Re: day of questions - Hangars

2015-01-29 Thread Travis Mack
Definitely Air Force project.  Reviewer claims that since NFPA 409 says 
to do design and installation according to NFPA 13, he is claiming the 
30% increase is mandatory.  Any specific standard or code that I can 
refute this? It was never specified.  Just a reviewer comment.  
Contractor doesn't want to eat material increases due to this comment - 
as you can imagine.


Travis Mack, SET
MFP Design, LLC
2508 E Lodgepole Drive
Gilbert, AZ 85298
480-505-9271
fax: 866-430-6107
email:tm...@mfpdesign.com

http://www.mfpdesign.com
https://www.facebook.com/pages/MFP-Design-LLC/92218417692
Send large files to us via: https://www.hightail.com/u/MFPDesign

On 1/29/2015 12:19 PM, Cahill, Christopher wrote:

Assuming Air Force definitely no increase. 99% sure no increase in Navy and 
NFPA 409.

In all cases NFPA 13 defers design to other standards.  Those standards say 
nothing about increases.

But if specified for increase then its a contractual issue not a code issue.

Chris Cahill
Fire Protection Engineer
Burns  McDonnell
952-656-3652
ccah...@burnsmcd.com


 Original message 
From: Travis Mack
Date:01/29/2015 11:12 AM (GMT-08:00)
To: sprinklerforum@lists.firesprinkler.org
Subject: day of questions - Hangars

Does the 30% design area increase apply to an aircraft hangar that has a
roof slope in excess of 2:12?  Had a job that was specified with a given
density/area.  A new reviewer is requesting a 30% increase to design
area for slope.  This particular project also has a HiEx foam system as
well.

--
Travis Mack, SET
MFP Design, LLC
2508 E Lodgepole Drive
Gilbert, AZ 85298
480-505-9271
fax: 866-430-6107
email:tm...@mfpdesign.com

http://www.mfpdesign.com
https://www.facebook.com/pages/MFP-Design-LLC/92218417692
Send large files to us via: https://www.hightail.com/u/MFPDesign

___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org


___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org


RE: day of questions - Hangars

2015-01-29 Thread Cahill, Christopher
Assuming Air Force definitely no increase. 99% sure no increase in Navy and 
NFPA 409.

In all cases NFPA 13 defers design to other standards.  Those standards say 
nothing about increases.

But if specified for increase then its a contractual issue not a code issue.

Chris Cahill
Fire Protection Engineer
Burns  McDonnell
952-656-3652
ccah...@burnsmcd.com


 Original message 
From: Travis Mack
Date:01/29/2015 11:12 AM (GMT-08:00)
To: sprinklerforum@lists.firesprinkler.org
Subject: day of questions - Hangars

Does the 30% design area increase apply to an aircraft hangar that has a
roof slope in excess of 2:12?  Had a job that was specified with a given
density/area.  A new reviewer is requesting a 30% increase to design
area for slope.  This particular project also has a HiEx foam system as
well.

--
Travis Mack, SET
MFP Design, LLC
2508 E Lodgepole Drive
Gilbert, AZ 85298
480-505-9271
fax: 866-430-6107
email:tm...@mfpdesign.com

http://www.mfpdesign.com
https://www.facebook.com/pages/MFP-Design-LLC/92218417692
Send large files to us via: https://www.hightail.com/u/MFPDesign

___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org


RE: day of questions - Hangars

2015-01-29 Thread Cahill, Christopher
NFPA 409 is not applicable to Air Force. See first few pages of Etl 02-15.


Chris Cahill
Fire Protection Engineer
Burns  McDonnell
952-656-3652
ccah...@burnsmcd.com


 Original message 
From: Travis Mack
Date:01/29/2015 11:23 AM (GMT-08:00)
To: sprinklerforum@lists.firesprinkler.org
Subject: Re: day of questions - Hangars

Definitely Air Force project.  Reviewer claims that since NFPA 409 says
to do design and installation according to NFPA 13, he is claiming the
30% increase is mandatory.  Any specific standard or code that I can
refute this? It was never specified.  Just a reviewer comment.
Contractor doesn't want to eat material increases due to this comment -
as you can imagine.

Travis Mack, SET
MFP Design, LLC
2508 E Lodgepole Drive
Gilbert, AZ 85298
480-505-9271
fax: 866-430-6107
email:tm...@mfpdesign.com

http://www.mfpdesign.com
https://www.facebook.com/pages/MFP-Design-LLC/92218417692
Send large files to us via: https://www.hightail.com/u/MFPDesign

On 1/29/2015 12:19 PM, Cahill, Christopher wrote:
 Assuming Air Force definitely no increase. 99% sure no increase in Navy and 
 NFPA 409.

 In all cases NFPA 13 defers design to other standards.  Those standards say 
 nothing about increases.

 But if specified for increase then its a contractual issue not a code issue.

 Chris Cahill
 Fire Protection Engineer
 Burns  McDonnell
 952-656-3652
 ccah...@burnsmcd.com


  Original message 
 From: Travis Mack
 Date:01/29/2015 11:12 AM (GMT-08:00)
 To: sprinklerforum@lists.firesprinkler.org
 Subject: day of questions - Hangars

 Does the 30% design area increase apply to an aircraft hangar that has a
 roof slope in excess of 2:12?  Had a job that was specified with a given
 density/area.  A new reviewer is requesting a 30% increase to design
 area for slope.  This particular project also has a HiEx foam system as
 well.

 --
 Travis Mack, SET
 MFP Design, LLC
 2508 E Lodgepole Drive
 Gilbert, AZ 85298
 480-505-9271
 fax: 866-430-6107
 email:tm...@mfpdesign.com

 http://www.mfpdesign.com
 https://www.facebook.com/pages/MFP-Design-LLC/92218417692
 Send large files to us via: https://www.hightail.com/u/MFPDesign

 ___
 Sprinklerforum mailing list
 Sprinklerforum@lists.firesprinkler.org
 http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
 ___
 Sprinklerforum mailing list
 Sprinklerforum@lists.firesprinkler.org
 http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org


RE: day of questions - Hangars

2015-01-29 Thread Mark A. Sornsin, P.E.
Chris - The ETL references NFPA 13  409 at the beginning; then under the 
sprinkler design section (A1.3.1.1) it references NFPA 13. I don't see a 
statement NOT to increase design areas (though my experience has been that we 
do not on these Air Force jobs - just don't recall under what authority).

Mark A. Sornsin, P.E. | Karges-Faulconbridge, Inc. | Fire Protection Engineer | 
Fargo, ND | direct: 701.552.9905 | mobile: 701.371.5759 | 
http://www.kfiengineers.com

-Original Message-
From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On 
Behalf Of Cahill, Christopher
Sent: Thursday, January 29, 2015 1:28 PM
To: sprinklerforum@lists.firesprinkler.org
Subject: RE: day of questions - Hangars

NFPA 409 is not applicable to Air Force. See first few pages of Etl 02-15.


Chris Cahill
Fire Protection Engineer
Burns  McDonnell
952-656-3652
ccah...@burnsmcd.com


 Original message 
From: Travis Mack
Date:01/29/2015 11:23 AM (GMT-08:00)
To: sprinklerforum@lists.firesprinkler.org
Subject: Re: day of questions - Hangars

Definitely Air Force project.  Reviewer claims that since NFPA 409 says to do 
design and installation according to NFPA 13, he is claiming the 30% increase 
is mandatory.  Any specific standard or code that I can refute this? It was 
never specified.  Just a reviewer comment.
Contractor doesn't want to eat material increases due to this comment - as you 
can imagine.

Travis Mack, SET
MFP Design, LLC
2508 E Lodgepole Drive
Gilbert, AZ 85298
480-505-9271
fax: 866-430-6107
email:tm...@mfpdesign.com

http://www.mfpdesign.com
https://www.facebook.com/pages/MFP-Design-LLC/92218417692
Send large files to us via: https://www.hightail.com/u/MFPDesign

On 1/29/2015 12:19 PM, Cahill, Christopher wrote:
 Assuming Air Force definitely no increase. 99% sure no increase in Navy and 
 NFPA 409.

 In all cases NFPA 13 defers design to other standards.  Those standards say 
 nothing about increases.

 But if specified for increase then its a contractual issue not a code issue.

 Chris Cahill
 Fire Protection Engineer
 Burns  McDonnell
 952-656-3652
 ccah...@burnsmcd.com


  Original message 
 From: Travis Mack
 Date:01/29/2015 11:12 AM (GMT-08:00)
 To: sprinklerforum@lists.firesprinkler.org
 Subject: day of questions - Hangars

 Does the 30% design area increase apply to an aircraft hangar that has
 a roof slope in excess of 2:12?  Had a job that was specified with a
 given density/area.  A new reviewer is requesting a 30% increase to
 design area for slope.  This particular project also has a HiEx foam
 system as well.

 --
 Travis Mack, SET
 MFP Design, LLC
 2508 E Lodgepole Drive
 Gilbert, AZ 85298
 480-505-9271
 fax: 866-430-6107
 email:tm...@mfpdesign.com

 http://www.mfpdesign.com
 https://www.facebook.com/pages/MFP-Design-LLC/92218417692
 Send large files to us via: https://www.hightail.com/u/MFPDesign

 ___
 Sprinklerforum mailing list
 Sprinklerforum@lists.firesprinkler.org
 http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkl
 er.org ___
 Sprinklerforum mailing list
 Sprinklerforum@lists.firesprinkler.org
 http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkl
 er.org

___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

__
This email has been scanned by the Symantec Email Security.cloud service.
For more information please visit http://www.symanteccloud.com 
__

__
This email has been scanned by the Symantec Email Security.cloud service.
For more information please visit http://www.symanteccloud.com
__
___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org


RE: day of questions - Hangars

2015-01-29 Thread Marc Walter, SET
Travis,

I don't have a 409 in front of me, but I am looking at the NFPA site and the
Second Draft Report that is available. In section 6.2.4.5.1 it cites  The
design area of the closed head water sprinkler system shall not be required
to be increased for ceiling slope.

If you have a current 409, check out that section and see if reads the same.

Marc Walter
Sprinkler Design Services
(503) 956-4019

-Original Message-
From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org]
On Behalf Of Travis Mack
Sent: Thursday, January 29, 2015 11:52 AM
To: sprinklerforum@lists.firesprinkler.org
Subject: Re: day of questions - Hangars

 From the ETL:

Sprinkler protection must be designed for the occupancy hazard present in
accordance with this ETL, UFC 3-600-01, NFPA 33, and the following NFPA
standards (if there is a conflict between this ETL and any provisions of an
NFPA standard or code, this ETL will take
precedence):

It gives a specific criteria of 0.2/5000 in this case.  Would that be able
to take precedence over any modifications that NFPA 13 may require?

Travis Mack, SET
MFP Design, LLC
2508 E Lodgepole Drive
Gilbert, AZ 85298
480-505-9271
fax: 866-430-6107
email:tm...@mfpdesign.com

http://www.mfpdesign.com
https://www.facebook.com/pages/MFP-Design-LLC/92218417692
Send large files to us via: https://www.hightail.com/u/MFPDesign

On 1/29/2015 12:49 PM, Mark A. Sornsin, P.E. wrote:
 Chris - The ETL references NFPA 13  409 at the beginning; then under the
sprinkler design section (A1.3.1.1) it references NFPA 13. I don't see a
statement NOT to increase design areas (though my experience has been that
we do not on these Air Force jobs - just don't recall under what authority).

 Mark A. Sornsin, P.E. | Karges-Faulconbridge, Inc. | Fire Protection 
 Engineer | Fargo, ND | direct: 701.552.9905 | mobile: 701.371.5759 | 
 http://www.kfiengineers.com

 -Original Message-
 From: Sprinklerforum 
 [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On Behalf Of 
 Cahill, Christopher
 Sent: Thursday, January 29, 2015 1:28 PM
 To: sprinklerforum@lists.firesprinkler.org
 Subject: RE: day of questions - Hangars

 NFPA 409 is not applicable to Air Force. See first few pages of Etl 02-15.


 Chris Cahill
 Fire Protection Engineer
 Burns  McDonnell
 952-656-3652
 ccah...@burnsmcd.com


  Original message 
 From: Travis Mack
 Date:01/29/2015 11:23 AM (GMT-08:00)
 To: sprinklerforum@lists.firesprinkler.org
 Subject: Re: day of questions - Hangars

 Definitely Air Force project.  Reviewer claims that since NFPA 409 says to
do design and installation according to NFPA 13, he is claiming the 30%
increase is mandatory.  Any specific standard or code that I can refute
this? It was never specified.  Just a reviewer comment.
 Contractor doesn't want to eat material increases due to this comment - as
you can imagine.

 Travis Mack, SET
 MFP Design, LLC
 2508 E Lodgepole Drive
 Gilbert, AZ 85298
 480-505-9271
 fax: 866-430-6107
 email:tm...@mfpdesign.com

 http://www.mfpdesign.com
 https://www.facebook.com/pages/MFP-Design-LLC/92218417692
 Send large files to us via: https://www.hightail.com/u/MFPDesign

 On 1/29/2015 12:19 PM, Cahill, Christopher wrote:
 Assuming Air Force definitely no increase. 99% sure no increase in Navy
and NFPA 409.

 In all cases NFPA 13 defers design to other standards.  Those standards
say nothing about increases.

 But if specified for increase then its a contractual issue not a code
issue.

 Chris Cahill
 Fire Protection Engineer
 Burns  McDonnell
 952-656-3652
 ccah...@burnsmcd.com


  Original message 
 From: Travis Mack
 Date:01/29/2015 11:12 AM (GMT-08:00)
 To: sprinklerforum@lists.firesprinkler.org
 Subject: day of questions - Hangars

 Does the 30% design area increase apply to an aircraft hangar that 
 has a roof slope in excess of 2:12?  Had a job that was specified 
 with a given density/area.  A new reviewer is requesting a 30% 
 increase to design area for slope.  This particular project also has 
 a HiEx foam system as well.

 --
 Travis Mack, SET
 MFP Design, LLC
 2508 E Lodgepole Drive
 Gilbert, AZ 85298
 480-505-9271
 fax: 866-430-6107
 email:tm...@mfpdesign.com

 http://www.mfpdesign.com
 https://www.facebook.com/pages/MFP-Design-LLC/92218417692
 Send large files to us via: https://www.hightail.com/u/MFPDesign

 ___
 Sprinklerforum mailing list
 Sprinklerforum@lists.firesprinkler.org
 http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprink
 l er.org ___
 Sprinklerforum mailing list
 Sprinklerforum@lists.firesprinkler.org
 http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprink
 l
 er.org
 ___
 Sprinklerforum mailing list
 Sprinklerforum@lists.firesprinkler.org
 http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkl
 er.org

RE: day of questions - Hangars

2015-01-29 Thread Bill Brooks
I specify the area increase for the excessive slope.

Bill Brooks

-Original Message-
From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org]
On Behalf Of Scott A Futrell
Sent: Thursday, January 29, 2015 2:59 PM
To: sprinklerforum@lists.firesprinkler.org
Subject: RE: day of questions - Hangars

This must be one of those design features of a hangar where the fire, the
building and the sprinkler system realize it isn't a NFPA 13 design and the
sprinklers operate differently (quicker and more effectively) with a slope
exceeding 2 in 12 then they do for a sprinkler system installed in a
different building with a slope exceeding 2 in 12, right?

We always require the thirty percent increase because why would it be any
different unless the original specified design area included the increase
already?

Scott
 
Office: (763) 425-1001x12
Cell: (612) 759-5556

-Original Message-
From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org]
On Behalf Of Mark A. Sornsin, P.E.
Sent: Thursday, January 29, 2015 1:50 PM
To: sprinklerforum@lists.firesprinkler.org
Subject: RE: day of questions - Hangars

Chris - The ETL references NFPA 13  409 at the beginning; then under the
sprinkler design section (A1.3.1.1) it references NFPA 13. I don't see a
statement NOT to increase design areas (though my experience has been that
we do not on these Air Force jobs - just don't recall under what authority).

Mark A. Sornsin, P.E. | Karges-Faulconbridge, Inc. | Fire Protection
Engineer | Fargo, ND | direct: 701.552.9905 | mobile: 701.371.5759 |
http://www.kfiengineers.com


___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org


Re: day of questions - Hangars

2015-01-29 Thread Travis Mack
That is exactly what I am trying to determine.  Based on the 2nd draft 
report that indicates a new section of 6.2.4.5.1, it seems that is 
exactly the case.  However, my contractor would like to be certain 
before we go and make changes or not.


Now, there are definite differences in the design areas and densities 
required in 409 and the ETL.  So, this is just left in the middle.  Is 
the specific criteria given in the ETL just what it says and no 
application for slope is needed?  Do we use the 2nd draft proposal as an 
intent to what the 409 committee intended? Does that section even 
apply?  These are where the questions arise.


I have done quite a few hangars where the criteria has been outlined as 
was on this project.  A slope modifier was not applied as the criteria 
was specifically given.  So, I am just trying to get to the 
justification if we have to increase the slope or not. So far, it seems 
to be 50/50 in responses.


It turns out we just got a reply (while I was typing this novel and 
taking phone calls) from this reviewer when approached with the 
6.2.4.5.1 that he agrees with that statement and no increase is needed 
for this project.


Travis Mack, SET
MFP Design, LLC
2508 E Lodgepole Drive
Gilbert, AZ 85298
480-505-9271
fax: 866-430-6107
email:tm...@mfpdesign.com

http://www.mfpdesign.com
https://www.facebook.com/pages/MFP-Design-LLC/92218417692
Send large files to us via: https://www.hightail.com/u/MFPDesign

On 1/29/2015 1:15 PM, Mark A. Sornsin, P.E. wrote:

Scott, I think if there is an allowance to not increase the area due to slope, 
it is specifically because it has already been figured into the design in some 
way. That's ultimately what we're trying to confirm.

Mark A. Sornsin, P.E. | Karges-Faulconbridge, Inc. | Fire Protection Engineer | 
Fargo, ND | direct: 701.552.9905 | mobile: 701.371.5759 | 
http://www.kfiengineers.com

-Original Message-
From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On 
Behalf Of Scott A Futrell
Sent: Thursday, January 29, 2015 1:59 PM
To: sprinklerforum@lists.firesprinkler.org
Subject: RE: day of questions - Hangars

This must be one of those design features of a hangar where the fire, the 
building and the sprinkler system realize it isn't a NFPA 13 design and the 
sprinklers operate differently (quicker and more effectively) with a slope 
exceeding 2 in 12 then they do for a sprinkler system installed in a different 
building with a slope exceeding 2 in 12, right?

We always require the thirty percent increase because why would it be any 
different unless the original specified design area included the increase 
already?

Scott

Office: (763) 425-1001x12
Cell: (612) 759-5556




___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org


RE: day of questions - Hangars

2015-01-29 Thread Mark A. Sornsin, P.E.
Scott, I think if there is an allowance to not increase the area due to slope, 
it is specifically because it has already been figured into the design in some 
way. That's ultimately what we're trying to confirm.

Mark A. Sornsin, P.E. | Karges-Faulconbridge, Inc. | Fire Protection Engineer | 
Fargo, ND | direct: 701.552.9905 | mobile: 701.371.5759 | 
http://www.kfiengineers.com

-Original Message-
From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On 
Behalf Of Scott A Futrell
Sent: Thursday, January 29, 2015 1:59 PM
To: sprinklerforum@lists.firesprinkler.org
Subject: RE: day of questions - Hangars

This must be one of those design features of a hangar where the fire, the 
building and the sprinkler system realize it isn't a NFPA 13 design and the 
sprinklers operate differently (quicker and more effectively) with a slope 
exceeding 2 in 12 then they do for a sprinkler system installed in a different 
building with a slope exceeding 2 in 12, right?

We always require the thirty percent increase because why would it be any 
different unless the original specified design area included the increase 
already?

Scott

Office: (763) 425-1001x12
Cell: (612) 759-5556

-Original Message-
From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On 
Behalf Of Mark A. Sornsin, P.E.
Sent: Thursday, January 29, 2015 1:50 PM
To: sprinklerforum@lists.firesprinkler.org
Subject: RE: day of questions - Hangars

Chris - The ETL references NFPA 13  409 at the beginning; then under the 
sprinkler design section (A1.3.1.1) it references NFPA 13. I don't see a 
statement NOT to increase design areas (though my experience has been that we 
do not on these Air Force jobs - just don't recall under what authority).

Mark A. Sornsin, P.E. | Karges-Faulconbridge, Inc. | Fire Protection Engineer | 
Fargo, ND | direct: 701.552.9905 | mobile: 701.371.5759 | 
http://www.kfiengineers.com


___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

__
This email has been scanned by the Symantec Email Security.cloud service.
For more information please visit http://www.symanteccloud.com 
__

__
This email has been scanned by the Symantec Email Security.cloud service.
For more information please visit http://www.symanteccloud.com
__
___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org


RE: day of questions - Hangars

2015-01-29 Thread Cahill, Christopher
NFPA 13 - 11.2.3.2.1.1 The water supply requirement for sprinklers only shall 
be calculated from the density/area curves of Figure 11.2.3.1.1 or from Chapter 
22 where density/area criteria are specified for special occupancy hazards.

11.2.3.2.4 Sloped Ceilings. The system area of operation shall be increased by 
30 percent without revising the density when the following types of sprinklers 
are used on sloped ceilings with a
pitch exceeding 1 in 6 (a rise of 2 units in a run of 12 units, a roof slope of 
16.7 percent) in nonstorage applications:

(1) Spray sprinklers, including extended coverage sprinklers listed in 
accordance with 8.4.3(4), and quick-response sprinklers
(2) CMSA sprinklers

I think you have it backwards my friend.  You need a statement TO increase the 
area.  The above section tell you when to increase.  You didn't select a design 
from 11.2.3.1.1.  Think of it like all the other special applications, ESFR, 
residential, largest room, corridors,you can't get to 11.2.3.2.4 without 
going through 11.2.3.2.1.1. It's also not unlike 13R where you use the hanging 
and calculation methods from 13 but not the design approaches. 

As far as using NFPA 409 ETL 02-15 says This ETL is the Air Force alternative 
to NFPA Standard 409, and will be used except as noted. Attachment 1 provides 
criteria and technical guidance. The only exceptions I know of are for certain 
types of planes (think Cessna's).

Navy is a little different in they say use 409 except as modified in UFC 
4-211-10N.

Army - let's move on.  

Chris Cahill, PE*
Associate Fire Protection Engineer 
Burns  McDonnell
Phone:  952.656.3652
Fax:  952.229.2923
ccah...@burnsmcd.com
www.burnsmcd.com
*Registered in: MN


Proud to be #14 on FORTUNE's 2014 List of 100 Best Companies to Work For

-Original Message-
From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On 
Behalf Of Mark A. Sornsin, P.E.
Sent: Thursday, January 29, 2015 1:50 PM
To: sprinklerforum@lists.firesprinkler.org
Subject: RE: day of questions - Hangars

Chris - The ETL references NFPA 13  409 at the beginning; then under the 
sprinkler design section (A1.3.1.1) it references NFPA 13. I don't see a 
statement NOT to increase design areas (though my experience has been that we 
do not on these Air Force jobs - just don't recall under what authority).

Mark A. Sornsin, P.E. | Karges-Faulconbridge, Inc. | Fire Protection Engineer | 
Fargo, ND | direct: 701.552.9905 | mobile: 701.371.5759 | 
http://www.kfiengineers.com

-Original Message-
From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On 
Behalf Of Cahill, Christopher
Sent: Thursday, January 29, 2015 1:28 PM
To: sprinklerforum@lists.firesprinkler.org
Subject: RE: day of questions - Hangars

NFPA 409 is not applicable to Air Force. See first few pages of Etl 02-15.


Chris Cahill
Fire Protection Engineer
Burns  McDonnell
952-656-3652
ccah...@burnsmcd.com


 Original message 
From: Travis Mack
Date:01/29/2015 11:23 AM (GMT-08:00)
To: sprinklerforum@lists.firesprinkler.org
Subject: Re: day of questions - Hangars

Definitely Air Force project.  Reviewer claims that since NFPA 409 says to do 
design and installation according to NFPA 13, he is claiming the 30% increase 
is mandatory.  Any specific standard or code that I can refute this? It was 
never specified.  Just a reviewer comment.
Contractor doesn't want to eat material increases due to this comment - as you 
can imagine.

Travis Mack, SET
MFP Design, LLC
2508 E Lodgepole Drive
Gilbert, AZ 85298
480-505-9271
fax: 866-430-6107
email:tm...@mfpdesign.com

http://www.mfpdesign.com
https://www.facebook.com/pages/MFP-Design-LLC/92218417692
Send large files to us via: https://www.hightail.com/u/MFPDesign

On 1/29/2015 12:19 PM, Cahill, Christopher wrote:
 Assuming Air Force definitely no increase. 99% sure no increase in Navy and 
 NFPA 409.

 In all cases NFPA 13 defers design to other standards.  Those standards say 
 nothing about increases.

 But if specified for increase then its a contractual issue not a code issue.

 Chris Cahill
 Fire Protection Engineer
 Burns  McDonnell
 952-656-3652
 ccah...@burnsmcd.com


  Original message 
 From: Travis Mack
 Date:01/29/2015 11:12 AM (GMT-08:00)
 To: sprinklerforum@lists.firesprinkler.org
 Subject: day of questions - Hangars

 Does the 30% design area increase apply to an aircraft hangar that has 
 a roof slope in excess of 2:12?  Had a job that was specified with a 
 given density/area.  A new reviewer is requesting a 30% increase to 
 design area for slope.  This particular project also has a HiEx foam 
 system as well.

 --
 Travis Mack, SET
 MFP Design, LLC
 2508 E Lodgepole Drive
 Gilbert, AZ 85298
 480-505-9271
 fax: 866-430-6107
 email:tm...@mfpdesign.com

 http://www.mfpdesign.com
 https://www.facebook.com/pages/MFP-Design-LLC/92218417692
 Send large files to us via: https://www.hightail.com/u/MFPDesign

RE: day of questions - Hangars

2015-01-29 Thread Mark A. Sornsin, P.E.
Bill - as Chris just pointed out, The Air Force ETL (which this thread is 
discussing) references NFPA 13, but not for design densities. Because the ETL 
defines the design densities, you cannot get to the sloped ceiling requirements 
of NFPA 13 because they fall under the design densities section of 13, which we 
are not referencing. Apparently - absent the specific requirement by the ETL to 
increase design areas - the Air Force considers sloped ceiling to be a 
non-issue in a high-ex foam / overhead sprinkler system design (or that it is 
adequately addressed with the 5,000 sq.ft. design area).

Mark A. Sornsin, P.E. | Karges-Faulconbridge, Inc. | Fire Protection Engineer | 
Fargo, ND | direct: 701.552.9905 | mobile: 701.371.5759 | 
http://www.kfiengineers.com

-Original Message-
From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On 
Behalf Of Bill Brooks
Sent: Thursday, January 29, 2015 3:28 PM
To: sprinklerforum@lists.firesprinkler.org
Subject: RE: day of questions - Hangars

I specify the area increase for the excessive slope.

Bill Brooks

-Original Message-
From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org]
On Behalf Of Scott A Futrell
Sent: Thursday, January 29, 2015 2:59 PM
To: sprinklerforum@lists.firesprinkler.org
Subject: RE: day of questions - Hangars

This must be one of those design features of a hangar where the fire, the 
building and the sprinkler system realize it isn't a NFPA 13 design and the 
sprinklers operate differently (quicker and more effectively) with a slope 
exceeding 2 in 12 then they do for a sprinkler system installed in a different 
building with a slope exceeding 2 in 12, right?

We always require the thirty percent increase because why would it be any 
different unless the original specified design area included the increase 
already?

Scott

Office: (763) 425-1001x12
Cell: (612) 759-5556

-Original Message-
From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org]
On Behalf Of Mark A. Sornsin, P.E.
Sent: Thursday, January 29, 2015 1:50 PM
To: sprinklerforum@lists.firesprinkler.org
Subject: RE: day of questions - Hangars

Chris - The ETL references NFPA 13  409 at the beginning; then under the 
sprinkler design section (A1.3.1.1) it references NFPA 13. I don't see a 
statement NOT to increase design areas (though my experience has been that we 
do not on these Air Force jobs - just don't recall under what authority).

Mark A. Sornsin, P.E. | Karges-Faulconbridge, Inc. | Fire Protection Engineer | 
Fargo, ND | direct: 701.552.9905 | mobile: 701.371.5759 | 
http://www.kfiengineers.com


___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

__
This email has been scanned by the Symantec Email Security.cloud service.
For more information please visit http://www.symanteccloud.com 
__

__
This email has been scanned by the Symantec Email Security.cloud service.
For more information please visit http://www.symanteccloud.com
__
___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org


RE: day of questions - Hangars

2015-01-29 Thread Bill Brooks
Yes, I'm also referencing the ETL.  Have you had your opinion confirmed by
MED FPE?  I've never considered the ceiling slope provisions to be a density
issue.  So maybe I've been an overly conservative designer.

Bill Brooks 

-Original Message-
From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org]
On Behalf Of Mark A. Sornsin, P.E.
Sent: Thursday, January 29, 2015 4:41 PM
To: sprinklerforum@lists.firesprinkler.org
Subject: RE: day of questions - Hangars

Bill - as Chris just pointed out, The Air Force ETL (which this thread is
discussing) references NFPA 13, but not for design densities. Because the
ETL defines the design densities, you cannot get to the sloped ceiling
requirements of NFPA 13 because they fall under the design densities section
of 13, which we are not referencing. Apparently - absent the specific
requirement by the ETL to increase design areas - the Air Force considers
sloped ceiling to be a non-issue in a high-ex foam / overhead sprinkler
system design (or that it is adequately addressed with the 5,000 sq.ft.
design area).

Mark A. Sornsin, P.E. | Karges-Faulconbridge, Inc. | Fire Protection
Engineer | Fargo, ND | direct: 701.552.9905 | mobile: 701.371.5759 |
http://www.kfiengineers.com

-Original Message-
From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org]
On Behalf Of Bill Brooks
Sent: Thursday, January 29, 2015 3:28 PM
To: sprinklerforum@lists.firesprinkler.org
Subject: RE: day of questions - Hangars

I specify the area increase for the excessive slope.

Bill Brooks

-Original Message-
From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org]
On Behalf Of Scott A Futrell
Sent: Thursday, January 29, 2015 2:59 PM
To: sprinklerforum@lists.firesprinkler.org
Subject: RE: day of questions - Hangars

This must be one of those design features of a hangar where the fire, the
building and the sprinkler system realize it isn't a NFPA 13 design and the
sprinklers operate differently (quicker and more effectively) with a slope
exceeding 2 in 12 then they do for a sprinkler system installed in a
different building with a slope exceeding 2 in 12, right?

We always require the thirty percent increase because why would it be any
different unless the original specified design area included the increase
already?

Scott

Office: (763) 425-1001x12
Cell: (612) 759-5556

-Original Message-
From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org]
On Behalf Of Mark A. Sornsin, P.E.
Sent: Thursday, January 29, 2015 1:50 PM
To: sprinklerforum@lists.firesprinkler.org
Subject: RE: day of questions - Hangars

Chris - The ETL references NFPA 13  409 at the beginning; then under the
sprinkler design section (A1.3.1.1) it references NFPA 13. I don't see a
statement NOT to increase design areas (though my experience has been that
we do not on these Air Force jobs - just don't recall under what authority).

Mark A. Sornsin, P.E. | Karges-Faulconbridge, Inc. | Fire Protection
Engineer | Fargo, ND | direct: 701.552.9905 | mobile: 701.371.5759 |
http://www.kfiengineers.com


___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

__
This email has been scanned by the Symantec Email Security.cloud service.
For more information please visit http://www.symanteccloud.com
__

__
This email has been scanned by the Symantec Email Security.cloud service.
For more information please visit http://www.symanteccloud.com
__
___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org


RE: day of questions - Hangars

2015-01-29 Thread Cahill, Christopher
I can't tell you how or why I know this but this is a 95% assured position of 
none other than Fred Walker (Chief Air Force FPE):

4-4.5   Overhead Sprinkler System for Aircraft Storage and Servicing Areas.
Hydraulically design a system to provide 0.2 gpm/sq. ft. (8.0 L/min/sq. m) over 
the hydraulically most demanding 5,000 sq. ft. (465 sq. m) used for fueled 
aircraft. Do not increase design area for sloped ceilings or preaction systems.

I say 95% because he just retired end of December and anything could change 
between now and 100%. 

I've done a couple sloped hangars in the last few year and they were not 
increased, COE, TCX and Base reviewed.  

Chris Cahill, PE*
Associate Fire Protection Engineer 
Burns  McDonnell
Phone:  952.656.3652
Fax:  952.229.2923
ccah...@burnsmcd.com
www.burnsmcd.com
*Registered in: MN


Proud to be #14 on FORTUNE's 2014 List of 100 Best Companies to Work For


-Original Message-
From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On 
Behalf Of Bill Brooks
Sent: Thursday, January 29, 2015 5:41 PM
To: sprinklerforum@lists.firesprinkler.org
Subject: RE: day of questions - Hangars

Yes, I'm also referencing the ETL.  Have you had your opinion confirmed by MED 
FPE?  I've never considered the ceiling slope provisions to be a density issue. 
 So maybe I've been an overly conservative designer.

Bill Brooks 

-Original Message-
From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org]
On Behalf Of Mark A. Sornsin, P.E.
Sent: Thursday, January 29, 2015 4:41 PM
To: sprinklerforum@lists.firesprinkler.org
Subject: RE: day of questions - Hangars

Bill - as Chris just pointed out, The Air Force ETL (which this thread is
discussing) references NFPA 13, but not for design densities. Because the ETL 
defines the design densities, you cannot get to the sloped ceiling requirements 
of NFPA 13 because they fall under the design densities section of 13, which we 
are not referencing. Apparently - absent the specific requirement by the ETL to 
increase design areas - the Air Force considers sloped ceiling to be a 
non-issue in a high-ex foam / overhead sprinkler system design (or that it is 
adequately addressed with the 5,000 sq.ft.
design area).

Mark A. Sornsin, P.E. | Karges-Faulconbridge, Inc. | Fire Protection Engineer | 
Fargo, ND | direct: 701.552.9905 | mobile: 701.371.5759 | 
http://www.kfiengineers.com

-Original Message-
From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org]
On Behalf Of Bill Brooks
Sent: Thursday, January 29, 2015 3:28 PM
To: sprinklerforum@lists.firesprinkler.org
Subject: RE: day of questions - Hangars

I specify the area increase for the excessive slope.

Bill Brooks

-Original Message-
From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org]
On Behalf Of Scott A Futrell
Sent: Thursday, January 29, 2015 2:59 PM
To: sprinklerforum@lists.firesprinkler.org
Subject: RE: day of questions - Hangars

This must be one of those design features of a hangar where the fire, the 
building and the sprinkler system realize it isn't a NFPA 13 design and the 
sprinklers operate differently (quicker and more effectively) with a slope 
exceeding 2 in 12 then they do for a sprinkler system installed in a different 
building with a slope exceeding 2 in 12, right?

We always require the thirty percent increase because why would it be any 
different unless the original specified design area included the increase 
already?

Scott

Office: (763) 425-1001x12
Cell: (612) 759-5556

-Original Message-
From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org]
On Behalf Of Mark A. Sornsin, P.E.
Sent: Thursday, January 29, 2015 1:50 PM
To: sprinklerforum@lists.firesprinkler.org
Subject: RE: day of questions - Hangars

Chris - The ETL references NFPA 13  409 at the beginning; then under the 
sprinkler design section (A1.3.1.1) it references NFPA 13. I don't see a 
statement NOT to increase design areas (though my experience has been that we 
do not on these Air Force jobs - just don't recall under what authority).

Mark A. Sornsin, P.E. | Karges-Faulconbridge, Inc. | Fire Protection Engineer | 
Fargo, ND | direct: 701.552.9905 | mobile: 701.371.5759 | 
http://www.kfiengineers.com


___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

__
This email has been scanned by the Symantec Email Security.cloud service.
For more information please visit http://www.symanteccloud.com

Re: day of questions - Hangars

2015-01-29 Thread Roland Huggins
I agree with Mark and Chris so I guess that means I’m calling you overly 
conservative.  I’ve been called worse - lol.

I mainly piped in to comment that the Research Foundation just started a 
project to address developing criteria for sloped ceilings in storage.  If I 
were king for a day (or the soup nazi), I’d decree give me some in-racks and be 
done with it.  It’ll be interesting to see what comes out at the end.

Roland


Roland Huggins, PE - VP Engineering
American Fire Sprinkler Assn.   ---  Fire Sprinklers Saves Lives
Dallas, TX
http://www.firesprinkler.org http://www.firesprinkler.org/





 On Jan 29, 2015, at 3:41 PM, Bill Brooks bill.bro...@brooksfpe.com wrote:
 
 Yes, I'm also referencing the ETL.  Have you had your opinion confirmed by
 MED FPE?  I've never considered the ceiling slope provisions to be a density
 issue.  So maybe I've been an overly conservative designer.
 