RE: Pipe Schedule Systems

2010-09-16 Thread Autry, David
What exactly would you add it to?

David Autry
Plans Examiner
Nebraska State Fire Marshal's Office
246 S. 14th Street
Lincoln, NE 68508
402-471-9659
402-471-3118 fax
www.sfm.ne.gov
 
** Note new email address: david.au...@nebraska.gov
 
-Original Message-
From: sprinklerforum-boun...@firesprinkler.org 
[mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of Brian Harris
Sent: Thursday, September 16, 2010 8:36 AM
To: sprinklerforum@firesprinkler.org
Subject: Pipe Schedule Systems

I swear I read somewhere that for a pipe schedule system you do not need to
add hose allowance, Am I nuts? 

 

Brian Harris

First Defense Fire Protection

11957 Ramah Church Road

Huntersville, NC 28078

Phone: 704.948.3506

Fax: 704.948.3507

Nicet # 128476

 





===
Email scanned by PC Tools - No viruses or spyware found.
(Email Guard: 7.0.0.21, Virus/Spyware Database: 6.15890)
http://www.pctools.com/
===
___
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: supp...@firesprinkler.org

To Unsubscribe, send an email to:sprinklerforum-requ...@firesprinkler.org
(Put the word unsubscribe in the subject field)
___
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: supp...@firesprinkler.org

To Unsubscribe, send an email to:sprinklerforum-requ...@firesprinkler.org
(Put the word unsubscribe in the subject field)


RE: Pipe Schedule Systems

2010-09-16 Thread Brian Harris
David-
We are doing some minor work to an existing warehouse that was done with the
pipe schedule method. Now the AHJ wants us to provide hydraulic calc's to
show him if the existing system will work. 

Brian Harris
FDFP Inc.
 
-Original Message-
From: sprinklerforum-boun...@firesprinkler.org
[mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of Autry, David
Sent: Thursday, September 16, 2010 9:39 AM
To: sprinklerforum@firesprinkler.org
Subject: RE: Pipe Schedule Systems

What exactly would you add it to?

David Autry
Plans Examiner
Nebraska State Fire Marshal's Office
246 S. 14th Street
Lincoln, NE 68508
402-471-9659
402-471-3118 fax
www.sfm.ne.gov
 
** Note new email address: david.au...@nebraska.gov
 
-Original Message-
From: sprinklerforum-boun...@firesprinkler.org
[mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of Brian Harris
Sent: Thursday, September 16, 2010 8:36 AM
To: sprinklerforum@firesprinkler.org
Subject: Pipe Schedule Systems

I swear I read somewhere that for a pipe schedule system you do not need to
add hose allowance, Am I nuts? 

 

Brian Harris

First Defense Fire Protection

11957 Ramah Church Road

Huntersville, NC 28078

Phone: 704.948.3506

Fax: 704.948.3507

Nicet # 128476

 





===
Email scanned by PC Tools - No viruses or spyware found.
(Email Guard: 7.0.0.21, Virus/Spyware Database: 6.15890)
http://www.pctools.com/
===
___
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: supp...@firesprinkler.org

To Unsubscribe, send an email to:sprinklerforum-requ...@firesprinkler.org
(Put the word unsubscribe in the subject field)
___
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: supp...@firesprinkler.org

To Unsubscribe, send an email to:sprinklerforum-requ...@firesprinkler.org
(Put the word unsubscribe in the subject field)





===
Email scanned by PC Tools - No viruses or spyware found.
(Email Guard: 7.0.0.21, Virus/Spyware Database: 6.15890)
http://www.pctools.com/
===





===
Email scanned by PC Tools - No viruses or spyware found.
(Email Guard: 7.0.0.21, Virus/Spyware Database: 6.15890)
http://www.pctools.com/
===
___
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: supp...@firesprinkler.org

To Unsubscribe, send an email to:sprinklerforum-requ...@firesprinkler.org
(Put the word unsubscribe in the subject field)


RE: Pipe Schedule Systems

2010-09-16 Thread Matthew J. Willis
Then it will no longer be a pipe schedule, but a calculated system. Which
requires hose streams.

R/
Matt

 

 

Matthew J. Willis, CET
Automatic Fire Sprinklers
Norred Fire Systems L.L.C.
318-387-1134 Voice
318-816-1087 Mobile
318-387-1163 Facsimile
m...@norredfire.com
 -Original Message-
 From: sprinklerforum-boun...@firesprinkler.org [mailto:sprinklerforum-
 boun...@firesprinkler.org] On Behalf Of Brian Harris
 Sent: Thursday, September 16, 2010 8:57 AM
 To: sprinklerforum@firesprinkler.org
 Subject: RE: Pipe Schedule Systems
 
 David-
 We are doing some minor work to an existing warehouse that was done with
 the
 pipe schedule method. Now the AHJ wants us to provide hydraulic calc's to
 show him if the existing system will work.
 
 Brian Harris
 FDFP Inc.
 
 -Original Message-
 From: sprinklerforum-boun...@firesprinkler.org
 [mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of Autry,
 David
 Sent: Thursday, September 16, 2010 9:39 AM
 To: sprinklerforum@firesprinkler.org
 Subject: RE: Pipe Schedule Systems
 
 What exactly would you add it to?
 
 David Autry
 Plans Examiner
 Nebraska State Fire Marshal's Office
 246 S. 14th Street
 Lincoln, NE 68508
 402-471-9659
 402-471-3118 fax
 www.sfm.ne.gov
 
 ** Note new email address: david.au...@nebraska.gov
 
 -Original Message-
 From: sprinklerforum-boun...@firesprinkler.org
 [mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of Brian
 Harris
 Sent: Thursday, September 16, 2010 8:36 AM
 To: sprinklerforum@firesprinkler.org
 Subject: Pipe Schedule Systems
 
 I swear I read somewhere that for a pipe schedule system you do not need
 to
 add hose allowance, Am I nuts?
 
 
 
 Brian Harris
 
 First Defense Fire Protection
 
 11957 Ramah Church Road
 
 Huntersville, NC 28078
 
 Phone: 704.948.3506
 
 Fax: 704.948.3507
 
 Nicet # 128476
 
 
 
 
 
 
 
 ===
 Email scanned by PC Tools - No viruses or spyware found.
 (Email Guard: 7.0.0.21, Virus/Spyware Database: 6.15890)
 http://www.pctools.com/
 ===
 ___
 Sprinklerforum mailing list
 Sprinklerforum@firesprinkler.org
 http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
 
 For Technical Assistance, send an email to: supp...@firesprinkler.org
 
 To Unsubscribe, send an email to:sprinklerforum-requ...@firesprinkler.org
 (Put the word unsubscribe in the subject field)
 ___
 Sprinklerforum mailing list
 Sprinklerforum@firesprinkler.org
 http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
 
 For Technical Assistance, send an email to: supp...@firesprinkler.org
 
 To Unsubscribe, send an email to:sprinklerforum-requ...@firesprinkler.org
 (Put the word unsubscribe in the subject field)
 
 
 
 
 
 ===
 Email scanned by PC Tools - No viruses or spyware found.
 (Email Guard: 7.0.0.21, Virus/Spyware Database: 6.15890)
 http://www.pctools.com/
 ===
 
 
 
 
 
 ===
 Email scanned by PC Tools - No viruses or spyware found.
 (Email Guard: 7.0.0.21, Virus/Spyware Database: 6.15890)
 http://www.pctools.com/
 ===
 ___
 Sprinklerforum mailing list
 Sprinklerforum@firesprinkler.org
 http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
 
 For Technical Assistance, send an email to: supp...@firesprinkler.org
 
 To Unsubscribe, send an email to:sprinklerforum-requ...@firesprinkler.org
 (Put the word unsubscribe in the subject field)
 No virus found in this incoming message.
 Checked by AVG - www.avg.com
 Version: 9.0.851 / Virus Database: 271.1.1/3137 - Release Date: 09/16/10
 01:34:00

___
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: supp...@firesprinkler.org

To Unsubscribe, send an email to:sprinklerforum-requ...@firesprinkler.org
(Put the word unsubscribe in the subject field)


RE: Pipe Schedule Systems

2010-09-16 Thread Autry, David
What Matt said.

David Autry
Plans Examiner
Nebraska State Fire Marshal's Office
246 S. 14th Street
Lincoln, NE 68508
402-471-9659
402-471-3118 fax
www.sfm.ne.gov
 
** Note new email address: david.au...@nebraska.gov
 

-Original Message-
From: sprinklerforum-boun...@firesprinkler.org 
[mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of Matthew J. Willis
Sent: Thursday, September 16, 2010 9:00 AM
To: sprinklerforum@firesprinkler.org
Subject: RE: Pipe Schedule Systems

Then it will no longer be a pipe schedule, but a calculated system. Which
requires hose streams.

R/
Matt

 

 

Matthew J. Willis, CET
Automatic Fire Sprinklers
Norred Fire Systems L.L.C.
318-387-1134 Voice
318-816-1087 Mobile
318-387-1163 Facsimile
m...@norredfire.com
 -Original Message-
 From: sprinklerforum-boun...@firesprinkler.org [mailto:sprinklerforum-
 boun...@firesprinkler.org] On Behalf Of Brian Harris
 Sent: Thursday, September 16, 2010 8:57 AM
 To: sprinklerforum@firesprinkler.org
 Subject: RE: Pipe Schedule Systems
 
 David-
 We are doing some minor work to an existing warehouse that was done with
 the
 pipe schedule method. Now the AHJ wants us to provide hydraulic calc's to
 show him if the existing system will work.
 
 Brian Harris
 FDFP Inc.
 
 -Original Message-
 From: sprinklerforum-boun...@firesprinkler.org
 [mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of Autry,
 David
 Sent: Thursday, September 16, 2010 9:39 AM
 To: sprinklerforum@firesprinkler.org
 Subject: RE: Pipe Schedule Systems
 
 What exactly would you add it to?
 
 David Autry
 Plans Examiner
 Nebraska State Fire Marshal's Office
 246 S. 14th Street
 Lincoln, NE 68508
 402-471-9659
 402-471-3118 fax
 www.sfm.ne.gov
 
 ** Note new email address: david.au...@nebraska.gov
 
 -Original Message-
 From: sprinklerforum-boun...@firesprinkler.org
 [mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of Brian
 Harris
 Sent: Thursday, September 16, 2010 8:36 AM
 To: sprinklerforum@firesprinkler.org
 Subject: Pipe Schedule Systems
 
 I swear I read somewhere that for a pipe schedule system you do not need
 to
 add hose allowance, Am I nuts?
 
 
 
 Brian Harris
 
 First Defense Fire Protection
 
 11957 Ramah Church Road
 
 Huntersville, NC 28078
 
 Phone: 704.948.3506
 
 Fax: 704.948.3507
 
 Nicet # 128476
 
 
 
 
 
 
 
 ===
 Email scanned by PC Tools - No viruses or spyware found.
 (Email Guard: 7.0.0.21, Virus/Spyware Database: 6.15890)
 http://www.pctools.com/
 ===
 ___
 Sprinklerforum mailing list
 Sprinklerforum@firesprinkler.org
 http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
 
 For Technical Assistance, send an email to: supp...@firesprinkler.org
 
 To Unsubscribe, send an email to:sprinklerforum-requ...@firesprinkler.org
 (Put the word unsubscribe in the subject field)
 ___
 Sprinklerforum mailing list
 Sprinklerforum@firesprinkler.org
 http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
 
 For Technical Assistance, send an email to: supp...@firesprinkler.org
 
 To Unsubscribe, send an email to:sprinklerforum-requ...@firesprinkler.org
 (Put the word unsubscribe in the subject field)
 
 
 
 
 
 ===
 Email scanned by PC Tools - No viruses or spyware found.
 (Email Guard: 7.0.0.21, Virus/Spyware Database: 6.15890)
 http://www.pctools.com/
 ===
 
 
 
 
 
 ===
 Email scanned by PC Tools - No viruses or spyware found.
 (Email Guard: 7.0.0.21, Virus/Spyware Database: 6.15890)
 http://www.pctools.com/
 ===
 ___
 Sprinklerforum mailing list
 Sprinklerforum@firesprinkler.org
 http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
 
 For Technical Assistance, send an email to: supp...@firesprinkler.org
 
 To Unsubscribe, send an email to:sprinklerforum-requ...@firesprinkler.org
 (Put the word unsubscribe in the subject field)
 No virus found in this incoming message.
 Checked by AVG - www.avg.com
 Version: 9.0.851 / Virus Database: 271.1.1/3137 - Release Date: 09/16/10
 01:34:00

___
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: supp...@firesprinkler.org

To Unsubscribe, send an email to:sprinklerforum-requ...@firesprinkler.org
(Put the word unsubscribe in the subject field)
___
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: supp...@firesprinkler.org

To Unsubscribe, send an email to:sprinklerforum-requ...@firesprinkler.org
(Put the word unsubscribe in the subject field)


RE: Pipe Schedule Systems

2010-09-16 Thread Brian Harris
I guess that makes sense..

Brian Harris
FDFP Inc.
 

-Original Message-
From: sprinklerforum-boun...@firesprinkler.org
[mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of Matthew J.
Willis
Sent: Thursday, September 16, 2010 10:00 AM
To: sprinklerforum@firesprinkler.org
Subject: RE: Pipe Schedule Systems

Then it will no longer be a pipe schedule, but a calculated system. Which
requires hose streams.

R/
Matt

 

 

Matthew J. Willis, CET
Automatic Fire Sprinklers
Norred Fire Systems L.L.C.
318-387-1134 Voice
318-816-1087 Mobile
318-387-1163 Facsimile
m...@norredfire.com
 -Original Message-
 From: sprinklerforum-boun...@firesprinkler.org [mailto:sprinklerforum-
 boun...@firesprinkler.org] On Behalf Of Brian Harris
 Sent: Thursday, September 16, 2010 8:57 AM
 To: sprinklerforum@firesprinkler.org
 Subject: RE: Pipe Schedule Systems
 
 David-
 We are doing some minor work to an existing warehouse that was done with
 the
 pipe schedule method. Now the AHJ wants us to provide hydraulic calc's to
 show him if the existing system will work.
 
 Brian Harris
 FDFP Inc.
 
 -Original Message-
 From: sprinklerforum-boun...@firesprinkler.org
 [mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of Autry,
 David
 Sent: Thursday, September 16, 2010 9:39 AM
 To: sprinklerforum@firesprinkler.org
 Subject: RE: Pipe Schedule Systems
 
 What exactly would you add it to?
 
 David Autry
 Plans Examiner
 Nebraska State Fire Marshal's Office
 246 S. 14th Street
 Lincoln, NE 68508
 402-471-9659
 402-471-3118 fax
 www.sfm.ne.gov
 
 ** Note new email address: david.au...@nebraska.gov
 
 -Original Message-
 From: sprinklerforum-boun...@firesprinkler.org
 [mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of Brian
 Harris
 Sent: Thursday, September 16, 2010 8:36 AM
 To: sprinklerforum@firesprinkler.org
 Subject: Pipe Schedule Systems
 
 I swear I read somewhere that for a pipe schedule system you do not need
 to
 add hose allowance, Am I nuts?
 
 
 
 Brian Harris
 
 First Defense Fire Protection
 
 11957 Ramah Church Road
 
 Huntersville, NC 28078
 
 Phone: 704.948.3506
 
 Fax: 704.948.3507
 
 Nicet # 128476
 
 
 
 
 
 
 
 ===
 Email scanned by PC Tools - No viruses or spyware found.
 (Email Guard: 7.0.0.21, Virus/Spyware Database: 6.15890)
 http://www.pctools.com/
 ===
 ___
 Sprinklerforum mailing list
 Sprinklerforum@firesprinkler.org
 http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
 
 For Technical Assistance, send an email to: supp...@firesprinkler.org
 
 To Unsubscribe, send an email to:sprinklerforum-requ...@firesprinkler.org
 (Put the word unsubscribe in the subject field)
 ___
 Sprinklerforum mailing list
 Sprinklerforum@firesprinkler.org
 http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
 
 For Technical Assistance, send an email to: supp...@firesprinkler.org
 
 To Unsubscribe, send an email to:sprinklerforum-requ...@firesprinkler.org
 (Put the word unsubscribe in the subject field)
 
 
 
 
 
 ===
 Email scanned by PC Tools - No viruses or spyware found.
 (Email Guard: 7.0.0.21, Virus/Spyware Database: 6.15890)
 http://www.pctools.com/
 ===
 
 
 
 
 
 ===
 Email scanned by PC Tools - No viruses or spyware found.
 (Email Guard: 7.0.0.21, Virus/Spyware Database: 6.15890)
 http://www.pctools.com/
 ===
 ___
 Sprinklerforum mailing list
 Sprinklerforum@firesprinkler.org
 http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
 
 For Technical Assistance, send an email to: supp...@firesprinkler.org
 
 To Unsubscribe, send an email to:sprinklerforum-requ...@firesprinkler.org
 (Put the word unsubscribe in the subject field)
 No virus found in this incoming message.
 Checked by AVG - www.avg.com
 Version: 9.0.851 / Virus Database: 271.1.1/3137 - Release Date: 09/16/10
 01:34:00

___
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: supp...@firesprinkler.org

To Unsubscribe, send an email to:sprinklerforum-requ...@firesprinkler.org
(Put the word unsubscribe in the subject field)





===
Email scanned by PC Tools - No viruses or spyware found.
(Email Guard: 7.0.0.21, Virus/Spyware Database: 6.15890)
http://www.pctools.com/
===





===
Email scanned by PC Tools - No viruses or spyware found.
(Email Guard: 7.0.0.21, Virus/Spyware Database: 6.15890)
http://www.pctools.com/
===
___
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: supp...@firesprinkler.org

To Unsubscribe, send an email to:sprinklerforum-requ...@firesprinkler.org
(Put

Re: Pipe Schedule Systems

2010-09-16 Thread steve
The standard requires a minimum pressure be available at the highest/most 
remote sprinkler - is that the calc that's been requested?   Still no 
requirement for a hose allowance though. 

Steve 


Sent from my Verizon Wireless BlackBerry

-Original Message-
From: Matthew J. Willis m...@norredfire.com
Sender: sprinklerforum-boun...@firesprinkler.org
Date: Thu, 16 Sep 2010 08:59:48 
To: sprinklerforum@firesprinkler.org
Reply-To: sprinklerforum@firesprinkler.org
Subject: RE: Pipe Schedule Systems

Then it will no longer be a pipe schedule, but a calculated system. Which
requires hose streams.

R/
Matt

 

 

Matthew J. Willis, CET
Automatic Fire Sprinklers
Norred Fire Systems L.L.C.
318-387-1134 Voice
318-816-1087 Mobile
318-387-1163 Facsimile
m...@norredfire.com
 -Original Message-
 From: sprinklerforum-boun...@firesprinkler.org [mailto:sprinklerforum-
 boun...@firesprinkler.org] On Behalf Of Brian Harris
 Sent: Thursday, September 16, 2010 8:57 AM
 To: sprinklerforum@firesprinkler.org
 Subject: RE: Pipe Schedule Systems
 
 David-
 We are doing some minor work to an existing warehouse that was done with
 the
 pipe schedule method. Now the AHJ wants us to provide hydraulic calc's to
 show him if the existing system will work.
 
 Brian Harris
 FDFP Inc.
 
 -Original Message-
 From: sprinklerforum-boun...@firesprinkler.org
 [mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of Autry,
 David
 Sent: Thursday, September 16, 2010 9:39 AM
 To: sprinklerforum@firesprinkler.org
 Subject: RE: Pipe Schedule Systems
 
 What exactly would you add it to?
 
 David Autry
 Plans Examiner
 Nebraska State Fire Marshal's Office
 246 S. 14th Street
 Lincoln, NE 68508
 402-471-9659
 402-471-3118 fax
 www.sfm.ne.gov
 
 ** Note new email address: david.au...@nebraska.gov
 
 -Original Message-
 From: sprinklerforum-boun...@firesprinkler.org
 [mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of Brian
 Harris
 Sent: Thursday, September 16, 2010 8:36 AM
 To: sprinklerforum@firesprinkler.org
 Subject: Pipe Schedule Systems
 
 I swear I read somewhere that for a pipe schedule system you do not need
 to
 add hose allowance, Am I nuts?
 
 
 
 Brian Harris
 
 First Defense Fire Protection
 
 11957 Ramah Church Road
 
 Huntersville, NC 28078
 
 Phone: 704.948.3506
 
 Fax: 704.948.3507
 
 Nicet # 128476
 
 
 
 
 
 
 
 ===
 Email scanned by PC Tools - No viruses or spyware found.
 (Email Guard: 7.0.0.21, Virus/Spyware Database: 6.15890)
 http://www.pctools.com/
 ===
 ___
 Sprinklerforum mailing list
 Sprinklerforum@firesprinkler.org
 http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
 
 For Technical Assistance, send an email to: supp...@firesprinkler.org
 
 To Unsubscribe, send an email to:sprinklerforum-requ...@firesprinkler.org
 (Put the word unsubscribe in the subject field)
 ___
 Sprinklerforum mailing list
 Sprinklerforum@firesprinkler.org
 http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
 
 For Technical Assistance, send an email to: supp...@firesprinkler.org
 
 To Unsubscribe, send an email to:sprinklerforum-requ...@firesprinkler.org
 (Put the word unsubscribe in the subject field)
 
 
 
 
 
 ===
 Email scanned by PC Tools - No viruses or spyware found.
 (Email Guard: 7.0.0.21, Virus/Spyware Database: 6.15890)
 http://www.pctools.com/
 ===
 
 
 
 
 
 ===
 Email scanned by PC Tools - No viruses or spyware found.
 (Email Guard: 7.0.0.21, Virus/Spyware Database: 6.15890)
 http://www.pctools.com/
 ===
 ___
 Sprinklerforum mailing list
 Sprinklerforum@firesprinkler.org
 http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
 
 For Technical Assistance, send an email to: supp...@firesprinkler.org
 
 To Unsubscribe, send an email to:sprinklerforum-requ...@firesprinkler.org
 (Put the word unsubscribe in the subject field)
 No virus found in this incoming message.
 Checked by AVG - www.avg.com
 Version: 9.0.851 / Virus Database: 271.1.1/3137 - Release Date: 09/16/10
 01:34:00

___
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: supp...@firesprinkler.org

To Unsubscribe, send an email to:sprinklerforum-requ...@firesprinkler.org
(Put the word unsubscribe in the subject field)
___
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: supp...@firesprinkler.org

To Unsubscribe, send an email to:sprinklerforum-requ...@firesprinkler.org
(Put the word unsubscribe in the subject field)


RE: Pipe Schedule Systems

2010-09-16 Thread George Church
Sounds like the AHJ may be overstepping his boundries. Additions to Pipe
schedule systems are allowed without calcs in #13.

-Original Message-
From: sprinklerforum-boun...@firesprinkler.org
[mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of steve
Sent: Thursday, September 16, 2010 10:10 AM
To: AFSA
Subject: Re: Pipe Schedule Systems

The standard requires a minimum pressure be available at the highest/most
remote sprinkler - is that the calc that's been requested?   Still no
requirement for a hose allowance though. 

Steve 


Sent from my Verizon Wireless BlackBerry

-Original Message-
From: Matthew J. Willis m...@norredfire.com
Sender: sprinklerforum-boun...@firesprinkler.org
Date: Thu, 16 Sep 2010 08:59:48
To: sprinklerforum@firesprinkler.org
Reply-To: sprinklerforum@firesprinkler.org
Subject: RE: Pipe Schedule Systems

Then it will no longer be a pipe schedule, but a calculated system. Which
requires hose streams.

R/
Matt

 

 

Matthew J. Willis, CET
Automatic Fire Sprinklers
Norred Fire Systems L.L.C.
318-387-1134 Voice
318-816-1087 Mobile
318-387-1163 Facsimile
m...@norredfire.com
 -Original Message-
 From: sprinklerforum-boun...@firesprinkler.org 
 [mailto:sprinklerforum- boun...@firesprinkler.org] On Behalf Of Brian 
 Harris
 Sent: Thursday, September 16, 2010 8:57 AM
 To: sprinklerforum@firesprinkler.org
 Subject: RE: Pipe Schedule Systems
 
 David-
 We are doing some minor work to an existing warehouse that was done 
 with the pipe schedule method. Now the AHJ wants us to provide 
 hydraulic calc's to show him if the existing system will work.
 
 Brian Harris
 FDFP Inc.
 
 -Original Message-
 From: sprinklerforum-boun...@firesprinkler.org
 [mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of Autry, 
 David
 Sent: Thursday, September 16, 2010 9:39 AM
 To: sprinklerforum@firesprinkler.org
 Subject: RE: Pipe Schedule Systems
 
 What exactly would you add it to?
 
 David Autry
 Plans Examiner
 Nebraska State Fire Marshal's Office
 246 S. 14th Street
 Lincoln, NE 68508
 402-471-9659
 402-471-3118 fax
 www.sfm.ne.gov
 
 ** Note new email address: david.au...@nebraska.gov
 
 -Original Message-
 From: sprinklerforum-boun...@firesprinkler.org
 [mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of Brian 
 Harris
 Sent: Thursday, September 16, 2010 8:36 AM
 To: sprinklerforum@firesprinkler.org
 Subject: Pipe Schedule Systems
 
 I swear I read somewhere that for a pipe schedule system you do not 
 need to add hose allowance, Am I nuts?
 
 
 
 Brian Harris
 
 First Defense Fire Protection
 
 11957 Ramah Church Road
 
 Huntersville, NC 28078
 
 Phone: 704.948.3506
 
 Fax: 704.948.3507
 
 Nicet # 128476
 
 
 
 
 
 
 
 ===
 Email scanned by PC Tools - No viruses or spyware found.
 (Email Guard: 7.0.0.21, Virus/Spyware Database: 6.15890) 
 http://www.pctools.com/ === 
 ___
 Sprinklerforum mailing list
 Sprinklerforum@firesprinkler.org
 http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
 
 For Technical Assistance, send an email to: supp...@firesprinkler.org
 
 To Unsubscribe, send an email 
 to:sprinklerforum-requ...@firesprinkler.org
 (Put the word unsubscribe in the subject field) 
 ___
 Sprinklerforum mailing list
 Sprinklerforum@firesprinkler.org
 http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
 
 For Technical Assistance, send an email to: supp...@firesprinkler.org
 
 To Unsubscribe, send an email 
 to:sprinklerforum-requ...@firesprinkler.org
 (Put the word unsubscribe in the subject field)
 
 
 
 
 
 ===
 Email scanned by PC Tools - No viruses or spyware found.
 (Email Guard: 7.0.0.21, Virus/Spyware Database: 6.15890) 
 http://www.pctools.com/ ===
 
 
 
 
 
 ===
 Email scanned by PC Tools - No viruses or spyware found.
 (Email Guard: 7.0.0.21, Virus/Spyware Database: 6.15890) 
 http://www.pctools.com/ === 
 ___
 Sprinklerforum mailing list
 Sprinklerforum@firesprinkler.org
 http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
 
 For Technical Assistance, send an email to: supp...@firesprinkler.org
 
 To Unsubscribe, send an email 
 to:sprinklerforum-requ...@firesprinkler.org
 (Put the word unsubscribe in the subject field) No virus found in 
 this incoming message.
 Checked by AVG - www.avg.com
 Version: 9.0.851 / Virus Database: 271.1.1/3137 - Release Date: 
 09/16/10
 01:34:00

___
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: supp...@firesprinkler.org

To Unsubscribe, send an email to:sprinklerforum-requ...@firesprinkler.org
(Put the word unsubscribe in the subject field)
___
Sprinklerforum mailing list
Sprinklerforum

Re: Pipe Schedule Systems

2010-09-16 Thread Ron Greenman
Although within his authority the AHJ is being unreasonable to require
the calcs. If minor modification is being done to pipe schedule
systems than the pipe schedule should apply and your new work just
needs to fit the schedule. The whole concept between pipe schedules
and calculations is that with calculations you can have more
flexibility of design and can more precisely predict performance and
thereby possibly reduce cost by using less materials, in our case
smaller diameter pipes. After you calc this scheduled system you'll
see how over built it is just like the residential plumbers' rules of
thumb for plumbing fixture pipe sizing.

On Thu, Sep 16, 2010 at 7:04 AM, Brian Harris
br...@firstdefensefire.com wrote:
 I guess that makes sense..

 Brian Harris
 FDFP Inc.


 -Original Message-
 From: sprinklerforum-boun...@firesprinkler.org
 [mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of Matthew J.
 Willis
 Sent: Thursday, September 16, 2010 10:00 AM
 To: sprinklerforum@firesprinkler.org
 Subject: RE: Pipe Schedule Systems

 Then it will no longer be a pipe schedule, but a calculated system. Which
 requires hose streams.

 R/
 Matt





 Matthew J. Willis, CET
 Automatic Fire Sprinklers
 Norred Fire Systems L.L.C.
 318-387-1134 Voice
 318-816-1087 Mobile
 318-387-1163 Facsimile
 m...@norredfire.com
 -Original Message-
 From: sprinklerforum-boun...@firesprinkler.org [mailto:sprinklerforum-
 boun...@firesprinkler.org] On Behalf Of Brian Harris
 Sent: Thursday, September 16, 2010 8:57 AM
 To: sprinklerforum@firesprinkler.org
 Subject: RE: Pipe Schedule Systems
 
 David-
 We are doing some minor work to an existing warehouse that was done with
 the
 pipe schedule method. Now the AHJ wants us to provide hydraulic calc's to
 show him if the existing system will work.
 
 Brian Harris
 FDFP Inc.
 
 -Original Message-
 From: sprinklerforum-boun...@firesprinkler.org
 [mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of Autry,
 David
 Sent: Thursday, September 16, 2010 9:39 AM
 To: sprinklerforum@firesprinkler.org
 Subject: RE: Pipe Schedule Systems
 
 What exactly would you add it to?
 
 David Autry
 Plans Examiner
 Nebraska State Fire Marshal's Office
 246 S. 14th Street
 Lincoln, NE 68508
 402-471-9659
 402-471-3118 fax
 www.sfm.ne.gov
 
 ** Note new email address: david.au...@nebraska.gov
 
 -Original Message-
 From: sprinklerforum-boun...@firesprinkler.org
 [mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of Brian
 Harris
 Sent: Thursday, September 16, 2010 8:36 AM
 To: sprinklerforum@firesprinkler.org
 Subject: Pipe Schedule Systems
 
 I swear I read somewhere that for a pipe schedule system you do not need
 to
 add hose allowance, Am I nuts?
 
 
 
 Brian Harris
 
 First Defense Fire Protection
 
 11957 Ramah Church Road
 
 Huntersville, NC 28078
 
 Phone: 704.948.3506
 
 Fax: 704.948.3507
 
 Nicet # 128476
 
 
 
 
 
 
 
 ===
 Email scanned by PC Tools - No viruses or spyware found.
 (Email Guard: 7.0.0.21, Virus/Spyware Database: 6.15890)
 http://www.pctools.com/
 ===
 ___
 Sprinklerforum mailing list
 Sprinklerforum@firesprinkler.org
 http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
 
 For Technical Assistance, send an email to: supp...@firesprinkler.org
 
 To Unsubscribe, send an email to:sprinklerforum-requ...@firesprinkler.org
 (Put the word unsubscribe in the subject field)
 ___
 Sprinklerforum mailing list
 Sprinklerforum@firesprinkler.org
 http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
 
 For Technical Assistance, send an email to: supp...@firesprinkler.org
 
 To Unsubscribe, send an email to:sprinklerforum-requ...@firesprinkler.org
 (Put the word unsubscribe in the subject field)
 
 
 
 
 
 ===
 Email scanned by PC Tools - No viruses or spyware found.
 (Email Guard: 7.0.0.21, Virus/Spyware Database: 6.15890)
 http://www.pctools.com/
 ===
 
 
 
 
 
 ===
 Email scanned by PC Tools - No viruses or spyware found.
 (Email Guard: 7.0.0.21, Virus/Spyware Database: 6.15890)
 http://www.pctools.com/
 ===
 ___
 Sprinklerforum mailing list
 Sprinklerforum@firesprinkler.org
 http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
 
 For Technical Assistance, send an email to: supp...@firesprinkler.org
 
 To Unsubscribe, send an email to:sprinklerforum-requ...@firesprinkler.org
 (Put the word unsubscribe in the subject field)
 No virus found in this incoming message.
 Checked by AVG - www.avg.com
 Version: 9.0.851 / Virus Database: 271.1.1/3137 - Release Date: 09/16/10
 01:34:00

 ___
 Sprinklerforum mailing list
 Sprinklerforum@firesprinkler.org
 http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

 For Technical Assistance, send an email to: supp...@firesprinkler.org

 To Unsubscribe, send

Re: Pipe Schedule Systems

2010-09-16 Thread Todd Williams

But if there is a change in occupancy?


At 10:19 AM 9/16/2010, you wrote:

Although within his authority the AHJ is being unreasonable to require
the calcs. If minor modification is being done to pipe schedule
systems than the pipe schedule should apply and your new work just
needs to fit the schedule. The whole concept between pipe schedules
and calculations is that with calculations you can have more
flexibility of design and can more precisely predict performance and
thereby possibly reduce cost by using less materials, in our case
smaller diameter pipes. After you calc this scheduled system you'll
see how over built it is just like the residential plumbers' rules of
thumb for plumbing fixture pipe sizing.

On Thu, Sep 16, 2010 at 7:04 AM, Brian Harris
br...@firstdefensefire.com wrote:
 I guess that makes sense..

 Brian Harris
 FDFP Inc.


 -Original Message-
 From: sprinklerforum-boun...@firesprinkler.org
 [mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of Matthew J.
 Willis
 Sent: Thursday, September 16, 2010 10:00 AM
 To: sprinklerforum@firesprinkler.org
 Subject: RE: Pipe Schedule Systems

 Then it will no longer be a pipe schedule, but a calculated system. Which
 requires hose streams.

 R/
 Matt





 Matthew J. Willis, CET
 Automatic Fire Sprinklers
 Norred Fire Systems L.L.C.
 318-387-1134 Voice
 318-816-1087 Mobile
 318-387-1163 Facsimile
 m...@norredfire.com
 -Original Message-
 From: sprinklerforum-boun...@firesprinkler.org [mailto:sprinklerforum-
 boun...@firesprinkler.org] On Behalf Of Brian Harris
 Sent: Thursday, September 16, 2010 8:57 AM
 To: sprinklerforum@firesprinkler.org
 Subject: RE: Pipe Schedule Systems
 
 David-
 We are doing some minor work to an existing warehouse that was done with
 the
 pipe schedule method. Now the AHJ wants us to provide hydraulic calc's to
 show him if the existing system will work.
 
 Brian Harris
 FDFP Inc.
 
 -Original Message-
 From: sprinklerforum-boun...@firesprinkler.org
 [mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of Autry,
 David
 Sent: Thursday, September 16, 2010 9:39 AM
 To: sprinklerforum@firesprinkler.org
 Subject: RE: Pipe Schedule Systems
 
 What exactly would you add it to?
 
 David Autry
 Plans Examiner
 Nebraska State Fire Marshal's Office
 246 S. 14th Street
 Lincoln, NE 68508
 402-471-9659
 402-471-3118 fax
 www.sfm.ne.gov
 
 ** Note new email address: david.au...@nebraska.gov
 
 -Original Message-
 From: sprinklerforum-boun...@firesprinkler.org
 [mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of Brian
 Harris
 Sent: Thursday, September 16, 2010 8:36 AM
 To: sprinklerforum@firesprinkler.org
 Subject: Pipe Schedule Systems
 
 I swear I read somewhere that for a pipe schedule system you do not need
 to
 add hose allowance, Am I nuts?
 
 
 
 Brian Harris
 
 First Defense Fire Protection
 
 11957 Ramah Church Road
 
 Huntersville, NC 28078
 
 Phone: 704.948.3506
 
 Fax: 704.948.3507
 
 Nicet # 128476
 
 
 
 
 
 
 
 ===
 Email scanned by PC Tools - No viruses or spyware found.
 (Email Guard: 7.0.0.21, Virus/Spyware Database: 6.15890)
 http://www.pctools.com/
 ===
 ___
 Sprinklerforum mailing list
 Sprinklerforum@firesprinkler.org
 http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
 
 For Technical Assistance, send an email to: supp...@firesprinkler.org
 
 To Unsubscribe, send an email to:sprinklerforum-requ...@firesprinkler.org
 (Put the word unsubscribe in the subject field)
 ___
 Sprinklerforum mailing list
 Sprinklerforum@firesprinkler.org
 http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
 
 For Technical Assistance, send an email to: supp...@firesprinkler.org
 
 To Unsubscribe, send an email to:sprinklerforum-requ...@firesprinkler.org
 (Put the word unsubscribe in the subject field)
 
 
 
 
 
 ===
 Email scanned by PC Tools - No viruses or spyware found.
 (Email Guard: 7.0.0.21, Virus/Spyware Database: 6.15890)
 http://www.pctools.com/
 ===
 
 
 
 
 
 ===
 Email scanned by PC Tools - No viruses or spyware found.
 (Email Guard: 7.0.0.21, Virus/Spyware Database: 6.15890)
 http://www.pctools.com/
 ===
 ___
 Sprinklerforum mailing list
 Sprinklerforum@firesprinkler.org
 http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
 
 For Technical Assistance, send an email to: supp...@firesprinkler.org
 
 To Unsubscribe, send an email to:sprinklerforum-requ...@firesprinkler.org
 (Put the word unsubscribe in the subject field)
 No virus found in this incoming message.
 Checked by AVG - www.avg.com
 Version: 9.0.851 / Virus Database: 271.1.1/3137 - Release Date: 09/16/10
 01:34:00

 ___
 Sprinklerforum mailing list
 Sprinklerforum@firesprinkler.org
 http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

 For Technical

Re: Pipe Schedule Systems

2010-09-16 Thread Ron Greenman
So what if the modifications are minor? Would the schedule
mysteriously then not apply? Even OH to EH if the schedule meets EH.
Or vice versa like my building.

On Thu, Sep 16, 2010 at 7:21 AM, Todd Williams t...@fpdc.com wrote:
 But if there is a change in occupancy?


 At 10:19 AM 9/16/2010, you wrote:

 Although within his authority the AHJ is being unreasonable to require
 the calcs. If minor modification is being done to pipe schedule
 systems than the pipe schedule should apply and your new work just
 needs to fit the schedule. The whole concept between pipe schedules
 and calculations is that with calculations you can have more
 flexibility of design and can more precisely predict performance and
 thereby possibly reduce cost by using less materials, in our case
 smaller diameter pipes. After you calc this scheduled system you'll
 see how over built it is just like the residential plumbers' rules of
 thumb for plumbing fixture pipe sizing.

 On Thu, Sep 16, 2010 at 7:04 AM, Brian Harris
 br...@firstdefensefire.com wrote:
  I guess that makes sense..
 
  Brian Harris
  FDFP Inc.
 
 
  -Original Message-
  From: sprinklerforum-boun...@firesprinkler.org
  [mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of Matthew
  J.
  Willis
  Sent: Thursday, September 16, 2010 10:00 AM
  To: sprinklerforum@firesprinkler.org
  Subject: RE: Pipe Schedule Systems
 
  Then it will no longer be a pipe schedule, but a calculated system.
  Which
  requires hose streams.
 
  R/
  Matt
 
 
 
 
 
  Matthew J. Willis, CET
  Automatic Fire Sprinklers
  Norred Fire Systems L.L.C.
  318-387-1134 Voice
  318-816-1087 Mobile
  318-387-1163 Facsimile
  m...@norredfire.com
  -Original Message-
  From: sprinklerforum-boun...@firesprinkler.org [mailto:sprinklerforum-
  boun...@firesprinkler.org] On Behalf Of Brian Harris
  Sent: Thursday, September 16, 2010 8:57 AM
  To: sprinklerforum@firesprinkler.org
  Subject: RE: Pipe Schedule Systems
  
  David-
  We are doing some minor work to an existing warehouse that was done
   with
  the
  pipe schedule method. Now the AHJ wants us to provide hydraulic calc's
   to
  show him if the existing system will work.
  
  Brian Harris
  FDFP Inc.
  
  -Original Message-
  From: sprinklerforum-boun...@firesprinkler.org
  [mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of Autry,
  David
  Sent: Thursday, September 16, 2010 9:39 AM
  To: sprinklerforum@firesprinkler.org
  Subject: RE: Pipe Schedule Systems
  
  What exactly would you add it to?
  
  David Autry
  Plans Examiner
  Nebraska State Fire Marshal's Office
  246 S. 14th Street
  Lincoln, NE 68508
  402-471-9659
  402-471-3118 fax
  www.sfm.ne.gov
  
  ** Note new email address: david.au...@nebraska.gov
  
  -Original Message-
  From: sprinklerforum-boun...@firesprinkler.org
  [mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of Brian
  Harris
  Sent: Thursday, September 16, 2010 8:36 AM
  To: sprinklerforum@firesprinkler.org
  Subject: Pipe Schedule Systems
  
  I swear I read somewhere that for a pipe schedule system you do not
   need
  to
  add hose allowance, Am I nuts?
  
  
  
  Brian Harris
  
  First Defense Fire Protection
  
  11957 Ramah Church Road
  
  Huntersville, NC 28078
  
  Phone: 704.948.3506
  
  Fax: 704.948.3507
  
  Nicet # 128476
  
  
  
  
  
  
  
  ===
  Email scanned by PC Tools - No viruses or spyware found.
  (Email Guard: 7.0.0.21, Virus/Spyware Database: 6.15890)
  http://www.pctools.com/
  ===
  ___
  Sprinklerforum mailing list
  Sprinklerforum@firesprinkler.org
  http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
  
  For Technical Assistance, send an email to: supp...@firesprinkler.org
  
  To Unsubscribe, send an email
   to:sprinklerforum-requ...@firesprinkler.org
  (Put the word unsubscribe in the subject field)
  ___
  Sprinklerforum mailing list
  Sprinklerforum@firesprinkler.org
  http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
  
  For Technical Assistance, send an email to: supp...@firesprinkler.org
  
  To Unsubscribe, send an email
   to:sprinklerforum-requ...@firesprinkler.org
  (Put the word unsubscribe in the subject field)
  
  
  
  
  
  ===
  Email scanned by PC Tools - No viruses or spyware found.
  (Email Guard: 7.0.0.21, Virus/Spyware Database: 6.15890)
  http://www.pctools.com/
  ===
  
  
  
  
  
  ===
  Email scanned by PC Tools - No viruses or spyware found.
  (Email Guard: 7.0.0.21, Virus/Spyware Database: 6.15890)
  http://www.pctools.com/
  ===
  ___
  Sprinklerforum mailing list
  Sprinklerforum@firesprinkler.org
  http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
  
  For Technical Assistance, send an email to: supp...@firesprinkler.org
  
  To Unsubscribe, send an email
   to:sprinklerforum-requ

RE: Pipe Schedule Systems

2010-09-16 Thread Thom

Then there's always the question of what C factor to use in your calc's of
an old PS system? Have you seen the inside of these pipes? Do you use 120 or
100 or maybe even 80? There is really no guide on what's appropriate. I had
one AHJ that just wanted the calc to fail, and required that we use a C of
80, when that calc still worked, he said oh I meant 60. 
There was a fight but we ended up doing an internal inspection of the pipe
and he accepted the calc that used 80. (Still just a guess on his part.)

Thom

___
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: supp...@firesprinkler.org

To Unsubscribe, send an email to:sprinklerforum-requ...@firesprinkler.org
(Put the word unsubscribe in the subject field)


RE: Pipe Schedule Systems

2010-09-16 Thread Chris Cahill
Not entirely George.  Was the pipe schedule appropriate for the hazard when
installed?  Has the commodity changed?  Odds are if it is PS it's old thus
there have been many changes that rightfully should be investigated.  You
wouldn't be surprised how many old systems had no correlation to any
standard on how to protect a hazard.  I ran in to this often and always gave
the owner (through his reps) a chance to show when it was installed 13,
231c, FM or anything else this was the appropriate installation.

Chris 

-Original Message-
From: sprinklerforum-boun...@firesprinkler.org
[mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of George Church
Sent: Thursday, September 16, 2010 9:20 AM
To: sprinklerforum@firesprinkler.org; st...@protectiondesign.com
Subject: RE: Pipe Schedule Systems

Sounds like the AHJ may be overstepping his boundries. Additions to Pipe
schedule systems are allowed without calcs in #13.

-Original Message-
From: sprinklerforum-boun...@firesprinkler.org
[mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of steve
Sent: Thursday, September 16, 2010 10:10 AM
To: AFSA
Subject: Re: Pipe Schedule Systems

The standard requires a minimum pressure be available at the highest/most
remote sprinkler - is that the calc that's been requested?   Still no
requirement for a hose allowance though. 

Steve 


Sent from my Verizon Wireless BlackBerry

-Original Message-
From: Matthew J. Willis m...@norredfire.com
Sender: sprinklerforum-boun...@firesprinkler.org
Date: Thu, 16 Sep 2010 08:59:48
To: sprinklerforum@firesprinkler.org
Reply-To: sprinklerforum@firesprinkler.org
Subject: RE: Pipe Schedule Systems

Then it will no longer be a pipe schedule, but a calculated system. Which
requires hose streams.

R/
Matt

 

 

Matthew J. Willis, CET
Automatic Fire Sprinklers
Norred Fire Systems L.L.C.
318-387-1134 Voice
318-816-1087 Mobile
318-387-1163 Facsimile
m...@norredfire.com
 -Original Message-
 From: sprinklerforum-boun...@firesprinkler.org 
 [mailto:sprinklerforum- boun...@firesprinkler.org] On Behalf Of Brian 
 Harris
 Sent: Thursday, September 16, 2010 8:57 AM
 To: sprinklerforum@firesprinkler.org
 Subject: RE: Pipe Schedule Systems
 
 David-
 We are doing some minor work to an existing warehouse that was done 
 with the pipe schedule method. Now the AHJ wants us to provide 
 hydraulic calc's to show him if the existing system will work.
 
 Brian Harris
 FDFP Inc.
 
 -Original Message-
 From: sprinklerforum-boun...@firesprinkler.org
 [mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of Autry, 
 David
 Sent: Thursday, September 16, 2010 9:39 AM
 To: sprinklerforum@firesprinkler.org
 Subject: RE: Pipe Schedule Systems
 
 What exactly would you add it to?
 
 David Autry
 Plans Examiner
 Nebraska State Fire Marshal's Office
 246 S. 14th Street
 Lincoln, NE 68508
 402-471-9659
 402-471-3118 fax
 www.sfm.ne.gov
 
 ** Note new email address: david.au...@nebraska.gov
 
 -Original Message-
 From: sprinklerforum-boun...@firesprinkler.org
 [mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of Brian 
 Harris
 Sent: Thursday, September 16, 2010 8:36 AM
 To: sprinklerforum@firesprinkler.org
 Subject: Pipe Schedule Systems
 
 I swear I read somewhere that for a pipe schedule system you do not 
 need to add hose allowance, Am I nuts?
 
 
 
 Brian Harris
 
 First Defense Fire Protection
 
 11957 Ramah Church Road
 
 Huntersville, NC 28078
 
 Phone: 704.948.3506
 
 Fax: 704.948.3507
 
 Nicet # 128476
 
 
 
 
 
 
 
 ===
 Email scanned by PC Tools - No viruses or spyware found.
 (Email Guard: 7.0.0.21, Virus/Spyware Database: 6.15890) 
 http://www.pctools.com/ === 
 ___
 Sprinklerforum mailing list
 Sprinklerforum@firesprinkler.org
 http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
 
 For Technical Assistance, send an email to: supp...@firesprinkler.org
 
 To Unsubscribe, send an email 
 to:sprinklerforum-requ...@firesprinkler.org
 (Put the word unsubscribe in the subject field) 
 ___
 Sprinklerforum mailing list
 Sprinklerforum@firesprinkler.org
 http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
 
 For Technical Assistance, send an email to: supp...@firesprinkler.org
 
 To Unsubscribe, send an email 
 to:sprinklerforum-requ...@firesprinkler.org
 (Put the word unsubscribe in the subject field)
 
 
 
 
 
 ===
 Email scanned by PC Tools - No viruses or spyware found.
 (Email Guard: 7.0.0.21, Virus/Spyware Database: 6.15890) 
 http://www.pctools.com/ ===
 
 
 
 
 
 ===
 Email scanned by PC Tools - No viruses or spyware found.
 (Email Guard: 7.0.0.21, Virus/Spyware Database: 6.15890) 
 http://www.pctools.com/ === 
 ___
 Sprinklerforum mailing list
 Sprinklerforum@firesprinkler.org
 http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

Re: Pipe Schedule Systems

2010-09-16 Thread Ron Greenman
And what is the C factor of any given system but a guess? I just saw a
picture of a relatively new system (five years) that had complete
clogging of some pipes. C = 0? I'm surprised your AHJ didn't make you
calculate for each pipe one diameter smaller than the installed size
so as to adjust for age shrinkage.

On Thu, Sep 16, 2010 at 9:23 AM, Thom tmcma...@firetechinc.com wrote:

 Then there's always the question of what C factor to use in your calc's of
 an old PS system? Have you seen the inside of these pipes? Do you use 120 or
 100 or maybe even 80? There is really no guide on what's appropriate. I had
 one AHJ that just wanted the calc to fail, and required that we use a C of
 80, when that calc still worked, he said oh I meant 60.
 There was a fight but we ended up doing an internal inspection of the pipe
 and he accepted the calc that used 80. (Still just a guess on his part.)

 Thom

 ___
 Sprinklerforum mailing list
 Sprinklerforum@firesprinkler.org
 http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

 For Technical Assistance, send an email to: supp...@firesprinkler.org

 To Unsubscribe, send an email to:sprinklerforum-requ...@firesprinkler.org
 (Put the word unsubscribe in the subject field)




-- 
Ron Greenman
Instructor
Fire Protection Engineering Technology
Bates Technical College
1101 So. Yakima Ave.
Tacoma, WA 98405

rgreen...@bates.ctc.edu

http://www.bates.ctc.edu/fireprotection/

253.680.7346
253.576.9700 (cell)

Member:
AFSA, SFPE, ASCET, NFPA, NFSA, AFAA, ASEE, NIBS, WSAFM, WFC

They are happy men whose natures sort with their vocations. -Francis
Bacon, essayist, philosopher, and statesman (1561-1626)
___
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: supp...@firesprinkler.org

To Unsubscribe, send an email to:sprinklerforum-requ...@firesprinkler.org
(Put the word unsubscribe in the subject field)


RE: Pipe Schedule Systems

2010-09-16 Thread Matthew J. Willis
C value for new steel 140, we use 120 Wet, 100 Dry to allow for age. There
are systems out there approaching 30 years that were calculated (+/-). I
wonder the condition of these. Was the 120/100 used correct? I would think
not based on the inside of piping I have seen over the years. The flushing
required by 25 is a good starting point to control this. At what point
though do we consider the C worse that the allotted for aging?

R/
Matt 

 

Matthew J. Willis, CET
Automatic Fire Sprinklers
Norred Fire Systems L.L.C.
318-387-1134 Voice
318-816-1087 Mobile
318-387-1163 Facsimile
m...@norredfire.com

 -Original Message-
 From: sprinklerforum-boun...@firesprinkler.org [mailto:sprinklerforum-
 boun...@firesprinkler.org] On Behalf Of Ron Greenman
 Sent: Thursday, September 16, 2010 11:30 AM
 To: sprinklerforum@firesprinkler.org
 Subject: Re: Pipe Schedule Systems
 
 And what is the C factor of any given system but a guess? I just saw a
 picture of a relatively new system (five years) that had complete
 clogging of some pipes. C = 0? I'm surprised your AHJ didn't make you
 calculate for each pipe one diameter smaller than the installed size
 so as to adjust for age shrinkage.
 
 On Thu, Sep 16, 2010 at 9:23 AM, Thom tmcma...@firetechinc.com wrote:
 
  Then there's always the question of what C factor to use in your calc's
 of
  an old PS system? Have you seen the inside of these pipes? Do you use
 120 or
  100 or maybe even 80? There is really no guide on what's appropriate. I
 had
  one AHJ that just wanted the calc to fail, and required that we use a C
 of
  80, when that calc still worked, he said oh I meant 60.
  There was a fight but we ended up doing an internal inspection of the
 pipe
  and he accepted the calc that used 80. (Still just a guess on his
 part.)
 
  Thom
 
  ___
  Sprinklerforum mailing list
  Sprinklerforum@firesprinkler.org
  http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
 
  For Technical Assistance, send an email to: supp...@firesprinkler.org
 
  To Unsubscribe, send an email to:Sprinklerforum-
 requ...@firesprinkler.org
  (Put the word unsubscribe in the subject field)
 
 
 
 
 --
 Ron Greenman
 Instructor
 Fire Protection Engineering Technology
 Bates Technical College
 1101 So. Yakima Ave.
 Tacoma, WA 98405
 
 rgreen...@bates.ctc.edu
 
 http://www.bates.ctc.edu/fireprotection/
 
 253.680.7346
 253.576.9700 (cell)
 
 Member:
 AFSA, SFPE, ASCET, NFPA, NFSA, AFAA, ASEE, NIBS, WSAFM, WFC
 
 They are happy men whose natures sort with their vocations. -Francis
 Bacon, essayist, philosopher, and statesman (1561-1626)
 ___
 Sprinklerforum mailing list
 Sprinklerforum@firesprinkler.org
 http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
 
 For Technical Assistance, send an email to: supp...@firesprinkler.org
 
 To Unsubscribe, send an email to:sprinklerforum-requ...@firesprinkler.org
 (Put the word unsubscribe in the subject field)
 No virus found in this incoming message.
 Checked by AVG - www.avg.com
 Version: 9.0.851 / Virus Database: 271.1.1/3137 - Release Date: 09/16/10
 01:34:00

___
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: supp...@firesprinkler.org

To Unsubscribe, send an email to:sprinklerforum-requ...@firesprinkler.org
(Put the word unsubscribe in the subject field)


Re: Pipe Schedule Systems

2010-09-16 Thread Ron Greenman
Chris,

But if this isn't the case, or if there's no criteria to assume extra
corrosion then you just use what the code says. If you expect extra
corrosion you have to look, and then, as Thom says, what is the
arbitrary value you assign to C? And, if as I said in my first comment
in this thread, schedules always are always based on empirical results
of what has been observed to work and not work over time with
allowance for the worst cases (those that didn't work) then most
things end up over built when building to a schedule. Back in the
early days of Friedrich Grinnell and John Wormald maximum coverage per
head for ordinary hazard was 90 sqft and extra hazard was 60 sqft. We
all know 3/4 pipe was used. Hopefully we all know that 52K and 40K
maximum per system are based on how high the pipe schedule went. That
the bell was by the FDC not so the FDC could be found but because the
WMG was the ONLY alarm device, that it was cheapest to put it as close
to the riser as possible, that it was cheapest to put the FDC as close
to the riser as possible and so the bell and FDC were in the same spot
for economic reasons. As you've said many times the AHJ can't just
decide something based on whim.

On Thu, Sep 16, 2010 at 9:28 AM, Chris Cahill fpech...@embarqmail.com wrote:
 Not entirely George.  Was the pipe schedule appropriate for the hazard when
 installed?  Has the commodity changed?  Odds are if it is PS it's old thus
 there have been many changes that rightfully should be investigated.  You
 wouldn't be surprised how many old systems had no correlation to any
 standard on how to protect a hazard.  I ran in to this often and always gave
 the owner (through his reps) a chance to show when it was installed 13,
 231c, FM or anything else this was the appropriate installation.

 Chris

 -Original Message-
 From: sprinklerforum-boun...@firesprinkler.org
 [mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of George Church
 Sent: Thursday, September 16, 2010 9:20 AM
 To: sprinklerforum@firesprinkler.org; st...@protectiondesign.com
 Subject: RE: Pipe Schedule Systems

 Sounds like the AHJ may be overstepping his boundries. Additions to Pipe
 schedule systems are allowed without calcs in #13.

 -Original Message-
 From: sprinklerforum-boun...@firesprinkler.org
 [mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of steve
 Sent: Thursday, September 16, 2010 10:10 AM
 To: AFSA
 Subject: Re: Pipe Schedule Systems

 The standard requires a minimum pressure be available at the highest/most
 remote sprinkler - is that the calc that's been requested?   Still no
 requirement for a hose allowance though.

 Steve


 Sent from my Verizon Wireless BlackBerry

 -Original Message-
 From: Matthew J. Willis m...@norredfire.com
 Sender: sprinklerforum-boun...@firesprinkler.org
 Date: Thu, 16 Sep 2010 08:59:48
 To: sprinklerforum@firesprinkler.org
 Reply-To: sprinklerforum@firesprinkler.org
 Subject: RE: Pipe Schedule Systems

 Then it will no longer be a pipe schedule, but a calculated system. Which
 requires hose streams.

 R/
 Matt





 Matthew J. Willis, CET
 Automatic Fire Sprinklers
 Norred Fire Systems L.L.C.
 318-387-1134 Voice
 318-816-1087 Mobile
 318-387-1163 Facsimile
 m...@norredfire.com
 -Original Message-
 From: sprinklerforum-boun...@firesprinkler.org
 [mailto:sprinklerforum- boun...@firesprinkler.org] On Behalf Of Brian
 Harris
 Sent: Thursday, September 16, 2010 8:57 AM
 To: sprinklerforum@firesprinkler.org
 Subject: RE: Pipe Schedule Systems
 
 David-
 We are doing some minor work to an existing warehouse that was done
 with the pipe schedule method. Now the AHJ wants us to provide
 hydraulic calc's to show him if the existing system will work.
 
 Brian Harris
 FDFP Inc.
 
 -Original Message-
 From: sprinklerforum-boun...@firesprinkler.org
 [mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of Autry,
 David
 Sent: Thursday, September 16, 2010 9:39 AM
 To: sprinklerforum@firesprinkler.org
 Subject: RE: Pipe Schedule Systems
 
 What exactly would you add it to?
 
 David Autry
 Plans Examiner
 Nebraska State Fire Marshal's Office
 246 S. 14th Street
 Lincoln, NE 68508
 402-471-9659
 402-471-3118 fax
 www.sfm.ne.gov
 
 ** Note new email address: david.au...@nebraska.gov
 
 -Original Message-
 From: sprinklerforum-boun...@firesprinkler.org
 [mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of Brian
 Harris
 Sent: Thursday, September 16, 2010 8:36 AM
 To: sprinklerforum@firesprinkler.org
 Subject: Pipe Schedule Systems
 
 I swear I read somewhere that for a pipe schedule system you do not
 need to add hose allowance, Am I nuts?
 
 
 
 Brian Harris
 
 First Defense Fire Protection
 
 11957 Ramah Church Road
 
 Huntersville, NC 28078
 
 Phone: 704.948.3506
 
 Fax: 704.948.3507
 
 Nicet # 128476
 
 
 
 
 
 
 
 ===
 Email scanned by PC Tools - No viruses or spyware found.
 (Email Guard: 7.0.0.21, Virus/Spyware Database: 6.15890)
 http