Question on old sprinkler heads
Could anybody tell me where and if there is a code that says you have to replace sprinkler heads with new ones once they are removed? ___ Sprinklerforum mailing list Sprinklerforum@lists.firesprinkler.org http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
RE: Question on old sprinkler heads
NFPA 13, 2013 edition 6.2.1.1 When a sprinkler has been removed for any reason, it shall not be reinstalled. This particular text is new, but it's really just meant as a clarification for the existing 6.2.1 which states only new sprinklers shall be installed which I believe has been in the standard for several editions. Mike Morey, CFPS, SET Planner Scheduler/Designer BMWC Constructors, Inc. 1740 W. Michigan St, Indianapolis, IN 46222 O: 317.651.0596 | C: 317.586.8111 mo...@bmwc.com | www.bmwc.com From: sprinklerforum-boun...@lists.firesprinkler.org [sprinklerforum-boun...@lists.firesprinkler.org] on behalf of djj8...@aol.com [djj8...@aol.com] Sent: Thursday, March 13, 2014 2:08 PM To: sprinklerforum@lists.firesprinkler.org Subject: Question on old sprinkler heads Could anybody tell me where and if there is a code that says you have to replace sprinkler heads with new ones once they are removed? ___ Sprinklerforum mailing list Sprinklerforum@lists.firesprinkler.org http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org ___ Sprinklerforum mailing list Sprinklerforum@lists.firesprinkler.org http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
RE: Question on old sprinkler heads
From the 2013 ed. of NFPA 2013 6.2.1.1 When a sprinkler has been removed for any reason, it shall not be reinstalled. BJ Newlin Service Sales Aegis Fire Protection LLC. Whoever is careless with the truth in small matters cannot be trusted with important matters ― Albert Einstein -Original Message- From: sprinklerforum-boun...@lists.firesprinkler.org [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On Behalf Of djj8...@aol.com Sent: Thursday, March 13, 2014 1:09 PM To: sprinklerforum@lists.firesprinkler.org Subject: Question on old sprinkler heads Could anybody tell me where and if there is a code that says you have to replace sprinkler heads with new ones once they are removed? ___ Sprinklerforum mailing list Sprinklerforum@lists.firesprinkler.org http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org ___ Sprinklerforum mailing list Sprinklerforum@lists.firesprinkler.org http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
Re: Question on old sprinkler heads
1-8.1.1 in the 1977 edition. On Thu, Mar 13, 2014 at 11:15 AM, BJ Newlin bjnew...@aegisfirepro.comwrote: From the 2013 ed. of NFPA 2013 6.2.1.1 When a sprinkler has been removed for any reason, it shall not be reinstalled. BJ Newlin Service Sales Aegis Fire Protection LLC. Whoever is careless with the truth in small matters cannot be trusted with important matters -- Albert Einstein -Original Message- From: sprinklerforum-boun...@lists.firesprinkler.org [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On Behalf Of djj8...@aol.com Sent: Thursday, March 13, 2014 1:09 PM To: sprinklerforum@lists.firesprinkler.org Subject: Question on old sprinkler heads Could anybody tell me where and if there is a code that says you have to replace sprinkler heads with new ones once they are removed? ___ Sprinklerforum mailing list Sprinklerforum@lists.firesprinkler.org http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org ___ Sprinklerforum mailing list Sprinklerforum@lists.firesprinkler.org http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org -- Ron Greenman Instructor Fire Protection Engineering Technology Bates Technical College 1101 So. Yakima Ave. Tacoma, WA 98405 rgreen...@bates.ctc.edu http://www.bates.ctc.edu/fireprotection/ 253.680.7346 253.576.9700 (cell) Member: ASEE, SFPE, ASCET, NFPA, AFSA, NFSA, AFAA, NIBS, WSAFM, WFC, WFSC They are happy men whose natures sort with their vocations. -Francis Bacon, essayist, philosopher, and statesman (1561-1626) A problem well stated is a problem half solved. -Charles F. Kettering, inventor and engineer (1876-1958) ___ Sprinklerforum mailing list Sprinklerforum@lists.firesprinkler.org http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
Re: Question on old sprinkler heads
Show off... Sent from my iPhone Jamie Seidl On Mar 13, 2014, at 2:30 PM, rongreenman . rongreen...@gmail.com wrote: 1-8.1.1 in the 1977 edition. On Thu, Mar 13, 2014 at 11:15 AM, BJ Newlin bjnew...@aegisfirepro.comwrote: From the 2013 ed. of NFPA 2013 6.2.1.1 When a sprinkler has been removed for any reason, it shall not be reinstalled. BJ Newlin Service Sales Aegis Fire Protection LLC. Whoever is careless with the truth in small matters cannot be trusted with important matters -- Albert Einstein -Original Message- From: sprinklerforum-boun...@lists.firesprinkler.org [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On Behalf Of djj8...@aol.com Sent: Thursday, March 13, 2014 1:09 PM To: sprinklerforum@lists.firesprinkler.org Subject: Question on old sprinkler heads Could anybody tell me where and if there is a code that says you have to replace sprinkler heads with new ones once they are removed? ___ Sprinklerforum mailing list Sprinklerforum@lists.firesprinkler.org http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org ___ Sprinklerforum mailing list Sprinklerforum@lists.firesprinkler.org http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org -- Ron Greenman Instructor Fire Protection Engineering Technology Bates Technical College 1101 So. Yakima Ave. Tacoma, WA 98405 rgreen...@bates.ctc.edu http://www.bates.ctc.edu/fireprotection/ 253.680.7346 253.576.9700 (cell) Member: ASEE, SFPE, ASCET, NFPA, AFSA, NFSA, AFAA, NIBS, WSAFM, WFC, WFSC They are happy men whose natures sort with their vocations. -Francis Bacon, essayist, philosopher, and statesman (1561-1626) A problem well stated is a problem half solved. -Charles F. Kettering, inventor and engineer (1876-1958) ___ Sprinklerforum mailing list Sprinklerforum@lists.firesprinkler.org http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org ___ Sprinklerforum mailing list Sprinklerforum@lists.firesprinkler.org http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org