RE: FDC & Pump

2018-01-31 Thread Jason Norton
Last time I looked the FDC was not allowed on the suction side.  That 
requirement was in NFPA 13 under the FDC location section.


Jason Norton, PE – RLH Fire Protection
Direct: (661) 410-1334, Mobile: (661) 979-6301, Fax: (661) 322-6816
Mailing Address: PO Box 42470, Bakersfield, CA 93384

From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On 
Behalf Of Jamie Seidl
Sent: Wednesday, January 31, 2018 1:30 PM
To: sprinklerforum@lists.firesprinkler.org
Subject: FDC & Pump

I have always installed FDC's on the discharge side of fire pumps.  Looking 
through 2013 NFPA 20, I don't see anything precluding the instillation on the 
supply side.  Is the FDC allowed to be installed on the supply?
I have a contractor that has installed the FDC on the supply run-in, instead of 
stubing up a secondary line from the remote FDC.
Thanks,
Jamie
___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org


Storage Containers

2008-02-12 Thread Jason Norton
This is a first for me..
 
A storage warehouse where the storage is 40'x10'x5' high metal
containers are stacked three high. Inside the containers is anything
from Class I to Class IV commodity. I can't seem to located any guidance
within code relating to this storage configuration. Is there any code
guidance for this type of storage method? FM testing, maybe?
 
Thanks for you input.
 
Jason Norton
RLH Fire Protection
___
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)


RE: Cow barns

2008-01-11 Thread Jason Norton
Methane Gas?
It is Friday!

Jason 

-Original Message-
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of G. Tim
Stone
Sent: Friday, January 11, 2008 2:06 PM
To: sprinklerforum@firesprinkler.org
Subject: Cow barns

I have been asked to design a sprinkler system for brand new Cow Barn
with Hay Storage on the upper level. It is a wood structure (Post and
Beam) with a 9:12 pitch roof.

 

Any ideas about Hazard Occupancy or design criteria that might be
available?


 

NFPA document #150 states to follow NFPA 13 for design and installation.
Not much help there!?

 

Would coverage in accordance with Extra Hazard Group 1 be enough along
with a 120 min water supply?

Would .3 GPM over 2500 SF +30% for dry system +30% for sloped roof be
adequate?

 

Has any one designed for Hay Storage?

 

G. Tim Stone

 

G. Tim Stone Consulting, LLC 

NICET Level III Engineering Technician

Fire Protection Sprinkler Design

and Consulting Services

 

117 Old Stage Rd. - Essex Jct., VT. 05452

TEL: (802) 434-2968  Fax: (802) 434-4343

[EMAIL PROTECTED]

 

___
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)


RE: Riser or Riser Nipple Revisited

2008-01-08 Thread Jason Norton
I think Roland it the nail on the head with excessively literal mind.
There is no way NFPA can come up with a code that tells you exactly what
to do in every situation. 

DSA is quickly becoming the new OSHPD. Just double your bid next time
and you can afford to do what the excessively literal mind wants. Of
course that is not the best solution, education is.

Jason 

-Original Message-
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Ed Cyr
Sent: Tuesday, January 08, 2008 8:58 AM
To: sprinklerforum@firesprinkler.org
Subject: RE: Riser or Riser Nipple Revisited

Thanks for the feed back.

I'd like to pursue this thread further.

When running a branch line with offsets for duct work or any other
obstruction, do you 4 way brace both sides of the vertical offset or
just the riser side in the direction of water flow?

Is there a point to when to much bracing can be detrimental? 

Wouldn't line restraint in lieu of seismic bracing prove to be adequate
for all portion of the branch line including the riser nipple? Also
finding adequate structure to brace to can also become a problem.

Utilizing a 4 way brace on a 1 1/4 x 06 RN seems like over kill.

Do you subtract lateral load factors from main braces for the added
bracing of the branch line?

Thanks,
Ed Cyr




-Original Message-
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Jason
Norton
Sent: Monday, January 07, 2008 3:33 PM
To: sprinklerforum@firesprinkler.org
Subject: RE: Riser or Riser Nipple?

DSA has also been trying to require all drops over 4 ft. to be
restrained. Seems they think a drop is no different than a sprig. Go
figure.
Jason

-Original Message-
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Roland
Huggins
Sent: Monday, January 07, 2008 3:07 PM
To: sprinklerforum@firesprinkler.org
Subject: Re: Riser or Riser Nipple?

Sprigs are a separate category independent from risers.  That alone
would not convince many folks  that have an excessively literal mind.
Fortunately, we can then ask, if a 4-way brace is required why would 13
state:  Sprigs greater than 4 ft shall be restrained?

This issue come to our attention when looking at riser nipples.   
That's why we now have the 3 ft allowance.  Beyond that, if it's feeding
more than one sprinkler, I think you have to treat it like any other
riser.

Roland

On Jan 7, 2008, at 2:36 PM, Ed Cyr wrote:

 Forum,



 In the past I posted a thread about an AHJ requiring that riser 
 nipples regardless of length be 4- way braced at the top. NFPA 13 
 defines a riser as any vertical pipe.

 Recently, the Dept of State Architects (DSA) in California has brought

 this issue up again.



 Riser nipples of any length with or without flexible couplings are on 
 their radar.



 Question:

 1.Is a riser nipple a riser requiring a 4 way brace, or a branch
line
 component requiring restraint only?
 2.Does every change of elevation (vertically) on a branch line
also
 require a 4 way brace?



 Comments anyone?



 Thanks,

 Ed Cyr



 Alpha Fire Sprinkler Corp.

 San Luis Obispo, CA



 ___
 Sprinklerforum mailing list
 Sprinklerforum@firesprinkler.org
 http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

 To Unsubscribe, send an email to:Sprinklerforum- 
 [EMAIL PROTECTED] (Put the word unsubscribe in the subject
 field)


___
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email
to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)
___
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email
to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

___
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email
to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)
___
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)


RE: Riser or Riser Nipple?

2008-01-07 Thread Jason Norton
DSA has also been trying to require all drops over 4 ft. to be
restrained. Seems they think a drop is no different than a sprig. Go
figure.
Jason

-Original Message-
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Roland
Huggins
Sent: Monday, January 07, 2008 3:07 PM
To: sprinklerforum@firesprinkler.org
Subject: Re: Riser or Riser Nipple?

Sprigs are a separate category independent from risers.  That alone
would not convince many folks  that have an excessively literal mind.
Fortunately, we can then ask, if a 4-way brace is required why would 13
state:  Sprigs greater than 4 ft shall be restrained?

This issue come to our attention when looking at riser nipples.   
That's why we now have the 3 ft allowance.  Beyond that, if it's feeding
more than one sprinkler, I think you have to treat it like any other
riser.

Roland

On Jan 7, 2008, at 2:36 PM, Ed Cyr wrote:

 Forum,



 In the past I posted a thread about an AHJ requiring that riser 
 nipples regardless of length be 4- way braced at the top. NFPA 13 
 defines a riser as any vertical pipe.

 Recently, the Dept of State Architects (DSA) in California has brought

 this issue up again.



 Riser nipples of any length with or without flexible couplings are on 
 their radar.



 Question:

 1.Is a riser nipple a riser requiring a 4 way brace, or a branch
line
 component requiring restraint only?
 2.Does every change of elevation (vertically) on a branch line
also
 require a 4 way brace?



 Comments anyone?



 Thanks,

 Ed Cyr



 Alpha Fire Sprinkler Corp.

 San Luis Obispo, CA



 ___
 Sprinklerforum mailing list
 Sprinklerforum@firesprinkler.org
 http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

 To Unsubscribe, send an email to:Sprinklerforum- 
 [EMAIL PROTECTED] (Put the word unsubscribe in the subject 
 field)


___
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email
to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)
___
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)


RE: Room Design

2007-12-21 Thread Jason Norton
While we are on this topic...We have a small debate in our office regarding the 
density/area method.  Some say to ignore the walls completely through the 
entire calculation process, just like the example that NFPA 13 describes (which 
works great for a the typical warehouse with equal sprinkler spacing). Others 
say ignore the walls with regard to the general location of the remote area 
(1.2 rectangle) and then use the walls to determine the actual square footage 
of the remote area and to determine the actual gpm required from each sprinkler 
within the remote area. What do you all say? 

Jason

-Original Message-
From: [EMAIL PROTECTED] [mailto:[EMAIL PROTECTED] On Behalf Of Mark Sornsin
Sent: Friday, December 21, 2007 8:35 AM
To: sprinklerforum@firesprinkler.org
Subject: RE: Room Design

I can't see a good reason for NFPA to nix the room design method - I've seen 
enough locations where the self-closing doors actually remain closed. But I 
can't see a contractor willingly avoid the room design either - not without 
potentially losing more work to the other guy.

A classic example of why NFPA 13 is a minimum standard; and why (many times) 
there should be a third party taking responsibility for the design. Say, like 
an engineer of record for instance - one that knows what's going on, that is.

Mark 
 

-Original Message-
From: [EMAIL PROTECTED] [mailto:[EMAIL PROTECTED] On Behalf Of å... 
Sent: Friday, December 21, 2007 9:53 AM
To: sprinklerforum@firesprinkler.org
Subject: Room Design

propped open doors?
propped open self-closing doors?
that IS reality.

that is why the Room Design method
  has to wake up and smell the coffee.
not that the Room Design method is bad in intention.
  one, two,  three sprinklers kabosh most LH/OH fires.
just that there are some bad assumptions
  to the Room Design method.
  Like doors being closed.


scot deal
excelsior fire
___
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field) 
___
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)
___
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)


RE: Room Design

2007-12-21 Thread Jason Norton
Let me explain a little further. It seems logical to locate the remote area 
(1.2 rectangle) without respect to the walls. Then fine tune the square footage 
of the remote area at the perimeter of that rectangle by taking the edge of the 
remote area to the nearest wall that gives you at least the 1.2 dimension of 
the rectangle. Imagine a typical office building without self closing doors. By 
a literal interpretation of code using the density/area method you would 
completely ignore the walls then perform the calcs as described in NFPA. Which 
would work fine if all of the sprinklers where centered in the room. One 
sprinkler may be 10'-0 from the adjacent sprinkler when ignoring the wall. And 
the same sprinkler 7'-6 off the wall when not ignoring the wall. Assume the 
spacing between this sprinkler and those in the other direction is 14'. Also, 
assume this is not a small room. Ignoring the walls completely then the 
sprinkler gpm required is (10' x 14')0.10 = 14 gpm or (7 psi). Not ignoring the 
walls then the sprinkler gpm would be [(7.5' x 2)x14']0.10 = 21.0 gpm. If you 
use the 21.0 gpm as the sprinkler demand then logic follows that this same area 
to the wall can also be included as being part of the remote area inorder to 
satisfy the minimum area size. In essence you ignore the wall to get started 
only, then use the walls for the remainder of the calculation process. Does 
that help?

Jason 



 

-Original Message-
From: [EMAIL PROTECTED] [mailto:[EMAIL PROTECTED] On Behalf Of Paul Pinigis
Sent: Friday, December 21, 2007 1:29 PM
To: sprinklerforum@firesprinkler.org
Subject: RE: Room Design

I am not sure if I understand your question completely, but here is my attempt 
at an answer.  The remote area is the actual physical area and not the 
hydraulic area.  For example, consider a 22'x22' room with four sprinklers on 
14' centers, the actual physical area is 484 sq. feet, but the hydraulic area 
is 784 square feet.  Only 484 sq. ft. is in the design area.  

Have I interpreted your question properly?

Paul J. Pinigis, P.E.
Chief Life Safety Engineer

-Original Message-
From: [EMAIL PROTECTED] [mailto:[EMAIL PROTECTED] On Behalf Of Jason Norton
Sent: Friday, December 21, 2007 1:19 PM
To: sprinklerforum@firesprinkler.org
Subject: RE: Room Design

While we are on this topic...We have a small debate in our office regarding the 
density/area method.  Some say to ignore the walls completely through the 
entire calculation process, just like the example that NFPA 13 describes (which 
works great for a the typical warehouse with equal sprinkler spacing). Others 
say ignore the walls with regard to the general location of the remote area 
(1.2 rectangle) and then use the walls to determine the actual square footage 
of the remote area and to determine the actual gpm required from each sprinkler 
within the remote area. What do you all say? 

Jason

-Original Message-
From: [EMAIL PROTECTED] [mailto:[EMAIL PROTECTED] On Behalf Of Mark Sornsin
Sent: Friday, December 21, 2007 8:35 AM
To: sprinklerforum@firesprinkler.org
Subject: RE: Room Design

I can't see a good reason for NFPA to nix the room design method - I've seen 
enough locations where the self-closing doors actually remain closed. But I 
can't see a contractor willingly avoid the room design either - not without 
potentially losing more work to the other guy.

A classic example of why NFPA 13 is a minimum standard; and why (many times) 
there should be a third party taking responsibility for the design. Say, like 
an engineer of record for instance - one that knows what's going on, that is.

Mark 
 

-Original Message-
From: [EMAIL PROTECTED] [mailto:[EMAIL PROTECTED] On Behalf Of å... 
Sent: Friday, December 21, 2007 9:53 AM
To: sprinklerforum@firesprinkler.org
Subject: Room Design

propped open doors?
propped open self-closing doors?
that IS reality.

that is why the Room Design method
  has to wake up and smell the coffee.
not that the Room Design method is bad in intention.
  one, two,  three sprinklers kabosh most LH/OH fires.
just that there are some bad assumptions
  to the Room Design method.
  Like doors being closed.


scot deal
excelsior fire
___
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field) 
___
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field) 
___
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED

Sound Wall Penetration - Waveguide?

2007-04-10 Thread Jason Norton
I am looking for information on penetrating a sound wall with dielectric
fittings or a waveguide or something of that sort. I have sprinkler
piping passing through a sound wall for a government job, lots of spec's
very little direction, and they want something that will minimize the
sound transfer from one room to the other.  Can someone point me in the
right direction. Any help would be appreciated.
 
Thanks,
 
Jason 