RE: No hydraulic name plate, no existing plans

2014-11-06 Thread Aaron Peck
I agree Scott. A fire official saying it was the water supply is questionable 
throws red flags up. Even if he said it was questionable after 13 years of 
being in service it would mean, to me, the contractor should definitely make 
sure they do their due diligence in make sure that the system is acceptable as 
life safety.  And not assume.

--
AMP Fire Protection Design
Aaron Peck, SET  •  Freelance Designer
C: (202) 407-9079 NICET Certified NFPA Member
**Currently in Manama, Bahrain UTC/GMT +3:00 hours (7:00 Hours ahead of EST)**
**Bahrain Number #(+973)39605669 Skype forwards to this #**



-Original Message-
From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On 
Behalf Of Scott A Futrell
Sent: Thursday, November 06, 2014 6:08 AM
To: sprinklerforum@lists.firesprinkler.org
Subject: RE: No hydraulic name plate, no existing plans

This has been an interesting thread.



It's a retirement home so the sprinkler system would seem to be essential to 
me, not that any aren't, but...I’d like to know my parents were living 
somewhere that had a sprinkler system installed properly and not by cutting 
corners, or making guesses.  And, doesn’t “questionable” water supply bother 
anyone other than me?



The correct and only answer is, 1)take a water flow test in accordance with 
NFPA 291, not messing around with a main drain.  2)Survey the existing system 
in accordance with NFPA 13 and determine all of the existing pipe size and 
as-built routing to the new addition.  3)Calculate the new addition with the 
existing pipe size and fittings, valves, elevation, and so on back to the flow 
test location.



Anything less would not be minimum standard of care sprinkler system design, 
would it?



Scott Futrell



Office: (763) 425-1001 x 12

Cell: (612) 759-5556



-Original Message-

From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On 
Behalf Of Douglas Hicks

Sent: Wednesday, November 05, 2014 3:17 PM

To: sprinklerforum@lists.firesprinkler.org

Subject: No hydraulic name plate, no existing plans



I have been asked to extend sprinkler coverage to an addition, 17.5’ long x 13’ 
across.  The ceiling is a cathedral ceiling, 13’ 2” at the ceiling and 9’ 3 “ 
high at the sidewall.  The existing sprinkler piping is behind the 13’ wall, 
pointing down the 17.5’ length.  No body can find plans from the original 
construction, there is not a hydraulic nameplate on the sprinkler system.  The 
Fire Chief remembers that during construction, the water supply was 
“questionable”.There is not a forward flow port so  I can not get a water 
GPM/psi measurement.  There is a 1.5 “ FDC at the front of the building. There 
is a fire hydrant across the parking lot, about 75 feet away.  The 5 year 
average for the static pressure is 34 psi and the residual is 27 psi, through 
the main drain.



The building is about 13 years old and is a retirement home.



My concern is the lack of information about the water supply.  The building is 
on a hill, about the level of the municipal water tank, which is on another 
hill.



Can I get an accurate reading on the water supply from the fire hydrant, or the 
2” main drain?  Or should I put a Forward Flow test port in before doing 
anything else?  And if I do get a good water reading, I still will not know 
what the system demand is.  So then do I need to hire someone to crawl the 
attic and take measurements of the piping?









___

Sprinklerforum mailing list

Sprinklerforum@lists.firesprinkler.org

http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org


RE: No hydraulic name plate, no existing plans

2014-11-06 Thread Duane Johnson
I would recommend doing the test inside the building, even if it means 
modifying the system such as adding a tee to perform a test downstream of the 
valves, meters, etc. This will take out the guess work of elevation, unknown 
friction losses in unknown fittings/valves, etc...especially if the water 
supply is questionable.

On a side note, we put forward flow test outlets on our systems as code 
requires.

Duane Johnson, PE
Design Manager
Strickland Fire Protection
301-474-1136 Office
301-455-0010 Cell



-Original Message-
From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On 
Behalf Of Scott A Futrell
Sent: Wednesday, November 05, 2014 10:08 PM
To: sprinklerforum@lists.firesprinkler.org
Subject: RE: No hydraulic name plate, no existing plans

This has been an interesting thread.



It's a retirement home so the sprinkler system would seem to be essential to 
me, not that any aren't, but...I’d like to know my parents were living 
somewhere that had a sprinkler system installed properly and not by cutting 
corners, or making guesses.  And, doesn’t “questionable” water supply bother 
anyone other than me?



The correct and only answer is, 1)take a water flow test in accordance with 
NFPA 291, not messing around with a main drain.  2)Survey the existing system 
in accordance with NFPA 13 and determine all of the existing pipe size and 
as-built routing to the new addition.  3)Calculate the new addition with the 
existing pipe size and fittings, valves, elevation, and so on back to the flow 
test location.



Anything less would not be minimum standard of care sprinkler system design, 
would it?



Scott Futrell



Office: (763) 425-1001 x 12

Cell: (612) 759-5556



-Original Message-

From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On 
Behalf Of Douglas Hicks

Sent: Wednesday, November 05, 2014 3:17 PM

To: sprinklerforum@lists.firesprinkler.org

Subject: No hydraulic name plate, no existing plans



I have been asked to extend sprinkler coverage to an addition, 17.5’ long x 13’ 
across.  The ceiling is a cathedral ceiling, 13’ 2” at the ceiling and 9’ 3 “ 
high at the sidewall.  The existing sprinkler piping is behind the 13’ wall, 
pointing down the 17.5’ length.  No body can find plans from the original 
construction, there is not a hydraulic nameplate on the sprinkler system.  The 
Fire Chief remembers that during construction, the water supply was 
“questionable”.There is not a forward flow port so  I can not get a water 
GPM/psi measurement.  There is a 1.5 “ FDC at the front of the building. There 
is a fire hydrant across the parking lot, about 75 feet away.  The 5 year 
average for the static pressure is 34 psi and the residual is 27 psi, through 
the main drain.



The building is about 13 years old and is a retirement home.



My concern is the lack of information about the water supply.  The building is 
on a hill, about the level of the municipal water tank, which is on another 
hill.



Can I get an accurate reading on the water supply from the fire hydrant, or the 
2” main drain?  Or should I put a Forward Flow test port in before doing 
anything else?  And if I do get a good water reading, I still will not know 
what the system demand is.  So then do I need to hire someone to crawl the 
attic and take measurements of the piping?









___

Sprinklerforum mailing list

Sprinklerforum@lists.firesprinkler.org

http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org


RE: No hydraulic name plate, no existing plans

2014-11-06 Thread Cahill, Christopher
So anyone would take the word of a fire official?  Really?  Sure there are a 
few that know what they are talking about but the vast majority not so much.  
Oh and OP said Fire Chief, not fire official , even less credibility on 
average.  

And questionable water is a dumb statement IMO any way.  Nearly all systems 
have about 5-10 psi safety margin, right?  So it doesn't matter if there is 20 
psi in the street or 120 psi in the street they ALL are questionable the day 
they were put in.  And what does questionable even mean, so there is no ability 
to add a pump on weak water?  And you end up with 5-10 psi safety. There are 
water thieves that steal water from otherwise good tank and pump systems (that 
originally had 5-10 psi safety)?  Did the Fire Chief think the water was 
involved with organized crime?  Maybe they weren't sure it was two hydrogens 
and an oxygen as the primary constituent? Grain alcohol looks like water. Heavy 
water or light water because they are near a nuclear reactor of that flavor?  

I agree, the owner rarely has the original plans.  What about the original 
contractor, sprinkler or general?  What about the City?  Is it a licensed 
facility?  Licensing agency?

This is an addition = new construction.  I don't even see the question on 
determining the water supply and sizing the pipe.  Where in NFPA 13 does it say 
anything but NFPA 291?  Where in NFPA 291 does it talk about drain test?  

If you want to use existing pipe fine, trace it and model the relevant 
portions. In many cases the plan will only get you in the neighborhood anyway.  
I'd want you to actually verify the existing piping is as show on the existing 
drawing in the relevant areas.   

Let me save you the trouble of asking about the rant portions of the above, YES:

Its just one of those days (weeks, months)
When you don't wanna wake up
 Everything is @#%#$%
 Everybody sux
 You don't really know why
 But you want justify
 Rippin' someone's head off
 No human contact
 And if you interact
 Your life is on contract
 Your best bet is to stay away @#$#%^^
 It's just one of those days!! 

Chris Cahill, PE*
Associate Fire Protection Engineer 
Burns  McDonnell
Phone:  952.656.3652
Fax:  952.229.2923
ccah...@burnsmcd.com
www.burnsmcd.com
*Registered in: MN


Proud to be #14 on FORTUNE's 2014 List of 100 Best Companies to Work For





-Original Message-
From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On 
Behalf Of Aaron Peck
Sent: Thursday, November 06, 2014 7:22 AM
To: sprinklerforum@lists.firesprinkler.org
Subject: RE: No hydraulic name plate, no existing plans

I agree Scott. A fire official saying it was the water supply is questionable 
throws red flags up. Even if he said it was questionable after 13 years of 
being in service it would mean, to me, the contractor should definitely make 
sure they do their due diligence in make sure that the system is acceptable as 
life safety.  And not assume.

--
AMP Fire Protection Design
Aaron Peck, SET  •  Freelance Designer
C: (202) 407-9079 NICET Certified NFPA Member **Currently in Manama, Bahrain 
UTC/GMT +3:00 hours (7:00 Hours ahead of EST)** **Bahrain Number 
#(+973)39605669 Skype forwards to this #**



-Original Message-
From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On 
Behalf Of Scott A Futrell
Sent: Thursday, November 06, 2014 6:08 AM
To: sprinklerforum@lists.firesprinkler.org
Subject: RE: No hydraulic name plate, no existing plans

This has been an interesting thread.



It's a retirement home so the sprinkler system would seem to be essential to 
me, not that any aren't, but...I’d like to know my parents were living 
somewhere that had a sprinkler system installed properly and not by cutting 
corners, or making guesses.  And, doesn’t “questionable” water supply bother 
anyone other than me?



The correct and only answer is, 1)take a water flow test in accordance with 
NFPA 291, not messing around with a main drain.  2)Survey the existing system 
in accordance with NFPA 13 and determine all of the existing pipe size and 
as-built routing to the new addition.  3)Calculate the new addition with the 
existing pipe size and fittings, valves, elevation, and so on back to the flow 
test location.



Anything less would not be minimum standard of care sprinkler system design, 
would it?



Scott Futrell



Office: (763) 425-1001 x 12

Cell: (612) 759-5556



-Original Message-

From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On 
Behalf Of Douglas Hicks

Sent: Wednesday, November 05, 2014 3:17 PM

To: sprinklerforum@lists.firesprinkler.org

Subject: No hydraulic name plate, no existing plans



I have been asked to extend sprinkler coverage to an addition, 17.5’ long x 13’ 
across.  The ceiling is a cathedral ceiling, 13’ 2” at the ceiling and 9’ 3 “ 
high at the sidewall.  The existing sprinkler piping is behind the 13’ wall, 
pointing down the 17.5’ 

RE: No hydraulic name plate, no existing plans

2014-11-06 Thread Craig.Prahl
Someone go and take all the Red Bull from Chris.  ;)

When I have a fire chief or fire official (semantics) tell me the water supply 
is questionable I take that to mean it's not very reliable or consistent.  If 
he's the guy on the front line actually flowing hoses, and not just some desk 
jockey with a title, he would have firsthand knowledge of the water supply 
conditions.He's doing you a favor in pointing out there are issues instead 
of letting you wander aimlessly to figure this out on your own somewhere down 
the road in the course of the project.

No, not all systems have a safety margin, most designers like to push it to the 
limit and as long as the results are on the positive side of the curve and not 
negative, they are done.  It's a bad assumption that systems are designed with 
a safety margin.   

So why are there no plans and why are there no tags on the risers?   Aren't 
riser tags a requirement of NFPA 13?  

It would be awesome if a set of plans and calcs were put in a tube and left in 
the riser room chained to the riser and if the guy filling out the tag actually 
knew what all those numbers and words meant so that the tag was filled out 
properly, completely and legibly and not in pencil.  

So,
+1 for the local fire chief for trying to help, 

-1 for the slack contractor who didn't finish the job.

Would there happen to be any inspection tags on the system or a record of last 
inspection?  If yes, that may be a place to start digging for info.   Often the 
installing contractor ends up doing the follow-up inspections or may know who 
did the original work.If the sprinkler system was put in when the building 
was built, does the owner know who the General Contractor was?  

For systems that are designed to protect life and property we have a lot of 
slackness in our industry and this is a prime example of such.   Mediocrity 
should never be an acceptable level of performance.

Craig L. Prahl 
Fire Protection Group Lead
CH2MHILL
Lockwood Greene
1500 International Drive
Spartanburg, SC  29303
Direct - 864.599.4102
Fax - 864.599.8439
CH2MHILL Extension  74102
craig.pr...@ch2m.com


-Original Message-
From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On 
Behalf Of Cahill, Christopher
Sent: Thursday, November 06, 2014 8:57 AM
To: sprinklerforum@lists.firesprinkler.org
Subject: RE: No hydraulic name plate, no existing plans

So anyone would take the word of a fire official?  Really?  Sure there are a 
few that know what they are talking about but the vast majority not so much.  
Oh and OP said Fire Chief, not fire official , even less credibility on 
average.  

And questionable water is a dumb statement IMO any way.  Nearly all systems 
have about 5-10 psi safety margin, right?  So it doesn't matter if there is 20 
psi in the street or 120 psi in the street they ALL are questionable the day 
they were put in.  And what does questionable even mean, so there is no ability 
to add a pump on weak water?  And you end up with 5-10 psi safety. There are 
water thieves that steal water from otherwise good tank and pump systems (that 
originally had 5-10 psi safety)?  Did the Fire Chief think the water was 
involved with organized crime?  Maybe they weren't sure it was two hydrogens 
and an oxygen as the primary constituent? Grain alcohol looks like water. Heavy 
water or light water because they are near a nuclear reactor of that flavor?  

I agree, the owner rarely has the original plans.  What about the original 
contractor, sprinkler or general?  What about the City?  Is it a licensed 
facility?  Licensing agency?

This is an addition = new construction.  I don't even see the question on 
determining the water supply and sizing the pipe.  Where in NFPA 13 does it say 
anything but NFPA 291?  Where in NFPA 291 does it talk about drain test?  

If you want to use existing pipe fine, trace it and model the relevant 
portions. In many cases the plan will only get you in the neighborhood anyway.  
I'd want you to actually verify the existing piping is as show on the existing 
drawing in the relevant areas.   

Let me save you the trouble of asking about the rant portions of the above, YES:

Its just one of those days (weeks, months) When you don't wanna wake up  
Everything is @#%#$%  Everybody sux  You don't really know why  But you want 
justify  Rippin' someone's head off  No human contact  And if you interact  
Your life is on contract  Your best bet is to stay away @#$#%^^  It's just 
one of those days!! 

Chris Cahill, PE*
Associate Fire Protection Engineer
Burns  McDonnell
Phone:  952.656.3652
Fax:  952.229.2923
ccah...@burnsmcd.com
www.burnsmcd.com
*Registered in: MN


Proud to be #14 on FORTUNE's 2014 List of 100 Best Companies to Work For





-Original Message-
From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On 
Behalf Of Aaron Peck
Sent: Thursday, November 06, 2014 7:22 AM
To: 

NFPA 13

2014-11-06 Thread Smith, Steven D. (CSFD)
Had a question posed to me that I couldn't answer completely.

If NFPA 13 was the first document from NFPA why isn't it NFPA 1?

Steve
___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org


Re: NFPA 13

2014-11-06 Thread Todd - Work
That sounds like something I would ask. Triskaidekaphobia was obviously not a 
concern. 

Todd G Williams, PE
Fire Protection Design/Consulting
Stonington, CT
www.fpdc.com
860-535-2080 (ofc)

 On Nov 6, 2014, at 10:53 AM, Smith, Steven D. (CSFD) sdsm...@springsgov.com 
 wrote:
 
 Had a question posed to me that I couldn't answer completely.
 
 If NFPA 13 was the first document from NFPA why isn't it NFPA 1?
 
 Steve
 ___
 Sprinklerforum mailing list
 Sprinklerforum@lists.firesprinkler.org
 http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org


Re: NFPA 13

2014-11-06 Thread rongreenman .
It was but before NFPA was NFPA. Cecil has this down. Ask him.

On Thu, Nov 6, 2014 at 8:09 AM, Todd - Work t...@fpdc.com wrote:

 That sounds like something I would ask. Triskaidekaphobia was obviously
 not a concern.

 Todd G Williams, PE
 Fire Protection Design/Consulting
 Stonington, CT
 www.fpdc.com
 860-535-2080 (ofc)

  On Nov 6, 2014, at 10:53 AM, Smith, Steven D. (CSFD) 
 sdsm...@springsgov.com wrote:
 
  Had a question posed to me that I couldn't answer completely.
 
  If NFPA 13 was the first document from NFPA why isn't it NFPA 1?
 
  Steve
  ___
  Sprinklerforum mailing list
  Sprinklerforum@lists.firesprinkler.org
 
 http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
 ___
 Sprinklerforum mailing list
 Sprinklerforum@lists.firesprinkler.org

 http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org




-- 
Ron Greenman
Instructor
Fire Protection Engineering Technology
Bates Technical College
1101 So. Yakima Ave.
Tacoma, WA 98405

rgreen...@bates.ctc.edu

http://www.bates.ctc.edu/fireprotection/

253.680.7346
253.576.9700 (cell)

Member:
ASEE, SFPE, ASCET, NFPA, AFSA, NFSA, AFAA, NIBS, WSAFM, WFC, WFSC

They are happy men whose natures sort with their vocations. -Francis Bacon,
essayist, philosopher, and statesman (1561-1626)

A problem well stated is a problem half solved. -Charles F. Kettering,
inventor and engineer (1876-1958)
___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org


RE: NFPA 13

2014-11-06 Thread Jeff Bridges
Life Safety Code or something similar covered everything in the early days- 



-Original Message-
From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org]
On Behalf Of rongreenman .
Sent: Thursday, November 06, 2014 8:38 AM
To: sprinklerforum@lists.firesprinkler.org
Subject: Re: NFPA 13

It was but before NFPA was NFPA. Cecil has this down. Ask him.

On Thu, Nov 6, 2014 at 8:09 AM, Todd - Work t...@fpdc.com wrote:

 That sounds like something I would ask. Triskaidekaphobia was 
 obviously not a concern.

 Todd G Williams, PE
 Fire Protection Design/Consulting
 Stonington, CT
 www.fpdc.com
 860-535-2080 (ofc)

  On Nov 6, 2014, at 10:53 AM, Smith, Steven D. (CSFD) 
 sdsm...@springsgov.com wrote:
 
  Had a question posed to me that I couldn't answer completely.
 
  If NFPA 13 was the first document from NFPA why isn't it NFPA 1?
 
  Steve
  ___
  Sprinklerforum mailing list
  Sprinklerforum@lists.firesprinkler.org
 
 http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkl
 er.org ___
 Sprinklerforum mailing list
 Sprinklerforum@lists.firesprinkler.org

 http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkl
 er.org




--
Ron Greenman
Instructor
Fire Protection Engineering Technology
Bates Technical College
1101 So. Yakima Ave.
Tacoma, WA 98405

rgreen...@bates.ctc.edu

http://www.bates.ctc.edu/fireprotection/

253.680.7346
253.576.9700 (cell)

Member:
ASEE, SFPE, ASCET, NFPA, AFSA, NFSA, AFAA, NIBS, WSAFM, WFC, WFSC

They are happy men whose natures sort with their vocations. -Francis Bacon,
essayist, philosopher, and statesman (1561-1626)

A problem well stated is a problem half solved. -Charles F. Kettering,
inventor and engineer (1876-1958)
___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org


RE: NFPA 13

2014-11-06 Thread David Blackwell
While it doesn't address the NFPA numbering issue [1 vs. lucky 13...] the 
following article entitled History Of The NFPA Codes and Standards-Making 
System is on NFPA website and worth a read if you are into studying the 
history...

http://www.nfpa.org/~/media/Files/Codes%20and%20standards/Standards%20development%20process/HistoryNFPACodesStandards.pdf


Respectfully,


David W. S. Blackwell, II, PE, CFPE, CFI I
Chief Engineer
Office of State Fire Marshal
SC Department of Labor, Licensing,  Regulation, 141 Monticello Trail, 
Columbia, SC 29203
Telephone: 803.896.9800 [Office] 803.896.9833 [Direct]
Fax: 803.896.9806 [Office]
Email:   david.blackw...@llr.sc.gov
Website:  http://www.scfiremarshal.llronline.com/


Please note that you can sign up to receive automatic information on SC 
Division of Fire and Life Safety current events, policies, laws and procedures 
by visiting our Web site at:  http://www.scfiremarshal.llronline.com/

-Original Message-
From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On 
Behalf Of David Autry
Sent: Thursday, November 06, 2014 12:08 PM
To: sprinklerforum@lists.firesprinkler.org
Subject: RE: NFPA 13

My 1961 version is NBFU No. 13.
Standard of the National Board of Fire Underwriters for the Installation of 
Sprinkler Systems as recommended by the National Fire Protection Association

David Autry

Meininger Fire Protection
2521 West L Street, Suite 5
Lincoln, NE 68522
402.466.2616
402.466.2617 fax
da...@mfp-inc.com

-Original Message-
From: Sprinklerforum
[mailto:sprinklerforum-boun...@lists.firesprinkler.org] On Behalf Of 
rongreenman .
Sent: Thursday, November 06, 2014 10:38 AM
To: sprinklerforum@lists.firesprinkler.org
Subject: Re: NFPA 13

It was but before NFPA was NFPA. Cecil has this down. Ask him.

On Thu, Nov 6, 2014 at 8:09 AM, Todd - Work t...@fpdc.com wrote:

 That sounds like something I would ask. Triskaidekaphobia was 
 obviously not a concern.

 Todd G Williams, PE
 Fire Protection Design/Consulting
 Stonington, CT
 www.fpdc.com
 860-535-2080 (ofc)

  On Nov 6, 2014, at 10:53 AM, Smith, Steven D. (CSFD) 
 sdsm...@springsgov.com wrote:
 
  Had a question posed to me that I couldn't answer completely.
 
  If NFPA 13 was the first document from NFPA why isn't it NFPA 1?
 
  Steve
  ___
  Sprinklerforum mailing list
  Sprinklerforum@lists.firesprinkler.org
 
 http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkl
 er.org ___
 Sprinklerforum mailing list
 Sprinklerforum@lists.firesprinkler.org

 http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkl
 er.org




--
Ron Greenman
Instructor
Fire Protection Engineering Technology
Bates Technical College
1101 So. Yakima Ave.
Tacoma, WA 98405

rgreen...@bates.ctc.edu

http://www.bates.ctc.edu/fireprotection/

253.680.7346
253.576.9700 (cell)

Member:
ASEE, SFPE, ASCET, NFPA, AFSA, NFSA, AFAA, NIBS, WSAFM, WFC, WFSC

They are happy men whose natures sort with their vocations. -Francis Bacon, 
essayist, philosopher, and statesman (1561-1626)

A problem well stated is a problem half solved. -Charles F. Kettering, inventor 
and engineer (1876-1958) ___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.o
rg
___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org


Re: NFPA 13

2014-11-06 Thread Forest Wilson
Maybe it's like ordering checks...you never start with number one, usually
a higher number.

On Thu, Nov 6, 2014 at 12:16 PM, David Blackwell david.blackw...@llr.sc.gov
 wrote:

 While it doesn't address the NFPA numbering issue [1 vs. lucky 13...]
 the following article entitled History Of The NFPA Codes and
 Standards-Making System is on NFPA website and worth a read if you are
 into studying the history...


 http://www.nfpa.org/~/media/Files/Codes%20and%20standards/Standards%20development%20process/HistoryNFPACodesStandards.pdf


 Respectfully,


 David W. S. Blackwell, II, PE, CFPE, CFI I
 Chief Engineer
 Office of State Fire Marshal
 SC Department of Labor, Licensing,  Regulation, 141 Monticello Trail,
 Columbia, SC 29203
 Telephone: 803.896.9800 [Office] 803.896.9833 [Direct]
 Fax: 803.896.9806 [Office]
 Email:   david.blackw...@llr.sc.gov
 Website:  http://www.scfiremarshal.llronline.com/


 Please note that you can sign up to receive automatic information on SC
 Division of Fire and Life Safety current events, policies, laws and
 procedures by visiting our Web site at:
 http://www.scfiremarshal.llronline.com/

 -Original Message-
 From: Sprinklerforum [mailto:
 sprinklerforum-boun...@lists.firesprinkler.org] On Behalf Of David Autry
 Sent: Thursday, November 06, 2014 12:08 PM
 To: sprinklerforum@lists.firesprinkler.org
 Subject: RE: NFPA 13

 My 1961 version is NBFU No. 13.
 Standard of the National Board of Fire Underwriters for the Installation
 of Sprinkler Systems as recommended by the National Fire Protection
 Association

 David Autry

 Meininger Fire Protection
 2521 West L Street, Suite 5
 Lincoln, NE 68522
 402.466.2616
 402.466.2617 fax
 da...@mfp-inc.com

 -Original Message-
 From: Sprinklerforum
 [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On Behalf Of
 rongreenman .
 Sent: Thursday, November 06, 2014 10:38 AM
 To: sprinklerforum@lists.firesprinkler.org
 Subject: Re: NFPA 13

 It was but before NFPA was NFPA. Cecil has this down. Ask him.

 On Thu, Nov 6, 2014 at 8:09 AM, Todd - Work t...@fpdc.com wrote:

  That sounds like something I would ask. Triskaidekaphobia was
  obviously not a concern.
 
  Todd G Williams, PE
  Fire Protection Design/Consulting
  Stonington, CT
  www.fpdc.com
  860-535-2080 (ofc)
 
   On Nov 6, 2014, at 10:53 AM, Smith, Steven D. (CSFD) 
  sdsm...@springsgov.com wrote:
  
   Had a question posed to me that I couldn't answer completely.
  
   If NFPA 13 was the first document from NFPA why isn't it NFPA 1?
  
   Steve
   ___
   Sprinklerforum mailing list
   Sprinklerforum@lists.firesprinkler.org
  
  http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkl
  er.org ___
  Sprinklerforum mailing list
  Sprinklerforum@lists.firesprinkler.org
 
  http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkl
  er.org
 



 --
 Ron Greenman
 Instructor
 Fire Protection Engineering Technology
 Bates Technical College
 1101 So. Yakima Ave.
 Tacoma, WA 98405

 rgreen...@bates.ctc.edu

 http://www.bates.ctc.edu/fireprotection/

 253.680.7346
 253.576.9700 (cell)

 Member:
 ASEE, SFPE, ASCET, NFPA, AFSA, NFSA, AFAA, NIBS, WSAFM, WFC, WFSC

 They are happy men whose natures sort with their vocations. -Francis
 Bacon, essayist, philosopher, and statesman (1561-1626)

 A problem well stated is a problem half solved. -Charles F. Kettering,
 inventor and engineer (1876-1958)
 ___
 Sprinklerforum mailing list
 Sprinklerforum@lists.firesprinkler.org
 http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.o
 rg
 http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
 ___
 Sprinklerforum mailing list
 Sprinklerforum@lists.firesprinkler.org

 http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
 ___
 Sprinklerforum mailing list
 Sprinklerforum@lists.firesprinkler.org

 http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org