Re: Dust Collection

2020-05-22 Thread Fpdcdesign via Sprinklerforum
  
  

 The N95 masks that everyone is talking about means that is will filter out of 
95% of the 3 microns or larger. The Covid 19 virus is approximately 0.17 
microns but usually travels attached to a fluid droplet, which is larger. The 
thickness of a piece of paper is about 100 microns.   
  

  

  

  
  
  

  
  
>   
> On May 22, 2020 at 7:14 PM,   (mailto:sprinklerforum@lists.firesprinkler.org)>  wrote:
>   
>   
>   On May 22, 2020, at 2:49 PM, Sprinkler Academy - C Bilbo via Sprinklerforum 
>   (mailto:sprinklerforum@lists.firesprinkler.org)>  wrote:
>   
>   
> >
> >   
> > 
> >   
> > . for the record a micron is about the thickness of a sheet of paper.   
> >   
> >   
> >   
>   
> No way. Is not a micron a millionth of a meter? A meter is about 39 inches. 
> That means an inch is slightly more than 25641 microns. I’ve got an unopened 
> ream of printer paper here that is 2 1/8” thick and it consists of 500 
> sheets. Say it is 2” thick to make the numbers easier. So 1” is 250 sheets, 
> not 25641 sheets. A micron being the thickness of a sheet of paper is two 
> orders of magnitude off the mark. You meant to say a micron is about one 
> hundredth the thickness of a sheet of paper. A lot of microns can fit on the 
> head of a pin.
>  ___ Sprinklerforum mailing list 
> Sprinklerforum@lists.firesprinkler.org 
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
>   
  
  
 ___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org


Re: Dust Collection

2020-05-22 Thread AKS-Gmail-IMAP via Sprinklerforum
On May 22, 2020, at 2:49 PM, Sprinkler Academy - C Bilbo via Sprinklerforum 
 wrote:
> 
> . for the record a micron is about the thickness of a sheet of paper.  
> 

No way. Is not a micron a millionth of a meter? A meter is about 39 inches. 
That means an inch is slightly more than 25641 microns. I’ve got an unopened 
ream of printer paper here that is 2 1/8” thick and it consists of 500 sheets. 
Say it is 2” thick to make the numbers easier. So 1” is 250 sheets, not 25641 
sheets. A micron being the thickness of a sheet of paper is two orders of 
magnitude off the mark. You meant to say a micron is about one hundredth the 
thickness of a sheet of paper. A lot of microns can fit on the head of a pin.___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org


Re: Dust Collection

2020-05-22 Thread John Denhardt via Sprinklerforum
Now that’s is just funny but unfortunately is sometimes typical for a technical 
committee. 

Happy Memorial Day weekend. 


John

John August Denhardt, P.E.
Vice-President Engineering and Technical Services
American Fire Sprinkler Association 
301-343-1457

> On May 22, 2020, at 3:49 PM, Sprinkler Academy - C Bilbo via Sprinklerforum 
>  wrote:
> 
> 
> To lighten the mood as we go into Memorial Day weekend
> 
> Sometime around 2007, there was a rather large discussion on the size of a 
> piece of combustible dust.  The standards are not aligned (see 'combustible 
> dust' in the Glossary of Terms).  The argument, I mean debate, of the floor 
> of the worldwide NFPA Technical Meeting was intense.  People got very 
> emotional about how many microns it takes to be an official dust particulate. 
>  From all sides of the room came shouts of "360 microns", "400 microns", "500 
> microns", and what seemed HUGE: "600 microns". for the record a micron is 
> about the thickness of a sheet of paper.  
> 
> The debate went for what seemed like hours! (it was about 60 minutes) And the 
> vote failed to change anything
> 
> I could listen to hours and hours of fire sprinkler debate, but I was dyin' 
> that day!!
> 
> 
> 
> 
> 
> 
> It should be recognized that the above is my opinion as a member of the NFPA, 
> and has not been processed as a formal interpretation in accordance with the 
> NFPA Regulations Governing Committee Projects and should therefore not be 
> considered, nor relied upon, as the official position of the the NFPA, nor 
> any of their technical committees. 
> 
> Sincerely,
> 
> 
> Cecil Bilbo, president 
> Academy of Fire Sprinkler Technology
> Champaign, IL
> 217.607.0325
> www.sprinkleracademy.com
> ce...@sprinkleracademy.com
> ??
> OUR STUDENTS SAVE LIVES!!
> 
> 
> From: Sprinklerforum  on 
> behalf of Ron Greenman via Sprinklerforum 
> 
> Sent: Friday, May 22, 2020 12:36 PM
> To: sprinklerforum@lists.firesprinkler.org 
> 
> Cc: Ron Greenman 
> Subject: Dust Collection
>  
> Does anyone know the NFPA references for dust ducting and collection for 
> compressed paper laminate production? I am home (of course) and my books are 
> 75 miles away. Thanks.
> 
> 
> Ron Greenman
> 
> rongreen...@gmail.com
> 
> 253.576.9700
> 
> The Universe is monstrously indifferent to the presence of man. -Werner 
> Herzog, screenwriter, film director, author, actor and opera director (1942-)
> ___
> Sprinklerforum mailing list
> Sprinklerforum@lists.firesprinkler.org
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org


Re: Dust Collection

2020-05-22 Thread Sprinkler Academy - C Bilbo via Sprinklerforum
To lighten the mood as we go into Memorial Day weekend

Sometime around 2007, there was a rather large discussion on the size of a 
piece of combustible dust.  The standards are not aligned (see 'combustible 
dust' in the Glossary of Terms).  The argument, I mean debate, of the floor of 
the worldwide NFPA Technical Meeting was intense.  People got very emotional 
about how many microns it takes to be an official dust particulate.  From all 
sides of the room came shouts of "360 microns", "400 microns", "500 microns", 
and what seemed HUGE: "600 microns". for the record a micron is about the 
thickness of a sheet of paper.

The debate went for what seemed like hours! (it was about 60 minutes) And the 
vote failed to change anything

I could listen to hours and hours of fire sprinkler debate, but I was dyin' 
that day!!






It should be recognized that the above is my opinion as a member of the NFPA, 
and has not been processed as a formal interpretation in accordance with the 
NFPA Regulations Governing Committee Projects and should therefore not be 
considered, nor relied upon, as the official position of the the NFPA, nor any 
of their technical committees.

Sincerely,


Cecil Bilbo, president
Academy of Fire Sprinkler Technology
Champaign, IL
217.607.0325
www.sprinkleracademy.com<http://www.sprinkleracademy.com>
ce...@sprinkleracademy.com<mailto:ce...@sprinkleracademy.com>
??
OUR STUDENTS SAVE LIVES!!



From: Sprinklerforum  on behalf 
of Ron Greenman via Sprinklerforum 
Sent: Friday, May 22, 2020 12:36 PM
To: sprinklerforum@lists.firesprinkler.org 

Cc: Ron Greenman 
Subject: Dust Collection

Does anyone know the NFPA references for dust ducting and collection for 
compressed paper laminate production? I am home (of course) and my books are 75 
miles away. Thanks.


Ron Greenman

rongreen...@gmail.com<mailto:rongreen...@gmail.com>

253.576.9700

The Universe is monstrously indifferent to the presence of man. -Werner Herzog, 
screenwriter, film director, author, actor and opera director (1942-)
___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org


RE: Dust Collection

2020-05-22 Thread Reed A. Roisum, SET via Sprinklerforum
These might also be applicable…
NFPA 652: Standard on the Fundamentals of Combustible Dust
NFPA 664: Standard for the Prevention of Fires and Explosions in Wood 
Processing and Woodworking Facilities



Reed A. Roisum, SET | KFI Engineers | Senior Fire Protection Designer | Fargo, 
ND | direct: 701.552.9903 | mobile: 701.388.1352 | 
KFIengineers.com<http://www.kfiengineers.com>
From: Sprinklerforum  On Behalf 
Of Scott Futrell via Sprinklerforum
Sent: Friday, May 22, 2020 12:59 PM
To: sprinklerforum@lists.firesprinkler.org
Cc: Scott Futrell ; Ron Greenman 
Subject: RE: Dust Collection

NFPA 91: Standard for Exhaust Systems for Air Conveying of Vapors, Gases, 
Mists, and Particulate Solids
NFPA 654: Standard for the Prevention of Fire and Dust Explosions from the 
Manufacturing, Processing, and Handling of Combustible Particulate Solids
Does that help?

Scott

Office: (763) 425-1001 x 2
Cell: (612) 759-5556

From: Sprinklerforum 
mailto:sprinklerforum-boun...@lists.firesprinkler.org>>
 On Behalf Of Ron Greenman via Sprinklerforum
Sent: Friday, May 22, 2020 12:37 PM
To: 
sprinklerforum@lists.firesprinkler.org<mailto:sprinklerforum@lists.firesprinkler.org>
Cc: Ron Greenman mailto:rongreen...@gmail.com>>
Subject: Dust Collection

Does anyone know the NFPA references for dust ducting and collection for 
compressed paper laminate production? I am home (of course) and my books are 75 
miles away. Thanks.


Ron Greenman

rongreen...@gmail.com<mailto:rongreen...@gmail.com>

253.576.9700

The Universe is monstrously indifferent to the presence of man. -Werner Herzog, 
screenwriter, film director, author, actor and opera director (1942-)

__
This email originated from an external source and has been scanned by the 
Symantec Email Security.cloud service.
For more information please visit http://www.symanteccloud.com
__

__
This email has been scanned by the Symantec Email Security.cloud service.
For more information please visit http://www.symanteccloud.com
__
___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org


RE: Dust Collection

2020-05-22 Thread Scott Futrell via Sprinklerforum
NFPA 91: Standard for Exhaust Systems for Air Conveying of Vapors, Gases, 
Mists, and Particulate Solids
NFPA 654: Standard for the Prevention of Fire and Dust Explosions from the 
Manufacturing, Processing, and Handling of Combustible Particulate Solids
Does that help?

Scott

Office: (763) 425-1001 x 2
Cell: (612) 759-5556

From: Sprinklerforum  On Behalf 
Of Ron Greenman via Sprinklerforum
Sent: Friday, May 22, 2020 12:37 PM
To: sprinklerforum@lists.firesprinkler.org
Cc: Ron Greenman 
Subject: Dust Collection

Does anyone know the NFPA references for dust ducting and collection for 
compressed paper laminate production? I am home (of course) and my books are 75 
miles away. Thanks.


Ron Greenman

rongreen...@gmail.com<mailto:rongreen...@gmail.com>

253.576.9700

The Universe is monstrously indifferent to the presence of man. -Werner Herzog, 
screenwriter, film director, author, actor and opera director (1942-)
___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org


Dust Collection

2020-05-22 Thread Ron Greenman via Sprinklerforum
Does anyone know the NFPA references for dust ducting and collection for
compressed paper laminate production? I am home (of course) and my books
are 75 miles away. Thanks.


Ron Greenman

rongreen...@gmail.com

253.576.9700

The Universe is monstrously indifferent to the presence of man. -Werner
Herzog, screenwriter, film director, author, actor and opera
director (1942-)
___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org


Dust collection - where/when are sprinklers required

2013-09-19 Thread Steve Leyton
I have looked through the California editions of International Fire Code
and Building Code and cannot find any prescriptives for sprinklers in
dust collection systems in woodworking facilities.   Does anyone know
where the triggers are published, if anywhere?  Is it in NFPA 664?

 

Steve Leyton

PROTECTION DESIGN  CONSULTING

2851 Camino del Rio South, Suite 400

San Diego, CA 92108

-

Ph:  858.751.2930 - ext. 102

Fax:858.751.2933

Cell:  619.972.5696

 

 

 

 

___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org


RE: Dust collection - where/when are sprinklers required

2013-09-19 Thread Steve Leyton
Got it - thanks.

Steve 




-Original Message-
From: sprinklerforum-boun...@lists.firesprinkler.org 
[mailto:sprinklerforum-boun...@lists.firesprinkler.org] On Behalf Of Cahill, 
Christopher
Sent: Thursday, September 19, 2013 9:50 AM
To: sprinklerforum@lists.firesprinkler.org
Subject: RE: Dust collection - where/when are sprinklers required

IFC - 903.2.11.4 Ducts conveying hazardous exhausts.

IMC - 510.7 Suppression required.
Ducts shall be protected with an approved automatic fire suppression system 
installed in accordance with the International Building Code.

[F] 510.2.1 Lumber yards and woodworking facilities.
Equipment or machinery located inside buildings at lumber yards and woodworking 
facilities which generates or emits combustible dust shall be provided with an 
approved dust-collection and exhaust system installed in conformance with this 
section and the International Fire Code. Equipment and systems that are used to 
collect, process or convey combustible dusts shall be provided with an approved 
explosion-control system.

There are several interpretations out there of what to actually do - sprinklers 
(IMC 510.7), sprinkler and explosion venting(IMC 510.7 and 510.2.1), spark 
suppression systems (IMC 510.2.1)

Chris Cahill, PE*
Senior Fire Protection Engineer
Burns  McDonnell
8201 Norman Center Drive
Bloomington, MN 55437
Phone:  952.656.3652
Fax:  952.229.2923
ccah...@burnsmcd.com
www.burnsmcd.com

Proud to be one of FORTUNE's 100 Best Companies to Work For *Registered in: MN





-Original Message-
From: sprinklerforum-boun...@lists.firesprinkler.org 
[mailto:sprinklerforum-boun...@lists.firesprinkler.org] On Behalf Of Steve 
Leyton
Sent: Thursday, September 19, 2013 11:33 AM
To: sprinklerfo...@firesprinkler.org
Subject: Dust collection - where/when are sprinklers required

I have looked through the California editions of International Fire Code and 
Building Code and cannot find any prescriptives for sprinklers in
dust collection systems in woodworking facilities.   Does anyone know
where the triggers are published, if anywhere?  Is it in NFPA 664?

 

Steve Leyton

PROTECTION DESIGN  CONSULTING

2851 Camino del Rio South, Suite 400

San Diego, CA 92108

-

Ph:  858.751.2930 - ext. 102

Fax:858.751.2933

Cell:  619.972.5696

 

 

 

 

___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org


RE: Dust collection - where/when are sprinklers required

2013-09-19 Thread Taylor, Galen
Steve,

Section 506.6 of the Mechanical Code requires sprinklers inside ducts exceeding 
10-inches that convey flammable vapors or fumes, but I cannot find a similar 
mandate for ducts conveying sawdust in either NFPA 664, CBC or CFC.

Interestingly, NFPA 664 speaks about duct sprinklers free of debris where 
provided, but there is no mandate to actually provide duct protection. I used 
to work for a large aerospace firm and I don't recall any of the ducts having 
sprinklers, except those that conveyed flammable vapors. 

Galen Taylor
County of Los Angeles Fire Department
Fire Prevention Engineering
323-890-4339
galen.tay...@fire.lacounty.gov


-Original Message-
From: sprinklerforum-boun...@lists.firesprinkler.org 
[mailto:sprinklerforum-boun...@lists.firesprinkler.org] On Behalf Of Steve 
Leyton
Sent: Thursday, September 19, 2013 9:33 AM
To: sprinklerfo...@firesprinkler.org
Subject: Dust collection - where/when are sprinklers required

I have looked through the California editions of International Fire Code and 
Building Code and cannot find any prescriptives for sprinklers in
dust collection systems in woodworking facilities.   Does anyone know
where the triggers are published, if anywhere?  Is it in NFPA 664?

 

Steve Leyton

PROTECTION DESIGN  CONSULTING

2851 Camino del Rio South, Suite 400

San Diego, CA 92108

-

Ph:  858.751.2930 - ext. 102

Fax:858.751.2933

Cell:  619.972.5696

 

 

 

 

___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org


RE: Dust collection - where/when are sprinklers required

2013-09-19 Thread Steve Leyton
Thanks Galen - this exactly the same info I arrived at through my own
process this morning. It's a DSA project where and existing dust
collection system was moved from an old non sprinklered wood shop building
into an interim housing environment. It originally had a couple sprinklers
in it, piped from domestic water as the shell building was not protected.
Now they want to move this same system back into the new permanent
disability, which is fully sprinklered. My advice to them is simply to
move it without protection and let someone tell us that sprinklers are
required and cite the appropriate code sections that mandates it. DSA
doen't have and IR for this, so its all purely subjective it seems.

Steve

Taylor, Galen galen.tay...@fire.lacounty.gov wrote:

Steve,

Section 506.6 of the Mechanical Code requires sprinklers inside ducts
exceeding 10-inches that convey flammable vapors or fumes, but I cannot
find a similar mandate for ducts conveying sawdust in either NFPA 664, CBC
or CFC.

Interestingly, NFPA 664 speaks about duct sprinklers free of debris where
provided, but there is no mandate to actually provide duct protection. I
used to work for a large aerospace firm and I don't recall any of the
ducts having sprinklers, except those that conveyed flammable vapors.

Galen Taylor
County of Los Angeles Fire Department
Fire Prevention Engineering
323-890-4339
galen.tay...@fire.lacounty.gov


-Original Message-
From: sprinklerforum-boun...@lists.firesprinkler.org
[mailto:sprinklerforum-boun...@lists.firesprinkler.org] On Behalf Of Steve
Leyton
Sent: Thursday, September 19, 2013 9:33 AM
To: sprinklerfo...@firesprinkler.org
Subject: Dust collection - where/when are sprinklers required

I have looked through the California editions of International Fire Code
and Building Code and cannot find any prescriptives for sprinklers in
dust collection systems in woodworking facilities.   Does anyone know
where the triggers are published, if anywhere?  Is it in NFPA 664?



Steve Leyton

PROTECTION DESIGN  CONSULTING

2851 Camino del Rio South, Suite 400

San Diego, CA 92108

-

Ph:  858.751.2930 - ext. 102

Fax:858.751.2933

Cell:  619.972.5696









___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.o
rg
___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.o
rg

___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org


RE: Dust collection - where/when are sprinklers required

2013-09-19 Thread Cahill, Christopher
IFC - 903.2.11.4 Ducts conveying hazardous exhausts.

IMC - 510.7 Suppression required.
Ducts shall be protected with an approved automatic fire suppression system 
installed in accordance with the International Building Code.

[F] 510.2.1 Lumber yards and woodworking facilities.
Equipment or machinery located inside buildings at lumber yards and woodworking 
facilities which generates or emits combustible dust shall be provided with an 
approved dust-collection and exhaust system installed in conformance with this 
section and the International Fire Code. Equipment and systems that are used to 
collect, process or convey combustible dusts shall be provided with an approved 
explosion-control system.

There are several interpretations out there of what to actually do - sprinklers 
(IMC 510.7), sprinkler and explosion venting(IMC 510.7 and 510.2.1), spark 
suppression systems (IMC 510.2.1)

Chris Cahill, PE*
Senior Fire Protection Engineer 
Burns  McDonnell
8201 Norman Center Drive
Bloomington, MN 55437
Phone:  952.656.3652
Fax:  952.229.2923
ccah...@burnsmcd.com
www.burnsmcd.com

Proud to be one of FORTUNE's 100 Best Companies to Work For
*Registered in: MN





-Original Message-
From: sprinklerforum-boun...@lists.firesprinkler.org 
[mailto:sprinklerforum-boun...@lists.firesprinkler.org] On Behalf Of Steve 
Leyton
Sent: Thursday, September 19, 2013 11:33 AM
To: sprinklerfo...@firesprinkler.org
Subject: Dust collection - where/when are sprinklers required

I have looked through the California editions of International Fire Code and 
Building Code and cannot find any prescriptives for sprinklers in
dust collection systems in woodworking facilities.   Does anyone know
where the triggers are published, if anywhere?  Is it in NFPA 664?

 

Steve Leyton

PROTECTION DESIGN  CONSULTING

2851 Camino del Rio South, Suite 400

San Diego, CA 92108

-

Ph:  858.751.2930 - ext. 102

Fax:858.751.2933

Cell:  619.972.5696

 

 

 

 

___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org


Re: Dust collection - where/when are sprinklers required

2013-09-19 Thread Ron Greenman
A how to, not a when, but:

NFPA 68: Standard on Explosion Protection by Deflagration Venting.


On Thu, Sep 19, 2013 at 11:54 AM, Steve Leyton
st...@protectiondesign.comwrote:

 Thanks Galen - this exactly the same info I arrived at through my own
 process this morning. It's a DSA project where and existing dust
 collection system was moved from an old non sprinklered wood shop building
 into an interim housing environment. It originally had a couple sprinklers
 in it, piped from domestic water as the shell building was not protected.
 Now they want to move this same system back into the new permanent
 disability, which is fully sprinklered. My advice to them is simply to
 move it without protection and let someone tell us that sprinklers are
 required and cite the appropriate code sections that mandates it. DSA
 doen't have and IR for this, so its all purely subjective it seems.

 Steve

 Taylor, Galen galen.tay...@fire.lacounty.gov wrote:

 Steve,

 Section 506.6 of the Mechanical Code requires sprinklers inside ducts
 exceeding 10-inches that convey flammable vapors or fumes, but I cannot
 find a similar mandate for ducts conveying sawdust in either NFPA 664, CBC
 or CFC.

 Interestingly, NFPA 664 speaks about duct sprinklers free of debris where
 provided, but there is no mandate to actually provide duct protection. I
 used to work for a large aerospace firm and I don't recall any of the
 ducts having sprinklers, except those that conveyed flammable vapors.

 Galen Taylor
 County of Los Angeles Fire Department
 Fire Prevention Engineering
 323-890-4339
 galen.tay...@fire.lacounty.gov


 -Original Message-
 From: sprinklerforum-boun...@lists.firesprinkler.org
 [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On Behalf Of Steve
 Leyton
 Sent: Thursday, September 19, 2013 9:33 AM
 To: sprinklerfo...@firesprinkler.org
 Subject: Dust collection - where/when are sprinklers required

 I have looked through the California editions of International Fire Code
 and Building Code and cannot find any prescriptives for sprinklers in
 dust collection systems in woodworking facilities.   Does anyone know
 where the triggers are published, if anywhere?  Is it in NFPA 664?



 Steve Leyton

 PROTECTION DESIGN  CONSULTING

 2851 Camino del Rio South, Suite 400

 San Diego, CA 92108

 -

 Ph:  858.751.2930 - ext. 102

 Fax:858.751.2933

 Cell:  619.972.5696









 ___
 Sprinklerforum mailing list
 Sprinklerforum@lists.firesprinkler.org
 http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.o
 rg
 ___
 Sprinklerforum mailing list
 Sprinklerforum@lists.firesprinkler.org
 http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.o
 rg

 ___
 Sprinklerforum mailing list
 Sprinklerforum@lists.firesprinkler.org

 http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org




-- 
Ron Greenman
Instructor
Fire Protection Engineering Technology
Bates Technical College
1101 So. Yakima Ave.
Tacoma, WA 98405

rgreen...@bates.ctc.edu

http://www.bates.ctc.edu/fireprotection/

253.680.7346
253.576.9700 (cell)

Member:
ASEE, SFPE, ASCET, NFPA, AFSA, NFSA, AFAA, NIBS, WSAFM, WFC, WFSC

They are happy men whose natures sort with their vocations. -Francis Bacon,
essayist, philosopher, and statesman (1561-1626)
___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org