Re: K for a 2½" Hose Valve
K=113.85 In the same way that a nominal 1/2" sprinkler with a Coefficient of Discharge of .75 has a K=5.6, a nominal 2.5" hose valve with a Coefficient of Discharge of .61 has a K=113.85. Brad On Feb 17, 2017 8:28 AM, "Vince Sabolik" <vi...@wtfp.net> wrote: > Good morning, everyone... > > Does anybody have a decent K Factor for a 2½" hose valve? > > Thanks! Vince > > 11351 Pearl Road / Suite 101 > Strongsville, Ohio 44136 > Phone 440 238-4800 <(440)%20238-4800> Fax 440 238-4876 <(440)%20238-4876> Cell > 440 724-7601 <(440)%20724-7601> > > > * Vince Sabolik * > > ___ > Sprinklerforum mailing list > Sprinklerforum@lists.firesprinkler.org > http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler. > org > > ___ Sprinklerforum mailing list Sprinklerforum@lists.firesprinkler.org http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
Re: K for a 2½" Hose Valve
I often get too excited and blurt things out and reply to myself several times with corrections and clarifications, like now: 1) I have done a lot of standpipe calcs and I use K=Q/SQRT (P) just like everyone has said here, and I use equivalent length for the valve=31 ft. 2) What I mean by K Value should be more useful than K Factor is, for instance, at 250 GPM eql.=23.65 ft and at 500 GPM it is 26.24 ft. Just another example of the excellence of the NFPA Standards as standards. And if you are pitoting a 2.5" hose valve to estimate the GPM as if it were a hydrant butt, if my concept of K Value is correct, C=.61 should be 'decent'. 3) Coefficient of Discharge = actual measured / ideal, and that is always less than 1. Brad On Feb 17, 2017 5:19 PM, "Brad Casterline" <bcasterli...@gmail.com> wrote: > Shazbot! > 2g=64.4 > (62.4 is the weight in pounds of a cubic foot of water). > On Feb 17, 2017 5:05 PM, "Brad Casterline" <bcasterli...@gmail.com> wrote: > >> Vince, >> >> I think you are looking for something with a little more meat on its >> bones than rearranging Q=K*SQRT(P). A few years ago you mentioned K Value. >> Counselor Greenman presented this evidence: >> >> http://www.metropumps.com/ResourcesFrictionLossData.pdf >> >> The first item is Angle Valve, which might be close enough to Hose Valve, >> but the problem is the second item is also Angle Valve with a different >> value and I saw no clarification of what's what with that. But when Steve L >> testified to 3-5 psi loss at 250 gpm I rearanged and I think the second one >> is correct; K Value=2.7- - - >> >> Using the 5 psi loss, hf=11.55 ft. >> I converted 250 gpm to .557 ft^3/sec and 2.5" nominal to .034 ft^2 and >> dividing the first by the second got v= 16.38 ft/sec, squared that, divided >> by 2g (62.4), and then divided 11.55 by that for K Value = 2.77. >> This should be more useful for you because friction head is directly >> proportional to the square of the velocity, and K Value is a counter part >> of Coefficient of Discharge in that C of D = the ideal world based on >> nominal / the reality of the measurement. >> >> still yours after forty years, your first grasshopper, >> >> Brad >> On Feb 17, 2017 8:28 AM, "Vince Sabolik" <vi...@wtfp.net> wrote: >> >>> Good morning, everyone... >>> >>> Does anybody have a decent K Factor for a 2½" hose valve? >>> >>> Thanks! Vince >>> >>> 11351 Pearl Road / Suite 101 >>> Strongsville, Ohio 44136 >>> Phone 440 238-4800 <(440)%20238-4800> Fax 440 238-4876 >>> <(440)%20238-4876> Cell 440 724-7601 <(440)%20724-7601> >>> >>> >>> * Vince Sabolik * >>> >>> ___ >>> Sprinklerforum mailing list >>> Sprinklerforum@lists.firesprinkler.org >>> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-f >>> iresprinkler.org >>> >>> ___ Sprinklerforum mailing list Sprinklerforum@lists.firesprinkler.org http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
Re: K for a 2½" Hose Valve
Shazbot! 2g=64.4 (62.4 is the weight in pounds of a cubic foot of water). On Feb 17, 2017 5:05 PM, "Brad Casterline" <bcasterli...@gmail.com> wrote: > Vince, > > I think you are looking for something with a little more meat on its bones > than rearranging Q=K*SQRT(P). A few years ago you mentioned K Value. > Counselor Greenman presented this evidence: > > http://www.metropumps.com/ResourcesFrictionLossData.pdf > > The first item is Angle Valve, which might be close enough to Hose Valve, > but the problem is the second item is also Angle Valve with a different > value and I saw no clarification of what's what with that. But when Steve L > testified to 3-5 psi loss at 250 gpm I rearanged and I think the second one > is correct; K Value=2.7- - - > > Using the 5 psi loss, hf=11.55 ft. > I converted 250 gpm to .557 ft^3/sec and 2.5" nominal to .034 ft^2 and > dividing the first by the second got v= 16.38 ft/sec, squared that, divided > by 2g (62.4), and then divided 11.55 by that for K Value = 2.77. > This should be more useful for you because friction head is directly > proportional to the square of the velocity, and K Value is a counter part > of Coefficient of Discharge in that C of D = the ideal world based on > nominal / the reality of the measurement. > > still yours after forty years, your first grasshopper, > > Brad > On Feb 17, 2017 8:28 AM, "Vince Sabolik" <vi...@wtfp.net> wrote: > >> Good morning, everyone... >> >> Does anybody have a decent K Factor for a 2½" hose valve? >> >> Thanks! Vince >> >> 11351 Pearl Road / Suite 101 >> Strongsville, Ohio 44136 >> Phone 440 238-4800 <(440)%20238-4800> Fax 440 238-4876 <(440)%20238-4876> >> Cell >> 440 724-7601 <(440)%20724-7601> >> >> >> * Vince Sabolik * >> >> ___ >> Sprinklerforum mailing list >> Sprinklerforum@lists.firesprinkler.org >> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum- >> firesprinkler.org >> >> ___ Sprinklerforum mailing list Sprinklerforum@lists.firesprinkler.org http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
Re: K for a 2½" Hose Valve
Vince, I think you are looking for something with a little more meat on its bones than rearranging Q=K*SQRT(P). A few years ago you mentioned K Value. Counselor Greenman presented this evidence: http://www.metropumps.com/ResourcesFrictionLossData.pdf The first item is Angle Valve, which might be close enough to Hose Valve, but the problem is the second item is also Angle Valve with a different value and I saw no clarification of what's what with that. But when Steve L testified to 3-5 psi loss at 250 gpm I rearanged and I think the second one is correct; K Value=2.7- - - Using the 5 psi loss, hf=11.55 ft. I converted 250 gpm to .557 ft^3/sec and 2.5" nominal to .034 ft^2 and dividing the first by the second got v= 16.38 ft/sec, squared that, divided by 2g (62.4), and then divided 11.55 by that for K Value = 2.77. This should be more useful for you because friction head is directly proportional to the square of the velocity, and K Value is a counter part of Coefficient of Discharge in that C of D = the ideal world based on nominal / the reality of the measurement. still yours after forty years, your first grasshopper, Brad On Feb 17, 2017 8:28 AM, "Vince Sabolik" <vi...@wtfp.net> wrote: > Good morning, everyone... > > Does anybody have a decent K Factor for a 2½" hose valve? > > Thanks! Vince > > 11351 Pearl Road / Suite 101 > Strongsville, Ohio 44136 > Phone 440 238-4800 <(440)%20238-4800> Fax 440 238-4876 <(440)%20238-4876> Cell > 440 724-7601 <(440)%20724-7601> > > > * Vince Sabolik * > > ___ > Sprinklerforum mailing list > Sprinklerforum@lists.firesprinkler.org > http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler. > org > > ___ Sprinklerforum mailing list Sprinklerforum@lists.firesprinkler.org http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
RE: K for a 2½" Hose Valve
K of 25 for a 250 flow at 100 and 50 for a 500 flow at 100 have always worked for me in doing a simple standpipe calc to verify 150 at the FDC. That would be on the inlet side of the valve. 2½” angle and globe pattern hose valves have losses of 3-5 psi at 250 gpm, so the discharge side “K” at 100 psi might be as low as 24.4 at 250 gpm. But my point is still, why? SL Dear All 250gpm flow at 100psi for 2-1/2" angle valve, K-factor shall be 25 ( 250/sqrt(100))=25 With warm regards D.RADHAKRISHNAN ___ Sprinklerforum mailing list Sprinklerforum@lists.firesprinkler.org http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
RE: K for a 2½" Hose Valve
That would be on the inlet side of the valve. 2½” angle and globe pattern hose valves have losses of 3-5 psi at 250 gpm, so the discharge side “K” at 100 psi might be as low as 24.4 at 250 gpm. But my point is still, why? SL From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On Behalf Of Drad Duraikkannu Sent: Friday, February 17, 2017 7:23 AM To: sprinklerforum@lists.firesprinkler.org Subject: Re: K for a 2½" Hose Valve Dear All 250gpm flow at 100psi for 2-1/2" angle valve, K-factor shall be 25 ( 250/sqrt(100))=25 With warm regards D.RADHAKRISHNAN Mobile: 00971 55 967 4864<tel:00971%2055%20967%204864> On Fri, Feb 17, 2017 at 7:18 PM, Glen Buelow, Inc. <gwb...@gmail.com<mailto:gwb...@gmail.com>> wrote: Vince, That was not right 24.82 [https://docs.google.com/uc?export=download=0B7SYmRowbxfLWWlIRHA2UmJqaFE=0B7SYmRowbxfLMHpWaGVTRjhPR0NMN3BtUVZrZWNoZlFFZzBzPQ] Glen Buelow Glen W. Buelow, Inc. Fire Protection Design and Consulting Cleveland 330.220.7201 ● Akron 330.665.4439 On Fri, Feb 17, 2017 at 10:17 AM, Glen Buelow, Inc. <gwb...@gmail.com<mailto:gwb...@gmail.com>> wrote: Vince, 6.07 [https://docs.google.com/uc?export=download=0B7SYmRowbxfLWWlIRHA2UmJqaFE=0B7SYmRowbxfLMHpWaGVTRjhPR0NMN3BtUVZrZWNoZlFFZzBzPQ] Glen Buelow Glen W. Buelow, Inc. Fire Protection Design and Consulting Cleveland 330.220.7201 ● Akron 330.665.4439 On Fri, Feb 17, 2017 at 9:52 AM, Shawn Foor <shawn.f...@gmail.com<mailto:shawn.f...@gmail.com>> wrote: Just take your gallons divide by square root of pressure and you can get your k factor that way. On Fri, Feb 17, 2017 at 8:42 AM, Vince Sabolik <vi...@wtfp.net<mailto:vi...@wtfp.net>> wrote: I'm doing this by hand. On 2/17/2017 9:35 AM, Mark Phillips wrote: What program are you using to calc? ___ Sprinklerforum mailing list Sprinklerforum@lists.firesprinkler.org<mailto:Sprinklerforum@lists.firesprinkler.org> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org -- Shawn Foor, SET FOOR DESIGN, LLC 6227 S. 87TH E. AVE TULSA, OK 74133 P:918-237-1400<tel:(918)%20237-1400> ___ Sprinklerforum mailing list Sprinklerforum@lists.firesprinkler.org<mailto:Sprinklerforum@lists.firesprinkler.org> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org ___ Sprinklerforum mailing list Sprinklerforum@lists.firesprinkler.org<mailto:Sprinklerforum@lists.firesprinkler.org> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org ___ Sprinklerforum mailing list Sprinklerforum@lists.firesprinkler.org http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
RE: K for a 2½" Hose Valve
What if the valve is only half-open? Vince - why are you trying to establish a key factor for a device that can have infinitely variable flow rates? Steve Original message From: "Glen Buelow, Inc." <gwb...@gmail.com> Date: 2/17/17 7:19 AM (GMT-08:00) To: sprinklerforum@lists.firesprinkler.org Subject: Re: K for a 2½" Hose Valve Vince, That was not right 24.82 [https://docs.google.com/uc?export=download=0B7SYmRowbxfLWWlIRHA2UmJqaFE=0B7SYmRowbxfLMHpWaGVTRjhPR0NMN3BtUVZrZWNoZlFFZzBzPQ] Glen Buelow Glen W. Buelow, Inc. Fire Protection Design and Consulting Cleveland 330.220.7201 ● Akron 330.665.4439 On Fri, Feb 17, 2017 at 10:17 AM, Glen Buelow, Inc. <gwb...@gmail.com<mailto:gwb...@gmail.com>> wrote: Vince, 6.07 [https://docs.google.com/uc?export=download=0B7SYmRowbxfLWWlIRHA2UmJqaFE=0B7SYmRowbxfLMHpWaGVTRjhPR0NMN3BtUVZrZWNoZlFFZzBzPQ] Glen Buelow Glen W. Buelow, Inc. Fire Protection Design and Consulting Cleveland 330.220.7201 ● Akron 330.665.4439 On Fri, Feb 17, 2017 at 9:52 AM, Shawn Foor <shawn.f...@gmail.com<mailto:shawn.f...@gmail.com>> wrote: Just take your gallons divide by square root of pressure and you can get your k factor that way. On Fri, Feb 17, 2017 at 8:42 AM, Vince Sabolik <vi...@wtfp.net<mailto:vi...@wtfp.net>> wrote: I'm doing this by hand. On 2/17/2017 9:35 AM, Mark Phillips wrote: What program are you using to calc? ___ Sprinklerforum mailing list Sprinklerforum@lists.firesprinkler.org<mailto:Sprinklerforum@lists.firesprinkler.org> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org -- Shawn Foor, SET FOOR DESIGN, LLC 6227 S. 87TH E. AVE TULSA, OK 74133 P:918-237-1400<tel:(918)%20237-1400> ___ Sprinklerforum mailing list Sprinklerforum@lists.firesprinkler.org<mailto:Sprinklerforum@lists.firesprinkler.org> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org ___ Sprinklerforum mailing list Sprinklerforum@lists.firesprinkler.org http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
Re: K for a 2½" Hose Valve
Dear All 250gpm flow at 100psi for 2-1/2" angle valve, K-factor shall be 25 ( 250/sqrt(100))=25 With warm regards *D.RADHAKRISHNAN* Mobile: 00971 55 967 4864On Fri, Feb 17, 2017 at 7:18 PM, Glen Buelow, Inc. wrote: > Vince, > That was not right > 24.82 > > > > *Glen Bue**low* > > *Glen W. Buelow, Inc.* > *Fire Protection Design and ConsultingCleveland 330.220.7201 > <330.220.7201> *●* Akron 330.665.4439 <330.665.4439>* > > On Fri, Feb 17, 2017 at 10:17 AM, Glen Buelow, Inc. > wrote: > >> Vince, >> 6.07 >> >> >> >> *Glen Bue**low* >> >> *Glen W. Buelow, Inc.* >> *Fire Protection Design and ConsultingCleveland 330.220.7201 >> <330.220.7201> *●* Akron 330.665.4439 <330.665.4439>* >> >> On Fri, Feb 17, 2017 at 9:52 AM, Shawn Foor wrote: >> >>> Just take your gallons divide by square root of pressure and you can get >>> your k factor that way. >>> >>> On Fri, Feb 17, 2017 at 8:42 AM, Vince Sabolik wrote: >>> I'm doing this by hand. On 2/17/2017 9:35 AM, Mark Phillips wrote: What program are you using to calc? ___ Sprinklerforum mailing list Sprinklerforum@lists.firesprinkler.org http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-f iresprinkler.org >>> >>> >>> -- >>> Shawn Foor, SET >>> >>> *FOOR DESIGN, LLC* >>> *6227 S. 87TH E. AVE* >>> *TULSA, OK 74133* >>> *P:918-237-1400 <(918)%20237-1400>* >>> >>> ___ >>> Sprinklerforum mailing list >>> Sprinklerforum@lists.firesprinkler.org >>> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-f >>> iresprinkler.org >>> >>> >> > > ___ > Sprinklerforum mailing list > Sprinklerforum@lists.firesprinkler.org > http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler. > org > > ___ Sprinklerforum mailing list Sprinklerforum@lists.firesprinkler.org http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
Re: K for a 2½" Hose Valve
Vince, That was not right 24.82 *Glen Bue**low* *Glen W. Buelow, Inc.* *Fire Protection Design and ConsultingCleveland 330.220.7201 <330.220.7201> *●* Akron 330.665.4439 <330.665.4439>* On Fri, Feb 17, 2017 at 10:17 AM, Glen Buelow, Inc.wrote: > Vince, > 6.07 > > > > *Glen Bue**low* > > *Glen W. Buelow, Inc.* > *Fire Protection Design and ConsultingCleveland 330.220.7201 > <330.220.7201> *●* Akron 330.665.4439 <330.665.4439>* > > On Fri, Feb 17, 2017 at 9:52 AM, Shawn Foor wrote: > >> Just take your gallons divide by square root of pressure and you can get >> your k factor that way. >> >> On Fri, Feb 17, 2017 at 8:42 AM, Vince Sabolik wrote: >> >>> I'm doing this by hand. >>> >>> >>> On 2/17/2017 9:35 AM, Mark Phillips wrote: >>> >>> What program are you using to calc? >>> >>> >>> >>> >>> >>> ___ >>> Sprinklerforum mailing list >>> Sprinklerforum@lists.firesprinkler.org >>> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-f >>> iresprinkler.org >>> >>> >> >> >> -- >> Shawn Foor, SET >> >> *FOOR DESIGN, LLC* >> *6227 S. 87TH E. AVE* >> *TULSA, OK 74133* >> *P:918-237-1400 <(918)%20237-1400>* >> >> ___ >> Sprinklerforum mailing list >> Sprinklerforum@lists.firesprinkler.org >> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum- >> firesprinkler.org >> >> > ___ Sprinklerforum mailing list Sprinklerforum@lists.firesprinkler.org http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
Re: K for a 2½" Hose Valve
Just take your gallons divide by square root of pressure and you can get your k factor that way. On Fri, Feb 17, 2017 at 8:42 AM, Vince Sabolikwrote: > I'm doing this by hand. > > > On 2/17/2017 9:35 AM, Mark Phillips wrote: > > What program are you using to calc? > > > > > > ___ > Sprinklerforum mailing list > Sprinklerforum@lists.firesprinkler.org > http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler. > org > > -- Shawn Foor, SET *FOOR DESIGN, LLC* *6227 S. 87TH E. AVE* *TULSA, OK 74133* *P:918-237-1400* ___ Sprinklerforum mailing list Sprinklerforum@lists.firesprinkler.org http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
Re: K for a 2½" Hose Valve
I'm doing this by hand. On 2/17/2017 9:35 AM, Mark Phillips wrote: What program are you using to calc? ___ Sprinklerforum mailing list Sprinklerforum@lists.firesprinkler.org http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
RE: K for a 2½" Hose Valve
What program are you using to calc? From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On Behalf Of Vince Sabolik Sent: Friday, February 17, 2017 9:28 AM To: sprinklerforum@lists.firesprinkler.org Subject: K for a 2½" Hose Valve Good morning, everyone... Does anybody have a decent K Factor for a 2½" hose valve? Thanks! Vince [cid:image001.jpg@01D28901.30315E00] 11351 Pearl Road / Suite 101 Strongsville, Ohio 44136 Phone 440 238-4800 Fax 440 238-4876 Cell 440 724-7601 Vince Sabolik ___ Sprinklerforum mailing list Sprinklerforum@lists.firesprinkler.org http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
K for a 2½" Hose Valve
Good morning, everyone... Does anybody have a decent K Factor for a 2½" hose valve? Thanks! Vince 11351 Pearl Road / Suite 101 Strongsville, Ohio 44136 Phone 440 238-4800 Fax 440 238-4876Cell 440 724-7601 / Vince Sabolik / ___ Sprinklerforum mailing list Sprinklerforum@lists.firesprinkler.org http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org