NFPA 13R Attics

2012-04-02 Thread Joel Chaim
We have a job that is classified as a 13R [2007] and they have regular
walk-up stairs to the attic which is enclosed and sealed from the dwelling
unit, our position is that the attic is required to be sprinklerd because
section A.6.9.6 states small openings and not walk-up stairs. 

 

please chime in with your opinions. 

 

6.9.6* Sprinklers shall not be required in attics, penthouse equipment
rooms, elevator

machine rooms, concealed spaces dedicated exclusively to and containing only
dwelling unit

ventilation equipment, crawl spaces, floor/ceiling spaces, noncombustible
elevator shafts

where the elevator cars comply with ANSI A17.1, Safety Code for Elevators
and Escalators,

and other concealed spaces that are not used or intended for living purposes
or storage and

do not contain fuel-fired equipment.

 

A.6.9.6 Concealed spaces are permitted to have small openings such as
grilles for return

air when the space is being used as a plenum. Such small openings do not
disqualify the

space from being considered as a concealed space, and sprinklers are still
permitted to be

omitted.

 

 

-- next part --
An HTML attachment was scrubbed...
URL: 
http://fireball.firesprinkler.org/mailman/private/sprinklerforum/attachments/20120402/28801310/attachment.html
___
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum


RE: NFPA 13R Attics

2012-04-02 Thread Steve Mackinnon
Joel, 

I believe NFPA-13R would only require the attic to be sprinklered if
this space was being used for living space or storage... the method of
getting up the attic does not come into play in this scenario... my take
on this. lol

Steven MacKinnon
Senior Fire Protection Engineer
Hartcorn Plumbing  Heating Inc.
850 South 2nd Street
Ronkonkoma, NY 11779
631-580-2300 - Office
631-580-1090 - Fax
ste...@hartcorn.com
 
 
-Original Message-
From: sprinklerforum-boun...@firesprinkler.org
[mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of Joel
Chaim
Sent: Monday, April 02, 2012 12:31 PM
To: sprinklerforum@firesprinkler.org
Subject: NFPA 13R Attics

We have a job that is classified as a 13R [2007] and they have regular
walk-up stairs to the attic which is enclosed and sealed from the
dwelling
unit, our position is that the attic is required to be sprinklerd
because
section A.6.9.6 states small openings and not walk-up stairs. 

 

please chime in with your opinions. 

 

6.9.6* Sprinklers shall not be required in attics, penthouse equipment
rooms, elevator

machine rooms, concealed spaces dedicated exclusively to and containing
only
dwelling unit

ventilation equipment, crawl spaces, floor/ceiling spaces,
noncombustible
elevator shafts

where the elevator cars comply with ANSI A17.1, Safety Code for
Elevators
and Escalators,

and other concealed spaces that are not used or intended for living
purposes
or storage and

do not contain fuel-fired equipment.

 

A.6.9.6 Concealed spaces are permitted to have small openings such as
grilles for return

air when the space is being used as a plenum. Such small openings do not
disqualify the

space from being considered as a concealed space, and sprinklers are
still
permitted to be

omitted.

 

 

-- next part --
An HTML attachment was scrubbed...
URL:
http://fireball.firesprinkler.org/mailman/private/sprinklerforum/attach
ments/20120402/28801310/attachment.html
___
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
___
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum


Re: NFPA 13R Attics

2012-04-02 Thread Ron Greenman
Look at your commas. Sprinklers shall not be required in attics
(comma) penthouse equipment rooms (comma) concealed spaces dedicated
exclusively to and containing only
dwelling unit ventilation equipment (comma) crawl spaces (comma)
floor/ceiling spaces (comma) noncombustible elevator shafts where the
elevator cars comply with ANSI A17.1, Safety Code for Elevators and
Escalators (comma) and other concealed spaces that are not used or intended
for living purposes or storage and do not contain fuel-fired equipment.
Each one of these items is separate from the other. The annex material only
to concealed spaces which your attic is not. Permanent stairs, drop down
stairs, ladder access through a hatch or a door doesn't change attic to
something else. Heated space on the other hand would make it a living
compartment. My opinion is that it is, as described, an attic and no matter
how you access it is still exempt from sprinklering.

On Mon, Apr 2, 2012 at 9:31 AM, Joel Chaim
activefireprotect...@gmail.comwrote:

 We have a job that is classified as a 13R [2007] and they have regular
 walk-up stairs to the attic which is enclosed and sealed from the dwelling
 unit, our position is that the attic is required to be sprinklerd because
 section A.6.9.6 states small openings and not walk-up stairs.



 please chime in with your opinions.



 6.9.6* Sprinklers shall not be required in attics, penthouse equipment
 rooms, elevator

 machine rooms, concealed spaces dedicated exclusively to and containing
 only
 dwelling unit

 ventilation equipment, crawl spaces, floor/ceiling spaces, noncombustible
 elevator shafts

 where the elevator cars comply with ANSI A17.1, Safety Code for Elevators
 and Escalators,

 and other concealed spaces that are not used or intended for living
 purposes
 or storage and

 do not contain fuel-fired equipment.



 A.6.9.6 Concealed spaces are permitted to have small openings such as
 grilles for return

 air when the space is being used as a plenum. Such small openings do not
 disqualify the

 space from being considered as a concealed space, and sprinklers are still
 permitted to be

 omitted.





 -- next part --
 An HTML attachment was scrubbed...
 URL: 
 http://fireball.firesprinkler.org/mailman/private/sprinklerforum/attachments/20120402/28801310/attachment.html
 
 ___
 Sprinklerforum mailing list
 Sprinklerforum@firesprinkler.org
 http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum




-- 
Ron Greenman
Instructor
Fire Protection Engineering Technology
Bates Technical College
1101 So. Yakima Ave.
Tacoma, WA 98405

rgreen...@bates.ctc.edu

http://www.bates.ctc.edu/fireprotection/

253.680.7346
253.576.9700 (cell)

Member:
ASEE, SFPE, ASCET, NFPA, AFSA, NFSA, AFAA, NIBS, WSAFM, WFC

They are happy men whose natures sort with their vocations. -Francis Bacon,
essayist, philosopher, and statesman (1561-1626)
-- next part --
An HTML attachment was scrubbed...
URL: 
http://fireball.firesprinkler.org/mailman/private/sprinklerforum/attachments/20120402/ec719a41/attachment.html
___
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum


Re: NFPA 13R Attics

2012-04-02 Thread Todd Williams
I would look at it as the stairs make storage in the space a real possibility. 
I would think that if there are stairs, there is probably a plywood or other 
solid platform in the attic space, which would be ripe for storage. No access 
within the dwelling units has no impact; it is access in general. If by 
sealed, you mean the door has been sheetrocked over and there is no access, 
then there would be a good case that it is a vacant attic. 

While we are on semantics,  that are not used or intended for living 
purposes or storage and do not contain fuel-fired equipment. Does this mean if 
they are being used for living purposes or storage and there is not any fuel 
fired equipment (i.e electric heat), that sprinklers are not required? 



At 01:15 PM 4/2/2012, you wrote:
Look at your commas. Sprinklers shall not be required in attics
(comma) penthouse equipment rooms (comma) concealed spaces dedicated
exclusively to and containing only
dwelling unit ventilation equipment (comma) crawl spaces (comma)
floor/ceiling spaces (comma) noncombustible elevator shafts where the
elevator cars comply with ANSI A17.1, Safety Code for Elevators and
Escalators (comma) and other concealed spaces that are not used or intended
for living purposes or storage and do not contain fuel-fired equipment.
Each one of these items is separate from the other. The annex material only
to concealed spaces which your attic is not. Permanent stairs, drop down
stairs, ladder access through a hatch or a door doesn't change attic to
something else. Heated space on the other hand would make it a living
compartment. My opinion is that it is, as described, an attic and no matter
how you access it is still exempt from sprinklering.

On Mon, Apr 2, 2012 at 9:31 AM, Joel Chaim
activefireprotect...@gmail.comwrote:

 We have a job that is classified as a 13R [2007] and they have regular
 walk-up stairs to the attic which is enclosed and sealed from the dwelling
 unit, our position is that the attic is required to be sprinklerd because
 section A.6.9.6 states small openings and not walk-up stairs.



 please chime in with your opinions.



 6.9.6* Sprinklers shall not be required in attics, penthouse equipment
 rooms, elevator

 machine rooms, concealed spaces dedicated exclusively to and containing
 only
 dwelling unit

 ventilation equipment, crawl spaces, floor/ceiling spaces, noncombustible
 elevator shafts

 where the elevator cars comply with ANSI A17.1, Safety Code for Elevators
 and Escalators,

 and other concealed spaces that are not used or intended for living
 purposes
 or storage and

 do not contain fuel-fired equipment.



 A.6.9.6 Concealed spaces are permitted to have small openings such as
 grilles for return

 air when the space is being used as a plenum. Such small openings do not
 disqualify the

 space from being considered as a concealed space, and sprinklers are still
 permitted to be

 omitted.





 -- next part --
 An HTML attachment was scrubbed...
 URL: 
 http://fireball.firesprinkler.org/mailman/private/sprinklerforum/attachments/20120402/28801310/attachment.html
 
 ___
 Sprinklerforum mailing list
 Sprinklerforum@firesprinkler.org
 http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum




-- 
Ron Greenman
Instructor
Fire Protection Engineering Technology
Bates Technical College
1101 So. Yakima Ave.
Tacoma, WA 98405

rgreen...@bates.ctc.edu

http://www.bates.ctc.edu/fireprotection/

253.680.7346
253.576.9700 (cell)

Member:
ASEE, SFPE, ASCET, NFPA, AFSA, NFSA, AFAA, NIBS, WSAFM, WFC

They are happy men whose natures sort with their vocations. -Francis Bacon,
essayist, philosopher, and statesman (1561-1626)
-- next part --
An HTML attachment was scrubbed...
URL: 
http://fireball.firesprinkler.org/mailman/private/sprinklerforum/attachments/20120402/ec719a41/attachment.html
___
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

Todd G. Williams, PE
Fire Protection Design/Consulting
Stonington, CT
860.535.2080
www.fpdc.com

___
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum


RE: NFPA 13R Attics

2012-04-02 Thread Joel Chaim
But when it says and all concealed spaces that are not used or
intended... that would mean attic as well, an attic is basically a
concealed space the only difference is that there is a possibility for fuel
burning equipment. 

-Original Message-
From: sprinklerforum-boun...@firesprinkler.org
[mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of Ron Greenman
Sent: Monday, April 02, 2012 1:15 PM
To: sprinklerforum@firesprinkler.org
Subject: Re: NFPA 13R Attics

Look at your commas. Sprinklers shall not be required in attics
(comma) penthouse equipment rooms (comma) concealed spaces dedicated
exclusively to and containing only dwelling unit ventilation equipment
(comma) crawl spaces (comma) floor/ceiling spaces (comma) noncombustible
elevator shafts where the elevator cars comply with ANSI A17.1, Safety Code
for Elevators and Escalators (comma) and other concealed spaces that are not
used or intended for living purposes or storage and do not contain
fuel-fired equipment.
Each one of these items is separate from the other. The annex material only
to concealed spaces which your attic is not. Permanent stairs, drop down
stairs, ladder access through a hatch or a door doesn't change attic to
something else. Heated space on the other hand would make it a living
compartment. My opinion is that it is, as described, an attic and no matter
how you access it is still exempt from sprinklering.

On Mon, Apr 2, 2012 at 9:31 AM, Joel Chaim
activefireprotect...@gmail.comwrote:

 We have a job that is classified as a 13R [2007] and they have regular 
 walk-up stairs to the attic which is enclosed and sealed from the 
 dwelling unit, our position is that the attic is required to be 
 sprinklerd because section A.6.9.6 states small openings and not walk-up
stairs.



 please chime in with your opinions.



 6.9.6* Sprinklers shall not be required in attics, penthouse equipment 
 rooms, elevator

 machine rooms, concealed spaces dedicated exclusively to and 
 containing only dwelling unit

 ventilation equipment, crawl spaces, floor/ceiling spaces, 
 noncombustible elevator shafts

 where the elevator cars comply with ANSI A17.1, Safety Code for 
 Elevators and Escalators,

 and other concealed spaces that are not used or intended for living 
 purposes or storage and

 do not contain fuel-fired equipment.



 A.6.9.6 Concealed spaces are permitted to have small openings such as 
 grilles for return

 air when the space is being used as a plenum. Such small openings do 
 not disqualify the

 space from being considered as a concealed space, and sprinklers are 
 still permitted to be

 omitted.





 -- next part -- An HTML attachment was 
 scrubbed...
 URL: 
 http://fireball.firesprinkler.org/mailman/private/sprinklerforum/attac
 hments/20120402/28801310/attachment.html
 
 ___
 Sprinklerforum mailing list
 Sprinklerforum@firesprinkler.org
 http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum




--
Ron Greenman
Instructor
Fire Protection Engineering Technology
Bates Technical College
1101 So. Yakima Ave.
Tacoma, WA 98405

rgreen...@bates.ctc.edu

http://www.bates.ctc.edu/fireprotection/

253.680.7346
253.576.9700 (cell)

Member:
ASEE, SFPE, ASCET, NFPA, AFSA, NFSA, AFAA, NIBS, WSAFM, WFC

They are happy men whose natures sort with their vocations. -Francis Bacon,
essayist, philosopher, and statesman (1561-1626)
-- next part --
An HTML attachment was scrubbed...
URL:
http://fireball.firesprinkler.org/mailman/private/sprinklerforum/attachment
s/20120402/ec719a41/attachment.html
___
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

___
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum


Re: NFPA 13R Attics

2012-04-02 Thread Ron Greenman
While I'd agree that stairs indicate that the space will become a living
space that can't be my concern other than to point out that the way it's
constructed it could lend itself to future living space, and so
sprinklering might be prudent, but if it's not heated then sprinklering is
a bad idea. 13R is a truncated version of 13 for a reason and it's not so
we can guess at future activities and force heating or a dry system into an
attic. We used to have the same problem in Santa Cruz when I was with the
building department. Housing and land was at such a premium everybody
wanted a mother-in-law second house on their plot. This was a no-no per
zoning but you could build a second building for other than living purposes
if you met all the set-back  lot size requirements. What differentiated a
house a secondary building was a kitchen. You'd be surprised how many 3500+
sqft artist's studios were permitted that had a very suspicious room
layout with built in cabinets that had a space the was just range size but
designated for the kiln. There'd always be another space just refrigerator
width and a kitchen size sink for cleaning up. Everybody knew what was
going to happen the day after final and CO, but An attic is an attic no
matter how obvious the intention to make it living space.

On Mon, Apr 2, 2012 at 10:34 AM, Todd Williams t...@fpdc.com wrote:

 I would look at it as the stairs make storage in the space a real
 possibility. I would think that if there are stairs, there is probably a
 plywood or other solid platform in the attic space, which would be ripe for
 storage. No access within the dwelling units has no impact; it is access in
 general. If by sealed, you mean the door has been sheetrocked over and
 there is no access, then there would be a good case that it is a vacant
 attic.

 While we are on semantics,  that are not used or intended for living
 purposes or storage and do not contain fuel-fired equipment. Does this
 mean if they are being used for living purposes or storage and there is not
 any fuel fired equipment (i.e electric heat), that sprinklers are not
 required?



 At 01:15 PM 4/2/2012, you wrote:
 Look at your commas. Sprinklers shall not be required in attics
 (comma) penthouse equipment rooms (comma) concealed spaces dedicated
 exclusively to and containing only
 dwelling unit ventilation equipment (comma) crawl spaces (comma)
 floor/ceiling spaces (comma) noncombustible elevator shafts where the
 elevator cars comply with ANSI A17.1, Safety Code for Elevators and
 Escalators (comma) and other concealed spaces that are not used or
 intended
 for living purposes or storage and do not contain fuel-fired equipment.
 Each one of these items is separate from the other. The annex material
 only
 to concealed spaces which your attic is not. Permanent stairs, drop down
 stairs, ladder access through a hatch or a door doesn't change attic to
 something else. Heated space on the other hand would make it a living
 compartment. My opinion is that it is, as described, an attic and no
 matter
 how you access it is still exempt from sprinklering.
 
 On Mon, Apr 2, 2012 at 9:31 AM, Joel Chaim
 activefireprotect...@gmail.comwrote:
 
  We have a job that is classified as a 13R [2007] and they have regular
  walk-up stairs to the attic which is enclosed and sealed from the
 dwelling
  unit, our position is that the attic is required to be sprinklerd
 because
  section A.6.9.6 states small openings and not walk-up stairs.
 
 
 
  please chime in with your opinions.
 
 
 
  6.9.6* Sprinklers shall not be required in attics, penthouse equipment
  rooms, elevator
 
  machine rooms, concealed spaces dedicated exclusively to and containing
  only
  dwelling unit
 
  ventilation equipment, crawl spaces, floor/ceiling spaces,
 noncombustible
  elevator shafts
 
  where the elevator cars comply with ANSI A17.1, Safety Code for
 Elevators
  and Escalators,
 
  and other concealed spaces that are not used or intended for living
  purposes
  or storage and
 
  do not contain fuel-fired equipment.
 
 
 
  A.6.9.6 Concealed spaces are permitted to have small openings such as
  grilles for return
 
  air when the space is being used as a plenum. Such small openings do not
  disqualify the
 
  space from being considered as a concealed space, and sprinklers are
 still
  permitted to be
 
  omitted.
 
 
 
 
 
  -- next part --
  An HTML attachment was scrubbed...
  URL: 
 
 http://fireball.firesprinkler.org/mailman/private/sprinklerforum/attachments/20120402/28801310/attachment.html
  
  ___
  Sprinklerforum mailing list
  Sprinklerforum@firesprinkler.org
  http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
 
 
 
 
 --
 Ron Greenman
 Instructor
 Fire Protection Engineering Technology
 Bates Technical College
 1101 So. Yakima Ave.
 Tacoma, WA 98405
 
 rgreen...@bates.ctc.edu
 
 http://www.bates.ctc.edu/fireprotection

Re: NFPA 13R Attics

2012-04-02 Thread Ron Greenman
No, an attic is an attic, and a concealed space is something other than an
attic. If it were then the passage would read all concealed spaces with
annex material listing spaces, but not limited, that could be considered
concealed. Remember when your grade school teacher harped on punctuation?
There was a reason. I where I wish I were at work where I have the entire
NFC. There's an entire volume dedicated to general definitions. I'd like to
see if concealed space and attic are in there. And the business about
intended for storage or living space is a qualifier related to the
concealed spaces clause in the sentence, not the entire passage. Just
saying.

On Mon, Apr 2, 2012 at 10:50 AM, Joel Chaim
activefireprotect...@gmail.comwrote:

 But when it says and all concealed spaces that are not used or
 intended... that would mean attic as well, an attic is basically a
 concealed space the only difference is that there is a possibility for fuel
 burning equipment.

 -Original Message-
 From: sprinklerforum-boun...@firesprinkler.org
 [mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of Ron
 Greenman
 Sent: Monday, April 02, 2012 1:15 PM
 To: sprinklerforum@firesprinkler.org
 Subject: Re: NFPA 13R Attics

 Look at your commas. Sprinklers shall not be required in attics
 (comma) penthouse equipment rooms (comma) concealed spaces dedicated
 exclusively to and containing only dwelling unit ventilation equipment
 (comma) crawl spaces (comma) floor/ceiling spaces (comma) noncombustible
 elevator shafts where the elevator cars comply with ANSI A17.1, Safety Code
 for Elevators and Escalators (comma) and other concealed spaces that are
 not
 used or intended for living purposes or storage and do not contain
 fuel-fired equipment.
 Each one of these items is separate from the other. The annex material only
 to concealed spaces which your attic is not. Permanent stairs, drop down
 stairs, ladder access through a hatch or a door doesn't change attic to
 something else. Heated space on the other hand would make it a living
 compartment. My opinion is that it is, as described, an attic and no matter
 how you access it is still exempt from sprinklering.

 On Mon, Apr 2, 2012 at 9:31 AM, Joel Chaim
 activefireprotect...@gmail.comwrote:

  We have a job that is classified as a 13R [2007] and they have regular
  walk-up stairs to the attic which is enclosed and sealed from the
  dwelling unit, our position is that the attic is required to be
  sprinklerd because section A.6.9.6 states small openings and not walk-up
 stairs.
 
 
 
  please chime in with your opinions.
 
 
 
  6.9.6* Sprinklers shall not be required in attics, penthouse equipment
  rooms, elevator
 
  machine rooms, concealed spaces dedicated exclusively to and
  containing only dwelling unit
 
  ventilation equipment, crawl spaces, floor/ceiling spaces,
  noncombustible elevator shafts
 
  where the elevator cars comply with ANSI A17.1, Safety Code for
  Elevators and Escalators,
 
  and other concealed spaces that are not used or intended for living
  purposes or storage and
 
  do not contain fuel-fired equipment.
 
 
 
  A.6.9.6 Concealed spaces are permitted to have small openings such as
  grilles for return
 
  air when the space is being used as a plenum. Such small openings do
  not disqualify the
 
  space from being considered as a concealed space, and sprinklers are
  still permitted to be
 
  omitted.
 
 
 
 
 
  -- next part -- An HTML attachment was
  scrubbed...
  URL: 
  http://fireball.firesprinkler.org/mailman/private/sprinklerforum/attac
  hments/20120402/28801310/attachment.html
  
  ___
  Sprinklerforum mailing list
  Sprinklerforum@firesprinkler.org
  http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
 



 --
 Ron Greenman
 Instructor
 Fire Protection Engineering Technology
 Bates Technical College
 1101 So. Yakima Ave.
 Tacoma, WA 98405

 rgreen...@bates.ctc.edu

 http://www.bates.ctc.edu/fireprotection/

 253.680.7346
 253.576.9700 (cell)

 Member:
 ASEE, SFPE, ASCET, NFPA, AFSA, NFSA, AFAA, NIBS, WSAFM, WFC

 They are happy men whose natures sort with their vocations. -Francis Bacon,
 essayist, philosopher, and statesman (1561-1626)
 -- next part --
 An HTML attachment was scrubbed...
 URL:
 
 http://fireball.firesprinkler.org/mailman/private/sprinklerforum/attachment
 s/20120402/ec719a41/attachment.html
 ___
 Sprinklerforum mailing list
 Sprinklerforum@firesprinkler.org
 http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

 ___
 Sprinklerforum mailing list
 Sprinklerforum@firesprinkler.org
 http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum




-- 
Ron Greenman
Instructor
Fire Protection Engineering Technology
Bates Technical College
1101 So. Yakima Ave.
Tacoma, WA 98405

rgreen...@bates.ctc.edu

Flow Test

2012-04-02 Thread Jamey Prentice
We are looking at a project that involves an addition to an existing
Institutional occupancy(University)in Ontario Canada. Existing flow tests
indicate available flows as follows:

 

Static 68 PSI

 

Test 1-50 PSI @ 223 USGPM

Test 2-39 PSI @ 416 USGPM

Test 3-13 PSI @ 538 USGPM

 

Existing Hydraulic calculations show a most demanding area calculation for
the boiler room requiring 23.1 PSI @ 247.12 USGPM @ BOR plus 250 USPM hose
allowance. What flow test results should have been used for this system
design? I  bet you can't guess what numbers the existing system has been
designed too?? I can find nothing that requires the design contractor to use
the most demanding curve, If test three had not been performed we would have
no real indication of the water available! Can contractors arbitrarily
choose curves to meet their design needs, can interpreted points on a graph
such as those used in test two be used over real numbers such as those in
test three? My gut tells me no, but it seems the wallet once again decides.

 

Thanks in advance.

 

Jamey

 

-- next part --
An HTML attachment was scrubbed...
URL: 
http://fireball.firesprinkler.org/mailman/private/sprinklerforum/attachments/20120402/5b9871be/attachment.html
___
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum


Re: Flow Test

2012-04-02 Thread Todd Williams
You can make a stretch and say that the hydraulically most demanding system 
would include the weakest water supply and well as the most hydraulically 
remote area. More water usually equals better test. Ran into a water supply 
problem a while back where static pressures vary +/- 25 psi. Found this out 
from discrepancy between flow test provided by city and the pressure at the 
riser. A flow test is only a snapshot in time.


At 01:48 PM 4/2/2012, you wrote:
We are looking at a project that involves an addition to an existing
Institutional occupancy(University)in Ontario Canada. Existing flow tests
indicate available flows as follows:

 

Static 68 PSI

 

Test 1-50 PSI @ 223 USGPM

Test 2-39 PSI @ 416 USGPM

Test 3-13 PSI @ 538 USGPM

 

Existing Hydraulic calculations show a most demanding area calculation for
the boiler room requiring 23.1 PSI @ 247.12 USGPM @ BOR plus 250 USPM hose
allowance. What flow test results should have been used for this system
design? I  bet you can't guess what numbers the existing system has been
designed too?? I can find nothing that requires the design contractor to use
the most demanding curve, If test three had not been performed we would have
no real indication of the water available! Can contractors arbitrarily
choose curves to meet their design needs, can interpreted points on a graph
such as those used in test two be used over real numbers such as those in
test three? My gut tells me no, but it seems the wallet once again decides.

 

Thanks in advance.

 

Jamey

 

-- next part --
An HTML attachment was scrubbed...
URL: 
http://fireball.firesprinkler.org/mailman/private/sprinklerforum/attachments/20120402/5b9871be/attachment.html
___
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

Todd G. Williams, PE
Fire Protection Design/Consulting
Stonington, CT
860.535.2080
www.fpdc.com

___
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum


RE: Flow Test

2012-04-02 Thread CH Fire - Mike Gallello
Technically the hydrant flow test should be conducted in accordance with
NFPA 291.  It's rare anyone does it though, it's the generic static, 1
ports then two ports for a 3 point graph.  Look in the back of 13 for
Fig A.22.3.4 for the idiot proof method for the flow test data.
Beyond this, in 291 there's a line (4.3.6) to flow the total demand
necessary for fire fighting purposes.  Well, spin that into sprinkler
system demand values and it's pretty simple.  Plot your 3-4 point graph
depending on how many points you need to represent your sprinkler demand
flow and get an actual curve, not a 2 point line.
IE We had a tire storage facility here, approximate estimated gallons
for the system demand was around 3000 gpm.  We had to static one as
usual, but then we had to pop 2 separate hydrants with both 2.5 outlets
to simulate the drop in the water system for the sprinkler system
demand.
Long story even longer, you cannot extrapolate a water supply curve
from a static and a single residual point - you have to get enough flow
out of the hydrants to approximate sprinkler demand flows.  At least
that's my take on it anyway...


-Original Message-
From: sprinklerforum-boun...@firesprinkler.org
[mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of Jamey
Prentice
Sent: Monday, April 02, 2012 1:49 PM
To: sprinklerforum@firesprinkler.org
Subject: Flow Test

We are looking at a project that involves an addition to an existing
Institutional occupancy(University)in Ontario Canada. Existing flow
tests indicate available flows as follows:

 

Static 68 PSI

 

Test 1-50 PSI @ 223 USGPM

Test 2-39 PSI @ 416 USGPM

Test 3-13 PSI @ 538 USGPM

 

Existing Hydraulic calculations show a most demanding area calculation
for the boiler room requiring 23.1 PSI @ 247.12 USGPM @ BOR plus 250
USPM hose allowance. What flow test results should have been used for
this system design? I  bet you can't guess what numbers the existing
system has been designed too?? I can find nothing that requires the
design contractor to use the most demanding curve, If test three had not
been performed we would have no real indication of the water available!
Can contractors arbitrarily choose curves to meet their design needs,
can interpreted points on a graph such as those used in test two be used
over real numbers such as those in test three? My gut tells me no, but
it seems the wallet once again decides.

 

Thanks in advance.

 

Jamey

 

-- next part --
An HTML attachment was scrubbed...
URL:
http://fireball.firesprinkler.org/mailman/private/sprinklerforum/attach
ments/20120402/5b9871be/attachment.html
___
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
___
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum


RE: Flow Test

2012-04-02 Thread Jamey Prentice
That is also my take on the matter, the standard however does not appear to
specifically require this!!! As indicated NFPA 291-2010 4.3.6 states  To
obtain satisfactory test results of theoretical calculations of expected
flows or rated capacities, sufficient discharge should be achieved to cause
a drop in pressure at the residual hydrant of at least 25% OR to flow the
total demand necessary for fire-fighting purposes. It does not require the
contractor to use whichever demand is greater. In this case all tests
achieve a drop of 25% as required by the standard however only one test of
the three meets the system demand and only when using theoretical numbers
extrapolated from the curve. What is to prevent a contractor from only
flowing until a 25% drop in residual pressure has been achieved? On small
dead end water mains this would be very easy to achieve however it would
not provide a good indication of the actual condition or availability at the
main. 

-Original Message-
From: sprinklerforum-boun...@firesprinkler.org
[mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of CH Fire -
Mike Gallello
Sent: Monday, April 02, 2012 2:40 PM
To: sprinklerforum@firesprinkler.org
Subject: RE: Flow Test

Technically the hydrant flow test should be conducted in accordance with
NFPA 291.  It's rare anyone does it though, it's the generic static, 1 ports
then two ports for a 3 point graph.  Look in the back of 13 for Fig A.22.3.4
for the idiot proof method for the flow test data.
Beyond this, in 291 there's a line (4.3.6) to flow the total demand
necessary for fire fighting purposes.  Well, spin that into sprinkler
system demand values and it's pretty simple.  Plot your 3-4 point graph
depending on how many points you need to represent your sprinkler demand
flow and get an actual curve, not a 2 point line.
IE We had a tire storage facility here, approximate estimated gallons for
the system demand was around 3000 gpm.  We had to static one as usual, but
then we had to pop 2 separate hydrants with both 2.5 outlets to simulate
the drop in the water system for the sprinkler system demand.
Long story even longer, you cannot extrapolate a water supply curve
from a static and a single residual point - you have to get enough flow out
of the hydrants to approximate sprinkler demand flows.  At least that's my
take on it anyway...


-Original Message-
From: sprinklerforum-boun...@firesprinkler.org
[mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of Jamey
Prentice
Sent: Monday, April 02, 2012 1:49 PM
To: sprinklerforum@firesprinkler.org
Subject: Flow Test

We are looking at a project that involves an addition to an existing
Institutional occupancy(University)in Ontario Canada. Existing flow tests
indicate available flows as follows:

 

Static 68 PSI

 

Test 1-50 PSI @ 223 USGPM

Test 2-39 PSI @ 416 USGPM

Test 3-13 PSI @ 538 USGPM

 

Existing Hydraulic calculations show a most demanding area calculation for
the boiler room requiring 23.1 PSI @ 247.12 USGPM @ BOR plus 250 USPM hose
allowance. What flow test results should have been used for this system
design? I  bet you can't guess what numbers the existing system has been
designed too?? I can find nothing that requires the design contractor to use
the most demanding curve, If test three had not been performed we would have
no real indication of the water available!
Can contractors arbitrarily choose curves to meet their design needs, can
interpreted points on a graph such as those used in test two be used over
real numbers such as those in test three? My gut tells me no, but it seems
the wallet once again decides.

 

Thanks in advance.

 

Jamey

 

-- next part --
An HTML attachment was scrubbed...
URL:
http://fireball.firesprinkler.org/mailman/private/sprinklerforum/attach
ments/20120402/5b9871be/attachment.html
___
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
___
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

___
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum


RE: Flow Test

2012-04-02 Thread Mark Sornsin
Subject: Flow Test

We are looking at a project that involves an addition to an existing 
Institutional occupancy(University)in Ontario Canada. Existing flow tests 
indicate available flows as follows:

 

Static 68 PSI

 

Test 1-50 PSI @ 223 USGPM

Test 2-39 PSI @ 416 USGPM

Test 3-13 PSI @ 538 USGPM

 

Existing Hydraulic calculations show a most demanding area calculation for the 
boiler room requiring 23.1 PSI @ 247.12 USGPM @ BOR plus 250 USPM hose 
allowance. What flow test results should have been used for this system design? 
I  bet you can't guess what numbers the existing system has been designed too?? 
I can find nothing that requires the design contractor to use the most 
demanding curve, If test three had not been performed we would have no real 
indication of the water available!
Can contractors arbitrarily choose curves to meet their design needs, can 
interpreted points on a graph such as those used in test two be used over real 
numbers such as those in test three? My gut tells me no, but it seems the 
wallet once again decides.

 

Thanks in advance.

 

Jamey

 

-- next part --
An HTML attachment was scrubbed...
URL:
http://fireball.firesprinkler.org/mailman/private/sprinklerforum/attach
ments/20120402/5b9871be/attachment.html
___
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
___
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

___
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
___
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum


RE: Flow Test

2012-04-02 Thread Jamey Prentice
 a line (4.3.6) to flow the total demand
necessary for fire fighting purposes.  Well, spin that into sprinkler
system demand values and it's pretty simple.  Plot your 3-4 point graph
depending on how many points you need to represent your sprinkler demand
flow and get an actual curve, not a 2 point line.
IE We had a tire storage facility here, approximate estimated gallons for
the system demand was around 3000 gpm.  We had to static one as usual, but
then we had to pop 2 separate hydrants with both 2.5 outlets to simulate
the drop in the water system for the sprinkler system demand.
Long story even longer, you cannot extrapolate a water supply curve
from a static and a single residual point - you have to get enough flow out
of the hydrants to approximate sprinkler demand flows.  At least that's my
take on it anyway...


-Original Message-
From: sprinklerforum-boun...@firesprinkler.org
[mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of Jamey
Prentice
Sent: Monday, April 02, 2012 1:49 PM
To: sprinklerforum@firesprinkler.org
Subject: Flow Test

We are looking at a project that involves an addition to an existing
Institutional occupancy(University)in Ontario Canada. Existing flow tests
indicate available flows as follows:

 

Static 68 PSI

 

Test 1-50 PSI @ 223 USGPM

Test 2-39 PSI @ 416 USGPM

Test 3-13 PSI @ 538 USGPM

 

Existing Hydraulic calculations show a most demanding area calculation for
the boiler room requiring 23.1 PSI @ 247.12 USGPM @ BOR plus 250 USPM hose
allowance. What flow test results should have been used for this system
design? I  bet you can't guess what numbers the existing system has been
designed too?? I can find nothing that requires the design contractor to use
the most demanding curve, If test three had not been performed we would have
no real indication of the water available!
Can contractors arbitrarily choose curves to meet their design needs, can
interpreted points on a graph such as those used in test two be used over
real numbers such as those in test three? My gut tells me no, but it seems
the wallet once again decides.

 

Thanks in advance.

 

Jamey

 

-- next part --
An HTML attachment was scrubbed...
URL:
http://fireball.firesprinkler.org/mailman/private/sprinklerforum/attach
ments/20120402/5b9871be/attachment.html
___
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
___
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

___
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
___
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

___
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum


RE: Flow Test

2012-04-02 Thread Craig.Prahl
[mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of Jamey
Prentice
Sent: Monday, April 02, 2012 2:12 PM
To: sprinklerforum@firesprinkler.org
Subject: RE: Flow Test

That is also my take on the matter, the standard however does not appear to
specifically require this!!! As indicated NFPA 291-2010 4.3.6 states  To
obtain satisfactory test results of theoretical calculations of expected
flows or rated capacities, sufficient discharge should be achieved to cause
a drop in pressure at the residual hydrant of at least 25% OR to flow the
total demand necessary for fire-fighting purposes. It does not require the
contractor to use whichever demand is greater. In this case all tests
achieve a drop of 25% as required by the standard however only one test of
the three meets the system demand and only when using theoretical numbers
extrapolated from the curve. What is to prevent a contractor from only
flowing until a 25% drop in residual pressure has been achieved? On small
dead end water mains this would be very easy to achieve however it would not
provide a good indication of the actual condition or availability at the
main. 

-Original Message-
From: sprinklerforum-boun...@firesprinkler.org
[mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of CH Fire -
Mike Gallello
Sent: Monday, April 02, 2012 2:40 PM
To: sprinklerforum@firesprinkler.org
Subject: RE: Flow Test

Technically the hydrant flow test should be conducted in accordance with
NFPA 291.  It's rare anyone does it though, it's the generic static, 1 ports
then two ports for a 3 point graph.  Look in the back of 13 for Fig A.22.3.4
for the idiot proof method for the flow test data.
Beyond this, in 291 there's a line (4.3.6) to flow the total demand
necessary for fire fighting purposes.  Well, spin that into sprinkler
system demand values and it's pretty simple.  Plot your 3-4 point graph
depending on how many points you need to represent your sprinkler demand
flow and get an actual curve, not a 2 point line.
IE We had a tire storage facility here, approximate estimated gallons for
the system demand was around 3000 gpm.  We had to static one as usual, but
then we had to pop 2 separate hydrants with both 2.5 outlets to simulate
the drop in the water system for the sprinkler system demand.
Long story even longer, you cannot extrapolate a water supply curve
from a static and a single residual point - you have to get enough flow out
of the hydrants to approximate sprinkler demand flows.  At least that's my
take on it anyway...


-Original Message-
From: sprinklerforum-boun...@firesprinkler.org
[mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of Jamey
Prentice
Sent: Monday, April 02, 2012 1:49 PM
To: sprinklerforum@firesprinkler.org
Subject: Flow Test

We are looking at a project that involves an addition to an existing
Institutional occupancy(University)in Ontario Canada. Existing flow tests
indicate available flows as follows:

 

Static 68 PSI

 

Test 1-50 PSI @ 223 USGPM

Test 2-39 PSI @ 416 USGPM

Test 3-13 PSI @ 538 USGPM

 

Existing Hydraulic calculations show a most demanding area calculation for
the boiler room requiring 23.1 PSI @ 247.12 USGPM @ BOR plus 250 USPM hose
allowance. What flow test results should have been used for this system
design? I  bet you can't guess what numbers the existing system has been
designed too?? I can find nothing that requires the design contractor to use
the most demanding curve, If test three had not been performed we would have
no real indication of the water available!
Can contractors arbitrarily choose curves to meet their design needs, can
interpreted points on a graph such as those used in test two be used over
real numbers such as those in test three? My gut tells me no, but it seems
the wallet once again decides.

 

Thanks in advance.

 

Jamey

 

-- next part --
An HTML attachment was scrubbed...
URL:
http://fireball.firesprinkler.org/mailman/private/sprinklerforum/attach
ments/20120402/5b9871be/attachment.html
___
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
___
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

___
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
___
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

___
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
___
Sprinklerforum mailing list

RE: Flow Test

2012-04-02 Thread Bill Brooks
Common practice in my experience is to list these flows as part of the
contract documents and then require the winning contractor to conduct a
confirming flow test prior to submitting drawings and calculations.  I
assume you've accounted for elevation in your example in that the
static/residual hydrant is at the same elevation as the BOR.  But I'm not
saying I would list these flows or issue this documentation as you've
described.

Bill Brooks

William N. Brooks, P.E.
Brooks Fire Protection Engineering Inc.
372 Wilett Drive
Severna Park, MD 21146-1904
410-544-3620
410-544-3032 FAX
412-400-6528 Cell

-Original Message-
From: sprinklerforum-boun...@firesprinkler.org
[mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of Jamey
Prentice
Sent: Monday, April 02, 2012 1:49 PM
To: sprinklerforum@firesprinkler.org
Subject: Flow Test

We are looking at a project that involves an addition to an existing
Institutional occupancy(University)in Ontario Canada. Existing flow tests
indicate available flows as follows:

 

Static 68 PSI

 

Test 1-50 PSI @ 223 USGPM

Test 2-39 PSI @ 416 USGPM

Test 3-13 PSI @ 538 USGPM

 

Existing Hydraulic calculations show a most demanding area calculation for
the boiler room requiring 23.1 PSI @ 247.12 USGPM @ BOR plus 250 USPM hose
allowance. What flow test results should have been used for this system
design? I  bet you can't guess what numbers the existing system has been
designed too?? I can find nothing that requires the design contractor to use
the most demanding curve, If test three had not been performed we would have
no real indication of the water available! Can contractors arbitrarily
choose curves to meet their design needs, can interpreted points on a graph
such as those used in test two be used over real numbers such as those in
test three? My gut tells me no, but it seems the wallet once again decides.

 

Thanks in advance.

 

Jamey

 

-- next part --
An HTML attachment was scrubbed...
URL:
http://fireball.firesprinkler.org/mailman/private/sprinklerforum/attachment
s/20120402/5b9871be/attachment.html
___
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

___
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum


RE: Flow Test

2012-04-02 Thread Mark Sornsin
.

Mark A. Sornsin, PE| Fire Protection Engineer Ulteig Engineers, Inc.| Fargo, ND 
mark.sorn...@ulteig.com 




-Original Message-
From: sprinklerforum-boun...@firesprinkler.org
[mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of Jamey Prentice
Sent: Monday, April 02, 2012 2:12 PM
To: sprinklerforum@firesprinkler.org
Subject: RE: Flow Test

That is also my take on the matter, the standard however does not appear to 
specifically require this!!! As indicated NFPA 291-2010 4.3.6 states  To 
obtain satisfactory test results of theoretical calculations of expected flows 
or rated capacities, sufficient discharge should be achieved to cause a drop in 
pressure at the residual hydrant of at least 25% OR to flow the total demand 
necessary for fire-fighting purposes. It does not require the contractor to 
use whichever demand is greater. In this case all tests achieve a drop of 25% 
as required by the standard however only one test of the three meets the system 
demand and only when using theoretical numbers extrapolated from the curve. 
What is to prevent a contractor from only flowing until a 25% drop in residual 
pressure has been achieved? On small dead end water mains this would be very 
easy to achieve however it would not provide a good indication of the actual 
condition or availability at the main. 

-Original Message-
From: sprinklerforum-boun...@firesprinkler.org
[mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of CH Fire - Mike 
Gallello
Sent: Monday, April 02, 2012 2:40 PM
To: sprinklerforum@firesprinkler.org
Subject: RE: Flow Test

Technically the hydrant flow test should be conducted in accordance with NFPA 
291.  It's rare anyone does it though, it's the generic static, 1 ports then 
two ports for a 3 point graph.  Look in the back of 13 for Fig A.22.3.4 for the 
idiot proof method for the flow test data.
Beyond this, in 291 there's a line (4.3.6) to flow the total demand necessary 
for fire fighting purposes.  Well, spin that into sprinkler system demand 
values and it's pretty simple.  Plot your 3-4 point graph depending on how many 
points you need to represent your sprinkler demand flow and get an actual 
curve, not a 2 point line.
IE We had a tire storage facility here, approximate estimated gallons for the 
system demand was around 3000 gpm.  We had to static one as usual, but then we 
had to pop 2 separate hydrants with both 2.5 outlets to simulate the drop in 
the water system for the sprinkler system demand.
Long story even longer, you cannot extrapolate a water supply curve
from a static and a single residual point - you have to get enough flow out of 
the hydrants to approximate sprinkler demand flows.  At least that's my take on 
it anyway...


-Original Message-
From: sprinklerforum-boun...@firesprinkler.org
[mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of Jamey Prentice
Sent: Monday, April 02, 2012 1:49 PM
To: sprinklerforum@firesprinkler.org
Subject: Flow Test

We are looking at a project that involves an addition to an existing 
Institutional occupancy(University)in Ontario Canada. Existing flow tests 
indicate available flows as follows:

 

Static 68 PSI

 

Test 1-50 PSI @ 223 USGPM

Test 2-39 PSI @ 416 USGPM

Test 3-13 PSI @ 538 USGPM

 

Existing Hydraulic calculations show a most demanding area calculation for the 
boiler room requiring 23.1 PSI @ 247.12 USGPM @ BOR plus 250 USPM hose 
allowance. What flow test results should have been used for this system design? 
I  bet you can't guess what numbers the existing system has been designed too?? 
I can find nothing that requires the design contractor to use the most 
demanding curve, If test three had not been performed we would have no real 
indication of the water available!
Can contractors arbitrarily choose curves to meet their design needs, can 
interpreted points on a graph such as those used in test two be used over real 
numbers such as those in test three? My gut tells me no, but it seems the 
wallet once again decides.

 

Thanks in advance.

 

Jamey

 

-- next part --
An HTML attachment was scrubbed...
URL:
http://fireball.firesprinkler.org/mailman/private/sprinklerforum/attach
ments/20120402/5b9871be/attachment.html
___
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
___
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

___
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
___
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

RE: Flow Test

2012-04-02 Thread Mark Sornsin
Sadly, common practice in my part of the world is to have no water flow data 
whatsoever. At most, you may get a requirement to do a hydrant flow test. I 
have seen projects for new facilities in new parts of towns that did not have a 
water supply at the time of bidding (muni water not yet extended to that area), 
yet the EOR didn't see a problem with not providing an estimated water supply. 
Once in my contracting days we challenged the EOR during bidding - their 
solution was to add an addendum to include a booster pump... no controls in 
place to eliminate the pump if the muni water was adequate. Just let the owner 
pick up the extra cost regardless if it is needed. And since these guys usually 
get paid on a percentage of construction, it was win-win right?

Mark A. Sornsin, PE| Fire Protection Engineer 
Ulteig Engineers, Inc.| Fargo, ND  
mark.sorn...@ulteig.com 




-Original Message-
From: sprinklerforum-boun...@firesprinkler.org 
[mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of Bill Brooks
Sent: Monday, April 02, 2012 4:50 PM
To: sprinklerforum@firesprinkler.org
Subject: RE: Flow Test

Common practice in my experience is to list these flows as part of the contract 
documents and then require the winning contractor to conduct a confirming 
flow test prior to submitting drawings and calculations.  I assume you've 
accounted for elevation in your example in that the static/residual hydrant is 
at the same elevation as the BOR.  But I'm not saying I would list these flows 
or issue this documentation as you've described.

Bill Brooks

William N. Brooks, P.E.
Brooks Fire Protection Engineering Inc.
372 Wilett Drive
Severna Park, MD 21146-1904
410-544-3620
410-544-3032 FAX
412-400-6528 Cell

-Original Message-
From: sprinklerforum-boun...@firesprinkler.org
[mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of Jamey Prentice
Sent: Monday, April 02, 2012 1:49 PM
To: sprinklerforum@firesprinkler.org
Subject: Flow Test

We are looking at a project that involves an addition to an existing 
Institutional occupancy(University)in Ontario Canada. Existing flow tests 
indicate available flows as follows:

 

Static 68 PSI

 

Test 1-50 PSI @ 223 USGPM

Test 2-39 PSI @ 416 USGPM

Test 3-13 PSI @ 538 USGPM

 

Existing Hydraulic calculations show a most demanding area calculation for the 
boiler room requiring 23.1 PSI @ 247.12 USGPM @ BOR plus 250 USPM hose 
allowance. What flow test results should have been used for this system design? 
I  bet you can't guess what numbers the existing system has been designed too?? 
I can find nothing that requires the design contractor to use the most 
demanding curve, If test three had not been performed we would have no real 
indication of the water available! Can contractors arbitrarily choose curves to 
meet their design needs, can interpreted points on a graph such as those used 
in test two be used over real numbers such as those in test three? My gut tells 
me no, but it seems the wallet once again decides.

 

Thanks in advance.

 

Jamey

 

-- next part --
An HTML attachment was scrubbed...
URL:
http://fireball.firesprinkler.org/mailman/private/sprinklerforum/attachment
s/20120402/5b9871be/attachment.html
___
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

___
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
___
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum


Re: Rack Storage of Cars?

2012-04-02 Thread Dave Phelan
I also recall a short blurb in Sprinkler Quarterly a few years (maybe even
6) back.  I scanned the article and will try to find it if you'd like - just
drop me an email off list.  The takeaway from the article was so simple and
straightforward I never forgot it
By definition Extra Hazard Grp 2 occupancy classification includes the
phrase '... or occupancies where shielding of combustibles is extensive.'
One might argue that one or more cars positioned over a lower car which is
on fire would extensively shield the fire from the sprinkler discharge at
the ceiling level.  Perhaps that explains why the stackers in this metro
area all seem to be outside in open parking lots

Dave Phelan


___
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum


Re: Flow Test

2012-04-02 Thread Ron Greenman
Email needs a like button.

On Mon, Apr 2, 2012 at 3:10 PM, Mark Sornsin mark.sorn...@ulteig.comwrote:

 Sadly, common practice in my part of the world is to have no water flow
 data whatsoever. At most, you may get a requirement to do a hydrant flow
 test. I have seen projects for new facilities in new parts of towns that
 did not have a water supply at the time of bidding (muni water not yet
 extended to that area), yet the EOR didn't see a problem with not providing
 an estimated water supply. Once in my contracting days we challenged the
 EOR during bidding - their solution was to add an addendum to include a
 booster pump... no controls in place to eliminate the pump if the muni
 water was adequate. Just let the owner pick up the extra cost regardless if
 it is needed. And since these guys usually get paid on a percentage of
 construction, it was win-win right?

 Mark A. Sornsin, PE| Fire Protection Engineer
 Ulteig Engineers, Inc.| Fargo, ND
 mark.sorn...@ulteig.com




 -Original Message-
 From: sprinklerforum-boun...@firesprinkler.org [mailto:
 sprinklerforum-boun...@firesprinkler.org] On Behalf Of Bill Brooks
 Sent: Monday, April 02, 2012 4:50 PM
 To: sprinklerforum@firesprinkler.org
 Subject: RE: Flow Test

 Common practice in my experience is to list these flows as part of the
 contract documents and then require the winning contractor to conduct a
 confirming flow test prior to submitting drawings and calculations.  I
 assume you've accounted for elevation in your example in that the
 static/residual hydrant is at the same elevation as the BOR.  But I'm not
 saying I would list these flows or issue this documentation as you've
 described.

 Bill Brooks

 William N. Brooks, P.E.
 Brooks Fire Protection Engineering Inc.
 372 Wilett Drive
 Severna Park, MD 21146-1904
 410-544-3620
 410-544-3032 FAX
 412-400-6528 Cell

 -Original Message-
 From: sprinklerforum-boun...@firesprinkler.org
 [mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of Jamey
 Prentice
 Sent: Monday, April 02, 2012 1:49 PM
 To: sprinklerforum@firesprinkler.org
 Subject: Flow Test

 We are looking at a project that involves an addition to an existing
 Institutional occupancy(University)in Ontario Canada. Existing flow tests
 indicate available flows as follows:



 Static 68 PSI



 Test 1-50 PSI @ 223 USGPM

 Test 2-39 PSI @ 416 USGPM

 Test 3-13 PSI @ 538 USGPM



 Existing Hydraulic calculations show a most demanding area calculation for
 the boiler room requiring 23.1 PSI @ 247.12 USGPM @ BOR plus 250 USPM hose
 allowance. What flow test results should have been used for this system
 design? I  bet you can't guess what numbers the existing system has been
 designed too?? I can find nothing that requires the design contractor to
 use the most demanding curve, If test three had not been performed we would
 have no real indication of the water available! Can contractors arbitrarily
 choose curves to meet their design needs, can interpreted points on a graph
 such as those used in test two be used over real numbers such as those in
 test three? My gut tells me no, but it seems the wallet once again decides.



 Thanks in advance.



 Jamey



 -- next part --
 An HTML attachment was scrubbed...
 URL:
 
 http://fireball.firesprinkler.org/mailman/private/sprinklerforum/attachment
 s/20120402/5b9871be/attachment.htmlhttp://fireball.firesprinkler.org/mailman/private/sprinklerforum/attachments/20120402/5b9871be/attachment.html
 
 ___
 Sprinklerforum mailing list
 Sprinklerforum@firesprinkler.org
 http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

 ___
 Sprinklerforum mailing list
 Sprinklerforum@firesprinkler.org
 http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
 ___
 Sprinklerforum mailing list
 Sprinklerforum@firesprinkler.org
 http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum




-- 
Ron Greenman
Instructor
Fire Protection Engineering Technology
Bates Technical College
1101 So. Yakima Ave.
Tacoma, WA 98405

rgreen...@bates.ctc.edu

http://www.bates.ctc.edu/fireprotection/

253.680.7346
253.576.9700 (cell)

Member:
ASEE, SFPE, ASCET, NFPA, AFSA, NFSA, AFAA, NIBS, WSAFM, WFC

They are happy men whose natures sort with their vocations. -Francis Bacon,
essayist, philosopher, and statesman (1561-1626)
-- next part --
An HTML attachment was scrubbed...
URL: 
http://fireball.firesprinkler.org/mailman/private/sprinklerforum/attachments/20120402/602d2941/attachment.html
___
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum


RE: Flow Test

2012-04-02 Thread Russell Carol Gregory
 here, approximate estimated gallons for
the system demand was around 3000 gpm.  We had to static one as usual, but
then we had to pop 2 separate hydrants with both 2.5 outlets to simulate
the drop in the water system for the sprinkler system demand.
Long story even longer, you cannot extrapolate a water supply curve
from a static and a single residual point - you have to get enough flow out
of the hydrants to approximate sprinkler demand flows.  At least that's my
take on it anyway...


-Original Message-
From: sprinklerforum-boun...@firesprinkler.org
[mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of Jamey
Prentice
Sent: Monday, April 02, 2012 1:49 PM
To: sprinklerforum@firesprinkler.org
Subject: Flow Test

We are looking at a project that involves an addition to an existing
Institutional occupancy(University)in Ontario Canada. Existing flow tests
indicate available flows as follows:

 

Static 68 PSI

 

Test 1-50 PSI @ 223 USGPM

Test 2-39 PSI @ 416 USGPM

Test 3-13 PSI @ 538 USGPM

 

Existing Hydraulic calculations show a most demanding area calculation for
the boiler room requiring 23.1 PSI @ 247.12 USGPM @ BOR plus 250 USPM hose
allowance. What flow test results should have been used for this system
design? I  bet you can't guess what numbers the existing system has been
designed too?? I can find nothing that requires the design contractor to use
the most demanding curve, If test three had not been performed we would have
no real indication of the water available!
Can contractors arbitrarily choose curves to meet their design needs, can
interpreted points on a graph such as those used in test two be used over
real numbers such as those in test three? My gut tells me no, but it seems
the wallet once again decides.

 

Thanks in advance.

 

Jamey

 

-- next part --
An HTML attachment was scrubbed...
URL:
http://fireball.firesprinkler.org/mailman/private/sprinklerforum/attach
ments/20120402/5b9871be/attachment.html
___
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
___
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

___
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
___
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

___
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
___
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum


___
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum