I agree Scott. A fire official saying it was the water supply is "questionable" 
throws red flags up. Even if he said it was questionable after 13 years of 
being in service it would mean, to me, the contractor should definitely make 
sure they do their due diligence in make sure that the system is acceptable as 
life safety.  And not assume.

--
AMP Fire Protection Design
Aaron Peck, SET  •  Freelance Designer
C: (202) 407-9079 NICET Certified NFPA Member
**Currently in Manama, Bahrain UTC/GMT +3:00 hours (7:00 Hours ahead of EST)**
**Bahrain Number #(+973)39605669 Skype forwards to this #**



-----Original Message-----
From: Sprinklerforum [mailto:[email protected]] On 
Behalf Of Scott A Futrell
Sent: Thursday, November 06, 2014 6:08 AM
To: [email protected]
Subject: RE: No hydraulic name plate, no existing plans

This has been an interesting thread.



It's a retirement home so the sprinkler system would seem to be essential to 
me, not that any aren't, but...I’d like to know my parents were living 
somewhere that had a sprinkler system installed properly and not by cutting 
corners, or making guesses.  And, doesn’t “questionable” water supply bother 
anyone other than me?



The correct and only answer is, 1)take a water flow test in accordance with 
NFPA 291, not messing around with a main drain.  2)Survey the existing system 
in accordance with NFPA 13 and determine all of the existing pipe size and 
as-built routing to the new addition.  3)Calculate the new addition with the 
existing pipe size and fittings, valves, elevation, and so on back to the flow 
test location.



Anything less would not be minimum standard of care sprinkler system design, 
would it?



Scott Futrell



Office: (763) 425-1001 x 12

Cell: (612) 759-5556



-----Original Message-----

From: Sprinklerforum [mailto:[email protected]] On 
Behalf Of Douglas Hicks

Sent: Wednesday, November 05, 2014 3:17 PM

To: [email protected]

Subject: No hydraulic name plate, no existing plans



I have been asked to extend sprinkler coverage to an addition, 17.5’ long x 13’ 
across.  The ceiling is a cathedral ceiling, 13’ 2” at the ceiling and 9’ 3 “ 
high at the sidewall.  The existing sprinkler piping is behind the 13’ wall, 
pointing down the 17.5’ length.  No body can find plans from the original 
construction, there is not a hydraulic nameplate on the sprinkler system.  The 
Fire Chief remembers that during construction, the water supply was 
“questionable”.    There is not a forward flow port so  I can not get a water 
GPM/psi measurement.  There is a 1.5 “ FDC at the front of the building. There 
is a fire hydrant across the parking lot, about 75 feet away.  The 5 year 
average for the static pressure is 34 psi and the residual is 27 psi, through 
the main drain.



The building is about 13 years old and is a retirement home.



My concern is the lack of information about the water supply.  The building is 
on a hill, about the level of the municipal water tank, which is on another 
hill.



Can I get an accurate reading on the water supply from the fire hydrant, or the 
2” main drain?  Or should I put a Forward Flow test port in before doing 
anything else?  And if I do get a good water reading, I still will not know 
what the system demand is.  So then do I need to hire someone to crawl the 
attic and take measurements of the piping?









_______________________________________________

Sprinklerforum mailing list

[email protected]

http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to