent: Tuesday, August 09, 2011 12:41 PM
To: sprinklerforum@firesprinkler.org
Subject: Water storage

The duration of water supply for a hydraulically calculated ord. hazard
sprinkler system is 60 to 90 minutes. So if the sprinkler demand is 250 gpm
the required water storage is 15,000 gallons using the lower duration. There
used to be a requirement (which I don't see now) that the water supply
should be 150% of the pump rating. Is that still required? The rated
capacity of the pump in this case is 250 gpm. 

Also, is 60 minute duration enough for fire department hose streams? So,
water storage for hose streams is another 15,000 gallons?

Tony  

___
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: supp...@firesprinkler.org

To Unsubscribe, send an email to:sprinklerforum-requ...@firesprinkler.org
(Put the word unsubscribe in the subject field)
___
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: supp...@firesprinkler.org

To Unsubscribe, send an email to:sprinklerforum-requ...@firesprinkler.org
(Put the word unsubscribe in the subject field)


RE: Water storage

2011-08-09 Thread George Church
And it is unusual in our operating areas to have the fire flows enforced.
So if you have an OH1 density, you may only need to furnish 15,000 gallons if 
you have no hydrants or hose supplied by the tank pump.
I sell a lot of tanks and pumps with 30,000 gal for OH II retail when my 
competitor figures 45,000 gallons stored.
Read the standard. Understand the building code. Talk to the AHJ so you're not 
15,000 gallons short. Clarify in proposal you have 15k.
Read the indemnification clause in the GC contract before signing and 
returning. Install, add water, invoice and sell em ITM.

George L.  Church, Jr., CET , GAC
Rowe Sprinkler Systems, Inc.
PO Box 407, Middleburg, PA 17842
877-324-ROWE   570-837-6335 fax
g...@rowesprinkler.com



-Original Message-
From: sprinklerforum-boun...@firesprinkler.org 
[mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of 
craig.pr...@ch2m.com
Sent: Tuesday, August 09, 2011 1:14 PM
To: sprinklerforum@firesprinkler.org
Subject: RE: Water storage

Assuming Ord. II at .20/gpm sf over 1500 sf would be 300 gpm flow rate minimum. 
 Now remember that sprinkler system flows will always exceed the base design 
criteria because the .20gpm/sf is the hyd. remote sprinkler and those upstream 
will put out more. So typically you will see a 10-15% overage in actual system 
flow.  To be conservative for a wet system if you take that 300 gpm and than 
increase that by 15% you'd get 345 gpm.  Just say 350 for simplicity.  Then add 
the 250 gpm for hose stream allowance and you've got 600 gpm total system 
demand.  For total capacity at 60  minutes (IF THE SPRINKLER SYSTEM WATERFLOW, 
TAMPER SWITCHES AND SUPERVISORY DEVICES ARE ELECTRICALLY SUPERVISED) 600 GPM X 
60 MINUTES = 36000 gallons.  If you have to use the higher value you'd be 
looking at 54000 gallons.   

Fire department hydrant hose streams fall under the category of Fire Flow 
within the Fire Code.  This is a whole other topic of discussion that can get 
rather muddied and is very often totally overlooked by the EOR or others 
designing underground fire service piping systems.   If the local Fire Service 
requires a site or building to provide Fire Flow the flow rates and durations 
can be considerably higher.   One recent project I had was requiring over a 
million gallons of storage for fire flow based on unprotected building size and 
construction types.  IFC Appendix B was applied as the approved method.   I 
have encountered few fire protection system designers and engineers who 
understand or even implement the fire flow section of the Code.

Craig L. Prahl, CET   
Fire Protection 
CH2MHILL
Lockwood Greene
1500 International Drive
Spartanburg, SC  29304-0491
Direct - 864.599.4102
Fax - 864.599.8439
CH2MHILL Extension  74102
craig.pr...@ch2m.com


-Original Message-
From: sprinklerforum-boun...@firesprinkler.org 
[mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of A.P.Silva
Sent: Tuesday, August 09, 2011 12:41 PM
To: sprinklerforum@firesprinkler.org
Subject: Water storage

The duration of water supply for a hydraulically calculated ord. hazard
sprinkler system is 60 to 90 minutes. So if the sprinkler demand is 250 gpm
the required water storage is 15,000 gallons using the lower duration. There
used to be a requirement (which I don't see now) that the water supply
should be 150% of the pump rating. Is that still required? The rated
capacity of the pump in this case is 250 gpm. 

Also, is 60 minute duration enough for fire department hose streams? So,
water storage for hose streams is another 15,000 gallons?

Tony  

___
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: supp...@firesprinkler.org

To Unsubscribe, send an email to:sprinklerforum-requ...@firesprinkler.org
(Put the word unsubscribe in the subject field)
___
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: supp...@firesprinkler.org

To Unsubscribe, send an email to:sprinklerforum-requ...@firesprinkler.org
(Put the word unsubscribe in the subject field)
___
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: supp...@firesprinkler.org

To Unsubscribe, send an email to:sprinklerforum-requ...@firesprinkler.org
(Put the word unsubscribe in the subject field)


RE: Water storage

2011-08-09 Thread A.P.Silva
The maximum sprinkler demand was 250 gpm. This is a health centre with three
mechanical rooms, the largest being about 1100 sq.ft. The most demanding
area is this mech. room, which I classified as OH 1. 

Providing water for the fire flow is not my responsibility, and I don't want
to go there. This site doesn't have any water (even domestic water is
stored). Disregarding the fireflow, I think I should ensure that at least
the hose allowances are available. My question was, would you use the same
duration, 60 to 90 minutes for the hose allowances? I'm asking this question
as depending on response time, the demand for sprinlers and hose may not
occur concurrently.

Another reason is to understand the concept. Is the hose allowance just a
glorified safety factor? I would think the fire department would be pulling
more than 100 gpm or 250 gpm when the pumper truck connects to a hydrant.

Tony 

-Original Message-
From: sprinklerforum-boun...@firesprinkler.org
[mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of
craig.pr...@ch2m.com
Sent: August 9, 2011 11:14 AM
To: sprinklerforum@firesprinkler.org
Subject: RE: Water storage

Assuming Ord. II at .20/gpm sf over 1500 sf would be 300 gpm flow rate
minimum.  Now remember that sprinkler system flows will always exceed the
base design criteria because the .20gpm/sf is the hyd. remote sprinkler and
those upstream will put out more. So typically you will see a 10-15% overage
in actual system flow.  To be conservative for a wet system if you take that
300 gpm and than increase that by 15% you'd get 345 gpm.  Just say 350 for
simplicity.  Then add the 250 gpm for hose stream allowance and you've got
600 gpm total system demand.  For total capacity at 60  minutes (IF THE
SPRINKLER SYSTEM WATERFLOW, TAMPER SWITCHES AND SUPERVISORY DEVICES ARE
ELECTRICALLY SUPERVISED) 600 GPM X 60 MINUTES = 36000 gallons.  If you have
to use the higher value you'd be looking at 54000 gallons.   

Fire department hydrant hose streams fall under the category of Fire Flow
within the Fire Code.  This is a whole other topic of discussion that can
get rather muddied and is very often totally overlooked by the EOR or others
designing underground fire service piping systems.   If the local Fire
Service requires a site or building to provide Fire Flow the flow rates and
durations can be considerably higher.   One recent project I had was
requiring over a million gallons of storage for fire flow based on
unprotected building size and construction types.  IFC Appendix B was
applied as the approved method.   I have encountered few fire protection
system designers and engineers who understand or even implement the fire
flow section of the Code.

Craig L. Prahl, CET   
Fire Protection
CH2MHILL
Lockwood Greene
1500 International Drive
Spartanburg, SC  29304-0491
Direct - 864.599.4102
Fax - 864.599.8439
CH2MHILL Extension  74102
craig.pr...@ch2m.com


-Original Message-
From: sprinklerforum-boun...@firesprinkler.org
[mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of A.P.Silva
Sent: Tuesday, August 09, 2011 12:41 PM
To: sprinklerforum@firesprinkler.org
Subject: Water storage

The duration of water supply for a hydraulically calculated ord. hazard
sprinkler system is 60 to 90 minutes. So if the sprinkler demand is 250 gpm
the required water storage is 15,000 gallons using the lower duration. There
used to be a requirement (which I don't see now) that the water supply
should be 150% of the pump rating. Is that still required? The rated
capacity of the pump in this case is 250 gpm. 

Also, is 60 minute duration enough for fire department hose streams? So,
water storage for hose streams is another 15,000 gallons?

Tony  

___
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: supp...@firesprinkler.org

To Unsubscribe, send an email to:sprinklerforum-requ...@firesprinkler.org
(Put the word unsubscribe in the subject field)
___
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: supp...@firesprinkler.org

To Unsubscribe, send an email to:sprinklerforum-requ...@firesprinkler.org
(Put the word unsubscribe in the subject field)

___
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: supp...@firesprinkler.org

To Unsubscribe, send an email to:sprinklerforum-requ...@firesprinkler.org
(Put the word unsubscribe in the subject field)


RE: Water storage

2011-08-09 Thread Bill Brooks
13-494 Log #356 AUT-SSD Final Action: Accept
(23.1.2)

Submitter: Kenneth E. Isman, National Fire Sprinkler Association, Inc.
Recommendation: Revise text to read as follows:
23.1.2 Capacity. Water supplies shall be capable of providing the required
flow and pressure for the remote design area determined using the procedures
in Chapters 11 through 22 for the required duration as specified in Chapter
11,
Chapter 12 and through Chapter 21.
Substantiation: The water supply only needs to provide the duration for the
remote area, not the closer sprinklers in the system that will discharge
more
water. Also, all of the discharge chapters need to be specified, not just
the basic
storage Chapter 12.
Committee Meeting Action: Accept
Number Eligible to Vote: 25
Ballot Results: Affirmative: 22
Ballot Not Returned: 3 Brown, T., Hogan, A., McNamara, T.


Bill Brooks

William N. Brooks, P.E.
Brooks Fire Protection Engineering Inc.
372 Wilett Drive
Severna Park, MD 21146-1904
410-544-3620
410-544-3032 FAX
412-400-6528 Cell


-Original Message-
From: sprinklerforum-boun...@firesprinkler.org
[mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of
craig.pr...@ch2m.com
Sent: Tuesday, August 09, 2011 1:14 PM
To: sprinklerforum@firesprinkler.org
Subject: RE: Water storage

Assuming Ord. II at .20/gpm sf over 1500 sf would be 300 gpm flow rate
minimum.  Now remember that sprinkler system flows will always exceed the
base design criteria because the .20gpm/sf is the hyd. remote sprinkler and
those upstream will put out more. So typically you will see a 10-15% overage
in actual system flow.  To be conservative for a wet system if you take that
300 gpm and than increase that by 15% you'd get 345 gpm.  Just say 350 for
simplicity.  Then add the 250 gpm for hose stream allowance and you've got
600 gpm total system demand.  For total capacity at 60  minutes (IF THE
SPRINKLER SYSTEM WATERFLOW, TAMPER SWITCHES AND SUPERVISORY DEVICES ARE
ELECTRICALLY SUPERVISED) 600 GPM X 60 MINUTES = 36000 gallons.  If you have
to use the higher value you'd be looking at 54000 gallons.   

Fire department hydrant hose streams fall under the category of Fire Flow
within the Fire Code.  This is a whole other topic of discussion that can
get rather muddied and is very often totally overlooked by the EOR or others
designing underground fire service piping systems.   If the local Fire
Service requires a site or building to provide Fire Flow the flow rates and
durations can be considerably higher.   One recent project I had was
requiring over a million gallons of storage for fire flow based on
unprotected building size and construction types.  IFC Appendix B was
applied as the approved method.   I have encountered few fire protection
system designers and engineers who understand or even implement the fire
flow section of the Code.

Craig L. Prahl, CET   
Fire Protection 
CH2MHILL
Lockwood Greene
1500 International Drive
Spartanburg, SC  29304-0491
Direct - 864.599.4102
Fax - 864.599.8439
CH2MHILL Extension  74102
craig.pr...@ch2m.com


-Original Message-
From: sprinklerforum-boun...@firesprinkler.org
[mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of A.P.Silva
Sent: Tuesday, August 09, 2011 12:41 PM
To: sprinklerforum@firesprinkler.org
Subject: Water storage

The duration of water supply for a hydraulically calculated ord. hazard
sprinkler system is 60 to 90 minutes. So if the sprinkler demand is 250 gpm
the required water storage is 15,000 gallons using the lower duration. There
used to be a requirement (which I don't see now) that the water supply
should be 150% of the pump rating. Is that still required? The rated
capacity of the pump in this case is 250 gpm. 

Also, is 60 minute duration enough for fire department hose streams? So,
water storage for hose streams is another 15,000 gallons?

Tony  

___
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: supp...@firesprinkler.org

To Unsubscribe, send an email to:sprinklerforum-requ...@firesprinkler.org
(Put the word unsubscribe in the subject field)
___
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: supp...@firesprinkler.org

To Unsubscribe, send an email to:sprinklerforum-requ...@firesprinkler.org
(Put the word unsubscribe in the subject field)

___
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: supp...@firesprinkler.org

To Unsubscribe, send an email to:sprinklerforum-requ...@firesprinkler.org
(Put the word 

RE: Water storage

2011-08-09 Thread Craig.Prahl
If you have no municipal water and no hydrants and no interior hose valves then 
the hose stream allowance is not a factor.  Use the most demanding sprinkler 
flow to determine duration.

Question, is there a fire alarm system that is monitoring the sprinkler 
supervisory devices?  

We've addressed the hose stream allowance in regard to sprinkler calcs in depth 
on another thread.



Craig L. Prahl, CET   
Fire Protection 
CH2MHILL
Lockwood Greene
1500 International Drive
Spartanburg, SC  29304-0491
Direct - 864.599.4102
Fax - 864.599.8439
CH2MHILL Extension  74102
craig.pr...@ch2m.com



-Original Message-
From: sprinklerforum-boun...@firesprinkler.org 
[mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of A.P.Silva
Sent: Tuesday, August 09, 2011 1:59 PM
To: sprinklerforum@firesprinkler.org
Subject: RE: Water storage

The maximum sprinkler demand was 250 gpm. This is a health centre with three
mechanical rooms, the largest being about 1100 sq.ft. The most demanding
area is this mech. room, which I classified as OH 1. 

Providing water for the fire flow is not my responsibility, and I don't want
to go there. This site doesn't have any water (even domestic water is
stored). Disregarding the fireflow, I think I should ensure that at least
the hose allowances are available. My question was, would you use the same
duration, 60 to 90 minutes for the hose allowances? I'm asking this question
as depending on response time, the demand for sprinlers and hose may not
occur concurrently.

Another reason is to understand the concept. Is the hose allowance just a
glorified safety factor? I would think the fire department would be pulling
more than 100 gpm or 250 gpm when the pumper truck connects to a hydrant.

Tony 

-Original Message-
From: sprinklerforum-boun...@firesprinkler.org
[mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of
craig.pr...@ch2m.com
Sent: August 9, 2011 11:14 AM
To: sprinklerforum@firesprinkler.org
Subject: RE: Water storage

Assuming Ord. II at .20/gpm sf over 1500 sf would be 300 gpm flow rate
minimum.  Now remember that sprinkler system flows will always exceed the
base design criteria because the .20gpm/sf is the hyd. remote sprinkler and
those upstream will put out more. So typically you will see a 10-15% overage
in actual system flow.  To be conservative for a wet system if you take that
300 gpm and than increase that by 15% you'd get 345 gpm.  Just say 350 for
simplicity.  Then add the 250 gpm for hose stream allowance and you've got
600 gpm total system demand.  For total capacity at 60  minutes (IF THE
SPRINKLER SYSTEM WATERFLOW, TAMPER SWITCHES AND SUPERVISORY DEVICES ARE
ELECTRICALLY SUPERVISED) 600 GPM X 60 MINUTES = 36000 gallons.  If you have
to use the higher value you'd be looking at 54000 gallons.   

Fire department hydrant hose streams fall under the category of Fire Flow
within the Fire Code.  This is a whole other topic of discussion that can
get rather muddied and is very often totally overlooked by the EOR or others
designing underground fire service piping systems.   If the local Fire
Service requires a site or building to provide Fire Flow the flow rates and
durations can be considerably higher.   One recent project I had was
requiring over a million gallons of storage for fire flow based on
unprotected building size and construction types.  IFC Appendix B was
applied as the approved method.   I have encountered few fire protection
system designers and engineers who understand or even implement the fire
flow section of the Code.

Craig L. Prahl, CET   
Fire Protection
CH2MHILL
Lockwood Greene
1500 International Drive
Spartanburg, SC  29304-0491
Direct - 864.599.4102
Fax - 864.599.8439
CH2MHILL Extension  74102
craig.pr...@ch2m.com


-Original Message-
From: sprinklerforum-boun...@firesprinkler.org
[mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of A.P.Silva
Sent: Tuesday, August 09, 2011 12:41 PM
To: sprinklerforum@firesprinkler.org
Subject: Water storage

The duration of water supply for a hydraulically calculated ord. hazard
sprinkler system is 60 to 90 minutes. So if the sprinkler demand is 250 gpm
the required water storage is 15,000 gallons using the lower duration. There
used to be a requirement (which I don't see now) that the water supply
should be 150% of the pump rating. Is that still required? The rated
capacity of the pump in this case is 250 gpm. 

Also, is 60 minute duration enough for fire department hose streams? So,
water storage for hose streams is another 15,000 gallons?

Tony  

___
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: supp...@firesprinkler.org

To Unsubscribe, send an email to:sprinklerforum-requ...@firesprinkler.org
(Put the word unsubscribe in the subject field)
___

RE: Water storage

2011-08-09 Thread Craig.Prahl
OK?

Craig L. Prahl, CET   
Fire Protection 
CH2MHILL
Lockwood Greene
1500 International Drive
Spartanburg, SC  29304-0491
Direct - 864.599.4102
Fax - 864.599.8439
CH2MHILL Extension  74102
craig.pr...@ch2m.com



-Original Message-
From: sprinklerforum-boun...@firesprinkler.org 
[mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of Bill Brooks
Sent: Tuesday, August 09, 2011 2:02 PM
To: sprinklerforum@firesprinkler.org
Subject: RE: Water storage

13-494 Log #356 AUT-SSD Final Action: Accept
(23.1.2)

Submitter: Kenneth E. Isman, National Fire Sprinkler Association, Inc.
Recommendation: Revise text to read as follows:
23.1.2 Capacity. Water supplies shall be capable of providing the required
flow and pressure for the remote design area determined using the procedures
in Chapters 11 through 22 for the required duration as specified in Chapter
11,
Chapter 12 and through Chapter 21.
Substantiation: The water supply only needs to provide the duration for the
remote area, not the closer sprinklers in the system that will discharge
more
water. Also, all of the discharge chapters need to be specified, not just
the basic
storage Chapter 12.
Committee Meeting Action: Accept
Number Eligible to Vote: 25
Ballot Results: Affirmative: 22
Ballot Not Returned: 3 Brown, T., Hogan, A., McNamara, T.


Bill Brooks

William N. Brooks, P.E.
Brooks Fire Protection Engineering Inc.
372 Wilett Drive
Severna Park, MD 21146-1904
410-544-3620
410-544-3032 FAX
412-400-6528 Cell


-Original Message-
From: sprinklerforum-boun...@firesprinkler.org
[mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of
craig.pr...@ch2m.com
Sent: Tuesday, August 09, 2011 1:14 PM
To: sprinklerforum@firesprinkler.org
Subject: RE: Water storage

Assuming Ord. II at .20/gpm sf over 1500 sf would be 300 gpm flow rate
minimum.  Now remember that sprinkler system flows will always exceed the
base design criteria because the .20gpm/sf is the hyd. remote sprinkler and
those upstream will put out more. So typically you will see a 10-15% overage
in actual system flow.  To be conservative for a wet system if you take that
300 gpm and than increase that by 15% you'd get 345 gpm.  Just say 350 for
simplicity.  Then add the 250 gpm for hose stream allowance and you've got
600 gpm total system demand.  For total capacity at 60  minutes (IF THE
SPRINKLER SYSTEM WATERFLOW, TAMPER SWITCHES AND SUPERVISORY DEVICES ARE
ELECTRICALLY SUPERVISED) 600 GPM X 60 MINUTES = 36000 gallons.  If you have
to use the higher value you'd be looking at 54000 gallons.   

Fire department hydrant hose streams fall under the category of Fire Flow
within the Fire Code.  This is a whole other topic of discussion that can
get rather muddied and is very often totally overlooked by the EOR or others
designing underground fire service piping systems.   If the local Fire
Service requires a site or building to provide Fire Flow the flow rates and
durations can be considerably higher.   One recent project I had was
requiring over a million gallons of storage for fire flow based on
unprotected building size and construction types.  IFC Appendix B was
applied as the approved method.   I have encountered few fire protection
system designers and engineers who understand or even implement the fire
flow section of the Code.

Craig L. Prahl, CET   
Fire Protection 
CH2MHILL
Lockwood Greene
1500 International Drive
Spartanburg, SC  29304-0491
Direct - 864.599.4102
Fax - 864.599.8439
CH2MHILL Extension  74102
craig.pr...@ch2m.com


-Original Message-
From: sprinklerforum-boun...@firesprinkler.org
[mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of A.P.Silva
Sent: Tuesday, August 09, 2011 12:41 PM
To: sprinklerforum@firesprinkler.org
Subject: Water storage

The duration of water supply for a hydraulically calculated ord. hazard
sprinkler system is 60 to 90 minutes. So if the sprinkler demand is 250 gpm
the required water storage is 15,000 gallons using the lower duration. There
used to be a requirement (which I don't see now) that the water supply
should be 150% of the pump rating. Is that still required? The rated
capacity of the pump in this case is 250 gpm. 

Also, is 60 minute duration enough for fire department hose streams? So,
water storage for hose streams is another 15,000 gallons?

Tony  

___
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: supp...@firesprinkler.org

To Unsubscribe, send an email to:sprinklerforum-requ...@firesprinkler.org
(Put the word unsubscribe in the subject field)
___
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: 

RE: Water storage

2011-08-09 Thread A.P.Silva
I need to supply a fire hydrant, but will categorically state that the water
storage is not for the fire flow. Yes, there is an alarm system monitoring
the sprinkler supervisory devices. The building code requires all
sprinklered buildings to have an alarm system.

Tony  

-Original Message-
From: sprinklerforum-boun...@firesprinkler.org
[mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of
craig.pr...@ch2m.com
Sent: August 9, 2011 12:06 PM
To: sprinklerforum@firesprinkler.org
Subject: RE: Water storage

If you have no municipal water and no hydrants and no interior hose valves
then the hose stream allowance is not a factor.  Use the most demanding
sprinkler flow to determine duration.

Question, is there a fire alarm system that is monitoring the sprinkler
supervisory devices?  

We've addressed the hose stream allowance in regard to sprinkler calcs in
depth on another thread.



Craig L. Prahl, CET   
Fire Protection
CH2MHILL
Lockwood Greene
1500 International Drive
Spartanburg, SC  29304-0491
Direct - 864.599.4102
Fax - 864.599.8439
CH2MHILL Extension  74102
craig.pr...@ch2m.com



-Original Message-
From: sprinklerforum-boun...@firesprinkler.org
[mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of A.P.Silva
Sent: Tuesday, August 09, 2011 1:59 PM
To: sprinklerforum@firesprinkler.org
Subject: RE: Water storage

The maximum sprinkler demand was 250 gpm. This is a health centre with three
mechanical rooms, the largest being about 1100 sq.ft. The most demanding
area is this mech. room, which I classified as OH 1. 

Providing water for the fire flow is not my responsibility, and I don't want
to go there. This site doesn't have any water (even domestic water is
stored). Disregarding the fireflow, I think I should ensure that at least
the hose allowances are available. My question was, would you use the same
duration, 60 to 90 minutes for the hose allowances? I'm asking this question
as depending on response time, the demand for sprinlers and hose may not
occur concurrently.

Another reason is to understand the concept. Is the hose allowance just a
glorified safety factor? I would think the fire department would be pulling
more than 100 gpm or 250 gpm when the pumper truck connects to a hydrant.

Tony 

-Original Message-
From: sprinklerforum-boun...@firesprinkler.org
[mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of
craig.pr...@ch2m.com
Sent: August 9, 2011 11:14 AM
To: sprinklerforum@firesprinkler.org
Subject: RE: Water storage

Assuming Ord. II at .20/gpm sf over 1500 sf would be 300 gpm flow rate
minimum.  Now remember that sprinkler system flows will always exceed the
base design criteria because the .20gpm/sf is the hyd. remote sprinkler and
those upstream will put out more. So typically you will see a 10-15% overage
in actual system flow.  To be conservative for a wet system if you take that
300 gpm and than increase that by 15% you'd get 345 gpm.  Just say 350 for
simplicity.  Then add the 250 gpm for hose stream allowance and you've got
600 gpm total system demand.  For total capacity at 60  minutes (IF THE
SPRINKLER SYSTEM WATERFLOW, TAMPER SWITCHES AND SUPERVISORY DEVICES ARE
ELECTRICALLY SUPERVISED) 600 GPM X 60 MINUTES = 36000 gallons.  If you have
to use the higher value you'd be looking at 54000 gallons.   

Fire department hydrant hose streams fall under the category of Fire Flow
within the Fire Code.  This is a whole other topic of discussion that can
get rather muddied and is very often totally overlooked by the EOR or others
designing underground fire service piping systems.   If the local Fire
Service requires a site or building to provide Fire Flow the flow rates and
durations can be considerably higher.   One recent project I had was
requiring over a million gallons of storage for fire flow based on
unprotected building size and construction types.  IFC Appendix B was
applied as the approved method.   I have encountered few fire protection
system designers and engineers who understand or even implement the fire
flow section of the Code.

Craig L. Prahl, CET   
Fire Protection
CH2MHILL
Lockwood Greene
1500 International Drive
Spartanburg, SC  29304-0491
Direct - 864.599.4102
Fax - 864.599.8439
CH2MHILL Extension  74102
craig.pr...@ch2m.com


-Original Message-
From: sprinklerforum-boun...@firesprinkler.org
[mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of A.P.Silva
Sent: Tuesday, August 09, 2011 12:41 PM
To: sprinklerforum@firesprinkler.org
Subject: Water storage

The duration of water supply for a hydraulically calculated ord. hazard
sprinkler system is 60 to 90 minutes. So if the sprinkler demand is 250 gpm
the required water storage is 15,000 gallons using the lower duration. There
used to be a requirement (which I don't see now) that the water supply
should be 150% of the pump rating. Is that still required? The rated
capacity of the pump in this case is 250 gpm. 

Also, is 60 minute duration enough for 

RE: Water storage

2011-08-09 Thread Craig.Prahl
Does the alarm system only sound at the building or does it auto-dial the fire 
department, that's the issue.

So you're going to provide a fire hydrant supplied off a storage tank that is 
also supplying the building sprinklers?   What will be the point of the hydrant 
if its anticipated flow is not part of the overall duration and storage 
capacity?   Just a convenience point for neighborhood dogs?

Craig L. Prahl, CET   
Fire Protection 
CH2MHILL
Lockwood Greene
1500 International Drive
Spartanburg, SC  29304-0491
Direct - 864.599.4102
Fax - 864.599.8439
CH2MHILL Extension  74102
craig.pr...@ch2m.com



-Original Message-
From: sprinklerforum-boun...@firesprinkler.org 
[mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of A.P.Silva
Sent: Tuesday, August 09, 2011 2:18 PM
To: sprinklerforum@firesprinkler.org
Subject: RE: Water storage

I need to supply a fire hydrant, but will categorically state that the water
storage is not for the fire flow. Yes, there is an alarm system monitoring
the sprinkler supervisory devices. The building code requires all
sprinklered buildings to have an alarm system.

Tony  

-Original Message-
From: sprinklerforum-boun...@firesprinkler.org
[mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of
craig.pr...@ch2m.com
Sent: August 9, 2011 12:06 PM
To: sprinklerforum@firesprinkler.org
Subject: RE: Water storage

If you have no municipal water and no hydrants and no interior hose valves
then the hose stream allowance is not a factor.  Use the most demanding
sprinkler flow to determine duration.

Question, is there a fire alarm system that is monitoring the sprinkler
supervisory devices?  

We've addressed the hose stream allowance in regard to sprinkler calcs in
depth on another thread.



Craig L. Prahl, CET   
Fire Protection
CH2MHILL
Lockwood Greene
1500 International Drive
Spartanburg, SC  29304-0491
Direct - 864.599.4102
Fax - 864.599.8439
CH2MHILL Extension  74102
craig.pr...@ch2m.com



-Original Message-
From: sprinklerforum-boun...@firesprinkler.org
[mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of A.P.Silva
Sent: Tuesday, August 09, 2011 1:59 PM
To: sprinklerforum@firesprinkler.org
Subject: RE: Water storage

The maximum sprinkler demand was 250 gpm. This is a health centre with three
mechanical rooms, the largest being about 1100 sq.ft. The most demanding
area is this mech. room, which I classified as OH 1. 

Providing water for the fire flow is not my responsibility, and I don't want
to go there. This site doesn't have any water (even domestic water is
stored). Disregarding the fireflow, I think I should ensure that at least
the hose allowances are available. My question was, would you use the same
duration, 60 to 90 minutes for the hose allowances? I'm asking this question
as depending on response time, the demand for sprinlers and hose may not
occur concurrently.

Another reason is to understand the concept. Is the hose allowance just a
glorified safety factor? I would think the fire department would be pulling
more than 100 gpm or 250 gpm when the pumper truck connects to a hydrant.

Tony 

-Original Message-
From: sprinklerforum-boun...@firesprinkler.org
[mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of
craig.pr...@ch2m.com
Sent: August 9, 2011 11:14 AM
To: sprinklerforum@firesprinkler.org
Subject: RE: Water storage

Assuming Ord. II at .20/gpm sf over 1500 sf would be 300 gpm flow rate
minimum.  Now remember that sprinkler system flows will always exceed the
base design criteria because the .20gpm/sf is the hyd. remote sprinkler and
those upstream will put out more. So typically you will see a 10-15% overage
in actual system flow.  To be conservative for a wet system if you take that
300 gpm and than increase that by 15% you'd get 345 gpm.  Just say 350 for
simplicity.  Then add the 250 gpm for hose stream allowance and you've got
600 gpm total system demand.  For total capacity at 60  minutes (IF THE
SPRINKLER SYSTEM WATERFLOW, TAMPER SWITCHES AND SUPERVISORY DEVICES ARE
ELECTRICALLY SUPERVISED) 600 GPM X 60 MINUTES = 36000 gallons.  If you have
to use the higher value you'd be looking at 54000 gallons.   

Fire department hydrant hose streams fall under the category of Fire Flow
within the Fire Code.  This is a whole other topic of discussion that can
get rather muddied and is very often totally overlooked by the EOR or others
designing underground fire service piping systems.   If the local Fire
Service requires a site or building to provide Fire Flow the flow rates and
durations can be considerably higher.   One recent project I had was
requiring over a million gallons of storage for fire flow based on
unprotected building size and construction types.  IFC Appendix B was
applied as the approved method.   I have encountered few fire protection
system designers and engineers who understand or even implement the fire
flow section of the Code.

Craig L. Prahl, CET   
Fire Protection

RE: Water storage

2011-08-09 Thread Bill Brooks
Well, I guess my point would be that you don't have to figure any hydraulic
imbalance in your sprinkler water quantity.  Just density x area x time.
Perhaps Ken's approved proposal could be clarified to confirm.

Bill Brooks

William N. Brooks, P.E.
Brooks Fire Protection Engineering Inc.
372 Wilett Drive
Severna Park, MD 21146-1904
410-544-3620
410-544-3032 FAX
412-400-6528 Cell


-Original Message-
From: sprinklerforum-boun...@firesprinkler.org
[mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of
craig.pr...@ch2m.com
Sent: Tuesday, August 09, 2011 2:10 PM
To: sprinklerforum@firesprinkler.org
Subject: RE: Water storage

OK?

Craig L. Prahl, CET   
Fire Protection 
CH2MHILL
Lockwood Greene
1500 International Drive
Spartanburg, SC  29304-0491
Direct - 864.599.4102
Fax - 864.599.8439
CH2MHILL Extension  74102
craig.pr...@ch2m.com



-Original Message-
From: sprinklerforum-boun...@firesprinkler.org
[mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of Bill Brooks
Sent: Tuesday, August 09, 2011 2:02 PM
To: sprinklerforum@firesprinkler.org
Subject: RE: Water storage

13-494 Log #356 AUT-SSD Final Action: Accept
(23.1.2)

Submitter: Kenneth E. Isman, National Fire Sprinkler Association, Inc.
Recommendation: Revise text to read as follows:
23.1.2 Capacity. Water supplies shall be capable of providing the required
flow and pressure for the remote design area determined using the procedures
in Chapters 11 through 22 for the required duration as specified in Chapter
11,
Chapter 12 and through Chapter 21.
Substantiation: The water supply only needs to provide the duration for the
remote area, not the closer sprinklers in the system that will discharge
more
water. Also, all of the discharge chapters need to be specified, not just
the basic
storage Chapter 12.
Committee Meeting Action: Accept
Number Eligible to Vote: 25
Ballot Results: Affirmative: 22
Ballot Not Returned: 3 Brown, T., Hogan, A., McNamara, T.


Bill Brooks

William N. Brooks, P.E.
Brooks Fire Protection Engineering Inc.
372 Wilett Drive
Severna Park, MD 21146-1904
410-544-3620
410-544-3032 FAX
412-400-6528 Cell


-Original Message-
From: sprinklerforum-boun...@firesprinkler.org
[mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of
craig.pr...@ch2m.com
Sent: Tuesday, August 09, 2011 1:14 PM
To: sprinklerforum@firesprinkler.org
Subject: RE: Water storage

Assuming Ord. II at .20/gpm sf over 1500 sf would be 300 gpm flow rate
minimum.  Now remember that sprinkler system flows will always exceed the
base design criteria because the .20gpm/sf is the hyd. remote sprinkler and
those upstream will put out more. So typically you will see a 10-15% overage
in actual system flow.  To be conservative for a wet system if you take that
300 gpm and than increase that by 15% you'd get 345 gpm.  Just say 350 for
simplicity.  Then add the 250 gpm for hose stream allowance and you've got
600 gpm total system demand.  For total capacity at 60  minutes (IF THE
SPRINKLER SYSTEM WATERFLOW, TAMPER SWITCHES AND SUPERVISORY DEVICES ARE
ELECTRICALLY SUPERVISED) 600 GPM X 60 MINUTES = 36000 gallons.  If you have
to use the higher value you'd be looking at 54000 gallons.   

Fire department hydrant hose streams fall under the category of Fire Flow
within the Fire Code.  This is a whole other topic of discussion that can
get rather muddied and is very often totally overlooked by the EOR or others
designing underground fire service piping systems.   If the local Fire
Service requires a site or building to provide Fire Flow the flow rates and
durations can be considerably higher.   One recent project I had was
requiring over a million gallons of storage for fire flow based on
unprotected building size and construction types.  IFC Appendix B was
applied as the approved method.   I have encountered few fire protection
system designers and engineers who understand or even implement the fire
flow section of the Code.

Craig L. Prahl, CET   
Fire Protection 
CH2MHILL
Lockwood Greene
1500 International Drive
Spartanburg, SC  29304-0491
Direct - 864.599.4102
Fax - 864.599.8439
CH2MHILL Extension  74102
craig.pr...@ch2m.com


-Original Message-
From: sprinklerforum-boun...@firesprinkler.org
[mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of A.P.Silva
Sent: Tuesday, August 09, 2011 12:41 PM
To: sprinklerforum@firesprinkler.org
Subject: Water storage

The duration of water supply for a hydraulically calculated ord. hazard
sprinkler system is 60 to 90 minutes. So if the sprinkler demand is 250 gpm
the required water storage is 15,000 gallons using the lower duration. There
used to be a requirement (which I don't see now) that the water supply
should be 150% of the pump rating. Is that still required? The rated
capacity of the pump in this case is 250 gpm. 

Also, is 60 minute duration enough for fire department hose streams? So,
water storage for hose streams is 

RE: Water storage

2011-08-09 Thread A.P.Silva
It is a centrally monitored alarm system that dials the fire department. The
GC has requested storage tank to also supply a fire hydrant. I have informed
them that it will not provide the fire flow. But now I'm obligated (I think)
to ensure that the volume for hose allowances is also provided.

Tony 

-Original Message-
From: sprinklerforum-boun...@firesprinkler.org
[mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of
craig.pr...@ch2m.com
Sent: August 9, 2011 12:25 PM
To: sprinklerforum@firesprinkler.org
Subject: RE: Water storage

Does the alarm system only sound at the building or does it auto-dial the
fire department, that's the issue.

So you're going to provide a fire hydrant supplied off a storage tank that
is also supplying the building sprinklers?   What will be the point of the
hydrant if its anticipated flow is not part of the overall duration and
storage capacity?   Just a convenience point for neighborhood dogs?

Craig L. Prahl, CET   
Fire Protection
CH2MHILL
Lockwood Greene
1500 International Drive
Spartanburg, SC  29304-0491
Direct - 864.599.4102
Fax - 864.599.8439
CH2MHILL Extension  74102
craig.pr...@ch2m.com



-Original Message-
From: sprinklerforum-boun...@firesprinkler.org
[mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of A.P.Silva
Sent: Tuesday, August 09, 2011 2:18 PM
To: sprinklerforum@firesprinkler.org
Subject: RE: Water storage

I need to supply a fire hydrant, but will categorically state that the water
storage is not for the fire flow. Yes, there is an alarm system monitoring
the sprinkler supervisory devices. The building code requires all
sprinklered buildings to have an alarm system.

Tony  

-Original Message-
From: sprinklerforum-boun...@firesprinkler.org
[mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of
craig.pr...@ch2m.com
Sent: August 9, 2011 12:06 PM
To: sprinklerforum@firesprinkler.org
Subject: RE: Water storage

If you have no municipal water and no hydrants and no interior hose valves
then the hose stream allowance is not a factor.  Use the most demanding
sprinkler flow to determine duration.

Question, is there a fire alarm system that is monitoring the sprinkler
supervisory devices?  

We've addressed the hose stream allowance in regard to sprinkler calcs in
depth on another thread.



Craig L. Prahl, CET   
Fire Protection
CH2MHILL
Lockwood Greene
1500 International Drive
Spartanburg, SC  29304-0491
Direct - 864.599.4102
Fax - 864.599.8439
CH2MHILL Extension  74102
craig.pr...@ch2m.com



-Original Message-
From: sprinklerforum-boun...@firesprinkler.org
[mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of A.P.Silva
Sent: Tuesday, August 09, 2011 1:59 PM
To: sprinklerforum@firesprinkler.org
Subject: RE: Water storage

The maximum sprinkler demand was 250 gpm. This is a health centre with three
mechanical rooms, the largest being about 1100 sq.ft. The most demanding
area is this mech. room, which I classified as OH 1. 

Providing water for the fire flow is not my responsibility, and I don't want
to go there. This site doesn't have any water (even domestic water is
stored). Disregarding the fireflow, I think I should ensure that at least
the hose allowances are available. My question was, would you use the same
duration, 60 to 90 minutes for the hose allowances? I'm asking this question
as depending on response time, the demand for sprinlers and hose may not
occur concurrently.

Another reason is to understand the concept. Is the hose allowance just a
glorified safety factor? I would think the fire department would be pulling
more than 100 gpm or 250 gpm when the pumper truck connects to a hydrant.

Tony 

-Original Message-
From: sprinklerforum-boun...@firesprinkler.org
[mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of
craig.pr...@ch2m.com
Sent: August 9, 2011 11:14 AM
To: sprinklerforum@firesprinkler.org
Subject: RE: Water storage

Assuming Ord. II at .20/gpm sf over 1500 sf would be 300 gpm flow rate
minimum.  Now remember that sprinkler system flows will always exceed the
base design criteria because the .20gpm/sf is the hyd. remote sprinkler and
those upstream will put out more. So typically you will see a 10-15% overage
in actual system flow.  To be conservative for a wet system if you take that
300 gpm and than increase that by 15% you'd get 345 gpm.  Just say 350 for
simplicity.  Then add the 250 gpm for hose stream allowance and you've got
600 gpm total system demand.  For total capacity at 60  minutes (IF THE
SPRINKLER SYSTEM WATERFLOW, TAMPER SWITCHES AND SUPERVISORY DEVICES ARE
ELECTRICALLY SUPERVISED) 600 GPM X 60 MINUTES = 36000 gallons.  If you have
to use the higher value you'd be looking at 54000 gallons.   

Fire department hydrant hose streams fall under the category of Fire Flow
within the Fire Code.  This is a whole other topic of discussion that can
get rather muddied and is very often totally overlooked by the EOR or others
designing 

RE: Water storage

2011-08-09 Thread Craig.Prahl
But we all know that a .15 gpm/sf over 1500 gpm doesn't calc out to exactly 225 
gpm of flow and we know that most fires are controlled by 3 or less sprinklers. 
 So if someone wants to cut it that close, go for it.  

Related to the question of whether to include hose stream or not, what's 
interesting is that in other areas of 13, it is clearly spelled out that the 
demand is to include both hose and sprinklers.

But in the NFSA response it's talking about not considering the excess flow 
that is typical of sprinklers closer to the riser which are OUTSIDE of the 
remote area.  It is NOT saying anything about factoring the imbalance or 
overage for the remote area sprinklers.   

Craig L. Prahl, CET   
Fire Protection 
CH2MHILL
Lockwood Greene
1500 International Drive
Spartanburg, SC  29304-0491
Direct - 864.599.4102
Fax - 864.599.8439
CH2MHILL Extension  74102
craig.pr...@ch2m.com



-Original Message-
From: sprinklerforum-boun...@firesprinkler.org 
[mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of Bill Brooks
Sent: Tuesday, August 09, 2011 2:41 PM
To: sprinklerforum@firesprinkler.org
Subject: RE: Water storage

Well, I guess my point would be that you don't have to figure any hydraulic
imbalance in your sprinkler water quantity.  Just density x area x time.
Perhaps Ken's approved proposal could be clarified to confirm.

Bill Brooks

William N. Brooks, P.E.
Brooks Fire Protection Engineering Inc.
372 Wilett Drive
Severna Park, MD 21146-1904
410-544-3620
410-544-3032 FAX
412-400-6528 Cell


-Original Message-
From: sprinklerforum-boun...@firesprinkler.org
[mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of
craig.pr...@ch2m.com
Sent: Tuesday, August 09, 2011 2:10 PM
To: sprinklerforum@firesprinkler.org
Subject: RE: Water storage

OK?

Craig L. Prahl, CET   
Fire Protection 
CH2MHILL
Lockwood Greene
1500 International Drive
Spartanburg, SC  29304-0491
Direct - 864.599.4102
Fax - 864.599.8439
CH2MHILL Extension  74102
craig.pr...@ch2m.com



-Original Message-
From: sprinklerforum-boun...@firesprinkler.org
[mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of Bill Brooks
Sent: Tuesday, August 09, 2011 2:02 PM
To: sprinklerforum@firesprinkler.org
Subject: RE: Water storage

13-494 Log #356 AUT-SSD Final Action: Accept
(23.1.2)

Submitter: Kenneth E. Isman, National Fire Sprinkler Association, Inc.
Recommendation: Revise text to read as follows:
23.1.2 Capacity. Water supplies shall be capable of providing the required
flow and pressure for the remote design area determined using the procedures
in Chapters 11 through 22 for the required duration as specified in Chapter
11,
Chapter 12 and through Chapter 21.
Substantiation: The water supply only needs to provide the duration for the
remote area, not the closer sprinklers in the system that will discharge
more
water. Also, all of the discharge chapters need to be specified, not just
the basic
storage Chapter 12.
Committee Meeting Action: Accept
Number Eligible to Vote: 25
Ballot Results: Affirmative: 22
Ballot Not Returned: 3 Brown, T., Hogan, A., McNamara, T.


Bill Brooks

William N. Brooks, P.E.
Brooks Fire Protection Engineering Inc.
372 Wilett Drive
Severna Park, MD 21146-1904
410-544-3620
410-544-3032 FAX
412-400-6528 Cell


-Original Message-
From: sprinklerforum-boun...@firesprinkler.org
[mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of
craig.pr...@ch2m.com
Sent: Tuesday, August 09, 2011 1:14 PM
To: sprinklerforum@firesprinkler.org
Subject: RE: Water storage

Assuming Ord. II at .20/gpm sf over 1500 sf would be 300 gpm flow rate
minimum.  Now remember that sprinkler system flows will always exceed the
base design criteria because the .20gpm/sf is the hyd. remote sprinkler and
those upstream will put out more. So typically you will see a 10-15% overage
in actual system flow.  To be conservative for a wet system if you take that
300 gpm and than increase that by 15% you'd get 345 gpm.  Just say 350 for
simplicity.  Then add the 250 gpm for hose stream allowance and you've got
600 gpm total system demand.  For total capacity at 60  minutes (IF THE
SPRINKLER SYSTEM WATERFLOW, TAMPER SWITCHES AND SUPERVISORY DEVICES ARE
ELECTRICALLY SUPERVISED) 600 GPM X 60 MINUTES = 36000 gallons.  If you have
to use the higher value you'd be looking at 54000 gallons.   

Fire department hydrant hose streams fall under the category of Fire Flow
within the Fire Code.  This is a whole other topic of discussion that can
get rather muddied and is very often totally overlooked by the EOR or others
designing underground fire service piping systems.   If the local Fire
Service requires a site or building to provide Fire Flow the flow rates and
durations can be considerably higher.   One recent project I had was
requiring over a million gallons of storage for fire flow based on
unprotected building size and construction types.  IFC Appendix B 

RE: Water storage

2011-08-09 Thread Craig.Prahl
Yeah, I'd say you since you're providing a hydrant, you'll need to factor in 
the hose stream demand as all outside but it does need to be added to the 
sprinkler demand to determine total required capacity for the designated 
duration.

Craig L. Prahl, CET   
Fire Protection 
CH2MHILL
Lockwood Greene
1500 International Drive
Spartanburg, SC  29304-0491
Direct - 864.599.4102
Fax - 864.599.8439
CH2MHILL Extension  74102
craig.pr...@ch2m.com



-Original Message-
From: sprinklerforum-boun...@firesprinkler.org 
[mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of A.P.Silva
Sent: Tuesday, August 09, 2011 2:45 PM
To: sprinklerforum@firesprinkler.org
Subject: RE: Water storage

It is a centrally monitored alarm system that dials the fire department. The
GC has requested storage tank to also supply a fire hydrant. I have informed
them that it will not provide the fire flow. But now I'm obligated (I think)
to ensure that the volume for hose allowances is also provided.

Tony 

-Original Message-
From: sprinklerforum-boun...@firesprinkler.org
[mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of
craig.pr...@ch2m.com
Sent: August 9, 2011 12:25 PM
To: sprinklerforum@firesprinkler.org
Subject: RE: Water storage

Does the alarm system only sound at the building or does it auto-dial the
fire department, that's the issue.

So you're going to provide a fire hydrant supplied off a storage tank that
is also supplying the building sprinklers?   What will be the point of the
hydrant if its anticipated flow is not part of the overall duration and
storage capacity?   Just a convenience point for neighborhood dogs?

Craig L. Prahl, CET   
Fire Protection
CH2MHILL
Lockwood Greene
1500 International Drive
Spartanburg, SC  29304-0491
Direct - 864.599.4102
Fax - 864.599.8439
CH2MHILL Extension  74102
craig.pr...@ch2m.com



-Original Message-
From: sprinklerforum-boun...@firesprinkler.org
[mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of A.P.Silva
Sent: Tuesday, August 09, 2011 2:18 PM
To: sprinklerforum@firesprinkler.org
Subject: RE: Water storage

I need to supply a fire hydrant, but will categorically state that the water
storage is not for the fire flow. Yes, there is an alarm system monitoring
the sprinkler supervisory devices. The building code requires all
sprinklered buildings to have an alarm system.

Tony  

-Original Message-
From: sprinklerforum-boun...@firesprinkler.org
[mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of
craig.pr...@ch2m.com
Sent: August 9, 2011 12:06 PM
To: sprinklerforum@firesprinkler.org
Subject: RE: Water storage

If you have no municipal water and no hydrants and no interior hose valves
then the hose stream allowance is not a factor.  Use the most demanding
sprinkler flow to determine duration.

Question, is there a fire alarm system that is monitoring the sprinkler
supervisory devices?  

We've addressed the hose stream allowance in regard to sprinkler calcs in
depth on another thread.



Craig L. Prahl, CET   
Fire Protection
CH2MHILL
Lockwood Greene
1500 International Drive
Spartanburg, SC  29304-0491
Direct - 864.599.4102
Fax - 864.599.8439
CH2MHILL Extension  74102
craig.pr...@ch2m.com



-Original Message-
From: sprinklerforum-boun...@firesprinkler.org
[mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of A.P.Silva
Sent: Tuesday, August 09, 2011 1:59 PM
To: sprinklerforum@firesprinkler.org
Subject: RE: Water storage

The maximum sprinkler demand was 250 gpm. This is a health centre with three
mechanical rooms, the largest being about 1100 sq.ft. The most demanding
area is this mech. room, which I classified as OH 1. 

Providing water for the fire flow is not my responsibility, and I don't want
to go there. This site doesn't have any water (even domestic water is
stored). Disregarding the fireflow, I think I should ensure that at least
the hose allowances are available. My question was, would you use the same
duration, 60 to 90 minutes for the hose allowances? I'm asking this question
as depending on response time, the demand for sprinlers and hose may not
occur concurrently.

Another reason is to understand the concept. Is the hose allowance just a
glorified safety factor? I would think the fire department would be pulling
more than 100 gpm or 250 gpm when the pumper truck connects to a hydrant.

Tony 

-Original Message-
From: sprinklerforum-boun...@firesprinkler.org
[mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of
craig.pr...@ch2m.com
Sent: August 9, 2011 11:14 AM
To: sprinklerforum@firesprinkler.org
Subject: RE: Water storage

Assuming Ord. II at .20/gpm sf over 1500 sf would be 300 gpm flow rate
minimum.  Now remember that sprinkler system flows will always exceed the
base design criteria because the .20gpm/sf is the hyd. remote sprinkler and
those upstream will put out more. So typically you will see a 10-15% overage
in actual system flow.  To be conservative for a wet 

misc storage under pitched roof

2011-08-09 Thread Todd Williams
I am working on a building with a 3:12 roof trusses where they want to store 
Class III commodities to 12 ft. Since the storage area will exceed 10% of the 
building area, it is not considered miscellaneous storage (Chapter 13). 
However, chapter 14 (NFPA 13 - 2010) refers storage 12 ft and under back to 
Chapter 13. Section 12.1.2, which restricts roof slope to less than 2:12, 
states only references Chapters 12 and 14-20. I have 2 questions:

1) If I am using chapter 14 to determine criteria and it refers back to Chapter 
13, does section 12.1.2 apply?

2) Does this mean that miscellaneous storage can be protected using Chapter 13 
criteria without regard to roof slope? So if I have someone who wants to store 
to 16 ft in a building with a 4:12 pitch, a legitimate option would be to lower 
the storage to 12 ft?

Todd G. Williams, PE
Fire Protection Design/Consulting
Stonington, CT
860.535.2080
www.fpdc.com

___
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: supp...@firesprinkler.org

To Unsubscribe, send an email to:sprinklerforum-requ...@firesprinkler.org
(Put the word unsubscribe in the subject field)


RE: misc storage under pitched roof

2011-08-09 Thread Ronl . Fletcher
1. No
2. Yes


Ron Fletcher
Aero Automatic
Phoenix, AZ



-Original Message-
From: sprinklerforum-boun...@firesprinkler.org 
[mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of Todd Williams
Sent: Tuesday, August 09, 2011 1:18 PM
To: sprinklerforum@firesprinkler.org
Subject: misc storage under pitched roof

I am working on a building with a 3:12 roof trusses where they want to store 
Class III commodities to 12 ft. Since the storage area will exceed 10% of the 
building area, it is not considered miscellaneous storage (Chapter 13). 
However, chapter 14 (NFPA 13 - 2010) refers storage 12 ft and under back to 
Chapter 13. Section 12.1.2, which restricts roof slope to less than 2:12, 
states only references Chapters 12 and 14-20. I have 2 questions:

1) If I am using chapter 14 to determine criteria and it refers back to Chapter 
13, does section 12.1.2 apply?

2) Does this mean that miscellaneous storage can be protected using Chapter 13 
criteria without regard to roof slope? So if I have someone who wants to store 
to 16 ft in a building with a 4:12 pitch, a legitimate option would be to lower 
the storage to 12 ft?

Todd G. Williams, PE
Fire Protection Design/Consulting
Stonington, CT
860.535.2080
www.fpdc.com

___
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: supp...@firesprinkler.org

To Unsubscribe, send an email to:sprinklerforum-requ...@firesprinkler.org
(Put the word unsubscribe in the subject field)


___
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: supp...@firesprinkler.org

To Unsubscribe, send an email to:sprinklerforum-requ...@firesprinkler.org
(Put the word unsubscribe in the subject field)


RE: misc storage under pitched roof

2011-08-09 Thread Jack Carlson

Todd,

I do not have the 2010 handbook, but the commentary to the 2007 edition
for 12.1 states It is important to note that all of the rules of
Chapter 12 apply to all storage arrangements addressed by chapter 12 and
Chapters 14 through 20.  Chapter 13 Miscellaneous Storage, and all
protection methods that refer to Chapter 13 for design criteria, use the
occupancy design approach in Chapter 11, and Chapter 12 requirements do
not apply. 


Jack W. Carlson, SET
Triple A Fire Protection, Inc.
Cell - 706.247.5050 

-Original Message-
From: sprinklerforum-boun...@firesprinkler.org
[mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of Todd
Williams
Sent: Tuesday, August 09, 2011 4:18 PM
To: sprinklerforum@firesprinkler.org
Subject: misc storage under pitched roof

I am working on a building with a 3:12 roof trusses where they want to
store Class III commodities to 12 ft. Since the storage area will exceed
10% of the building area, it is not considered miscellaneous storage
(Chapter 13). However, chapter 14 (NFPA 13 - 2010) refers storage 12 ft
and under back to Chapter 13. Section 12.1.2, which restricts roof slope
to less than 2:12, states only references Chapters 12 and 14-20. I have
2 questions:

1) If I am using chapter 14 to determine criteria and it refers back to
Chapter 13, does section 12.1.2 apply?

2) Does this mean that miscellaneous storage can be protected using
Chapter 13 criteria without regard to roof slope? So if I have someone
who wants to store to 16 ft in a building with a 4:12 pitch, a
legitimate option would be to lower the storage to 12 ft?

Todd G. Williams, PE
Fire Protection Design/Consulting
Stonington, CT
860.535.2080
www.fpdc.com

___
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: supp...@firesprinkler.org

To Unsubscribe, send an email
to:sprinklerforum-requ...@firesprinkler.org
(Put the word unsubscribe in the subject field)
___
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: supp...@firesprinkler.org

To Unsubscribe, send an email to:sprinklerforum-requ...@firesprinkler.org
(Put the word unsubscribe in the subject field)


RE: Water storage/NFPA 13 Proposal

2011-08-09 Thread Mark Sornsin
I concur with Craig. 

It seems the proposal was written to clarify for AHJs that one needs NOT run a 
separate calculation for sprinklers closest to the source simply to identify 
maximum flows (and therefore maximum supply requirements). The remote area 
calculation(s) is 'good enough'.  I do not think the proposal is suggesting you 
can calc a tank based merely on 'density x area x duration = volume'. The 
procedures in Chapters 11 through 22 for the required duration as specified in 
Chapter 11, Chapter 12 and through Chapter 21 do not allow you to omit 
overages within the design area.

Mark A. Sornsin, PE| Fire Protection Engineer 
Ulteig Engineers, Inc.| Fargo, ND  
mark.sorn...@ulteig.com 



-Original Message-
From: sprinklerforum-boun...@firesprinkler.org 
[mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of 
craig.pr...@ch2m.com
Sent: Tuesday, August 09, 2011 2:26 PM
To: sprinklerforum@firesprinkler.org
Subject: RE: Water storage

But we all know that a .15 gpm/sf over 1500 gpm doesn't calc out to exactly 225 
gpm of flow and we know that most fires are controlled by 3 or less sprinklers. 
 So if someone wants to cut it that close, go for it.  

Related to the question of whether to include hose stream or not, what's 
interesting is that in other areas of 13, it is clearly spelled out that the 
demand is to include both hose and sprinklers.

But in the NFSA response it's talking about not considering the excess flow 
that is typical of sprinklers closer to the riser which are OUTSIDE of the 
remote area.  It is NOT saying anything about factoring the imbalance or 
overage for the remote area sprinklers.   

Craig L. Prahl, CET   
Fire Protection 
CH2MHILL
Lockwood Greene
1500 International Drive
Spartanburg, SC  29304-0491
Direct - 864.599.4102
Fax - 864.599.8439
CH2MHILL Extension  74102
craig.pr...@ch2m.com



-Original Message-
From: sprinklerforum-boun...@firesprinkler.org 
[mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of Bill Brooks
Sent: Tuesday, August 09, 2011 2:41 PM
To: sprinklerforum@firesprinkler.org
Subject: RE: Water storage

Well, I guess my point would be that you don't have to figure any hydraulic
imbalance in your sprinkler water quantity.  Just density x area x time.
Perhaps Ken's approved proposal could be clarified to confirm.

Bill Brooks

William N. Brooks, P.E.
Brooks Fire Protection Engineering Inc.
372 Wilett Drive
Severna Park, MD 21146-1904
410-544-3620
410-544-3032 FAX
412-400-6528 Cell


-Original Message-
From: sprinklerforum-boun...@firesprinkler.org
[mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of
craig.pr...@ch2m.com
Sent: Tuesday, August 09, 2011 2:10 PM
To: sprinklerforum@firesprinkler.org
Subject: RE: Water storage

OK?

Craig L. Prahl, CET   
Fire Protection 
CH2MHILL
Lockwood Greene
1500 International Drive
Spartanburg, SC  29304-0491
Direct - 864.599.4102
Fax - 864.599.8439
CH2MHILL Extension  74102
craig.pr...@ch2m.com



-Original Message-
From: sprinklerforum-boun...@firesprinkler.org
[mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of Bill Brooks
Sent: Tuesday, August 09, 2011 2:02 PM
To: sprinklerforum@firesprinkler.org
Subject: RE: Water storage

13-494 Log #356 AUT-SSD Final Action: Accept
(23.1.2)

Submitter: Kenneth E. Isman, National Fire Sprinkler Association, Inc.
Recommendation: Revise text to read as follows:
23.1.2 Capacity. Water supplies shall be capable of providing the required
flow and pressure for the remote design area determined using the procedures
in Chapters 11 through 22 for the required duration as specified in Chapter
11,
Chapter 12 and through Chapter 21.
Substantiation: The water supply only needs to provide the duration for the
remote area, not the closer sprinklers in the system that will discharge
more
water. Also, all of the discharge chapters need to be specified, not just
the basic
storage Chapter 12.
Committee Meeting Action: Accept
Number Eligible to Vote: 25
Ballot Results: Affirmative: 22
Ballot Not Returned: 3 Brown, T., Hogan, A., McNamara, T.


Bill Brooks

William N. Brooks, P.E.
Brooks Fire Protection Engineering Inc.
372 Wilett Drive
Severna Park, MD 21146-1904
410-544-3620
410-544-3032 FAX
412-400-6528 Cell
___