Re: Listed sprinkler guard for horizontal or vertical spray sidewalls

2020-06-24 Thread John Denhardt via Sprinklerforum
Agree. This forum is a valuable asset. Thanks to all for their contribution. 

John

John August Denhardt, P.E.
Vice-President Engineering and Technical Services
American Fire Sprinkler Association 
301-343-1457

> On Jun 24, 2020, at 7:03 PM, Mark Phillips via Sprinklerforum 
>  wrote:
> 
> 
> Gotta love all the great people here!
> 
> Sent from my mobile device
> Please excuse spelling, grammar, and auto correction.
> 
> Mark Phillips
> Branch Manager
> Fire Sprinkler Design, Install, Inspections
> Service, Backflows, Fire Alarm Inspections
> 
> 832-101 Purser Drive
> Raleigh NC 27603
> Phone: 919-779-4010
> Fax : 919-779-4014
> Cell : 919-268-7587
> Email : philli...@pyebarkerfire.com
> Web : www.pyebarkerfire.com
> 
> From: Sprinklerforum  on 
> behalf of Steve Leyton via Sprinklerforum 
> 
> Sent: Wednesday, June 24, 2020 6:03:28 PM
> To: sprinklerforum@lists.firesprinkler.org 
> 
> Cc: Steve Leyton ; Dennis Wilson 
> 
> Subject: RE: Listed sprinkler guard for horizontal or vertical spray sidewalls
>  
> [EXTERNAL]
> Thank you – a direct HIT!
>  
> SL
>  
> From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] 
> On Behalf Of Dennis Wilson via Sprinklerforum
> Sent: Wednesday, June 24, 2020 2:27 PM
> To: sprinklerforum@lists.firesprinkler.org
> Cc: Dennis Wilson 
> Subject: RE: Listed sprinkler guard for horizontal or vertical spray sidewalls
>  
> Reliable F1FR-56
>  
> From: Sprinklerforum  On 
> Behalf Of Steve Leyton via Sprinklerforum
> Sent: Wednesday, June 24, 2020 4:21 PM
> To: sprinklerforum@lists.firesprinkler.org
> Cc: Steve Leyton 
> Subject: Listed sprinkler guard for horizontal or vertical spray sidewalls
>  
> Does anyone know if any manufacturers have a listed guard for standard 
> sidewall sprinklers?   We specified Viking on a project where the sprinklers 
> are installed on the piping, running alongside beams in an open area of a 
> tilt-up building that is being repurposed as a charter school, so Light 
> Hazard occupancy class.   The client has requested that these particular 
> sprinklers be protected from potential damage, but they are already installed 
> so our first choice is to find a solution for horizontal sidewalls.   2nd 
> choice is to roll the piping and install vertical sidewalls (I think we 
> should have designed it that way in the first place in hindsight), so if no 
> guards are available, at least the piping will protect the sprinklers.   Any 
> of the manufacturers have a listed solution for horizontal or vertical?
>  
>  
> 
>  
>  
> ___
> Sprinklerforum mailing list
> Sprinklerforum@lists.firesprinkler.org
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org


Re: Listed sprinkler guard for horizontal or vertical spray sidewalls

2020-06-24 Thread Mark Phillips via Sprinklerforum
Gotta love all the great people here!

Sent from my mobile device
Please excuse spelling, grammar, and auto correction.

Mark Phillips
Branch Manager
Fire Sprinkler Design, Install, Inspections
Service, Backflows, Fire Alarm Inspections

832-101 Purser Drive
Raleigh NC 27603
Phone: 919-779-4010
Fax : 919-779-4014
Cell : 919-268-7587
Email : philli...@pyebarkerfire.com
Web : www.pyebarkerfire.com


From: Sprinklerforum  on behalf 
of Steve Leyton via Sprinklerforum 
Sent: Wednesday, June 24, 2020 6:03:28 PM
To: sprinklerforum@lists.firesprinkler.org 

Cc: Steve Leyton ; Dennis Wilson 

Subject: RE: Listed sprinkler guard for horizontal or vertical spray sidewalls


[EXTERNAL]

Thank you – a direct HIT!



SL



From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On 
Behalf Of Dennis Wilson via Sprinklerforum
Sent: Wednesday, June 24, 2020 2:27 PM
To: sprinklerforum@lists.firesprinkler.org
Cc: Dennis Wilson 
Subject: RE: Listed sprinkler guard for horizontal or vertical spray sidewalls



Reliable F1FR-56



From: Sprinklerforum 
mailto:sprinklerforum-boun...@lists.firesprinkler.org>>
 On Behalf Of Steve Leyton via Sprinklerforum
Sent: Wednesday, June 24, 2020 4:21 PM
To: 
sprinklerforum@lists.firesprinkler.org
Cc: Steve Leyton mailto:st...@protectiondesign.com>>
Subject: Listed sprinkler guard for horizontal or vertical spray sidewalls



Does anyone know if any manufacturers have a listed guard for standard sidewall 
sprinklers?   We specified Viking on a project where the sprinklers are 
installed on the piping, running alongside beams in an open area of a tilt-up 
building that is being repurposed as a charter school, so Light Hazard 
occupancy class.   The client has requested that these particular sprinklers be 
protected from potential damage, but they are already installed so our first 
choice is to find a solution for horizontal sidewalls.   2nd choice is to roll 
the piping and install vertical sidewalls (I think we should have designed it 
that way in the first place in hindsight), so if no guards are available, at 
least the piping will protect the sprinklers.   Any of the manufacturers have a 
listed solution for horizontal or vertical?





[cid:image001.jpg@01D64A38.9D731FC0]




___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org


RE: Listed sprinkler guard for horizontal or vertical spray sidewalls

2020-06-24 Thread Steve Leyton via Sprinklerforum
Thank you - a direct HIT!

SL

From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On 
Behalf Of Dennis Wilson via Sprinklerforum
Sent: Wednesday, June 24, 2020 2:27 PM
To: sprinklerforum@lists.firesprinkler.org
Cc: Dennis Wilson 
Subject: RE: Listed sprinkler guard for horizontal or vertical spray sidewalls

Reliable F1FR-56

From: Sprinklerforum 
mailto:sprinklerforum-boun...@lists.firesprinkler.org>>
 On Behalf Of Steve Leyton via Sprinklerforum
Sent: Wednesday, June 24, 2020 4:21 PM
To: 
sprinklerforum@lists.firesprinkler.org
Cc: Steve Leyton mailto:st...@protectiondesign.com>>
Subject: Listed sprinkler guard for horizontal or vertical spray sidewalls

Does anyone know if any manufacturers have a listed guard for standard sidewall 
sprinklers?   We specified Viking on a project where the sprinklers are 
installed on the piping, running alongside beams in an open area of a tilt-up 
building that is being repurposed as a charter school, so Light Hazard 
occupancy class.   The client has requested that these particular sprinklers be 
protected from potential damage, but they are already installed so our first 
choice is to find a solution for horizontal sidewalls.   2nd choice is to roll 
the piping and install vertical sidewalls (I think we should have designed it 
that way in the first place in hindsight), so if no guards are available, at 
least the piping will protect the sprinklers.   Any of the manufacturers have a 
listed solution for horizontal or vertical?


[cid:image001.jpg@01D64A38.9D731FC0]


___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org


RE: Listed sprinkler guard for horizontal or vertical spray sidewalls

2020-06-24 Thread Dennis Wilson via Sprinklerforum
Reliable F1FR-56

From: Sprinklerforum  On Behalf 
Of Steve Leyton via Sprinklerforum
Sent: Wednesday, June 24, 2020 4:21 PM
To: sprinklerforum@lists.firesprinkler.org
Cc: Steve Leyton 
Subject: Listed sprinkler guard for horizontal or vertical spray sidewalls

Does anyone know if any manufacturers have a listed guard for standard sidewall 
sprinklers?   We specified Viking on a project where the sprinklers are 
installed on the piping, running alongside beams in an open area of a tilt-up 
building that is being repurposed as a charter school, so Light Hazard 
occupancy class.   The client has requested that these particular sprinklers be 
protected from potential damage, but they are already installed so our first 
choice is to find a solution for horizontal sidewalls.   2nd choice is to roll 
the piping and install vertical sidewalls (I think we should have designed it 
that way in the first place in hindsight), so if no guards are available, at 
least the piping will protect the sprinklers.   Any of the manufacturers have a 
listed solution for horizontal or vertical?


[cid:image001.jpg@01D64A44.4E9F42A0]


___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org


Listed sprinkler guard for horizontal or vertical spray sidewalls

2020-06-24 Thread Steve Leyton via Sprinklerforum
Does anyone know if any manufacturers have a listed guard for standard sidewall 
sprinklers?   We specified Viking on a project where the sprinklers are 
installed on the piping, running alongside beams in an open area of a tilt-up 
building that is being repurposed as a charter school, so Light Hazard 
occupancy class.   The client has requested that these particular sprinklers be 
protected from potential damage, but they are already installed so our first 
choice is to find a solution for horizontal sidewalls.   2nd choice is to roll 
the piping and install vertical sidewalls (I think we should have designed it 
that way in the first place in hindsight), so if no guards are available, at 
least the piping will protect the sprinklers.   Any of the manufacturers have a 
listed solution for horizontal or vertical?