2023-02-27 Thread Joan Leedy
Make sure the foam is listed with the application equipment. The new synthetic fluorine free foams (SFFF) as they are called in NFPA 11 typically require a higher expansion rate than AFFF. So you need to make sure the application device has sufficient air aspiration and pressure. Joan Leed Tech

RE: Contractor's Material and Test Cert from NFPA 11

2018-04-01 Thread Joan Leedy
for bringing this to the attention of the NFPA 11 committee. Joan Leedy Dyne Fire Protection Labs 2357 Ventura Drive, Suite 108 Woodbury, MN 55125 800-632-2304 651-917-0644 www.dyneusa.com From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On Behalf Of Jerry Van Kolken

RE: Shelf life of AR-AFFF foam concentrate

2017-01-04 Thread Joan Leedy
NFPA 11 requires foam concentrate be tested annually. I work for Dyne Technologies and we provide field foam testing services. If you would like more information, contact Dyne at the number below. Joan Leedy Dyne Technologies, LLC 2357 Ventura Drive, Suite 108 Woodbury, MN 55125 800-632-2304