 if I remember correctly, the issue is that the ground at the house is  
 not a real ground when the earth is frozen, as the resistance of frozen  
 earth goes up substantially over non-frozen earth. So it's like not having  
 grounded the wires at all.

Yes, that's why in Switzerland you have to bury the grounding loop/wires
at least 1m deep (IIRC), in cold areas even 1.5m deep(again IIRC) to ensure
that the earth never freezes.

I would have assumed that the building rules in the north have similar
requirements, just with deeper digging.

Of course, if you live on permafrost, you will never have a decent ground :-)
  
 This is a real issue for cables brought to the house (cable TV, telephone,  
 etc etc) as those cables are grounded somewhere else on the other side, and 
 thus  there may be 1000's or even 1's Volts between the two grounds, 
 even (or  especially) for just a proximity strike. As mentioned by someone 
 else, all bets  are off anyway's for direct hits, not much will survive a 
 direct hit.

Well.. if you have a near hit on some long cable. you're lucky if the
attached electronics survive. But it shouldn't kill everything in the
house. My point was that, with proper ground connection, your house
potential should increase to many 1000s of volt, even with a near hit.
Again, i might miss there something.

  
 It's been a long time since I designed cable TV receivers, but the specs  
 are here, and I think there are some explanations in there somewhere:
  
 _http://www.nordig.org/specifications.htm_ 
 (http://www.nordig.org/specifications.htm) 

Thanks, i'll have a look at those.

Attila Kinali

-- 
The trouble with you, Shev, is you don't say anything until you've saved
up a whole truckload of damned heavy brick arguments and then you dump
them all out and never look at the bleeding body mangled beneath the heap
-- Tirin, The Dispossessed, U. Le Guin

___
time-nuts mailing list -- time-nuts@febo.com
To unsubscribe, go to https://www.febo.com/cgi-bin/mailman/listinfo/time-nuts
and follow the instructions there.


Re: [time-nuts] Thoughts on lightning protection measures....

2012-04-13 Thread Chuck Harris

As the power line worker strapped to the million volt wires he is
working on shows, what is important is that all the grounds in the
house stay at the same potential... not that they stay at some
perfect earth ground potential.

It really doesn't matter if a house ground jumps up many
thousands of volts for an instant during a lightning strike, as
long as everything electronic in the house, and everything
structural in the house jumps too.

-Chuck Harris


Attila Kinali wrote:

Moin,

On Thu, 12 Apr 2012 18:28:24 -0400 (EDT)
saidj...@aol.com wrote:


if I remember correctly, the issue is that the ground at the house is
not a real ground when the earth is frozen, as the resistance of frozen
earth goes up substantially over non-frozen earth. So it's like not having
grounded the wires at all.


Yes, that's why in Switzerland you have to bury the grounding loop/wires
at least 1m deep (IIRC), in cold areas even 1.5m deep(again IIRC) to ensure
that the earth never freezes.

I would have assumed that the building rules in the north have similar
requirements, just with deeper digging.

Of course, if you live on permafrost, you will never have a decent ground :-)


This is a real issue for cables brought to the house (cable TV, telephone,
etc etc) as those cables are grounded somewhere else on the other side, and
thus  there may be 1000's or even 1's Volts between the two grounds,
even (or  especially) for just a proximity strike. As mentioned by someone
else, all bets  are off anyway's for direct hits, not much will survive a
direct hit.


Well.. if you have a near hit on some long cable. you're lucky if the
attached electronics survive. But it shouldn't kill everything in the
house. My point was that, with proper ground connection, your house
potential should increase to many 1000s of volt, even with a near hit.
Again, i might miss there something.



It's been a long time since I designed cable TV receivers, but the specs
are here, and I think there are some explanations in there somewhere:

_http://www.nordig.org/specifications.htm_
(http://www.nordig.org/specifications.htm)


Thanks, i'll have a look at those.

Attila Kinali



___
time-nuts mailing list -- time-nuts@febo.com
To unsubscribe, go to https://www.febo.com/cgi-bin/mailman/listinfo/time-nuts
and follow the instructions there.


Re: [time-nuts] Thoughts on lightning protection measures....

2012-04-13 Thread Bob Camp
Hi

Yes indeed, very true. 

Things like telephone lines and cable lines need to jump at the same time
as the house ground. The fact that they don't is what makes cordless phone
base stations, modems (remember them?) and cable boxes the main victims in
lightning hits.

Bob 

-Original Message-
From: time-nuts-boun...@febo.com [mailto:time-nuts-boun...@febo.com] On
Behalf Of Chuck Harris
Sent: Friday, April 13, 2012 9:14 AM
To: Discussion of precise time and frequency measurement
Subject: Re: [time-nuts] Thoughts on lightning protection measures

As the power line worker strapped to the million volt wires he is
working on shows, what is important is that all the grounds in the
house stay at the same potential... not that they stay at some
perfect earth ground potential.

It really doesn't matter if a house ground jumps up many
thousands of volts for an instant during a lightning strike, as
long as everything electronic in the house, and everything
structural in the house jumps too.

-Chuck Harris


Attila Kinali wrote:
 Moin,

 On Thu, 12 Apr 2012 18:28:24 -0400 (EDT)
 saidj...@aol.com wrote:

 if I remember correctly, the issue is that the ground at the house is
 not a real ground when the earth is frozen, as the resistance of frozen
 earth goes up substantially over non-frozen earth. So it's like not
having
 grounded the wires at all.

 Yes, that's why in Switzerland you have to bury the grounding loop/wires
 at least 1m deep (IIRC), in cold areas even 1.5m deep(again IIRC) to
ensure
 that the earth never freezes.

 I would have assumed that the building rules in the north have similar
 requirements, just with deeper digging.

 Of course, if you live on permafrost, you will never have a decent ground
:-)

 This is a real issue for cables brought to the house (cable TV,
telephone,
 etc etc) as those cables are grounded somewhere else on the other side,
and
 thus  there may be 1000's or even 1's Volts between the two
grounds,
 even (or  especially) for just a proximity strike. As mentioned by
someone
 else, all bets  are off anyway's for direct hits, not much will survive a
 direct hit.

 Well.. if you have a near hit on some long cable. you're lucky if the
 attached electronics survive. But it shouldn't kill everything in the
 house. My point was that, with proper ground connection, your house
 potential should increase to many 1000s of volt, even with a near hit.
 Again, i might miss there something.


 It's been a long time since I designed cable TV receivers, but the specs
 are here, and I think there are some explanations in there somewhere:

 _http://www.nordig.org/specifications.htm_
 (http://www.nordig.org/specifications.htm)

 Thanks, i'll have a look at those.

   Attila Kinali


___
time-nuts mailing list -- time-nuts@febo.com
To unsubscribe, go to
https://www.febo.com/cgi-bin/mailman/listinfo/time-nuts
and follow the instructions there.


___
time-nuts mailing list -- time-nuts@febo.com
To unsubscribe, go to https://www.febo.com/cgi-bin/mailman/listinfo/time-nuts
and follow the instructions there.


Re: [time-nuts] Thoughts on lightning protection measures....

2012-04-13 Thread Lee Mushel

Chuck,

You and Atilla must be right!   when the basement for my home was dug I 
pounded in four standard eight foot plated ground rods horizontally just a 
few inches above the concrete footing which means they're down nearly six 
feet.   I happen to respect a lot of the ideas of my maternal grandfather so 
I also have what might be called a classic lightning rod system with 
appropriate ground rods.   While I do not claim to have some of the 
suggested elements of a ground field I do have more than 20 additional 
grounding points that accompany my ham radio antennas.  And I learned about 
the wisdom of having home perimeter grounding too late to install that but 
all wiring in the house is metallic: EMT, greenfield or BX.   So I think I 
have some elements of that as well.  Anyway, while my neighbors, also living 
on the hill, have lost numerous TV sets, etc. I have never had a single loss 
to what I could plainly see was lightning.   Even though a tree less than 30 
feet from the house took a direct strike which killed the tree!  Whenever 
the power company appears for whatever reason they always check my ground. 
They haven't complained yet!


No, I'm no fool, when a storm is predicted or I hear the first faint thunder 
rumble all antennas and sensitive stuff power is disconnected.  I've seen 
pieces of homes disappear when Old Mother Nature uses that particularly 
destructive tool of hers!


Lee Mushel   K9WRU
- Original Message - 
From: Chuck Harris cfhar...@erols.com
To: Discussion of precise time and frequency measurement 
time-nuts@febo.com

Sent: Friday, April 13, 2012 7:14 AM
Subject: Re: [time-nuts] Thoughts on lightning protection measures






___
time-nuts mailing list -- time-nuts@febo.com
To unsubscribe, go to https://www.febo.com/cgi-bin/mailman/listinfo/time-nuts
and follow the instructions there.


Re: [time-nuts] Thoughts on lightning protection measures....

2012-04-13 Thread Chuck Harris

Hi Bob,

When I had my lightning protection survey done on my house,
there was a requirement that all of the lightning grounds
be tied to the power, telephone, cable, and water grounds
at a single point.  Before I did this, I lost modems, network
cards, fax machines, etc.. afterward, no problems.

I do lose the occasional phone surge protector in the network
interface block, but they seem to do their job, and protect
everything else.

-Chuck Harris (knocking on wood!)

Bob Camp wrote:

Hi

Yes indeed, very true.

Things like telephone lines and cable lines need to jump at the same time
as the house ground. The fact that they don't is what makes cordless phone
base stations, modems (remember them?) and cable boxes the main victims in
lightning hits.

Bob

-Original Message-
From: time-nuts-boun...@febo.com [mailto:time-nuts-boun...@febo.com] On
Behalf Of Chuck Harris
Sent: Friday, April 13, 2012 9:14 AM
To: Discussion of precise time and frequency measurement
Subject: Re: [time-nuts] Thoughts on lightning protection measures

As the power line worker strapped to the million volt wires he is
working on shows, what is important is that all the grounds in the
house stay at the same potential... not that they stay at some
perfect earth ground potential.

It really doesn't matter if a house ground jumps up many
thousands of volts for an instant during a lightning strike, as
long as everything electronic in the house, and everything
structural in the house jumps too.

-Chuck Harris


Attila Kinali wrote:

Moin,

On Thu, 12 Apr 2012 18:28:24 -0400 (EDT)
saidj...@aol.com wrote:


if I remember correctly, the issue is that the ground at the house is
not a real ground when the earth is frozen, as the resistance of frozen
earth goes up substantially over non-frozen earth. So it's like not

having

grounded the wires at all.


Yes, that's why in Switzerland you have to bury the grounding loop/wires
at least 1m deep (IIRC), in cold areas even 1.5m deep(again IIRC) to

ensure

that the earth never freezes.

I would have assumed that the building rules in the north have similar
requirements, just with deeper digging.

Of course, if you live on permafrost, you will never have a decent ground

:-)



This is a real issue for cables brought to the house (cable TV,

telephone,

etc etc) as those cables are grounded somewhere else on the other side,

and

thus  there may be 1000's or even 1's Volts between the two

grounds,

even (or  especially) for just a proximity strike. As mentioned by

someone

else, all bets  are off anyway's for direct hits, not much will survive a
direct hit.


Well.. if you have a near hit on some long cable. you're lucky if the
attached electronics survive. But it shouldn't kill everything in the
house. My point was that, with proper ground connection, your house
potential should increase to many 1000s of volt, even with a near hit.
Again, i might miss there something.



It's been a long time since I designed cable TV receivers, but the specs
are here, and I think there are some explanations in there somewhere:

_http://www.nordig.org/specifications.htm_
(http://www.nordig.org/specifications.htm)


Thanks, i'll have a look at those.

Attila Kinali



___
time-nuts mailing list -- time-nuts@febo.com
To unsubscribe, go to
https://www.febo.com/cgi-bin/mailman/listinfo/time-nuts
and follow the instructions there.


___
time-nuts mailing list -- time-nuts@febo.com
To unsubscribe, go to https://www.febo.com/cgi-bin/mailman/listinfo/time-nuts
and follow the instructions there.



___
time-nuts mailing list -- time-nuts@febo.com
To unsubscribe, go to https://www.febo.com/cgi-bin/mailman/listinfo/time-nuts
and follow the instructions there.


Re: [time-nuts] Thoughts on lightning protection measures....

2012-04-13 Thread Bob Camp
Hi

The process of bonding everything together is a lot easier if the house is set 
up with all the stuff coming in at one point. If phone, water, power, and 
cable all come in on their own corner - not quite so easy.

Bob

On Apr 13, 2012, at 5:34 PM, Chuck Harris wrote:

 Hi Bob,
 
 When I had my lightning protection survey done on my house,
 there was a requirement that all of the lightning grounds
 be tied to the power, telephone, cable, and water grounds
 at a single point.  Before I did this, I lost modems, network
 cards, fax machines, etc.. afterward, no problems.
 
 I do lose the occasional phone surge protector in the network
 interface block, but they seem to do their job, and protect
 everything else.
 
 -Chuck Harris (knocking on wood!)
 
 Bob Camp wrote:
 Hi
 
 Yes indeed, very true.
 
 Things like telephone lines and cable lines need to jump at the same time
 as the house ground. The fact that they don't is what makes cordless phone
 base stations, modems (remember them?) and cable boxes the main victims in
 lightning hits.
 
 Bob
 
 -Original Message-
 From: time-nuts-boun...@febo.com [mailto:time-nuts-boun...@febo.com] On
 Behalf Of Chuck Harris
 Sent: Friday, April 13, 2012 9:14 AM
 To: Discussion of precise time and frequency measurement
 Subject: Re: [time-nuts] Thoughts on lightning protection measures
 
 As the power line worker strapped to the million volt wires he is
 working on shows, what is important is that all the grounds in the
 house stay at the same potential... not that they stay at some
 perfect earth ground potential.
 
 It really doesn't matter if a house ground jumps up many
 thousands of volts for an instant during a lightning strike, as
 long as everything electronic in the house, and everything
 structural in the house jumps too.
 
 -Chuck Harris
 
 
 Attila Kinali wrote:
 Moin,
 
 On Thu, 12 Apr 2012 18:28:24 -0400 (EDT)
 saidj...@aol.com wrote:
 
 if I remember correctly, the issue is that the ground at the house is
 not a real ground when the earth is frozen, as the resistance of frozen
 earth goes up substantially over non-frozen earth. So it's like not
 having
 grounded the wires at all.
 
 Yes, that's why in Switzerland you have to bury the grounding loop/wires
 at least 1m deep (IIRC), in cold areas even 1.5m deep(again IIRC) to
 ensure
 that the earth never freezes.
 
 I would have assumed that the building rules in the north have similar
 requirements, just with deeper digging.
 
 Of course, if you live on permafrost, you will never have a decent ground
 :-)
 
 This is a real issue for cables brought to the house (cable TV,
 telephone,
 etc etc) as those cables are grounded somewhere else on the other side,
 and
 thus  there may be 1000's or even 1's Volts between the two
 grounds,
 even (or  especially) for just a proximity strike. As mentioned by
 someone
 else, all bets  are off anyway's for direct hits, not much will survive a
 direct hit.
 
 Well.. if you have a near hit on some long cable. you're lucky if the
 attached electronics survive. But it shouldn't kill everything in the
 house. My point was that, with proper ground connection, your house
 potential should increase to many 1000s of volt, even with a near hit.
 Again, i might miss there something.
 
 
 It's been a long time since I designed cable TV receivers, but the specs
 are here, and I think there are some explanations in there somewhere:
 
 _http://www.nordig.org/specifications.htm_
 (http://www.nordig.org/specifications.htm)
 
 Thanks, i'll have a look at those.
 
 Attila Kinali
 
 
 ___
 time-nuts mailing list -- time-nuts@febo.com
 To unsubscribe, go to
 https://www.febo.com/cgi-bin/mailman/listinfo/time-nuts
 and follow the instructions there.
 
 
 ___
 time-nuts mailing list -- time-nuts@febo.com
 To unsubscribe, go to https://www.febo.com/cgi-bin/mailman/listinfo/time-nuts
 and follow the instructions there.
 
 
 ___
 time-nuts mailing list -- time-nuts@febo.com
 To unsubscribe, go to https://www.febo.com/cgi-bin/mailman/listinfo/time-nuts
 and follow the instructions there.


___
time-nuts mailing list -- time-nuts@febo.com
To unsubscribe, go to https://www.febo.com/cgi-bin/mailman/listinfo/time-nuts
and follow the instructions there.


[time-nuts] Thoughts on lightning protection measures....

2012-04-12 Thread Michael Baker

Time-nutters--

Around here (N. Central Flori-DUH) it is not uncommon for
near-by lightning strikes to damage underground cables and
wiring.   This is why buried wiring to things like driveway
gate-openers are often placed in conduit rather than done
with direct-burial wiring so that if lightning damages the
wiring a new cable can be pulled through the conduit without
having to re-dig the burial trench.

Some years ago I had occasion to hold some long discussions
with Martin Uman, one of the worlds most distinguished and
eminent lightning researchers.  He commented that even with
the most extraordinary and costly efforts to install protection
measures, that-- sooner or later-- there was a good chance that
lightning would find a way to damage things.

His lightning research laboratory was located here in
N.Central Florida because it is in the heart of the most
dense strike area in N. America.

Mike Baker


___
time-nuts mailing list -- time-nuts@febo.com
To unsubscribe, go to https://www.febo.com/cgi-bin/mailman/listinfo/time-nuts
and follow the instructions there.


Re: [time-nuts] Thoughts on lightning protection measures....

2012-04-12 Thread Jim Lux

On 4/12/12 6:22 AM, Michael Baker wrote:

Time-nutters--

Around here (N. Central Flori-DUH) it is not uncommon for
near-by lightning strikes to damage underground cables and
wiring. This is why buried wiring to things like driveway
gate-openers are often placed in conduit rather than done
with direct-burial wiring so that if lightning damages the
wiring a new cable can be pulled through the conduit without
having to re-dig the burial trench.

Some years ago I had occasion to hold some long discussions
with Martin Uman, one of the worlds most distinguished and
eminent lightning researchers. He commented that even with
the most extraordinary and costly efforts to install protection
measures, that-- sooner or later-- there was a good chance that
lightning would find a way to damage things.




Dr. Uman (and his colleague Dr. Rakov) probably know about lightning and 
effects than any other humans alive.   He's making an excellent point: 
at some point, the cost to replace the gear (or the cost of being off 
the air) is smaller than the cost of the protection scheme.


Sometimes, you're better off having a sacrificial element, and a spare 
in the closet for speedy repair.




His lightning research laboratory was located here in
N.Central Florida because it is in the heart of the most
dense strike area in N. America.




___
time-nuts mailing list -- time-nuts@febo.com
To unsubscribe, go to https://www.febo.com/cgi-bin/mailman/listinfo/time-nuts
and follow the instructions there.


Re: [time-nuts] Thoughts on lightning protection measures....

2012-04-12 Thread EWKehren
True if you do not include the cost of the burned down house which is a  
possibility.
Bert Kehren
 
 
In a message dated 4/12/2012 9:59:08 A.M. Eastern Daylight Time,  
jim...@earthlink.net writes:

On  4/12/12 6:22 AM, Michael Baker wrote:
 Time-nutters--

  Around here (N. Central Flori-DUH) it is not uncommon for
 near-by  lightning strikes to damage underground cables and
 wiring. This is why  buried wiring to things like driveway
 gate-openers are often placed in  conduit rather than done
 with direct-burial wiring so that if  lightning damages the
 wiring a new cable can be pulled through the  conduit without
 having to re-dig the burial trench.

  Some years ago I had occasion to hold some long discussions
 with  Martin Uman, one of the worlds most distinguished and
 eminent  lightning researchers. He commented that even with
 the most  extraordinary and costly efforts to install protection
 measures,  that-- sooner or later-- there was a good chance that
 lightning would  find a way to damage things.



Dr. Uman (and his colleague  Dr. Rakov) probably know about lightning and 
effects than any other humans  alive.   He's making an excellent point: 
at some point, the cost  to replace the gear (or the cost of being off 
the air) is smaller than  the cost of the protection scheme.

Sometimes, you're better off having  a sacrificial element, and a spare 
in the closet for speedy  repair.


 His lightning research laboratory was located here  in
 N.Central Florida because it is in the heart of the most
  dense strike area in N.  America.



___
time-nuts  mailing list -- time-nuts@febo.com
To unsubscribe, go to  
https://www.febo.com/cgi-bin/mailman/listinfo/time-nuts
and follow the  instructions there.

___
time-nuts mailing list -- time-nuts@febo.com
To unsubscribe, go to https://www.febo.com/cgi-bin/mailman/listinfo/time-nuts
and follow the instructions there.


Re: [time-nuts] Thoughts on lightning protection measures....

2012-04-12 Thread Azelio Boriani
I have 2 TBolts but now I'm thinking to buy others to save them from the
sacrifice...

On Thu, Apr 12, 2012 at 3:58 PM, Jim Lux jim...@earthlink.net wrote:

 On 4/12/12 6:22 AM, Michael Baker wrote:

 Time-nutters--

 Around here (N. Central Flori-DUH) it is not uncommon for
 near-by lightning strikes to damage underground cables and
 wiring. This is why buried wiring to things like driveway
 gate-openers are often placed in conduit rather than done
 with direct-burial wiring so that if lightning damages the
 wiring a new cable can be pulled through the conduit without
 having to re-dig the burial trench.

 Some years ago I had occasion to hold some long discussions
 with Martin Uman, one of the worlds most distinguished and
 eminent lightning researchers. He commented that even with
 the most extraordinary and costly efforts to install protection
 measures, that-- sooner or later-- there was a good chance that
 lightning would find a way to damage things.



 Dr. Uman (and his colleague Dr. Rakov) probably know about lightning and
 effects than any other humans alive.   He's making an excellent point: at
 some point, the cost to replace the gear (or the cost of being off the
 air) is smaller than the cost of the protection scheme.

 Sometimes, you're better off having a sacrificial element, and a spare in
 the closet for speedy repair.


  His lightning research laboratory was located here in
 N.Central Florida because it is in the heart of the most
 dense strike area in N. America.




 ___
 time-nuts mailing list -- time-nuts@febo.com
 To unsubscribe, go to
 https://www.febo.com/cgi-bin/mailman/listinfo/time-nuts
 and follow the instructions there.

___
time-nuts mailing list -- time-nuts@febo.com
To unsubscribe, go to https://www.febo.com/cgi-bin/mailman/listinfo/time-nuts
and follow the instructions there.


Re: [time-nuts] Thoughts on lightning protection measures....

2012-04-12 Thread Bob Camp
Hi

Is your house hit multiple times per year now? If so, I'd suggest that's the
issue that needs to be solved. If not, then mount the antenna lower than the
peak of the house and move on.

Bob

-Original Message-
From: time-nuts-boun...@febo.com [mailto:time-nuts-boun...@febo.com] On
Behalf Of Azelio Boriani
Sent: Thursday, April 12, 2012 10:04 AM
To: Discussion of precise time and frequency measurement
Subject: Re: [time-nuts] Thoughts on lightning protection measures

I have 2 TBolts but now I'm thinking to buy others to save them from the
sacrifice...

On Thu, Apr 12, 2012 at 3:58 PM, Jim Lux jim...@earthlink.net wrote:

 On 4/12/12 6:22 AM, Michael Baker wrote:

 Time-nutters--

 Around here (N. Central Flori-DUH) it is not uncommon for
 near-by lightning strikes to damage underground cables and
 wiring. This is why buried wiring to things like driveway
 gate-openers are often placed in conduit rather than done
 with direct-burial wiring so that if lightning damages the
 wiring a new cable can be pulled through the conduit without
 having to re-dig the burial trench.

 Some years ago I had occasion to hold some long discussions
 with Martin Uman, one of the worlds most distinguished and
 eminent lightning researchers. He commented that even with
 the most extraordinary and costly efforts to install protection
 measures, that-- sooner or later-- there was a good chance that
 lightning would find a way to damage things.



 Dr. Uman (and his colleague Dr. Rakov) probably know about lightning and
 effects than any other humans alive.   He's making an excellent point: at
 some point, the cost to replace the gear (or the cost of being off the
 air) is smaller than the cost of the protection scheme.

 Sometimes, you're better off having a sacrificial element, and a spare in
 the closet for speedy repair.


  His lightning research laboratory was located here in
 N.Central Florida because it is in the heart of the most
 dense strike area in N. America.




 ___
 time-nuts mailing list -- time-nuts@febo.com
 To unsubscribe, go to
 https://www.febo.com/cgi-bin/mailman/listinfo/time-nuts
 and follow the instructions there.

___
time-nuts mailing list -- time-nuts@febo.com
To unsubscribe, go to
https://www.febo.com/cgi-bin/mailman/listinfo/time-nuts
and follow the instructions there.


___
time-nuts mailing list -- time-nuts@febo.com
To unsubscribe, go to https://www.febo.com/cgi-bin/mailman/listinfo/time-nuts
and follow the instructions there.


Re: [time-nuts] Thoughts on lightning protection measures....

2012-04-12 Thread MailLists

Only if it's not part of the sacrificial ritual...

On the more serious part, while the lightning processes, and effects are 
scientifically researched for ages, an efficient lighting protection 
still borders black magic.



On 4/12/2012 5:01 PM, ewkeh...@aol.com wrote:

True if you do not include the cost of the burned down house which is a
possibility.
Bert Kehren


In a message dated 4/12/2012 9:59:08 A.M. Eastern Daylight Time,
jim...@earthlink.net writes:

On  4/12/12 6:22 AM, Michael Baker wrote:

Time-nutters--

  Around here (N. Central Flori-DUH) it is not uncommon for
near-by  lightning strikes to damage underground cables and
wiring. This is why  buried wiring to things like driveway
gate-openers are often placed in  conduit rather than done
with direct-burial wiring so that if  lightning damages the
wiring a new cable can be pulled through the  conduit without
having to re-dig the burial trench.

  Some years ago I had occasion to hold some long discussions
with  Martin Uman, one of the worlds most distinguished and
eminent  lightning researchers. He commented that even with
the most  extraordinary and costly efforts to install protection
measures,  that-- sooner or later-- there was a good chance that
lightning would  find a way to damage things.




Dr. Uman (and his colleague  Dr. Rakov) probably know about lightning and
effects than any other humans  alive.   He's making an excellent point:
at some point, the cost  to replace the gear (or the cost of being off
the air) is smaller than  the cost of the protection scheme.

Sometimes, you're better off having  a sacrificial element, and a spare
in the closet for speedy  repair.



His lightning research laboratory was located here  in
N.Central Florida because it is in the heart of the most
  dense strike area in N.  America.




___
time-nuts  mailing list -- time-nuts@febo.com
To unsubscribe, go to
https://www.febo.com/cgi-bin/mailman/listinfo/time-nuts
and follow the  instructions there.

___
time-nuts mailing list -- time-nuts@febo.com
To unsubscribe, go to https://www.febo.com/cgi-bin/mailman/listinfo/time-nuts
and follow the instructions there.


___
time-nuts mailing list -- time-nuts@febo.com
To unsubscribe, go to https://www.febo.com/cgi-bin/mailman/listinfo/time-nuts
and follow the instructions there.


Re: [time-nuts] Thoughts on lightning protection measures....

2012-04-12 Thread MailLists
A very efficient solution would be to get the signal/power conducting 
cables out of the lightning path - that means a GPS receiver near the 
antenna, with a local power supply (photo cell panels / buffer 
accumulator) and signal transmission over optical fiber. Quite feasible, 
as a GPS Rx has low power requirements.
If the delay from receiver to the disciplined oscillator is critical, or 
too high, a compensation scheme comes to mind - 2 identical optical 
paths in a loop, with the sent pps signal phase adjusted so that the 
received GPS pps is centered between the sent and the looped one.


Regarding the TBs, even if they are the only ones directly connected to 
the antenna, the cable is already punching through the house Faraday 
cage, and chances are quite high that the lightning discharge won't stop 
at them.



On 4/12/2012 5:03 PM, Azelio Boriani wrote:

I have 2 TBolts but now I'm thinking to buy others to save them from the
sacrifice...

On Thu, Apr 12, 2012 at 3:58 PM, Jim Luxjim...@earthlink.net  wrote:


On 4/12/12 6:22 AM, Michael Baker wrote:


Time-nutters--

Around here (N. Central Flori-DUH) it is not uncommon for
near-by lightning strikes to damage underground cables and
wiring. This is why buried wiring to things like driveway
gate-openers are often placed in conduit rather than done
with direct-burial wiring so that if lightning damages the
wiring a new cable can be pulled through the conduit without
having to re-dig the burial trench.

Some years ago I had occasion to hold some long discussions
with Martin Uman, one of the worlds most distinguished and
eminent lightning researchers. He commented that even with
the most extraordinary and costly efforts to install protection
measures, that-- sooner or later-- there was a good chance that
lightning would find a way to damage things.




Dr. Uman (and his colleague Dr. Rakov) probably know about lightning and
effects than any other humans alive.   He's making an excellent point: at
some point, the cost to replace the gear (or the cost of being off the
air) is smaller than the cost of the protection scheme.

Sometimes, you're better off having a sacrificial element, and a spare in
the closet for speedy repair.


  His lightning research laboratory was located here in

N.Central Florida because it is in the heart of the most
dense strike area in N. America.





___
time-nuts mailing list -- time-nuts@febo.com
To unsubscribe, go to
https://www.febo.com/cgi-bin/mailman/listinfo/time-nuts
and follow the instructions there.


___
time-nuts mailing list -- time-nuts@febo.com
To unsubscribe, go to https://www.febo.com/cgi-bin/mailman/listinfo/time-nuts
and follow the instructions there.


___
time-nuts mailing list -- time-nuts@febo.com
To unsubscribe, go to https://www.febo.com/cgi-bin/mailman/listinfo/time-nuts
and follow the instructions there.


Re: [time-nuts] Thoughts on lightning protection measures....

2012-04-12 Thread Attila Kinali
On Thu, 12 Apr 2012 17:39:57 +0300
MailLists li...@medesign.ro wrote:

 Regarding the TBs, even if they are the only ones directly connected to 
 the antenna, the cable is already punching through the house Faraday 
 cage, and chances are quite high that the lightning discharge won't stop 
 at them.

A house isnt a faraday cage. Not by far. Unless you live in a box made out
of solid 5mm steal plates.

If a lightning hits your house directly and is going down the lightning
rod down into earth there is a good chance that the electric and magnetic
fields you have in the house will fry sensitive electronic equipment


Attila Kinali
-- 
The trouble with you, Shev, is you don't say anything until you've saved
up a whole truckload of damned heavy brick arguments and then you dump
them all out and never look at the bleeding body mangled beneath the heap
-- Tirin, The Dispossessed, U. Le Guin

___
time-nuts mailing list -- time-nuts@febo.com
To unsubscribe, go to https://www.febo.com/cgi-bin/mailman/listinfo/time-nuts
and follow the instructions there.


Re: [time-nuts] Thoughts on lightning protection measures....

2012-04-12 Thread MailLists
You're right, but it's highly depending on the used construction 
materials... The building I live in, is quite like a Faraday cage - 
reinforced concrete. Even higher frequency radio signals have a tough 
time entering, mostly through the windows.
What I wanted to underline is that, even if the house would be build 
like a Faraday cage, any conductor from the outside represents a 
potential dangerous ingress path.


Of course, the generated fields would affect any sensitive equipment, 
but with the low impedance path of an antenna cable, even the less 
sensitive ones could suffer catastrophic failure. Not to neglect are all 
the other conductors entering from the outside - power lines, metallic 
pipes, etc.
Full protection is quite difficult, almost impossible, to obtain, but 
an antenna cable is the preferred path.



On 4/12/2012 6:02 PM, Attila Kinali wrote:

On Thu, 12 Apr 2012 17:39:57 +0300
MailListsli...@medesign.ro  wrote:


Regarding the TBs, even if they are the only ones directly connected to
the antenna, the cable is already punching through the house Faraday
cage, and chances are quite high that the lightning discharge won't stop
at them.


A house isnt a faraday cage. Not by far. Unless you live in a box made out
of solid 5mm steal plates.

If a lightning hits your house directly and is going down the lightning
rod down into earth there is a good chance that the electric and magnetic
fields you have in the house will fry sensitive electronic equipment


Attila Kinali


___
time-nuts mailing list -- time-nuts@febo.com
To unsubscribe, go to https://www.febo.com/cgi-bin/mailman/listinfo/time-nuts
and follow the instructions there.


Re: [time-nuts] Thoughts on lightning protection measures....

2012-04-12 Thread Said Jackson
One interesting fact: frozen ground is a bad conductor.

The ground potential around your house may go up many 1000s of volts even with 
just a proximity strike, while the power feed stays down, blowing up anything 
connected to ground. Thus the special Nordig surge protection requirements 
for TV receivers in northern European countries..





On Apr 12, 2012, at 6:58, Jim Lux jim...@earthlink.net wrote:

 On 4/12/12 6:22 AM, Michael Baker wrote:
 Time-nutters--
 
 Around here (N. Central Flori-DUH) it is not uncommon for
 near-by lightning strikes to damage underground cables and
 wiring. This is why buried wiring to things like driveway
 gate-openers are often placed in conduit rather than done
 with direct-burial wiring so that if lightning damages the
 wiring a new cable can be pulled through the conduit without
 having to re-dig the burial trench.
 
 Some years ago I had occasion to hold some long discussions
 with Martin Uman, one of the worlds most distinguished and
 eminent lightning researchers. He commented that even with
 the most extraordinary and costly efforts to install protection
 measures, that-- sooner or later-- there was a good chance that
 lightning would find a way to damage things.
 
 
 
 Dr. Uman (and his colleague Dr. Rakov) probably know about lightning and 
 effects than any other humans alive.   He's making an excellent point: at 
 some point, the cost to replace the gear (or the cost of being off the air) 
 is smaller than the cost of the protection scheme.
 
 Sometimes, you're better off having a sacrificial element, and a spare in the 
 closet for speedy repair.
 
 
 His lightning research laboratory was located here in
 N.Central Florida because it is in the heart of the most
 dense strike area in N. America.
 
 
 
 ___
 time-nuts mailing list -- time-nuts@febo.com
 To unsubscribe, go to https://www.febo.com/cgi-bin/mailman/listinfo/time-nuts
 and follow the instructions there.

___
time-nuts mailing list -- time-nuts@febo.com
To unsubscribe, go to https://www.febo.com/cgi-bin/mailman/listinfo/time-nuts
and follow the instructions there.


Re: [time-nuts] Thoughts on lightning protection measures....

2012-04-12 Thread Bob Camp
Hi

The lightning hit is both a great big voltage and a wallop of current. The
voltage is the thing many people get worried about. Almost all of the damage
I've had has come from current induced into near by conductors and similar
magnetic field issues.

That said, the voltage spike has likely jumped several hundred feet to get
into the vicinity of your house. Hopping from this to that while trying to
run through the house is trivial compared to the distance it's already
traveled. 

There are indeed ways to take care of this stuff. Some systems are set up
for a how many strikes per hour type of operation. They do indeed run
properly in a high hit rate environment. You do *not* want to foot the cost
for an installation like that. Having the (insured) house burn down is much
cheaper 

Bob

-Original Message-
From: time-nuts-boun...@febo.com [mailto:time-nuts-boun...@febo.com] On
Behalf Of MailLists
Sent: Thursday, April 12, 2012 11:22 AM
To: Discussion of precise time and frequency measurement
Subject: Re: [time-nuts] Thoughts on lightning protection measures

You're right, but it's highly depending on the used construction 
materials... The building I live in, is quite like a Faraday cage - 
reinforced concrete. Even higher frequency radio signals have a tough 
time entering, mostly through the windows.
What I wanted to underline is that, even if the house would be build 
like a Faraday cage, any conductor from the outside represents a 
potential dangerous ingress path.

Of course, the generated fields would affect any sensitive equipment, 
but with the low impedance path of an antenna cable, even the less 
sensitive ones could suffer catastrophic failure. Not to neglect are all 
the other conductors entering from the outside - power lines, metallic 
pipes, etc.
Full protection is quite difficult, almost impossible, to obtain, but 
an antenna cable is the preferred path.


On 4/12/2012 6:02 PM, Attila Kinali wrote:
 On Thu, 12 Apr 2012 17:39:57 +0300
 MailListsli...@medesign.ro  wrote:

 Regarding the TBs, even if they are the only ones directly connected to
 the antenna, the cable is already punching through the house Faraday
 cage, and chances are quite high that the lightning discharge won't stop
 at them.

 A house isnt a faraday cage. Not by far. Unless you live in a box made out
 of solid 5mm steal plates.

 If a lightning hits your house directly and is going down the lightning
 rod down into earth there is a good chance that the electric and magnetic
 fields you have in the house will fry sensitive electronic equipment


   Attila Kinali

___
time-nuts mailing list -- time-nuts@febo.com
To unsubscribe, go to
https://www.febo.com/cgi-bin/mailman/listinfo/time-nuts
and follow the instructions there.


___
time-nuts mailing list -- time-nuts@febo.com
To unsubscribe, go to https://www.febo.com/cgi-bin/mailman/listinfo/time-nuts
and follow the instructions there.


Re: [time-nuts] Thoughts on lightning protection measures....

2012-04-12 Thread Attila Kinali
On Thu, 12 Apr 2012 09:20:37 -0700
Said Jackson saidj...@aol.com wrote:

 One interesting fact: frozen ground is a bad conductor.
 
 The ground potential around your house may go up many 1000s of volts
 even with just a proximity strike, while the power feed stays down,
 blowing up anything connected to ground. Thus the special Nordig surge
 protection requirements for TV receivers in northern European countries..

Hmm? That sounds interesting. In switzerland, and AFAIK in most european
countries, power feeds have to be grounded at the entry of the house
(ie the neutral conductor is grounded). This should protect the electrical
equipment from such ground jumps as you discribe. Or do i miss something?

Attila Kinali

-- 
The trouble with you, Shev, is you don't say anything until you've saved
up a whole truckload of damned heavy brick arguments and then you dump
them all out and never look at the bleeding body mangled beneath the heap
-- Tirin, The Dispossessed, U. Le Guin

___
time-nuts mailing list -- time-nuts@febo.com
To unsubscribe, go to https://www.febo.com/cgi-bin/mailman/listinfo/time-nuts
and follow the instructions there.


Re: [time-nuts] Thoughts on lightning protection measures....

2012-04-12 Thread Antonio Amandio Sanches de Magalhaes

Fortunately, it seems that lightning is not as frequent in high
northern and southern latitudes as is in tropical regions.

I was told about a story of a group of Swedish scientists
involved in thunderstorm studies, having built a little lab
in the village with the best reputation of high probability
of lightning, receiving after several years without events
a delegation of the residents very grateful because after
the lab installation there was no more lightning.

Best regards,
Antonio
CT1TE

Em 2012-04-12 17:20, Said Jackson escreveu:

One interesting fact: frozen ground is a bad conductor.

The ground potential around your house may go up many 1000s of volts
even with just a proximity strike, while the power feed stays down,
blowing up anything connected to ground. Thus the special Nordig
surge protection requirements for TV receivers in northern European
countries..





On Apr 12, 2012, at 6:58, Jim Lux jim...@earthlink.net wrote:


On 4/12/12 6:22 AM, Michael Baker wrote:

Time-nutters--

Around here (N. Central Flori-DUH) it is not uncommon for
near-by lightning strikes to damage underground cables and
wiring. This is why buried wiring to things like driveway
gate-openers are often placed in conduit rather than done
with direct-burial wiring so that if lightning damages the
wiring a new cable can be pulled through the conduit without
having to re-dig the burial trench.

Some years ago I had occasion to hold some long discussions
with Martin Uman, one of the worlds most distinguished and
eminent lightning researchers. He commented that even with
the most extraordinary and costly efforts to install protection
measures, that-- sooner or later-- there was a good chance that
lightning would find a way to damage things.




Dr. Uman (and his colleague Dr. Rakov) probably know about lightning 
and effects than any other humans alive.   He's making an excellent 
point: at some point, the cost to replace the gear (or the cost of 
being off the air) is smaller than the cost of the protection 
scheme.


Sometimes, you're better off having a sacrificial element, and a 
spare in the closet for speedy repair.




His lightning research laboratory was located here in
N.Central Florida because it is in the heart of the most
dense strike area in N. America.




___
time-nuts mailing list -- time-nuts@febo.com
To unsubscribe, go to 
https://www.febo.com/cgi-bin/mailman/listinfo/time-nuts

and follow the instructions there.


___
time-nuts mailing list -- time-nuts@febo.com
To unsubscribe, go to 
https://www.febo.com/cgi-bin/mailman/listinfo/time-nuts

and follow the instructions there.



___
time-nuts mailing list -- time-nuts@febo.com
To unsubscribe, go to https://www.febo.com/cgi-bin/mailman/listinfo/time-nuts
and follow the instructions there.


Re: [time-nuts] Thoughts on lightning protection measures....

2012-04-12 Thread Chris Albertson
On Thu, Apr 12, 2012 at 7:22 AM, Bob Camp li...@rtty.us wrote:
 Hi

 Is your house hit multiple times per year now? If so, I'd suggest that's the
 issue that needs to be solved. If not, then mount the antenna lower than the
 peak of the house and move on.

Did you not read the first post in this thread?   He said it is common
to have buried cables dangaged by near by strikes.   I assume under
ground is not the tallest thing around

The point about lightening is NOT if the object is directly struct.
There is nothing you can do in that case, a  ightening arrestor is
kind of a joke to a bolt that just jumped across a miles long air gap.

What destroyed the underground cable is the EMP pulse from a strike
that was 100 feet away.  EMP induced a current and the current was
greater then the current carrying ability of the conductor.


Chris Albertson
Redondo Beach, California

___
time-nuts mailing list -- time-nuts@febo.com
To unsubscribe, go to https://www.febo.com/cgi-bin/mailman/listinfo/time-nuts
and follow the instructions there.


Re: [time-nuts] Thoughts on lightning protection measures....

2012-04-12 Thread SAIDJACK
Hi Attila,
 
if I remember correctly, the issue is that the ground at the house is  
not a real ground when the earth is frozen, as the resistance of frozen  
earth goes up substantially over non-frozen earth. So it's like not having  
grounded the wires at all.
 
This is a real issue for cables brought to the house (cable TV, telephone,  
etc etc) as those cables are grounded somewhere else on the other side, and 
thus  there may be 1000's or even 1's Volts between the two grounds, 
even (or  especially) for just a proximity strike. As mentioned by someone 
else, all bets  are off anyway's for direct hits, not much will survive a 
direct hit.
 
It's been a long time since I designed cable TV receivers, but the specs  
are here, and I think there are some explanations in there somewhere:
 
_http://www.nordig.org/specifications.htm_ 
(http://www.nordig.org/specifications.htm) 
 
bye,
Said
 
 
 
 
In a message dated 4/12/2012 09:54:40 Pacific Daylight Time,  
att...@kinali.ch writes:

Hmm?  That sounds interesting. In switzerland, and AFAIK in most  european
countries, power feeds have to be grounded at the entry of the  house
(ie the neutral conductor is grounded). This should protect the  electrical
equipment from such ground jumps as you discribe. Or do i miss  something?

Attila  Kinali


___
time-nuts mailing list -- time-nuts@febo.com
To unsubscribe, go to https://www.febo.com/cgi-bin/mailman/listinfo/time-nuts
and follow the instructions there.


Re: [time-nuts] Thoughts on lightning protection measures....

2012-04-12 Thread bg
Said,

The ground is a decent thermal isolator. And will in nordic countries not
often go deeper than about 1 meter. You need to build your houses
foundation deep enough to stand on non frozen ground. Otherwise your
house will move to much with the seasons and likely break. It is not that
hard to get your ground pole deep enough to avoid freezing problems.

-- 

   Björn

 Hi Attila,

 if I remember correctly, the issue is that the ground at the house is
 not a real ground when the earth is frozen, as the resistance of frozen
 earth goes up substantially over non-frozen earth. So it's like not having
 grounded the wires at all.

 This is a real issue for cables brought to the house (cable TV, telephone,
 etc etc) as those cables are grounded somewhere else on the other side,
 and
 thus  there may be 1000's or even 1's Volts between the two grounds,
 even (or  especially) for just a proximity strike. As mentioned by someone
 else, all bets  are off anyway's for direct hits, not much will survive a
 direct hit.

 It's been a long time since I designed cable TV receivers, but the specs
 are here, and I think there are some explanations in there somewhere:

 _http://www.nordig.org/specifications.htm_
 (http://www.nordig.org/specifications.htm)

 bye,
 Said




 In a message dated 4/12/2012 09:54:40 Pacific Daylight Time,
 att...@kinali.ch writes:

 Hmm?  That sounds interesting. In switzerland, and AFAIK in most  european
 countries, power feeds have to be grounded at the entry of the  house
 (ie the neutral conductor is grounded). This should protect the
 electrical
 equipment from such ground jumps as you discribe. Or do i miss  something?

 Attila  Kinali


 ___
 time-nuts mailing list -- time-nuts@febo.com
 To unsubscribe, go to
 https://www.febo.com/cgi-bin/mailman/listinfo/time-nuts
 and follow the instructions there.




___
time-nuts mailing list -- time-nuts@febo.com
To unsubscribe, go to https://www.febo.com/cgi-bin/mailman/listinfo/time-nuts
and follow the instructions there.


Re: [time-nuts] Thoughts on lightning protection measures....

2012-04-12 Thread SAIDJACK
Hi Bjoern,
 
Possibly, I am just reciting what I read in the Nordig requirements a  
looong time ago. Maybe they are worried about far north permafrost scenarios  
that go deeper? The requirements for receiver RF input surge protection were  
much higher than the usual US requirements..
 
bye,
Said
 
 
In a message dated 4/12/2012 15:38:55 Pacific Daylight Time,  
b...@lysator.liu.se writes:

Said,

The ground is a decent thermal isolator. And will in  nordic countries not
often go deeper than about 1 meter. You need to build  your houses
foundation deep enough to stand on non frozen ground.  Otherwise your
house will move to much with the seasons and likely break.  It is not that
hard to get your ground pole deep enough to avoid freezing  problems.

-- 

Björn