Question on old sprinkler heads

2014-03-13 Thread DJJ8389
Could anybody tell me where and if there is a code that says you have to  
replace sprinkler heads with new ones once they are removed? 
___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org


RE: Question on old sprinkler heads

2014-03-13 Thread Morey, Mike
NFPA 13, 2013 edition 
6.2.1.1 When a sprinkler has been removed for any reason, it shall not be 
reinstalled.

This particular text is new, but it's really just meant as a clarification for 
the existing 6.2.1 which states only new sprinklers shall be installed which I 
believe has been in the standard for several editions.

Mike Morey, CFPS, SET
Planner Scheduler/Designer
BMWC Constructors, Inc.
1740 W. Michigan St, Indianapolis, IN 46222
O: 317.651.0596 | C: 317.586.8111
mo...@bmwc.com | www.bmwc.com


From: sprinklerforum-boun...@lists.firesprinkler.org 
[sprinklerforum-boun...@lists.firesprinkler.org] on behalf of djj8...@aol.com 
[djj8...@aol.com]
Sent: Thursday, March 13, 2014 2:08 PM
To: sprinklerforum@lists.firesprinkler.org
Subject: Question on old sprinkler heads

Could anybody tell me where and if there is a code that says you have to
replace sprinkler heads with new ones once they are removed?
___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org


RE: Question on old sprinkler heads

2014-03-13 Thread BJ Newlin
From the 2013 ed. of NFPA 2013


6.2.1.1 When a sprinkler has been removed for any reason, it shall not be
reinstalled.

BJ Newlin
Service Sales
Aegis Fire Protection LLC.

Whoever is careless with the truth in small matters cannot be trusted with
important matters 
― Albert Einstein



-Original Message-
From: sprinklerforum-boun...@lists.firesprinkler.org
[mailto:sprinklerforum-boun...@lists.firesprinkler.org] On Behalf Of
djj8...@aol.com
Sent: Thursday, March 13, 2014 1:09 PM
To: sprinklerforum@lists.firesprinkler.org
Subject: Question on old sprinkler heads

Could anybody tell me where and if there is a code that says you have to
replace sprinkler heads with new ones once they are removed? 
___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org


Re: Question on old sprinkler heads

2014-03-13 Thread rongreenman .
1-8.1.1 in the 1977 edition.


On Thu, Mar 13, 2014 at 11:15 AM, BJ Newlin bjnew...@aegisfirepro.comwrote:

 From the 2013 ed. of NFPA 2013


 6.2.1.1 When a sprinkler has been removed for any reason, it shall not be
 reinstalled.

 BJ Newlin
 Service Sales
 Aegis Fire Protection LLC.

 Whoever is careless with the truth in small matters cannot be trusted with
 important matters
 -- Albert Einstein



 -Original Message-
 From: sprinklerforum-boun...@lists.firesprinkler.org
 [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On Behalf Of
 djj8...@aol.com
 Sent: Thursday, March 13, 2014 1:09 PM
 To: sprinklerforum@lists.firesprinkler.org
 Subject: Question on old sprinkler heads

 Could anybody tell me where and if there is a code that says you have to
 replace sprinkler heads with new ones once they are removed?
 ___
 Sprinklerforum mailing list
 Sprinklerforum@lists.firesprinkler.org

 http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

 ___
 Sprinklerforum mailing list
 Sprinklerforum@lists.firesprinkler.org

 http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org




-- 
Ron Greenman
Instructor
Fire Protection Engineering Technology
Bates Technical College
1101 So. Yakima Ave.
Tacoma, WA 98405

rgreen...@bates.ctc.edu

http://www.bates.ctc.edu/fireprotection/

253.680.7346
253.576.9700 (cell)

Member:
ASEE, SFPE, ASCET, NFPA, AFSA, NFSA, AFAA, NIBS, WSAFM, WFC, WFSC

They are happy men whose natures sort with their vocations. -Francis Bacon,
essayist, philosopher, and statesman (1561-1626)

A problem well stated is a problem half solved. -Charles F. Kettering,
inventor and engineer (1876-1958)
___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org


Re: Question on old sprinkler heads

2014-03-13 Thread Jamie Seidl
Show off...

Sent from my iPhone
Jamie Seidl 

 On Mar 13, 2014, at 2:30 PM, rongreenman . rongreen...@gmail.com wrote:
 
 1-8.1.1 in the 1977 edition.
 
 
 On Thu, Mar 13, 2014 at 11:15 AM, BJ Newlin bjnew...@aegisfirepro.comwrote:
 
 From the 2013 ed. of NFPA 2013
 
 
 6.2.1.1 When a sprinkler has been removed for any reason, it shall not be
 reinstalled.
 
 BJ Newlin
 Service Sales
 Aegis Fire Protection LLC.
 
 Whoever is careless with the truth in small matters cannot be trusted with
 important matters
 -- Albert Einstein
 
 
 
 -Original Message-
 From: sprinklerforum-boun...@lists.firesprinkler.org
 [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On Behalf Of
 djj8...@aol.com
 Sent: Thursday, March 13, 2014 1:09 PM
 To: sprinklerforum@lists.firesprinkler.org
 Subject: Question on old sprinkler heads
 
 Could anybody tell me where and if there is a code that says you have to
 replace sprinkler heads with new ones once they are removed?
 ___
 Sprinklerforum mailing list
 Sprinklerforum@lists.firesprinkler.org
 
 http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
 
 ___
 Sprinklerforum mailing list
 Sprinklerforum@lists.firesprinkler.org
 
 http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
 
 
 
 -- 
 Ron Greenman
 Instructor
 Fire Protection Engineering Technology
 Bates Technical College
 1101 So. Yakima Ave.
 Tacoma, WA 98405
 
 rgreen...@bates.ctc.edu
 
 http://www.bates.ctc.edu/fireprotection/
 
 253.680.7346
 253.576.9700 (cell)
 
 Member:
 ASEE, SFPE, ASCET, NFPA, AFSA, NFSA, AFAA, NIBS, WSAFM, WFC, WFSC
 
 They are happy men whose natures sort with their vocations. -Francis Bacon,
 essayist, philosopher, and statesman (1561-1626)
 
 A problem well stated is a problem half solved. -Charles F. Kettering,
 inventor and engineer (1876-1958)
 ___
 Sprinklerforum mailing list
 Sprinklerforum@lists.firesprinkler.org
 http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org